is there any way (I mean OTG command) how to read boiler counters like HBS (Central heating burner starts), HBH (Central heating burner operation hours), HPS (Central heating pump starts), ...?
I've successfully installed OTG between QAA73 (Siemens) and LMU64 (Geminox THRi 5-25 DC). But it seems, that there are two mesgs, that are not decoded. There are:
Hex Dec Dir Description Freq Value
81 129 Write MessageID 129 25 513
82 130 Write MessageID 130 25 3442
Anybody have any idea what it is for?
Thank you for advice,
--
roman
Msg ID129, Msg ID130
Moderator: hvxl
Re: Msg ID129, Msg ID130
These ID's are in the default list of alternative messages. So unless you manually removed them or your boiler doesn't support them, the OTGW should already be requesting these counters and gauges.rpav wrote:is there any way (I mean OTG command) how to read boiler counters like HBS (Central heating burner starts), HBH (Central heating burner operation hours), HPS (Central heating pump starts), ...?
Any message with an ID of 128 or higher is "for test & diagnostic purposes only" and may freely be defined by each manufacturer. So the same ID may have a totally different meaning depending on the brand of equipment. The meaning of these ID's is usually not published. That's why otmonitor cannot provide a translation for these messages.rpav wrote:there are two mesgs, that are not decoded. There are:
Hex Dec Dir Description Freq Value
81 129 Write MessageID 129 25 513
82 130 Write MessageID 130 25 3442
Schelte
Re: Msg ID129, Msg ID130
It seems, that Geminox THRi doesn't support them:hvxl wrote:These ID's are in the default list of alternative messages. So unless you manually removed them or your boiler doesn't support them, the OTGW should already be requesting these counters and gauges.rpav wrote:is there any way (I mean OTG command) how to read boiler counters like HBS (Central heating burner starts), HBH (Central heating burner operation hours), HPS (Central heating pump starts), ...?
14:34:21.634046 Command (via websocket from 192.168.111.1:55844): PS=1
14:34:21.648423 PS: 1
14:34:21.792636 00000010/00001100,10.00,00000111/00000111,100.00,0/0,17.00,30.00,2.26,22.94,69.31,42.69,13.86,48.78,65/10,89/20,53.00,89.00,0,0,0,0,0,0,0,0
It's clear now, thank you.hvxl wrote:Any message with an ID of 128 or higher is "for test & diagnostic purposes only" and may freely be defined by each manufacturer. So the same ID may have a totally different meaning depending on the brand of equipment. The meaning of these ID's is usually not published. That's why otmonitor cannot provide a translation for these messages.rpav wrote:there are two mesgs, that are not decoded. There are:
Hex Dec Dir Description Freq Value
81 129 Write MessageID 129 25 513
82 130 Write MessageID 130 25 3442
--
rp