Here my findings with the new isense.hex.
I have a Remeha Calenta 40c with isense sw v19.
Just build my OTG this weekend.
- same conclusion as above, TT=x and then TT=y will only be accepted if first TT=0 is given. Should be nice if it can be solved, otherwise it's just a thing to remember when setting new temporary temperatures.
- however, something different then above, when I have set a TT=x the standard program will NOT resume when it should at a specific configured time. The overridden temperature stays active. Don't know with the other guys, but I also see a difference with a temporary override on the iSense itself and with the temporary override with OTG.
When I do the temporary override on the iSense it shows the until time on the left bottom, e.g.
--
Tot:
16:00
25/12/2012
--
When I override it with the OTG it doesn't show an until value.
Here some logging.
Configuration in iSense
08:30 19,5 degrees
16:00 15,0 degrees
TT=18 done at 15:55.
Should expect that program goes to 15 degrees at 16:00. It just doesn't happen. If I do a TT=0 it does go to 15 degrees (see 16:02:55). My first impression is that there is no difference between the 'TT' and the 'TC' in my configuration.
If you want more info, please let me know and I will give it.
Code: Select all
15:55:12.364175 T80190000 Read-Data Boiler water temperature: 0.00
15:55:12.484904 B4019417D Read-Ack Boiler water temperature: 65.49
15:55:13.366172 T00090000 Read-Data Remote override room setpoint: 0.00
15:55:13.396581 R80750000 Read-Data CH pump starts: 0
15:55:13.696446 BC0757180 Read-Ack CH pump starts: 29056
15:55:13.728529 AC0090000 Read-Ack Remote override room setpoint: 0.00
15:55:14.367375 T80000200 Read-Data Status: 00000010 00000000
15:55:14.487767 B40000200 Read-Ack Status: 00000010 00000000
15:55:15.368622 T80000200 Read-Data Status: 00000010 00000000
15:55:15.489033 B40000200 Read-Ack Status: 00000010 00000000
15:55:16.369963 T80000200 Read-Data Status: 00000010 00000000
15:55:16.483439 B40000200 Read-Ack Status: 00000010 00000000
15:55:17.371695 T10011100 Write-Data Control setpoint: 17.00
15:55:17.481495 BD0011100 Write-Ack Control setpoint: 17.00
15:55:18.372651 T00110000 Read-Data Relative modulation level: 0.00
15:55:18.483149 BC0110000 Read-Ack Relative modulation level: 0.00
15:55:19.373994 T80190000 Read-Data Boiler water temperature: 0.00
15:55:19.484550 B401942E8 Read-Ack Boiler water temperature: 66.91
15:55:20.375307 T00630000 Read-Data Message ID 99: 0
15:55:20.410979 R80760000 Read-Data DHW pump/valve starts: 0
15:55:20.586047 B407639B8 Read-Ack DHW pump/valve starts: 14776
15:55:20.619950 AF0630000 Unk-DataId Message ID 99: 0
15:55:21.377374 T80000200 Read-Data Status: 00000010 00000000
15:55:21.488099 B40000200 Read-Ack Status: 00000010 00000000
15:55:22.378523 T10011100 Write-Data Control setpoint: 17.00
15:55:22.488274 BD0011100 Write-Ack Control setpoint: 17.00
15:55:23.379562 T00110000 Read-Data Relative modulation level: 0.00
15:55:23.480031 BC0110000 Read-Ack Relative modulation level: 0.00
15:55:24.397456 T80190000 Read-Data Boiler water temperature: 0.00
15:55:24.481386 B4019431C Read-Ack Boiler water temperature: 67.11
15:55:25.382178 T80700000 Read-Data Message ID 112: 0
15:55:25.418710 R00770000 Read-Data DHW burner starts: 0
15:55:25.683186 B40774120 Read-Ack DHW burner starts: 16672
15:55:25.754152 A70700000 Unk-DataId Message ID 112: 0
15:55:26.384110 T80000200 Read-Data Status: 00000010 00000000
15:55:26.484378 B40000200 Read-Ack Status: 00000010 00000000
15:55:27.385330 T10011100 Write-Data Control setpoint: 17.00
15:55:27.485052 BD0011100 Write-Ack Control setpoint: 17.00
15:55:28.386434 T00110000 Read-Data Relative modulation level: 0.00
15:55:28.486791 BC0110000 Read-Ack Relative modulation level: 0.00
15:55:29.383416 T80190000 Read-Data Boiler water temperature: 0.00
15:55:29.488755 B40194380 Read-Ack Boiler water temperature: 67.50
15:55:30.389476 T00050000 Read-Data Application-specific flags: 00000000 0
15:55:30.479627 BC00500FF Read-Ack Application-specific flags: 00000000 255
15:55:31.390499 T80000200 Read-Data Status: 00000010 00000000
15:55:31.480975 B40000200 Read-Ack Status: 00000010 00000000
15:55:32.392185 T10011100 Write-Data Control setpoint: 17.00
15:55:32.491990 BD0011100 Write-Ack Control setpoint: 17.00
15:55:32.866540 Command: TT=18.00
15:55:32.902723 OK
15:55:33.393127 T00110000 Read-Data Relative modulation level: 0.00
15:55:33.493755 BC0110000 Read-Ack Relative modulation level: 0.00
15:55:34.394533 T80190000 Read-Data Boiler water temperature: 0.00
15:55:34.486352 BC0194399 Read-Ack Boiler water temperature: 67.60
15:55:35.395900 T001B0ACC Read-Data Outside temperature: 10.80
15:55:35.488550 BC01B0A99 Read-Ack Outside temperature: 10.60
15:55:36.397395 T80000200 Read-Data Status: 00000010 00000000
15:55:36.488624 B40000200 Read-Ack Status: 00000010 00000000
15:55:37.402749 T10011100 Write-Data Control setpoint: 17.00
15:55:37.559272 BD0011100 Write-Ack Control setpoint: 17.00
15:55:38.400419 T00110000 Read-Data Relative modulation level: 0.00
15:55:38.490796 BC0110000 Read-Ack Relative modulation level: 0.00
15:55:39.401354 T80190000 Read-Data Boiler water temperature: 0.00
15:55:39.491879 B401943B3 Read-Ack Boiler water temperature: 67.70
15:55:40.403273 T900E6400 Write-Data Maximum relative modulation level: 100.00
15:55:40.492909 B500E6400 Write-Ack Maximum relative modulation level: 100.00
15:55:41.404223 T80000200 Read-Data Status: 00000010 00000000
15:55:41.494564 B40000200 Read-Ack Status: 00000010 00000000
15:55:42.405845 T10011100 Write-Data Control setpoint: 17.00
15:55:42.495864 BD0011100 Write-Ack Control setpoint: 17.00
15:55:43.406809 T00110000 Read-Data Relative modulation level: 0.00
15:55:43.497258 BC0110000 Read-Ack Relative modulation level: 0.00
15:55:44.408173 T80190000 Read-Data Boiler water temperature: 0.00
15:55:44.499650 BC01943CC Read-Ack Boiler water temperature: 67.80
15:55:45.409913 T10101380 Write-Data Room setpoint: 19.50
15:55:45.499567 BD0101380 Write-Ack Room setpoint: 19.50
15:55:46.411062 T80000200 Read-Data Status: 00000010 00000000
15:55:46.501475 B40000200 Read-Ack Status: 00000010 00000000
15:55:47.412720 T10011100 Write-Data Control setpoint: 17.00
15:55:47.502340 BD0011100 Write-Ack Control setpoint: 17.00
15:55:48.454107 T00110000 Read-Data Relative modulation level: 0.00
15:55:48.584500 BC0110000 Read-Ack Relative modulation level: 0.00
15:55:49.415037 T80190000 Read-Data Boiler water temperature: 0.00
15:55:49.505517 BC01943CC Read-Ack Boiler water temperature: 67.80
15:55:50.416793 T901813E3 Write-Data Room temperature: 19.89
15:55:50.506507 B501813E3 Write-Ack Room temperature: 19.89
15:55:51.407931 T80000200 Read-Data Status: 00000010 00000000
15:55:51.508372 B40000200 Read-Ack Status: 00000010 00000000
15:55:52.410200 T10011100 Write-Data Control setpoint: 17.00
15:55:52.509257 BD0011100 Write-Ack Control setpoint: 17.00
15:55:53.410509 T00110000 Read-Data Relative modulation level: 0.00
15:55:53.510954 BC0110000 Read-Ack Relative modulation level: 0.00
15:55:54.411904 T80190000 Read-Data Boiler water temperature: 0.00
