With my OTGW connected the Chronotherm 4 room thermostat sometimes switches back to its daily program. I didn't experience this during summer, but now in the colder season, when the room setpoint is manually increased to 20.5°C, I notice that every now and then the room thermostat witches back to its daily program, which defaults to 18.5 °C. The house gets a litte chilly then, as so gets my wife --> the WAF is heavily compromised!!!

As I suspected the OTGW to somehow influence the room thermostat, as it provide power supply to the Chronotherm, I disconnected it. Since then (and as it has been in the pre-OTGW era) the room thermostat works as it should.

So it seems that the OTGW is critical in the power supply to the Chronotherm. How can I check the OTGW output with respect to the power supplied to the room thermostat. I guess a simple voltage meter is not sufficient as the communication with the room thermostat is modulated (voltage and current) over the two wires. And how can I improve the power supply to be outside the critical range for the Chronotherm?
** Maurice **
hvxl
Senior Member
Senior Member
Posts: 2031
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Chronotherm 4 defaults to program - WAF compromised!!

Post by hvxl »

The gateway is supplying a current to the thermostat, either 7mA or 20mA. It seems unlikely to me that you have a problem there if you don't see any other symptoms than the thermostat returning to its program.

I suspect the gateway may be providing an override setpoint for some reason. If it later cancels that, the thermostat returns to its scheduled program. Please provide some logs of when the problem occurs for me to verify whether that is the case.

You can also try to disable the remote override functionality in the thermostat and see if that makes the problem go away.
Schelte
mo046
Member
Member
Posts: 186
Joined: Thu Nov 08, 2007 4:12 pm
Location: Netherlands

Re: Chronotherm 4 defaults to program - WAF compromised!!

Post by mo046 »

I checked my log and couldn't find anything strange. But I'll record them and send you the log. I'll try to find out whether the setpoint override can be ignored by the thermostat and if that helps.
** Maurice **
evanes
Starting Member
Starting Member
Posts: 3
Joined: Sat Apr 05, 2008 9:29 am
Location: Netherlands
Contact:

Re: Chronotherm 4 defaults to program - WAF compromised!!

Post by evanes »

I too have this situation.

When I remotely try to change the temperature the setpoint keeps jumping back to the thermostat program.
And in order to keep the wife happy I am having to return to all day high temperature settings. :cry:

I use Openhab as a controller, I receive status from the opentherm gateway using MQTT and I send a TCP message from openhab to the gateway with a TT=21.0 command. And the gateway gives a good confirmation. Well I actually send multiple TT= commands because in Openhab I have a thermostat defined. It shows the program temperature. For instance 16.0 I then click "up" multiple times to the temp gauge goes 16.5 17.0 17.5 etc until 21.0.

I will try and record a log session with opentherm gateway and post it here.

thanks Evert
evanes
Starting Member
Starting Member
Posts: 3
Joined: Sat Apr 05, 2008 9:29 am
Location: Netherlands
Contact:

Re: Chronotherm 4 defaults to program - WAF compromised!!

Post by evanes »

hmm, while getting together my logs I did notice a silly mistake in my openhab configuration.

I do not however see how this could create the error situation...

In openhab you can define an item for receiving through mqtt and an item for sending through tcp.
I used the sending item to link to the UI. What happened however is when I click on the temp gauge in the UI to go up, a command was send to opentherm gateway. And after about 30-60 seconds the opentherm gateway processes the new setpoint and sends this back through MQTT.
Which I receive in openhab and then use to update the UI. Which in turn is recorded as a change and triggers the send to opentherm.

I will continue to test and post updated findings here.
mo046
Member
Member
Posts: 186
Joined: Thu Nov 08, 2007 4:12 pm
Location: Netherlands

Re: Chronotherm 4 defaults to program - WAF compromised!!

Post by mo046 »

I've checked for a setting in the thermostat to disable the remote setpoint override, but I could'nt find any.

When operating with a manual setpoint of 20.5 °C after a random time the setpoint is being reset to the daily program of 18.5 °C. In this example at 19:45:40.644131

