Yesterday i upgraded my gateway from 3.3 to 3.4 and this morning i came down into a very hot living room. I`m not sure what happend because the thermostat gave me back a setpoint of 15.5 degrees ( as it is set every night)
What happend ?
Gateway Firmware upgrade 3.3 to 3.4
Moderator: hvxl
Gateway Firmware upgrade 3.3 to 3.4
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s
Re: Gateway Firmware upgrade 3.3 to 3.4
This morning i had the same issue and both the OTmonitor and the thermostat told me the set-point was 15,5 degrees but the boiler kept on burning.
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s
Re: Gateway Firmware upgrade 3.3 to 3.4
The problem for this issue is resolved, the issue was caused by a broken 3-way valve, also with a disconnected termostat the boiler kept burning
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s
Re: Gateway Firmware upgrade 3.3 to 3.4
Thanks for the update, and clearing the gateway from blame.
Schelte
Re: Gateway Firmware upgrade 3.3 to 3.4
The gateway is fine, Although it was a brain cracker to find the issuehvxl wrote:Thanks for the update, and clearing the gateway from blame.
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s