Dear Schelte,
I just upgraded my device with 4.2.8 firmware with this file: http://otgw.tclcode.com/download/gateway.hex via OTMonitor Web Interface (http://XX.XX.XX.XX:8081/upgrade.html
The upgrade was performed without any problem, so I stopped otmonitor.service, downloaded new version of otmonitor to my raspberry pi, added +x attribute and started service.
Unfortunately since upgrade to 4.2.8 my OTGW is not working = no messages in otmonitor except configuration changes made via webconfig.
I tried to switch on/off my boiler and otgw, but no success.
Did I missed something during update?
Is 4.2.5 version available for downgrade?
Thank you.
I just upgraded my device with 4.2.8 firmware with this file: http://otgw.tclcode.com/download/gateway.hex via OTMonitor Web Interface (http://XX.XX.XX.XX:8081/upgrade.html
The upgrade was performed without any problem, so I stopped otmonitor.service, downloaded new version of otmonitor to my raspberry pi, added +x attribute and started service.
Unfortunately since upgrade to 4.2.8 my OTGW is not working = no messages in otmonitor except configuration changes made via webconfig.
I tried to switch on/off my boiler and otgw, but no success.
Did I missed something during update?
Is 4.2.5 version available for downgrade?
Thank you.
Re: OpenTherm Gateway 4.2.8
Strange. I have been using 4.2.8 myself for several days without any issue.
The following old versions are available: Somehow I lost 4.2.4
The following old versions are available: Somehow I lost 4.2.4
Schelte
Re: OpenTherm Gateway 4.2.8
Thank you very much,
I appreciate such a quick help.
Downgrade to 4.2.5 firmware helped, then I tried 4.2.6 a 4.2.7 and both worked.
Unfortunately 4.2.8 not working.
I don't know if there is any HW limitation so for now I just switched back to last working firmware and will wait if anybody report same behaviour.
Thnak you.
I appreciate such a quick help.
Downgrade to 4.2.5 firmware helped, then I tried 4.2.6 a 4.2.7 and both worked.
Unfortunately 4.2.8 not working.
Code: Select all
22:15:27.695791 OpenTherm Gateway 4.2.5
22:15:27.705456 Command: SC=22:15/7
22:15:27.733620 SC: 22:15/7
22:15:28.161527 T001B0000 Read-Data Outside temperature: 0.00
22:15:28.532564 B601B0000 Data-Inv Outside temperature: 0.00
22:15:29.153498 T00300000 Read-Data DHW setpoint boundaries: 0 0
22:15:29.521473 BC030410A Read-Ack DHW setpoint boundaries: 65 10
22:15:30.142650 T00000000 Read-Data Status: 00000000 00000000
22:15:30.510649 BC0000000 Read-Ack Status: 00000000 00000000
22:15:31.132561 T10380500 Write-Data DHW setpoint: 5.00
22:15:31.499466 BD0380500 Write-Ack DHW setpoint: 5.00
22:15:32.121529 T00390000 Read-Data Max CH water setpoint: 0.00
22:15:32.489428 BC0395900 Read-Ack Max CH water setpoint: 89.00
22:15:33.160647 T80800000 Read-Data Message ID 128: 0
22:15:33.478498 BE0800000 Data-Inv Message ID 128: 0
22:15:34.149428 T90810500 Write-Data Message ID 129: 1280
22:15:34.466362 B50810500 Write-Ack Message ID 129: 1280
22:15:35.138412 T10823D50 Write-Data Message ID 130: 15696
22:15:35.456416 BD0823D50 Write-Ack Message ID 130: 15696
22:15:36.127531 T00000000 Read-Data Status: 00000000 00000000
22:15:36.445552 BC0000000 Read-Ack Status: 00000000 00000000
