Re: OTGW with MQTT and Node Red.

Post by mike7 »

According to timestamp returnwatertemperature is very old (retained ?). I suggest to install MQTT Explorer.
Remove from MQTT Explorer all topics related to otmonitor and restart it. Then check with MQTT Explorer structure of topics.
mwtheplumber
Starting Member
Starting Member
Posts: 24
Joined: Wed Feb 13, 2019 9:10 am

Re: OTGW with MQTT and Node Red.

Post by mwtheplumber »

On the MQTT explorer I can see that boilerwatertemperature is being transmitted but doesn't change. If I use the Windows version of OTGW it all works fine so I assume it is a bug in the Raspberry Pi version.
mike7
Member
Member
Posts: 102
Joined: Mon Dec 02, 2013 8:45 am

Re: OTGW with MQTT and Node Red.

Post by mike7 »

There are no such bug in armf or aarch64 version of otmotitor, all versions use the same tcl code. Only runtime is different.
Please compare you configuration for windows and raspi.

boilerwatertemperature shouldn't be retained, please check. Try to remove the whole tree of event/# topic from MQTT Explorer.
mwtheplumber
Starting Member
Starting Member
Posts: 24
Joined: Wed Feb 13, 2019 9:10 am

Re: OTGW with MQTT and Node Red.

Post by mwtheplumber »

Thanks Mike, I will have a look.
mwtheplumber
Starting Member
Starting Member
Posts: 24
Joined: Wed Feb 13, 2019 9:10 am

Re: OTGW with MQTT and Node Red.

Post by mwtheplumber »

On further investigation of this I can see that with the windows desktop version everything works fine. On the RaspberryPi version, the boiler water temperature is transmitted once via MQTT, then never transmitted again. I have double checked the MQTT settings in both instances and they are identical.
mike7
Member
Member
Posts: 102
Joined: Mon Dec 02, 2013 8:45 am

Re: OTGW with MQTT and Node Red.

Post by mike7 »

I think the value of boilerwatertemperature is retained in your case, I have no idea why. Which mqtt broker are in use?
mwtheplumber
Starting Member
Starting Member
Posts: 24
Joined: Wed Feb 13, 2019 9:10 am

Re: OTGW with MQTT and Node Red.

Post by mwtheplumber »

I have tried two different MQTT brokers, Mosquitto and HiveMQ. The results are the same.
mike7
Member
Member
Posts: 102
Joined: Mon Dec 02, 2013 8:45 am

Re: OTGW with MQTT and Node Red.

Post by mike7 »

Please describe how do you run otmonitor on rpi, command line, content of configuration file.
mwtheplumber
Starting Member
Starting Member
Posts: 24
Joined: Wed Feb 13, 2019 9:10 am

Re: OTGW with MQTT and Node Red.

Post by mwtheplumber »

I followed the instructions at https://otgw.tclcode.com/raspi.html to run headless set up. OTmonitor starts automatically on reboot.
mike7
Member
Member
Posts: 102
Joined: Mon Dec 02, 2013 8:45 am

Re: OTGW with MQTT and Node Red.

Post by mike7 »

OK, lets continue without details of configuration...
Assume you are using mosquitto ...

please run mosquitto_sub on the same rpi on which you are running otmonitor:

mosquitto_sub -h <broker ip> -p <broker port> -u <username> --pw <password> -t events/#

<broker ip> <broker port> must be the same as for otmonitor (that is the reason why I asked for a content of config file)

Log from the broker also will be usefull..
mwtheplumber
Starting Member
Starting Member
Posts: 24
Joined: Wed Feb 13, 2019 9:10 am

Re: OTGW with MQTT and Node Red.

Post by mwtheplumber »