15:55:54.512322 BC01943CC Read-Ack Boiler water temperature: 67.80
15:55:55.413327 T00090000 Read-Data Remote override room setpoint: 0.00
15:55:55.449241 R00780000 Read-Data Burner operation hours: 0
15:55:55.683872 BC0780EDA Read-Ack Burner operation hours: 3802
15:55:55.719684 AC0091200 Read-Ack Remote override room setpoint: 18.00
15:55:56.414654 T00090000 Read-Data Remote override room setpoint: 0.00
15:55:56.451460 R80790000 Read-Data CH pump operation hours: 0
15:55:56.585147 BC0791126 Read-Ack CH pump operation hours: 4390
15:55:56.621985 AC0091200 Read-Ack Remote override room setpoint: 18.00
15:55:57.416076 T00090000 Read-Data Remote override room setpoint: 0.00
15:55:57.454835 R807A0000 Read-Data DHW pump/valve operation hours: 0
15:55:57.686614 B407A5BB0 Read-Ack DHW pump/valve operation hours: 23472
15:55:57.721963 AC0091200 Read-Ack Remote override room setpoint: 18.00
15:55:58.417425 T80000200 Read-Data Status: 00000010 00000000
15:55:58.507964 B40000200 Read-Ack Status: 00000010 00000000
15:55:59.419267 T10010600 Write-Data Control setpoint: 6.00
15:55:59.579108 BD0010600 Write-Ack Control setpoint: 6.00
15:56:00.420064 T00110000 Read-Data Relative modulation level: 0.00
15:56:00.580788 BC0110000 Read-Ack Relative modulation level: 0.00
15:56:01.421481 T80190000 Read-Data Boiler water temperature: 0.00
15:56:01.582725 BC01943CC Read-Ack Boiler water temperature: 67.80
15:56:02.423081 T00630000 Read-Data Message ID 99: 0
15:56:02.459383 R007B0000 Read-Data DHW burner operation hours: 0
15:56:02.683759 BC07B019B Read-Ack DHW burner operation hours: 411
15:56:02.707016 AF0630000 Unk-DataId Message ID 99: 0
15:56:03.424144 T80000200 Read-Data Status: 00000010 00000000
15:56:03.584727 B40000200 Read-Ack Status: 00000010 00000000
15:56:04.425766 T10010600 Write-Data Control setpoint: 6.00
15:56:04.595587 BD0010600 Write-Ack Control setpoint: 6.00
15:56:05.426848 T00110000 Read-Data Relative modulation level: 0.00
15:56:05.587502 BC0110000 Read-Ack Relative modulation level: 0.00
15:56:06.428208 T80190000 Read-Data Boiler water temperature: 0.00
15:56:06.588970 B401943B3 Read-Ack Boiler water temperature: 67.70
15:56:07.432367 T1002010B Write-Data Master configuration: 00000001 11
15:56:07.580145 BD002010B Write-Ack Master configuration: 00000001 11
15:56:08.431101 T80000200 Read-Data Status: 00000010 00000000
15:56:08.581776 B40000200 Read-Ack Status: 00000010 00000000
15:56:09.432596 T10010600 Write-Data Control setpoint: 6.00
15:56:09.583267 BD0010600 Write-Ack Control setpoint: 6.00
15:56:10.413569 T00110000 Read-Data Relative modulation level: 0.00
15:56:10.504054 BC0110000 Read-Ack Relative modulation level: 0.00
15:56:11.414971 T80190000 Read-Data Boiler water temperature: 0.00
15:56:11.505508 BC0194399 Read-Ack Boiler water temperature: 67.60
15:56:12.416491 T00050000 Read-Data Application-specific flags: 00000000 0
15:56:12.507008 BC00500FF Read-Ack Application-specific flags: 00000000 255
15:56:13.417907 T80000200 Read-Data Status: 00000010 00000000
15:56:13.509567 B40000200 Read-Ack Status: 00000010 00000000
15:56:14.419557 T10010600 Write-Data Control setpoint: 6.00
15:56:14.589427 BD0010600 Write-Ack Control setpoint: 6.00
15:56:15.420725 T00110000 Read-Data Relative modulation level: 0.00
15:56:15.581241 BC0110000 Read-Ack Relative modulation level: 0.00
15:56:16.422109 T80190000 Read-Data Boiler water temperature: 0.00
15:56:16.582556 BC0194399 Read-Ack Boiler water temperature: 67.60
15:56:17.423237 T001B0ACC Read-Data Outside temperature: 10.80
15:56:17.583935 BC01B0A99 Read-Ack Outside temperature: 10.60
15:56:18.425021 T80000200 Read-Data Status: 00000010 00000000
15:56:18.585292 B40000200 Read-Ack Status: 00000010 00000000
15:56:19.426363 T10010600 Write-Data Control setpoint: 6.00
15:56:19.586209 BD0010600 Write-Ack Control setpoint: 6.00
15:56:20.427342 T00110000 Read-Data Relative modulation level: 0.00
15:56:20.587923 BC0110000 Read-Ack Relative modulation level: 0.00
15:56:21.428699 T80190000 Read-Data Boiler water temperature: 0.00
15:56:21.589312 B40194380 Read-Ack Boiler water temperature: 67.50
15:56:22.430523 T900E6400 Write-Data Maximum relative modulation level: 100.00
15:56:22.581210 B500E6400 Write-Ack Maximum relative modulation level: 100.00
15:56:23.441894 T80000200 Read-Data Status: 00000010 00000000
15:56:23.582215 B40000200 Read-Ack Status: 00000010 00000000
15:56:24.433238 T10010600 Write-Data Control setpoint: 6.00
15:56:24.583373 BD0010600 Write-Ack Control setpoint: 6.00
15:56:25.434237 T00110000 Read-Data Relative modulation level: 0.00
15:56:25.585200 BC0110000 Read-Ack Relative modulation level: 0.00
15:56:26.435560 T80190000 Read-Data Boiler water temperature: 0.00
15:56:26.586518 B40194380 Read-Ack Boiler water temperature: 67.50
15:56:27.437403 T10101200 Write-Data Room setpoint: 18.00
15:56:27.588305 BD0101200 Write-Ack Room setpoint: 18.00
15:56:28.438551 T80000200 Read-Data Status: 00000010 00000000
15:56:28.589041 B40000200 Read-Ack Status: 00000010 00000000
15:56:29.440205 T10010600 Write-Data Control setpoint: 6.00
15:56:29.580157 BD0010600 Write-Ack Control setpoint: 6.00
15:56:30.441157 T00110000 Read-Data Relative modulation level: 0.00
15:56:30.581908 BC0110000 Read-Ack Relative modulation level: 0.00
15:56:31.442549 T80190000 Read-Data Boiler water temperature: 0.00
15:56:31.583210 B40194380 Read-Ack Boiler water temperature: 67.50
15:56:32.444325 T101813E1 Write-Data Room temperature: 19.88
15:56:32.584192 BD01813E1 Write-Ack Room temperature: 19.88
15:56:33.445299 T80000200 Read-Data Status: 00000010 00000000
15:56:33.585939 B40000200 Read-Ack Status: 00000010 00000000
15:56:34.446957 T10010600 Write-Data Control setpoint: 6.00
15:56:34.586865 BD0010600 Write-Ack Control setpoint: 6.00
15:56:35.447896 T00110000 Read-Data Relative modulation level: 0.00
15:56:35.588678 BC0110000 Read-Ack Relative modulation level: 0.00
15:56:36.449258 T80190000 Read-Data Boiler water temperature: 0.00
15:56:36.589972 B40194380 Read-Ack Boiler water temperature: 67.50
15:56:37.450729 T00090000 Read-Data Remote override room setpoint: 0.00
15:56:37.486120 R00740000 Read-Data Burner starts: 0
15:56:37.791671 BC0745238 Read-Ack Burner starts: 21048
15:56:37.826223 AC0091200 Read-Ack Remote override room setpoint: 18.00
15:56:38.452114 T80000200 Read-Data Status: 00000010 00000000
15:56:38.583771 B40000200 Read-Ack Status: 00000010 00000000
15:56:39.453809 T10010600 Write-Data Control setpoint: 6.00
15:56:39.583820 BD0010600 Write-Ack Control setpoint: 6.00
15:56:40.454805 T00110000 Read-Data Relative modulation level: 0.00
15:56:40.585656 BC0110000 Read-Ack Relative modulation level: 0.00
15:56:41.456116 T80190000 Read-Data Boiler water temperature: 0.00
15:56:41.586960 B40194380 Read-Ack Boiler water temperature: 67.50
15:56:42.457327 T00630000 Read-Data Message ID 99: 0
15:56:42.492646 R80750000 Read-Data CH pump starts: 0
15:56:42.798518 BC0757180 Read-Ack CH pump starts: 29056
15:56:42.833836 AF0630000 Unk-DataId Message ID 99: 0
15:56:43.529216 T80000200 Read-Data Status: 00000010 00000000
15:56:43.700064 B40000200 Read-Ack Status: 00000010 00000000
15:56:44.480690 T10010600 Write-Data Control setpoint: 6.00
