[FIXED] Possible OTG failure ?

Post by raymonvdm »

For quite some time i was using the OpenThermGateway but after today it seems to be dead. I`m not shure whats happening. And if it is software / hardware / or maybe even interference related.

The gateway was sitting happy next to the boiler on a shelf and today i finished another project "Starcase Lights" and i think it is just coincidence but all of a sudden the boiler started heating. Hmm strange let check HS2 nope seems fine should not be heating. Next check down stairs on the thermostat, hmmm no display.. Back to the attic i disconnected the OTG en connected the thermostat directly to the boiler. Tada problem solved. Placed the OTG back in business and yet again the problem is back. Disconnected the adapter of "Starcase Light" which is giving me a loud noise sound next to my pc speaker so it is pending replacement but this should not be an issue when it is unplugged


I measured X1 and it gave me 21,5 volts when the thermostat is not connected and around 6 volts when the thermostat is connect (but the display is not working) i`m not sure what to do next. The 5 volt on IC1 and IC2 are fine as stated in the trouble shoot link


Serial communication is working

Code: Select all

22:30:07.153668	Command: PR=A
22:30:07.187522	OpenTherm Gateway 3.4

Code: Select all

22:30:48.408234	Command: PR=M
22:30:48.424156	BV
22:31:49.118202	Command: PR=V
22:31:49.134696	3
22:32:04.245730	Command: PR=L
22:32:04.261271	RXOF
Last edited by raymonvdm on Thu Aug 28, 2014 8:24 pm, edited 1 time in total.
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s
raymonvdm
Senior Member
Senior Member
Posts: 1153
Joined: Sun Dec 18, 2011 1:23 am

Re: Possible OTG failure ?

Post by raymonvdm »

I just reconnected the gateway and i`m only receving "Error 03" change of VR=2 till VR=5 did not make a difference (VR=3) is normal. It looks like the gateway setting Gateway or Monitor is also no longer available and the boiler is heating like its mid winter :shock:


NOTE: OTmonitor 3.3 or 4.0 does not make a difference
NOTE2: I also reupgrade the gateway to firmware 3.4 but the issue remains (although the firmware upgrade is successful)
NOTE3: The thermostat display is blank
Last edited by raymonvdm on Mon Aug 25, 2014 11:20 pm, edited 1 time in total.
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s
hvxl
Senior Member
Senior Member
Posts: 1967
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Possible OTG failure ?

Post by hvxl »

So you don't see any messages from the thermostat, just Error 03? Then you could try to disconnect the thermostat. With firmware 4.0.1 the gateway is supposed to start communicating with the boiler on its own. If that works, it narrows down where the problem might be.
Schelte
raymonvdm
Senior Member
Senior Member
Posts: 1153
Joined: Sun Dec 18, 2011 1:23 am

Re: Possible OTG failure ?

Post by raymonvdm »

I will try this tomorrow because the temperature is 25 decrees so its time for bed now (Boiler disconnected :D )
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s
raymonvdm
Senior Member
Senior Member
Posts: 1153
Joined: Sun Dec 18, 2011 1:23 am

Re: Possible OTG failure ?

Post by raymonvdm »

Code: Select all


07:58:53.683830	OpenTherm Gateway 4.0.1
07:58:55.806780	Error 03
07:58:58.253901	Error 03
07:59:00.825526	Error 03
07:59:03.398340	Error 03
07:59:05.836799	Error 03
07:59:08.415601	Error 03
07:59:10.995831	Error 03
07:59:13.567244	Error 02
07:59:13.577540	E55555555
07:59:16.137969	Error 02
07:59:16.149601	E55555555
07:59:18.577549	Error 03
07:59:21.169408	Error 03
07:59:23.737683	Error 02
07:59:23.764439	E55555555
07:59:26.376817	Error 03
07:59:28.889643	Error 03
07:59:31.334687	Error 03