Code: Select all

19:45:00.078158  Command (via relay server, from 127.0.0.1:56316): PS=1
19:45:00.118722  PS: 1
19:45:00.291230  00000010/00001100,10.00,00000001/00000001,100.00,0/0,20.50,76.00,0.00,20.88,67.00,0.00,14.00,44.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
19:45:01.684367  Command (via relay server, from 127.0.0.1:56317): PS=1
19:45:01.710740  PS: 1
19:45:01.878667  00000010/00001100,10.00,00000001/00000001,100.00,0/0,20.50,76.00,0.00,20.88,67.00,0.00,14.00,44.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
19:45:02.104248  Command (via relay server, from 127.0.0.1:56318): PR=T
19:45:02.195188  PR: T=11
19:45:02.281036  Command (via relay server, from 127.0.0.1:56319): PR=R
19:45:02.371593  PR: R=D
19:45:02.477212  Command (via relay server, from 127.0.0.1:56320): PR=M
19:45:02.539779  PR: M=G
19:45:02.614557  Command (via relay server, from 127.0.0.1:56321): PR=V
19:45:02.710336  PR: V=3
19:45:02.864314  Command (via relay server, from 127.0.0.1:56324): PR=O
19:45:02.969060  PR: O=N
19:45:03.056465  Command (via relay server, from 127.0.0.1:56325): PR=W
19:45:03.191965  PR: W=A
19:45:03.238186  Command (via relay server, from 127.0.0.1:56326): PR=L
19:45:03.273467  PR: L=FXOMPC
19:45:03.329629  Command (via relay server, from 127.0.0.1:56327): PS=0
19:45:03.405164  PS: 0
19:45:03.636165  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:45:03.859908  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:45:04.703191  T80190000  Read-Data   Boiler water temperature: 0.00
19:45:04.770105  B40194400  Read-Ack    Boiler water temperature: 68.00
19:45:05.679399  T10010A00  Write-Data  Control setpoint: 10.00
19:45:05.765106  BD0010A00  Write-Ack   Control setpoint: 10.00
19:45:06.683165  T00110000  Read-Data   Relative modulation level: 0.00
19:45:06.758031  BC0114200  Read-Ack    Relative modulation level: 66.00
19:45:07.642302  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:45:07.766865  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:45:08.636284  T80190000  Read-Data   Boiler water temperature: 0.00
19:45:08.735148  B40194400  Read-Ack    Boiler water temperature: 68.00
19:45:09.620596  T10010A00  Write-Data  Control setpoint: 10.00
19:45:09.751131  BD0010A00  Write-Ack   Control setpoint: 10.00
19:45:10.698050  T001B0000  Read-Data   Outside temperature: 0.00
19:45:10.772241  B401B0E00  Read-Ack    Outside temperature: 14.00
19:45:11.651694  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:45:11.780693  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:45:12.653676  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:45:12.855991  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:45:13.652079  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:45:13.835964  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:45:14.667884  T80190000  Read-Data   Boiler water temperature: 0.00
19:45:14.743095  BC0194500  Read-Ack    Boiler water temperature: 69.00
19:45:15.656277  T10010A00  Write-Data  Control setpoint: 10.00
19:45:15.760774  BD0010A00  Write-Ack   Control setpoint: 10.00
19:45:16.624288  T00110000  Read-Data   Relative modulation level: 0.00
19:45:16.745070  B40113700  Read-Ack    Relative modulation level: 55.00
19:45:17.620112  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:45:17.735152  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:45:18.655993  T80190000  Read-Data   Boiler water temperature: 0.00
19:45:18.776503  BC0194500  Read-Ack    Boiler water temperature: 69.00
19:45:19.651547  T10010A00  Write-Data  Control setpoint: 10.00
19:45:19.763116  BD0010A00  Write-Ack   Control setpoint: 10.00
19:45:20.668732  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:45:20.815171  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:45:21.636540  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:45:21.776482  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:45:22.636394  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:45:22.794056  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:45:23.621073  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:45:23.806017  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:45:24.667953  T80190000  Read-Data   Boiler water temperature: 0.00
19:45:24.797583  BC0194600  Read-Ack    Boiler water temperature: 70.00
19:45:25.651797  T10010A00  Write-Data  Control setpoint: 10.00
19:45:25.764558  BD0010A00  Write-Ack   Control setpoint: 10.00
19:45:26.651724  T80380000  Read-Data   DHW setpoint: 0.00
