I took several captures of different things what source is doing, init & query data after launch, add device when it seeks devices from network. Unfortunately I do not have network initialization code, like what is done after fresh installing circle+ into network. How source sets up the network.
Well to my posting, here is something about plugwise zigbee network query. It looks like the query is what circle devices are stored in circle+'s allowed circle-devices.
How I did this - I installed USB Trace (with annoying shareware limitation), attached plugwise stick. Ran source, started capture and clicked "add device" from setup. First the source looks that all circles are there.
Then I wrote a perl program to analyze protocol which was HTML exported by USB Trace. There are a lot of (01 60) hex codes flying, but this time I concentrated to 05 05 03 03 * 0D 0A -lines. I masked my circle MAC-addresses with "CIR[+|2-9]" text to ease up seeing what is happening.
Then I looked at dump which is attached here, with my own comment of potential command:
IN | OUT is direction of USB packet. Out = source -> stick.
H: command in HEX, frame start, CRC and frame end omitted
A: print in ASCII for printable characters
I hope you can confirm my findings and potentially implement an autodiscovery circles to Domotiga when Circle+ is just entered. I also have a lot more captures - but here is my first analyzed because it is late.
(unfortunately I cannot set courier-font on forum so output column goes away)
$ ./analyze_protocol.pl checking_network_circle_plus_found.html
05 05 03 03 30 30 30 44 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 5F 43 52 43 0D 0A
OUT: H: 30|30|30|44|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22
OUT: A: 0 0 0 D 0 0 0 D 6 F 0 0 0 0 " C I R + "
OUT: ?: 000D (?? request, attach zigbee device?)
05 05 03 03 30 30 30 30 30 30 43 31 41 42 39 32 0D 0A
IN : H: 30|30|30|30|30|30|43|31
IN : A: 0 0 0 0 0 0 C 1
IN : ?: 0000 (?? ACK, COMMAND RECEIVED, SEARCHING INDEX??)
05 05 03 03 30 30 30 45 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 42 45 42 41 30 30 35 32 36 45 36 34 0D 0A
IN : H: 30|30|30|45|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|42|45|42|41|30|30|35|32
IN : A: 0 0 0 E 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " B E B A 0 0 5 2
IN : ?: 000E (?? response, zigbee network id, secret key?)(BEBA0052)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 30 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|30
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 0
OUT: ?: 0018 (MAC or device index request)(Index: 00)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 30 30 30 44 36 46 30 30 30 30 22 43 49 52 35 22 30 30 39 41 39 33 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|30|30|30|44|36|46|30|30|30|30|22|43|49|52|35|22|30|30
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " 0 0 0 D 6 F 0 0 0 0 " C I R 5 " 0 0
IN : ?: 0019 (MAC or device index response)(Index: 00)(000D6F0000"CIR5")
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 31 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|31
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 1
OUT: ?: 0018 (MAC or device index request)(Index: 01)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 30 30 30 44 36 46 30 30 30 30 22 43 49 52 39 22 30 31 42 30 44 41 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|30|30|30|44|36|46|30|30|30|30|22|43|49|52|39|22|30|31
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " 0 0 0 D 6 F 0 0 0 0 " C I R 9 " 0 1
IN : ?: 0019 (MAC or device index response)(Index: 01)(000D6F0000"CIR9")
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 32 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|32
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 2
OUT: ?: 0018 (MAC or device index request)(Index: 02)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 30 30 30 44 36 46 30 30 30 30 22 43 49 52 36 22 30 32 35 31 31 42 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|30|30|30|44|36|46|30|30|30|30|22|43|49|52|36|22|30|32
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " 0 0 0 D 6 F 0 0 0 0 " C I R 6 " 0 2
IN : ?: 0019 (MAC or device index response)(Index: 02)(000D6F0000"CIR6")
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 33 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|33
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 3
OUT: ?: 0018 (MAC or device index request)(Index: 03)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 30 30 30 44 36 46 30 30 30 30 22 43 49 52 34 22 30 33 39 36 31 36 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|30|30|30|44|36|46|30|30|30|30|22|43|49|52|34|22|30|33
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " 0 0 0 D 6 F 0 0 0 0 " C I R 4 " 0 3
IN : ?: 0019 (MAC or device index response)(Index: 03)(000D6F0000"CIR4")
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 34 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|34
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 4
OUT: ?: 0018 (MAC or device index request)(Index: 04)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 30 30 30 44 36 46 30 30 30 30 22 43 49 52 32 22 30 34 36 45 33 30 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|30|30|30|44|36|46|30|30|30|30|22|43|49|52|32|22|30|34
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " 0 0 0 D 6 F 0 0 0 0 " C I R 2 " 0 4
IN : ?: 0019 (MAC or device index response)(Index: 04)(000D6F0000"CIR2")
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 35 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|35
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 5
OUT: ?: 0018 (MAC or device index request)(Index: 05)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 30 30 30 44 36 46 30 30 30 30 22 43 49 52 37 22 30 35 41 39 42 31 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|30|30|30|44|36|46|30|30|30|30|22|43|49|52|37|22|30|35
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " 0 0 0 D 6 F 0 0 0 0 " C I R 7 " 0 5
IN : ?: 0019 (MAC or device index response)(Index: 05)(000D6F0000"CIR7")
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 36 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|36
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 6
OUT: ?: 0018 (MAC or device index request)(Index: 06)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 30 30 30 44 36 46 30 30 30 30 22 43 49 52 38 22 30 36 34 31 36 35 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|30|30|30|44|36|46|30|30|30|30|22|43|49|52|38|22|30|36
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " 0 0 0 D 6 F 0 0 0 0 " C I R 8 " 0 6
IN : ?: 0019 (MAC or device index response)(Index: 06)(000D6F0000"CIR8")
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 37 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|37
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 7
OUT: ?: 0018 (MAC or device index request)(Index: 07)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 30 30 30 44 36 46 30 30 30 30 22 43 49 52 33 22 30 37 34 37 46 30 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|30|30|30|44|36|46|30|30|30|30|22|43|49|52|33|22|30|37
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " 0 0 0 D 6 F 0 0 0 0 " C I R 3 " 0 7
IN : ?: 0019 (MAC or device index response)(Index: 07)(000D6F0000"CIR3")
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 38 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|38