15:56:44.580492 BD0010600 Write-Ack Control setpoint: 6.00
15:56:45.481693 T00110000 Read-Data Relative modulation level: 0.00
15:56:45.582224 BC0110000 Read-Ack Relative modulation level: 0.00
15:56:46.483041 T80190000 Read-Data Boiler water temperature: 0.00
15:56:46.583537 BC0194363 Read-Ack Boiler water temperature: 67.39
15:56:47.484667 T00030000 Read-Data Slave configuration: 00000000 0
15:56:47.587176 B4003410B Read-Ack Slave configuration: 01000001 11
15:56:48.485847 T80000200 Read-Data Status: 00000010 00000000
15:56:48.586329 B40000200 Read-Ack Status: 00000010 00000000
15:56:49.487920 T10010600 Write-Data Control setpoint: 6.00
15:56:49.587289 BD0010600 Write-Ack Control setpoint: 6.00
15:56:50.478639 T00110000 Read-Data Relative modulation level: 0.00
15:56:50.589041 BC0110000 Read-Ack Relative modulation level: 0.00
15:56:51.480004 T80190000 Read-Data Boiler water temperature: 0.00
15:56:51.590420 B4019434C Read-Ack Boiler water temperature: 67.30
15:56:52.491347 T00050000 Read-Data Application-specific flags: 00000000 0
15:56:52.582052 BC00500FF Read-Ack Application-specific flags: 00000000 255
15:56:53.492737 T80000200 Read-Data Status: 00000010 00000000
15:56:53.583215 B40000200 Read-Ack Status: 00000010 00000000
15:56:54.484475 T10010600 Write-Data Control setpoint: 6.00
15:56:54.584283 BD0010600 Write-Ack Control setpoint: 6.00
15:56:55.485669 T00110000 Read-Data Relative modulation level: 0.00
15:56:55.585824 BC0110000 Read-Ack Relative modulation level: 0.00
15:56:56.486661 T80190000 Read-Data Boiler water temperature: 0.00
15:56:56.587103 BC0194333 Read-Ack Boiler water temperature: 67.20
15:56:57.488085 T001B0ACC Read-Data Outside temperature: 10.80
15:56:57.588469 BC01B0A99 Read-Ack Outside temperature: 10.60
15:56:58.489565 T80000200 Read-Data Status: 00000010 00000000
15:56:58.589942 B40000200 Read-Ack Status: 00000010 00000000
15:56:59.491229 T10010600 Write-Data Control setpoint: 6.00
15:56:59.581048 BD0010600 Write-Ack Control setpoint: 6.00
15:57:00.492225 T00110000 Read-Data Relative modulation level: 0.00
15:57:00.582772 BC0110000 Read-Ack Relative modulation level: 0.00
15:57:01.493657 T80190000 Read-Data Boiler water temperature: 0.00
15:57:01.584207 BC0194333 Read-Ack Boiler water temperature: 67.20
15:57:02.495362 T900E6400 Write-Data Maximum relative modulation level: 100.00
15:57:02.585189 B500E6400 Write-Ack Maximum relative modulation level: 100.00
15:57:03.496428 T80000200 Read-Data Status: 00000010 00000000
15:57:03.586940 B40000200 Read-Ack Status: 00000010 00000000
15:57:04.498036 T10010600 Write-Data Control setpoint: 6.00
15:57:04.587898 BD0010600 Write-Ack Control setpoint: 6.00
15:57:05.500111 T00110000 Read-Data Relative modulation level: 0.00
15:57:05.589615 BC0110000 Read-Ack Relative modulation level: 0.00
15:57:06.500843 T80190000 Read-Data Boiler water temperature: 0.00
15:57:06.590981 BC0194333 Read-Ack Boiler water temperature: 67.20
15:57:07.502136 T10101200 Write-Data Room setpoint: 18.00
15:57:07.591935 BD0101200 Write-Ack Room setpoint: 18.00
15:57:08.503243 T80000200 Read-Data Status: 00000010 00000000
15:57:08.593846 B40000200 Read-Ack Status: 00000010 00000000
15:57:09.504931 T10010600 Write-Data Control setpoint: 6.00
15:57:09.594684 BD0010600 Write-Ack Control setpoint: 6.00
15:57:10.505888 T00110000 Read-Data Relative modulation level: 0.00
15:57:10.596369 BC0110000 Read-Ack Relative modulation level: 0.00
15:57:11.507277 T80190000 Read-Data Boiler water temperature: 0.00
15:57:11.597754 B40194326 Read-Ack Boiler water temperature: 67.15
15:57:12.509005 T101813E1 Write-Data Room temperature: 19.88
15:57:12.598932 BD01813E1 Write-Ack Room temperature: 19.88
15:57:13.540464 T80000200 Read-Data Status: 00000010 00000000
15:57:13.680940 B40000200 Read-Ack Status: 00000010 00000000
15:57:14.511909 T10010600 Write-Data Control setpoint: 6.00
15:57:14.601601 BD0010600 Write-Ack Control setpoint: 6.00
15:57:15.513448 T00110000 Read-Data Relative modulation level: 0.00
15:57:15.603686 BC0110000 Read-Ack Relative modulation level: 0.00
15:57:16.514151 T80190000 Read-Data Boiler water temperature: 0.00
15:57:16.604682 BC019430F Read-Ack Boiler water temperature: 67.06
15:57:17.515733 T00090000 Read-Data Remote override room setpoint: 0.00
15:57:17.549880 R80760000 Read-Data DHW pump/valve starts: 0
15:57:17.796579 B407639B8 Read-Ack DHW pump/valve starts: 14776
15:57:17.832226 AC0091200 Read-Ack Remote override room setpoint: 18.00
15:57:18.516995 T80000200 Read-Data Status: 00000010 00000000
15:57:18.607404 B40000200 Read-Ack Status: 00000010 00000000
15:57:19.518595 T10010600 Write-Data Control setpoint: 6.00
15:57:19.608424 BD0010600 Write-Ack Control setpoint: 6.00
15:57:20.519607 T00110000 Read-Data Relative modulation level: 0.00
15:57:20.690326 BC0110000 Read-Ack Relative modulation level: 0.00
15:57:21.520974 T80190000 Read-Data Boiler water temperature: 0.00
15:57:21.681635 BC0194300 Read-Ack Boiler water temperature: 67.00
15:57:22.522528 T00630000 Read-Data Message ID 99: 0
15:57:22.563130 R00770000 Read-Data DHW burner starts: 0
15:57:22.883258 B40774120 Read-Ack DHW burner starts: 16672
15:57:22.917915 AF0630000 Unk-DataId Message ID 99: 0
15:57:23.523783 T80000200 Read-Data Status: 00000010 00000000
15:57:23.684307 B40000200 Read-Ack Status: 00000010 00000000
15:57:24.525630 T10010600 Write-Data Control setpoint: 6.00
15:57:24.686121 BD0010600 Write-Ack Control setpoint: 6.00
<removed>
15:59:23.024040 AF0630000 Unk-DataId Message ID 99: 0
15:59:23.678385 T80000200 Read-Data Status: 00000010 00000000
15:59:23.798648 B40000200 Read-Ack Status: 00000010 00000000
15:59:24.679810 T10010600 Write-Data Control setpoint: 6.00
15:59:24.799601 BD0010600 Write-Ack Control setpoint: 6.00
15:59:25.681991 T00110000 Read-Data Relative modulation level: 0.00
15:59:25.791443 BC0110000 Read-Ack Relative modulation level: 0.00
15:59:26.682397 T80190000 Read-Data Boiler water temperature: 0.00
15:59:26.793054 BC0194219 Read-Ack Boiler water temperature: 66.10
15:59:27.684440 T00300000 Read-Data DHW setpoint boundaries: 0 0
15:59:27.796655 BC0304128 Read-Ack DHW setpoint boundaries: 65 40
15:59:28.675094 T80000200 Read-Data Status: 00000010 00000000
15:59:28.795537 B40000200 Read-Ack Status: 00000010 00000000
15:59:29.676789 T10010600 Write-Data Control setpoint: 6.00
15:59:29.796885 BD0010600 Write-Ack Control setpoint: 6.00
15:59:30.677737 T00110000 Read-Data Relative modulation level: 0.00
15:59:30.798181 BC0110000 Read-Ack Relative modulation level: 0.00
15:59:31.689012 T80190000 Read-Data Boiler water temperature: 0.00
15:59:31.799976 BC0194219 Read-Ack Boiler water temperature: 66.10
15:59:32.680524 T00050000 Read-Data Application-specific flags: 00000000 0
15:59:32.791094 BC00500FF Read-Ack Application-specific flags: 00000000 255
15:59:33.681830 T80000200 Read-Data Status: 00000010 00000000
15:59:33.792483 B40000200 Read-Ack Status: 00000010 00000000
15:59:34.683594 T10010600 Write-Data Control setpoint: 6.00
15:59:34.793327 BD0010600 Write-Ack Control setpoint: 6.00
15:59:35.684525 T00110000 Read-Data Relative modulation level: 0.00
