I've checked for a setting in the thermostat to disable the remote setpoint override, but I could'nt find any.
When operating with a manual setpoint of 20.5 °C after a random time the setpoint is being reset to the daily program of 18.5 °C. In this example at 19:45:40.644131
Code: Select all
19:45:00.078158 Command (via relay server, from 127.0.0.1:56316): PS=1
19:45:00.118722 PS: 1
19:45:00.291230 00000010/00001100,10.00,00000001/00000001,100.00,0/0,20.50,76.00,0.00,20.88,67.00,0.00,14.00,44.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
19:45:01.684367 Command (via relay server, from 127.0.0.1:56317): PS=1
19:45:01.710740 PS: 1
19:45:01.878667 00000010/00001100,10.00,00000001/00000001,100.00,0/0,20.50,76.00,0.00,20.88,67.00,0.00,14.00,44.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
19:45:02.104248 Command (via relay server, from 127.0.0.1:56318): PR=T
19:45:02.195188 PR: T=11
19:45:02.281036 Command (via relay server, from 127.0.0.1:56319): PR=R
19:45:02.371593 PR: R=D
19:45:02.477212 Command (via relay server, from 127.0.0.1:56320): PR=M
19:45:02.539779 PR: M=G
19:45:02.614557 Command (via relay server, from 127.0.0.1:56321): PR=V
19:45:02.710336 PR: V=3
19:45:02.864314 Command (via relay server, from 127.0.0.1:56324): PR=O
19:45:02.969060 PR: O=N
19:45:03.056465 Command (via relay server, from 127.0.0.1:56325): PR=W
19:45:03.191965 PR: W=A
19:45:03.238186 Command (via relay server, from 127.0.0.1:56326): PR=L
19:45:03.273467 PR: L=FXOMPC
19:45:03.329629 Command (via relay server, from 127.0.0.1:56327): PS=0
19:45:03.405164 PS: 0
19:45:03.636165 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:45:03.859908 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:45:04.703191 T80190000 Read-Data Boiler water temperature: 0.00
19:45:04.770105 B40194400 Read-Ack Boiler water temperature: 68.00
19:45:05.679399 T10010A00 Write-Data Control setpoint: 10.00
19:45:05.765106 BD0010A00 Write-Ack Control setpoint: 10.00
19:45:06.683165 T00110000 Read-Data Relative modulation level: 0.00
19:45:06.758031 BC0114200 Read-Ack Relative modulation level: 66.00
19:45:07.642302 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:45:07.766865 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:45:08.636284 T80190000 Read-Data Boiler water temperature: 0.00
19:45:08.735148 B40194400 Read-Ack Boiler water temperature: 68.00
19:45:09.620596 T10010A00 Write-Data Control setpoint: 10.00
19:45:09.751131 BD0010A00 Write-Ack Control setpoint: 10.00
19:45:10.698050 T001B0000 Read-Data Outside temperature: 0.00
19:45:10.772241 B401B0E00 Read-Ack Outside temperature: 14.00
19:45:11.651694 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:45:11.780693 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:45:12.653676 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:45:12.855991 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:45:13.652079 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:45:13.835964 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:45:14.667884 T80190000 Read-Data Boiler water temperature: 0.00
19:45:14.743095 BC0194500 Read-Ack Boiler water temperature: 69.00
19:45:15.656277 T10010A00 Write-Data Control setpoint: 10.00
19:45:15.760774 BD0010A00 Write-Ack Control setpoint: 10.00
19:45:16.624288 T00110000 Read-Data Relative modulation level: 0.00
19:45:16.745070 B40113700 Read-Ack Relative modulation level: 55.00
19:45:17.620112 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:45:17.735152 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:45:18.655993 T80190000 Read-Data Boiler water temperature: 0.00
19:45:18.776503 BC0194500 Read-Ack Boiler water temperature: 69.00
