Hello,

I build the usb opentherm gateway for controlling my celcia 20 thermostat with the Remeha Quinta 28C boiler. Everything is working fine except the temperature override. The boiler doesn't support the override function, but the celcia 20 should support that function. The gateway firmware doesn't recognize the celcia20 (PR:D). I tried different firmware versions. How can i force the firmware to celcia thermostat (PR:C)?
hvxl
Senior Member
Senior Member
Posts: 1967
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Celcia20 and OpenthermGateway

Post by hvxl »

Did you allow enough time for the gateway to figure out which thermostat you have? It may take up to 15 minutes before all the necessary information has been provided by the thermostat.

If waiting a bit longer doesn't help, please enter the command DP=63 and then collect 30 minutes of logs and send them to me.
Schelte
b@s
Starting Member
Starting Member
Posts: 2
Joined: Fri Aug 22, 2014 4:40 pm

Re: Celcia20 and OpenthermGateway

Post by b@s »

My gateway is working oké now.

Thank you Schelte for the firmware with the celcia bit at default.

Bas
MtenHoorn
Starting Member
Starting Member
Posts: 1
Joined: Thu Dec 13, 2012 3:54 pm
Location: Alkmaar

Re: Celcia20 and OpenthermGateway

Post by MtenHoorn »

I have the same problem. Can you share the firmware which solved the problem?
hvxl
Senior Member
Senior Member
Posts: 1967
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Celcia20 and OpenthermGateway

Post by hvxl »

MtenHoorn wrote:I have the same problem. Can you share the firmware which solved the problem?
Can you provide some logs so I can make sure it is the same problem? For one user I'm happy to use a hack. But if this is a more common problem, I have to find a better solution.
Schelte
hvxl
Senior Member
Senior Member
Posts: 1967
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Celcia20 and OpenthermGateway

Post by hvxl »

Thanks for the log. You indeed seem to have the same firmware as b@s, which doesn't provide any information about the make and model of the thermostat. So the gateway can't auto-detect that it's dealing with a Celcia 20.

I guess I'll have to add a serial command to allow you to manually configure it. But for now I'll send you the firmware that has this bit hardcoded so you can start controlling your Celcia.
Schelte
salorob
Starting Member
Starting Member
Posts: 1
Joined: Tue Mar 19, 2013 9:50 pm

Re: Celcia20 and OpenthermGateway

Post by salorob »

Hi Schelte,

I've got the same problem. PR=R returns D, on a celcia 20.

Used to work fine with older firmware and the TR=xx command for overriding.

Can you send me this firmware to, or is there another fix already?

Dank,

Robert
hvxl
Senior Member
Senior Member
Posts: 1967
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Celcia20 and OpenthermGateway

Post by hvxl »

Firmware 4.1 now allows you to configure which thermostat model you have via the FT serial command.
Schelte