Room Setpoint command is not working on my thermostat

This Forum is about the Opentherm gateway (OTGW) from Schelte

Moderator: hvxl

Post Reply
cakiroglu
Starting Member
Starting Member
Posts: 4
Joined: Wed Oct 16, 2013 12:09 am

Room Setpoint command is not working on my thermostat

Post by cakiroglu »

Hi,

I have got problem with my thermostat because it is not setting room temperature value sent by opentherm gateway.

My thermostat is Bosch TRZ200. But when I open the case I can read Honeywell CS0257A-LS
I coluldn't find much details about it on google.
This is a pic of it while it is without case.
Image


Here is an example log output that showing the problem. I think. it is not recognising the code as it says.


...
23:43:03.836158 BC000030A Read-Ack Status: 00000011 00001010
23:43:04.663132 T90013700 Write-Data Control setpoint: 55.00
23:43:04.835026 B50013700 Write-Ack Control setpoint: 55.00
23:43:05.661618 T900E6400 Write-Data Maximum relative modulation level: 100.00
23:43:05.833217 B700E0000 Unk-DataId Maximum relative modulation level: 0.00
23:43:06.659749 T80190000 Read-Data Boiler water temperature: 0.00
23:43:06.831574 BC0193706 Read-Ack Boiler water temperature: 55.02
23:43:07.674121 T90101600 Write-Data Room setpoint: 22.00
23:43:07.845311 B70100000 Unk-DataId Room setpoint: 0.00
23:43:07.850364 AD0100000 Write-Ack Room setpoint: 0.00

- CH enable: enabled (1)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
23:43:08.656658 T00000300 Read-Data Status: 00000011 00000000
- Fault indication: no fault (0)
- CH mode: active (1)
- DHW mode: not active (0)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
23:43:08.828131 BC000030A Read-Ack Status: 00000011 00001010
23:43:09.670582 T90013700 Write-Data Control setpoint: 55.00
23:43:09.842589 B50013700 Write-Ack Control setpoint: 55.00
23:43:10.668803 T900E6400 Write-Data Maximum relative modulation level: 100.00
23:43:10.840486 B700E0000 Unk-DataId Maximum relative modulation level: 0.00
23:43:11.666559 T80190000 Read-Data Boiler water temperature: 0.00
23:43:11.839171 BC0193706 Read-Ack Boiler water temperature: 55.02
23:43:12.665670 T101814DC Write-Data Room temperature: 20.86
23:43:12.836017 BF0180000 Unk-DataId Room temperature: 0.00
- CH enable: enabled (1)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)

...

If it is going to help I can provide more logs and info.

Do you have any advise on that kind of situation ?

Thanks.
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Room Setpoint command is not working on my thermostat

Post by hvxl »

This only shows that the gateway is not sending an override setpoint to the thermostat. Why not is unclear from the available data.

So yes, more logs would be necessary to determine what is going on. From a few minutes before you give the TT or TC command until 10 or 15 minutes after would be preferred. Please also indicate which firmware version you are using.
Schelte