Hi all,

I have already read a lot about the Opentherm Gateway, but I still have some questions. Hopefully you can help me:

1. Can you read the temperature, using the gateway, that has been entered into the thermostat? So if someone changes the temperature using the thermostat you can detect this.
2. I read you can connect an outside temperature to the gateway, but is it also possible to use your own (internal) temperature sensor and send the values to the thermostat?
3. Is there a list that shows all the possible data id's?

Thanks!
hvxl
Senior Member
Senior Member
Posts: 1966
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Opentherm gateway general questions

Post by hvxl »

1. Depends on the thermostat. Some thermostats report the setpoint, others don't. Check the equipment matrix for thermostats that send MsgID 16.
2. Yes.
3. Take a look at the opentherm specification (version 2.2 is available on line somewhere).
Schelte
eggn1n3
Starting Member
Starting Member
Posts: 7
Joined: Tue Aug 12, 2014 8:01 pm

Re: Opentherm gateway general questions

Post by eggn1n3 »

Great, thanks for your answers!