19:45:26.763439  BE0380000  Data-Inv    DHW setpoint: 0.00
19:45:27.636189  T00390000  Read-Data   Max CH water setpoint: 0.00
19:45:27.745169  BF0390000  Unk-DataId  Max CH water setpoint: 0.00
19:45:27.763761  AC0395A00  Read-Ack    Max CH water setpoint: 90.00
19:45:28.636054  T80190000  Read-Data   Boiler water temperature: 0.00
19:45:28.738109  BC0194600  Read-Ack    Boiler water temperature: 70.00
19:45:29.625131  T10010A00  Write-Data  Control setpoint: 10.00
19:45:29.745465  BD0010A00  Write-Ack   Control setpoint: 10.00
19:45:30.132816  Command (via relay server, from 127.0.0.1:56333): PS=1
19:45:30.162468  PS: 1
19:45:30.292305  00000010/00001100,10.00,00000001/00000001,100.00,0/0,20.50,55.00,0.00,20.88,70.00,0.00,14.00,44.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
19:45:31.701644  Command (via relay server, from 127.0.0.1:56335): PS=1
19:45:31.730484  PS: 1
19:45:31.877414  00000010/00001100,10.00,00000001/00000001,100.00,0/0,20.50,55.00,0.00,20.88,70.00,0.00,14.00,44.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
19:45:32.095692  Command (via relay server, from 127.0.0.1:56336): PR=T
19:45:32.138265  PR: T=11
19:45:32.170361  Command (via relay server, from 127.0.0.1:56337): PR=R
19:45:32.201634  PR: R=D
19:45:32.222066  Command (via relay server, from 127.0.0.1:56338): PR=M
19:45:32.248735  PR: M=G
19:45:32.275191  Command (via relay server, from 127.0.0.1:56339): PR=V
19:45:32.303716  PR: V=3
19:45:32.325282  Command (via relay server, from 127.0.0.1:56340): PR=O
19:45:32.356575  PR: O=N
19:45:32.377605  Command (via relay server, from 127.0.0.1:56341): PR=W
19:45:32.398510  PR: W=A
19:45:32.446996  Command (via relay server, from 127.0.0.1:56342): PR=L
19:45:32.493218  PR: L=FXOMPC
19:45:32.524240  Command (via relay server, from 127.0.0.1:56343): PS=0
19:45:32.545899  PS: 0
19:45:32.651411  T80640000  Read-Data   Remote override function: 00000000
19:45:32.780073  B70640000  Unk-DataId  Remote override function: 00000000
19:45:32.795583  A40640303  Read-Ack    Remote override function: 00000011
                               - Manual change priority: enable overrule (1)
                               - Program change priority: enable overrule (1)
19:45:33.631948  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:45:33.961084  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:45:34.636884  T80190000  Read-Data   Boiler water temperature: 0.00
19:45:34.745938  B40194700  Read-Ack    Boiler water temperature: 71.00
19:45:35.636145  T10010A00  Write-Data  Control setpoint: 10.00
19:45:35.745843  BD0010A00  Write-Ack   Control setpoint: 10.00
19:45:36.620495  T00110000  Read-Data   Relative modulation level: 0.00
19:45:36.741568  B40112300  Read-Ack    Relative modulation level: 35.00
19:45:37.667097  T901814EE  Write-Data  Room temperature: 20.93
19:45:37.773806  B501814EE  Write-Ack   Room temperature: 20.93
19:45:38.667494  T80190000  Read-Data   Boiler water temperature: 0.00
19:45:38.817224  B40194700  Read-Ack    Boiler water temperature: 71.00
19:45:39.651288  T10010A00  Write-Data  Control setpoint: 10.00
19:45:39.756621  BD0010A00  Write-Ack   Control setpoint: 10.00
19:45:40.644131  T90101280  Write-Data  Room setpoint: 18.50
19:45:40.744925  B50101280  Write-Ack   Room setpoint: 18.50
19:45:41.636322  T9014532E  Write-Data  Day of week and time of day: Tue 19:46
19:45:41.745330  BF014532E  Unk-DataId  Day of week and time of day: Tue 19:46
19:45:41.752588  A5014532E  Write-Ack   Day of week and time of day: Tue 19:46
19:45:42.625058  T801C0000  Read-Data   Return water temperature: 0.00
19:45:42.749038  BC01C3700  Read-Ack    Return water temperature: 55.00
19:45:43.620313  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:45:43.780046  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:45:44.656018  T80190000  Read-Data   Boiler water temperature: 0.00
19:45:44.776765  B40194700  Read-Ack    Boiler water temperature: 71.00
19:45:45.652598  T10010A00  Write-Data  Control setpoint: 10.00
19:45:45.774395  BD0010A00  Write-Ack   Control setpoint: 10.00
19:45:46.670406  T00110000  Read-Data   Relative modulation level: 0.00
19:45:46.756107  B40111600  Read-Ack    Relative modulation level: 22.00
19:45:47.651269  T801A0000  Read-Data   DHW temperature: 0.00
19:45:47.761889  BE01A0000  Data-Inv    DHW temperature: 0.00
19:45:48.635744  T80190000  Read-Data   Boiler water temperature: 0.00
19:45:48.755771  B40194700  Read-Ack    Boiler water temperature: 71.00
19:45:49.637785  T10010A00  Write-Data  Control setpoint: 10.00