22:15:37.117369 T90010E00 Write-Data Control setpoint: 14.00
22:15:37.434318 B50010E00 Write-Ack Control setpoint: 14.00
22:15:38.106390 T20080000 Inv-Data Control setpoint 2: 0.00
22:15:38.423295 BE0080000 Data-Inv Control setpoint 2: 0.00
22:15:39.145277 T10380500 Write-Data DHW setpoint: 5.00
22:15:39.412300 BD0380500 Write-Ack DHW setpoint: 5.00
22:15:40.134228 T80200000 Read-Data DHW2 temperature: 0.00
22:15:40.402240 BE0200000 Data-Inv DHW2 temperature: 0.00
22:15:41.124330 T801A0000 Read-Data DHW temperature: 0.00
22:15:41.390226 B401A3E70 Read-Ack DHW temperature: 62.44
22:15:42.112307 T00000000 Read-Data Status: 00000000 00000000
22:15:42.380254 BC0000000 Read-Ack Status: 00000000 00000000
22:15:43.102217 T001B0000 Read-Data Outside temperature: 0.00
22:15:43.369176 B601B0000 Data-Inv Outside temperature: 0.00
22:15:44.090206 T80190000 Read-Data Boiler water temperature: 0.00
22:15:44.358153 B401913D0 Read-Ack Boiler water temperature: 19.81
22:15:45.130177 T801C0000 Read-Data Return water temperature: 0.00
22:15:45.412194 B401C1304 Read-Ack Return water temperature: 19.02
22:15:46.083192 T801F0000 Read-Data Flow temperature CH2: 0.00
22:15:46.401123 BE01F0000 Data-Inv Flow temperature CH2: 0.00
22:15:47.123126 T00110000 Read-Data Relative modulation level: 0.00
22:15:47.390094 BC0110000 Read-Ack Relative modulation level: 0.00
22:15:48.112167 T00000000 Read-Data Status: 00000000 00000000
22:15:48.379080 BC0000000 Read-Ack Status: 00000000 00000000
22:15:49.101165 T80130000 Read-Data DHW flow rate: 0.00
22:15:49.368095 B70130000 Unk-DataId DHW flow rate: 0.00
22:15:50.090087 T001D0000 Read-Data Solar storage temperature: 0.00
22:15:50.358048 BF01D0000 Unk-DataId Solar storage temperature: 0.00
22:15:51.080175 T001E0000 Read-Data Solar collector temperature: 0.00
22:15:51.347062 B601E0000 Data-Inv Solar collector temperature: 0.00
22:15:52.069032 T00210000 Read-Data Exhaust temperature: 0
22:15:52.336025 BC0210017 Read-Ack Exhaust temperature: 23
22:15:53.108029 T90810500 Write-Data Message ID 129: 1280
22:15:53.458006 B50810500 Write-Ack Message ID 129: 1280
22:15:54.079047 T00000000 Read-Data Status: 00000000 00000000
22:15:54.448079 BC0000000 Read-Ack Status: 00000000 00000000
22:15:55.068999 T90100E00 Write-Data Room setpoint: 14.00
22:15:55.437000 B50100E00 Write-Ack Room setpoint: 14.00
22:15:56.107961 T90170000 Write-Data Room Setpoint CH2: 0.00
22:15:56.425975 B50170000 Write-Ack Room Setpoint CH2: 0.00
22:15:57.096973 T90180FE4 Write-Data Room temperature: 15.89
22:15:57.414960 B50180FE4 Write-Ack Room temperature: 15.89
22:15:58.086944 T80800000 Read-Data Message ID 128: 0
22:15:58.428794 BE0800000 Data-Inv Message ID 128: 0
22:15:59.075888 T10823D50 Write-Data Message ID 130: 15696
22:15:59.392791 BD0823D50 Write-Ack Message ID 130: 15696
22:16:00.001494 Command: SC=22:16/7
22:16:00.029762 SC: 22:16/7
22:16:00.066723 T90020004 Write-Data Master configuration: 00000000 4
22:16:00.481544 B50020004 Write-Ack Master configuration: 00000000 4
22:16:01.054044 T00000000 Read-Data Status: 00000000 00000000
22:16:01.371926 BC0000000 Read-Ack Status: 00000000 00000000
22:16:02.042918 T90010E00 Write-Data Control setpoint: 14.00
