OTGW gateway mode problem

This Forum is about the Opentherm gateway (OTGW) from Schelte

Moderator: hvxl

Post Reply
george
Starting Member
Starting Member
Posts: 15
Joined: Tue Jan 31, 2023 10:41 pm

OTGW gateway mode problem

Post by george »

Hello,

I recently bought a OTGW from Nodo Shop which is giving me a hard time when running in gateway mode.

Board v2.8 running FW 6.4 coupled with WeMos D1 mini running rvdbreemen/OTGW-firmware v0.10.0.
Boiler is a Keston C36 Combi and thermostat a Salus RT520RF.

The setup seems to work just fine in monitor mode (except for a random Error FF):

Code: Select all

2:21:29.419651	Command: PR=A
22:21:29.485344	PR: A=OpenTherm Gateway 6.4
22:21:30.251362	Error FF
22:21:30.252154	T80130000	Read-Data 	DHW flow rate (MsgID=19): 0.00
22:21:30.346328	B70130000	Unk-DataId	DHW flow rate (MsgID=19): 0.00
22:21:31.630022	T80130000	Read-Data 	DHW flow rate (MsgID=19): 0.00
22:21:31.637324	B70130000	Unk-DataId	DHW flow rate (MsgID=19): 0.00
22:21:32.451395	T80130000	Read-Data 	DHW flow rate (MsgID=19): 0.00
22:21:32.455342	B70130000	Unk-DataId	DHW flow rate (MsgID=19): 0.00
22:21:33.379911	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:21:33.385592	B40192E00	Read-Ack  	Boiler water temperature (MsgID=25): 46.00
22:21:34.168486	PR: I=11
22:21:34.543333	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:21:34.545341	B40192E00	Read-Ack  	Boiler water temperature (MsgID=25): 46.00
22:21:35.428297	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:21:35.435129	BD0010A00	Write-Ack 	Control setpoint (MsgID=1): 10.00
22:21:36.439884	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:21:36.482733	B40000200	Read-Ack  	Status (MsgID=0): 00000010 00000000
22:21:37.449169	T00300000	Read-Data 	DHW setpoint boundaries (MsgID=48): 0 0
22:21:38.482442	T00300000	Read-Data 	DHW setpoint boundaries (MsgID=48): 0 0
22:21:38.870250	BC0304128	Read-Ack  	DHW setpoint boundaries (MsgID=48): 65 40
22:21:39.499493	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:21:39.547552	B40192E00	Read-Ack  	Boiler water temperature (MsgID=25): 46.00
22:21:40.536701	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:21:40.593868	BD0010A00	Write-Ack 	Control setpoint (MsgID=1): 10.00
22:21:41.553145	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:21:41.599985	B40000200	Read-Ack  	Status (MsgID=0): 00000010 00000000
22:21:42.570590	T80730000	Read-Data 	OEM diagnostic code (MsgID=115): 0
22:21:42.617161	B70730000	Unk-DataId	OEM diagnostic code (MsgID=115): 0
22:21:43.605372	T80730000	Read-Data 	OEM diagnostic code (MsgID=115): 0
22:21:43.649687	B70730000	Unk-DataId	OEM diagnostic code (MsgID=115): 0
22:21:44.210516	PR: I=11
22:21:44.620270	T80730000	Read-Data 	OEM diagnostic code (MsgID=115): 0
22:21:44.667866	B70730000	Unk-DataId	OEM diagnostic code (MsgID=115): 0
22:21:45.650964	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:21:45.700262	B40192E00	Read-Ack  	Boiler water temperature (MsgID=25): 46.00
22:21:46.671095	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:21:46.717481	BD0010A00	Write-Ack 	Control setpoint (MsgID=1): 10.00
22:21:47.685560	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:21:47.734860	BD0010A00	Write-Ack 	Control setpoint (MsgID=1): 10.00
22:21:48.717268	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:21:48.766040	BD0010A00	Write-Ack 	Control setpoint (MsgID=1): 10.00
22:21:49.754071	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:21:49.801123	B40000200	Read-Ack  	Status (MsgID=0): 00000010 00000000
22:21:50.770956	T000F0000	Read-Data 	Boiler capacity and modulation limits (MsgID=15): 0 0
22:21:50.817551	BF00F0000	Unk-DataId	Boiler capacity and modulation limits (MsgID=15): 0 0
22:21:51.784081	T000F0000	Read-Data 	Boiler capacity and modulation limits (MsgID=15): 0 0
22:21:51.832394	BF00F0000	Unk-DataId	Boiler capacity and modulation limits (MsgID=15): 0 0
22:21:52.826029	T000F0000	Read-Data 	Boiler capacity and modulation limits (MsgID=15): 0 0
22:21:52.883888	BF00F0000	Unk-DataId	Boiler capacity and modulation limits (MsgID=15): 0 0
22:21:53.834994	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:21:53.883260	B40192E00	Read-Ack  	Boiler water temperature (MsgID=25): 46.00
22:21:54.235733	PR: I=11
22:21:54.870495	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:21:54.917077	B40192E00	Read-Ack  	Boiler water temperature (MsgID=25): 46.00
22:21:55.996202	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:21:56.059953	BD0010A00	Write-Ack 	Control setpoint (MsgID=1): 10.00
22:21:56.918242	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:21:56.967097	B40000200	Read-Ack  	Status (MsgID=0): 00000010 00000000
22:21:58.048285	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:21:58.109056	B40000200	Read-Ack  	Status (MsgID=0): 00000010 00000000
22:21:58.959432	T10620000	Write-Data	RF sensor status information (MsgID=98): 0 0 0 0
22:21:59.019920	B70620000	Unk-DataId	RF sensor status information (MsgID=98): 0 0 0 0
22:21:59.987628	T10620000	Write-Data	RF sensor status information (MsgID=98): 0 0 0 0
22:22:00.037331	B70620000	Unk-DataId	RF sensor status information (MsgID=98): 0 0 0 0
22:22:01.001490	T10620000	Write-Data	RF sensor status information (MsgID=98): 0 0 0 0
22:22:01.051285	SC: 22:22/3
22:22:01.054765	B70620000	Unk-DataId	RF sensor status information (MsgID=98): 0 0 0 0
22:22:02.033822	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:22:02.084432	B40192E00	Read-Ack  	Boiler water temperature (MsgID=25): 46.00
22:22:03.051450	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:22:03.102265	BD0010A00	Write-Ack 	Control setpoint (MsgID=1): 10.00
22:22:04.092759	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:22:04.140206	BD0010A00	Write-Ack 	Control setpoint (MsgID=1): 10.00
22:22:04.273167	PR: I=11
22:22:05.104119	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:22:05.151467	B40000200	Read-Ack  	Status (MsgID=0): 00000010 00000000
22:22:06.135987	T001B0000	Read-Data 	Outside temperature (MsgID=27): 0.00
22:22:06.183818	B401B0400	Read-Ack  	Outside temperature (MsgID=27): 4.00
22:22:07.174709	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:22:07.222481	B40192E00	Read-Ack  	Boiler water temperature (MsgID=25): 46.00
22:22:08.187970	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:22:08.235419	BD0010A00	Write-Ack 	Control setpoint (MsgID=1): 10.00
22:22:09.207767	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:22:09.257431	B40000200	Read-Ack  	Status (MsgID=0): 00000010 00000000
22:22:10.204139	Error FF
22:22:10.211382	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:22:10.258618	B40000200	Read-Ack  	Status (MsgID=0): 00000010 00000000
22:22:11.252797	T90110000	Write-Data	Relative modulation level (MsgID=17): 0.00
22:22:12.280509	T90110000	Write-Data	Relative modulation level (MsgID=17): 0.00
22:22:12.336282	BF0110000	Unk-DataId	Relative modulation level (MsgID=17): 0.00
22:22:13.314816	T90110000	Write-Data	Relative modulation level (MsgID=17): 0.00
22:22:13.369581	BF0110000	Unk-DataId	Relative modulation level (MsgID=17): 0.00
22:22:14.303467	PR: I=11
22:22:14.321128	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:22:14.354713	B40192E00	Read-Ack  	Boiler water temperature (MsgID=25): 46.00
22:22:15.355675	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:22:15.403616	B40192E00	Read-Ack  	Boiler water temperature (MsgID=25): 46.00
but in gateway mode I get this:

Code: Select all

22:37:40.823004	Command: GW=R
22:37:42.130528	OpenTherm Gateway 6.4
22:37:42.298435	T00060000	Read-Data 	Remote parameter flags (MsgID=6): 00000000 00000000
22:37:42.396956	Error 03
22:37:43.332479	T00060000	Read-Data 	Remote parameter flags (MsgID=6): 00000000 00000000
22:37:43.378831	Error 03
22:37:44.348062	T00060000	Read-Data 	Remote parameter flags (MsgID=6): 00000000 00000000
22:37:44.464990	Error 03
22:37:45.612089	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:37:45.624451	Error 03
22:37:46.401378	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:37:46.447497	Error 03
22:37:47.434711	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:37:47.482722	Error 03
22:37:48.346517	PR: I=11
22:37:48.453543	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:37:48.511306	Error 03
22:37:49.469524	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:37:49.566745	Error 03
22:37:50.501753	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:37:50.548337	Error 03
22:37:51.693256	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:37:51.746765	Error 03
22:37:52.550668	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:37:52.602512	Error 03
22:37:53.566773	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:37:53.662952	Error 03
22:37:54.598458	T10393700	Write-Data	Max CH water setpoint (MsgID=57): 55.00
22:37:54.989491	Error 03
22:37:55.788810	T10393700	Write-Data	Max CH water setpoint (MsgID=57): 55.00
22:37:55.844615	Error 03
22:37:56.631293	T10393700	Write-Data	Max CH water setpoint (MsgID=57): 55.00
22:37:56.952565	Error 03
22:37:57.666777	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:37:57.718705	Error 03
22:37:58.369024	PR: I=11
22:37:58.700249	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:37:58.753037	Error 04
22:37:58.757437	ED55D7F55
22:37:59.831581	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:38:00.732397	Error 03
22:38:01.136390	SC: 22:38/3
22:38:01.950316	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:38:01.957807	Error 03
22:38:02.792417	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:38:02.863537	Error 03
22:38:04.099757	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:04.156336	Error 03
22:38:04.973433	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:04.981167	Error 03
22:38:05.864204	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:05.914339	Error 03
22:38:06.891658	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:06.945191	Error 03
22:38:07.898343	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:07.998047	Error 03
22:38:08.425749	PR: I=11
22:38:08.933355	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:08.983266	Error 03
22:38:09.950812	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:38:10.047968	Error 03
22:38:10.984160	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:38:11.031159	Error 03
22:38:12.003047	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:38:12.118316	Error 03
22:38:13.198427	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:38:13.250075	Error 03
22:38:14.051764	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:38:14.150444	Error 03
22:38:15.071239	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:38:15.171313	Error 03
22:38:16.101586	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:16.199741	Error 03
22:38:17.116462	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:17.214842	Error 03
22:38:18.152211	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:18.202729	Error 03
22:38:18.450064	PR: I=11
22:38:19.169588	T90101600	Write-Data	Room setpoint (MsgID=16): 22.00
22:38:19.265565	Error 03
22:38:20.202083	T90101600	Write-Data	Room setpoint (MsgID=16): 22.00
22:38:20.251590	Error 03
22:38:21.216004	T90101600	Write-Data	Room setpoint (MsgID=16): 22.00
22:38:21.315879	Error 03
22:38:22.252456	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:38:22.301528	Error 03
22:38:23.438971	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:38:23.482288	Error 03
22:38:24.307554	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:38:24.354397	Error 03
22:38:25.323843	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:38:25.385627	Error 03
22:38:26.335557	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:38:26.435702	Error 03
22:38:27.375354	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:38:27.436223	Error 03
22:38:28.397438	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:28.451841	PR: I=11
22:38:28.460477	Error 03
22:38:29.417598	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:29.469894	Error 03
22:38:30.443852	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:30.512807	Error 03
22:38:31.466368	T10181600	Write-Data	Room temperature (MsgID=24): 22.00
22:38:31.517371	Error 03
22:38:32.484636	T10181600	Write-Data	Room temperature (MsgID=24): 22.00
22:38:32.564602	Error 03
22:38:33.503507	T10181600	Write-Data	Room temperature (MsgID=24): 22.00
22:38:33.598976	Error 03
22:38:34.535356	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:38:34.586269	Error 03
22:38:35.551819	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:38:35.650708	Error 03
22:38:36.571221	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:38:36.665023	Error 03
22:38:37.603122	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:38:37.703275	Error 03
22:38:38.517737	PR: I=11
22:38:38.621871	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:38:38.717690	Error 03
22:38:39.652856	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:38:39.703763	Error 03
22:38:40.671713	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:40.765952	Error 03
22:38:41.711345	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:41.775603	Error 03
22:38:42.717104	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:42.837095	Error 03
22:38:43.753618	T801A0000	Read-Data 	DHW temperature (MsgID=26): 0.00
22:38:43.852639	Error 03
22:38:44.767819	T801A0000	Read-Data 	DHW temperature (MsgID=26): 0.00
22:38:44.867138	Error 03
22:38:45.813714	T801A0000	Read-Data 	DHW temperature (MsgID=26): 0.00
22:38:45.868180	Error 03
22:38:46.817602	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:38:46.921686	Error 03
22:38:47.851815	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:38:47.904249	Error 03
22:38:48.538013	PR: I=11
22:38:48.870181	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:38:48.931314	Error 03
22:38:50.063958	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:38:50.118187	Error 03
22:38:50.919509	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:38:50.969443	Error 03
22:38:51.946052	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:38:52.021959	Error 03
22:38:52.968359	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:53.020252	Error 03
22:38:53.986878	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:54.086573	Error 03
22:38:55.025648	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:38:55.085257	Error 03
22:38:56.036180	T900E6400	Write-Data	Maximum relative modulation level (MsgID=14): 100.00
22:38:56.136733	Error 03
22:38:57.069555	T900E6400	Write-Data	Maximum relative modulation level (MsgID=14): 100.00
22:38:57.120336	Error 03
22:38:58.095756	T900E6400	Write-Data	Maximum relative modulation level (MsgID=14): 100.00
22:38:58.161316	Error 03
22:38:58.568101	PR: I=11
22:38:59.117001	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:38:59.169230	Error 03
22:39:00.304417	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:39:00.347197	Error 03
22:39:01.124275	SC: 22:39/3
22:39:01.168786	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:39:01.219592	Error 03
22:39:02.187636	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:02.286865	Error 03
22:39:03.204755	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:03.302961	Error 03
22:39:04.237535	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:04.286562	Error 03
22:39:05.254777	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:39:05.357640	Error 03
22:39:06.287846	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:39:06.333164	Error 03
22:39:07.305027	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:39:07.401999	Error 03
22:39:08.337765	T00120000	Read-Data 	CH water pressure (MsgID=18): 0.00
22:39:08.591133	Error 03
22:39:08.597533	PR: I=11
22:39:08.602776	PR: I=11
22:39:09.353504	T00120000	Read-Data 	CH water pressure (MsgID=18): 0.00
22:39:09.669431	Error 03
22:39:10.397619	T00120000	Read-Data 	CH water pressure (MsgID=18): 0.00
22:39:10.739388	Error 03
22:39:11.407705	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:39:11.476219	Error 03
22:39:12.422105	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:39:12.519806	Error 03
22:39:13.469391	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:39:13.527740	Error 03
