I'm using OTGW since a while and lately I've rebuilt my CH so it uses only boiler pump.
I was able to set TSP (so boiler-parameter) of minimum pump-speed and I'd like to be able to change it remotely.
Here is the log when I go to Remeha thermostat and check the value of P028 field (TSP) which is 10 (x10 - 100% speed) and change to 7 (x10 - 70% pump speed).
I'd like to do just the same with OTGW.
Any help is appreciated, PM=10 doesn't provide any feedback in log.
A lot of minutes later, randomly, I can see in log that it says TSPs supported amount is 45.
Code: Select all
20:57:24.785240 T000B1C0A Read-Data TSP setting: 28 10
20:57:24.842692 BC00B1C0A Read-Ack TSP setting: 28 10
20:57:25.839763 T10012D00 Write-Data Control setpoint: 45.00
20:57:25.875013 BD0012D00 Write-Ack Control setpoint: 45.00
20:57:26.756896 T00110000 Read-Data Relative modulation level: 0.00
20:57:26.852193 BC0110000 Read-Ack Relative modulation level: 0.00
20:57:27.785434 T80190000 Read-Data Boiler water temperature: 0.00
20:57:27.856187 B401923E6 Read-Ack Boiler water temperature: 35.90
20:57:28.721632 T100B1C07 Write-Data TSP setting: 28 7
20:57:28.861630 BD00B1C07 Write-Ack TSP setting: 28 7
20:57:29.792804 T00090000 Read-Data Remote override room setpoint: 0.00
20:57:29.867578 BC0090000 Read-Ack Remote override room setpoint: 0.00
20:57:29.888734 AC0091680 Read-Ack Remote override room setpoint: 22.50
20:57:30.755353 T800B1C07 Read-Data TSP setting: 28 7
20:57:30.959664 B400B1C07 Read-Ack TSP setting: 28 7