Hi all!
Sometimes I see sporadic changes of remote override room setpoint. New value is fractional. I presume it's influence of electromagnetic fields or power violations. But log not contain any garbage. Value simply changes. Thermostat is Honeywell Round Modulation. Boiler is Baxi Main Four 240F.
Any help appreciated.
Sporadic shanges of remote override room setpoint.
Moderator: hvxl
Re: Sporadic shanges of remote override room setpoint.
At 14:31:49 Remote override room setpoint changes to 19.38 without any external action.
Code: Select all
14:31:25.961923 BD0010A00 Write-Ack Control setpoint: 10.00
14:31:26.800391 T80000200 Read-Data Status: 00000010 00000000
14:31:27.046132 B40000200 Read-Ack Status: 00000010 00000000
14:31:27.863133 T00090000 Read-Data Remote override room setpoint: 0.00
14:31:27.894585 R00030000 Read-Data Slave configuration: 00000000 0
14:31:28.121564 BC0030101 Read-Ack Slave configuration: 00000001 1
14:31:28.125791 AC0090000 Read-Ack Remote override room setpoint: 0.00
14:31:28.939421 T80190000 Read-Data Boiler water temperature: 0.00
14:31:29.187126 B40193600 Read-Ack Boiler water temperature: 54.00
14:31:30.011780 T10010A00 Write-Data Control setpoint: 10.00
14:31:30.277186 BD0010A00 Write-Ack Control setpoint: 10.00
14:31:31.103629 T80000200 Read-Data Status: 00000010 00000000
14:31:31.327919 B40000200 Read-Ack Status: 00000010 00000000
14:31:32.155013 T90101000 Write-Data Room setpoint: 16.00
14:31:32.163812 R801A0000 Read-Data DHW temperature: 0.00
14:31:32.436689 BC01A3400 Read-Ack DHW temperature: 52.00
14:31:32.437730 A50101000 Write-Ack Room setpoint: 16.00
14:31:33.235174 T80190000 Read-Data Boiler water temperature: 0.00
14:31:33.476728 B40193600 Read-Ack Boiler water temperature: 54.00
14:31:34.336326 T10010A00 Write-Data Control setpoint: 10.00
14:31:34.543167 BD0010A00 Write-Ack Control setpoint: 10.00
14:31:35.381881 T80000200 Read-Data Status: 00000010 00000000
14:31:35.630023 B40000284 Read-Ack Status: 00000010 10000100
14:31:36.446584 T9018170F Write-Data Room temperature: 23.06
14:31:36.487093 R80380000 Read-Data DHW setpoint: 0.00
14:31:36.710946 BC0383700 Read-Ack DHW setpoint: 55.00
14:31:36.711934 AF018170F Unk-DataId Room temperature: 23.06
14:31:37.509103 T80190000 Read-Data Boiler water temperature: 0.00
14:31:37.759086 B40193600 Read-Ack Boiler water temperature: 54.00
14:31:38.599966 T10010A00 Write-Data Control setpoint: 10.00
14:31:38.817956 BD0010A00 Write-Ack Control setpoint: 10.00
14:31:39.658298 T80000200 Read-Data Status: 00000010 00000000
14:31:39.892894 BC000028C Read-Ack Status: 00000010 10001100
14:31:40.755778 T00110000 Read-Data Relative modulation level: 0.00
14:31:40.978862 B40116400 Read-Ack Relative modulation level: 100.00
14:31:41.790733 T80190000 Read-Data Boiler water temperature: 0.00
14:31:42.035302 B40193600 Read-Ack Boiler water temperature: 54.00
14:31:42.876500 T10010A00 Write-Data Control setpoint: 10.00
14:31:43.131715 BD0010A00 Write-Ack Control setpoint: 10.00
14:31:43.945155 T80000200 Read-Data Status: 00000010 00000000
14:31:44.254733 BC0000208 Read-Ack Status: 00000010 00001000
14:31:45.035442 T00390000 Read-Data Max CH water setpoint: 0.00
14:31:45.249247 B4039004C Read-Ack Max CH water setpoint: 0.30
14:31:46.097038 T80190000 Read-Data Boiler water temperature: 0.00
14:31:46.383720 BC0193B00 Read-Ack Boiler water temperature: 59.00
14:31:47.161385 T10010A00 Write-Data Control setpoint: 10.00
14:31:47.387702 BD0010A00 Write-Ack Control setpoint: 10.00
14:31:48.239351 T80000200 Read-Data Status: 00000010 00000000
14:31:48.475277 B40000200 Read-Ack Status: 00000010 00000000
14:31:49.308222 T00090000 Read-Data Remote override room setpoint: 0.00
14:31:49.313922 R00030000 Read-Data Slave configuration: 00000000 0
14:31:49.537984 BC0030101 Read-Ack Slave configuration: 00000001 1
14:31:49.546444 AC0091260 Read-Ack Remote override room setpoint: 18.38
14:31:50.366899 T80190000 Read-Data Boiler water temperature: 0.00
14:31:50.631306 BC0193700 Read-Ack Boiler water temperature: 55.00
14:31:51.670457 T10010A00 Write-Data Control setpoint: 10.00
14:31:51.676503 BD0010A00 Write-Ack Control setpoint: 10.00
14:31:52.533647 T80000200 Read-Data Status: 00000010 00000000
14:31:52.759731 B40000200 Read-Ack Status: 00000010 00000000
14:31:53.600361 T90101000 Write-Data Room setpoint: 16.00
14:31:53.601273 R801A0000 Read-Data DHW temperature: 0.00
14:31:53.836766 BC01A2900 Read-Ack DHW temperature: 41.00
14:31:53.837666 A50101000 Write-Ack Room setpoint: 16.00
14:31:54.727949 T80190000 Read-Data Boiler water temperature: 0.00
14:31:54.951811 B40193600 Read-Ack Boiler water temperature: 54.00
14:31:55.791112 T10010A00 Write-Data Control setpoint: 10.00
14:31:56.116935 BD0010A00 Write-Ack Control setpoint: 10.00
14:31:56.901140 T80000200 Read-Data Status: 00000010 00000000
14:31:57.121154 B40000200 Read-Ack Status: 00000010 00000000
14:31:57.941468 T9018170F Write-Data Room temperature: 23.06
14:31:57.954356 R80380000 Read-Data DHW setpoint: 0.00
14:31:58.181168 BC0383700 Read-Ack DHW setpoint: 55.00
14:31:58.210129 AF018170F Unk-DataId Room temperature: 23.06
14:31:59.005117 T80190000 Read-Data Boiler water temperature: 0.00
14:31:59.242461 B40193600 Read-Ack Boiler water temperature: 54.00
14:32:00.081696 T10010A00 Write-Data Control setpoint: 10.00
14:32:00.302311 BD0010A00 Write-Ack Control setpoint: 10.00
14:32:01.157212 T80000200 Read-Data Status: 00000010 00000000
14:32:01.394219 B40000200 Read-Ack Status: 00000010 00000000
14:32:02.234213 T00110000 Read-Data Relative modulation level: 0.00
14:32:02.468298 BC0110000 Read-Ack Relative modulation level: 0.00
