OTmonitor reports incorrect value for Date message

Post by Bororo »

Hi Schelte,
I just connect OTGW between Siemens QAA73 Thermostat and Geminox THRi 2-17 M75 and found this strange settings for "Day of week and time of day" and "Date" :
Image

Why I see Oct 11 and Saturday there?
I tried to use "Send the current date to the gateway" function, but no change.
Best regards,
Ivan
yjb
Member
Member
Posts: 211
Joined: Fri Apr 17, 2009 1:15 pm
Location: Venhuizen, Netherlands

Re: OTmonitor reports incorrect value for Date message

Post by yjb »

Not sure if this is related, but I have the "time injection" option enabled, which used to work ok, but it failed on 7 dec:

Code: Select all

12:57:00.001068  Command: SC=12:57/7
12:58:00.000645  Command: SC=12:58/7
12:59:00.001212  Command: SC=12:59/7
Even injecting it manually doesn't seem to work:

Code: Select all

20:11:37.159175  Command (via websocket from 84.107.138.62:61590): SC=20:12/5
20:11:37.187292  SC: 20:12/5
20:11:37.209211  BC01C2600  Read-Ack    Return water temperature: 38.00
20:11:37.790218  T800500CB  Read-Data   Application-specific flags: 00000000 203
20:11:38.175948  R801C0000  Read-Data   Return water temperature: 0.00
20:11:38.283822  BC01C2600  Read-Ack    Return water temperature: 38.00
20:11:38.781405  T800500CB  Read-Data   Application-specific flags: 00000000 203
20:11:39.249244  R80190000  Read-Data   Boiler water temperature: 0.00
20:11:39.356315  BC0192900  Read-Ack    Boiler water temperature: 41.00
And again

Code: Select all

20:14:10.506865  BD0010A00  Write-Ack   Control setpoint: 10.00
20:14:10.559087  Command (via websocket from 84.107.138.62:61590): SC=20:17/5
20:14:10.587640  SC: 20:17/5
20:14:10.790828  T800500CB  Read-Data   Application-specific flags: 00000000 203
20:14:11.472455  R801C0000  Read-Data   Return water temperature: 0.00
20:14:11.580523  BC01C2600  Read-Ack    Return water temperature: 38.00
Tried to reboot the gateway, but that didn't work. It's not very important I think, but still...
hvxl
Senior Member
Senior Member
Posts: 1967
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: OTmonitor reports incorrect value for Date message

Post by hvxl »

Bororo wrote:Why I see Oct 11 and Saturday there?
Probably because that's what the thermostat sent or the boiler returned. Check the message log for MsgIDs 20 and 21.
Schelte
hvxl
Senior Member
Senior Member
Posts: 1967
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: OTmonitor reports incorrect value for Date message

Post by hvxl »

yjb wrote:Not sure if this is related, but I have the "time injection" option enabled, which used to work ok, but it failed on 7 dec:
12:57:00.001068 Command: SC=12:57/7
12:58:00.000645 Command: SC=12:58/7
12:59:00.001212 Command: SC=12:59/7
You don't appear to have any communication with the gateway here. Notice how you don't get any message for several minutes.
yjb wrote:Even injecting it manually doesn't seem to work:
20:11:37.159175 Command (via websocket from 84.107.138.62:61590): SC=20:12/5
20:11:37.187292 SC: 20:12/5
In what way doesn't that seem to work? The gateway correctly acknowledges the command. (You don't show enough logs to be able to determine whether or not it returns the correct value in response to MsgID 20.)
Schelte
yjb
Member
Member
Posts: 211
Joined: Fri Apr 17, 2009 1:15 pm
Location: Venhuizen, Netherlands

Re: OTmonitor reports incorrect value for Date message

Post by yjb »

Sorry schelte:
The 1st log is just a summary from the log by doing a "grep "Command: SC"", it was just to demonstrate the last few instances that the command was executed by otmonitor. After that I never san it again while it is configured to do so:

Code: Select all

/opt/opentherm//otmonitor --daemon -f /opt/opentherm/otmonitor.conf
and:

Code: Select all

 cat /opt/opentherm/otmonitor.conf
<SNIP>clock {
  year false
  date false
  auto true
}
<SNIP>
For the rest: because the timestamp in the log did not reflect the new time, I assumed it was not accepted.
Not sue how much log I need to provide, let's give this a try, otherwise I can send you an entire days worth of logs