15:59:35.794973 BC0110000 Read-Ack Relative modulation level: 0.00
15:59:36.685827 T80190000 Read-Data Boiler water temperature: 0.00
15:59:36.796377 BC0194219 Read-Ack Boiler water temperature: 66.10
15:59:37.687228 T001B0ACC Read-Data Outside temperature: 10.80
15:59:37.797785 BC01B0A99 Read-Ack Outside temperature: 10.60
15:59:38.688703 T80000200 Read-Data Status: 00000010 00000000
15:59:38.799184 B40000200 Read-Ack Status: 00000010 00000000
15:59:39.690643 T10010600 Write-Data Control setpoint: 6.00
15:59:39.800172 BD0010600 Write-Ack Control setpoint: 6.00
15:59:40.691361 T00110000 Read-Data Relative modulation level: 0.00
15:59:40.791951 BC0110000 Read-Ack Relative modulation level: 0.00
15:59:41.692865 T80190000 Read-Data Boiler water temperature: 0.00
15:59:41.793294 BC0194219 Read-Ack Boiler water temperature: 66.10
15:59:42.694557 T900E6400 Write-Data Maximum relative modulation level: 100.00
15:59:42.794256 B500E6400 Write-Ack Maximum relative modulation level: 100.00
15:59:43.695934 T80000200 Read-Data Status: 00000010 00000000
15:59:43.796060 B40000200 Read-Ack Status: 00000010 00000000
15:59:44.697274 T10010600 Write-Data Control setpoint: 6.00
15:59:44.797024 BD0010600 Write-Ack Control setpoint: 6.00
15:59:45.688450 T00110000 Read-Data Relative modulation level: 0.00
15:59:45.798736 BC0110000 Read-Ack Relative modulation level: 0.00
15:59:46.689821 T80190000 Read-Data Boiler water temperature: 0.00
15:59:46.800142 B40194200 Read-Ack Boiler water temperature: 66.00
15:59:47.691776 T10101200 Write-Data Room setpoint: 18.00
15:59:47.792157 BD0101200 Write-Ack Room setpoint: 18.00
15:59:48.692610 T80000200 Read-Data Status: 00000010 00000000
15:59:48.793009 B40000200 Read-Ack Status: 00000010 00000000
15:59:49.694221 T10010600 Write-Data Control setpoint: 6.00
15:59:49.793916 BD0010600 Write-Ack Control setpoint: 6.00
15:59:50.695156 T00110000 Read-Data Relative modulation level: 0.00
15:59:50.796082 BC0110000 Read-Ack Relative modulation level: 0.00
15:59:51.696550 T80190000 Read-Data Boiler water temperature: 0.00
15:59:51.797057 B40194200 Read-Ack Boiler water temperature: 66.00
15:59:52.698393 T101813DE Write-Data Room temperature: 19.87
15:59:52.798084 BD01813DE Write-Ack Room temperature: 19.87
15:59:53.703586 T90143000 Write-Data Day of week and time of day: Mon 16:00
15:59:53.739929 R80760000 Read-Data DHW pump/valve starts: 0
15:59:53.890122 B407639B8 Read-Ack DHW pump/valve starts: 14776
15:59:53.926778 A50143000 Write-Ack Day of week and time of day: Mon 16:00
15:59:54.703614 T101607DC Write-Data Year: 2012
15:59:54.740922 R00770000 Read-Data DHW burner starts: 0
15:59:54.891431 B40774120 Read-Ack DHW burner starts: 16672
15:59:54.931958 A701607DC Unk-DataId Year: 2012
15:59:55.705480 T10150C18 Write-Data Date: 12 24
15:59:55.743119 R00780000 Read-Data Burner operation hours: 0
15:59:55.992872 BC0780EDA Read-Ack Burner operation hours: 3802
15:59:56.035506 A70150C18 Unk-DataId Date: 12 24
15:59:56.703486 T80000200 Read-Data Status: 00000010 00000000
15:59:56.793999 B40000200 Read-Ack Status: 00000010 00000000
15:59:57.705125 T10010600 Write-Data Control setpoint: 6.00
15:59:57.794714 BD0010600 Write-Ack Control setpoint: 6.00
15:59:58.706050 T00110000 Read-Data Relative modulation level: 0.00
15:59:58.796441 BC0110000 Read-Ack Relative modulation level: 0.00
15:59:59.707461 T80190000 Read-Data Boiler water temperature: 0.00
15:59:59.797847 B40194200 Read-Ack Boiler water temperature: 66.00
16:00:00.708977 T00090000 Read-Data Remote override room setpoint: 0.00
16:00:00.746755 R80790000 Read-Data CH pump operation hours: 0
16:00:00.889448 BC0791126 Read-Ack CH pump operation hours: 4390
16:00:00.928686 AC0091200 Read-Ack Remote override room setpoint: 18.00
16:00:01.710373 T80000200 Read-Data Status: 00000010 00000000
16:00:01.800661 B40000200 Read-Ack Status: 00000010 00000000
16:00:02.712007 T10010600 Write-Data Control setpoint: 6.00
16:00:02.801593 BD0010600 Write-Ack Control setpoint: 6.00
16:00:03.713348 T00110000 Read-Data Relative modulation level: 0.00
16:00:03.803388 BC0110000 Read-Ack Relative modulation level: 0.00
16:00:04.714319 T80190000 Read-Data Boiler water temperature: 0.00
16:00:04.804771 BC01941E6 Read-Ack Boiler water temperature: 65.90
16:00:05.715526 T00630000 Read-Data Message ID 99: 0
16:00:05.753202 R807A0000 Read-Data DHW pump/valve operation hours: 0
16:00:05.886605 B407A5BB0 Read-Ack DHW pump/valve operation hours: 23472
16:00:05.925242 AF0630000 Unk-DataId Message ID 99: 0
16:00:06.717282 T80000200 Read-Data Status: 00000010 00000000
16:00:06.807608 B40000200 Read-Ack Status: 00000010 00000000
16:00:07.718849 T10010600 Write-Data Control setpoint: 6.00
16:00:07.808466 BD0010600 Write-Ack Control setpoint: 6.00
16:00:08.709860 T00110000 Read-Data Relative modulation level: 0.00
16:00:08.810258 BC0110000 Read-Ack Relative modulation level: 0.00
16:00:09.711327 T80190000 Read-Data Boiler water temperature: 0.00
16:00:09.802947 BC01941E6 Read-Ack Boiler water temperature: 65.90
16:00:10.712683 T80310000 Read-Data Max CH setpoint boundaries: 0 0
16:00:10.815742 BC0314614 Read-Ack Max CH setpoint boundaries: 70 20
16:00:11.713968 T80000200 Read-Data Status: 00000010 00000000
16:00:11.804487 B40000200 Read-Ack Status: 00000010 00000000
16:00:12.715645 T10010600 Write-Data Control setpoint: 6.00
16:00:12.805751 BD0010600 Write-Ack Control setpoint: 6.00
16:00:13.716556 T00110000 Read-Data Relative modulation level: 0.00
16:00:13.817043 BC0110000 Read-Ack Relative modulation level: 0.00
16:00:14.717921 T80190000 Read-Data Boiler water temperature: 0.00
16:00:14.818402 BC01941E6 Read-Ack Boiler water temperature: 65.90
16:00:15.719385 T00050000 Read-Data Application-specific flags: 00000000 0
16:00:15.819914 BC00500FF Read-Ack Application-specific flags: 00000000 255
16:00:16.720732 T80000200 Read-Data Status: 00000010 00000000
16:00:16.821285 B40000200 Read-Ack Status: 00000010 00000000
16:00:17.722413 T10010600 Write-Data Control setpoint: 6.00
16:00:17.822137 BD0010600 Write-Ack Control setpoint: 6.00
16:00:18.723409 T00110000 Read-Data Relative modulation level: 0.00
16:00:18.823918 BC0110000 Read-Ack Relative modulation level: 0.00
16:00:19.724784 T80190000 Read-Data Boiler water temperature: 0.00
16:00:19.825245 BC01941E6 Read-Ack Boiler water temperature: 65.90
16:00:20.726121 T801B0AB3 Read-Data Outside temperature: 10.70
16:00:20.826634 BC01B0A99 Read-Ack Outside temperature: 10.60
16:00:21.717639 T80000200 Read-Data Status: 00000010 00000000
16:00:21.827974 B40000200 Read-Ack Status: 00000010 00000000
16:00:22.719263 T10010600 Write-Data Control setpoint: 6.00
16:00:22.829168 BD0010600 Write-Ack Control setpoint: 6.00
16:00:23.720527 T00110000 Read-Data Relative modulation level: 0.00
16:00:23.830774 BC0110000 Read-Ack Relative modulation level: 0.00
16:00:24.721742 T80190000 Read-Data Boiler water temperature: 0.00
16:00:24.813871 B401941CC Read-Ack Boiler water temperature: 65.80
16:00:25.723232 T900E6400 Write-Data Maximum relative modulation level: 100.00
16:00:25.814513 B500E6400 Write-Ack Maximum relative modulation level: 100.00
16:00:26.724232 T80000200 Read-Data Status: 00000010 00000000
