Search found 4 matches
- Mon Nov 09, 2015 1:17 pm
- Forum: Opentherm Gateway Forum
- Topic: Communication only in Monitor mode
- Replies: 9
- Views: 10174
Re: Communication only in Monitor mode
I'm trying to understand the logic behind the UI, KI, AA and DA commands. My OTGW is operational for almost a year but keeps generating errors 03 and 04. I suspected the cabling and have played with resistor values and reference voltage settings (VR) but all to no avail. When I saw this post, which ...
- Mon Nov 02, 2015 5:04 pm
- Forum: Opentherm Gateway Forum
- Topic: Setpoint override not working
- Replies: 3
- Views: 4164
Re: Setpoint override not working
You have to configure the iSense to accept this.
This is done via: Menu > Instellingen > Installateur > Externe Ingang > Toestaan.
(assuming Dutch language version)
This is done via: Menu > Instellingen > Installateur > Externe Ingang > Toestaan.
(assuming Dutch language version)
- Fri Jan 16, 2015 10:27 am
- Forum: Opentherm Gateway Forum
- Topic: [SOLVED]Erratic behaviour/lock-ups/com errors Calenta/iSense
- Replies: 26
- Views: 27919
Re: [SOLVED]Erratic behaviour/lock-ups/com errors Calenta/iSense
I can confirm that after setting IT back to 1, the OTGW has been running perfectly stable for the past week, and not shown Error01 anymore.hvxl wrote:Correct, with IT=1 Error 01 can not occur.
It must have been cause by me when exploring the effect of all settings.
- Tue Jan 06, 2015 3:49 pm
- Forum: Opentherm Gateway Forum
- Topic: [SOLVED]Erratic behaviour/lock-ups/com errors Calenta/iSense
- Replies: 26
- Views: 27919
Re: Erratic behaviour/lock-ups/comm errors Calenta/iSense
I get the impression you are not running your gateway with the default setting for IT, i.e.: PR=T will return a 0 in the first position. The first thing to try is to set it back to default with the IT=1 command. The OTGW doc says about IT: Ignore Transitions - If the opentherm signal doesn't cleanl...