14:32:03.312247 T80190000 Read-Data Boiler water temperature: 0.00
14:32:03.548657 B40193600 Read-Ack Boiler water temperature: 54.00
14:32:04.375546 T10010A00 Write-Data Control setpoint: 10.00
14:32:04.626240 BD0010A00 Write-Ack Control setpoint: 10.00
14:32:05.434006 T80000200 Read-Data Status: 00000010 00000000
14:32:05.677678 B40000200 Read-Ack Status: 00000010 00000000
14:32:06.505524 T00390000 Read-Data Max CH water setpoint: 0.00
14:32:06.755627 B4039004C Read-Ack Max CH water setpoint: 0.30
14:32:07.584954 T80190000 Read-Data Boiler water temperature: 0.00
14:32:07.804145 B40193600 Read-Ack Boiler water temperature: 54.00
14:32:08.662636 T10010A00 Write-Data Control setpoint: 10.00
14:32:08.911165 BD0010A00 Write-Ack Control setpoint: 10.00
14:32:09.725794 T80000200 Read-Data Status: 00000010 00000000
14:32:09.964164 B40000200 Read-Ack Status: 00000010 00000000
14:32:10.799557 T00090000 Read-Data Remote override room setpoint: 0.00
14:32:10.800504 R00030000 Read-Data Slave configuration: 00000000 0
14:32:11.035807 BC0030101 Read-Ack Slave configuration: 00000001 1
14:32:11.036879 AC0091260 Read-Ack Remote override room setpoint: 18.38
14:32:11.875924 T80190000 Read-Data Boiler water temperature: 0.00
14:32:12.101598 B40193500 Read-Ack Boiler water temperature: 53.00
14:32:12.929198 T10010A00 Write-Data Control setpoint: 10.00
14:32:13.170701 BD0010A00 Write-Ack Control setpoint: 10.00
14:32:14.008581 T80000200 Read-Data Status: 00000010 00000000
14:32:14.338340 B40000200 Read-Ack Status: 00000010 00000000
14:32:15.109059 T90101000 Write-Data Room setpoint: 16.00
14:32:15.110093 R801A0000 Read-Data DHW temperature: 0.00
14:32:15.319639 BC01A2A00 Read-Ack DHW temperature: 42.00
14:32:15.336540 A50101000 Write-Ack Room setpoint: 16.00
14:32:16.199069 T80190000 Read-Data Boiler water temperature: 0.00
14:32:16.401210 B40193500 Read-Ack Boiler water temperature: 53.00
14:32:17.267991 T10010A00 Write-Data Control setpoint: 10.00
14:32:17.461502 BD0010A00 Write-Ack Control setpoint: 10.00
14:32:18.400104 T80000200 Read-Data Status: 00000010 00000000
14:32:18.581310 B40000200 Read-Ack Status: 00000010 00000000
14:32:19.431446 T9018170F Write-Data Room temperature: 23.06
14:32:19.438409 R80380000 Read-Data DHW setpoint: 0.00
14:32:19.677239 BC0383700 Read-Ack DHW setpoint: 55.00
14:32:19.679468 AF018170F Unk-DataId Room temperature: 23.06
14:32:20.507040 T80190000 Read-Data Boiler water temperature: 0.00
14:32:20.782833 B40193500 Read-Ack Boiler water temperature: 53.00
14:32:21.597537 T10010A00 Write-Data Control setpoint: 10.00
14:32:21.802960 BD0010A00 Write-Ack Control setpoint: 10.00
14:32:22.656066 T80000200 Read-Data Status: 00000010 00000000
14:32:22.894722 B40000200 Read-Ack Status: 00000010 00000000
14:32:23.722142 T00110000 Read-Data Relative modulation level: 0.00
14:32:23.949628 BC0110000 Read-Ack Relative modulation level: 0.00
14:32:24.784340 T80190000 Read-Data Boiler water temperature: 0.00
14:32:25.029154 B40193500 Read-Ack Boiler water temperature: 53.00
14:32:25.870638 T10010A00 Write-Data Control setpoint: 10.00
14:32:26.102281 BD0010A00 Write-Ack Control setpoint: 10.00
14:32:26.938568 T80000200 Read-Data Status: 00000010 00000000
14:32:27.161179 B40000200 Read-Ack Status: 00000010 00000000
14:32:28.022092 T00390000 Read-Data Max CH water setpoint: 0.00
14:32:28.285267 B4039004C Read-Ack Max CH water setpoint: 0.30
14:32:29.067279 T80190000 Read-Data Boiler water temperature: 0.00
14:32:29.305880 B40193600 Read-Ack Boiler water temperature: 54.00
14:32:30.177142 T10010A00 Write-Data Control setpoint: 10.00
14:32:30.383977 BD0010A00 Write-Ack Control setpoint: 10.00
14:32:31.222721 T80000200 Read-Data Status: 00000010 00000000
14:32:31.445054 B40000200 Read-Ack Status: 00000010 00000000
14:32:32.288282 T00090000 Read-Data Remote override room setpoint: 0.00
14:32:32.383337 R00030000 Read-Data Slave configuration: 00000000 0
14:32:32.536139 BC0030101 Read-Ack Slave configuration: 00000001 1
14:32:32.541022 AC0091260 Read-Ack Remote override room setpoint: 18.38
14:32:33.375682 T80190000 Read-Data Boiler water temperature: 0.00
14:32:33.583997 BC0193700 Read-Ack Boiler water temperature: 55.00
14:32:34.432396 T10010A00 Write-Data Control setpoint: 10.00
14:32:34.685580 BD0010A00 Write-Ack Control setpoint: 10.00
14:32:35.496990 T80000200 Read-Data Status: 00000010 00000000
14:32:35.752540 B40000200 Read-Ack Status: 00000010 00000000
14:32:36.572480 T90101000 Write-Data Room setpoint: 16.00
14:32:36.579600 R801A0000 Read-Data DHW temperature: 0.00
14:32:36.813262 B401A3000 Read-Ack DHW temperature: 48.00
14:32:36.819247 A50101000 Write-Ack Room setpoint: 16.00
14:32:37.655584 T80190000 Read-Data Boiler water temperature: 0.00
14:32:37.887637 BC0193700 Read-Ack Boiler water temperature: 55.00
14:32:38.717719 T10010A00 Write-Data Control setpoint: 10.00
14:32:38.943127 BD0010A00 Write-Ack Control setpoint: 10.00
14:32:39.800883 T80000200 Read-Data Status: 00000010 00000000
14:32:40.030928 B40000200 Read-Ack Status: 00000010 00000000
14:32:40.878134 T90181711 Write-Data Room temperature: 23.07
14:32:40.879368 R80380000 Read-Data DHW setpoint: 0.00
14:32:41.103468 BC0383700 Read-Ack DHW setpoint: 55.00
14:32:41.117100 AF0181711 Unk-DataId Room temperature: 23.07
14:32:41.936519 T80190000 Read-Data Boiler water temperature: 0.00
14:32:42.214404 BC0193800 Read-Ack Boiler water temperature: 56.00
14:32:43.004076 T10010A00 Write-Data Control setpoint: 10.00
14:32:43.275968 BD0010A00 Write-Ack Control setpoint: 10.00
14:32:44.068444 T80000200 Read-Data Status: 00000010 00000000
14:32:44.340069 B40000200 Read-Ack Status: 00000010 00000000