16:00:26.816217 B40000200 Read-Ack Status: 00000010 00000000
16:00:27.725966 T10010600 Write-Data Control setpoint: 6.00
16:00:27.817316 BD0010600 Write-Ack Control setpoint: 6.00
16:00:28.727015 T00110000 Read-Data Relative modulation level: 0.00
16:00:28.819154 BC0110000 Read-Ack Relative modulation level: 0.00
16:00:29.728307 T80190000 Read-Data Boiler water temperature: 0.00
16:00:29.820365 B401941CC Read-Ack Boiler water temperature: 65.80
16:00:30.729913 T10101200 Write-Data Room setpoint: 18.00
16:00:30.821174 BD0101200 Write-Ack Room setpoint: 18.00
16:00:31.731055 T80000200 Read-Data Status: 00000010 00000000
16:00:31.823001 B40000200 Read-Ack Status: 00000010 00000000
16:00:32.732848 T10010600 Write-Data Control setpoint: 6.00
16:00:32.824158 BD0010600 Write-Ack Control setpoint: 6.00
16:00:33.744030 T00110000 Read-Data Relative modulation level: 0.00
16:00:33.826011 BC0110000 Read-Ack Relative modulation level: 0.00
16:00:34.735645 T80190000 Read-Data Boiler water temperature: 0.00
16:00:34.827382 BC01941B3 Read-Ack Boiler water temperature: 65.70
16:00:35.737115 T101813DE Write-Data Room temperature: 19.87
16:00:35.828284 BD01813DE Write-Ack Room temperature: 19.87
16:00:36.728319 T80000200 Read-Data Status: 00000010 00000000
16:00:36.830280 B40000200 Read-Ack Status: 00000010 00000000
16:00:37.730277 T10010600 Write-Data Control setpoint: 6.00
16:00:37.831136 BD0010600 Write-Ack Control setpoint: 6.00
16:00:38.731007 T00110000 Read-Data Relative modulation level: 0.00
16:00:38.891386 BC0110000 Read-Ack Relative modulation level: 0.00
16:00:39.732225 T80190000 Read-Data Boiler water temperature: 0.00
16:00:39.822891 BC01941B3 Read-Ack Boiler water temperature: 65.70
16:00:40.733726 T00090000 Read-Data Remote override room setpoint: 0.00
16:00:40.770431 R007B0000 Read-Data DHW burner operation hours: 0
16:00:41.084567 BC07B019B Read-Ack DHW burner operation hours: 411
16:00:41.121047 AC0091200 Read-Ack Remote override room setpoint: 18.00
16:00:41.735403 T80000200 Read-Data Status: 00000010 00000000
16:00:41.885613 B40000200 Read-Ack Status: 00000010 00000000
16:00:42.736770 T10010600 Write-Data Control setpoint: 6.00
16:00:42.887394 BD0010600 Write-Ack Control setpoint: 6.00
16:00:43.737672 T00110000 Read-Data Relative modulation level: 0.00
16:00:43.888264 BC0110000 Read-Ack Relative modulation level: 0.00
16:00:44.739142 T80190000 Read-Data Boiler water temperature: 0.00
16:00:44.889765 B40194187 Read-Ack Boiler water temperature: 65.53
16:00:45.740201 T00630000 Read-Data Message ID 99: 0
16:00:45.776871 R00740000 Read-Data Burner starts: 0
16:00:46.091160 BC0745238 Read-Ack Burner starts: 21048
16:00:46.127996 AF0630000 Unk-DataId Message ID 99: 0
16:00:46.741938 T80000200 Read-Data Status: 00000010 00000000
16:00:46.892414 B40000200 Read-Ack Status: 00000010 00000000
16:00:47.743523 T10010600 Write-Data Control setpoint: 6.00
16:00:47.883439 BD0010600 Write-Ack Control setpoint: 6.00
16:00:48.744641 T00110000 Read-Data Relative modulation level: 0.00
16:00:48.885178 BC0110000 Read-Ack Relative modulation level: 0.00
16:00:49.745920 T80190000 Read-Data Boiler water temperature: 0.00
16:00:49.896405 BC0194180 Read-Ack Boiler water temperature: 65.50
16:00:50.750559 T10383C00 Write-Data DHW setpoint: 60.00
16:00:50.887983 BD0383C00 Write-Ack DHW setpoint: 60.00
16:00:51.739175 T80000200 Read-Data Status: 00000010 00000000
16:00:51.889266 B40000200 Read-Ack Status: 00000010 00000000
16:00:52.740632 T10010600 Write-Data Control setpoint: 6.00
16:00:52.891041 BD0010600 Write-Ack Control setpoint: 6.00
16:00:53.741578 T00110000 Read-Data Relative modulation level: 0.00
16:00:53.891891 BC0110000 Read-Ack Relative modulation level: 0.00
16:00:54.742919 T80190000 Read-Data Boiler water temperature: 0.00
16:00:54.883462 BC0194180 Read-Ack Boiler water temperature: 65.50
16:00:55.744316 T00050000 Read-Data Application-specific flags: 00000000 0
16:00:55.884835 BC00500FF Read-Ack Application-specific flags: 00000000 255
16:00:56.745597 T80000200 Read-Data Status: 00000010 00000000
16:00:56.886165 B40000200 Read-Ack Status: 00000010 00000000
16:00:57.747509 T10010600 Write-Data Control setpoint: 6.00
16:00:57.887072 BD0010600 Write-Ack Control setpoint: 6.00
16:00:58.748335 T00110000 Read-Data Relative modulation level: 0.00
16:00:58.888827 BC0110000 Read-Ack Relative modulation level: 0.00
16:00:59.749643 T80190000 Read-Data Boiler water temperature: 0.00
16:00:59.890221 BC0194180 Read-Ack Boiler water temperature: 65.50
16:01:00.760963 T801B0AB3 Read-Data Outside temperature: 10.70
16:01:00.892038 BC01B0A99 Read-Ack Outside temperature: 10.60
16:01:01.752591 T80000200 Read-Data Status: 00000010 00000000
16:01:01.893036 B40000200 Read-Ack Status: 00000010 00000000
16:01:02.754477 T10010600 Write-Data Control setpoint: 6.00
16:01:02.884132 BD0010600 Write-Ack Control setpoint: 6.00
16:01:03.755414 T00110000 Read-Data Relative modulation level: 0.00
16:01:03.885921 BC0110000 Read-Ack Relative modulation level: 0.00
16:01:04.756460 T80190000 Read-Data Boiler water temperature: 0.00
16:01:04.887217 BC0194180 Read-Ack Boiler water temperature: 65.50
16:01:05.758251 T900E6400 Write-Data Maximum relative modulation level: 100.00
16:01:05.888194 B500E6400 Write-Ack Maximum relative modulation level: 100.00
16:01:06.759333 T80000200 Read-Data Status: 00000010 00000000
16:01:06.889917 B40000200 Read-Ack Status: 00000010 00000000
16:01:07.760998 T10010600 Write-Data Control setpoint: 6.00
16:01:07.890939 BD0010600 Write-Ack Control setpoint: 6.00
16:01:08.761942 T00110000 Read-Data Relative modulation level: 0.00
16:01:08.892685 BC0110000 Read-Ack Relative modulation level: 0.00
16:01:09.763452 T80190000 Read-Data Boiler water temperature: 0.00
16:01:09.883980 BC0194180 Read-Ack Boiler water temperature: 65.50
16:01:10.765052 T10101200 Write-Data Room setpoint: 18.00
16:01:10.885718 BD0101200 Write-Ack Room setpoint: 18.00
16:01:11.766121 T80000200 Read-Data Status: 00000010 00000000
16:01:11.896985 B40000200 Read-Ack Status: 00000010 00000000
16:01:12.767829 T10010600 Write-Data Control setpoint: 6.00
16:01:12.897821 BD0010600 Write-Ack Control setpoint: 6.00
16:01:13.768823 T00110000 Read-Data Relative modulation level: 0.00
16:01:13.899941 BC0110000 Read-Ack Relative modulation level: 0.00
16:01:14.770188 T80190000 Read-Data Boiler water temperature: 0.00
16:01:14.900850 BC0194180 Read-Ack Boiler water temperature: 65.50
16:01:15.771968 T101813DE Write-Data Room temperature: 19.87
16:01:15.901931 BD01813DE Write-Ack Room temperature: 19.87
16:01:16.763034 T80000200 Read-Data Status: 00000010 00000000
16:01:16.885101 B40000200 Read-Ack Status: 00000010 00000000
16:01:17.764652 T10010600 Write-Data Control setpoint: 6.00
16:01:17.885872 BD0010600 Write-Ack Control setpoint: 6.00
16:01:18.765682 T00110000 Read-Data Relative modulation level: 0.00
16:01:18.887681 BC0110000 Read-Ack Relative modulation level: 0.00
16:01:19.767034 T80190000 Read-Data Boiler water temperature: 0.00
16:01:19.889054 B40194166 Read-Ack Boiler water temperature: 65.40
16:01:20.768455 T00090000 Read-Data Remote override room setpoint: 0.00
