I am experimenting in controlling my CV (Nefit TopLine Aquapower HRC 45/CW6 + EMS-OT) with the Honeywell chronotherm wireless modulation cmt957m1011 thermostat by means of the OpenTherm Gateway. After connecting everything I can read the communications (with Domoticz and otmonitor). So fa so good....
But at least I want to interfere with the Room setpoint, and it seems that the CV (or thermostat) just ignore everthing I send them, as if I only have a read-only gateway.
I've uploaded my log files to http://otgw.tclcode.com/matrix.cgi#boilers and the room setpoint (DataId 16) is not marked. What can I do to get this to work?
Here's a snippet of the otmonitor log:
Code: Select all
15:36:35.759915 AF0050000 Unk-DataId Application-specific flags: 00000000 0
15:36:36.204631 T80190000 Read-Data Boiler water temperature: 0.00
15:36:36.282871 BC0192BB3 Read-Ack Boiler water temperature: 43.70
15:36:36.735828 T10013A00 Write-Data Control setpoint: 58.00
15:36:36.830470 BD0013A00 Write-Ack Control setpoint: 58.00
15:36:37.283768 T00000300 Read-Data Status: 00000011 00000000
15:36:37.360856 B40000302 Read-Ack Status: 00000011 00000010
15:36:37.814197 T00000300 Read-Data Status: 00000011 00000000
15:36:37.908447 B40000302 Read-Ack Status: 00000011 00000010
15:36:38.361866 T00000300 Read-Data Status: 00000011 00000000
15:36:38.454666 B40000302 Read-Ack Status: 00000011 00000010
15:36:38.908719 T00000300 Read-Data Status: 00000011 00000000
15:36:38.986136 B40000302 Read-Ack Status: 00000011 00000010
15:36:39.439188 T00000300 Read-Data Status: 00000011 00000000
15:36:39.533618 B40000302 Read-Ack Status: 00000011 00000010
15:36:39.986477 T00000300 Read-Data Status: 00000011 00000000
15:36:40.080329 B40000302 Read-Ack Status: 00000011 00000010
15:36:40.533615 T00000300 Read-Data Status: 00000011 00000000
15:36:40.611219 B40000302 Read-Ack Status: 00000011 00000010
15:36:41.063871 T80385000 Read-Data DHW setpoint: 80.00
15:36:41.073581 R00770000 Read-Data DHW burner starts: 0
15:36:41.157644 B40770824 Read-Ack DHW burner starts: 2084
15:36:41.167484 A40385000 Read-Ack DHW setpoint: 80.00
15:36:41.611348 T00395500 Read-Data Max CH water setpoint: 85.00
15:36:41.689088 BC0395500 Read-Ack Max CH water setpoint: 85.00
15:36:42.142340 T900E6400 Write-Data Maximum relative modulation level: 100.00
15:36:42.236663 B500E6400 Write-Ack Maximum relative modulation level: 100.00
15:36:42.688982 T00050000 Read-Data Application-specific flags: 00000000 0
15:36:42.698757 R00780000 Read-Data Burner operation hours: 0
15:36:42.783217 B40780516 Read-Ack Burner operation hours: 1302
15:36:42.791804 AF0050000 Unk-DataId Application-specific flags: 00000000 0
15:36:43.220319 T80190000 Read-Data Boiler water temperature: 0.00
15:36:43.314504 BC01929CC Read-Ack Boiler water temperature: 41.80
15:36:43.768101 T10013A00 Write-Data Control setpoint: 58.00
15:36:43.862116 BD0013A00 Write-Ack Control setpoint: 58.00
15:36:44.298622 T90181400 Write-Data Room temperature: 20.00
15:36:44.330931 R00740000 Read-Data Burner starts: 0
15:36:44.392377 B40740F97 Read-Ack Burner starts: 3991
15:36:44.400020 AF0181400 Unk-DataId Room temperature: 20.00
15:36:44.845361 T90101600 Write-Data Room setpoint: 22.00
15:36:44.855076 R00770000 Read-Data DHW burner starts: 0
15:36:44.939209 B40770824 Read-Ack DHW burner starts: 2084
15:36:44.948015 A50101600 Write-Ack Room setpoint: 22.00
15:36:45.393432 T801C0000 Read-Data Return water temperature: 0.00
15:36:45.470624 BC01C1EB3 Read-Ack Return water temperature: 30.70
15:36:45.923590 T00050000 Read-Data Application-specific flags: 00000000 0
15:36:45.933682 R00780000 Read-Data Burner operation hours: 0
15:36:46.017252 B40780516 Read-Ack Burner operation hours: 1302
15:36:46.027080 AF0050000 Unk-DataId Application-specific flags: 00000000 0
15:36:46.471600 T80190000 Read-Data Boiler water temperature: 0.00
15:36:46.548679 B40192919 Read-Ack Boiler water temperature: 41.10
15:36:47.018375 T10013A00 Write-Data Control setpoint: 58.00
15:36:47.095933 BD0013A00 Write-Ack Control setpoint: 58.00
15:36:47.549057 T00110000 Read-Data Relative modulation level: 0.00
15:36:47.643600 BC0110000 Read-Ack Relative modulation level: 0.00
15:36:48.095759 T00090000 Read-Data Remote override room setpoint: 0.00
15:36:48.105409 R00740000 Read-Data Burner starts: 0
15:36:48.189598 B40740F97 Read-Ack Burner starts: 3991
15:36:48.199336 A40091710 Read-Ack Remote override room setpoint: 23.06