22:39:14.472986	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:14.568417	Error 03
22:39:15.503954	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:15.553726	Error 03
22:39:16.531307	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:16.599018	Error 03
22:39:17.553129	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:39:17.601542	Error 03
22:39:18.570743	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:39:18.619356	PR: I=11
22:39:18.669662	Error 03
22:39:19.606140	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:39:19.655884	Error 03
22:39:20.619543	T80130000	Read-Data 	DHW flow rate (MsgID=19): 0.00
22:39:20.718698	Error 03
22:39:21.474740	Command: GW=1
22:39:21.538083	GW: 1
22:39:21.640175	T80130000	Read-Data 	DHW flow rate (MsgID=19): 0.00
22:39:21.751903	Error 03
22:39:22.669405	T80130000	Read-Data 	DHW flow rate (MsgID=19): 0.00
22:39:22.721819	Error 03
22:39:23.706047	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:39:23.759087	Error 03
22:39:24.722529	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:39:24.775656	Error 03
22:39:25.752005	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:39:25.804814	Error 03
22:39:26.781655	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:26.843540	Error 03
22:39:27.790789	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:27.889840	Error 03
22:39:28.691231	PR: I=11
22:39:28.819812	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:28.870558	Error 03
22:39:29.841188	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:39:29.939215	Error 03
22:39:30.874566	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:39:30.925645	Error 03
22:39:31.888874	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:39:31.952147	Error 04
22:39:32.010565	E55555755
22:39:32.922558	T00300000	Read-Data 	DHW setpoint boundaries (MsgID=48): 0 0
22:39:33.947864	Error 03
22:39:34.958788	T00300000	Read-Data 	DHW setpoint boundaries (MsgID=48): 0 0
22:39:35.229315	Error 03
22:39:35.992064	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:39:36.046653	Error 03
22:39:37.006863	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:39:37.105300	Error 03
22:39:38.042729	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:39:38.086841	Error 03
22:39:38.721578	PR: I=11
22:39:39.056841	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:39.154686	Error 03
22:39:40.098468	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:40.162516	Error 03
22:39:41.104689	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:41.205691	Error 03
22:39:42.290080	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:39:42.340542	Error 04
22:39:42.344367	E55555755
22:39:43.155437	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:39:44.191854	Error 03
22:39:45.208353	T80730000	Read-Data 	OEM diagnostic code (MsgID=115): 0
22:39:45.336329	Error 03
22:39:46.224863	T80730000	Read-Data 	OEM diagnostic code (MsgID=115): 0
22:39:46.319323	Error 03
22:39:47.259451	T80730000	Read-Data 	OEM diagnostic code (MsgID=115): 0
22:39:47.314388	Error 03
22:39:48.275801	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:39:48.316053	Command: PR=V
22:39:48.318632	Command: PR=T
22:39:48.323761	Command: PR=S
22:39:48.343424	Error 03
22:39:48.392562	PR: V=5
22:39:48.395008	PR: T=11
22:39:48.400087	PR: S=16.00
22:39:48.756204	PR: I=11
22:39:49.306985	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:39:49.360041	Error 03
22:39:50.329419	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:39:50.449395	Error 03
22:39:51.356486	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:51.406801	Error 03
22:39:52.397126	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:52.455467	Error 03
22:39:53.391359	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:39:53.489530	Error 03
22:39:53.886586	Command: VR=0
22:39:53.965575	VR: 0
22:39:54.432860	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:39:54.489145	Error 03
22:39:55.451429	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:39:55.524129	Error 03
22:39:56.472222	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:39:56.526471	Error 03
22:39:57.507127	T000F0000	Read-Data 	Boiler capacity and modulation limits (MsgID=15): 0 0
22:39:57.553785	Error 03
22:39:58.523721	T000F0000	Read-Data 	Boiler capacity and modulation limits (MsgID=15): 0 0
22:39:58.576090	Error 03
22:39:58.791507	PR: I=11
22:39:59.540726	T000F0000	Read-Data 	Boiler capacity and modulation limits (MsgID=15): 0 0
22:39:59.657428	Error 03
22:40:00.572656	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:00.624464	Error 03
22:40:01.121676	SC: 22:40/3
22:40:01.593849	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:01.649880	Error 03
22:40:02.631061	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:02.692349	Error 03
22:40:03.643797	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:40:03.743288	Error 03
22:40:04.658102	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:40:04.755765	Error 03
22:40:05.691841	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:40:05.748434	Error 03
22:40:06.713156	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:40:06.804749	Error 03
22:40:07.744946	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:40:07.795888	Error 03
22:40:08.761075	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:40:08.809967	PR: I=11
22:40:08.856350	Error 03
22:40:09.940722	T10620000	Write-Data	RF sensor status information (MsgID=98): 0 0 0 0
22:40:09.992131	Error 03
22:40:10.811892	T10620000	Write-Data	RF sensor status information (MsgID=98): 0 0 0 0
22:40:10.930125	Error 03
22:40:11.844575	T10620000	Write-Data	RF sensor status information (MsgID=98): 0 0 0 0
22:40:11.890831	Error 03
22:40:13.011608	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:13.064212	Error 03
22:40:13.893091	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:13.941175	Error 03
22:40:14.750735	Command: VR=1
22:40:14.830366	VR: 1
22:40:14.883636	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:14.992416	Error 03
22:40:15.940179	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:40:16.006856	Error 03
22:40:16.956900	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:40:17.009155	Error 03
22:40:18.001670	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:40:18.067062	Error 03
22:40:18.892194	PR: I=11
22:40:19.008864	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:40:19.058004	Error 03
22:40:20.025449	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:40:20.122768	Error 03
22:40:21.057462	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:40:21.106990	Error 03
22:40:22.076123	T001B0000	Read-Data 	Outside temperature (MsgID=27): 0.00
22:40:22.172351	Error 03
22:40:23.094012	T001B0000	Read-Data 	Outside temperature (MsgID=27): 0.00
22:40:23.191937	Error 03
22:40:24.123067	T001B0000	Read-Data 	Outside temperature (MsgID=27): 0.00
22:40:24.176482	Error 03
22:40:25.160310	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:25.205936	Error 03
22:40:26.177924	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:26.226017	Error 03
22:40:27.203713	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:27.269587	Error 03
22:40:28.222234	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:40:28.324660	Error 03
22:40:28.908873	PR: I=11
22:40:29.244506	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:40:29.357878	Error 03
22:40:30.277980	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:40:30.330262	Error 03
22:40:31.293482	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:40:31.408370	Error 03
22:40:32.324770	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:40:32.337806	Command: VR=2
22:40:32.411107	VR: 2
22:40:32.414728	Error 03
22:40:33.347034	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:40:33.396465	Error 03
22:40:34.376571	T90110000	Write-Data	Relative modulation level (MsgID=17): 0.00
22:40:34.435596	Error 03
22:40:35.398464	T90110000	Write-Data	Relative modulation level (MsgID=17): 0.00
22:40:35.444183	Error 03
22:40:36.421512	T90110000	Write-Data	Relative modulation level (MsgID=17): 0.00
22:40:36.486064	Error 03
22:40:37.444390	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:37.494946	Error 03
22:40:38.467129	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:38.537801	B555D7F55	Write-Ack 	Message ID 93 (MsgID=93): 32597
22:40:38.961338	PR: I=11
22:40:39.494516	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:40.526170	Error 03
22:40:41.538268	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:40:41.604602	Error 03
22:40:42.560386	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:40:42.612690	Error 03
22:40:43.596083	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:40:43.649497	Error 04
