Verified the bytesize of the downloaded firmware and it was exactly the same.
Redownloaded the firmware and put the new file into the OTGW.
No changes.
Removed the iSense (firmware version 19 b.t.w.) and then powered down the boiler. Waited a minute or so and powered the boiler up.
OT Monitor was in Gateway mode and started generating 03 errors when the boiler startup had finished.
Put it into Monitor mode and data stopped appearing into the log pane.
Again switch to Monitor and Gateway. Still 01 errors.
Plugged the iSense back in while in Monitor mode and data was flowing into the log pane.
Suddenly the 03 errors started to appear in Monitor mode. And disappeared after a while.
Here's the log from OT Monitor. No lines where excluded.
Put the OTGW in Gateway mode and let the 03 errors run for a while.
Switched back to Monitor mode and then loaded the Diagnostics firmware.
Code: Select all
Invalid test
Opentherm gateway diagnostics - Version 1.1
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 3
501,508,502,503,503,1004,1009,1008,501,505,501,503,503,506,494,512,501,505,501,505,502,505,497,509,501,498,508,506,1004,1008,501,500,506,506,492,514,501,505,1001,508,502,1008,501,506,500,504,502,506,495,511,501,506,500,506,501,505,497,509,997.
D0010600 Write-Ack Control setpoint: 6.00
494,516,502,504,502,1009,500,499,508,505,501,506,499,507,501,500,506,505,493,514,500,506,1001,1012,493,513,501,505,1003,1010,496,510,501,497,509,505,501,506,498,508,501,499,507,506,500,506,500,506,501,501,505,506,492,514,500,506,501,503,503,506,1004.
C0110000 Read-Ack Relative modulation level: 0.00
509,508,503,504,499,1011,495,511,501,506,500,505,502,505,497,509,501,498,508,506,501,505,1005,504,497,1013,493,513,1005,1005,504,506,1004,504,503,503,501,506,502,499,507,1008,1005,1008,498,509,997,511,502,1009,499,507,1000,508,502.
C0193E99 Read-Ack Boiler water temperature: 62.60
502,508,502,501,505,1002,507,506,501,505,500,506,501,501,506,505,493,513,501,506,500,504,503,505,495,512,1004,1008,1005,1008,501,498,508,506,500,506,499,507,501,500,506,506,492,514,1005,504,499,507,503,496,510,504,502,504,501,505,503,499,507,504,494.
C00500FF Read-Ack Application-specific flags: 00000000 255
506,1004,1012,1009,498,508,500,500,507,505,501,506,500,506,501,501,505,506,493,513,501,505,501,503,503,506,495,511,501,505,501,506,500,506,497,509,501,498,508,506,501,505,1005,1003,506,505,492,515,500,506,501,502,504,505,494,512,501,506,501,504,1005.
40000200 Read-Ack Status: 00000010 00000000
498,511,502,497,510,1008,1003,1009,496,511,500,506,501,505,501,506,497,509,501,498,508,505,501,506,499,507,501,501,1009,1008,501,505,501,503,503,506,494,512,1005,504,501,1009,496,510,501,498,508,506,501,505,499,508,500,500,507,505,501,505,1004.
D0010600 Write-Ack Control setpoint: 6.00
508,508,502,504,502,1009,496,510,501,497,509,506,500,506,498,508,501,499,507,506,501,505,1005,1004,505,505,493,514,1004,1006,503,505,496,511,501,505,501,506,500,506,497,509,501,498,508,506,501,505,499,508,500,501,506,505,493,514,500,506,501,502,1007.
C0110000 Read-Ack Relative modulation level: 0.00
495,1018,1005,1008,501,501,505,505,493,514,500,506,501,503,503,505,495,512,500,506,1004,505,502,1008,501,497,1013,1008,498,508,999,510,502,495,511,504,502,504,499,1012,1004,1008,501,504,502,506,495,511,501,505,501,506,501,505,1004.
40193E80 Read-Ack Boiler water temperature: 62.50
507,1013,1004,504,502,1008,501,498,508,506,501,505,499,507,501,500,506,506,492,514,1004,504,500,1011,1004,504,503,1007,501,506,496,510,501,497,509,506,501,505,498,508,501,499,507,506,501,505,500,507,500,502,505,505,493,513,501,506,501,503,1006.