14:32:45.154773 T00110000 Read-Data Relative modulation level: 0.00
14:32:45.401498 BC0110000 Read-Ack Relative modulation level: 0.00
14:32:46.237826 T80190000 Read-Data Boiler water temperature: 0.00
14:32:46.456930 BC0193800 Read-Ack Boiler water temperature: 56.00
14:32:47.282200 T10010A00 Write-Data Control setpoint: 10.00
14:32:47.523158 BD0010A00 Write-Ack Control setpoint: 10.00
14:32:48.390947 T80000200 Read-Data Status: 00000010 00000000
14:32:48.597281 B40000200 Read-Ack Status: 00000010 00000000
14:32:49.431909 T00390000 Read-Data Max CH water setpoint: 0.00
14:32:49.664077 B4039004C Read-Ack Max CH water setpoint: 0.30
14:32:50.500950 T80190000 Read-Data Boiler water temperature: 0.00
14:32:50.803235 BC0193800 Read-Ack Boiler water temperature: 56.00
14:32:51.572141 T10010A00 Write-Data Control setpoint: 10.00
14:32:51.816885 BD0010A00 Write-Ack Control setpoint: 10.00
14:32:52.643668 T80000200 Read-Data Status: 00000010 00000000
14:32:52.890010 B40000200 Read-Ack Status: 00000010 00000000
14:32:53.725282 T00090000 Read-Data Remote override room setpoint: 0.00
14:32:53.726317 R00030000 Read-Data Slave configuration: 00000000 0
14:32:53.985875 BC0030101 Read-Ack Slave configuration: 00000001 1
14:32:53.986953 AC0091260 Read-Ack Remote override room setpoint: 18.38
14:32:54.786809 T80190000 Read-Data Boiler water temperature: 0.00
14:32:55.026541 BC0193800 Read-Ack Boiler water temperature: 56.00
14:32:55.854768 T10015A00 Write-Data Control setpoint: 90.00
14:32:56.087313 BD0015A00 Write-Ack Control setpoint: 90.00
14:32:56.926922 T80000200 Read-Data Status: 00000010 00000000
14:32:57.184249 B40000284 Read-Ack Status: 00000010 10000100
14:32:58.022215 T9010125E Write-Data Room setpoint: 18.37
14:32:58.026762 R801A0000 Read-Data DHW temperature: 0.00
14:32:58.356521 B401A3300 Read-Ack DHW temperature: 51.00
14:32:58.357393 A5010125E Write-Ack Room setpoint: 18.37
14:32:59.073817 T80190000 Read-Data Boiler water temperature: 0.00
14:32:59.305543 BC0193800 Read-Ack Boiler water temperature: 56.00
14:33:00.146638 T10010A00 Write-Data Control setpoint: 10.00
14:33:00.420072 BD0010A00 Write-Ack Control setpoint: 10.00
14:33:01.228248 T80000200 Read-Data Status: 00000010 00000000
14:33:01.458718 B40000200 Read-Ack Status: 00000010 00000000
14:33:02.284601 T90181711 Write-Data Room temperature: 23.07
14:33:02.363697 R80380000 Read-Data DHW setpoint: 0.00
14:33:02.546095 BC0383700 Read-Ack DHW setpoint: 55.00
14:33:02.547155 AF0181711 Unk-DataId Room temperature: 23.07
14:33:03.364248 T80190000 Read-Data Boiler water temperature: 0.00
14:33:03.588332 BC0193400 Read-Ack Boiler water temperature: 52.00
14:33:04.473864 T10010A00 Write-Data Control setpoint: 10.00
14:33:04.706409 BD0010A00 Write-Ack Control setpoint: 10.00
14:33:05.510090 T80000200 Read-Data Status: 00000010 00000000
14:33:05.733060 B40000200 Read-Ack Status: 00000010 00000000
14:33:06.584159 T00110000 Read-Data Relative modulation level: 0.00
14:33:06.831921 BC0110000 Read-Ack Relative modulation level: 0.00
14:33:07.646426 T80190000 Read-Data Boiler water temperature: 0.00
14:33:07.877019 B40192E00 Read-Ack Boiler water temperature: 46.00
14:33:08.725187 T10010A00 Write-Data Control setpoint: 10.00
14:33:08.969193 BD0010A00 Write-Ack Control setpoint: 10.00
14:33:09.799536 T80000200 Read-Data Status: 00000010 00000000
14:33:10.032907 B40000200 Read-Ack Status: 00000010 00000000
14:33:10.862660 T00390000 Read-Data Max CH water setpoint: 0.00
14:33:11.089187 B4039004C Read-Ack Max CH water setpoint: 0.30
14:33:12.075547 T80190000 Read-Data Boiler water temperature: 0.00
14:33:12.216697 BC0192C00 Read-Ack Boiler water temperature: 44.00
14:33:13.003552 T10010A00 Write-Data Control setpoint: 10.00
14:33:13.240507 BD0010A00 Write-Ack Control setpoint: 10.00
14:33:14.068631 T80000200 Read-Data Status: 00000010 00000000
14:33:14.389741 B40000200 Read-Ack Status: 00000010 00000000
14:33:15.207225 T00090000 Read-Data Remote override room setpoint: 0.00
14:33:15.218084 R00030000 Read-Data Slave configuration: 00000000 0
14:33:15.450151 BC0030101 Read-Ack Slave configuration: 00000001 1
14:33:15.482635 AC0091260 Read-Ack Remote override room setpoint: 18.38
14:33:16.281137 T80190000 Read-Data Boiler water temperature: 0.00
14:33:16.527330 BC0192C00 Read-Ack Boiler water temperature: 44.00
14:33:17.348513 T10010A00 Write-Data Control setpoint: 10.00
14:33:17.603074 BD0010A00 Write-Ack Control setpoint: 10.00
14:33:18.453522 T80000200 Read-Data Status: 00000010 00000000
14:33:18.698763 B40000200 Read-Ack Status: 00000010 00000000
14:33:19.489686 T9010125E Write-Data Room setpoint: 18.37
14:33:19.505878 R801A0000 Read-Data DHW temperature: 0.00
14:33:19.743374 BC01A2900 Read-Ack DHW temperature: 41.00
14:33:19.744420 A5010125E Write-Ack Room setpoint: 18.37
14:33:20.571060 T80190000 Read-Data Boiler water temperature: 0.00
14:33:20.805599 BC0192C00 Read-Ack Boiler water temperature: 44.00
14:33:21.647182 T10010A00 Write-Data Control setpoint: 10.00
14:33:21.885622 BD0010A00 Write-Ack Control setpoint: 10.00
14:33:22.730191 T80000200 Read-Data Status: 00000010 00000000
14:33:23.026908 B40000200 Read-Ack Status: 00000010 00000000
14:33:23.794593 T90181714 Write-Data Room temperature: 23.08
14:33:23.795702 R80380000 Read-Data DHW setpoint: 0.00
14:33:24.020137 BC0383700 Read-Ack DHW setpoint: 55.00
14:33:24.047059 AF0181714 Unk-DataId Room temperature: 23.08
14:33:24.926070 T80190000 Read-Data Boiler water temperature: 0.00
14:33:25.156377 BC0192C00 Read-Ack Boiler water temperature: 44.00
14:33:26.046921 T10010A00 Write-Data Control setpoint: 10.00
14:33:26.283385 BD0010A00 Write-Ack Control setpoint: 10.00
