I've been using my OTGW for over a month now, my setup is as follows: (pre-built) OTGW is connected in between my Remeha Tzerra (Plus) and iSense thermostat, positioned right next to the boiler and connected to a Raspberry Pi through USB. Everything is up-to-date, running v4.2 of the firmware and otmonitor. OTMonitor on the Pi is acting as a relay for another OTmonitor instance on my server, which I use to store the logs and override the temperature if desired. The Pi is connected through WiFi, my server through Gbit ethernet, both are connected to my Experiabox (modem/router).
It's been running very nicely over the past month: temperature override is working fine, I'm able to set the outside temperature on the iSense, graphs are properly displayed and no errors are reported. A couple of weeks back the first error occurred when I wanted to take a shower in the morning: the boiler heated up for a minute, but the water turned cold again. Waiting a few minutes seemed to resolve the issue, but what I saw in the otmonitor graph (through the web interface) was that the "boiler water temperature" rose to about 100 degrees when I turned on the shower, then dropped to below 40 and, remarkably, my attempts to turn on the shower again in the minutes after the error occurred were not detected as DHW taps (so the flame stayed off). About a week later it happened again and I was able to have a look at the error code the boiler showed: green blinking LED indicating "error 6", which means the boiler encountered an error and is trying to resolve it. I had my Pi disconnected for a couple of days (for maintenance, the OTGW was still connected though) and the issue didn't occur.
In the mean time I reconnected my Pi to the OTGW and last week the error happened again, but waiting a few minutes didn't seem to help (or I was too impatient), so I stopped otmonitor on my Pi: that instantly resolved the issue. Yesterday, I was able to verify this with full logging: the boiler heated up to about 100 degrees, my DHW taps a few minutes after the error were not detected and right after I stopped otmonitor on my Pi, it was working fine again.
So, my own thoughts on this:
- Because the OTGW was physically connected the whole time, I don't think the problem is in the OTGW or firmware
- The problem only seems to occur when otmonitor is running and does not happen every time I use DHW; it only seems to occur when otmonitor is running for some time (I'd say about a week, I hardly restart my Pi)
- It looks as if the boiler fails to lower the relative modulation level (in time), causing the boiler temperature to rise to about 100 degrees and ending up in an error state.
Code: Select all
07:31:29.254126 T00110000 Read-Data Relative modulation level: 0.00
07:31:29.383551 BC0110000 Read-Ack Relative modulation level: 0.00
07:31:30.256902 T80190000 Read-Data Boiler water temperature: 0.00
07:31:30.383243 BC01929CA Read-Ack Boiler water temperature: 41.79
07:31:31.261386 T00090000 Read-Data Remote override room setpoint: 0.00
07:31:31.384179 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:31:31.394893 A40091180 Read-Ack Remote override room setpoint: 17.50
07:31:32.271034 T00630000 Read-Data Message ID 99: 0
07:31:32.393124 BC0630000 Read-Ack Message ID 99: 0
07:31:33.269526 T00050000 Read-Data Application-specific flags: 00000000 0
07:31:33.386656 BC00500FF Read-Ack Application-specific flags: 00000000 255
07:31:34.273431 T00000000 Read-Data Status: 00000000 00000000
07:31:34.392905 B40000004 Read-Ack Status: 00000000 00000100
