OTGW - Thermostat gets disconnected after a few seconds

Postby Luc_S » Sun Aug 26, 2018 3:50 pm

Hi all,

I soldered an OTGW diy package which worked perfectly for months. After reconnecting the OTGW because of a new thermostat my home was getting heated continuously even though the thermostat was set to 19 degrees and my home temperature was 24+. When the OTGW was removed the issue was gone. Because I didn't have the time and tools to investigate I left the OTGW disconnected for a while.

Today I hooked up the OTGW to a Windows system and noticed that the thermostat is getting some 'T80190000' signals but gets disconnected automatically after a few seconds resulting in 'R00000000' messages (see attachment). When I manually reconnect the thermostat it is again connected, but only for a few seconds.

I tried to troubleshoot using webpage http://otgw.tclcode.com/debugging.html but the measurements seem correct. Then http://otgw.tclcode.com/diagnose.html, I soldered the LED's and they are blinking in order when the first diagnostic test is started. They are however blinking in the exact opposite direction as shown on the page (from right to left). Test 2 is successful until the thermostat gets automatically disconnected again, then there is no result shown anymore. I didn't do any other diagnostic tests.

Has anyone an idea about how to proceed and maybe fix this issue?
Attachments
OTGW.png
Diagnostics screen
OTGW.png (10.68 KiB) Viewed 762 times
Luc_S
Starting Member
Starting Member
 
Posts: 25
Joined: June 2018

Re: OTGW - Thermostat gets disconnected after a few seconds

Postby Cooter » Wed Aug 29, 2018 8:12 pm

Is your new thermostat listed in the otgw thermostat matrix?
Cooter
Starting Member
Starting Member
 
Posts: 11
Joined: August 2018

Re: OTGW - Thermostat gets disconnected after a few seconds

Postby Luc_S » Thu Aug 30, 2018 8:31 am

Yes, the new thermostat is the Quby (Toon) but while hooking it up to the laptop I used my old one which is also in the matrix (AgpoTherm Plus). So the info provided in the topic-start is with the Agpo thermostat.
Luc_S
Starting Member
Starting Member
 
Posts: 25
Joined: June 2018

Re: OTGW - Thermostat gets disconnected after a few seconds

Postby hvxl » Thu Aug 30, 2018 9:17 pm

The Diagnostics window is only supposed to be used with the diagnostic firmware. It is not very useful when used with the normal firmware. In that situation, you get much better information by looking at the Log tab.

T-messages are reports of what the thermostat is sending, not what it is getting. But there are no B-messages, so the boiler doesn't appear to respond.

It is unclear if the thermostat stops sending messages due to the lack of responses and switches to on/off mode, causing the "Thermostat disconnected" message, or if the voltage on the thermostat interface is close to the threshold and the disconnection detection is falsely triggered.

To check, you can use the command DP=57. This will report the measured line voltage after each message. A connected opentherm thermostat should normally result in values between 6 and 122. Values outside that range are assumed to be caused by the thermostat being disconnected, or using an on/off thermostat.
Schelte
hvxl
Senior Member
Senior Member
 
Posts: 1111
Joined: June 2010

Re: OTGW - Thermostat gets disconnected after a few seconds

Postby Luc_S » Sat Sep 01, 2018 6:03 pm

Ah ok, clear. Well the boiler wasn't connected at all. I just thought I could troubleshoot with the OTGW and old thermostat first and then noticed the automatic disconnects. I had no idea the disconnect could be a result of an absent boiler.

Because of my holiday I won't be able to test this right now but I will report back once I checked this out. Thanks!
Luc_S
Starting Member
Starting Member
 
Posts: 25
Joined: June 2018

Re: OTGW - Thermostat gets disconnected after a few seconds

Postby hvxl » Sat Sep 01, 2018 8:09 pm

I don't know if the absence of a boiler is the cause of the disconnect in this case. But I know there are thermostats out there that will switch to on/off mode if they don't get an opentherm reply within a certain amount of tries after startup. So it's a possibility. More data will be needed to make sure.

The opentherm spec actually prescribes that a master should first try to use OT/+ communication. If no valid response is received for 20 seconds, it should switch to OT/- mode, which is basically on/off mode. Your screen shot shows 20 attempts before the "Thermostat disconnected" message. Coincidence?
Schelte
hvxl
Senior Member
Senior Member
 
Posts: 1111
Joined: June 2010