19:45:19.651547 T10010A00 Write-Data Control setpoint: 10.00
19:45:19.763116 BD0010A00 Write-Ack Control setpoint: 10.00
19:45:20.668732 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:45:20.815171 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:45:21.636540 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:45:21.776482 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:45:22.636394 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:45:22.794056 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:45:23.621073 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:45:23.806017 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:45:24.667953 T80190000 Read-Data Boiler water temperature: 0.00
19:45:24.797583 BC0194600 Read-Ack Boiler water temperature: 70.00
19:45:25.651797 T10010A00 Write-Data Control setpoint: 10.00
19:45:25.764558 BD0010A00 Write-Ack Control setpoint: 10.00
19:45:26.651724 T80380000 Read-Data DHW setpoint: 0.00
19:45:26.763439 BE0380000 Data-Inv DHW setpoint: 0.00
19:45:27.636189 T00390000 Read-Data Max CH water setpoint: 0.00
19:45:27.745169 BF0390000 Unk-DataId Max CH water setpoint: 0.00
19:45:27.763761 AC0395A00 Read-Ack Max CH water setpoint: 90.00
19:45:28.636054 T80190000 Read-Data Boiler water temperature: 0.00
19:45:28.738109 BC0194600 Read-Ack Boiler water temperature: 70.00
19:45:29.625131 T10010A00 Write-Data Control setpoint: 10.00
19:45:29.745465 BD0010A00 Write-Ack Control setpoint: 10.00
19:45:30.132816 Command (via relay server, from 127.0.0.1:56333): PS=1
19:45:30.162468 PS: 1
19:45:30.292305 00000010/00001100,10.00,00000001/00000001,100.00,0/0,20.50,55.00,0.00,20.88,70.00,0.00,14.00,44.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
19:45:31.701644 Command (via relay server, from 127.0.0.1:56335): PS=1
19:45:31.730484 PS: 1
19:45:31.877414 00000010/00001100,10.00,00000001/00000001,100.00,0/0,20.50,55.00,0.00,20.88,70.00,0.00,14.00,44.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
19:45:32.095692 Command (via relay server, from 127.0.0.1:56336): PR=T
19:45:32.138265 PR: T=11
19:45:32.170361 Command (via relay server, from 127.0.0.1:56337): PR=R
19:45:32.201634 PR: R=D
19:45:32.222066 Command (via relay server, from 127.0.0.1:56338): PR=M
19:45:32.248735 PR: M=G
19:45:32.275191 Command (via relay server, from 127.0.0.1:56339): PR=V
19:45:32.303716 PR: V=3
19:45:32.325282 Command (via relay server, from 127.0.0.1:56340): PR=O
19:45:32.356575 PR: O=N
19:45:32.377605 Command (via relay server, from 127.0.0.1:56341): PR=W
19:45:32.398510 PR: W=A
19:45:32.446996 Command (via relay server, from 127.0.0.1:56342): PR=L
19:45:32.493218 PR: L=FXOMPC
19:45:32.524240 Command (via relay server, from 127.0.0.1:56343): PS=0
19:45:32.545899 PS: 0
19:45:32.651411 T80640000 Read-Data Remote override function: 00000000
19:45:32.780073 B70640000 Unk-DataId Remote override function: 00000000
19:45:32.795583 A40640303 Read-Ack Remote override function: 00000011
- Manual change priority: enable overrule (1)
- Program change priority: enable overrule (1)
19:45:33.631948 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:45:33.961084 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:45:34.636884 T80190000 Read-Data Boiler water temperature: 0.00
19:45:34.745938 B40194700 Read-Ack Boiler water temperature: 71.00
19:45:35.636145 T10010A00 Write-Data Control setpoint: 10.00
19:45:35.745843 BD0010A00 Write-Ack Control setpoint: 10.00
19:45:36.620495 T00110000 Read-Data Relative modulation level: 0.00
19:45:36.741568 B40112300 Read-Ack Relative modulation level: 35.00
19:45:37.667097 T901814EE Write-Data Room temperature: 20.93