When i i disconnect the thermostat this it the result

Code: Select all

8:44:23.945664	R00110000	Read-Data 	Relative modulation level: 0.00
08:44:24.251448	B40117300	Read-Ack  	Relative modulation level: 115.00
08:44:24.987400	R001B0000	Read-Data 	Outside temperature: 0.00
08:44:25.130329	B601BDD00	Data-Inv  	Outside temperature: -35.00
08:44:26.017116	R801C0000	Read-Data 	Return water temperature: 0.00
08:44:26.271082	B401C3F00	Read-Ack  	Return water temperature: 63.00
08:44:27.073114	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
08:44:27.355484	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
08:44:28.100779	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
08:44:28.421106	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
08:44:29.126623	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
08:44:29.490355	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
08:44:30.163943	R80190000	Read-Data 	Boiler water temperature: 0.00
08:44:30.416488	B40193F00	Read-Ack  	Boiler water temperature: 63.00
08:44:31.207124	R10010A00	Write-Data	Control setpoint: 10.00
08:44:31.357067	BD0010A00	Write-Ack 	Control setpoint: 10.00

Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s
hvxl
Senior Member
Senior Member
Posts: 1967
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Possible OTG failure ?

Post by hvxl »

So this definitely is a problem on the thermostat interface. The gateway seems to be picking up random noise. Especially the E55555555 reports are curious. That's quite a difficult pattern to create. Maybe your work on the staircase lighting has shifted some cables around and moved something close enough to the thermostat cable to cause interference. It doesn't look like a 50Hz interference signal though, there would only be 2 or 3 zero crossings of a 50Hz signal during the 34ms it takes to transmit an opentherm message.

Do you see a chance to connect the thermostat close to the gateway to see if it works that way? That test would tell if the problem is interference or broken hardware on the thermostat interface. Given the very low complexity of the thermostat interface, I don't expect much can go wrong there, unless there has been a big spike on the thermostat lines that blew the PIC input. Another possibility to check the thermostat interface is to run test #4 of the diagnostic firmware.

If the hardware is fine, you have to figure out/eliminate the source of the interference. Perhaps adding some capacitor over the opentherm line or passing the cable through a ferrite bead may improve the situation.
Schelte
raymonvdm
Senior Member
Senior Member
Posts: 1153
Joined: Sun Dec 18, 2011 1:23 am

Re: Possible OTG failure ?

Post by raymonvdm »

The cable is quite straight forward running vertically over the wall, The power for the staircase lights are running over the same wall but horizontally. The power has been shutdown and the issue remains. When connecting the thermostat without the gateway the thermostat seems to be doing fine. The cable used for the thermostat is a normal 2 wire in a house build in 1982 and it is not possible to replace the cable.

This evening i will connect the thermostat to the gateway directly :D


Note: One other thing is that i replaced a tablet from one corner in the room to another corner in the room but that should not be an issue. It is in both case placed 2 meter from the thermostat
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s
raymonvdm
Senior Member
Senior Member
Posts: 1153
Joined: Sun Dec 18, 2011 1:23 am

Re: Possible OTG failure ?

Post by raymonvdm »

I did some more testing and i`m out of ideas.

- Connected the thermostat directly to the boiler = OK
- Connected the thermostat directly to the gateway = Thermostat display does not power up
- Connected the thermostat and boiler to the gateway = Thermostats powers up and setpoint = 25 degrees
- ShortCircuit the cable in the livingroom and measure ohms in the attic 0.0.1 Ohm
- Connect the gateway to the boiler with a new cable and the thermostat in the living room with the old cable no display but thermostat seems to be reporting something
- Reset of boiler no difference
- Boiler and Thermostat connection measure around 6 volt when boiler and thermostat are connected
- After some time Error 03 pops up and after some time goes away again
- All this time the thermostat display is not working
- PowerSupply input measures 230 Volt
- Hot Water is not working

I`m out of options and the Wife is hunting me :cry:

http://files.raqxs.nl/domotica/openther ... 140826.txt
http://files.raqxs.nl/domotica/openther ... n_vast.txt


Update: I also tested with a long new cable with foil (normaly used for PIR installation for alarm systems) and when i reset the gateway the thermostat powers-on. But when i measure the power they all look the same. Due to the placement of the cable i cannot replace it.