07:31:35.278357 T00000000 Read-Data Status: 00000000 00000000
07:31:35.386476 BC000000C Read-Ack Status: 00000000 00001100
07:31:36.283171 T00000000 Read-Data Status: 00000000 00000000
07:31:36.387701 BC000000C Read-Ack Status: 00000000 00001100
07:31:37.289081 T00000000 Read-Data Status: 00000000 00000000
07:31:37.388575 BC000000C Read-Ack Status: 00000000 00001100
07:31:38.292371 T90010800 Write-Data Control setpoint: 8.00
07:31:38.388874 B50010800 Write-Ack Control setpoint: 8.00
07:31:39.306230 T00110000 Read-Data Relative modulation level: 0.00
07:31:39.390154 BC0115C00 Read-Ack Relative modulation level: 92.00
07:31:40.301203 T80190000 Read-Data Boiler water temperature: 0.00
07:31:40.393253 B40192E5C Read-Ack Boiler water temperature: 46.36
07:31:41.304960 T00090000 Read-Data Remote override room setpoint: 0.00
07:31:41.397566 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:31:41.408026 A40091180 Read-Ack Remote override room setpoint: 17.50
07:31:42.312051 T00630000 Read-Data Message ID 99: 0
07:31:42.403047 BC0630000 Read-Ack Message ID 99: 0
07:31:43.315083 T001B01E6 Read-Data Outside temperature: 1.90
07:31:43.408546 B601B0000 Data-Inv Outside temperature: 0.00
07:31:43.419970 A401B0200 Read-Ack Outside temperature: 2.00
07:31:44.319050 T00000000 Read-Data Status: 00000000 00000000
07:31:44.410857 BC000000C Read-Ack Status: 00000000 00001100
07:31:45.326987 T90010800 Write-Data Control setpoint: 8.00
07:31:45.416151 B50010800 Write-Ack Control setpoint: 8.00
07:31:46.326666 T00110000 Read-Data Relative modulation level: 0.00
07:31:46.419420 B40115E00 Read-Ack Relative modulation level: 94.00
07:31:47.331184 T80190000 Read-Data Boiler water temperature: 0.00
07:31:47.494280 B40193F05 Read-Ack Boiler water temperature: 63.02
07:31:48.334844 T00090000 Read-Data Remote override room setpoint: 0.00
07:31:48.496558 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:31:48.508330 A40091180 Read-Ack Remote override room setpoint: 17.50
07:31:49.340722 T00630000 Read-Data Message ID 99: 0
07:31:49.497132 BC0630000 Read-Ack Message ID 99: 0
07:31:50.344697 T900E6400 Write-Data Maximum relative modulation level: 100.00
07:31:50.497983 B500E6400 Write-Ack Maximum relative modulation level: 100.00
07:31:51.346687 T00000000 Read-Data Status: 00000000 00000000
07:31:51.497710 BC000000C Read-Ack Status: 00000000 00001100
07:31:52.350576 T90010800 Write-Data Control setpoint: 8.00
07:31:52.498431 B50010800 Write-Ack Control setpoint: 8.00
07:31:53.354698 T00110000 Read-Data Relative modulation level: 0.00
07:31:53.499524 B40115E00 Read-Ack Relative modulation level: 94.00
07:31:54.358983 T80190000 Read-Data Boiler water temperature: 0.00
07:31:54.499719 BC0195640 Read-Ack Boiler water temperature: 86.25
07:31:55.362774 T00090000 Read-Data Remote override room setpoint: 0.00
07:31:55.501051 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:31:55.511525 A40091180 Read-Ack Remote override room setpoint: 17.50
07:31:56.367675 T00630000 Read-Data Message ID 99: 0
07:31:56.533056 BC0630000 Read-Ack Message ID 99: 0
07:31:57.371398 T90101000 Write-Data Room setpoint: 16.00
07:31:57.533685 B50101000 Write-Ack Room setpoint: 16.00
07:31:58.373693 T00000000 Read-Data Status: 00000000 00000000
07:31:58.537312 B40000004 Read-Ack Status: 00000000 00000100
07:31:59.377338 T00000000 Read-Data Status: 00000000 00000000
07:31:59.534968 B40000004 Read-Ack Status: 00000000 00000100
07:32:00.382177 T00000000 Read-Data Status: 00000000 00000000
07:32:00.535823 B40000004 Read-Ack Status: 00000000 00000100