22:16:02.359888 B50010E00 Write-Ack Control setpoint: 14.00
22:16:03.081867 T20080000 Inv-Data Control setpoint 2: 0.00
22:16:03.349840 BE0080000 Data-Inv Control setpoint 2: 0.00
22:16:04.071966 T10380500 Write-Data DHW setpoint: 5.00
22:16:04.338862 BD0380500 Write-Ack DHW setpoint: 5.00
22:16:05.060839 T80200000 Read-Data DHW2 temperature: 0.00
22:16:05.327818 BE0200000 Data-Inv DHW2 temperature: 0.00
22:16:06.049750 T801A0000 Read-Data DHW temperature: 0.00
22:16:06.316694 B401A3E70 Read-Ack DHW temperature: 62.44
22:16:07.038702 T00000000 Read-Data Status: 00000000 00000000
22:16:07.306655 BC0000000 Read-Ack Status: 00000000 00000000
22:16:08.027841 T001B0000 Read-Data Outside temperature: 0.00
22:16:08.295819 B601B0000 Data-Inv Outside temperature: 0.00
22:16:09.067793 T80190000 Read-Data Boiler water temperature: 0.00
22:16:09.348778 B401913D0 Read-Ack Boiler water temperature: 19.81
22:16:10.070818 T801C0000 Read-Data Return water temperature: 0.00
22:16:10.337761 B401C1304 Read-Ack Return water temperature: 19.02
22:16:11.059778 T801F0000 Read-Data Flow temperature CH2: 0.00
22:16:11.327769 BE01F0000 Data-Inv Flow temperature CH2: 0.00
22:16:12.049743 T00110000 Read-Data Relative modulation level: 0.00
22:16:12.315721 BC0110000 Read-Ack Relative modulation level: 0.00
22:16:13.037709 T00000000 Read-Data Status: 00000000 00000000
22:16:13.305697 BC0000000 Read-Ack Status: 00000000 00000000
22:16:14.027731 T80130000 Read-Data DHW flow rate: 0.00
22:16:14.294714 B70130000 Unk-DataId DHW flow rate: 0.00
22:16:15.016593 T001D0000 Read-Data Solar storage temperature: 0.00
22:16:15.283500 BF01D0000 Unk-DataId Solar storage temperature: 0.00
22:16:16.055464 T001E0000 Read-Data Solar collector temperature: 0.00
22:16:16.406441 B601E0000 Data-Inv Solar collector temperature: 0.00
22:16:17.027707 T00210000 Read-Data Exhaust temperature: 0
22:16:17.395628 BC0210017 Read-Ack Exhaust temperature: 23
22:16:18.016633 T90810500 Write-Data Message ID 129: 1280
22:16:18.384584 B50810500 Write-Ack Message ID 129: 1280
22:16:19.005570 T00000000 Read-Data Status: 00000000 00000000
22:16:19.373542 BC0000000 Read-Ack Status: 00000000 00000000
22:16:20.045624 T90100E00 Write-Data Room setpoint: 14.00
22:16:20.362579 B50100E00 Write-Ack Room setpoint: 14.00
22:16:21.034572 T90170000 Write-Data Room Setpoint CH2: 0.00
22:16:21.351535 B50170000 Write-Ack Room Setpoint CH2: 0.00
22:16:22.023546 T90180FE4 Write-Data Room temperature: 15.89
22:16:22.340500 B50180FE4 Write-Ack Room temperature: 15.89
22:16:23.012520 T80800000 Read-Data Message ID 128: 0
22:16:23.330481 BE0800000 Data-Inv Message ID 128: 0
22:16:24.002484 T10823D50 Write-Data Message ID 130: 15696
22:16:24.319452 BD0823D50 Write-Ack Message ID 130: 15696
22:16:24.990437 T00030000 Read-Data Slave configuration: 00000000 0
22:16:25.308441 B40030904 Read-Ack Slave configuration: 00001001 4
22:16:26.030524 T00000000 Read-Data Status: 00000000 00000000
22:16:26.297440 BC0000000 Read-Ack Status: 00000000 00000000
22:16:27.019433 T90010E00 Write-Data Control setpoint: 14.00
22:16:27.286427 B50010E00 Write-Ack Control setpoint: 14.00
22:16:28.008414 T20080000 Inv-Data Control setpoint 2: 0.00