Code: Select all

22:09:05.410952  Command (via websocket from 192.168.0.179:56223): SC=22:15/5
22:09:05.439462  SC: 22:15/5
22:09:06.215888  R80190000  Read-Data   Boiler water temperature: 0.00
22:09:06.314707  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:07.266769  R10010A00  Write-Data  Control setpoint: 10.00
22:09:07.306717  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:08.314770  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:08.340864  R801C0000  Read-Data   Return water temperature: 0.00
22:09:08.448828  BC01C2000  Read-Ack    Return water temperature: 32.00
22:09:09.305490  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:09.414423  R00120000  Read-Data   CH water pressure: 0.00
22:09:09.521476  B60120000  Data-Inv    CH water pressure: 0.00
22:09:10.314398  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:10.487437  R80190000  Read-Data   Boiler water temperature: 0.00
22:09:10.595469  B40192200  Read-Ack    Boiler water temperature: 34.00
22:09:11.305850  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:11.561846  R801C0000  Read-Data   Return water temperature: 0.00
22:09:11.669838  BC01C2000  Read-Ack    Return water temperature: 32.00
22:09:12.313552  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:12.635603  R001B0000  Read-Data   Outside temperature: 0.00
22:09:12.742714  B601B0000  Data-Inv    Outside temperature: 0.00
22:09:13.305516  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:13.316542  R800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:13.707528  R900E6400  Write-Data  Maximum relative modulation level: 100.00
22:09:13.815546  B500E6400  Write-Ack   Maximum relative modulation level: 100.00
22:09:14.313320  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:14.782432  R00000000  Read-Data   Status: 00000000 00000000
22:09:14.889339  BC0000000  Read-Ack    Status: 00000000 00000000
22:09:15.305230  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:15.854282  R10010A00  Write-Data  Control setpoint: 10.00
22:09:15.962263  BD0010A00  Write-Ack   Control setpoint: 10.00
22:09:16.313777  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:16.928719  R801C0000  Read-Data   Return water temperature: 0.00
22:09:17.036708  BC01C2000  Read-Ack    Return water temperature: 32.00
22:09:17.305616  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:18.002458  R00120000  Read-Data   CH water pressure: 0.00
22:09:18.111650  B60120000  Data-Inv    CH water pressure: 0.00
22:09:18.313641  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:19.075360  R80190000  Read-Data   Boiler water temperature: 0.00
22:09:19.183389  B40192200  Read-Ack    Boiler water temperature: 34.00
22:09:19.234332  Error 03
22:09:19.269314  Error 03
22:09:19.353314  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:19.478362  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:19.806412  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:20.274213  R001B0000  Read-Data   Outside temperature: 0.00
22:09:20.382275  B601B0000  Data-Inv    Outside temperature: 0.00
22:09:20.798109  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:20.809585  R800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:21.019434  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:21.030488  R800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:21.390204  R801C0000  Read-Data   Return water temperature: 0.00
22:09:21.498207  BC01C2000  Read-Ack    Return water temperature: 32.00
22:09:21.823168  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:22.455725  R80190000  Read-Data   Boiler water temperature: 0.00
22:09:22.563822  B40192200  Read-Ack    Boiler water temperature: 34.00
22:09:22.859493  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:23.524483  R80380000  Read-Data   DHW setpoint: 0.00
22:09:23.631597  BE0380000  Data-Inv    DHW setpoint: 0.00
22:09:23.823595  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:24.586391  R801C0000  Read-Data   Return water temperature: 0.00
22:09:24.696382  BC01C2000  Read-Ack    Return water temperature: 32.00
22:09:24.858195  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:25.654788  R00000000  Read-Data   Status: 00000000 00000000
22:09:25.761807  BC0000000  Read-Ack    Status: 00000000 00000000
22:09:25.796783  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:26.723341  R10010A00  Write-Data  Control setpoint: 10.00
22:09:26.805354  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:27.797611  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:27.823643  R00110000  Read-Data   Relative modulation level: 0.00
22:09:27.931545  BC0110000  Read-Ack    Relative modulation level: 0.00
22:09:28.805138  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:28.897854  R801C0000  Read-Data   Return water temperature: 0.00
22:09:29.004810  BC01C2000  Read-Ack    Return water temperature: 32.00
22:09:29.796736  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:29.971833  R801C0000  Read-Data   Return water temperature: 0.00
22:09:30.080853  BC01C2000  Read-Ack    Return water temperature: 32.00
22:09:30.832789  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:31.038867  R80190000  Read-Data   Boiler water temperature: 0.00
22:09:31.145790  B40192200  Read-Ack    Boiler water temperature: 34.00
22:09:31.796735  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:32.101833  R80380000  Read-Data   DHW setpoint: 0.00
22:09:32.208857  BE0380000  Data-Inv    DHW setpoint: 0.00
22:09:32.805791  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:33.175804  R801C0000  Read-Data   Return water temperature: 0.00
22:09:33.283804  BC01C2000  Read-Ack    Return water temperature: 32.00
22:09:33.796759  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:34.248787  R00000000  Read-Data   Status: 00000000 00000000
22:09:34.355759  BC0000000  Read-Ack    Status: 00000000 00000000
22:09:34.805765  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:35.322770  R10010A00  Write-Data  Control setpoint: 10.00
22:09:35.429879  BD0010A00  Write-Ack   Control setpoint: 10.00
22:09:35.795766  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:36.395755  R00110000  Read-Data   Relative modulation level: 0.00
22:09:36.502794  BC0110000  Read-Ack    Relative modulation level: 0.00
22:09:36.805801  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:37.469809  R801C0000  Read-Data   Return water temperature: 0.00
22:09:37.577837  BC01C2000  Read-Ack    Return water temperature: 32.00
22:09:37.796687  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:38.543769  R801C0000  Read-Data   Return water temperature: 0.00
22:09:38.650868  BC01C2000  Read-Ack    Return water temperature: 32.00
22:09:38.804799  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:39.616734  R80190000  Read-Data   Boiler water temperature: 0.00
22:09:39.723747  B40192200  Read-Ack    Boiler water temperature: 34.00
22:09:39.795687  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:40.689771  R80380000  Read-Data   DHW setpoint: 0.00
22:09:40.804787  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:41.730862  R801C0000  Read-Data   Return water temperature: 0.00
22:09:41.808690  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:42.817744  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:42.829699  R00120000  Read-Data   CH water pressure: 0.00
22:09:42.935762  B60120000  Data-Inv    CH water pressure: 0.00
22:09:43.808763  T800500CB  Read-Data   Application-specific flags: 00000000 203
22:09:43.900834  R80190000  Read-Data   Boiler water temperature: 0.00
22:09:44.008689  B40192200  Read-Ack    Boiler water temperature: 34.00
Also just noticed that I get a "Fout 203" on my Celcia-20. But that might not be related.