Any ideas left ?
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s
hvxl
Senior Member
Senior Member
Posts: 1967
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Possible OTG failure ?

Post by hvxl »

Hot water is not working? The boiler doesn't need the thermostat for hot water. That should always work.

I'm not sure why you are resetting the boiler and replacing the cable there. We have established that that side is working fine. So unless you want more problems I'd leave that part alone.

It's not entirely clear to me in what configuration you captured the log, but the fact that the thermostat keeps sending the same message is suspicious. That probably means the thermostat is not receiving/understanding the opentherm transmissions from the gateway. Please measure the current on the X1 interface as described on the troubleshooting page. There may be a problem with Q2/Q3.

The thermostat may not show anything on its display until it has received some transmissions. I know for example the Honeywell Round Modulation acts like that.
Schelte
raymonvdm
Senior Member
Senior Member
Posts: 1153
Joined: Sun Dec 18, 2011 1:23 am

Re: Possible OTG failure ?

Post by raymonvdm »

Honeywell Round Modulation it is indeed :shock:

I placed a 120 Ohm resistor on X1 and measured 0.72 volt so this look ok

I also connected the thermostat to X1 using a cable of 50 cm and this is the result

Code: Select all


		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
22:44:09.969427	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
22:44:10.959154	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
22:44:11.960569	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
22:44:12.963826	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
22:44:13.941809	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:14.001455	R80190000	Read-Data 	Boiler water temperature: 0.00
22:44:14.996877	R80190000	Read-Data 	Boiler water temperature: 0.00
22:44:15.150235	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:16.029633	R10010A00	Write-Data	Control setpoint: 10.00
22:44:16.355014	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:17.043084	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
22:44:17.564672	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:18.083435	R00110000	Read-Data 	Relative modulation level: 0.00
22:44:18.769452	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:19.117698	R001B0000	Read-Data 	Outside temperature: 0.00
22:44:19.983944	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:20.138481	R801C0000	Read-Data 	Return water temperature: 0.00
22:44:21.128430	R801C0000	Read-Data 	Return water temperature: 0.00
22:44:21.181108	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:22.166782	R900E6400	Write-Data	Maximum relative modulation level: 100.00
22:44:22.391188	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:23.195753	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
22:44:23.600446	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:24.218767	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
22:44:24.809358	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:25.250163	R80190000	Read-Data 	Boiler water temperature: 0.00
22:44:26.017287	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:26.273241	R10010A00	Write-Data	Control setpoint: 10.00
22:44:27.225664	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:27.301821	R80380000	Read-Data 	DHW setpoint: 0.00
22:44:28.308834	R80380000	Read-Data 	DHW setpoint: 0.00
22:44:28.433838	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:29.324517	R00390000	Read-Data 	Max CH water setpoint: 0.00
22:44:29.641914	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:30.348593	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
22:44:30.841795	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:31.376733	R00120000	Read-Data 	CH water pressure: 0.00
22:44:32.057825	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:32.413795	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
22:44:33.264169	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:33.435214	R80190000	Read-Data 	Boiler water temperature: 0.00
22:44:34.436997	R80190000	Read-Data 	Boiler water temperature: 0.00
22:44:34.477908	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:35.462574	R10010A00	Write-Data	Control setpoint: 10.00
22:44:35.680433	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:36.494689	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
22:44:36.885572	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:37.512040	R00110000	Read-Data 	Relative modulation level: 0.00
22:44:37.939718	Error 03
22:44:38.078393	Error 03
22:44:38.539454	R00110000	Read-Data 	Relative modulation level: 0.00
22:44:39.531782	R00110000	Read-Data 	Relative modulation level: 0.00
22:44:40.527994	R00110000	Read-Data 	Relative modulation level: 0.00
22:44:41.523536	R00110000	Read-Data 	Relative modulation level: 0.00
22:44:42.510669	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:42.549937	R001B0000	Read-Data 	Outside temperature: 0.00
22:44:43.552179	R001B0000	Read-Data 	Outside temperature: 0.00
22:44:43.716202	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:44.572030	R801C0000	Read-Data 	Return water temperature: 0.00
22:44:44.921490	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:45.601522	R900E6400	Write-Data	Maximum relative modulation level: 100.00
22:44:46.131340	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:46.632105	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
22:44:47.343605	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:47.655361	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
22:44:48.542429	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:48.689904	R80190000	Read-Data 	Boiler water temperature: 0.00
22:44:49.682305	R80190000	Read-Data 	Boiler water temperature: 0.00
22:44:49.754620	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:50.728600	R10010A00	Write-Data	Control setpoint: 10.00
22:44:50.962673	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:51.739023	R80380000	Read-Data 	DHW setpoint: 0.00
22:44:52.166817	T80190000	Read-Data 	Boiler water temperature: 0.00
22:44:52.761239	R00390000	Read-Data 	Max CH water setpoint: 0.00