14:33:27.068276 T80000200 Read-Data Status: 00000010 00000000
14:33:27.301482 B40000200 Read-Ack Status: 00000010 00000000
14:33:28.178533 T00110000 Read-Data Relative modulation level: 0.00
14:33:28.385297 BC0110000 Read-Ack Relative modulation level: 0.00
14:33:29.205883 T80190000 Read-Data Boiler water temperature: 0.00
14:33:29.440156 BC0192C00 Read-Ack Boiler water temperature: 44.00
14:33:30.326153 T10010A00 Write-Data Control setpoint: 10.00
14:33:30.515817 BD0010A00 Write-Ack Control setpoint: 10.00
14:33:31.339792 T80000200 Read-Data Status: 00000010 00000000
14:33:31.579972 B40000200 Read-Ack Status: 00000010 00000000
14:33:32.425772 T00390000 Read-Data Max CH water setpoint: 0.00
14:33:32.656596 B4039004C Read-Ack Max CH water setpoint: 0.30
14:33:33.495243 T80190000 Read-Data Boiler water temperature: 0.00
14:33:33.725761 BC0192C00 Read-Ack Boiler water temperature: 44.00
14:33:34.584068 T10010A00 Write-Data Control setpoint: 10.00
14:33:34.825195 BD0010A00 Write-Ack Control setpoint: 10.00
14:33:35.702056 T80000200 Read-Data Status: 00000010 00000000
14:33:35.955318 B40000200 Read-Ack Status: 00000010 00000000
14:33:36.773809 T00090000 Read-Data Remote override room setpoint: 0.00
14:33:36.809979 R00030000 Read-Data Slave configuration: 00000000 0
14:33:37.000543 BC0030101 Read-Ack Slave configuration: 00000001 1
14:33:37.012662 AC0091260 Read-Ack Remote override room setpoint: 18.38
14:33:37.842657 T80190000 Read-Data Boiler water temperature: 0.00
14:33:38.094411 B40192B00 Read-Ack Boiler water temperature: 43.00
14:33:38.911807 T10010A00 Write-Data Control setpoint: 10.00
14:33:39.144638 BD0010A00 Write-Ack Control setpoint: 10.00
14:33:39.984059 T80000200 Read-Data Status: 00000010 00000000
14:33:40.276241 B40000200 Read-Ack Status: 00000010 00000000
14:33:41.051529 T9010125E Write-Data Room setpoint: 18.37
14:33:41.086568 R801A0000 Read-Data DHW temperature: 0.00
14:33:41.282459 BC01A2600 Read-Ack DHW temperature: 38.00
14:33:41.300943 A5010125E Write-Ack Room setpoint: 18.37
14:33:42.141427 T80190000 Read-Data Boiler water temperature: 0.00
14:33:42.384069 B40192B00 Read-Ack Boiler water temperature: 43.00
14:33:43.193896 T10010A00 Write-Data Control setpoint: 10.00
14:33:43.446947 BD0010A00 Write-Ack Control setpoint: 10.00
14:33:44.328309 T80000200 Read-Data Status: 00000010 00000000
14:33:44.503913 B40000200 Read-Ack Status: 00000010 00000000
14:33:45.338472 T90181714 Write-Data Room temperature: 23.08
14:33:45.369278 R80380000 Read-Data DHW setpoint: 0.00
14:33:45.596023 BC0383700 Read-Ack DHW setpoint: 55.00
14:33:45.600064 AF0181714 Unk-DataId Room temperature: 23.08
14:33:46.476344 T80190000 Read-Data Boiler water temperature: 0.00
14:33:46.698459 B40192B00 Read-Ack Boiler water temperature: 43.00
14:33:47.545870 T10010A00 Write-Data Control setpoint: 10.00
14:33:47.786726 BD0010A00 Write-Ack Control setpoint: 10.00
14:33:48.619004 T80000200 Read-Data Status: 00000010 00000000
14:33:48.867717 B40000200 Read-Ack Status: 00000010 00000000
14:33:49.695279 T00110000 Read-Data Relative modulation level: 0.00
14:33:49.924423 BC0110000 Read-Ack Relative modulation level: 0.00
14:33:50.788776 T80190000 Read-Data Boiler water temperature: 0.00
14:33:51.005039 B40192B00 Read-Ack Boiler water temperature: 43.00
14:33:51.854954 T10010A00 Write-Data Control setpoint: 10.00
14:33:52.066231 BD0010A00 Write-Ack Control setpoint: 10.00
14:33:52.906958 T80000200 Read-Data Status: 00000010 00000000
14:33:53.157632 B40000200 Read-Ack Status: 00000010 00000000
14:33:54.159831 T00390000 Read-Data Max CH water setpoint: 0.00
14:33:54.208621 B4039004C Read-Ack Max CH water setpoint: 0.30
14:33:55.041424 T80190000 Read-Data Boiler water temperature: 0.00
14:33:55.284335 BC0192A00 Read-Ack Boiler water temperature: 42.00
14:33:56.157447 T10010A00 Write-Data Control setpoint: 10.00
14:33:56.370426 BD0010A00 Write-Ack Control setpoint: 10.00
14:33:57.187753 T80000200 Read-Data Status: 00000010 00000000
14:33:57.424987 B40000200 Read-Ack Status: 00000010 00000000
14:33:58.273421 T00090000 Read-Data Remote override room setpoint: 0.00
14:33:58.366204 R00030000 Read-Data Slave configuration: 00000000 0
14:33:58.518721 BC0030101 Read-Ack Slave configuration: 00000001 1
14:33:58.519708 AC0091260 Read-Ack Remote override room setpoint: 18.38
14:33:59.340432 T80190000 Read-Data Boiler water temperature: 0.00
14:33:59.568663 BC0192A00 Read-Ack Boiler water temperature: 42.00
14:34:00.406895 T10010A00 Write-Data Control setpoint: 10.00
14:34:00.640590 BD0010A00 Write-Ack Control setpoint: 10.00
14:34:01.479685 T80000200 Read-Data Status: 00000010 00000000
14:34:01.703619 B40000200 Read-Ack Status: 00000010 00000000
14:34:02.540429 T9010125E Write-Data Room setpoint: 18.37
14:34:02.566096 R801A0000 Read-Data DHW temperature: 0.00
14:34:02.791661 BC01A1F00 Read-Ack DHW temperature: 31.00
14:34:02.802099 A5010125E Write-Ack Room setpoint: 18.37
14:34:03.625644 T80190000 Read-Data Boiler water temperature: 0.00
14:34:03.876698 BC0192A00 Read-Ack Boiler water temperature: 42.00
14:34:04.726504 T10010A00 Write-Data Control setpoint: 10.00
14:34:04.924613 BD0010A00 Write-Ack Control setpoint: 10.00
14:34:05.769283 T80000200 Read-Data Status: 00000010 00000000
14:34:06.049332 B40000200 Read-Ack Status: 00000010 00000000
14:34:06.847251 T90181717 Write-Data Room temperature: 23.09
14:34:06.848355 R80380000 Read-Data DHW setpoint: 0.00
14:34:07.059298 BC0383700 Read-Ack DHW setpoint: 55.00
14:34:07.085847 AF0181717 Unk-DataId Room temperature: 23.09
14:34:07.904459 T80190000 Read-Data Boiler water temperature: 0.00
14:34:08.186334 BC0192A00 Read-Ack Boiler water temperature: 42.00