19:45:49.733243  BD0010A00  Write-Ack   Control setpoint: 10.00
19:45:50.667120  T001B0000  Read-Data   Outside temperature: 0.00
19:45:50.776418  B401B0E00  Read-Ack    Outside temperature: 14.00
19:45:51.651502  T000F0000  Read-Data   Boiler capacity and modulation limits: 0 0
19:45:51.758105  BF00F0000  Unk-DataId  Boiler capacity and modulation limits: 0 0
19:45:52.659220  T00120000  Read-Data   CH water pressure: 0.00
19:45:52.760707  B60120000  Data-Inv    CH water pressure: 0.00
19:45:53.636207  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:45:53.771085  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:45:54.637297  T80190000  Read-Data   Boiler water temperature: 0.00
19:45:54.756237  B40194700  Read-Ack    Boiler water temperature: 71.00
19:45:55.656325  T10010A00  Write-Data  Control setpoint: 10.00
19:45:55.760814  BD0010A00  Write-Ack   Control setpoint: 10.00
19:45:56.639774  T00110000  Read-Data   Relative modulation level: 0.00
19:45:56.732087  B40110B00  Read-Ack    Relative modulation level: 11.00
19:45:57.656495  T001B0000  Read-Data   Outside temperature: 0.00
19:45:57.792086  B401B0E00  Read-Ack    Outside temperature: 14.00
19:45:58.671114  T80190000  Read-Data   Boiler water temperature: 0.00
19:45:58.785268  B40194700  Read-Ack    Boiler water temperature: 71.00
19:45:59.651615  T10010A00  Write-Data  Control setpoint: 10.00
19:45:59.760812  BD0010A00  Write-Ack   Control setpoint: 10.00
19:46:00.117620  Command (via relay server, from 127.0.0.1:56378): PS=1
19:46:00.159217  PS: 1
19:46:00.276362  00000010/00001100,10.00,00000001/00000001,100.00,0/0,18.50,11.00,0.00,20.93,71.00,0.00,14.00,55.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
19:46:01.711217  Command (via relay server, from 127.0.0.1:56379): PS=1
19:46:01.738536  PS: 1
19:46:01.961489  00000010/00001100,10.00,00000001/00000001,100.00,0/0,18.50,11.00,0.00,20.93,71.00,0.00,14.00,55.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
19:46:02.193091  Command (via relay server, from 127.0.0.1:56380): PR=T
19:46:02.241470  PR: T=11
19:46:02.302742  Command (via relay server, from 127.0.0.1:56382): PR=R
19:46:02.400273  PR: R=D
19:46:02.465130  Command (via relay server, from 127.0.0.1:56383): PR=M
19:46:02.513460  PR: M=G
19:46:02.586435  Command (via relay server, from 127.0.0.1:56384): PR=V
19:46:02.614576  PR: V=3
19:46:02.684890  Command (via relay server, from 127.0.0.1:56385): PR=O
19:46:02.707203  PR: O=N
19:46:02.727393  Command (via relay server, from 127.0.0.1:56386): PR=W
19:46:02.785947  PR: W=A
19:46:02.859219  Command (via relay server, from 127.0.0.1:56388): PR=L
19:46:02.940512  PR: L=FXOMPC
19:46:03.019267  Command (via relay server, from 127.0.0.1:56389): PS=0
19:46:03.044976  PS: 0
19:46:03.667699  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:46:03.843127  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:46:04.652025  T80190000  Read-Data   Boiler water temperature: 0.00
19:46:04.823983  BC0194600  Read-Ack    Boiler water temperature: 70.00
19:46:05.651821  T10010A00  Write-Data  Control setpoint: 10.00
19:46:05.753773  BD0010A00  Write-Ack   Control setpoint: 10.00
19:46:06.632501  T00110000  Read-Data   Relative modulation level: 0.00
19:46:06.745160  BC0110500  Read-Ack    Relative modulation level: 5.00
19:46:07.636287  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:46:07.792899  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:46:08.660638  T80190000  Read-Data   Boiler water temperature: 0.00
19:46:08.776360  BC0194600  Read-Ack    Boiler water temperature: 70.00
19:46:09.668059  T10010A00  Write-Data  Control setpoint: 10.00
19:46:09.760708  BD0010A00  Write-Ack   Control setpoint: 10.00
19:46:10.655173  T001B0000  Read-Data   Outside temperature: 0.00
19:46:10.778837  B401B0E00  Read-Ack    Outside temperature: 14.00
19:46:11.672366  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:46:11.825875  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:46:12.636268  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
19:46:12.774592  B4000020C  Read-Ack    Status: 00000010 00001100
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: active (1)
                               - Flame status: flame on (1)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
19:46:13.636388  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
I can't find any indication that the room thermostat is switched back to the daily program due to a (short) remote setpoint request.