07:32:01.391306 T90010800 Write-Data Control setpoint: 8.00
07:32:01.482202 B50010800 Write-Ack Control setpoint: 8.00
07:32:02.393209 T00110000 Read-Data Relative modulation level: 0.00
07:32:02.485664 BC0110000 Read-Ack Relative modulation level: 0.00
07:32:03.400030 T80190000 Read-Data Boiler water temperature: 0.00
07:32:03.492494 B401963F3 Read-Ack Boiler water temperature: 99.95
07:32:04.403508 T00090000 Read-Data Remote override room setpoint: 0.00
07:32:04.495960 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:32:04.506807 A40091180 Read-Ack Remote override room setpoint: 17.50
07:32:05.409157 T00630000 Read-Data Message ID 99: 0
07:32:05.572429 BC0630000 Read-Ack Message ID 99: 0
07:32:06.415954 T901810AE Write-Data Room temperature: 16.68
07:32:06.572785 B501810AE Write-Ack Room temperature: 16.68
07:32:07.419138 T00000000 Read-Data Status: 00000000 00000000
07:32:07.572895 BC0000000 Read-Ack Status: 00000000 00000000
07:32:08.422703 T00000000 Read-Data Status: 00000000 00000000
07:32:08.574062 BC0000000 Read-Ack Status: 00000000 00000000
07:32:09.428169 T00000000 Read-Data Status: 00000000 00000000
07:32:09.574638 BC0000000 Read-Ack Status: 00000000 00000000
07:32:10.434357 T90010800 Write-Data Control setpoint: 8.00
07:32:10.575383 B50010800 Write-Ack Control setpoint: 8.00
07:32:11.439019 T00110000 Read-Data Relative modulation level: 0.00
07:32:11.576274 BC0110000 Read-Ack Relative modulation level: 0.00
07:32:12.444680 T80190000 Read-Data Boiler water temperature: 0.00
07:32:12.577446 BC0194F0A Read-Ack Boiler water temperature: 79.04
07:32:13.448779 T00090000 Read-Data Remote override room setpoint: 0.00
07:32:13.577867 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:32:13.589497 A40091180 Read-Ack Remote override room setpoint: 17.50
07:32:14.454682 T00630000 Read-Data Message ID 99: 0
07:32:14.578167 BC0630000 Read-Ack Message ID 99: 0
07:32:15.460641 T80640000 Read-Data Remote override function: 00000000
07:32:15.578374 B40640000 Read-Ack Remote override function: 00000000
07:32:15.590123 A40640303 Read-Ack Remote override function: 00000011
07:32:16.464009 T00000000 Read-Data Status: 00000000 00000000
07:32:16.579590 BC0000000 Read-Ack Status: 00000000 00000000
07:32:17.470240 T90010800 Write-Data Control setpoint: 8.00
07:32:17.582906 B50010800 Write-Ack Control setpoint: 8.00
07:32:18.474994 T00110000 Read-Data Relative modulation level: 0.00
07:32:18.581257 BC0110000 Read-Ack Relative modulation level: 0.00
07:32:19.479715 T80190000 Read-Data Boiler water temperature: 0.00
07:32:19.580793 B40193D6B Read-Ack Boiler water temperature: 61.42
07:32:20.484411 T00090000 Read-Data Remote override room setpoint: 0.00
07:32:20.581426 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:32:20.592793 A40091180 Read-Ack Remote override room setpoint: 17.50
07:32:21.493902 T00630000 Read-Data Message ID 99: 0
07:32:21.582509 BC0630000 Read-Ack Message ID 99: 0
07:32:22.493721 T00050000 Read-Data Application-specific flags: 00000000 0
07:32:22.587298 B400501FF Read-Ack Application-specific flags: 00000001 255
07:32:23.498884 T00000000 Read-Data Status: 00000000 00000000
07:32:23.590985 BC0000000 Read-Ack Status: 00000000 00000000
07:32:24.503953 T90010800 Write-Data Control setpoint: 8.00
07:32:24.597279 B50010800 Write-Ack Control setpoint: 8.00
07:32:25.509181 T00110000 Read-Data Relative modulation level: 0.00
07:32:25.600776 BC0110000 Read-Ack Relative modulation level: 0.00
07:32:26.513439 T80190000 Read-Data Boiler water temperature: 0.00