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 8
OUT: ?: 0018 (MAC or device index request)(Index: 08)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 30 38 36 36 46 31 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|30|38
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 0 8
IN : ?: 0019 (MAC or device index response)(Index: 08)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 39 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|39
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 9
OUT: ?: 0018 (MAC or device index request)(Index: 09)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 30 39 37 36 44 30 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|30|39
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 0 9
IN : ?: 0019 (MAC or device index response)(Index: 09)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 41 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|41
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 A
OUT: ?: 0018 (MAC or device index request)(Index: 0A)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 30 41 38 39 34 46 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|30|41
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 0 A
IN : ?: 0019 (MAC or device index response)(Index: 0A)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 42 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|42
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 B
OUT: ?: 0018 (MAC or device index request)(Index: 0B)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 30 42 42 39 32 43 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|30|42
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 0 B
IN : ?: 0019 (MAC or device index response)(Index: 0B)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 43 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|43
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 C
OUT: ?: 0018 (MAC or device index request)(Index: 0C)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 30 43 41 39 30 44 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|30|43
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 0 C
IN : ?: 0019 (MAC or device index response)(Index: 0C)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 44 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|44
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 D
OUT: ?: 0018 (MAC or device index request)(Index: 0D)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 30 44 44 39 45 41 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|30|44
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 0 D
IN : ?: 0019 (MAC or device index response)(Index: 0D)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 45 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|45
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 E
OUT: ?: 0018 (MAC or device index request)(Index: 0E)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 30 45 43 39 43 42 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|30|45
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 0 E
IN : ?: 0019 (MAC or device index response)(Index: 0E)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 30 46 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|30|46
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 0 F
OUT: ?: 0018 (MAC or device index request)(Index: 0F)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 30 46 46 39 41 38 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|30|46
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 0 F
IN : ?: 0019 (MAC or device index response)(Index: 0F)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 30 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|30
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 0
OUT: ?: 0018 (MAC or device index request)(Index: 10)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 30 44 34 43 38 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|30
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 0
IN : ?: 0019 (MAC or device index response)(Index: 10)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 31 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|31
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 1
OUT: ?: 0018 (MAC or device index request)(Index: 11)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 31 43 34 45 39 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|31
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 1
IN : ?: 0019 (MAC or device index response)(Index: 11)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 32 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|32
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 2
OUT: ?: 0018 (MAC or device index request)(Index: 12)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 32 46 34 38 41 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|32
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 2
IN : ?: 0019 (MAC or device index response)(Index: 12)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 33 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|33
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 3
OUT: ?: 0018 (MAC or device index request)(Index: 13)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 33 45 34 41 42 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|33
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 3
IN : ?: 0019 (MAC or device index response)(Index: 13)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 34 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|34
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 4
OUT: ?: 0018 (MAC or device index request)(Index: 14)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 34 39 34 34 43 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|34
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 4
IN : ?: 0019 (MAC or device index response)(Index: 14)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 35 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|35
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 5
OUT: ?: 0018 (MAC or device index request)(Index: 15)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 35 38 34 36 44 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|35
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 5
IN : ?: 0019 (MAC or device index response)(Index: 15)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 36 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|36
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 6
OUT: ?: 0018 (MAC or device index request)(Index: 16)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 36 42 34 30 45 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|36
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 6
IN : ?: 0019 (MAC or device index response)(Index: 16)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 37 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|37
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 7
OUT: ?: 0018 (MAC or device index request)(Index: 17)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 37 41 34 32 46 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|37
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 7
IN : ?: 0019 (MAC or device index response)(Index: 17)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 38 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|38
