Honeywell lyric t6, Intergas HReco 36

Post by droombox »

Hi Guys,

I own a Honeywell lyric t6 thermo and a Intergas HReco 36 boiler. I tried to send a TT = 25 and got a response TT:25 back. The room temp was 20 at that time so i should expect that the heater would start. But nothing happens and the flame status stays off. The room setpoint was 15.

What is the problem? What am i doing wrong? Is there a way to change the room setpoint?

Grts,

Droombox
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Honeywell lyric t6, Intergas HReco 36

Post by hvxl »

Most likely your thermostat does not (fully) support OT message ID 9.
Schelte
yjb
Member
Member
Posts: 211
Joined: Fri Apr 17, 2009 1:15 pm
Location: Venhuizen, Netherlands

Re: Honeywell lyric t6, Intergas HReco 36

Post by yjb »

Correct, you can't set a temporary temperature with the Lyric Thermostat, at least not using the OTGW.

The only option that I''m aware off is using IFTTT. I'm using IFTTT combined with a html request from my server to IFTTT to regulate the temperature manually.

Ysbrand