07:32:26.605652 B401939F3 Read-Ack Boiler water temperature: 57.95
07:32:27.517106 T00090000 Read-Data Remote override room setpoint: 0.00
07:32:27.609339 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:32:27.621823 A40091180 Read-Ack Remote override room setpoint: 17.50
07:32:28.523618 T00630000 Read-Data Message ID 99: 0
07:32:28.687532 BC0630000 Read-Ack Message ID 99: 0
07:32:29.528415 T001B01E6 Read-Data Outside temperature: 1.90
07:32:29.688309 B601B0000 Data-Inv Outside temperature: 0.00
07:32:29.700073 A401B0200 Read-Ack Outside temperature: 2.00
07:32:30.533113 T00000000 Read-Data Status: 00000000 00000000
07:32:30.690149 BC0000000 Read-Ack Status: 00000000 00000000
07:32:31.536765 T90010800 Write-Data Control setpoint: 8.00
07:32:31.689644 B50010800 Write-Ack Control setpoint: 8.00
07:32:32.541762 T00110000 Read-Data Relative modulation level: 0.00
07:32:32.691011 BC0110000 Read-Ack Relative modulation level: 0.00
07:32:33.545899 T80190000 Read-Data Boiler water temperature: 0.00
07:32:33.691519 BC01939C2 Read-Ack Boiler water temperature: 57.76
07:32:34.550665 T00090000 Read-Data Remote override room setpoint: 0.00
07:32:34.691955 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:32:34.705069 A40091180 Read-Ack Remote override room setpoint: 17.50
07:32:35.556494 T00630000 Read-Data Message ID 99: 0
07:32:35.695026 BC0630000 Read-Ack Message ID 99: 0
07:32:36.559837 T900E6400 Write-Data Maximum relative modulation level: 100.00
07:32:36.691949 B500E6400 Write-Ack Maximum relative modulation level: 100.00
07:32:37.563949 T00000000 Read-Data Status: 00000000 00000000
07:32:37.693573 BC0000000 Read-Ack Status: 00000000 00000000
07:32:38.569149 T90010800 Write-Data Control setpoint: 8.00
07:32:38.697692 B50010800 Write-Ack Control setpoint: 8.00
07:32:39.574062 T00110000 Read-Data Relative modulation level: 0.00
07:32:39.695242 BC0110000 Read-Ack Relative modulation level: 0.00
07:32:40.580794 T80190000 Read-Data Boiler water temperature: 0.00
07:32:40.707355 BC01939C2 Read-Ack Boiler water temperature: 57.76
07:32:41.584071 T00090000 Read-Data Remote override room setpoint: 0.00
07:32:41.696768 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:32:41.707503 A40091180 Read-Ack Remote override room setpoint: 17.50
07:32:42.588777 T00630000 Read-Data Message ID 99: 0
07:32:42.696795 BC0630000 Read-Ack Message ID 99: 0
07:32:43.594514 T90101000 Write-Data Room setpoint: 16.00
07:32:43.697730 B50101000 Write-Ack Room setpoint: 16.00
07:32:44.597584 T00000000 Read-Data Status: 00000000 00000000
07:32:44.699248 BC0000000 Read-Ack Status: 00000000 00000000
07:32:45.603726 T90010800 Write-Data Control setpoint: 8.00
07:32:45.698394 B50010800 Write-Ack Control setpoint: 8.00
07:32:46.607196 T00110000 Read-Data Relative modulation level: 0.00
07:32:46.699392 BC0110000 Read-Ack Relative modulation level: 0.00
07:32:47.619428 T80190000 Read-Data Boiler water temperature: 0.00
07:32:47.708852 B401939A3 Read-Ack Boiler water temperature: 57.64
07:32:48.621547 T00090000 Read-Data Remote override room setpoint: 0.00
07:32:48.715200 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:32:48.726890 A40091180 Read-Ack Remote override room setpoint: 17.50
07:32:49.624155 T00630000 Read-Data Message ID 99: 0
07:32:49.716611 BC0630000 Read-Ack Message ID 99: 0
07:32:50.629358 T901810AE Write-Data Room temperature: 16.68
07:32:50.722551 B501810AE Write-Ack Room temperature: 16.68
07:32:51.637849 T00000000 Read-Data Status: 00000000 00000000
07:32:51.724328 BC0000000 Read-Ack Status: 00000000 00000000