601B0000 Data-Inv Outside temperature: 0.00
501,1012,1004,1004,505,506,492,514,501,506,500,503,504,505,495,511,501,506,500,505,502,505,497,510,500,498,509,505,501,505,499,507,501,500,507,505,493,514,500,506,501,501,1009,1008,500,506,501,504,502,505,496,511,500,506,501,506,500,506,497,509,997.
40000200 Read-Ack Status: 00000010 00000000
496,514,502,504,502,1008,1001,1012,493,513,501,505,501,503,503,505,496,511,500,506,501,505,501,506,496,510,500,499,1011,1009,498,508,500,501,506,505,492,514,1005,504,499,1011,494,512,501,506,500,504,502,506,495,511,501,505,501,506,500,506,1004.
D0010600 Write-Ack Control setpoint: 6.00
499,510,503,497,509,1008,501,505,501,506,496,510,501,497,509,505,501,506,498,508,501,499,1011,1008,500,506,501,502,1008,1008,501,506,500,504,503,505,495,511,501,506,500,506,501,505,497,510,500,499,508,505,501,505,499,508,500,501,506,505,493,514,1004.
C0110000 Read-Ack Relative modulation level: 0.00
497,1017,1004,1008,501,503,503,506,494,512,501,505,501,505,501,506,496,510,500,498,1013,503,503,1008,500,500,1010,1009,500,506,1000,508,502,497,510,503,503,504,500,1010,1005,1008,501,505,501,505,498,508,501,499,508,505,501,506,1004.
40193E80 Read-Ack Boiler water temperature: 62.50
509,1012,1002,1011,1004,1008,500,506,501,506,497,509,501,498,508,505,501,506,499,507,999,509,503,495,511,1008,501,502,1008,497,509,1008,501,504,1006,1008,501,497,509,505,501,506,497,509,501,499,507,505,501,506,500,506,501,501,1008.
500E6400 Write-Ack Maximum relative modulation level: 100.00
507,1011,1005,1008,497,509,501,498,508,506,500,506,499,507,501,500,506,505,493,514,500,506,501,502,504,505,495,512,500,506,501,504,502,505,497,510,500,498,508,506,501,506,1004,1002,507,505,501,506,500,506,501,501,505,505,493,514,500,506,500,504,1006.
40000200 Read-Ack Status: 00000010 00000000
494,515,502,505,502,1008,997,1016,501,505,499,507,501,500,507,505,492,514,501,506,500,502,505,505,494,512,501,506,1003,1009,496,511,500,506,501,505,501,506,1004,504,495,1015,501,506,499,507,501,500,506,506,492,514,501,505,501,502,504,506,1004.
D0010600 Write-Ack Control setpoint: 6.00
508,507,503,504,501,1009,497,510,500,498,508,506,501,505,499,508,500,500,507,505,501,505,1005,1004,505,505,493,514,1004,1006,503,505,495,511,501,506,500,506,501,505,497,510,500,499,508,505,501,505,499,508,500,501,506,505,493,514,500,506,500,503,1007.
C0110000 Read-Ack Relative modulation level: 0.00
510,1012,1000,1013,492,514,501,505,501,503,503,506,494,512,501,505,501,505,501,506,1004,504,495,1016,500,506,1004,1003,506,506,1004,504,503,504,498,508,502,497,509,1009,500,504,1006,1009,500,506,1004,504,503,1008,500,499,1011.
40193E4C Read-Ack Boiler water temperature: 62.30
493,516,501,505,503,1008,996,1016,501,505,498,509,501,499,507,505,501,505,500,507,1000,1012,493,513,501,506,501,503,503,505,495,512,500,506,1004,1009,496,510,500,498,1012,1009,498,508,501,500,506,506,492,514,501,505,501,502,504,506,1004.
D0101100 Write-Ack Room setpoint: 17.00
493,1020,1005,1008,500,498,509,505,501,506,498,508,500,500,507,505,493,514,500,506,501,501,505,505,494,513,500,506,501,503,503,505,496,511,500,506,501,505,501,505,498,508,998,1015,501,506,499,507,500,501,506,505,493,514,501,505,501,502,504,506,1004.
40000200 Read-Ack Status: 00000010 00000000
494,516,500,506,502,1008,1005,1008,501,505,497,509,501,498,508,506,501,505,499,507,501,500,506,506,492,514,501,506,1000,1012,493,513,501,505,501,504,502,506,1004,504,494,1017,500,506,497,509,501,498,508,505,501,506,499,507,501,500,506,505,1004.