22:16:28.275379 BE0080000 Data-Inv Control setpoint 2: 0.00
22:16:28.998365 T10380500 Write-Data DHW setpoint: 5.00
22:16:29.265369 BD0380500 Write-Ack DHW setpoint: 5.00
22:16:29.987484 T80200000 Read-Data DHW2 temperature: 0.00
22:16:30.486433 BE0200000 Data-Inv DHW2 temperature: 0.00
22:16:30.976500 T801A0000 Read-Data DHW temperature: 0.00
22:16:31.243392 B401A3E70 Read-Ack DHW temperature: 62.44
22:16:32.015364 T00000000 Read-Data Status: 00000000 00000000
22:16:32.297328 BC0000000 Read-Ack Status: 00000000 00000000
22:16:32.968434 T001B0000 Read-Data Outside temperature: 0.00
22:16:33.285330 B601B0000 Data-Inv Outside temperature: 0.00
22:16:34.007337 T80190000 Read-Data Boiler water temperature: 0.00
22:16:34.274290 B401913A8 Read-Ack Boiler water temperature: 19.66
22:16:34.996398 T801C0000 Read-Data Return water temperature: 0.00
22:16:35.264343 B401C1304 Read-Ack Return water temperature: 19.02
22:16:35.986357 T801F0000 Read-Data Flow temperature CH2: 0.00
22:16:36.253281 BE01F0000 Data-Inv Flow temperature CH2: 0.00
22:16:36.975239 T00110000 Read-Data Relative modulation level: 0.00
22:16:37.242333 BC0110000 Read-Ack Relative modulation level: 0.00
22:16:37.964435 T1014F610 Write-Data Day of week and time of day: Sun 22:16
22:16:38.231263 BD014F610 Write-Ack Day of week and time of day: Sun 22:16
22:16:38.953415 T10150C1B Write-Data Date: Dec 27
22:16:39.220309 BD0150C1B Write-Ack Date: Dec 27
22:16:39.992459 T901607E4 Write-Data Year: 2020
22:16:40.342230 B501607E4 Write-Ack Year: 2020
22:16:40.964226 T00000000 Read-Data Status: 00000000 00000000
22:16:41.332195 BC0000000 Read-Ack Status: 00000000 00000000
22:16:41.954173 T80130000 Read-Data DHW flow rate: 0.00
22:16:42.321162 B70130000 Unk-DataId DHW flow rate: 0.00
22:16:42.943190 T001D0000 Read-Data Solar storage temperature: 0.00
22:16:43.311127 BF01D0000 Unk-DataId Solar storage temperature: 0.00
22:16:43.982117 T001E0000 Read-Data Solar collector temperature: 0.00
22:16:44.300076 B601E0000 Data-Inv Solar collector temperature: 0.00
22:16:44.989147 T00210000 Read-Data Exhaust temperature: 0
22:16:45.289016 BC0210017 Read-Ack Exhaust temperature: 23
22:16:45.960004 T90810500 Write-Data Message ID 129: 1280
22:16:46.277927 B50810500 Write-Ack Message ID 129: 1280
22:16:46.949915 T00000000 Read-Data Status: 00000000 00000000
22:16:47.267074 BC0000000 Read-Ack Status: 00000000 00000000
22:16:47.939086 T90100E00 Write-Data Room setpoint: 14.00
22:16:48.256060 B50100E00 Write-Ack Room setpoint: 14.00
22:16:48.928077 T90170000 Write-Data Room Setpoint CH2: 0.00
22:16:49.245028 B50170000 Write-Ack Room Setpoint CH2: 0.00
22:16:49.967040 T90180FE4 Write-Data Room temperature: 15.89
22:16:50.234033 B50180FE4 Write-Ack Room temperature: 15.89
22:16:50.956041 T80800000 Read-Data Message ID 128: 0
22:16:51.223987 BE0800000 Data-Inv Message ID 128: 0
22:16:51.945973 T10823D50 Write-Data Message ID 130: 15696
22:16:52.212963 BD0823D50 Write-Ack Message ID 130: 15696
22:16:52.933944 T00060000 Read-Data Remote parameter flags: 00000000 00000000
22:16:53.201935 BC0060707 Read-Ack Remote parameter flags: 00000111 00000111
22:16:53.923971 T00000000 Read-Data Status: 00000000 00000000