When requesting a temporary setpoint override (through HS3 script), the setpoint is maintained and doesn't fall back to the daily program. In following example the room setpoint of 18.5 °C is switched to the remote override setpoint of 19 °C (activated at 10:36:14.443473):

Code: Select all

10:36:00.108785  Command (via relay server, from 127.0.0.1:65079): PS=1
10:36:00.263980  PS: 1
10:36:00.337652  00000010/00000000,10.00,00000001/00000001,100.00,0/0,18.50,0.00,0.00,20.16,34.00,0.00,14.00,33.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
10:36:01.711384  Command (via relay server, from 127.0.0.1:65080): PS=1
10:36:01.774503  PS: 1
10:36:01.882444  00000010/00000000,10.00,00000001/00000001,100.00,0/0,18.50,0.00,0.00,20.16,34.00,0.00,14.00,33.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
10:36:02.162867  Command (via relay server, from 127.0.0.1:65081): PR=T
10:36:02.384781  PR: T=11
10:36:02.481874  Command (via relay server, from 127.0.0.1:65082): PR=R
10:36:02.528248  PR: R=D
10:36:02.631255  Command (via relay server, from 127.0.0.1:65083): PR=M
10:36:02.681526  PR: M=G
10:36:02.754102  Command (via relay server, from 127.0.0.1:65084): PR=V
10:36:02.778695  PR: V=3
10:36:02.897455  Command (via relay server, from 127.0.0.1:65085): PR=O
10:36:02.994771  PR: O=N
10:36:03.216131  Command (via relay server, from 127.0.0.1:65086): PR=W
10:36:03.374722  PR: W=A
10:36:03.430952  Command (via relay server, from 127.0.0.1:65087): PR=L
10:36:03.469580  PR: L=FXOMPC
10:36:03.488697  Command (via relay server, from 127.0.0.1:65088): PS=0
10:36:03.517064  PS: 0
10:36:03.655707  T10010A00  Write-Data  Control setpoint: 10.00
10:36:03.832273  BD0010A00  Write-Ack   Control setpoint: 10.00
10:36:04.661250  T00110000  Read-Data   Relative modulation level: 0.00
10:36:04.780965  BC0110000  Read-Ack    Relative modulation level: 0.00
10:36:05.737314  T90181424  Write-Data  Room temperature: 20.14
10:36:05.777738  B50181424  Write-Ack   Room temperature: 20.14
10:36:06.656462  T80190000  Read-Data   Boiler water temperature: 0.00
10:36:06.772397  B40192200  Read-Ack    Boiler water temperature: 34.00
10:36:07.649900  T10010A00  Write-Data  Control setpoint: 10.00
10:36:07.752492  BD0010A00  Write-Ack   Control setpoint: 10.00
10:36:08.634225  T90101280  Write-Data  Room setpoint: 18.50
10:36:08.743473  B50101280  Write-Ack   Room setpoint: 18.50
10:36:09.672143  T10144A24  Write-Data  Day of week and time of day: Tue 10:36
10:36:09.774578  B70144A24  Unk-DataId  Day of week and time of day: Tue 10:36
10:36:09.791239  AD0144A24  Write-Ack   Day of week and time of day: Tue 10:36
10:36:10.693406  T801C0000  Read-Data   Return water temperature: 0.00
10:36:10.791940  B401C2100  Read-Ack    Return water temperature: 33.00
10:36:11.665559  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:36:12.025941  B40000200  Read-Ack    Status: 00000010 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:36:12.657719  T80190000  Read-Data   Boiler water temperature: 0.00
10:36:12.757119  B40192200  Read-Ack    Boiler water temperature: 34.00
10:36:13.757568  T10010A00  Write-Data  Control setpoint: 10.00
10:36:13.810111  BD0010A00  Write-Ack   Control setpoint: 10.00
10:36:14.443473  Command (via relay server, from 127.0.0.1:65091): TT=19.00
10:36:14.470754  TT: 19.00
10:36:14.680853  T00110000  Read-Data   Relative modulation level: 0.00
10:36:14.821742  BC0110000  Read-Ack    Relative modulation level: 0.00
10:36:15.665635  T801A0000  Read-Data   DHW temperature: 0.00
10:36:15.790087  BE01A0000  Data-Inv    DHW temperature: 0.00
10:36:16.676116  T80190000  Read-Data   Boiler water temperature: 0.00
10:36:16.788356  B40192200  Read-Ack    Boiler water temperature: 34.00
10:36:17.649810  T10010A00  Write-Data  Control setpoint: 10.00
10:36:17.800741  BD0010A00  Write-Ack   Control setpoint: 10.00
10:36:18.650259  T001B0000  Read-Data   Outside temperature: 0.00