19:45:37.773806 B501814EE Write-Ack Room temperature: 20.93
19:45:38.667494 T80190000 Read-Data Boiler water temperature: 0.00
19:45:38.817224 B40194700 Read-Ack Boiler water temperature: 71.00
19:45:39.651288 T10010A00 Write-Data Control setpoint: 10.00
19:45:39.756621 BD0010A00 Write-Ack Control setpoint: 10.00
19:45:40.644131 T90101280 Write-Data Room setpoint: 18.50
19:45:40.744925 B50101280 Write-Ack Room setpoint: 18.50
19:45:41.636322 T9014532E Write-Data Day of week and time of day: Tue 19:46
19:45:41.745330 BF014532E Unk-DataId Day of week and time of day: Tue 19:46
19:45:41.752588 A5014532E Write-Ack Day of week and time of day: Tue 19:46
19:45:42.625058 T801C0000 Read-Data Return water temperature: 0.00
19:45:42.749038 BC01C3700 Read-Ack Return water temperature: 55.00
19:45:43.620313 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:45:43.780046 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:45:44.656018 T80190000 Read-Data Boiler water temperature: 0.00
19:45:44.776765 B40194700 Read-Ack Boiler water temperature: 71.00
19:45:45.652598 T10010A00 Write-Data Control setpoint: 10.00
19:45:45.774395 BD0010A00 Write-Ack Control setpoint: 10.00
19:45:46.670406 T00110000 Read-Data Relative modulation level: 0.00
19:45:46.756107 B40111600 Read-Ack Relative modulation level: 22.00
19:45:47.651269 T801A0000 Read-Data DHW temperature: 0.00
19:45:47.761889 BE01A0000 Data-Inv DHW temperature: 0.00
19:45:48.635744 T80190000 Read-Data Boiler water temperature: 0.00
19:45:48.755771 B40194700 Read-Ack Boiler water temperature: 71.00
19:45:49.637785 T10010A00 Write-Data Control setpoint: 10.00
19:45:49.733243 BD0010A00 Write-Ack Control setpoint: 10.00
19:45:50.667120 T001B0000 Read-Data Outside temperature: 0.00
19:45:50.776418 B401B0E00 Read-Ack Outside temperature: 14.00
19:45:51.651502 T000F0000 Read-Data Boiler capacity and modulation limits: 0 0
19:45:51.758105 BF00F0000 Unk-DataId Boiler capacity and modulation limits: 0 0
19:45:52.659220 T00120000 Read-Data CH water pressure: 0.00
19:45:52.760707 B60120000 Data-Inv CH water pressure: 0.00
19:45:53.636207 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:45:53.771085 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:45:54.637297 T80190000 Read-Data Boiler water temperature: 0.00
19:45:54.756237 B40194700 Read-Ack Boiler water temperature: 71.00
19:45:55.656325 T10010A00 Write-Data Control setpoint: 10.00
19:45:55.760814 BD0010A00 Write-Ack Control setpoint: 10.00
19:45:56.639774 T00110000 Read-Data Relative modulation level: 0.00
19:45:56.732087 B40110B00 Read-Ack Relative modulation level: 11.00
19:45:57.656495 T001B0000 Read-Data Outside temperature: 0.00
19:45:57.792086 B401B0E00 Read-Ack Outside temperature: 14.00
19:45:58.671114 T80190000 Read-Data Boiler water temperature: 0.00
19:45:58.785268 B40194700 Read-Ack Boiler water temperature: 71.00
19:45:59.651615 T10010A00 Write-Data Control setpoint: 10.00
19:45:59.760812 BD0010A00 Write-Ack Control setpoint: 10.00
19:46:00.117620 Command (via relay server, from 127.0.0.1:56378): PS=1
19:46:00.159217 PS: 1
19:46:00.276362 00000010/00001100,10.00,00000001/00000001,100.00,0/0,18.50,11.00,0.00,20.93,71.00,0.00,14.00,55.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
19:46:01.711217 Command (via relay server, from 127.0.0.1:56379): PS=1
19:46:01.738536 PS: 1
19:46:01.961489 00000010/00001100,10.00,00000001/00000001,100.00,0/0,18.50,11.00,0.00,20.93,71.00,0.00,14.00,55.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
19:46:02.193091 Command (via relay server, from 127.0.0.1:56380): PR=T
19:46:02.241470 PR: T=11
19:46:02.302742 Command (via relay server, from 127.0.0.1:56382): PR=R
19:46:02.400273 PR: R=D