Note: No boiler connected

I also connected my old thermostat (Honeywell BasicStat Modulation) and this i the result

Code: Select all


22:49:59.042402	R80190000	Read-Data 	Boiler water temperature: 0.00
22:50:00.048771	R80190000	Read-Data 	Boiler water temperature: 0.00
22:50:00.466354	Error 03
22:50:01.049364	R80190000	Read-Data 	Boiler water temperature: 0.00
22:50:01.842166	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:02.122262	R10010A00	Write-Data	Control setpoint: 10.00
22:50:02.839245	Error 03
22:50:03.122184	R10010A00	Write-Data	Control setpoint: 10.00
22:50:03.830504	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:04.153270	R80380000	Read-Data 	DHW setpoint: 0.00
22:50:04.853009	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:05.186186	R00390000	Read-Data 	Max CH water setpoint: 0.00
22:50:05.843613	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:06.229491	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
22:50:06.862399	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:07.252204	R00120000	Read-Data 	CH water pressure: 0.00
22:50:07.848687	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:08.288161	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
22:50:08.840104	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:09.322576	R80190000	Read-Data 	Boiler water temperature: 0.00
22:50:09.527847	Error 03
22:50:10.357809	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:10.402083	R10010A00	Write-Data	Control setpoint: 10.00
22:50:11.352544	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:11.414169	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
22:50:12.341536	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:12.436313	R00110000	Read-Data 	Relative modulation level: 0.00
22:50:13.365385	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:13.469855	R001B0000	Read-Data 	Outside temperature: 0.00
22:50:14.345157	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:14.514964	R801C0000	Read-Data 	Return water temperature: 0.00
22:50:15.370627	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:15.537543	R900E6400	Write-Data	Maximum relative modulation level: 100.00
22:50:16.352954	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:16.582415	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
22:50:17.342022	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:17.621406	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
22:50:18.357279	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:18.656372	R80190000	Read-Data 	Boiler water temperature: 0.00
22:50:19.352651	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:19.690938	R10010A00	Write-Data	Control setpoint: 10.00
22:50:20.363388	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:20.721919	R80380000	Read-Data 	DHW setpoint: 0.00
22:50:21.354738	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:21.761759	R00390000	Read-Data 	Max CH water setpoint: 0.00
22:50:22.356104	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:22.797251	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
22:50:23.370654	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:23.821756	R00120000	Read-Data 	CH water pressure: 0.00
22:50:24.375946	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:24.867481	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
22:50:25.356816	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:25.903219	R80190000	Read-Data 	Boiler water temperature: 0.00
22:50:26.378961	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:26.941193	R10010A00	Write-Data	Control setpoint: 10.00
22:50:27.380445	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)
22:50:27.968456	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
22:50:28.362237	T90020002	Write-Data	Master configuration: 00000000 2
		   - Smart power: not supported (0)

Both gave an Error 03 and the strange thing is that in the beginning the log is still filled up with the following release even though the thermostat is no longer connected

Code: Select all

22:49:55.048012	R80190000	Read-Data 	Boiler water temperature: 0.00
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s
hvxl
Senior Member
Senior Member
Posts: 1967
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Possible OTG failure ?

Post by hvxl »

I can't follow the reasoning behind your debugging. If no boiler is connected, there will not be any messages from the gateway to the thermostat, which is the most likely trouble spot in my opinion. So your tests are not really producing very useful data points.