14:34:08.976701 T10010A00 Write-Data Control setpoint: 10.00
14:34:09.206463 BD0010A00 Write-Ack Control setpoint: 10.00
14:34:10.041563 T80000200 Read-Data Status: 00000010 00000000
14:34:10.343088 B40000200 Read-Ack Status: 00000010 00000000
14:34:11.124007 T00110000 Read-Data Relative modulation level: 0.00
14:34:11.361650 BC0110000 Read-Ack Relative modulation level: 0.00
14:34:12.226252 T80190000 Read-Data Boiler water temperature: 0.00
14:34:12.467898 BC0192A00 Read-Ack Boiler water temperature: 42.00
14:34:13.292890 T10010A00 Write-Data Control setpoint: 10.00
14:34:13.545093 BD0010A00 Write-Ack Control setpoint: 10.00
14:34:14.341689 T80000200 Read-Data Status: 00000010 00000000
14:34:14.568294 B40000200 Read-Ack Status: 00000010 00000000
14:34:15.403151 T00390000 Read-Data Max CH water setpoint: 0.00
14:34:15.649637 B4039004C Read-Ack Max CH water setpoint: 0.30
14:34:16.476205 T80190000 Read-Data Boiler water temperature: 0.00
14:34:16.711927 BC0192A00 Read-Ack Boiler water temperature: 42.00
14:34:17.570404 T10010A00 Write-Data Control setpoint: 10.00
14:34:17.794898 BD0010A00 Write-Ack Control setpoint: 10.00
14:34:18.635247 T80000200 Read-Data Status: 00000010 00000000
14:34:18.847759 B40000200 Read-Ack Status: 00000010 00000000
14:34:19.691335 T00090000 Read-Data Remote override room setpoint: 0.00
14:34:19.703967 R00030000 Read-Data Slave configuration: 00000000 0
14:34:19.938454 BC0030101 Read-Ack Slave configuration: 00000001 1
14:34:19.939485 AC0091260 Read-Ack Remote override room setpoint: 18.38
14:34:20.760807 T80190000 Read-Data Boiler water temperature: 0.00
14:34:21.004638 BC0192A00 Read-Ack Boiler water temperature: 42.00
14:34:21.836453 T10010A00 Write-Data Control setpoint: 10.00
14:34:22.066605 BD0010A00 Write-Ack Control setpoint: 10.00
14:34:22.898589 T80000200 Read-Data Status: 00000010 00000000
14:34:23.159522 B40000200 Read-Ack Status: 00000010 00000000
14:34:23.974688 T9010125E Write-Data Room setpoint: 18.37
14:34:23.981895 R801A0000 Read-Data DHW temperature: 0.00
14:34:24.239751 B401A2100 Read-Ack DHW temperature: 33.00
14:34:24.240645 A5010125E Write-Ack Room setpoint: 18.37
14:34:25.056737 T80190000 Read-Data Boiler water temperature: 0.00
14:34:25.284028 BC0192900 Read-Ack Boiler water temperature: 41.00
14:34:26.152696 T10010A00 Write-Data Control setpoint: 10.00
14:34:26.370228 BD0010A00 Write-Ack Control setpoint: 10.00
14:34:27.189128 T80000200 Read-Data Status: 00000010 00000000
14:34:27.436005 B40000200 Read-Ack Status: 00000010 00000000
14:34:28.333831 T90181717 Write-Data Room temperature: 23.09
14:34:28.334821 R80380000 Read-Data DHW setpoint: 0.00
14:34:28.505773 BC0383700 Read-Ack DHW setpoint: 55.00
14:34:28.626465 AF0181717 Unk-DataId Room temperature: 23.09
14:34:29.353313 T80190000 Read-Data Boiler water temperature: 0.00
14:34:29.583232 BC0192900 Read-Ack Boiler water temperature: 41.00
14:34:30.398246 T10010A00 Write-Data Control setpoint: 10.00
14:34:30.674865 BD0010A00 Write-Ack Control setpoint: 10.00
14:34:31.476709 T80000200 Read-Data Status: 00000010 00000000
14:34:31.712801 B40000200 Read-Ack Status: 00000010 00000000
14:34:32.552355 T00110000 Read-Data Relative modulation level: 0.00
14:34:32.785701 BC0110000 Read-Ack Relative modulation level: 0.00
14:34:33.613489 T80190000 Read-Data Boiler water temperature: 0.00
14:34:33.851117 BC0192900 Read-Ack Boiler water temperature: 41.00
14:34:34.696145 T10010A00 Write-Data Control setpoint: 10.00
14:34:34.934854 BD0010A00 Write-Ack Control setpoint: 10.00
14:34:35.768406 T80000200 Read-Data Status: 00000010 00000000
14:34:35.983969 B40000200 Read-Ack Status: 00000010 00000000
14:34:36.861478 T00390000 Read-Data Max CH water setpoint: 0.00
14:34:37.067185 B4039004C Read-Ack Max CH water setpoint: 0.30
14:34:37.905170 T80190000 Read-Data Boiler water temperature: 0.00
14:34:38.208491 BC0192900 Read-Ack Boiler water temperature: 41.00
14:34:38.985882 T10010A00 Write-Data Control setpoint: 10.00
14:34:39.284385 BD0010A00 Write-Ack Control setpoint: 10.00
14:34:40.053161 T80000200 Read-Data Status: 00000010 00000000
14:34:40.331764 B40000200 Read-Ack Status: 00000010 00000000
14:34:41.121600 T00090000 Read-Data Remote override room setpoint: 0.00
14:34:41.128694 R00030000 Read-Data Slave configuration: 00000000 0
14:34:41.360230 BC0030101 Read-Ack Slave configuration: 00000001 1
14:34:41.361489 AC0091260 Read-Ack Remote override room setpoint: 18.38
14:34:42.263830 T80190000 Read-Data Boiler water temperature: 0.00
14:34:42.630487 B40192800 Read-Ack Boiler water temperature: 40.00
14:34:43.275083 T10010A00 Write-Data Control setpoint: 10.00
14:34:43.507850 BD0010A00 Write-Ack Control setpoint: 10.00
14:34:44.333418 T80000200 Read-Data Status: 00000010 00000000
14:34:44.569096 B40000200 Read-Ack Status: 00000010 00000000
14:34:45.404914 T9010125E Write-Data Room setpoint: 18.37
14:34:45.412122 R801A0000 Read-Data DHW temperature: 0.00
14:34:45.650613 B401A2100 Read-Ack DHW temperature: 33.00
14:34:45.660581 A5010125E Write-Ack Room setpoint: 18.37
14:34:46.486224 T80190000 Read-Data Boiler water temperature: 0.00
14:34:46.714345 B40192800 Read-Ack Boiler water temperature: 40.00
14:34:47.575745 T10010A00 Write-Data Control setpoint: 10.00
14:34:47.793472 BD0010A00 Write-Ack Control setpoint: 10.00
14:34:48.626072 T80000200 Read-Data Status: 00000010 00000000
14:34:48.849679 B40000200 Read-Ack Status: 00000010 00000000
14:34:49.703975 T10181719 Write-Data Room temperature: 23.10
14:34:49.705082 R80380000 Read-Data DHW setpoint: 0.00
14:34:49.925182 BC0383700 Read-Ack DHW setpoint: 55.00
14:34:49.939465 A70181719 Unk-DataId Room temperature: 23.10
