USB Gateway no response on diagnostics

Post by joho500 »

Hi all,

I have a pre-assembled gateway, USB-type. First I flashed the gateway firmware and connected the thermostat. No respons and the display of the thermostat shows 'Wiring error'. For testing I attached the boiler and I did receive good data from that side.
To diagnose the problem with the thermostat side I flashed the diagnostic firmware. I get no respons entering options 2 and 3. Option 5 shows 0.00V both for the thermostat and the boiler and a reference voltage of 1.21V.

Does this mean that the gateway is physically broken? Or is something else wrong?

Thanks in advance for your help.

Joost
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: USB Gateway no response on diagnostics

Post by hvxl »

Unless you ran test 5 with the thermostat connector shorted, it should not show 0V for the thermostat. Given that the thermostat can be powered from the gateway, the problem can't be much else than a bad connection of R5.

However, I assume you ordered a pre-assembled gateway because you're not very comfortable with a soldering iron. If there's also not an acquaintance nearby who can help you sort out the problem around R5, you'll have to contact the webshop for a return request.
Schelte
joho500
Starting Member
Starting Member
Posts: 6
Joined: Fri Sep 19, 2014 11:16 am

Re: USB Gateway no response on diagnostics

Post by joho500 »

Thanks. I'll try to solder it myself and see if it helps.

Joost