10:36:18.758902  B401B0E00  Read-Ack    Outside temperature: 14.00
10:36:19.681167  T000F0000  Read-Data   Boiler capacity and modulation limits: 0 0
10:36:19.804110  BF00F0000  Unk-DataId  Boiler capacity and modulation limits: 0 0
10:36:20.670247  T00120000  Read-Data   CH water pressure: 0.00
10:36:20.774636  B60120000  Data-Inv    CH water pressure: 0.00
10:36:21.665397  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:36:21.919257  B40000200  Read-Ack    Status: 00000010 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:36:22.649869  T80190000  Read-Data   Boiler water temperature: 0.00
10:36:22.793237  B40192200  Read-Ack    Boiler water temperature: 34.00
10:36:23.634115  T10010A00  Write-Data  Control setpoint: 10.00
10:36:23.777947  BD0010A00  Write-Ack   Control setpoint: 10.00
10:36:24.702876  T00110000  Read-Data   Relative modulation level: 0.00
10:36:24.784118  BC0110000  Read-Ack    Relative modulation level: 0.00
10:36:25.665714  T001B0000  Read-Data   Outside temperature: 0.00
10:36:25.774837  B401B0E00  Read-Ack    Outside temperature: 14.00
10:36:26.649768  T80190000  Read-Data   Boiler water temperature: 0.00
10:36:26.816320  B40192200  Read-Ack    Boiler water temperature: 34.00
10:36:27.670887  T10010A00  Write-Data  Control setpoint: 10.00
10:36:27.747926  BD0010A00  Write-Ack   Control setpoint: 10.00
10:36:28.657892  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:36:28.811616  B40000200  Read-Ack    Status: 00000010 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:36:29.681081  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:36:29.839277  B40000200  Read-Ack    Status: 00000010 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:36:30.139514  Command (via relay server, from 127.0.0.1:65097): PS=1
10:36:30.201227  PS: 1
10:36:30.318987  00000010/00000000,10.00,00000001/00000001,100.00,0/0,18.50,0.00,0.00,20.14,34.00,0.00,14.00,33.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
10:36:31.666652  Command (via relay server, from 127.0.0.1:65098): PS=1
10:36:31.693642  PS: 1
10:36:31.844045  00000010/00000000,10.00,00000001/00000001,100.00,0/0,18.50,0.00,0.00,20.14,34.00,0.00,14.00,33.00,75/20,0/0,0.00,0.00,0,0,0,0,0,0,0,0
10:36:32.057614  Command (via relay server, from 127.0.0.1:65099): PR=T
10:36:32.085497  PR: T=11
10:36:32.113169  Command (via relay server, from 127.0.0.1:65100): PR=R
10:36:32.136053  PR: R=D
10:36:32.161224  Command (via relay server, from 127.0.0.1:65101): PR=M
10:36:32.192152  PR: M=G
10:36:32.219059  Command (via relay server, from 127.0.0.1:65102): PR=V
10:36:32.239818  PR: V=3
10:36:32.261287  Command (via relay server, from 127.0.0.1:65103): PR=O
10:36:32.292879  PR: O=t19.00
10:36:32.349914  Command (via relay server, from 127.0.0.1:65104): PR=W
10:36:32.377522  PR: W=A
10:36:32.394758  Command (via relay server, from 127.0.0.1:65105): PR=L
10:36:32.424487  PR: L=FXOMPC
10:36:32.442925  Command (via relay server, from 127.0.0.1:65106): PS=0
10:36:32.469595  PS: 0
10:36:32.653046  T80190000  Read-Data   Boiler water temperature: 0.00
10:36:32.774526  B40192200  Read-Ack    Boiler water temperature: 34.00
10:36:33.707565  T10010A00  Write-Data  Control setpoint: 10.00
10:36:33.781146  BD0010A00  Write-Ack   Control setpoint: 10.00
10:36:34.656852  T00110000  Read-Data   Relative modulation level: 0.00
10:36:34.774642  BC0110000  Read-Ack    Relative modulation level: 0.00
10:36:35.684799  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:36:35.817470  B40000200  Read-Ack    Status: 00000010 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:36:36.647259  T80190000  Read-Data   Boiler water temperature: 0.00
10:36:36.759071  B40192200  Read-Ack    Boiler water temperature: 34.00
10:36:37.634903  T10010A00  Write-Data  Control setpoint: 10.00
10:36:37.749432  BD0010A00  Write-Ack   Control setpoint: 10.00
10:36:38.682645  T001B0000  Read-Data   Outside temperature: 0.00
10:36:38.792698  B401B0E00  Read-Ack    Outside temperature: 14.00