14:34:50.774350 T80190000 Read-Data Boiler water temperature: 0.00
14:34:51.010138 B40192800 Read-Ack Boiler water temperature: 40.00
14:34:51.835329 T10010A00 Write-Data Control setpoint: 10.00
14:34:52.070401 BD0010A00 Write-Ack Control setpoint: 10.00
14:34:52.938508 T80000200 Read-Data Status: 00000010 00000000
14:34:53.151775 B40000200 Read-Ack Status: 00000010 00000000
14:34:54.054964 T00110000 Read-Data Relative modulation level: 0.00
14:34:54.318403 BC0110000 Read-Ack Relative modulation level: 0.00
14:34:55.140669 T80190000 Read-Data Boiler water temperature: 0.00
14:34:55.354170 B40192700 Read-Ack Boiler water temperature: 39.00
14:34:56.206201 T10010A00 Write-Data Control setpoint: 10.00
14:34:56.448475 BD0010A00 Write-Ack Control setpoint: 10.00
14:34:57.255168 T80000200 Read-Data Status: 00000010 00000000
14:34:57.498322 B40000200 Read-Ack Status: 00000010 00000000
14:34:58.324141 T00390000 Read-Data Max CH water setpoint: 0.00
14:34:58.582507 B4039004C Read-Ack Max CH water setpoint: 0.30
14:34:59.410499 T80190000 Read-Data Boiler water temperature: 0.00
14:34:59.632216 B40192700 Read-Ack Boiler water temperature: 39.00
14:35:00.476405 T10010A00 Write-Data Control setpoint: 10.00
14:35:00.714689 BD0010A00 Write-Ack Control setpoint: 10.00
14:35:01.707601 T80000200 Read-Data Status: 00000010 00000000
14:35:01.825013 B40000200 Read-Ack Status: 00000010 00000000
14:35:01.826683 Command (via relay server, from 10.10.100.3:42322): PS=1
14:35:01.872404 PS: 1
14:35:01.999597 00000010/00000000,10.00,00000000/00000000,0.00,0/0,18.37,0.00,0.00,23.10,39.00,33.00,19.38,0.00,0/0,0/0,55.00,0.30,0,0,0,0,0,0,0,0
14:35:02.896938 Command (via relay server, from 10.10.100.3:42323): PS=0
14:35:02.996623 PS: 0
14:35:03.697008 T80190000 Read-Data Boiler water temperature: 0.00
14:35:03.926248 B40192700 Read-Ack Boiler water temperature: 39.00
14:35:04.756256 T10010A00 Write-Data Control setpoint: 10.00
14:35:04.984357 BD0010A00 Write-Ack Control setpoint: 10.00
14:35:05.834197 T80000200 Read-Data Status: 00000010 00000000
14:35:06.076331 B40000200 Read-Ack Status: 00000010 00000000
14:35:06.940534 T9010125E Write-Data Room setpoint: 18.37
14:35:06.941540 R801A0000 Read-Data DHW temperature: 0.00
14:35:07.185683 BC01A2000 Read-Ack DHW temperature: 32.00
14:35:07.186571 A5010125E Write-Ack Room setpoint: 18.37
14:35:07.985776 T80190000 Read-Data Boiler water temperature: 0.00
14:35:08.310022 BC0192600 Read-Ack Boiler water temperature: 38.00
14:35:09.038523 T10010A00 Write-Data Control setpoint: 10.00
14:35:09.286064 BD0010A00 Write-Ack Control setpoint: 10.00
14:35:10.121783 T80000200 Read-Data Status: 00000010 00000000
14:35:10.345299 B40000200 Read-Ack Status: 00000010 00000000
14:35:11.185712 T10181719 Write-Data Room temperature: 23.10
14:35:11.195729 R80380000 Read-Data DHW setpoint: 0.00
14:35:11.427743 BC0383700 Read-Ack DHW setpoint: 55.00
14:35:11.448529 A70181719 Unk-DataId Room temperature: 23.10
14:35:12.284363 T80190000 Read-Data Boiler water temperature: 0.00
14:35:12.488415 BC0192600 Read-Ack Boiler water temperature: 38.00
14:35:13.338507 T10010A00 Write-Data Control setpoint: 10.00
14:35:13.599333 BD0010A00 Write-Ack Control setpoint: 10.00
14:35:14.428282 T80000200 Read-Data Status: 00000010 00000000
14:35:14.656644 B40000200 Read-Ack Status: 00000010 00000000
14:35:15.470942 T00110000 Read-Data Relative modulation level: 0.00
14:35:15.708507 BC0110000 Read-Ack Relative modulation level: 0.00
14:35:16.543880 T80190000 Read-Data Boiler water temperature: 0.00
14:35:16.781736 BC0192600 Read-Ack Boiler water temperature: 38.00
14:35:17.615597 T10010A00 Write-Data Control setpoint: 10.00
14:35:17.843385 BD0010A00 Write-Ack Control setpoint: 10.00
14:35:18.686695 T80000200 Read-Data Status: 00000010 00000000
14:35:18.918938 B40000200 Read-Ack Status: 00000010 00000000
14:35:19.749776 T00390000 Read-Data Max CH water setpoint: 0.00
14:35:19.984658 B4039004C Read-Ack Max CH water setpoint: 0.30
14:35:20.828011 T80190000 Read-Data Boiler water temperature: 0.00
14:35:21.061705 BC0192600 Read-Ack Boiler water temperature: 38.00
14:35:21.907381 T10010A00 Write-Data Control setpoint: 10.00
14:35:22.161795 BD0010A00 Write-Ack Control setpoint: 10.00
14:35:22.965907 T80000200 Read-Data Status: 00000010 00000000
14:35:23.242601 B40000200 Read-Ack Status: 00000010 00000000
14:35:24.054975 T00090000 Read-Data Remote override room setpoint: 0.00
14:35:24.055869 R00030000 Read-Data Slave configuration: 00000000 0
14:35:24.280606 BC0030101 Read-Ack Slave configuration: 00000001 1
14:35:24.290815 AC0091260 Read-Ack Remote override room setpoint: 18.38
14:35:25.120978 T80190000 Read-Data Boiler water temperature: 0.00
14:35:25.340777 BC0192600 Read-Ack Boiler water temperature: 38.00
14:35:26.219673 T10010A00 Write-Data Control setpoint: 10.00
14:35:26.425151 BD0010A00 Write-Ack Control setpoint: 10.00
14:35:27.256919 T80000200 Read-Data Status: 00000010 00000000
14:35:27.503271 B40000200 Read-Ack Status: 00000010 00000000
14:35:28.352099 T9010125E Write-Data Room setpoint: 18.37
14:35:28.353117 R801A0000 Read-Data DHW temperature: 0.00
14:35:28.578224 BC01A1F00 Read-Ack DHW temperature: 31.00
14:35:28.581290 A5010125E Write-Ack Room setpoint: 18.37
14:35:29.396786 T80190000 Read-Data Boiler water temperature: 0.00
14:35:29.642590 BC0192500 Read-Ack Boiler water temperature: 37.00
14:35:30.471243 T10010A00 Write-Data Control setpoint: 10.00
14:35:30.699455 BD0010A00 Write-Ack Control setpoint: 10.00
14:35:31.535636 T80000200 Read-Data Status: 00000010 00000000
14:35:31.799294 B40000200 Read-Ack Status: 00000010 00000000
14:35:32.614183 T10181719 Write-Data Room temperature: 23.10