Does this help?
Sorry I wasn't sure what config file you were referring to

{"name":"on","type":"boolean","value":true,"timestamp":1674313021303}
{"name":"on","type":"boolean","value":true,"timestamp":1674158019990}
{"name":"on","type":"boolean","value":false,"timestamp":1674158020042}
{"name":"on","type":"boolean","value":true,"timestamp":1674311170378}
{"name":"on","type":"boolean","value":false,"timestamp":1674311170382}
{"name":"on","type":"boolean","value":false,"timestamp":1674313111518}
{"name":"on","type":"boolean","value":false,"timestamp":1674158020046}
{"name":"on","type":"boolean","value":false,"timestamp":1674158020047}
{"name":"on","type":"boolean","value":false,"timestamp":1674158020048}
{"name":"on","type":"boolean","value":false,"timestamp":1674158020048}
{"name":"temp","type":"float","value":63.00,"timestamp":1674313018008}
{"name":"temp","type":"float","value":48.00,"timestamp":1674168123454}
{"name":"temp","type":"float","value":63.00,"timestamp":1674168123919}
{"name":"level","type":"float","value":0.00,"timestamp":1674312952639}
{"name":"temp","type":"float","value":20.00,"timestamp":1674168127071}
{"name":"temp","type":"float","value":20.00,"timestamp":1674232052067}
{"name":"level","type":"float","value":0.00,"timestamp":1674310480454}
{"name":"temp","type":"float","value":0.00,"timestamp":1674168130949}
{"name":"temp","type":"float","value":40.44,"timestamp":1674313502576}
{"name":"temp","type":"float","value":5.03,"timestamp":1674313201802}
{"name":"rate","type":"float","value":0.00,"timestamp":1674310482648}
{"name":"bar","type":"float","value":1.03,"timestamp":1674313443735}
{"name":"count","type":"unsigned","value":18096,"timestamp":1674313132561}
{"name":"count","type":"unsigned","value":6511,"timestamp":1674308480854}
{"name":"count","type":"unsigned","value":287,"timestamp":1674232592147}
{"name":"mode","type":"string","value":"low","timestamp":1674214576168}
{"name":"temp","type":"float","value":0.00,"timestamp":1673634130333}
{"name":"temp","type":"float","value":64.83,"timestamp":1674168128851}
{"name":"temp","type":"float","value":40.45,"timestamp":1674313564118}
{"name":"level","type":"float","value":100.00,"timestamp":1674313596976}
{"name":"temp","type":"float","value":40.44,"timestamp":1674313623634}
{"name":"bar","type":"float","value":1.02,"timestamp":1674313625232}
{"name":"temp","type":"float","value":40.48,"timestamp":1674313684067}
{"name":"bar","type":"float","value":1.03,"timestamp":1674313685663}
{"name":"on","type":"boolean","value":true,"timestamp":1674313712634}
{"name":"count","type":"unsigned","value":18097,"timestamp":1674313740679}
{"name":"temp","type":"float","value":40.51,"timestamp":1674313743996}
{"name":"temp","type":"float","value":5.12,"timestamp":1674313744500}
{"name":"bar","type":"float","value":1.02,"timestamp":1674313745596}
{"name":"temp","type":"float","value":40.53,"timestamp":1674313804431}
{"name":"temp","type":"float","value":5.15,"timestamp":1674313805031}
{"name":"bar","type":"float","value":1.03,"timestamp":1674313806032}
{"name":"on","type":"boolean","value":false,"timestamp":1674313808735}
{"name":"level","type":"float","value":0.00,"timestamp":1674313817283}
{"name":"on","type":"boolean","value":false,"timestamp":1674313817867}
{"name":"temp","type":"float","value":10.00,"timestamp":1674313819440}
mike7
Member
Member
Posts: 102
Joined: Mon Dec 02, 2013 8:45 am

Re: OTGW with MQTT and Node Red.

Post by mike7 »

Lets format the output from mosquitto_sub with "-F '%r %t : %p'"

So, run the following command:
mosquitto_sub -h <broker ip> -p <broker port> -u <username> --pw <password> -t events/# -F '%r %t : %p'

Output should look like this one:

Code: Select all

1 events/central_heating/otmonitor/chenable : {"name":"on","type":"boolean","value":true,"timestamp":1674213459326}
1 events/central_heating/otmonitor/dhwenable : {"name":"on","type":"boolean","value":false,"timestamp":1674172643644}
1 events/central_heating/otmonitor/fault : {"name":"on","type":"boolean","value":false,"timestamp":1674172659869}
1 events/central_heating/otmonitor/centralheating : {"name":"on","type":"boolean","value":true,"timestamp":1674314321069}
1 events/central_heating/otmonitor/hotwater : {"name":"on","type":"boolean","value":false,"timestamp":1674172645527}
1 events/central_heating/otmonitor/flame : {"name":"on","type":"boolean","value":true,"timestamp":1674314419495}
1 events/central_heating/otmonitor/cooling : {"name":"on","type":"boolean","value":false,"timestamp":1673208884737}
1 events/central_heating/otmonitor/centralheating2 : {"name":"on","type":"boolean","value":false,"timestamp":1673208884738}
1 events/central_heating/otmonitor/diagnostic : {"name":"on","type":"boolean","value":false,"timestamp":1673208884739}
1 events/central_heating/otmonitor/electricity : {"name":"on","type":"boolean","value":false,"timestamp":1674172645528}
1 events/central_heating/otmonitor/controlsetpoint : {"name":"temp","type":"float","value":36.00,"timestamp":1674316897886}
1 events/central_heating/otmonitor/modulation : {"name":"level","type":"float","value":19.00,"timestamp":1674316900224}
1 events/central_heating/otmonitor/returnwatertemperature : {"name":"temp","type":"float","value":30.40,"timestamp":1674316888101}
1 events/central_heating/otmonitor/setpoint : {"name":"temp","type":"float","value":16.00,"timestamp":1673208905652}
1 events/central_heating/otmonitor/roomtemperature : {"name":"temp","type":"float","value":15.70,"timestamp":1674316846807}
1 events/central_heating/otmonitor/chwaterdeltat : {"name":"temp","type":"float","value":6.49,"timestamp":1674316897076}
1 events/central_heating/otmonitor/boilerwatertemperature : {"name":"temp","type":"float","value":36.89,"timestamp":1674316897078}
1 events/central_heating/otmonitor/dhwtemperature : {"name":"temp","type":"float","value":21.00,"timestamp":1674316108812}
1 events/central_heating/otmonitor/outsidetemperature : {"name":"temp","type":"float","value":-3.00,"timestamp":1674314111441}
1 events/central_heating/otmonitor/exhausttemperature : {"name":"temp","type":"float","value":35.00,"timestamp":1674316895278}
1 events/central_heating/otmonitor/dhwsetpoint : {"name":"temp","type":"float","value":35.00,"timestamp":1674213464269}
1 events/central_heating/otmonitor/chsetpoint : {"name":"temp","type":"float","value":80.00,"timestamp":1673208887792}
1 events/central_heating/otmonitor/chwaterpresure : {"name":"bar","type":"float","value":1.30,"timestamp":1674315250977}
1 events/central_heating/otmonitor/remoteoverrideroomsetpoint : {"name":"temp","type":"float","value":0.00,"timestamp":1673208893221}
1 events/central_heating/otmonitor/maxmodulation : {"name":"level","type":"float","value":100.00,"timestamp":1673208894912}
1 events/central_heating/otmonitor/dhwflowrate : {"name":"rate","type":"float","value":0.00,"timestamp":1673252435865}
1 events/central_heating/otmonitor/chburnerstarts : {"name":"count","type":"unsigned","value":0,"timestamp":1673252435869}
1 events/central_heating/otmonitor/chpumpstarts : {"name":"count","type":"unsigned","value":0,"timestamp":1673252435871}
1 events/central_heating/otmonitor/dhwpumpstarts : {"name":"count","type":"unsigned","value":0,"timestamp":1673252435872}
1 events/central_heating/otmonitor/dhwburnerstarts : {"name":"count","type":"unsigned","value":0,"timestamp":1673252435874}
1 events/central_heating/otmonitor/chburnerhours : {"name":"count","type":"unsigned","value":0,"timestamp":1673252435875}
1 events/central_heating/otmonitor/chpumphours : {"name":"count","type":"unsigned","value":0,"timestamp":1673252435876}
1 events/central_heating/otmonitor/dhwpumphours : {"name":"count","type":"unsigned","value":0,"timestamp":1673252435878}
1 events/central_heating/otmonitor/dhwburnerhours : {"name":"count","type":"unsigned","value":0,"timestamp":1673252435879}
1 events/central_heating/otmonitor/thermostat : {"name":"connected","type":"boolean","value":true,"timestamp":1673070408443}
0 events/central_heating/otmonitor/modulation : {"name":"level","type":"float","value":17.00,"timestamp":1674316903829}
0 events/central_heating/otmonitor/error : {"name":"code","type":"byte","value":3,"timestamp":1674316904665}
0 events/central_heating/otmonitor/chwaterdeltat : {"name":"temp","type":"float","value":6.39,"timestamp":1674316908961}
0 events/central_heating/otmonitor/returnwatertemperature : {"name":"temp","type":"float","value":30.50,"timestamp":1674316908962}
0 events/central_heating/otmonitor/roomtemperature : {"name":"temp","type":"float","value":15.80,"timestamp":1674316912462}
0 events/central_heating/otmonitor/chwaterdeltat : {"name":"temp","type":"float","value":6.20,"timestamp":1674316914383}
0 events/central_heating/otmonitor/boilerwatertemperature : {"name":"temp","type":"float","value":36.70,"timestamp":1674316914384}
0 events/central_heating/otmonitor/dhwtemperature : {"name":"temp","type":"float","value":20.89,"timestamp":1674316916171}
0 events/central_heating/otmonitor/chwaterdeltat : {"name":"temp","type":"float","value":6.10,"timestamp":1674316921560}
0 events/central_heating/otmonitor/boilerwatertemperature : {"name":"temp","type":"float","value":36.60,"timestamp":1674316921561}
0 events/central_heating/otmonitor/chwaterdeltat : {"name":"temp","type":"float","value":5.90,"timestamp":1674316930476}
0 events/central_heating/otmonitor/returnwatertemperature : {"name":"temp","type":"float","value":30.70,"timestamp":1674316930477}
Where first 1 or 0 indicates retain flag. As you can see in my log, first boilerwatertemperature is retained, but the second is not.
You can try with -t events/central_heating/otmonitor/boilerwatertemperature and should receive something like:

Code: Select all

1 events/central_heating/otmonitor/boilerwatertemperature : {"name":"temp","type":"float","value":36.70,"timestamp":1674317205461}
0 events/central_heating/otmonitor/boilerwatertemperature : {"name":"temp","type":"float","value":36.60,"timestamp":1674317309360}
0 events/central_heating/otmonitor/boilerwatertemperature : {"name":"temp","type":"float","value":36.50,"timestamp":1674317431090}
0 events/central_heating/otmonitor/boilerwatertemperature : {"name":"temp","type":"float","value":36.60,"timestamp":1674317495607}
PS I asked for the content of .otmonitorrc file which is default configuration file for otmonitor
mwtheplumber
Starting Member
Starting Member
Posts: 24
Joined: Wed Feb 13, 2019 9:10 am

Re: OTGW with MQTT and Node Red.

Post by mwtheplumber »

1 events/central_heating/otmonitor/chenable : {"name":"on","type":"boolean","value":true,"timestamp":1674322108983}
1 events/central_heating/otmonitor/dhwenable : {"name":"on","type":"boolean","value":true,"timestamp":1674158019990}
1 events/central_heating/otmonitor/fault : {"name":"on","type":"boolean","value":false,"timestamp":1674158020042}
1 events/central_heating/otmonitor/centralheating : {"name":"on","type":"boolean","value":true,"timestamp":1674311170378}
1 events/central_heating/otmonitor/hotwater : {"name":"on","type":"boolean","value":false,"timestamp":1674311170382}
1 events/central_heating/otmonitor/flame : {"name":"on","type":"boolean","value":true,"timestamp":1674322818647}
1 events/central_heating/otmonitor/cooling : {"name":"on","type":"boolean","value":false,"timestamp":1674158020046}
1 events/central_heating/otmonitor/centralheating2 : {"name":"on","type":"boolean","value":false,"timestamp":1674158020047}
1 events/central_heating/otmonitor/diagnostic : {"name":"on","type":"boolean","value":false,"timestamp":1674158020048}
1 events/central_heating/otmonitor/electricity : {"name":"on","type":"boolean","value":false,"timestamp":1674158020048}
1 events/central_heating/otmonitor/controlsetpoint : {"name":"temp","type":"float","value":63.00,"timestamp":1674322110554}
1 events/central_heating/otmonitor/dhwsetpoint : {"name":"temp","type":"float","value":48.00,"timestamp":1674168123454}
1 events/central_heating/otmonitor/chsetpoint : {"name":"temp","type":"float","value":63.00,"timestamp":1674168123919}
1 events/central_heating/otmonitor/maxmodulation : {"name":"level","type":"float","value":100.00,"timestamp":1674322686648}
1 events/central_heating/otmonitor/roomtemperature : {"name":"temp","type":"float","value":20.00,"timestamp":1674168127071}
1 events/central_heating/otmonitor/setpoint : {"name":"temp","type":"float","value":20.00,"timestamp":1674232052067}
1 events/central_heating/otmonitor/modulation : {"name":"level","type":"float","value":0.00,"timestamp":1674310480454}
1 events/central_heating/otmonitor/remoteoverrideroomsetpoint : {"name":"temp","type":"float","value":0.00,"timestamp":1674168130949}
1 events/central_heating/otmonitor/dhwtemperature : {"name":"temp","type":"float","value":36.48,"timestamp":1674322867793}
1 events/central_heating/otmonitor/outsidetemperature : {"name":"temp","type":"float","value":1.31,"timestamp":1674322868393}
1 events/central_heating/otmonitor/dhwflowrate : {"name":"rate","type":"float","value":0.00,"timestamp":1674310482648}
1 events/central_heating/otmonitor/chwaterpresure : {"name":"bar","type":"float","value":1.02,"timestamp":1674322869396}
1 events/central_heating/otmonitor/chburnerstarts : {"name":"count","type":"unsigned","value":18108,"timestamp":1674322135475}
1 events/central_heating/otmonitor/chburnerhours : {"name":"count","type":"unsigned","value":6513,"timestamp":1674321893545}
1 events/central_heating/otmonitor/dhwburnerhours : {"name":"count","type":"unsigned","value":287,"timestamp":1674232592147}
1 events/central_heating/otmonitor/powermode : {"name":"mode","type":"string","value":"low","timestamp":1674214576168}
1 events/central_heating/otmonitor/controlsetpoint2 : {"name":"temp","type":"float","value":0.00,"timestamp":1673634130333}
1 events/central_heating/otmonitor/boilerwatertemperature : {"name":"temp","type":"float","value":64.83,"timestamp":1674168128851}
Where do I find the .otmonitorrc file ?
mike7
Member
Member
Posts: 102
Joined: Mon Dec 02, 2013 8:45 am