19:46:02.465130 Command (via relay server, from 127.0.0.1:56383): PR=M
19:46:02.513460 PR: M=G
19:46:02.586435 Command (via relay server, from 127.0.0.1:56384): PR=V
19:46:02.614576 PR: V=3
19:46:02.684890 Command (via relay server, from 127.0.0.1:56385): PR=O
19:46:02.707203 PR: O=N
19:46:02.727393 Command (via relay server, from 127.0.0.1:56386): PR=W
19:46:02.785947 PR: W=A
19:46:02.859219 Command (via relay server, from 127.0.0.1:56388): PR=L
19:46:02.940512 PR: L=FXOMPC
19:46:03.019267 Command (via relay server, from 127.0.0.1:56389): PS=0
19:46:03.044976 PS: 0
19:46:03.667699 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:46:03.843127 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:46:04.652025 T80190000 Read-Data Boiler water temperature: 0.00
19:46:04.823983 BC0194600 Read-Ack Boiler water temperature: 70.00
19:46:05.651821 T10010A00 Write-Data Control setpoint: 10.00
19:46:05.753773 BD0010A00 Write-Ack Control setpoint: 10.00
19:46:06.632501 T00110000 Read-Data Relative modulation level: 0.00
19:46:06.745160 BC0110500 Read-Ack Relative modulation level: 5.00
19:46:07.636287 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:46:07.792899 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:46:08.660638 T80190000 Read-Data Boiler water temperature: 0.00
19:46:08.776360 BC0194600 Read-Ack Boiler water temperature: 70.00
19:46:09.668059 T10010A00 Write-Data Control setpoint: 10.00
19:46:09.760708 BD0010A00 Write-Ack Control setpoint: 10.00
19:46:10.655173 T001B0000 Read-Data Outside temperature: 0.00
19:46:10.778837 B401B0E00 Read-Ack Outside temperature: 14.00
19:46:11.672366 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:46:11.825875 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:46:12.636268 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
19:46:12.774592 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
19:46:13.636388 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
I can't find any indication that the room thermostat is switched back to the daily program due to a (short) remote setpoint request.
When requesting a temporary setpoint override (through HS3 script), the setpoint is maintained and doesn't fall back to the daily program. In following example the room setpoint of 18.5 °C is switched to the remote override setpoint of 19 °C (activated at 10:36:14.443473):
Code: Select all
10:36:00.108785 Command (via relay server, from 127.0.0.1:65079): PS=1
10:36:00.263980 PS: 1
10:36:00.337652 00000010/00000000,10.00,00000001/00000001,100.00,0/0,18.50,0.00,0.00,20.16,34.00,0.00,14.00,33.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
10:36:01.711384 Command (via relay server, from 127.0.0.1:65080): PS=1
10:36:01.774503 PS: 1
10:36:01.882444 00000010/00000000,10.00,00000001/00000001,100.00,0/0,18.50,0.00,0.00,20.16,34.00,0.00,14.00,33.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
10:36:02.162867 Command (via relay server, from 127.0.0.1:65081): PR=T
10:36:02.384781 PR: T=11
10:36:02.481874 Command (via relay server, from 127.0.0.1:65082): PR=R
10:36:02.528248 PR: R=D
10:36:02.631255 Command (via relay server, from 127.0.0.1:65083): PR=M
10:36:02.681526 PR: M=G
10:36:02.754102 Command (via relay server, from 127.0.0.1:65084): PR=V
10:36:02.778695 PR: V=3
10:36:02.897455 Command (via relay server, from 127.0.0.1:65085): PR=O
10:36:02.994771 PR: O=N
10:36:03.216131 Command (via relay server, from 127.0.0.1:65086): PR=W
10:36:03.374722 PR: W=A
10:36:03.430952 Command (via relay server, from 127.0.0.1:65087): PR=L
10:36:03.469580 PR: L=FXOMPC
10:36:03.488697 Command (via relay server, from 127.0.0.1:65088): PS=0
10:36:03.517064 PS: 0