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 8
OUT: ?: 0018 (MAC or device index request)(Index: 18)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 38 35 35 43 30 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|38
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 8
IN : ?: 0019 (MAC or device index response)(Index: 18)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 39 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|39
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 9
OUT: ?: 0018 (MAC or device index request)(Index: 19)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 39 34 35 45 31 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|39
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 9
IN : ?: 0019 (MAC or device index response)(Index: 19)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 41 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|41
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 A
OUT: ?: 0018 (MAC or device index request)(Index: 1A)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 41 42 41 37 45 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|41
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 A
IN : ?: 0019 (MAC or device index response)(Index: 1A)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 42 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|42
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 B
OUT: ?: 0018 (MAC or device index request)(Index: 1B)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 42 38 41 31 44 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|42
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 B
IN : ?: 0019 (MAC or device index response)(Index: 1B)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 43 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|43
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 C
OUT: ?: 0018 (MAC or device index request)(Index: 1C)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 43 39 41 33 43 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|43
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 C
IN : ?: 0019 (MAC or device index response)(Index: 1C)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 44 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|44
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 D
OUT: ?: 0018 (MAC or device index request)(Index: 1D)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 44 45 41 44 42 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|44
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 D
IN : ?: 0019 (MAC or device index response)(Index: 1D)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 45 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|45
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 E
OUT: ?: 0018 (MAC or device index request)(Index: 1E)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 45 46 41 46 41 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|45
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 E
IN : ?: 0019 (MAC or device index response)(Index: 1E)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 31 46 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|31|46
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 1 F
OUT: ?: 0018 (MAC or device index request)(Index: 1F)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 31 46 43 41 39 39 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|31|46
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 1 F
IN : ?: 0019 (MAC or device index response)(Index: 1F)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 32 30 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|32|30
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 2 0
OUT: ?: 0018 (MAC or device index request)(Index: 20)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 32 30 38 31 39 42 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|32|30
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 2 0
IN : ?: 0019 (MAC or device index response)(Index: 20)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 32 31 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|32|31
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 2 1
OUT: ?: 0018 (MAC or device index request)(Index: 21)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 32 31 39 31 42 41 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|32|31
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 2 1
IN : ?: 0019 (MAC or device index response)(Index: 21)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 32 32 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|32|32
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 2 2
OUT: ?: 0018 (MAC or device index request)(Index: 22)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 32 32 41 31 44 39 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|32|32
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 2 2
IN : ?: 0019 (MAC or device index response)(Index: 22)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 32 33 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|32|33
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 2 3
OUT: ?: 0018 (MAC or device index request)(Index: 23)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 32 33 42 31 46 38 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|32|33
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 2 3
IN : ?: 0019 (MAC or device index response)(Index: 23)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 32 34 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|32|34
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 2 4
OUT: ?: 0018 (MAC or device index request)(Index: 24)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 32 34 43 31 31 46 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|32|34
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 2 4
IN : ?: 0019 (MAC or device index response)(Index: 24)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 32 35 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|32|35
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 2 5
OUT: ?: 0018 (MAC or device index request)(Index: 25)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 32 35 44 31 33 45 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|32|35
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 2 5
IN : ?: 0019 (MAC or device index response)(Index: 25)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 32 36 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|32|36
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 2 6
OUT: ?: 0018 (MAC or device index request)(Index: 26)
05 05 03 03 30 30 31 39 30 30 30 44 36 46 30 30 01 60 30 30 22 43 49 52 2B 22 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 46 32 36 45 31 35 44 0D 0A
IN : H: 30|30|31|39|30|30|30|44|36|46|30|30|01|60|30|30|22|43|49|52|2B|22|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|46|32|36
IN : A: 0 0 1 9 0 0 0 D 6 F 0 0 ` 0 0 " C I R + " F F F F F F F F F F F F F F F F 2 6
IN : ?: 0019 (MAC or device index response)(Index: 26)(FFFFFFFFFFFFFFFF)
05 05 03 03 30 30 31 38 30 30 30 44 36 46 30 30 30 30 22 43 49 52 2B 22 32 37 5F 43 52 43 0D 0A
OUT: H: 30|30|31|38|30|30|30|44|36|46|30|30|30|30|22|43|49|52|2B|22|32|37
OUT: A: 0 0 1 8 0 0 0 D 6 F 0 0 0 0 " C I R + " 2 7
OUT: ?: 0018 (MAC or device index request)(Index: 27)