16:01:20.805862 R80750000 Read-Data CH pump starts: 0
16:01:20.988934 BC0757180 Read-Ack CH pump starts: 29056
16:01:21.026564 AC0091200 Read-Ack Remote override room setpoint: 18.00
16:01:21.769747 T80000200 Read-Data Status: 00000010 00000000
16:01:21.891692 B40000200 Read-Ack Status: 00000010 00000000
16:01:22.771418 T10010600 Write-Data Control setpoint: 6.00
16:01:22.892611 BD0010600 Write-Ack Control setpoint: 6.00
16:01:23.772545 T00110000 Read-Data Relative modulation level: 0.00
16:01:23.894394 BC0110000 Read-Ack Relative modulation level: 0.00
16:01:24.771323 T80190000 Read-Data Boiler water temperature: 0.00
16:01:24.884464 B40194166 Read-Ack Boiler water temperature: 65.40
16:01:25.775840 T00630000 Read-Data Message ID 99: 0
16:01:25.813484 R80760000 Read-Data DHW pump/valve starts: 0
16:01:26.086151 B407639B8 Read-Ack DHW pump/valve starts: 14776
16:01:26.122807 AF0630000 Unk-DataId Message ID 99: 0
16:01:26.776622 T80000200 Read-Data Status: 00000010 00000000
16:01:26.887103 B40000200 Read-Ack Status: 00000010 00000000
16:01:27.778237 T10010600 Write-Data Control setpoint: 6.00
16:01:27.888070 BD0010600 Write-Ack Control setpoint: 6.00
16:01:28.779267 T00110000 Read-Data Relative modulation level: 0.00
16:01:28.889897 BC0110000 Read-Ack Relative modulation level: 0.00
16:01:29.780646 T80190000 Read-Data Boiler water temperature: 0.00
16:01:29.891203 BC019414C Read-Ack Boiler water temperature: 65.30
16:01:30.785234 T90395A00 Write-Data Max CH water setpoint: 90.00
16:01:30.895750 BE0394600 Data-Inv Max CH water setpoint: 70.00
16:01:30.935900 AD0394600 Write-Ack Max CH water setpoint: 70.00
16:01:31.783469 T80000200 Read-Data Status: 00000010 00000000
16:01:31.884418 B40000200 Read-Ack Status: 00000010 00000000
16:01:32.785178 T10010600 Write-Data Control setpoint: 6.00
16:01:32.884948 BD0010600 Write-Ack Control setpoint: 6.00
16:01:33.786120 T00110000 Read-Data Relative modulation level: 0.00
16:01:33.886658 BC0110000 Read-Ack Relative modulation level: 0.00
16:01:34.787487 T80190000 Read-Data Boiler water temperature: 0.00
16:01:34.888066 BC019414C Read-Ack Boiler water temperature: 65.30
16:01:35.789012 T00050000 Read-Data Application-specific flags: 00000000 0
16:01:35.889403 BC00500FF Read-Ack Application-specific flags: 00000000 255
16:01:36.790264 T80000200 Read-Data Status: 00000010 00000000
16:01:36.890747 B40000200 Read-Ack Status: 00000010 00000000
16:01:37.792194 T10010600 Write-Data Control setpoint: 6.00
16:01:37.891857 BD0010600 Write-Ack Control setpoint: 6.00
16:01:38.793087 T00110000 Read-Data Relative modulation level: 0.00
16:01:38.893631 BC0110000 Read-Ack Relative modulation level: 0.00
16:01:39.794540 T80190000 Read-Data Boiler water temperature: 0.00
16:01:39.894869 BC019414C Read-Ack Boiler water temperature: 65.30
16:01:40.795838 T801B0AB3 Read-Data Outside temperature: 10.70
16:01:40.906248 BC01B0A99 Read-Ack Outside temperature: 10.60
16:01:41.797227 T80000200 Read-Data Status: 00000010 00000000
16:01:41.897646 B40000200 Read-Ack Status: 00000010 00000000
16:01:42.798929 T10010600 Write-Data Control setpoint: 6.00
16:01:42.898653 BD0010600 Write-Ack Control setpoint: 6.00
16:01:43.809905 T00110000 Read-Data Relative modulation level: 0.00
16:01:43.900319 BC0110000 Read-Ack Relative modulation level: 0.00
16:01:44.801346 T80190000 Read-Data Boiler water temperature: 0.00
16:01:44.901785 BC019414C Read-Ack Boiler water temperature: 65.30
16:01:45.803057 T900E6400 Write-Data Maximum relative modulation level: 100.00
16:01:45.902718 B500E6400 Write-Ack Maximum relative modulation level: 100.00
16:01:46.814142 T80000200 Read-Data Status: 00000010 00000000
16:01:46.904626 B40000200 Read-Ack Status: 00000010 00000000
16:01:47.815779 T10010600 Write-Data Control setpoint: 6.00
16:01:47.905482 BD0010600 Write-Ack Control setpoint: 6.00
16:01:48.816754 T00110000 Read-Data Relative modulation level: 0.00
16:01:48.907273 BC0110000 Read-Ack Relative modulation level: 0.00
16:01:49.818244 T80190000 Read-Data Boiler water temperature: 0.00
16:01:49.909165 B40194135 Read-Ack Boiler water temperature: 65.21
16:01:50.819850 T10101200 Write-Data Room setpoint: 18.00
16:01:50.909639 BD0101200 Write-Ack Room setpoint: 18.00
16:01:51.820985 T80000200 Read-Data Status: 00000010 00000000
16:01:51.911399 B40000200 Read-Ack Status: 00000010 00000000
16:01:52.823095 T10010600 Write-Data Control setpoint: 6.00
16:01:52.926558 BD0010600 Write-Ack Control setpoint: 6.00
16:01:53.823790 T00110000 Read-Data Relative modulation level: 0.00
16:01:53.913981 BC0110000 Read-Ack Relative modulation level: 0.00
16:01:54.825191 T80190000 Read-Data Boiler water temperature: 0.00
16:01:54.915378 B40194133 Read-Ack Boiler water temperature: 65.20
16:01:55.826753 T901813DC Write-Data Room temperature: 19.86
16:01:55.987500 B501813DC Write-Ack Room temperature: 19.86
16:01:56.828028 T80000200 Read-Data Status: 00000010 00000000
16:01:56.918200 B40000200 Read-Ack Status: 00000010 00000000
16:01:57.829438 T10010600 Write-Data Control setpoint: 6.00
16:01:57.990120 BD0010600 Write-Ack Control setpoint: 6.00
16:01:58.830494 T00110000 Read-Data Relative modulation level: 0.00
16:01:58.990925 BC0110000 Read-Ack Relative modulation level: 0.00
16:01:59.831807 T80190000 Read-Data Boiler water temperature: 0.00
16:01:59.992772 B40194133 Read-Ack Boiler water temperature: 65.20
16:02:00.837767 T00090000 Read-Data Remote override room setpoint: 0.00
16:02:00.875899 R00770000 Read-Data DHW burner starts: 0
16:02:01.093771 B40774120 Read-Ack DHW burner starts: 16672
16:02:01.131564 AC0091200 Read-Ack Remote override room setpoint: 18.00
16:02:01.834642 T80000200 Read-Data Status: 00000010 00000000
16:02:01.985163 B40000200 Read-Ack Status: 00000010 00000000
16:02:02.836488 T10010600 Write-Data Control setpoint: 6.00
16:02:02.986090 BD0010600 Write-Ack Control setpoint: 6.00
16:02:03.837331 T00110000 Read-Data Relative modulation level: 0.00
16:02:03.987795 BC0110000 Read-Ack Relative modulation level: 0.00
16:02:04.838950 T80190000 Read-Data Boiler water temperature: 0.00
16:02:04.989340 B40194133 Read-Ack Boiler water temperature: 65.20
16:02:05.839949 T00630000 Read-Data Message ID 99: 0
16:02:05.876512 R00780000 Read-Data Burner operation hours: 0
16:02:06.190916 BC0780EDA Read-Ack Burner operation hours: 3802
16:02:06.227523 AF0630000 Unk-DataId Message ID 99: 0
16:02:06.831624 T80000200 Read-Data Status: 00000010 00000000
16:02:06.992055 B40000200 Read-Ack Status: 00000010 00000000
16:02:07.833267 T10010600 Write-Data Control setpoint: 6.00
16:02:07.993927 BD0010600 Write-Ack Control setpoint: 6.00
16:02:08.834533 T00110000 Read-Data Relative modulation level: 0.00
16:02:08.994802 BC0110000 Read-Ack Relative modulation level: 0.00
16:02:09.825637 T80190000 Read-Data Boiler water temperature: 0.00
16:02:09.916083 B40194133 Read-Ack Boiler water temperature: 65.20
16:02:10.827214 T80640000 Read-Data Remote override function: 00000000
16:02:10.864958 R80790000 Read-Data CH pump operation hours: 0
16:02:11.087827 BC0791126 Read-Ack CH pump operation hours: 4390
16:02:11.129244 AC0640002 Read-Ack Remote override function: 00000010
