Not sure if someone else can confirm the behavior that I'm seeing.
When I issue a TT command (Temporarily change the thermostat setpoint), the Remote override room setpoint stays at that level until:
- I send a TT=0 command
- I press a button on the Celcia-20
It was my understanding that the Celcia would return to it's week program once it "hits" the next setpoint in the weekprogram.
As far as I can see the gateway is just doing what it is supposed to do.
Celcia-20 not returning to week program after TT command?
Moderator: hvxl
Re: Celcia-20 not returning to week program after TT command?
The Celcia only has one type of remote setpoint change. It doesn't request MsgID 100 to find out if it's a temporary or continuous change. So TT and TC will actually result in the same behavior.
Schelte