Last, no rush from my side, all seems to be working fine. And I don't think that the time will make that much of a difference.

EDIT:
Power off of the gateway as well as the boiler cleared the 203 error, and guess what: I now also see the automatic time updates reappearing:

Code: Select all

22:32:59.429652  BC000030A  Read-Ack    Status: 00000011 00001010
22:33:00.000636  Command: SC=22:33/4
22:33:00.028941  SC: 22:33/4
22:33:00.392907  T10015500  Write-Data  Control setpoint: 85.00
hvxl
Senior Member
Senior Member
Posts: 1967
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: OTmonitor reports incorrect value for Date message

Post by hvxl »

The gateway basically only reports which opentherm messages it sends and receives. The timestamp in the log is added by otmonitor and reflects the time a report was received according to the clock of the PC otmonitor is running on. Also the translation of the opentherm messages is provided by otmonitor. So the gateway really only produces the second column you see in the logs.

The SC command tells the gateway which values to return in response to MsgID 20 in roughly the next minute. It has no effect on the timestamp added by otmonitor.

Read http://otgw.tclcode.com/firmware.html#operation to get a better understanding of which information the gateway provides and what the different commands do.

According to the equipment matrix, the Celcia 20 never requests MsgID 20, so sending the time to the gateway is not going to be very useful in that configuration.
Schelte
yjb
Member
Member
Posts: 211
Joined: Fri Apr 17, 2009 1:15 pm
Location: Venhuizen, Netherlands

Re: OTmonitor reports incorrect value for Date message

Post by yjb »

Thanks for explaining Schelte. I was aware of the equipment table, I just didn't realize that I couldn't set the time for the Celcia-20.