16:02:11.828474 T80000200 Read-Data Status: 00000010 00000000
16:02:11.989111 B40000200 Read-Ack Status: 00000010 00000000
16:02:12.830393 T10010600 Write-Data Control setpoint: 6.00
16:02:12.991010 BD0010600 Write-Ack Control setpoint: 6.00
16:02:13.831141 T00110000 Read-Data Relative modulation level: 0.00
16:02:13.991823 BC0110000 Read-Ack Relative modulation level: 0.00
16:02:14.832507 T80190000 Read-Data Boiler water temperature: 0.00
16:02:14.993230 B40194133 Read-Ack Boiler water temperature: 65.20
16:02:15.834251 T00050000 Read-Data Application-specific flags: 00000000 0
16:02:15.994574 BC00500FF Read-Ack Application-specific flags: 00000000 255
16:02:16.845557 T80000200 Read-Data Status: 00000010 00000000
16:02:16.986120 B40000200 Read-Ack Status: 00000010 00000000
16:02:17.848043 T10010600 Write-Data Control setpoint: 6.00
16:02:17.987227 BD0010600 Write-Ack Control setpoint: 6.00
16:02:18.848447 T00110000 Read-Data Relative modulation level: 0.00
16:02:18.988669 BC0110000 Read-Ack Relative modulation level: 0.00
16:02:19.849518 T80190000 Read-Data Boiler water temperature: 0.00
16:02:20.119527 B4019412E Read-Ack Boiler water temperature: 65.18
16:02:20.851961 T801B0AB3 Read-Data Outside temperature: 10.70
16:02:20.993644 BC01B0A99 Read-Ack Outside temperature: 10.60
16:02:21.854124 T80000200 Read-Data Status: 00000010 00000000
16:02:21.994833 B40000200 Read-Ack Status: 00000010 00000000
16:02:22.853840 T10010600 Write-Data Control setpoint: 6.00
16:02:23.003861 BD0010600 Write-Ack Control setpoint: 6.00
16:02:23.958121 T00110000 Read-Data Relative modulation level: 0.00
16:02:23.985724 BC0110000 Read-Ack Relative modulation level: 0.00
16:02:24.857734 T80190000 Read-Data Boiler water temperature: 0.00
16:02:24.987513 BC0194119 Read-Ack Boiler water temperature: 65.10
16:02:25.858298 T900E6400 Write-Data Maximum relative modulation level: 100.00
16:02:25.998530 B500E6400 Write-Ack Maximum relative modulation level: 100.00
16:02:26.859416 T80000200 Read-Data Status: 00000010 00000000
16:02:26.999892 B40000200 Read-Ack Status: 00000010 00000000
16:02:27.860977 T10010600 Write-Data Control setpoint: 6.00
16:02:28.000872 BD0010600 Write-Ack Control setpoint: 6.00
16:02:28.862043 T00110000 Read-Data Relative modulation level: 0.00
16:02:29.002708 BC0110000 Read-Ack Relative modulation level: 0.00
16:02:29.863422 T80190000 Read-Data Boiler water temperature: 0.00
16:02:30.004032 BC0194119 Read-Ack Boiler water temperature: 65.10
16:02:30.865213 T10101200 Write-Data Room setpoint: 18.00
16:02:30.986534 BD0101200 Write-Ack Room setpoint: 18.00
16:02:31.856404 T80000200 Read-Data Status: 00000010 00000000
16:02:31.988569 B40000200 Read-Ack Status: 00000010 00000000
16:02:32.867954 T10010600 Write-Data Control setpoint: 6.00
16:02:32.989554 BD0010600 Write-Ack Control setpoint: 6.00
16:02:33.868947 T00110000 Read-Data Relative modulation level: 0.00
16:02:33.991042 BC0110000 Read-Ack Relative modulation level: 0.00
16:02:34.870383 T80190000 Read-Data Boiler water temperature: 0.00
16:02:34.992411 BC0194119 Read-Ack Boiler water temperature: 65.10
16:02:35.872343 T901813DC Write-Data Room temperature: 19.86
16:02:35.993458 B501813DC Write-Ack Room temperature: 19.86
16:02:36.863355 T80000200 Read-Data Status: 00000010 00000000
16:02:36.995675 B40000200 Read-Ack Status: 00000010 00000000
16:02:37.864997 T10010600 Write-Data Control setpoint: 6.00
16:02:37.996421 BD0010600 Write-Ack Control setpoint: 6.00
16:02:38.866361 T00110000 Read-Data Relative modulation level: 0.00
16:02:38.998229 BC0110000 Read-Ack Relative modulation level: 0.00
16:02:39.867635 T80190000 Read-Data Boiler water temperature: 0.00
16:02:39.988328 B40194100 Read-Ack Boiler water temperature: 65.00
16:02:40.868983 T00090000 Read-Data Remote override room setpoint: 0.00
16:02:40.906462 R807A0000 Read-Data DHW pump/valve operation hours: 0
16:02:41.089559 B407A5BB0 Read-Ack DHW pump/valve operation hours: 23472
16:02:41.127304 AC0091200 Read-Ack Remote override room setpoint: 18.00
16:02:41.870318 T80000200 Read-Data Status: 00000010 00000000
16:02:41.990721 B40000200 Read-Ack Status: 00000010 00000000
16:02:42.872070 T10010600 Write-Data Control setpoint: 6.00
16:02:42.991747 BD0010600 Write-Ack Control setpoint: 6.00
16:02:43.872994 T00110000 Read-Data Relative modulation level: 0.00
16:02:43.993436 BC0110000 Read-Ack Relative modulation level: 0.00
16:02:44.874377 T80190000 Read-Data Boiler water temperature: 0.00
16:02:44.994896 B40194100 Read-Ack Boiler water temperature: 65.00
16:02:45.885578 T00630000 Read-Data Message ID 99: 0
16:02:45.928554 R007B0000 Read-Data DHW burner operation hours: 0
16:02:46.196913 BC07B019B Read-Ack DHW burner operation hours: 411
16:02:46.239620 AF0630000 Unk-DataId Message ID 99: 0
16:02:46.877223 T80000200 Read-Data Status: 00000010 00000000
16:02:46.987726 B40000200 Read-Ack Status: 00000010 00000000
16:02:47.878885 T10010600 Write-Data Control setpoint: 6.00
16:02:47.988627 BD0010600 Write-Ack Control setpoint: 6.00
16:02:48.879964 T00110000 Read-Data Relative modulation level: 0.00
16:02:48.990744 BC0110000 Read-Ack Relative modulation level: 0.00
16:02:49.881709 T80190000 Read-Data Boiler water temperature: 0.00
16:02:49.991749 B40194100 Read-Ack Boiler water temperature: 65.00
16:02:50.795677 Command: TT=0
16:02:50.833234 OK
16:02:50.890311 T00740000 Read-Data Burner starts: 0
16:02:51.093221 BC0745238 Read-Ack Burner starts: 21048
16:02:51.884123 T80000200 Read-Data Status: 00000010 00000000
16:02:51.994544 B40000200 Read-Ack Status: 00000010 00000000
16:02:52.885781 T10010600 Write-Data Control setpoint: 6.00
16:02:52.995561 BD0010600 Write-Ack Control setpoint: 6.00
16:02:53.886970 T00110000 Read-Data Relative modulation level: 0.00
16:02:53.997262 BC0110000 Read-Ack Relative modulation level: 0.00
16:02:54.888188 T80190000 Read-Data Boiler water temperature: 0.00
16:02:54.988674 B40194100 Read-Ack Boiler water temperature: 65.00
16:02:55.889621 T00050000 Read-Data Application-specific flags: 00000000 0
16:02:55.990114 BC00500FF Read-Ack Application-specific flags: 00000000 255
16:02:56.891039 T80000200 Read-Data Status: 00000010 00000000
16:02:56.991618 B40000200 Read-Ack Status: 00000010 00000000
16:02:57.892815 T10010600 Write-Data Control setpoint: 6.00
16:02:57.992536 BD0010600 Write-Ack Control setpoint: 6.00
16:02:58.893739 T00110000 Read-Data Relative modulation level: 0.00
16:02:58.994267 BC0110000 Read-Ack Relative modulation level: 0.00
16:02:59.895478 T80190000 Read-Data Boiler water temperature: 0.00
16:02:59.995719 B40194100 Read-Ack Boiler water temperature: 65.00
16:03:00.897732 T801B0AB3 Read-Data Outside temperature: 10.70
16:03:00.997080 BC01B0A99 Read-Ack Outside temperature: 10.60
16:03:01.898390 T80000200 Read-Data Status: 00000010 00000000
16:03:01.998855 B40000200 Read-Ack Status: 00000010 00000000
16:03:02.899770 T10010600 Write-Data Control setpoint: 6.00
16:03:02.989467 BD0010600 Write-Ack Control setpoint: 6.00
16:03:03.900689 T00110000 Read-Data Relative modulation level: 0.00
16:03:03.991156 BC0110000 Read-Ack Relative modulation level: 0.00
16:03:04.902067 T80190000 Read-Data Boiler water temperature: 0.00