10:36:03.655707 T10010A00 Write-Data Control setpoint: 10.00
10:36:03.832273 BD0010A00 Write-Ack Control setpoint: 10.00
10:36:04.661250 T00110000 Read-Data Relative modulation level: 0.00
10:36:04.780965 BC0110000 Read-Ack Relative modulation level: 0.00
10:36:05.737314 T90181424 Write-Data Room temperature: 20.14
10:36:05.777738 B50181424 Write-Ack Room temperature: 20.14
10:36:06.656462 T80190000 Read-Data Boiler water temperature: 0.00
10:36:06.772397 B40192200 Read-Ack Boiler water temperature: 34.00
10:36:07.649900 T10010A00 Write-Data Control setpoint: 10.00
10:36:07.752492 BD0010A00 Write-Ack Control setpoint: 10.00
10:36:08.634225 T90101280 Write-Data Room setpoint: 18.50
10:36:08.743473 B50101280 Write-Ack Room setpoint: 18.50
10:36:09.672143 T10144A24 Write-Data Day of week and time of day: Tue 10:36
10:36:09.774578 B70144A24 Unk-DataId Day of week and time of day: Tue 10:36
10:36:09.791239 AD0144A24 Write-Ack Day of week and time of day: Tue 10:36
10:36:10.693406 T801C0000 Read-Data Return water temperature: 0.00
10:36:10.791940 B401C2100 Read-Ack Return water temperature: 33.00
10:36:11.665559 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
10:36:12.025941 B40000200 Read-Ack Status: 00000010 00000000
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: not active (0)
- Flame status: flame off (0)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
10:36:12.657719 T80190000 Read-Data Boiler water temperature: 0.00
10:36:12.757119 B40192200 Read-Ack Boiler water temperature: 34.00
10:36:13.757568 T10010A00 Write-Data Control setpoint: 10.00
10:36:13.810111 BD0010A00 Write-Ack Control setpoint: 10.00
10:36:14.443473 Command (via relay server, from 127.0.0.1:65091): TT=19.00
10:36:14.470754 TT: 19.00
10:36:14.680853 T00110000 Read-Data Relative modulation level: 0.00
10:36:14.821742 BC0110000 Read-Ack Relative modulation level: 0.00
10:36:15.665635 T801A0000 Read-Data DHW temperature: 0.00
10:36:15.790087 BE01A0000 Data-Inv DHW temperature: 0.00
10:36:16.676116 T80190000 Read-Data Boiler water temperature: 0.00
10:36:16.788356 B40192200 Read-Ack Boiler water temperature: 34.00
10:36:17.649810 T10010A00 Write-Data Control setpoint: 10.00
10:36:17.800741 BD0010A00 Write-Ack Control setpoint: 10.00
10:36:18.650259 T001B0000 Read-Data Outside temperature: 0.00
10:36:18.758902 B401B0E00 Read-Ack Outside temperature: 14.00
10:36:19.681167 T000F0000 Read-Data Boiler capacity and modulation limits: 0 0
10:36:19.804110 BF00F0000 Unk-DataId Boiler capacity and modulation limits: 0 0
10:36:20.670247 T00120000 Read-Data CH water pressure: 0.00
10:36:20.774636 B60120000 Data-Inv CH water pressure: 0.00
10:36:21.665397 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
10:36:21.919257 B40000200 Read-Ack Status: 00000010 00000000
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: not active (0)
- Flame status: flame off (0)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
10:36:22.649869 T80190000 Read-Data Boiler water temperature: 0.00
10:36:22.793237 B40192200 Read-Ack Boiler water temperature: 34.00
10:36:23.634115 T10010A00 Write-Data Control setpoint: 10.00
10:36:23.777947 BD0010A00 Write-Ack Control setpoint: 10.00
10:36:24.702876 T00110000 Read-Data Relative modulation level: 0.00
10:36:24.784118 BC0110000 Read-Ack Relative modulation level: 0.00
10:36:25.665714 T001B0000 Read-Data Outside temperature: 0.00
10:36:25.774837 B401B0E00 Read-Ack Outside temperature: 14.00
10:36:26.649768 T80190000 Read-Data Boiler water temperature: 0.00
10:36:26.816320 B40192200 Read-Ack Boiler water temperature: 34.00
10:36:27.670887 T10010A00 Write-Data Control setpoint: 10.00