10:36:39.681385  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:36:39.819358  B40000200  Read-Ack    Status: 00000010 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:36:40.665697  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:36:40.865852  B40000200  Read-Ack    Status: 00000010 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:36:41.649966  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:36:41.790159  B40000200  Read-Ack    Status: 00000010 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:36:42.634498  T80190000  Read-Data   Boiler water temperature: 0.00
10:36:42.743361  B40192200  Read-Ack    Boiler water temperature: 34.00
10:36:43.665784  T10010A00  Write-Data  Control setpoint: 10.00
10:36:43.782104  BD0010A00  Write-Ack   Control setpoint: 10.00
10:36:44.666881  T00110000  Read-Data   Relative modulation level: 0.00
10:36:44.774497  BC0110000  Read-Ack    Relative modulation level: 0.00
10:36:45.650021  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:36:45.841813  B40000200  Read-Ack    Status: 00000010 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:36:46.637929  T80190000  Read-Data   Boiler water temperature: 0.00
10:36:46.758060  B40192200  Read-Ack    Boiler water temperature: 34.00
10:36:47.681197  T10010A00  Write-Data  Control setpoint: 10.00
10:36:47.790156  BD0010A00  Write-Ack   Control setpoint: 10.00
10:36:48.670234  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:36:48.837587  B40000200  Read-Ack    Status: 00000010 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:36:49.650296  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:36:49.836836  B40000200  Read-Ack    Status: 00000010 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:36:50.650330  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:36:50.819167  B40000200  Read-Ack    Status: 00000010 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:36:51.650695  T80000200  Read-Data   Status: 00000010 00000000
                               - CH enable: disabled (0)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:36:51.805126  B40000200  Read-Ack    Status: 00000010 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:36:52.666949  T80190000  Read-Data   Boiler water temperature: 0.00
10:36:52.792980  B40192200  Read-Ack    Boiler water temperature: 34.00
10:36:53.665665  T10010A00  Write-Data  Control setpoint: 10.00
10:36:53.798177  BD0010A00  Write-Ack   Control setpoint: 10.00
10:36:54.670299  T80380000  Read-Data   DHW setpoint: 0.00
10:36:54.763407  BE0380000  Data-Inv    DHW setpoint: 0.00
10:36:55.650120  T00390000  Read-Data   Max CH water setpoint: 0.00
10:36:55.764335  BF0390000  Unk-DataId  Max CH water setpoint: 0.00
10:36:55.771421  AC0395A00  Read-Ack    Max CH water setpoint: 90.00
10:36:56.634199  T80190000  Read-Data   Boiler water temperature: 0.00
10:36:56.749833  B40192200  Read-Ack    Boiler water temperature: 34.00
10:36:57.681217  T10010A00  Write-Data  Control setpoint: 10.00
10:36:57.780121  BD0010A00  Write-Ack   Control setpoint: 10.00
10:36:58.667031  T900E6400  Write-Data  Maximum relative modulation level: 100.00
10:36:58.766031  B500E6400  Write-Ack   Maximum relative modulation level: 100.00
10:36:59.663503  T00090000  Read-Data   Remote override room setpoint: 0.00
10:36:59.765218  BF0090000  Unk-DataId  Remote override room setpoint: 0.00
10:36:59.774099  A40091300  Read-Ack    Remote override room setpoint: 19.00
Although the override setpoint is set only once ("TT=xx") it is maintained without the thermostat is resetting to the daily program. However, the normal operation of the thermostat, with setpoint being adjusted on the thermostat, is not stable when the OTGW is attached ... very strange indeed!
** Maurice **
hvxl
Senior Member
Senior Member
Posts: 2031
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Chronotherm 4 defaults to program - WAF compromised!!