14:35:32.621585 R80380000 Read-Data DHW setpoint: 0.00
14:35:32.882264 BC0383700 Read-Ack DHW setpoint: 55.00
14:35:32.883389 A70181719 Unk-DataId Room temperature: 23.10
14:35:33.704794 T80190000 Read-Data Boiler water temperature: 0.00
14:35:33.926912 BC0192500 Read-Ack Boiler water temperature: 37.00
14:35:34.755586 T10010A00 Write-Data Control setpoint: 10.00
14:35:35.006462 BD0010A00 Write-Ack Control setpoint: 10.00
14:35:35.826816 T80000200 Read-Data Status: 00000010 00000000
14:35:36.057730 B40000200 Read-Ack Status: 00000010 00000000
14:35:36.897457 T00110000 Read-Data Relative modulation level: 0.00
14:35:37.135417 BC0110000 Read-Ack Relative modulation level: 0.00
14:35:37.988545 T80190000 Read-Data Boiler water temperature: 0.00
14:35:38.255001 BC0192500 Read-Ack Boiler water temperature: 37.00
14:35:39.038932 T10010A00 Write-Data Control setpoint: 10.00
14:35:39.283954 BD0010A00 Write-Ack Control setpoint: 10.00
14:35:40.171230 T80000200 Read-Data Status: 00000010 00000000
14:35:40.363352 B40000200 Read-Ack Status: 00000010 00000000
14:35:41.182048 T00390000 Read-Data Max CH water setpoint: 0.00
14:35:41.412581 B4039004C Read-Ack Max CH water setpoint: 0.30
14:35:42.266054 T80190000 Read-Data Boiler water temperature: 0.00
14:35:42.504372 BC0192500 Read-Ack Boiler water temperature: 37.00
14:35:43.335697 T10010A00 Write-Data Control setpoint: 10.00
14:35:43.562207 BD0010A00 Write-Ack Control setpoint: 10.00
14:35:44.405142 T80000200 Read-Data Status: 00000010 00000000
14:35:44.641824 B40000200 Read-Ack Status: 00000010 00000000
14:35:45.476495 T00090000 Read-Data Remote override room setpoint: 0.00
14:35:45.477448 R00030000 Read-Data Slave configuration: 00000000 0
14:35:45.724389 BC0030101 Read-Ack Slave configuration: 00000001 1
14:35:45.725464 AC0091260 Read-Ack Remote override room setpoint: 18.38
14:35:46.541053 T80190000 Read-Data Boiler water temperature: 0.00
14:35:46.784607 BC0192500 Read-Ack Boiler water temperature: 37.00
14:35:47.611145 T10010A00 Write-Data Control setpoint: 10.00
14:35:47.855883 BD0010A00 Write-Ack Control setpoint: 10.00
14:35:48.695088 T80000200 Read-Data Status: 00000010 00000000
14:35:48.922305 B40000200 Read-Ack Status: 00000010 00000000
14:35:49.761174 T9010125E Write-Data Room setpoint: 18.37
14:35:49.762160 R801A0000 Read-Data DHW temperature: 0.00
14:35:50.008100 BC01A1F00 Read-Ack DHW temperature: 31.00
14:35:50.009223 A5010125E Write-Ack Room setpoint: 18.37
14:35:50.834156 T80190000 Read-Data Boiler water temperature: 0.00
14:35:51.057633 B40192400 Read-Ack Boiler water temperature: 36.00
14:35:51.898438 T10010A00 Write-Data Control setpoint: 10.00
14:35:52.140462 BD0010A00 Write-Ack Control setpoint: 10.00
14:35:52.975787 T80000200 Read-Data Status: 00000010 00000000
14:35:53.226270 B40000200 Read-Ack Status: 00000010 00000000
14:35:54.062487 T1018171C Write-Data Room temperature: 23.11
14:35:54.063904 R80380000 Read-Data DHW setpoint: 0.00
14:35:54.309909 BC0383700 Read-Ack DHW setpoint: 55.00
14:35:54.310874 A7018171C Unk-DataId Room temperature: 23.11
14:35:55.115451 T80190000 Read-Data Boiler water temperature: 0.00
14:35:55.359647 B40192400 Read-Ack Boiler water temperature: 36.00
14:35:56.208291 T10010A00 Write-Data Control setpoint: 10.00
14:35:56.420444 BD0010A00 Write-Ack Control setpoint: 10.00
14:35:57.262204 T80000200 Read-Data Status: 00000010 00000000
14:35:57.501895 B40000200 Read-Ack Status: 00000010 00000000
14:35:58.347570 T00110000 Read-Data Relative modulation level: 0.00
14:35:58.554935 BC0110000 Read-Ack Relative modulation level: 0.00
14:35:59.399596 T80190000 Read-Data Boiler water temperature: 0.00
14:35:59.638974 B40192400 Read-Ack Boiler water temperature: 36.00
14:36:00.467964 T10010A00 Write-Data Control setpoint: 10.00
14:36:00.711794 BD0010A00 Write-Ack Control setpoint: 10.00
14:36:01.538338 T80000200 Read-Data Status: 00000010 00000000
14:36:01.789313 B40000200 Read-Ack Status: 00000010 00000000
14:36:02.616165 T00390000 Read-Data Max CH water setpoint: 0.00
14:36:02.854834 B4039004C Read-Ack Max CH water setpoint: 0.30
14:36:03.686279 T80190000 Read-Data Boiler water temperature: 0.00
14:36:03.915688 B40192400 Read-Ack Boiler water temperature: 36.00
14:36:04.766434 T10010A00 Write-Data Control setpoint: 10.00
14:36:05.011511 BD0010A00 Write-Ack Control setpoint: 10.00
14:36:05.834400 T80000200 Read-Data Status: 00000010 00000000
14:36:06.133386 B40000200 Read-Ack Status: 00000010 00000000
14:36:07.067311 T00090000 Read-Data Remote override room setpoint: 0.00
14:36:07.068391 R00030000 Read-Data Slave configuration: 00000000 0
14:36:07.135917 BC0030101 Read-Ack Slave configuration: 00000001 1
14:36:07.144972 AC0091260 Read-Ack Remote override room setpoint: 18.38
14:36:07.982762 T80190000 Read-Data Boiler water temperature: 0.00
14:36:08.232874 B40192400 Read-Ack Boiler water temperature: 36.00
14:36:09.056288 T10010A00 Write-Data Control setpoint: 10.00
14:36:09.276823 BD0010A00 Write-Ack Control setpoint: 10.00
14:36:10.148418 T80000200 Read-Data Status: 00000010 00000000
14:36:10.355977 B40000200 Read-Ack Status: 00000010 00000000
14:36:11.191619 T9010125E Write-Data Room setpoint: 18.37
14:36:11.192606 R801A0000 Read-Data DHW temperature: 0.00
14:36:11.435674 BC01A1F00 Read-Ack DHW temperature: 31.00
14:36:11.444616 A5010125E Write-Ack Room setpoint: 18.37
14:36:12.275615 T80190000 Read-Data Boiler water temperature: 0.00
14:36:12.495156 B40192400 Read-Ack Boiler water temperature: 36.00
14:36:13.354584 T10010A00 Write-Data Control setpoint: 10.00
14:36:13.587461 BD0010A00 Write-Ack Control setpoint: 10.00
14:36:14.397398 T80000200 Read-Data Status: 00000010 00000000