22:40:43.696743	E55555755
22:40:44.612438	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:40:45.644856	Error 03
22:40:46.661914	T00030000	Read-Data 	Slave configuration (MsgID=3): 00000000 0
22:40:46.760386	Error 03
22:40:47.678115	T00030000	Read-Data 	Slave configuration (MsgID=3): 00000000 0
22:40:47.794284	Error 03
22:40:48.711558	T00030000	Read-Data 	Slave configuration (MsgID=3): 00000000 0
22:40:48.760784	Error 03
22:40:48.994923	PR: I=11
22:40:49.134726	Command: VR=3
22:40:49.193597	VR: 3
22:40:49.725017	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:49.829168	Error 03
22:40:50.761921	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:50.810085	Error 03
22:40:51.778396	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:40:51.876858	Error 03
22:40:52.810716	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:40:52.910005	Error 03
22:40:53.835487	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:40:53.898918	Error 03
22:40:54.860187	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:40:54.913597	Error 03
22:40:55.887840	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:40:55.943720	Error 03
22:40:56.898311	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:40:57.008836	Error 04
22:40:57.014661	E55555755
22:40:57.925725	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:40:58.959012	Error 03
22:40:59.009815	PR: I=11
22:40:59.984601	T00060000	Read-Data 	Remote parameter flags (MsgID=6): 00000000 00000000
22:41:00.039580	Error 03
22:41:00.996742	T00060000	Read-Data 	Remote parameter flags (MsgID=6): 00000000 00000000
22:41:01.093716	Error 03
22:41:01.100486	SC: 22:41/3
22:41:02.025946	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:02.078918	Error 03
22:41:03.189857	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:03.243867	Error 03
22:41:04.078306	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:04.128813	Error 03
22:41:04.974659	Command: VR=4
22:41:05.046992	VR: 4
22:41:05.094645	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:05.195654	Error 03
22:41:06.262048	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:06.311148	Error 03
22:41:07.145431	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:07.195675	Error 03
22:41:08.181222	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:08.230162	Error 03
22:41:09.045829	PR: I=11
22:41:09.196026	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:09.246425	Error 03
22:41:10.213206	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:10.312568	Error 03
22:41:11.246018	T10393700	Write-Data	Max CH water setpoint (MsgID=57): 55.00
22:41:11.495437	Error 03
22:41:12.263192	T10393700	Write-Data	Max CH water setpoint (MsgID=57): 55.00
22:41:12.575896	Error 03
22:41:13.303164	T10393700	Write-Data	Max CH water setpoint (MsgID=57): 55.00
22:41:13.663319	Error 03
22:41:14.311138	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:14.420755	Error 03
22:41:15.345175	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:15.399861	Error 03
22:41:16.363531	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:16.424950	Error 03
22:41:17.400200	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:17.444376	Error 03
22:41:18.420787	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:18.487339	Error 03
22:41:19.083249	PR: I=11
22:41:19.444039	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:19.494383	Error 03
22:41:20.469665	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:20.535575	Error 03
22:41:21.481955	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:21.577491	Error 03
22:41:22.531895	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:22.580143	Error 03
22:41:23.536555	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:23.590976	Error 03
22:41:24.694946	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:24.745703	Error 03
22:41:25.246845	Command: VR=5
22:41:25.331864	VR: 5
22:41:25.586467	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:25.650948	Error 03
22:41:26.743023	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:26.796463	Error 03
22:41:27.632178	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:27.690211	Error 03
22:41:28.667257	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:28.719132	Error 03
22:41:29.112284	PR: I=11
22:41:29.684525	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:29.736176	Error 03
22:41:30.698332	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:30.795748	Error 03
22:41:31.729880	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:31.779516	Error 03
22:41:32.765512	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:32.819137	Error 03
22:41:33.781647	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:33.838738	Error 03
22:41:34.804745	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:34.868648	Error 03
22:41:35.831238	T90101600	Write-Data	Room setpoint (MsgID=16): 22.00
22:41:35.881937	Error 03
22:41:36.847544	T90101600	Write-Data	Room setpoint (MsgID=16): 22.00
22:41:36.947631	Error 03
22:41:37.882942	T90101600	Write-Data	Room setpoint (MsgID=16): 22.00
22:41:37.929176	Error 03
22:41:38.896210	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:38.959771	Error 03
22:41:39.152601	PR: I=11
22:41:39.930833	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:39.981055	Error 03
22:41:40.955043	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:41.026501	Error 03
22:41:41.506746	Command: VR=6
22:41:41.581691	VR: 6
22:41:41.966227	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:42.065865	Error 03
22:41:43.002279	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:43.068185	Error 04
22:41:43.072181	ED5555F55
22:41:44.017450	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:45.175734	Error 03
22:41:46.065718	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:46.129811	Error 03
22:41:47.100769	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:47.150207	Error 03
22:41:48.116143	T10181600	Write-Data	Room temperature (MsgID=24): 22.00
22:41:48.215078	Error 03
22:41:49.150657	T10181600	Write-Data	Room temperature (MsgID=24): 22.00
22:41:49.196968	PR: I=11
22:41:49.199623	Error 03
22:41:50.164710	T10181600	Write-Data	Room temperature (MsgID=24): 22.00
22:41:50.215774	Error 03
22:41:51.183901	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:51.281804	Error 03
22:41:52.216077	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:52.263433	Error 03
22:41:53.238138	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:41:53.302554	Error 03
22:41:54.263334	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:54.314000	Error 03
22:41:55.281182	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:55.333385	Error 03
22:41:56.316144	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:41:56.367894	Error 03
22:41:57.333937	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:41:57.447000	Error 03
22:42:02.557770	Error 03
22:42:03.481283	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:42:03.532885	Error 03
22:42:04.498180	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:42:04.596858	Error 03
22:42:05.520735	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:42:05.611839	Error 03
22:42:05.898642	Command: VR=6
22:42:05.965453	VR: 6
22:42:06.665391	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:06.714852	Error 03
22:42:07.574774	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:07.639307	Error 03
22:42:08.600643	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:08.697841	Error 03
22:42:09.298757	PR: I=11
22:42:09.618879	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:42:09.713016	Error 03
22:42:10.650303	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:42:10.699321	Error 03
22:42:11.664612	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:42:11.763368	Error 03
22:42:12.825657	T900E6400	Write-Data	Maximum relative modulation level (MsgID=14): 100.00
22:42:12.883716	Error 03
22:42:13.715406	T900E6400	Write-Data	Maximum relative modulation level (MsgID=14): 100.00
22:42:14.748707	Error 03
22:42:15.770376	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:42:15.836093	Error 03
22:42:16.783441	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:42:16.883155	Error 03
22:42:17.824210	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:42:17.890482	Error 03
22:42:18.835180	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:18.933643	Error 03
22:42:19.335136	PR: I=11
22:42:19.863792	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:19.919338	Error 03
22:42:20.698861	Command: VR=7
22:42:20.766120	VR: 7
22:42:20.884653	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:20.951549	Error 03
22:42:21.913670	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:42:21.972502	Error 03