D0010600 Write-Ack Control setpoint: 6.00
Opentherm gateway diagnostics - Version 1.1
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 2
490,518,488,1016,492,513,492,515,490,513,491,514,491,515,491,514,492,524,481,514,492,513,492,514,492,514,492,514,492,514,491,521,486,513,492,514,492,514,494,513,492,514,493,514,994,1018,491,514,492,513,492,514,492,514,491,514,493,513,491,514,492,516,993.
80000200 Read-Data Status: 00000010 00000000
501,1010,494,513,492,515,997,1019,492,515,493,520,487,515,493,515,492,515,492,515,492,515,492,515,493,515,492,515,995,1021,493,514,516,492,492,515,493,515,995,516,491,1019,492,515,511,496,492,516,492,515,492,516,492,516,492,516,492,514,996.
10010600 Write-Data Control setpoint: 6.00
491,1017,490,515,490,523,483,513,491,514,492,514,492,530,475,514,491,514,491,520,485,513,994,1016,493,512,492,514,993,1020,488,514,491,514,491,514,491,514,492,514,491,513,493,513,491,514,492,516,491,514,492,515,492,519,487,514,491,514,490,515,994.
00110000 Read-Data Relative modulation level: 0.00
456,515,492,1018,493,525,481,515,492,515,493,515,492,516,492,515,492,514,492,522,486,515,995,514,491,1017,492,514,994,1022,488,514,492,514,493,515,491,515,492,514,492,516,492,516,491,513,492,514,492,515,492,515,512,494,492,514,494,514,491,516,995.
80190000 Read-Data Boiler water temperature: 0.00
490,1018,491,513,493,513,492,513,492,513,492,522,484,513,492,514,492,513,994,515,492,1016,492,514,492,514,995,514,491,1017,519,487,492,514,492,514,491,514,492,515,491,515,492,514,514,492,491,514,493,513,492,514,491,514,493,513,492,514,511,495,994.
00630000 Read-Data Message ID 99: 0
490,516,489,1017,492,515,493,513,492,513,492,516,491,515,491,515,491,515,492,514,492,541,465,515,492,515,491,515,492,515,490,515,491,514,503,503,491,515,491,515,491,514,509,497,995,1017,499,506,492,514,492,514,492,515,492,514,493,514,491,514,496,510,1009.
80000200 Read-Data Status: 00000010 00000000
492,1018,491,514,492,514,1009,1003,491,515,491,514,492,514,492,514,493,513,493,523,481,514,491,514,493,515,490,514,994,1018,492,514,491,515,491,514,491,516,992,516,489,1019,492,513,492,514,491,514,492,515,490,514,516,489,491,515,490,515,993.
10010600 Write-Data Control setpoint: 6.00
492,1019,492,514,492,515,492,514,493,515,512,494,492,514,494,513,493,514,492,514,493,514,994,1018,492,516,491,514,995,1018,492,514,492,514,494,513,493,539,468,513,492,514,492,515,492,514,492,514,493,514,493,535,470,515,492,514,492,515,507,498,995.
00110000 Read-Data Relative modulation level: 0.00
500,506,491,1017,492,514,492,513,493,515,490,515,491,521,485,515,492,515,490,514,493,514,994,516,491,1017,491,515,994,1019,493,514,516,490,492,515,493,515,492,515,492,514,493,514,492,515,512,496,491,517,491,514,493,515,492,514,492,515,493,514,994.
80190000 Read-Data Boiler water temperature: 0.00
492,1020,491,515,492,514,493,541,466,515,492,514,492,514,492,516,491,515,491,515,1019,492,492,1018,493,514,
Opentherm gateway diagnostics - Version 1.1
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 5
Thermostat: 0.62, 0.63, 1.86
Boiler: 0.00, 3.47
Reference: 1.21
Opentherm gateway diagnostics - Version 1.1
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 6
B: 27.217
T: 914.841
B: 25.237
T: 918.213
B: 25.236
T: 917.613
B: 25.288
T: 917.910
B: 25.311
T: 917.864
B: 25.289
T: 917.316
B: 25.252
T: 919.500
B: 98.633
T: 842.934
B: 96.309
T: 846.916
B: 91.883
Opentherm gateway diagnostics - Version 1.1
I noticed you haven't made a comment on my results from test 4. The value for OK1A low-to-high is different from the other values. Is that good or bad?
The user in the topic you referred to had similar results.