Re: OTGW with MQTT and Node Red.

Post by mike7 »

There are no any new messages from otmonitor, you should receive output with 0 at the beginning of the line.
From your log:
all values are very old (from yesterday) and all of them are retained.

I'm using another way to run otmonitor, may be in your case .otmonitorrc will be in /root or /home/pi (I'm not sure).
Lets try from GUI...
The dataflow is:
otmonitor -> MQTT -> mosquitto_sub

- Run otmonitor on rpi
- Connect from browser and check messages in "Messages" tab (you should see the continues stream of messages)
- Open "Configure" window and check MQTT settings
- Post a screenshot with settings
- run mosquitto_sub on rpi with the connection to the same broker
- Post executed command
- Wait for output started with 0

What we are checking? Otmonitor and mosquitto_sub should be connected to the same broker.
If you will receive no messages started with 0 - check broker log for client connection. You should find connections from both otmonitor and mosquitto_sub.
mwtheplumber
Starting Member
Starting Member
Posts: 24
Joined: Wed Feb 13, 2019 9:10 am

Re: OTGW with MQTT and Node Red.

Post by mwtheplumber »

2023-01-22 3.jpg
2023-01-22 3.jpg (112.95 KiB) Viewed 6822 times
This screen shot shows the MQTT set up for Windows version of Otmonitor (right) and RPI (left). From the mosquitto_sub, I can see that boilerwatertemperature is transmitted to MQTT as expected when running windows version, but when running RPI version although I can see the boilerwatertemperature change on the messages in otmonitor, it never gets transmitted after the initial transmission to MQTT.

This is output on windows version.

0 events/central_heating/otmonitor/boilerwatertemperature :{"name":"temp","type":"float","value":48.85,"timestamp":1674383826916}
0 events/central_heating/otmonitor/boilerwatertemperature :{"name":"temp","type":"float","value":48.79,"timestamp":1674383830108}
0 events/central_heating/otmonitor/dhwtemperature :{"name":"temp","type":"float","value":40.42,"timestamp":1674383832293}
0 events/central_heating/otmonitor/outsidetemperature :{"name":"temp","type":"float","value":0.31,"timestamp":1674383832810}
0 events/central_heating/otmonitor/boilerwatertemperature :{"name":"temp","type":"float","value":48.78,"timestamp":1674383835596}
0 events/central_heating/otmonitor/boilerwatertemperature :{"name":"temp","type":"float","value":48.74,"timestamp":1674383839895}