22:16:54.190940 BC0000000 Read-Ack Status: 00000000 00000000
22:16:54.913040 T90010E00 Write-Data Control setpoint: 14.00
22:16:55.179958 B50010E00 Write-Ack Control setpoint: 14.00
22:16:56.142341 T20080000 Inv-Data Control setpoint 2: 0.00
22:16:56.233850 BE0080000 Data-Inv Control setpoint 2: 0.00
22:16:56.904859 T10380500 Write-Data DHW setpoint: 5.00
22:16:57.222765 BD0380500 Write-Ack DHW setpoint: 5.00
22:16:57.944771 T80200000 Read-Data DHW2 temperature: 0.00
22:16:58.211914 BE0200000 Data-Inv DHW2 temperature: 0.00
22:17:00.001953 Command: SC=22:17/7
22:17:26.815204 OpenTherm Gateway 4.2.6
22:17:26.816469 Command: SC=22:17/7
22:17:26.856414 SC: 22:17/7
22:17:26.857395 T80190000 Read-Data Boiler water temperature: 0.00
22:17:27.227423 B401913A8 Read-Ack Boiler water temperature: 19.66
22:17:27.849386 T801C0000 Read-Data Return water temperature: 0.00
22:17:28.216436 B401C12D8 Read-Ack Return water temperature: 18.84
22:17:28.838395 T801F0000 Read-Data Flow temperature CH2: 0.00
22:17:29.206381 BE01F0000 Data-Inv Flow temperature CH2: 0.00
22:17:29.828475 T00110000 Read-Data Relative modulation level: 0.00
22:17:30.460554 BC0110000 Read-Ack Relative modulation level: 0.00
22:17:30.867430 T00000000 Read-Data Status: 00000000 00000000
22:17:31.184424 BC0000000 Read-Ack Status: 00000000 00000000
22:17:31.856451 T80130000 Read-Data DHW flow rate: 0.00
22:17:32.173321 B70130000 Unk-DataId DHW flow rate: 0.00
22:17:32.845285 T001D0000 Read-Data Solar storage temperature: 0.00
22:17:33.163289 BF01D0000 Unk-DataId Solar storage temperature: 0.00
22:17:33.834318 T001E0000 Read-Data Solar collector temperature: 0.00
22:17:34.152297 B601E0000 Data-Inv Solar collector temperature: 0.00
22:17:34.823234 T00210000 Read-Data Exhaust temperature: 0
22:17:35.141333 BC0210017 Read-Ack Exhaust temperature: 23
22:17:35.812214 T90810500 Write-Data Message ID 129: 1280
22:17:36.130118 B50810500 Write-Ack Message ID 129: 1280
22:17:36.852070 T00000000 Read-Data Status: 00000000 00000000
22:17:37.119045 BC0000000 Read-Ack Status: 00000000 00000000
22:17:37.841244 T90100E00 Write-Data Room setpoint: 14.00
22:17:38.108307 B50100E00 Write-Ack Room setpoint: 14.00
22:17:38.830208 T90170000 Write-Data Room Setpoint CH2: 0.00
22:17:39.097187 B50170000 Write-Ack Room Setpoint CH2: 0.00
22:17:39.842867 T10180FDC Write-Data Room temperature: 15.86
22:17:40.086108 BD0180FDC Write-Ack Room temperature: 15.86
22:17:40.808057 T80800000 Read-Data Message ID 128: 0
22:17:41.076022 BE0800000 Data-Inv Message ID 128: 0
22:17:41.798165 T10823D50 Write-Data Message ID 130: 15696
22:17:42.065275 BD0823D50 Write-Ack Message ID 130: 15696
22:17:42.837352 T00120000 Read-Data CH water pressure: 0.00
22:17:43.118177 B40120181 Read-Ack CH water pressure: 1.50
22:17:43.790147 T00000000 Read-Data Status: 00000000 00000000
22:17:44.108143 BC0000000 Read-Ack Status: 00000000 00000000
22:17:44.830084 T90010E00 Write-Data Control setpoint: 14.00
22:17:45.097099 B50010E00 Write-Ack Control setpoint: 14.00
22:17:45.818113 T20080000 Inv-Data Control setpoint 2: 0.00
22:17:46.086086 BE0080000 Data-Inv Control setpoint 2: 0.00
22:17:46.808096 T10380500 Write-Data DHW setpoint: 5.00
22:17:47.075091 BD0380500 Write-Ack DHW setpoint: 5.00
