OTGW and on/off thermostat

This Forum is about the Opentherm gateway (OTGW) from Schelte

Moderator: hvxl

hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: OTGW and on/off thermostat

Post by hvxl »

Thanks, that's very helpful. I think I have an idea what might be going on. Now to fix it.

The gateway doesn't have a clock, so it doesn't know the concept of midnight. Possibly the gateway went through a reset at some point during the night for some reason.
Schelte
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: OTGW and on/off thermostat

Post by hvxl »

I sent you an experimental version of de firmware which hopefully fixes the problem. Please let me know either way.
Schelte
ABSolute
Starting Member
Starting Member
Posts: 4
Joined: Tue Sep 21, 2010 1:43 am

Re: OTGW and on/off thermostat

Post by ABSolute »

Thank you so much!
This seems to have fixed the problem.
I'll keep an eye on the log files for the coming few days.
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: OTGW and on/off thermostat

Post by hvxl »

Thank you for reporting. This probably also fixes the trouble I've seen with the gateway not always detecting when an opentherm thermostat was connected again. But whenever I wanted to investigate that, I could never reproduce it.
Schelte
breem
Starting Member
Starting Member
Posts: 8
Joined: Thu Dec 25, 2014 10:22 pm

Re: OTGW and on/off thermostat

Post by breem »

Hi,

I did not perform all the tests mentioned in this post yet. But my gateway does not seem to respond to signals from my on/off thermostat. Can this be the same problem? What do I need to test if this is the same problem?

Mark
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: OTGW and on/off thermostat

Post by hvxl »

The easiest test is to execute the serial command DP=5E. If you then see values other than 5E=00 or 5E=10, you probably have the same problem.
Schelte
breem
Starting Member
Starting Member
Posts: 8
Joined: Thu Dec 25, 2014 10:22 pm

Re: OTGW and on/off thermostat

Post by breem »

Hi,

I receive DP=20 or DP=30 messages when I send the DP=5E command. Would the new firmware solve this issue? I'll be glad to test it. If you need any results from the tests, please let me know what to monitor.
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: OTGW and on/off thermostat

Post by hvxl »

Yes, that's the same problem. Looks like I should release the new firmware sooner rather than later.

Edit: Firmware 4.2 is now available.
Schelte
breem
Starting Member
Starting Member
Posts: 8
Joined: Thu Dec 25, 2014 10:22 pm

Re: OTGW and on/off thermostat

Post by breem »

I installed the 4.2 firmware and the gateway responds correctly to the thermostat commands now. Thanks for the quick repair and release!
Post Reply