22:42:22.934487	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:42:23.033435	Error 03
22:42:23.976363	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:42:24.040233	Error 03
22:42:24.984257	T00120000	Read-Data 	CH water pressure (MsgID=18): 0.00
22:42:25.266961	Error 03
22:42:26.015676	T00120000	Read-Data 	CH water pressure (MsgID=18): 0.00
22:42:26.351745	Error 03
22:42:27.041778	T00120000	Read-Data 	CH water pressure (MsgID=18): 0.00
22:42:27.433827	Error 03
22:42:28.185877	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:42:28.236300	Error 03
22:42:28.298738	Command: VR=8
22:42:28.364827	VR: 8
22:42:29.209197	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:42:29.267774	Error 03
22:42:29.315904	PR: I=11
22:42:30.116733	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:42:30.165189	Error 03
22:42:31.135926	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:31.234898	Error 03
22:42:32.158428	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:32.223876	Error 03
22:42:33.188093	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:33.239782	Error 03
22:42:34.202039	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:42:34.298888	Error 03
22:42:35.235384	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:42:35.285699	Error 03
22:42:36.268946	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:42:36.317167	Error 03
22:42:37.285451	T80130000	Read-Data 	DHW flow rate (MsgID=19): 0.00
22:42:37.335786	Error 03
22:42:37.690817	Command: VR=9
22:42:37.750054	VR: 9
22:42:38.310457	T80130000	Read-Data 	DHW flow rate (MsgID=19): 0.00
22:42:38.372926	B75575555	Unk-DataId	Nominal ventilation value (MsgID=87): 85
22:42:39.336390	T80130000	Read-Data 	DHW flow rate (MsgID=19): 0.00
22:42:39.384010	PR: I=11
22:42:40.360547	Error 03
22:42:41.498118	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:42:41.549741	Error 03
22:42:42.411156	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:42:42.469151	Error 03
22:42:43.436981	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:43.484261	Error 03
22:42:44.453324	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:44.506669	Error 03
22:42:45.466932	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:45.572817	Error 03
22:42:46.500260	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:42:46.600299	Error 03
22:42:47.515361	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:42:47.615952	Error 03
22:42:48.666613	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:42:48.717486	Error 03
22:42:49.455615	PR: I=11
22:42:49.572889	T00300000	Read-Data 	DHW setpoint boundaries (MsgID=48): 0 0
22:42:49.925453	Error 03
22:42:50.601971	T00300000	Read-Data 	DHW setpoint boundaries (MsgID=48): 0 0
22:42:51.006941	Error 03
22:42:51.622007	T00300000	Read-Data 	DHW setpoint boundaries (MsgID=48): 0 0
22:42:51.904711	Error 03
22:42:52.653497	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:42:52.700033	Error 03
22:42:53.676656	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:42:53.748206	Error 03
22:42:54.499017	Command: VR=0
22:42:54.569716	VR: 0
22:42:54.704487	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:42:54.756080	Error 03
22:42:55.718364	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:55.814706	Error 03
22:42:56.736150	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:56.835555	Error 03
22:42:57.767810	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:42:57.818902	Error 03
22:42:58.786823	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:42:58.885635	Error 03
22:42:59.486287	PR: I=11
22:42:59.806644	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:42:59.901553	Error 03
22:43:00.837412	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:43:00.930371	Error 03
22:43:01.136738	SC: 22:43/3
22:43:01.862491	T80730000	Read-Data 	OEM diagnostic code (MsgID=115): 0
22:43:01.917153	Error 03
22:43:02.891853	T80730000	Read-Data 	OEM diagnostic code (MsgID=115): 0
22:43:02.938188	Error 03
22:43:03.917066	T80730000	Read-Data 	OEM diagnostic code (MsgID=115): 0
22:43:03.974144	Error 03
22:43:04.938671	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:43:04.986986	Error 03
22:43:05.960254	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:43:06.029037	Error 03
22:43:06.989594	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:43:07.040363	Error 03
22:43:07.498722	Command: VR=5
22:43:07.567552	VR: 5
22:43:08.002666	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:43:08.101986	Error 03
22:43:09.037653	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:43:09.086141	Error 03
22:43:09.518944	PR: I=11
22:43:10.060420	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:43:10.110330	Error 03
22:43:11.087781	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:43:11.135532	Error 03
22:43:12.105116	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:43:12.201709	Error 03
22:43:12.874837	Command: GW=0
22:43:12.941236	GW: 0
22:43:13.143434	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:43:13.188886	B40000200	Read-Ack  	Status (MsgID=0): 00000010 00000000
22:43:14.137760	Error FF
22:43:14.150515	T000F0000	Read-Data 	Boiler capacity and modulation limits (MsgID=15): 0 0
22:43:14.186102	BF00F0000	Unk-DataId	Boiler capacity and modulation limits (MsgID=15): 0 0
22:43:14.338835	Command: GW=1
22:43:14.402138	GW: 1
22:43:15.168336	T000F0000	Read-Data 	Boiler capacity and modulation limits (MsgID=15): 0 0
22:43:15.267033	Error 03
22:43:16.189859	T000F0000	Read-Data 	Boiler capacity and modulation limits (MsgID=15): 0 0
22:43:16.286928	Error 03
22:43:17.220426	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:43:17.317203	B555D7F55	Write-Ack 	Message ID 93 (MsgID=93): 32597
22:43:18.253494	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:43:19.269432	Error 03
22:43:19.562291	PR: I=11
22:43:20.304121	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:43:20.353521	Error 03
22:43:21.320486	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:43:21.368695	Error 03
22:43:22.347756	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:43:22.424051	Error 03
22:43:23.373523	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:43:23.422458	Error 03
22:43:24.389073	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:43:24.444527	Error 03
22:43:25.419884	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:43:25.470689	Error 03
22:43:26.445303	T10620000	Write-Data	RF sensor status information (MsgID=98): 0 0 0 0
22:43:26.520236	Error 03
22:43:27.470980	T10620000	Write-Data	RF sensor status information (MsgID=98): 0 0 0 0
22:43:27.519521	Error 03
22:43:28.498892	T10620000	Write-Data	RF sensor status information (MsgID=98): 0 0 0 0
22:43:28.565276	Error 03
22:43:29.524479	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:43:29.575082	PR: I=11
22:43:29.577811	Error 03
22:43:30.539401	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:43:30.587719	Error 03
22:43:31.555613	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:43:31.653364	Error 03
22:43:32.702285	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:43:32.756719	Error 03
22:43:33.606018	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:43:33.702883	Error 03
22:43:33.810953	Command: GW=R
22:43:35.104957	OpenTherm Gateway 6.4
22:43:35.676308	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:43:35.723371	Error 03
22:43:36.672850	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:43:36.770018	Error 03
22:43:37.706826	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:43:37.803722	Error 03
22:43:38.723670	T001B0000	Read-Data 	Outside temperature (MsgID=27): 0.00
22:43:38.818393	Error 03
22:43:39.621716	PR: I=11
22:43:39.756582	T001B0000	Read-Data 	Outside temperature (MsgID=27): 0.00
22:43:39.807712	Error 03
22:43:40.771404	T001B0000	Read-Data 	Outside temperature (MsgID=27): 0.00
22:43:40.873161	Error 03
22:43:42.019522	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:43:42.071269	B555D7F55	Write-Ack 	Message ID 93 (MsgID=93): 32597
22:43:42.830101	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
22:43:43.844848	Error 03
22:43:44.893389	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:43:44.949964	Error 03
22:43:45.890008	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:43:45.989413	Error 03
22:43:46.923377	T10010A00	Write-Data	Control setpoint (MsgID=1): 10.00
22:43:47.018181	Error 03
22:43:47.964977	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:43:48.023896	Error 03
22:43:48.970518	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
22:43:49.020500	Error 04
22:43:49.070470	E55555755
22:43:49.656649	PR: I=11
22:43:50.001802	T80000200	Read-Data 	Status (MsgID=0): 00000010 00000000
I also ran the diagnostic firmware and got this:

Code: Select all

Opentherm gateway diagnostics - Version 2.1

1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times

Enter test number: 5
Power supply: 3.292
Reference: 1.472
Thermostat: 0.697, 2.108
Boiler: 0.000, 2.626
Reference voltage setting (0..9) [4]: 5

Opentherm gateway diagnostics - Version 2.1

1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times

Enter test number: 2
496,1039,496,527,497,526,1009,1038,497,527,496,527,496,527,496,527,497,526,497,527,496,527,497,526,497,527,496,527,1008,1039,496,527,1008,527,496,1039,1008,1039,1008,1038,497,527,496,527,496,527,497,526,497,527,496,527,497,527,1008.
10013500  Write-Data  Control setpoint (MsgID=1): 53.00
497,1038,497,526,497,527,1008,1038,497,527,496,527,497,526,497,527,496,527,497,526,497,527,496,527,497,526,497,527,1008,1039,496,527,1008,527,497,1038,1008,1039,1008,1038,497,526,497,527,496,527,497,527,496,527,497,526,498,526,1008.
10013500  Write-Data  Control setpoint (MsgID=1): 53.00
497,1038,497,526,497,527,497,526,497,527,496,527,497,527,496,527,496,527,497,527,496,527,497,526,497,527,496,527,497,526,497,527,496,527,497,526,497,527,496,527,497,526,497,527,1008,527,497,1038,497,527,497,526,497,527,496,527,497,526,497,527,496,527,1009.
00000300  Read-Data   Status (MsgID=0): 00000011 00000000

Opentherm gateway diagnostics - Version 2.1

1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times

Enter test number: 3
24,1511,24,999,24,1512,24,1511,24,999,24,1000,24,999,24,1000,24,999,24,1512,24,1511,24,999,24,1512,24,2023,24,999,24,1512,24,1511,24,1511,24,1000,24,999,24,999,24,1000,24,1000,24,999,24,999,24,1000,24,1512,24,21907,507,945,979,468,483,479,493,946,491,480,482,471,492,477,484,471,491,477,485,471,974,950,492,474,487,471,972,952,981,466,484,957,490,471,969,955,491,470,492,471,491,471,491,471,491,471,491,471,491,471,491,471,491,471,968.
Error 01
24,998,24,1512,24,999,24,1000,24,999,24,1000,24,999,24,1000,24,999,24,1000,24,1512,24,999,24,1512,24,1511,24,1511,24,1000,24,1000,24,999,24,1000,24,999,24,1000,24,1000,24,999,24,1000,24,1000,24,999,24,1000,24,1000,24,999,24,1512,24,21902,506,498,485,488,494,976,502,494,488,481,501,481,501,483,526,454,502,480,502,481,507,475,989,489,493,986,491,481,989,975,516,467,988,500,483,975,989,975,502,497,485,481,501,481,502,480,513,470,501,481,501,481,502,495,487,480,989.
Error 01
24,1511,24,999,24,1512,24,1511,24,999,24,1000,24,1000,24,999,24,1000,24,999,24,1000,24,999,24,1000,24,1512,24,1512,24,1510,24,999,24,2023,24,2023,24,1511,24,999,24,1000,24,999,24,1000,24,999,24,1000,24,1512,24,21895,506,489,494,488,494,975,989,975,502,489,493,481,501,481,502,480,514,468,502,480,502,481,502,506,475,481,501,481,995,969,502,480,989,498,484,976,988,990,974,976,501,483,499,481,502,480,501,481,518,464,502,480,502,480,999.
Error 01

Opentherm gateway diagnostics - Version 2.1

1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times

Enter test number: 6
T: 936.099
B: 22.421
T: 936.233
B: 22.436
T: 936.417
B: 22.428
T: 1007.713
B: 22.428
T: 935.723
B: 22.425

Opentherm gateway diagnostics - Version 2.1

1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times

Enter test number: 4
OK1A high-to-low: 10.50us
OK1A low-to-high: 34.75us
OK1B high-to-low: 13.25us
OK1B low-to-high: 4.50us
Any help would be greatly appreciated!

Regards,

George
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: OTGW gateway mode problem

Post by hvxl »

First of all: My compliments for your truly excellent bug report. It contains all the information I need to investigate the issue.

I was already looking into a similar problem from another user, where the OTGW actually works fine in gateway mode, but only reports Error 03 for the boiler messages in monitor mode. His boiler also sends these strange 24µs pulses in addition to the opentherm messages.

Unfortunately, I haven't been able to reproduce the problem on the simulator so far. If I simulate the second protocol on the boiler interface, it is ignored, as expected. But I will try again, using your information as an example.

Your OK1B is quite asymmetrical. It's surprising that the short pulses of the strange protocol are still measured as 24µs. If they really are 24µs, I would have expected the difference between rise and fall times to cause an error of 8 or 9µs. So I may have to consider that the diagnostic firmware could be unable to accurately measure these short pulses and they are actually different from what I've been testing with. I don't suppose you have a scope so you can look at the signal?
Schelte
george
Starting Member
Starting Member
Posts: 15
Joined: Tue Jan 31, 2023 10:41 pm

Re: OTGW gateway mode problem

Post by george »

Hello and thank you for the quick reply and the willingness to help.

I started to investigate this using your troubleshooting guide and reading forum posts for similar issues, collecting as much debug info I could get my hands on, hoping you or someone on ther forum might help me.