22:17:47.797041 T80200000 Read-Data DHW2 temperature: 0.00
22:17:48.064163 BE0200000 Data-Inv DHW2 temperature: 0.00
22:17:48.786050 T801A0000 Read-Data DHW temperature: 0.00
22:17:49.053038 B401A3E70 Read-Ack DHW temperature: 62.44
22:17:49.775031 T00000000 Read-Data Status: 00000000 00000000
22:17:50.043007 BC0000000 Read-Ack Status: 00000000 00000000
22:17:50.815012 T001B0000 Read-Data Outside temperature: 0.00
22:17:51.165039 B601B0000 Data-Inv Outside temperature: 0.00
22:17:51.785980 T80190000 Read-Data Boiler water temperature: 0.00
22:17:52.153954 B401913A8 Read-Ack Boiler water temperature: 19.66
22:17:52.774929 T801C0000 Read-Data Return water temperature: 0.00
22:17:53.142937 B401C12D8 Read-Ack Return water temperature: 18.84
22:17:53.764942 T801F0000 Read-Data Flow temperature CH2: 0.00
22:17:54.132946 BE01F0000 Data-Inv Flow temperature CH2: 0.00
22:17:54.803812 T00110000 Read-Data Relative modulation level: 0.00
22:17:55.121740 BC0110000 Read-Ack Relative modulation level: 0.00
22:17:55.792708 T00000000 Read-Data Status: 00000000 00000000
22:17:56.110678 BC0000000 Read-Ack Status: 00000000 00000000
22:17:56.782828 T80130000 Read-Data DHW flow rate: 0.00
22:17:57.099811 B70130000 Unk-DataId DHW flow rate: 0.00
22:17:57.771839 T001D0000 Read-Data Solar storage temperature: 0.00
22:17:58.088790 BF01D0000 Unk-DataId Solar storage temperature: 0.00
22:17:58.760778 T001E0000 Read-Data Solar collector temperature: 0.00
22:17:59.077765 B601E0000 Data-Inv Solar collector temperature: 0.00
22:17:59.749769 T00210000 Read-Data Exhaust temperature: 0
22:18:00.001702 Command: SC=22:18/7
22:18:00.029768 SC: 22:18/7
22:18:00.087197 BC0210017 Read-Ack Exhaust temperature: 23
22:18:00.788885 T90810500 Write-Data Message ID 129: 1280
22:18:01.055780 B50810500 Write-Ack Message ID 129: 1280
22:18:01.777871 T00000000 Read-Data Status: 00000000 00000000
22:18:02.045751 BC0000000 Read-Ack Status: 00000000 00000000
22:18:02.767760 T90100E00 Write-Data Room setpoint: 14.00
22:18:03.220916 B50100E00 Write-Ack Room setpoint: 14.00
22:18:03.755680 T90170000 Write-Data Room Setpoint CH2: 0.00
22:18:04.023594 B50170000 Write-Ack Room Setpoint CH2: 0.00
22:18:04.745623 T90180FD8 Write-Data Room temperature: 15.84
22:18:05.012583 B50180FD8 Write-Ack Room temperature: 15.84
22:18:05.734759 T80800000 Read-Data Message ID 128: 0
22:18:06.001688 BE0800000 Data-Inv Message ID 128: 0
22:18:34.743999 OpenTherm Gateway 4.2.7
22:18:34.745290 Command: SC=22:18/7
22:18:34.773200 SC: 22:18/7
22:18:34.949192 BC0000000 Read-Ack Status: 00000000 00000000
22:18:35.671193 T90010E00 Write-Data Control setpoint: 14.00
22:18:35.938164 B50010E00 Write-Ack Control setpoint: 14.00
22:18:36.660219 T20080000 Inv-Data Control setpoint 2: 0.00
22:18:36.927135 BE0080000 Data-Inv Control setpoint 2: 0.00
22:18:37.649143 T10380500 Write-Data DHW setpoint: 5.00
22:18:37.916202 BD0380500 Write-Ack DHW setpoint: 5.00
22:18:38.688189 T80200000 Read-Data DHW2 temperature: 0.00
22:18:39.039105 BE0200000 Data-Inv DHW2 temperature: 0.00
22:18:39.660165 T801A0000 Read-Data DHW temperature: 0.00
22:18:40.028072 B401A3E70 Read-Ack DHW temperature: 62.44
22:18:40.649190 T00000000 Read-Data Status: 00000000 00000000