The T messages are thermostat -> gateway, the R messages are gateway -> boiler (even if no boiler is connected, the gateway tries to transmit those).

It is not strange that you see R messages when no thermostat is connected. The gateway generates them per design. However, it is strange that the gateway is generating its own R messages while it is receiving T messages. It's like it failed to detect that a thermostat is connected. You should see "Thermostat connected" and "Thermostat disconnected" messages when you attach or detach the thermostat.

It still seems to me like there is a problem with the thermostat interface of the gateway. Please go through all troubleshooting checks for that interface. If those checks don't provide a clue, load the diagnostic firmware and perform the relevant diagnostic tests.
Schelte
raymonvdm
Senior Member
Senior Member
Posts: 1153
Joined: Sun Dec 18, 2011 1:23 am

Re: Possible OTG failure ?

Post by raymonvdm »

Another Day in Paradise

Today i placed the gateway in the office so i can trouble shoot some more


- Connected thermostat and software says thermostat connectd / Disconnected thermostat / Connected / Disconnect and after several times Error 03
- Disconnected Thermostat
- Connect boiler on the boiler connection and Error03 Error03

Code: Select all

19:34:48.001668	Error 03
19:34:48.652178	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
19:34:48.859475	Error 03
19:34:49.704183	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
19:34:50.001222	Error 03
19:34:50.730622	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
19:34:50.879751	Error 03
19:34:51.752268	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocke
Gateway does not respond on commands like GW=0 or GW=1 or GW=R after power cycle the gateway is responding again. When i connect the boiler again the Error 03 returns but disappears when i switch the gateway to Monitor Mode

Code: Select all


19:42:11.605928	B40117300	Read-Ack  	Relative modulation level: 115.00
19:42:12.387321	T80190000	Read-Data 	Boiler water temperature: 0.00
19:42:12.481186	BC0193E00	Read-Ack  	Boiler water temperature: 62.00
19:42:13.406177	T10010A00	Write-Data	Control setpoint: 10.00
19:42:13.468786	BD0010A00	Write-Ack 	Control setpoint: 10.00
19:42:14.435434	T00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
19:42:14.572371	Command: GW=1
19:42:14.588058	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
19:42:14.721639	GW: 1
19:42:15.455180	T00390000	Read-Data 	Max CH water setpoint: 0.00
19:42:15.564849	Error 03
19:42:16.662780	T00390000	Read-Data 	Max CH water setpoint: 0.00
19:42:16.772439	Error 03
19:42:17.869060	T00390000	Read-Data 	Max CH water setpoint: 0.00
19:42:17.910015	Command: GW=0
19:42:17.924072	GW: P
19:42:17.938283	Command: PR=M
19:42:17.962791	PR: M=G
19:42:17.976238	Error 03
19:42:19.081136	T00390000	Read-Data 	Max CH water setpoint: 0.00
19:42:19.135792	BF0390000	Unk-DataId	Max CH water setpoint: 0.00
19:42:20.106159	T80190000	Read-Data 	Boiler water temperature: 0.00
19:42:20.262365	BC0193E00	Read-Ack  	Boiler water temperature: 62.00
19:42:21.123467	T10010A00	Write-Data	Control setpoint: 10.00
19:42:21.186116	BD0010A00	Write-Ack 	Control setpoint: 10.00
19:42:22.156509	T00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
19:42:22.344291	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
19:42:23.183788	T00090000	Read-Data 	Remote override room setpoint: 0.00
19:42:24.398074	T00090000	Read-Data 	Remote override room setpoint: 0.00
19:42:24.453834	BF0090000	Unk-DataId	Remote override room setpoint: 0.00
19:42:25.433849	T80190000	Read-Data 	Boiler water temperature: 0.00
19:42:25.746441	BC0193E00	Read-Ack  	Boiler water temperature: 62.00

I processed the complete troubleshooting guide and only have on thing

If you connect pin 3 of the IC1 socket to ground (e.g. pin 5), the current between the two terminals of X1 should be between 17mA and 23mA (1.7V and 2.3V across a 100O resistor). Deviations can be corrected by changing the value of R12. You increase the current by lowering the resistor value. Don't start manipulating R12 until the correct value of R11 has been determined (see above) because R11 influences both the low and high current values while R12 only affects the high current value.