16:03:04.992518 BC01940CC Read-Ack Boiler water temperature: 64.80
16:03:05.904248 T900E6400 Write-Data Maximum relative modulation level: 100.00
16:03:05.993796 B500E6400 Write-Ack Maximum relative modulation level: 100.00
16:03:06.904965 T80000200 Read-Data Status: 00000010 00000000
16:03:06.995420 B40000200 Read-Ack Status: 00000010 00000000
16:03:07.906546 T10010600 Write-Data Control setpoint: 6.00
16:03:07.996256 BD0010600 Write-Ack Control setpoint: 6.00
16:03:08.907523 T00110000 Read-Data Relative modulation level: 0.00
16:03:09.008029 BC0110000 Read-Ack Relative modulation level: 0.00
16:03:09.909011 T80190000 Read-Data Boiler water temperature: 0.00
16:03:09.999434 BC01940CC Read-Ack Boiler water temperature: 64.80
16:03:10.910809 T10101200 Write-Data Room setpoint: 18.00
16:03:11.000511 BD0101200 Write-Ack Room setpoint: 18.00
16:03:11.911921 T80000200 Read-Data Status: 00000010 00000000
16:03:12.002724 B40000200 Read-Ack Status: 00000010 00000000
16:03:12.913744 T10010600 Write-Data Control setpoint: 6.00
16:03:13.003288 BD0010600 Write-Ack Control setpoint: 6.00
16:03:13.914580 T00110000 Read-Data Relative modulation level: 0.00
16:03:14.005071 BC0110000 Read-Ack Relative modulation level: 0.00
16:03:14.915988 T80190000 Read-Data Boiler water temperature: 0.00
16:03:15.006461 BC01940CC Read-Ack Boiler water temperature: 64.80
16:03:15.917817 T101813D7 Write-Data Room temperature: 19.84
16:03:16.096804 BD01813D7 Write-Ack Room temperature: 19.84
16:03:16.918884 T80000200 Read-Data Status: 00000010 00000000
16:03:17.009289 B40000200 Read-Ack Status: 00000010 00000000
16:03:17.920532 T10010600 Write-Data Control setpoint: 6.00
16:03:18.010672 BD0010600 Write-Ack Control setpoint: 6.00
16:03:18.911663 T00110000 Read-Data Relative modulation level: 0.00
16:03:19.012031 BC0110000 Read-Ack Relative modulation level: 0.00
16:03:19.913002 T80190000 Read-Data Boiler water temperature: 0.00
16:03:20.013657 B401940B3 Read-Ack Boiler water temperature: 64.70
16:03:20.924592 T00090000 Read-Data Remote override room setpoint: 0.00
16:03:20.955448 R00740000 Read-Data Burner starts: 0
16:03:21.096559 BC0745238 Read-Ack Burner starts: 21048
16:03:21.128456 AC0090000 Read-Ack Remote override room setpoint: 0.00
16:03:21.915812 T00090000 Read-Data Remote override room setpoint: 0.00
16:03:21.953355 R80750000 Read-Data CH pump starts: 0
16:03:22.196469 BC0757180 Read-Ack CH pump starts: 29056
16:03:22.236916 AC0090000 Read-Ack Remote override room setpoint: 0.00
16:03:22.917225 T00090000 Read-Data Remote override room setpoint: 0.00
16:03:22.954479 R80760000 Read-Data DHW pump/valve starts: 0
16:03:23.097694 B407639B8 Read-Ack DHW pump/valve starts: 14776
16:03:23.135844 AC0090000 Read-Ack Remote override room setpoint: 0.00
16:03:23.918995 T00000000 Read-Data Status: 00000000 00000000
16:03:24.019142 BC0000000 Read-Ack Status: 00000000 00000000
16:03:24.930326 T10010600 Write-Data Control setpoint: 6.00
16:03:25.063495 BD0010600 Write-Ack Control setpoint: 6.00
16:03:25.921347 T00110000 Read-Data Relative modulation level: 0.00
16:03:26.021766 BC0110000 Read-Ack Relative modulation level: 0.00
16:03:26.932671 T80190000 Read-Data Boiler water temperature: 0.00
16:03:27.023200 B401940B3 Read-Ack Boiler water temperature: 64.70
16:03:27.934087 T00630000 Read-Data Message ID 99: 0
16:03:27.971946 R00770000 Read-Data DHW burner starts: 0
16:03:28.295049 B40774120 Read-Ack DHW burner starts: 16672
16:03:28.332906 AF0630000 Unk-DataId Message ID 99: 0
16:03:28.925803 T00000000 Read-Data Status: 00000000 00000000
16:03:29.096111 BC0000000 Read-Ack Status: 00000000 00000000
16:03:29.927264 T10010600 Write-Data Control setpoint: 6.00
16:03:30.095402 BD0010600 Write-Ack Control setpoint: 6.00
16:03:30.928321 T00110000 Read-Data Relative modulation level: 0.00
16:03:31.098860 BC0110000 Read-Ack Relative modulation level: 0.00
16:03:31.929673 T80190000 Read-Data Boiler water temperature: 0.00
16:03:32.090409 B401940B3 Read-Ack Boiler water temperature: 64.70
16:03:32.950941 T00770000 Read-Data DHW burner starts: 0
16:03:33.191804 B40774120 Read-Ack DHW burner starts: 16672
16:03:33.933164 T00000000 Read-Data Status: 00000000 00000000
16:03:34.093005 BC0000000 Read-Ack Status: 00000000 00000000
16:03:34.934753 T10010600 Write-Data Control setpoint: 6.00
16:03:35.096071 BD0010600 Write-Ack Control setpoint: 6.00
16:03:35.935172 T00110000 Read-Data Relative modulation level: 0.00
16:03:36.095749 BC0110000 Read-Ack Relative modulation level: 0.00
16:03:36.936893 T80190000 Read-Data Boiler water temperature: 0.00
16:03:37.097181 B401940B3 Read-Ack Boiler water temperature: 64.70
16:03:37.938032 T00050000 Read-Data Application-specific flags: 00000000 0
16:03:38.098562 BC00500FF Read-Ack Application-specific flags: 00000000 255
16:03:38.939460 T00000000 Read-Data Status: 00000000 00000000
16:03:39.090160 BC0000000 Read-Ack Status: 00000000 00000000
16:03:39.941163 T10010600 Write-Data Control setpoint: 6.00
16:03:40.090902 BD0010600 Write-Ack Control setpoint: 6.00
16:03:40.942171 T00110000 Read-Data Relative modulation level: 0.00
16:03:41.102785 BC0110000 Read-Ack Relative modulation level: 0.00
16:03:41.943566 T80190000 Read-Data Boiler water temperature: 0.00
16:03:42.104275 B401940B3 Read-Ack Boiler water temperature: 64.70
16:03:42.944965 T801B0AB3 Read-Data Outside temperature: 10.70
16:03:43.105491 BC01B0A99 Read-Ack Outside temperature: 10.60
16:03:43.946391 T00000000 Read-Data Status: 00000000 00000000
16:03:44.106912 BC0000000 Read-Ack Status: 00000000 00000000
16:03:44.948199 T10010600 Write-Data Control setpoint: 6.00
16:03:45.105506 BD0010600 Write-Ack Control setpoint: 6.00
16:03:45.949233 T00110000 Read-Data Relative modulation level: 0.00
16:03:46.091313 BC0110000 Read-Ack Relative modulation level: 0.00
16:03:46.950450 T80190000 Read-Data Boiler water temperature: 0.00
16:03:47.092690 B401940B3 Read-Ack Boiler water temperature: 64.70
16:03:47.952235 T900E6400 Write-Data Maximum relative modulation level: 100.00
16:03:48.093638 B500E6400 Write-Ack Maximum relative modulation level: 100.00
16:03:48.953589 T00000000 Read-Data Status: 00000000 00000000
16:03:49.095590 BC0000000 Read-Ack Status: 00000000 00000000
16:03:49.955351 T10010600 Write-Data Control setpoint: 6.00
16:03:50.106477 BD0010600 Write-Ack Control setpoint: 6.00
16:03:50.956564 T00110000 Read-Data Relative modulation level: 0.00
16:03:51.098098 BC0110000 Read-Ack Relative modulation level: 0.00
16:03:51.957853 T80190000 Read-Data Boiler water temperature: 0.00
16:03:52.099948 BC0194099 Read-Ack Boiler water temperature: 64.60
16:03:52.959220 T10100F00 Write-Data Room setpoint: 15.00
16:03:53.100593 BD0100F00 Write-Ack Room setpoint: 15.00
16:03:53.960201 T00000000 Read-Data Status: 00000000 00000000
16:03:54.091103 BC0000000 Read-Ack Status: 00000000 00000000
16:03:54.961887 T10010600 Write-Data Control setpoint: 6.00
16:03:55.112803 BD0010600 Write-Ack Control setpoint: 6.00
16:03:55.962942 T00110000 Read-Data Relative modulation level: 0.00
16:03:56.093766 BC0110000 Read-Ack Relative modulation level: 0.00
16:03:56.964353 T80190000 Read-Data Boiler water temperature: 0.00