07:32:52.641785 T90010800 Write-Data Control setpoint: 8.00
07:32:52.809078 B50010800 Write-Ack Control setpoint: 8.00
07:32:53.641681 T00110000 Read-Data Relative modulation level: 0.00
07:32:53.804020 BC0110000 Read-Ack Relative modulation level: 0.00
07:32:54.646505 T80190000 Read-Data Boiler water temperature: 0.00
07:32:54.805151 B401939A3 Read-Ack Boiler water temperature: 57.64
07:32:55.654442 T00090000 Read-Data Remote override room setpoint: 0.00
07:32:55.808287 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:32:55.817113 A40091180 Read-Ack Remote override room setpoint: 17.50
07:32:56.657486 T00630000 Read-Data Message ID 99: 0
07:32:56.807114 BC0630000 Read-Ack Message ID 99: 0
07:32:57.661851 T00740000 Read-Data Burner starts: 0
07:32:57.807036 BC0740000 Read-Ack Burner starts: 0
07:32:58.665424 T00000000 Read-Data Status: 00000000 00000000
07:32:58.808161 BC0000000 Read-Ack Status: 00000000 00000000
07:32:59.677179 T90010800 Write-Data Control setpoint: 8.00
07:32:59.808327 B50010800 Write-Ack Control setpoint: 8.00
07:33:00.673285 T00110000 Read-Data Relative modulation level: 0.00
07:33:00.809235 BC0110000 Read-Ack Relative modulation level: 0.00
07:33:01.679539 T80190000 Read-Data Boiler water temperature: 0.00
07:33:01.810274 B40193966 Read-Ack Boiler water temperature: 57.40
07:33:02.683537 T00090000 Read-Data Remote override room setpoint: 0.00
07:33:02.811540 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:33:02.821881 A40091180 Read-Ack Remote override room setpoint: 17.50
07:33:03.696281 T00630000 Read-Data Message ID 99: 0
07:33:03.810514 BC0630000 Read-Ack Message ID 99: 0
07:33:04.693082 T00050000 Read-Data Application-specific flags: 00000000 0
07:33:04.811426 B400501FF Read-Ack Application-specific flags: 00000001 255
07:33:05.697462 T00000000 Read-Data Status: 00000000 00000000
07:33:05.813236 BC0000000 Read-Ack Status: 00000000 00000000
07:33:06.701965 T90010800 Write-Data Control setpoint: 8.00
07:33:06.814305 B50010800 Write-Ack Control setpoint: 8.00
07:33:07.712664 T00110000 Read-Data Relative modulation level: 0.00
07:33:07.814086 BC0110000 Read-Ack Relative modulation level: 0.00
07:33:08.712813 T80190000 Read-Data Boiler water temperature: 0.00
07:33:08.815960 BC0193907 Read-Ack Boiler water temperature: 57.03
07:33:09.718122 T00090000 Read-Data Remote override room setpoint: 0.00
07:33:09.814685 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:33:09.826162 A40091180 Read-Ack Remote override room setpoint: 17.50
07:33:10.722382 T00630000 Read-Data Message ID 99: 0
07:33:10.817549 BC0630000 Read-Ack Message ID 99: 0
07:33:11.727693 T001B01E6 Read-Data Outside temperature: 1.90
07:33:11.817853 B601B0000 Data-Inv Outside temperature: 0.00
07:33:11.830130 A401B0200 Read-Ack Outside temperature: 2.00
07:33:12.731207 T00000000 Read-Data Status: 00000000 00000000
07:33:12.822283 BC0000000 Read-Ack Status: 00000000 00000000
07:33:13.734568 T90010800 Write-Data Control setpoint: 8.00
07:33:13.826033 B50010800 Write-Ack Control setpoint: 8.00
07:33:14.737222 T00110000 Read-Data Relative modulation level: 0.00
07:33:14.829618 BC0110000 Read-Ack Relative modulation level: 0.00
07:33:15.751139 T80190000 Read-Data Boiler water temperature: 0.00
07:33:15.835770 B401938AB Read-Ack Boiler water temperature: 56.67
07:33:16.744842 T00090000 Read-Data Remote override room setpoint: 0.00
07:33:16.836770 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:33:16.849784 A40091180 Read-Ack Remote override room setpoint: 17.50
07:33:17.749762 T00630000 Read-Data Message ID 99: 0