Outcome = 2.35Volt using 120 Ohm


http://files.raqxs.nl/domotica/openther ... ateway.odt
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s
raymonvdm
Senior Member
Senior Member
Posts: 1153
Joined: Sun Dec 18, 2011 1:23 am

Re: [FIXED] Possible OTG failure ?

Post by raymonvdm »

There was one adapter which created so much disturbance for my pc speakers and wifi netwerk and also seems to have messed up the gateway. After removing the adapter (smashed in with a hammer just to release the stress) the wifi and pc speakers where fine.

The gateway issues remained until u downgrade it back to Firmware 3.4 now all issues are solved expect one minor issue with the "domestic hotwater enable" my thermostat thinks it is disabled and also seems to disable it, but this is not possible for the thermostat since it is a T87M1003. When i send a HW=1 the hot water is working again but the thermostat still thinks hot water is turned off

I tried to place my old thermostat from years ago (which has the ability to enable / disable DHW when setting temp lower than 15.5 Degrees but i cannot trick the new thermostat and gateway to enable DHW using the old one. It looks like this setting is somewhere stored in the thermostat or gateway based on the OpenTherm adress of the thermostat.
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s
hvxl
Senior Member
Senior Member
Posts: 1967
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Possible OTG failure ?

Post by hvxl »

raymonvdm wrote:I processed the complete troubleshooting guide and only have on thing

If you connect pin 3 of the IC1 socket to ground (e.g. pin 5), the current between the two terminals of X1 should be between 17mA and 23mA (1.7V and 2.3V across a 100O resistor). Deviations can be corrected by changing the value of R12. You increase the current by lowering the resistor value. Don't start manipulating R12 until the correct value of R11 has been determined (see above) because R11 influences both the low and high current values while R12 only affects the high current value.

Outcome = 2.35Volt using 120 Ohm
That's 19.6mA, which is perfect. (The way you copy/pasted it it looks like a 1K resistor, but the web site says 100 Ohm using a Greek letter omega: 100Ω)
raymonvdm wrote:The gateway issues remained until u downgrade it back to Firmware 3.4 now all issues are solved expect one minor issue with the "domestic hotwater enable" my thermostat thinks it is disabled and also seems to disable it, but this is not possible for the thermostat since it is a T87M1003. When i send a HW=1 the hot water is working again but the thermostat still thinks hot water is turned off
The DHW enable bit (and therefor the HW command) only controls if the boiler should keep some amount of water pre-heated. Most boilers have a setting that can be set to eco, comfort, or auto. Only with the auto setting the thermostat controls if the water should be kept warm. But in any case the boiler should start heating when you open the hot water tap. I like to save energy, so mine is always off.
raymonvdm wrote:I tried to place my old thermostat from years ago (which has the ability to enable / disable DHW when setting temp lower than 15.5 Degrees but i cannot trick the new thermostat and gateway to enable DHW using the old one. It looks like this setting is somewhere stored in the thermostat or gateway based on the OpenTherm adress of the thermostat.
The gateway doesn't store this setting. Opentherm uses a point-to-point connection. There is no such thing as an "OpenTherm address". Possibly the T87M1003 and the T87M1011 share (some of) the same hardware and the interference managed to toggle the hot water button, which is just a phantom button on the T87M1003. Exposing the thermostat to interference again may toggle it back. If only you hadn't smashed that power supply ... :twisted:
Schelte
raymonvdm
Senior Member
Senior Member
Posts: 1153
Joined: Sun Dec 18, 2011 1:23 am

Re: [FIXED] Possible OTG failure ?

Post by raymonvdm »

I`m in the process of buying a T87M1011 :twisted:

And its too bad but connecting the empty terminals does not fix the issue
Last edited by raymonvdm on Thu Aug 28, 2014 10:19 pm, edited 1 time in total.
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s