10:36:27.747926 BD0010A00 Write-Ack Control setpoint: 10.00
10:36:28.657892 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
10:36:28.811616 B40000200 Read-Ack Status: 00000010 00000000
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: not active (0)
- Flame status: flame off (0)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
10:36:29.681081 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
10:36:29.839277 B40000200 Read-Ack Status: 00000010 00000000
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: not active (0)
- Flame status: flame off (0)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
10:36:30.139514 Command (via relay server, from 127.0.0.1:65097): PS=1
10:36:30.201227 PS: 1
10:36:30.318987 00000010/00000000,10.00,00000001/00000001,100.00,0/0,18.50,0.00,0.00,20.14,34.00,0.00,14.00,33.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
10:36:31.666652 Command (via relay server, from 127.0.0.1:65098): PS=1
10:36:31.693642 PS: 1
10:36:31.844045 00000010/00000000,10.00,00000001/00000001,100.00,0/0,18.50,0.00,0.00,20.14,34.00,0.00,14.00,33.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
10:36:32.057614 Command (via relay server, from 127.0.0.1:65099): PR=T
10:36:32.085497 PR: T=11
10:36:32.113169 Command (via relay server, from 127.0.0.1:65100): PR=R
10:36:32.136053 PR: R=D
10:36:32.161224 Command (via relay server, from 127.0.0.1:65101): PR=M
10:36:32.192152 PR: M=G
10:36:32.219059 Command (via relay server, from 127.0.0.1:65102): PR=V
10:36:32.239818 PR: V=3
10:36:32.261287 Command (via relay server, from 127.0.0.1:65103): PR=O
10:36:32.292879 PR: O=t19.00
10:36:32.349914 Command (via relay server, from 127.0.0.1:65104): PR=W
10:36:32.377522 PR: W=A
10:36:32.394758 Command (via relay server, from 127.0.0.1:65105): PR=L
10:36:32.424487 PR: L=FXOMPC
10:36:32.442925 Command (via relay server, from 127.0.0.1:65106): PS=0
10:36:32.469595 PS: 0
10:36:32.653046 T80190000 Read-Data Boiler water temperature: 0.00
10:36:32.774526 B40192200 Read-Ack Boiler water temperature: 34.00
10:36:33.707565 T10010A00 Write-Data Control setpoint: 10.00
10:36:33.781146 BD0010A00 Write-Ack Control setpoint: 10.00
10:36:34.656852 T00110000 Read-Data Relative modulation level: 0.00
10:36:34.774642 BC0110000 Read-Ack Relative modulation level: 0.00
10:36:35.684799 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
10:36:35.817470 B40000200 Read-Ack Status: 00000010 00000000
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: not active (0)
- Flame status: flame off (0)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
10:36:36.647259 T80190000 Read-Data Boiler water temperature: 0.00
10:36:36.759071 B40192200 Read-Ack Boiler water temperature: 34.00
10:36:37.634903 T10010A00 Write-Data Control setpoint: 10.00
10:36:37.749432 BD0010A00 Write-Ack Control setpoint: 10.00
10:36:38.682645 T001B0000 Read-Data Outside temperature: 0.00
10:36:38.792698 B401B0E00 Read-Ack Outside temperature: 14.00
10:36:39.681385 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
10:36:39.819358 B40000200 Read-Ack Status: 00000010 00000000
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: not active (0)
- Flame status: flame off (0)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
10:36:40.665697 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
10:36:40.865852 B40000200 Read-Ack Status: 00000010 00000000
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: not active (0)
- Flame status: flame off (0)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
10:36:41.649966 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
10:36:41.790159 B40000200 Read-Ack Status: 00000010 00000000