Post by hvxl »

I can't tell anything from this log. It starts too close to the point where you claim things go wrong and the PS=1 commands stop the output of the information I wanted to see. I need a clean log (no PS=1) starting at least several minutes before the point where the room setpoint reverts to the program.
Schelte
mo046
Member
Member
Posts: 186
Joined: Thu Nov 08, 2007 4:12 pm
Location: Netherlands

Re: Chronotherm 4 defaults to program - WAF compromised!!

Post by mo046 »

Meanwhile I've installed a Chronotherm Touch Modulation to replace the Chronotherm IV Modulation. Problem solved! The Touch seems to be more stable in combination with the OTGW.
** Maurice **
hvxl
Senior Member
Senior Member
Posts: 2031
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Chronotherm 4 defaults to program - WAF compromised!!

Post by hvxl »

Nonsense. I have developed the gateway with a Chronotherm Modulation and used it for years without any issue.

Unfortunately you never provided a usable log that would allow us to figure out what was really going on.

It's good that you found a solution that works for you, but please don't spread unfounded rumours that may give other users the wrong impression. The Chronotherm Modulation can work perfectly with the OTGW.
Schelte
mo046
Member
Member
Posts: 186
Joined: Thu Nov 08, 2007 4:12 pm
Location: Netherlands

Re: Chronotherm 4 defaults to program - WAF compromised!!

Post by mo046 »

Schelte, it's no nonsens but a fact that the new thermostat solved the problems I faced!

Let me be more precise on the issue.
First of all, since my last posting, I unfortunately had other issues on my mind than do logging and fiddling around with my OTGW and thermostat and send you the logs. So I had to put the OTGW aside. What I did notice meanwhile is that the screen on the thermostat slightly flickered in 1Hz frequency even without the OTGW so I assumed the power supply wasn't sufficient for my thermostat. The OTGW obviously triggered a problem with the themostat, so I concluded my thermostat is very sensitive to the power supply and it seems the OTGW is slightly lower on power output than my boiler. Nevertheless, assuming the OTGW was designed to meet the OpenTherm specs, it might be on the minimum side of the spec, or maybe due to component variations it could be off-spec. I just had to find a quick way to find out.
The easiest way for me to check whether my thermostat wasn't OK was to test another thermostat. That's what I did, and it solved my problem. Now with my new thermostat I don't experience any of the problems. So, the OTGW seems to be OK and the problem appeared to come from my old thermostat.

I'm sorry when I gave you or any other user the wrong impression that the OTGW is to be blamed, that was never my intention!
** Maurice **
hvxl
Senior Member
Senior Member
Posts: 2031
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Chronotherm 4 defaults to program - WAF compromised!!

Post by hvxl »

That's a different story. Your Chronotherm Touch works better than your Chronotherm Modulation. Could be that that one has a bad capacitor or other hardware fault. That doesn't mean that the Chronotherm Touch works better than the Chronotherm Modulation. That's all I wanted to make clear to other user who may stumble across your post in the future. It's likely also what you intended to say, but your remark came across to me as referring to the two thermostat types in general.
Schelte
Yugoos
Starting Member
Starting Member
Posts: 1
Joined: Sun Mar 20, 2016 2:23 am

Re: Chronotherm 4 defaults to program - WAF compromised!!

Post by Yugoos »

Hi,

I have similar issues with the same thermostat (chronotherm 4 modulation).
My goal is to use domoticz as a smart thermostat by setting temperature based on human presence and devices being online (lights and tv), but still using the heating curve algorithms from thermostat.

My setup:
Domoticz on raspberry pi2
Otgw connected via second raspberry pi b using ser2net
Intergas HR Compact boiler
Chronotherm 4 thermostat

The problems i have are:
Temporary temperature set by domoticz (tt=?) is cancelled by thermostat or overwritten by program
Screen flickers faintly too
An occasional error 03

My troubleshooting so far:
Remove program from thermostat by setting all timers to 0:00 16c
Testing different VR Values, current value 5

Setting the timers to 0:00 works pretty good so far, TT setting is not overwritten during the weekend yet.
The error3 i get is not reproducible so far but i guess it happens after setting TT

Any suggestions on troubleshooting this?
The capacitor suggested for fixing the screen flicker, is this on OTGW or thermostat?
Could the screenflicker be related to resetting the temp or the other way around?


Thanx,
Yuri
hvxl
Senior Member
Senior Member
Posts: 2031
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Chronotherm 4 defaults to program - WAF compromised!!

Post by hvxl »

The gateway is supposed to yield to the program in the thermostat if you set the override with the TT command. If that's not what you want, you should use the TC command. That's why there are two different commands.

The Chronotherm 4 modulation has to extract the power for its backlight from the opentherm signal. Unfortunately, that doesn't supply enough power and the thermostat doesn't take advantage of the opentherm Smart Power feature. To try to solve this problem, the thermostat charges a capacitor while the backlight is off, so it can use that charge when the backlight is wanted. The power on the line increases a bit when messages are exchanged (once per second). This assists the capacitor with the power for the backlight, which may be observable as a slight increase in brightness of the backlight.

An occasional error 03 is nothing to worry about. There is absolutely no reason to suspect that it happens after setting TT. The setpoint change is communicated in an Opentherm message like any other. The chance that an error occurs on that message is no higher or lower than on any other message.

So, to me it sounds like everything is working like it should.