Also, I need to congratulate you for your hard work and making the OT gateway project possible.

Regarding the scope for analysing the signal, unfortunetely I don't have one.

I also have another question, what if the boiler is OT lite, would that explain the behaviour?
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: OTGW gateway mode problem

Post by hvxl »

george wrote: Thu Feb 02, 2023 6:27 pm I also have another question, what if the boiler is OT lite, would that explain the behaviour?
No, for several reasons:
  1. The boiler is clearly sending OT/+ messages, along with the other pulses.
  2. The other pulses do not match the opentherm/lite specification, which says that the period of the signal must be between 2 and 10ms.
  3. In the opentherm/lite specification, it is the thermostat that sends the PWM signal. The boiler only sends a mostly steady signal; normally low, only going high in case of a fault condition.
Schelte
george
Starting Member
Starting Member
Posts: 15
Joined: Tue Jan 31, 2023 10:41 pm

Re: OTGW gateway mode problem

Post by george »

okay thanks!

Please let me know when you have more info.
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: OTGW gateway mode problem

Post by hvxl »

Serial output from the simulator:

Code: Select all

<04>OpenTherm Gateway 6.4
T80000200
Error 03
T80000200
Error 03
T80000200
Error 03
T80000200
Error 03
T80000200
Error 03
T80000200
Error 03
GW: 0
T80000200
B40000200
T10010A00
BD0010A00
T100E0000
BD00E0000
T00120000
BF0120000
T80190000
BC0191600
T001B0000
BF01B0000
T801C0000
B401C1519
In other words: I have reproduced the problem in the simulator. Now I can start to figure out what goes wrong.
Schelte
george
Starting Member
Starting Member
Posts: 15
Joined: Tue Jan 31, 2023 10:41 pm

Re: OTGW gateway mode problem

Post by george »

Glad to hear that; please let me know if I can help.
george
Starting Member
Starting Member
Posts: 15
Joined: Tue Jan 31, 2023 10:41 pm

Re: OTGW gateway mode problem

Post by george »

Hello Schelte,

I managed to find a solution after playing with the settings.

I deleted all the alternatives in the list (DA=116 to 123)
I added AA=28 for return water temp
After that I used VR command and found out that in gateway mode, it only works with VR=0.

For monitor mode VR=0 setting is too low and give error 03 (it works with VR setting higher than 3)

It may be something goes wrong when AA 116 to 126 are enabled (by defaul) because everithing started working after I deleted them.
Before doing that no VR setting worked in gateway mode.

maybe is's better to delete the AA=116 to 123 from the firmware's defaul AA and leave them for the users to fill in if they want (I dont thing most boilers are able to provide that anyway)

Here is a log of the working otgw in gatway mode:

Code: Select all

15:43:38.976084	Command: VR=0
15:43:39.061465	VR: 0
15:43:39.114754	T001B0000	Read-Data 	Outside temperature (MsgID=27): 0.00
15:43:39.176066	B401B0400	Read-Ack  	Outside temperature (MsgID=27): 4.00
15:43:40.454486	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
15:43:40.458651	B40192B00	Read-Ack  	Boiler water temperature (MsgID=25): 43.00
15:43:41.156230	T10012D00	Write-Data	Control setpoint (MsgID=1): 45.00
15:43:42.175205	T10012D00	Write-Data	Control setpoint (MsgID=1): 45.00
15:43:42.284578	BD0012D00	Write-Ack 	Control setpoint (MsgID=1): 45.00
15:43:43.318575	T00000300	Read-Data 	Status (MsgID=0): 00000011 00000000
15:43:43.363028	BC000030A	Read-Ack  	Status (MsgID=0): 00000011 00001010
15:43:44.238839	T10116400	Write-Data	Relative modulation level (MsgID=17): 100.00
15:43:44.285690	B70116400	Unk-DataId	Relative modulation level (MsgID=17): 100.00
15:43:45.255941	T10116400	Write-Data	Relative modulation level (MsgID=17): 100.00
15:43:45.362308	B70116400	Unk-DataId	Relative modulation level (MsgID=17): 100.00
15:43:46.282872	T10116400	Write-Data	Relative modulation level (MsgID=17): 100.00
15:43:46.330550	B70116400	Unk-DataId	Relative modulation level (MsgID=17): 100.00
15:43:47.310193	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
15:43:47.355740	BC0192C00	Read-Ack  	Boiler water temperature (MsgID=25): 44.00
15:43:48.455126	T10012D00	Write-Data	Control setpoint (MsgID=1): 45.00
15:43:48.456825	BD0012D00	Write-Ack 	Control setpoint (MsgID=1): 45.00
15:43:48.473357	PR: I=11
15:43:49.344059	T10012D00	Write-Data	Control setpoint (MsgID=1): 45.00
15:43:49.453356	BD0012D00	Write-Ack 	Control setpoint (MsgID=1): 45.00
15:43:50.372254	T00000300	Read-Data 	Status (MsgID=0): 00000011 00000000
15:43:50.481903	BC000030A	Read-Ack  	Status (MsgID=0): 00000011 00001010
15:43:51.405276	T00030000	Read-Data 	Slave configuration (MsgID=3): 00000000 0
15:43:51.453289	BC0030300	Read-Ack  	Slave configuration (MsgID=3): 00000011 0
15:43:52.522869	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
15:43:52.530780	BC0192C00	Read-Ack  	Boiler water temperature (MsgID=25): 44.00
15:43:53.447149	T10012E00	Write-Data	Control setpoint (MsgID=1): 46.00
15:43:53.499937	BD0012E00	Write-Ack 	Control setpoint (MsgID=1): 46.00
15:43:54.476651	T00000300	Read-Data 	Status (MsgID=0): 00000011 00000000
15:43:54.585833	BC000030A	Read-Ack  	Status (MsgID=0): 00000011 00001010
15:43:55.491566	T00060000	Read-Data 	Remote parameter flags (MsgID=6): 00000000 00000000
15:43:55.600147	BC0060303	Read-Ack  	Remote parameter flags (MsgID=6): 00000011 00000011
15:43:56.523292	T00060000	Read-Data 	Remote parameter flags (MsgID=6): 00000000 00000000
15:43:56.573474	BC0060303	Read-Ack  	Remote parameter flags (MsgID=6): 00000011 00000011
15:43:57.551020	T00060000	Read-Data 	Remote parameter flags (MsgID=6): 00000000 00000000
15:43:57.603100	BC0060303	Read-Ack  	Remote parameter flags (MsgID=6): 00000011 00000011
15:43:58.489432	PR: I=11
15:43:58.537293	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
15:43:58.658538	BC0192C00	Read-Ack  	Boiler water temperature (MsgID=25): 44.00
15:43:59.592458	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
15:43:59.685620	BC0192C00	Read-Ack  	Boiler water temperature (MsgID=25): 44.00
15:44:00.621194	T10012E00	Write-Data	Control setpoint (MsgID=1): 46.00
15:44:00.668718	BD0012E00	Write-Ack 	Control setpoint (MsgID=1): 46.00
15:44:00.993410	SC: 15:44/7
15:44:01.637352	T00000300	Read-Data 	Status (MsgID=0): 00000011 00000000
15:44:01.747768	BC000030A	Read-Ack  	Status (MsgID=0): 00000011 00001010
15:44:02.675189	T10393200	Write-Data	Max CH water setpoint (MsgID=57): 50.00
15:44:02.938337	B50393232	Write-Ack 	Max CH water setpoint (MsgID=57): 50.20
15:44:03.689074	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
15:44:03.797556	B40192B00	Read-Ack  	Boiler water temperature (MsgID=25): 43.00
15:44:04.719492	T10012E00	Write-Data	Control setpoint (MsgID=1): 46.00
15:44:04.766055	BD0012E00	Write-Ack 	Control setpoint (MsgID=1): 46.00
15:44:05.753049	T00000300	Read-Data 	Status (MsgID=0): 00000011 00000000
15:44:05.799987	BC000030A	Read-Ack  	Status (MsgID=0): 00000011 00001010
15:44:06.759796	T00000300	Read-Data 	Status (MsgID=0): 00000011 00000000
15:44:06.869366	BC000030A	Read-Ack  	Status (MsgID=0): 00000011 00001010
15:44:07.791102	T00000300	Read-Data 	Status (MsgID=0): 00000011 00000000
15:44:07.840434	BC000030A	Read-Ack  	Status (MsgID=0): 00000011 00001010
15:44:08.525004	PR: I=11
15:44:08.830744	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
15:44:08.878034	B40192B00	Read-Ack  	Boiler water temperature (MsgID=25): 43.00
15:44:09.834204	T10012E00	Write-Data	Control setpoint (MsgID=1): 46.00
15:44:09.941656	BD0012E00	Write-Ack 	Control setpoint (MsgID=1): 46.00
15:44:10.870365	T00000300	Read-Data 	Status (MsgID=0): 00000011 00000000
15:44:10.916032	BC000030A	Read-Ack  	Status (MsgID=0): 00000011 00001010
15:44:11.887044	T90101600	Write-Data	Room setpoint (MsgID=16): 22.00
15:44:11.901619	R00110000	Read-Data 	Relative modulation level (MsgID=17): 0.00
15:44:12.008846	BC0112D00	Read-Ack  	Relative modulation level (MsgID=17): 45.00
15:44:12.021472	A50101600	Write-Ack 	Room setpoint (MsgID=16): 22.00
15:44:12.904914	T90101600	Write-Data	Room setpoint (MsgID=16): 22.00
15:44:12.938761	R801C0000	Read-Data 	Return water temperature (MsgID=28): 0.00
15:44:13.203626	BC01C1C00	Read-Ack  	Return water temperature (MsgID=28): 28.00
15:44:13.231226	A50101600	Write-Ack 	Room setpoint (MsgID=16): 22.00
15:44:13.944008	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
15:44:14.012777	B40192B00	Read-Ack  	Boiler water temperature (MsgID=25): 43.00
15:44:14.947832	T10012E00	Write-Data	Control setpoint (MsgID=1): 46.00
15:44:15.056934	BD0012E00	Write-Ack 	Control setpoint (MsgID=1): 46.00
15:44:15.977188	T10012E00	Write-Data	Control setpoint (MsgID=1): 46.00
15:44:16.087362	BD0012E00	Write-Ack 	Control setpoint (MsgID=1): 46.00
15:44:17.007847	T00000300	Read-Data 	Status (MsgID=0): 00000011 00000000
15:44:17.099888	BC000030A	Read-Ack  	Status (MsgID=0): 00000011 00001010
15:44:18.021144	T901815E6	Write-Data	Room temperature (MsgID=24): 21.90
15:44:18.029281	R80380000	Read-Data 	DHW setpoint (MsgID=56): 0.00
15:44:18.114481	B40382800	Read-Ack  	DHW setpoint (MsgID=56): 40.00
15:44:18.121695	AF01815E6	Unk-DataId	Room temperature (MsgID=24): 21.90
15:44:18.553191	PR: I=11
15:44:19.050010	T901815E6	Write-Data	Room temperature (MsgID=24): 21.90
15:44:19.057804	R00110000	Read-Data 	Relative modulation level (MsgID=17): 0.00
15:44:19.158471	BC0112E00	Read-Ack  	Relative modulation level (MsgID=17): 46.00
15:44:19.176378	AF01815E6	Unk-DataId	Room temperature (MsgID=24): 21.90
15:44:20.075869	T901815E6	Write-Data	Room temperature (MsgID=24): 21.90
15:44:20.094310	R801C0000	Read-Data 	Return water temperature (MsgID=28): 0.00
15:44:20.403632	BC01C1C00	Read-Ack  	Return water temperature (MsgID=28): 28.00
15:44:20.412157	AF01815E6	Unk-DataId	Room temperature (MsgID=24): 21.90
15:44:21.107610	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
15:44:21.197273	B40192B00	Read-Ack  	Boiler water temperature (MsgID=25): 43.00
15:44:22.121526	T10012E00	Write-Data	Control setpoint (MsgID=1): 46.00
15:44:22.213548	BD0012E00	Write-Ack 	Control setpoint (MsgID=1): 46.00
15:44:23.154064	T00000300	Read-Data 	Status (MsgID=0): 00000011 00000000
15:44:23.203343	BC000030A	Read-Ack  	Status (MsgID=0): 00000011 00001010
15:44:24.165885	T00000300	Read-Data 	Status (MsgID=0): 00000011 00000000
15:44:24.275491	BC000030A	Read-Ack  	Status (MsgID=0): 00000011 00001010
15:44:25.196068	T801A0000	Read-Data 	DHW temperature (MsgID=26): 0.00
15:44:25.289614	BC01A2300	Read-Ack  	DHW temperature (MsgID=26): 35.00
15:44:26.213829	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
15:44:27.246052	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
15:44:27.296143	B40192B00	Read-Ack  	Boiler water temperature (MsgID=25): 43.00
15:44:28.274368	T80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
15:44:28.320376	B40192B00	Read-Ack  	Boiler water temperature (MsgID=25): 43.00
I am really happy that it finally works that way it was supposed to, and curious to know what you found by playing with the simulator.

Best regards,
George
george
Starting Member
Starting Member
Posts: 15
Joined: Tue Jan 31, 2023 10:41 pm

Re: OTGW gateway mode problem

Post by george »

And I'm back to square one!

The gateway stopped working again and behaves the same way I mentioned in the first post.

Looks like it had nothing to do with what I did, it's all hit and miss.
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: OTGW gateway mode problem

Post by hvxl »

george wrote: Sun Feb 05, 2023 11:57 pm The gateway stopped working again and behaves the same way I mentioned in the first post.
That doesn't surprise me at all. It didn't make any sense that the changes you made could have fixed the issue.

Can you try the attached experimental gateway firmware? It is just a quick hack that will most likely not be the final solution. But hopefully it helps you out for the moment and provides me with confirmation that I'm on the right track.
Attachments
gateway-6.4.1.hex.gz
Experimental firmware 6.4.1. Not for general use!
(10.34 KiB) Downloaded 83 times
Schelte
george
Starting Member
Starting Member
Posts: 15
Joined: Tue Jan 31, 2023 10:41 pm

Re: OTGW gateway mode problem

Post by george »

I just flashed the experimental firmware and it just works, no additional tweaking required.
Thank you!
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: OTGW gateway mode problem

Post by hvxl »

Excellent. That confirms I'm not chasing a ghost.
Schelte