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: not active (0)
- Flame status: flame off (0)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
10:36:42.634498 T80190000 Read-Data Boiler water temperature: 0.00
10:36:42.743361 B40192200 Read-Ack Boiler water temperature: 34.00
10:36:43.665784 T10010A00 Write-Data Control setpoint: 10.00
10:36:43.782104 BD0010A00 Write-Ack Control setpoint: 10.00
10:36:44.666881 T00110000 Read-Data Relative modulation level: 0.00
10:36:44.774497 BC0110000 Read-Ack Relative modulation level: 0.00
10:36:45.650021 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
10:36:45.841813 B40000200 Read-Ack Status: 00000010 00000000
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: not active (0)
- Flame status: flame off (0)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
10:36:46.637929 T80190000 Read-Data Boiler water temperature: 0.00
10:36:46.758060 B40192200 Read-Ack Boiler water temperature: 34.00
10:36:47.681197 T10010A00 Write-Data Control setpoint: 10.00
10:36:47.790156 BD0010A00 Write-Ack Control setpoint: 10.00
10:36:48.670234 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
10:36:48.837587 B40000200 Read-Ack Status: 00000010 00000000
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: not active (0)
- Flame status: flame off (0)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
10:36:49.650296 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
10:36:49.836836 B40000200 Read-Ack Status: 00000010 00000000
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: not active (0)
- Flame status: flame off (0)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
10:36:50.650330 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
10:36:50.819167 B40000200 Read-Ack Status: 00000010 00000000
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: not active (0)
- Flame status: flame off (0)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
10:36:51.650695 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
10:36:51.805126 B40000200 Read-Ack Status: 00000010 00000000
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: not active (0)
- Flame status: flame off (0)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
10:36:52.666949 T80190000 Read-Data Boiler water temperature: 0.00
10:36:52.792980 B40192200 Read-Ack Boiler water temperature: 34.00
10:36:53.665665 T10010A00 Write-Data Control setpoint: 10.00
10:36:53.798177 BD0010A00 Write-Ack Control setpoint: 10.00
10:36:54.670299 T80380000 Read-Data DHW setpoint: 0.00
10:36:54.763407 BE0380000 Data-Inv DHW setpoint: 0.00
10:36:55.650120 T00390000 Read-Data Max CH water setpoint: 0.00
10:36:55.764335 BF0390000 Unk-DataId Max CH water setpoint: 0.00
10:36:55.771421 AC0395A00 Read-Ack Max CH water setpoint: 90.00
10:36:56.634199 T80190000 Read-Data Boiler water temperature: 0.00
10:36:56.749833 B40192200 Read-Ack Boiler water temperature: 34.00
10:36:57.681217 T10010A00 Write-Data Control setpoint: 10.00
10:36:57.780121 BD0010A00 Write-Ack Control setpoint: 10.00
10:36:58.667031 T900E6400 Write-Data Maximum relative modulation level: 100.00
10:36:58.766031 B500E6400 Write-Ack Maximum relative modulation level: 100.00
10:36:59.663503 T00090000 Read-Data Remote override room setpoint: 0.00
10:36:59.765218 BF0090000 Unk-DataId Remote override room setpoint: 0.00
10:36:59.774099 A40091300 Read-Ack Remote override room setpoint: 19.00
Although the override setpoint is set only once ("TT=xx") it is maintained without the thermostat is resetting to the daily program. However, the normal operation of the thermostat, with setpoint being adjusted on the thermostat, is not stable when the OTGW is attached ... very strange indeed!