Search found 6 matches
- Tue Jan 10, 2023 10:27 pm
- Forum: Opentherm Gateway Forum
- Topic: No thermostat connected, but it is
- Replies: 5
- Views: 2613
Re: No thermostat connected, but it is
It seems that my measuring action has fixed the issue. Could be a loose soldering connection I guess, because after I tested with the multimeter, all of a sudden the diagnostics test (4) starts working. I guess tomorrow I will resolder R6 just to be sure and then reconnect the boiler and thermostat....
- Tue Jan 10, 2023 10:09 pm
- Forum: Opentherm Gateway Forum
- Topic: No thermostat connected, but it is
- Replies: 5
- Views: 2613
Re: No thermostat connected, but it is
I just got around to testing your conclusion. Unfortunately, R6 seems to be doing just fine. Connected to GND on one end (testing no resistance between the same end of R4, also tested connection to D1 and D2 successfully. Also pin17 of the PIC connects to the other end of R6. Testing the resistance ...
- Fri Jan 06, 2023 11:47 am
- Forum: Opentherm Gateway Forum
- Topic: No thermostat connected, but it is
- Replies: 5
- Views: 2613
Re: No thermostat connected, but it is
By keeps reporting it, I mean that I can't get the OTGW to detect the thermostat. So power cycling, resetting, reflashing firmware, nothing works. The requested outputs from the diagnostics firmware: Opentherm gateway diagnostics - Version 1.3 1. LED test 2. Bit timing thermostat 3. Bit timing boile...
- Thu Jan 05, 2023 6:16 pm
- Forum: Opentherm Gateway Forum
- Topic: No thermostat connected, but it is
- Replies: 5
- Views: 2613
No thermostat connected, but it is
Recently the transformer of my OTGW gave up. I've replaced it and everything seems to be working (boiler side), but whatever I'm trying, otmonitor keeps reporting Thermostat not connected . Also the diagnostics firmware does not register anything from the thermostat. I'm sure that the thermostat its...
- Wed May 07, 2014 7:10 pm
- Forum: Opentherm Gateway Forum
- Topic: Opentherm Gateway 4.0 alpha/beta testers wanted
- Replies: 285
- Views: 226108
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
For now, "ignore multiple mid-bit transitions" seems to have solved the connection issues. I don't understand why connecting the OTGW USB connector causes error 01 in gateway mode? Apparently, when running in gateway mode while nothing is connected, everything works fine... I guess I just...
- Mon May 05, 2014 12:23 pm
- Forum: Opentherm Gateway Forum
- Topic: Opentherm Gateway 4.0 alpha/beta testers wanted
- Replies: 285
- Views: 226108
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
I have the OTGW between my Honeywell Wireless Modulation thermostat and Bosch HRC35 Top boiler. As long as I don't have the USB connection connected there are no issues (but what's the point of having an OTWG without being able to read any values, right? ;- ) ). Whenever I connect it to my RasPi run...