14:36:14.643942 B40000200 Read-Ack Status: 00000010 00000000
14:36:15.466592 T1018171C Write-Data Room temperature: 23.11
14:36:15.483896 R80380000 Read-Data DHW setpoint: 0.00
14:36:15.726680 BC0383700 Read-Ack DHW setpoint: 55.00
14:36:15.727802 A7018171C Unk-DataId Room temperature: 23.11
14:36:16.535781 T80190000 Read-Data Boiler water temperature: 0.00
14:36:16.782167 BC0192300 Read-Ack Boiler water temperature: 35.00
14:36:17.611808 T10010A00 Write-Data Control setpoint: 10.00
14:36:17.857741 BD0010A00 Write-Ack Control setpoint: 10.00
14:36:18.688669 T80000200 Read-Data Status: 00000010 00000000
14:36:18.934452 B40000200 Read-Ack Status: 00000010 00000000
14:36:19.752060 T00110000 Read-Data Relative modulation level: 0.00
14:36:19.988749 BC0110000 Read-Ack Relative modulation level: 0.00
14:36:20.829348 T80190000 Read-Data Boiler water temperature: 0.00
14:36:21.072429 BC0192300 Read-Ack Boiler water temperature: 35.00
14:36:21.897438 T10010A00 Write-Data Control setpoint: 10.00
14:36:22.159578 BD0010A00 Write-Ack Control setpoint: 10.00
14:36:22.988829 T80000200 Read-Data Status: 00000010 00000000
14:36:23.265574 B40000200 Read-Ack Status: 00000010 00000000
14:36:24.052000 T00390000 Read-Data Max CH water setpoint: 0.00
14:36:24.321399 B4039004C Read-Ack Max CH water setpoint: 0.30
14:36:25.123651 T80190000 Read-Data Boiler water temperature: 0.00
14:36:25.346919 BC0192300 Read-Ack Boiler water temperature: 35.00
14:36:26.206021 T10010A00 Write-Data Control setpoint: 10.00
14:36:26.581716 BD0010A00 Write-Ack Control setpoint: 10.00
14:36:27.259817 T80000200 Read-Data Status: 00000010 00000000
14:36:27.497250 B40000200 Read-Ack Status: 00000010 00000000
14:36:28.380992 T00090000 Read-Data Remote override room setpoint: 0.00
14:36:28.382027 R00030000 Read-Data Slave configuration: 00000000 0
14:36:28.575188 BC0030101 Read-Ack Slave configuration: 00000001 1
14:36:28.576214 AC0091260 Read-Ack Remote override room setpoint: 18.38
14:36:29.406986 T80190000 Read-Data Boiler water temperature: 0.00
14:36:29.645670 BC0192300 Read-Ack Boiler water temperature: 35.00
14:36:30.477107 T10010A00 Write-Data Control setpoint: 10.00
14:36:30.703578 BD0010A00 Write-Ack Control setpoint: 10.00
14:36:31.538809 T80000200 Read-Data Status: 00000010 00000000
14:36:31.791575 B40000200 Read-Ack Status: 00000010 00000000
14:36:32.613025 T9010125E Write-Data Room setpoint: 18.37
14:36:32.622521 R801A0000 Read-Data DHW temperature: 0.00
14:36:32.840799 BC01A1F00 Read-Ack DHW temperature: 31.00
14:36:32.859305 A5010125E Write-Ack Room setpoint: 18.37
14:36:33.705215 T80190000 Read-Data Boiler water temperature: 0.00
14:36:33.924871 BC0192300 Read-Ack Boiler water temperature: 35.00
14:36:34.785456 T10010A00 Write-Data Control setpoint: 10.00
14:36:35.006065 BD0010A00 Write-Ack Control setpoint: 10.00
14:36:35.840205 T80000200 Read-Data Status: 00000010 00000000
14:36:36.057585 B40000200 Read-Ack Status: 00000010 00000000
14:36:36.918172 T9018171E Write-Data Room temperature: 23.12
14:36:36.919517 R80380000 Read-Data DHW setpoint: 0.00
14:36:37.145006 BC0383700 Read-Ack DHW setpoint: 55.00
14:36:37.152518 AF018171E Unk-DataId Room temperature: 23.12
14:36:37.986110 T80190000 Read-Data Boiler water temperature: 0.00
14:36:38.256800 BC0192300 Read-Ack Boiler water temperature: 35.00
14:36:39.042715 T10010A00 Write-Data Control setpoint: 10.00
14:36:39.292504 BD0010A00 Write-Ack Control setpoint: 10.00
14:36:40.150926 T80000200 Read-Data Status: 00000010 00000000
14:36:40.375781 B40000200 Read-Ack Status: 00000010 00000000
14:36:41.186967 T00110000 Read-Data Relative modulation level: 0.00
14:36:41.436326 BC0110000 Read-Ack Relative modulation level: 0.00
14:36:42.260994 T80190000 Read-Data Boiler water temperature: 0.00
14:36:42.528046 BC0192300 Read-Ack Boiler water temperature: 35.00
14:36:43.331588 T10010A00 Write-Data Control setpoint: 10.00
14:36:43.589304 BD0010A00 Write-Ack Control setpoint: 10.00
14:36:44.416626 T80000200 Read-Data Status: 00000010 00000000
14:36:44.634369 B40000200 Read-Ack Status: 00000010 00000000
14:36:45.465565 T00390000 Read-Data Max CH water setpoint: 0.00
Re: Sporadic shanges of remote override room setpoint.
Please report the results of the following commands:
PR=G
PR=I
PR=S
PR=G
PR=I
PR=S
Schelte
Re: Sporadic shanges of remote override room setpoint.
G=27
I=11
S=16.00
I'am using outside temperature sensor.
I=11
S=16.00
I'am using outside temperature sensor.
Re: Sporadic shanges of remote override room setpoint.
Yesterday value changes to integer 16.00 So fractional value sets not always. Also I have observed if value changes to not integer, after this changing over iphone.html can't set integer value. Only by using command?/TT=. One time per 5 minutes I'am sending PS=1 and PS=0 commands over relay port by using bash script. May it affect to remote override room temperature value changing? Also, it seems to working good around two month after installing. From july it starts to this behave.
Re: Sporadic shanges of remote override room setpoint.
This shouldn't happen and I can't think of any reason why it would. If things worked fine for a while and then suddenly started behaving differently without any change on the way the device is used, I'm starting to suspect a bit in the EEPROM may have flipped. An easy thing to try is to reflash the firmware. See if that makes any difference.
Schelte
Re: Sporadic shanges of remote override room setpoint.
I am glad to report, since I have disabled sending PS=1, PS=0 commands over relay port all working good around three weeks. Obviously, using outside temperature sensor by this way was bad idea.