Posted: Mon Feb 22, 2016 11:49 am
by holgera
Hi!

after getting the GW working, i get a lot of unknown data logged. Can someone help to identify what especially the IDs 130 to 135 are for?

Thx,
Holger

Code: Select all

09:40:31.355053  T80000B00  Read-Data   Status: 00001011 00000000
                               - CH enable: enabled (1)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: active (1)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
09:40:31.782707  BC0000B02  Read-Ack    Status: 00001011 00000010
                               - Fault indication: no fault (0)
                               - CH mode: active (1)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
09:40:32.513786  T801A0000  Read-Data   DHW temperature: 0.00
09:40:32.902487  B401A3900  Read-Ack    DHW temperature: 57.00
09:40:33.625039  T90383BC0  Write-Data  DHW setpoint: 59.75
09:40:34.056185  B50383BC0  Write-Ack   DHW setpoint: 59.75
09:40:34.745019  T001B0000  Read-Data   Outside temperature: 0.00
09:40:35.254934  BC01B0900  Read-Ack    Outside temperature: 9.00
09:40:35.970044  T801014CC  Read-Data   Room setpoint: 20.80
09:40:36.397390  B701014CC  Unk-DataId  Room setpoint: 20.80
09:40:36.408362  A401014CC  Read-Ack    Room setpoint: 20.80
09:40:37.107192  T001815EC  Read-Data   Room temperature: 21.92
09:40:37.496156  BF01815EC  Unk-DataId  Room temperature: 21.92
09:40:38.193156  T801F0000  Read-Data   Flow temperature CH2: 0.00
09:40:38.624382  B401F1D00  Read-Ack    Flow temperature CH2: 29.00
09:40:39.336719  T80873BC0  Read-Data   Message ID 135: 15296
09:40:39.845546  B70873BC0  Unk-DataId  Message ID 135: 15296
09:40:40.596777  T00860329  Read-Data   Message ID 134: 809
09:40:41.024164  BF0860329  Unk-DataId  Message ID 134: 809
09:40:41.760268  T80850000  Read-Data   Message ID 133: 0
09:40:42.150314  B70850000  Unk-DataId  Message ID 133: 0
09:40:42.882896  T00840000  Read-Data   Message ID 132: 0
09:40:43.314398  BF0840000  Unk-DataId  Message ID 132: 0
09:40:44.036705  T00831600  Read-Data   Message ID 131: 5632
09:40:44.545511  B7083A43E  Unk-DataId  Message ID 131: 42046
09:40:45.235257  T808200B3  Read-Data   Message ID 130: 179
09:40:45.662591  BF0824800  Unk-DataId  Message ID 130: 18432
09:40:46.376301  T10011B90  Write-Data  Control setpoint: 27.56
09:40:46.766209  BD0011B90  Write-Ack   Control setpoint: 27.56

Re: Unkown Data ID

Posted: Tue Feb 23, 2016 12:57 pm
by Templar
From the The OpenTherm Protocol Specification:
Id’s 0 .. 127 are reserved for OpenTherm pre-defined information, while id’s from 128 .. 255 can be used by manufacturers (members of the association) for test & diagnostic purposes only.
So the Data ID's are (only) known to the thermostat manufacturer. Perhaps reading the thermostat manual and/or observing the thermostat display readings provide some clues? What kind of brand and type of thermostat do you use? Is it the Theben RAMSES 786 OT?

Re: Unkown Data ID

Posted: Sat Feb 27, 2016 9:29 pm
by holgera
Yes, this is a Windhager REG 021A, Theben RAM 786 opentherm thermostat.

The thermostat is analog, so it shows no values.