07:33:17.857159 BC0630000 Read-Ack Message ID 99: 0
07:33:18.755521 T900E6400 Write-Data Maximum relative modulation level: 100.00
07:33:20.758176 B500E6400 Write-Ack Maximum relative modulation level: 100.00
07:33:20.768190 T00000000 Read-Data Status: 00000000 00000000
07:33:20.768337 BC0000000 Read-Ack Status: 00000000 00000000
07:33:20.768464 T90010800 Write-Data Control setpoint: 8.00
07:33:20.922972 B50010800 Write-Ack Control setpoint: 8.00
07:33:21.765926 T00110000 Read-Data Relative modulation level: 0.00
07:33:21.924099 BC0110000 Read-Ack Relative modulation level: 0.00
07:33:22.768777 T80190000 Read-Data Boiler water temperature: 0.00
07:33:22.923806 B4019386B Read-Ack Boiler water temperature: 56.42
07:33:23.783258 T00090000 Read-Data Remote override room setpoint: 0.00
07:33:23.928455 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:33:23.942963 A40091180 Read-Ack Remote override room setpoint: 17.50
07:33:24.779342 T00630000 Read-Data Message ID 99: 0
07:33:24.924633 BC0630000 Read-Ack Message ID 99: 0
07:33:25.789699 T90101000 Write-Data Room setpoint: 16.00
07:33:25.933147 B50101000 Write-Ack Room setpoint: 16.00
07:33:26.787274 T00000000 Read-Data Status: 00000000 00000000
07:33:26.927068 BC0000000 Read-Ack Status: 00000000 00000000
07:33:27.799027 T90010800 Write-Data Control setpoint: 8.00
07:33:27.931423 B50010800 Write-Ack Control setpoint: 8.00
07:33:28.798080 T00110000 Read-Data Relative modulation level: 0.00
07:33:28.928402 BC0110000 Read-Ack Relative modulation level: 0.00
07:33:29.800659 T80190000 Read-Data Boiler water temperature: 0.00
07:33:29.928897 BC019382E Read-Ack Boiler water temperature: 56.18
07:33:30.802930 T00090000 Read-Data Remote override room setpoint: 0.00
07:33:30.929946 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:33:30.940816 A40091180 Read-Ack Remote override room setpoint: 17.50
07:33:31.813532 T00630000 Read-Data Message ID 99: 0
07:33:31.930841 BC0630000 Read-Ack Message ID 99: 0
07:33:32.812124 T901810B0 Write-Data Room temperature: 16.69
07:33:32.930835 B501810B0 Write-Ack Room temperature: 16.69
07:33:33.817586 T00000000 Read-Data Status: 00000000 00000000
07:33:33.932418 BC0000000 Read-Ack Status: 00000000 00000000
07:33:34.820863 T100107E6 Write-Data Control setpoint: 7.90
07:33:34.932638 BD00107E6 Write-Ack Control setpoint: 7.90
07:33:35.830882 T00110000 Read-Data Relative modulation level: 0.00
07:33:35.934087 BC0110000 Read-Ack Relative modulation level: 0.00
07:33:36.827182 T80190000 Read-Data Boiler water temperature: 0.00
07:33:36.934252 BC01937EE Read-Ack Boiler water temperature: 55.93
07:33:37.831614 T00090000 Read-Data Remote override room setpoint: 0.00
07:33:37.935047 BC0090000 Read-Ack Remote override room setpoint: 0.00
07:33:37.946034 A40091180 Read-Ack Remote override room setpoint: 17.50
07:33:38.837478 T00630000 Read-Data Message ID 99: 0
07:33:38.936245 BC0630000 Read-Ack Message ID 99: 0
07:33:39.848507 T00770000 Read-Data DHW burner starts: 0
07:33:39.935462 BC0770000 Read-Ack DHW burner starts: 0
07:33:40.841737 T00000000 Read-Data Status: 00000000 00000000
07:33:40.936885 BC0000000 Read-Ack Status: 00000000 00000000
07:33:41.847556 T100107E6 Write-Data Control setpoint: 7.90
07:33:41.939597 BD00107E6 Write-Ack Control setpoint: 7.90
07:33:42.849233 T00110000 Read-Data Relative modulation level: 0.00
07:33:42.943201 BC0110000 Read-Ack Relative modulation level: 0.00
07:33:43.861014 T80190000 Read-Data Boiler water temperature: 0.00
07:33:43.946280 B401937B0 Read-Ack Boiler water temperature: 55.69