22:18:41.017089 BC0000000 Read-Ack Status: 00000000 00000000
22:18:41.639116 T001B0000 Read-Data Outside temperature: 0.00
22:18:42.006057 B601B0000 Data-Inv Outside temperature: 0.00
22:18:42.678079 T80190000 Read-Data Boiler water temperature: 0.00
22:18:42.995031 B401913A8 Read-Ack Boiler water temperature: 19.66
22:18:43.667081 T801C0000 Read-Data Return water temperature: 0.00
22:18:43.984030 B401C12D8 Read-Ack Return water temperature: 18.84
22:18:44.656282 T801F0000 Read-Data Flow temperature CH2: 0.00
22:18:44.974039 BE01F0000 Data-Inv Flow temperature CH2: 0.00
22:18:45.645212 T00110000 Read-Data Relative modulation level: 0.00
22:18:45.963026 BC0110000 Read-Ack Relative modulation level: 0.00
22:18:46.635014 T00000000 Read-Data Status: 00000000 00000000
22:18:46.952040 BC0000000 Read-Ack Status: 00000000 00000000
22:18:47.623029 T80130000 Read-Data DHW flow rate: 0.00
22:18:47.940949 B70130000 Unk-DataId DHW flow rate: 0.00
22:18:48.662960 T001D0000 Read-Data Solar storage temperature: 0.00
22:18:48.929923 BF01D0000 Unk-DataId Solar storage temperature: 0.00
22:18:49.651925 T001E0000 Read-Data Solar collector temperature: 0.00
22:18:49.919885 B601E0000 Data-Inv Solar collector temperature: 0.00
22:18:50.641917 T00210000 Read-Data Exhaust temperature: 0
22:18:50.908864 BC0210017 Read-Ack Exhaust temperature: 23
22:18:51.630868 T90810500 Write-Data Message ID 129: 1280
22:18:51.897882 B50810500 Write-Ack Message ID 129: 1280
22:18:52.618846 T00000000 Read-Data Status: 00000000 00000000
22:18:52.886806 BC0000000 Read-Ack Status: 00000000 00000000
22:18:53.608927 T90100E00 Write-Data Room setpoint: 14.00
22:18:53.875834 B50100E00 Write-Ack Room setpoint: 14.00
22:18:54.647895 T90170000 Write-Data Room Setpoint CH2: 0.00
22:18:54.928728 B50170000 Write-Ack Room Setpoint CH2: 0.00
22:18:55.650678 T90180FCC Write-Data Room temperature: 15.80
22:18:55.917680 B50180FCC Write-Ack Room temperature: 15.80
22:18:56.639883 T80800000 Read-Data Message ID 128: 0
22:18:56.907821 BE0800000 Data-Inv Message ID 128: 0
22:18:57.629837 T10823D50 Write-Data Message ID 130: 15696
22:18:57.895785 BD0823D50 Write-Ack Message ID 130: 15696
22:18:58.618775 T907E0101 Write-Data Master product version: 1 1
22:18:59.083769 B507E0101 Write-Ack Master product version: 1 1
22:18:59.603848 T00000000 Read-Data Status: 00000000 00000000
22:18:59.874788 BC0000000 Read-Ack Status: 00000000 00000000
22:19:00.001556 Command: SC=22:19/7
22:19:00.029753 SC: 22:19/7
22:19:00.596877 T90010E00 Write-Data Control setpoint: 14.00
22:19:00.864839 B50010E00 Write-Ack Control setpoint: 14.00
22:19:01.636801 T20080000 Inv-Data Control setpoint 2: 0.00
22:19:01.986745 BE0080000 Data-Inv Control setpoint 2: 0.00
22:19:02.607688 T10380500 Write-Data DHW setpoint: 5.00
22:19:02.975682 BD0380500 Write-Ack DHW setpoint: 5.00
22:19:03.596663 T80200000 Read-Data DHW2 temperature: 0.00
22:19:03.964678 BE0200000 Data-Inv DHW2 temperature: 0.00
22:19:04.586660 T801A0000 Read-Data DHW temperature: 0.00
22:19:04.969200 B401A3E70 Read-Ack DHW temperature: 62.44
22:19:05.625581 T00000000 Read-Data Status: 00000000 00000000
22:19:05.942485 BC0000000 Read-Ack Status: 00000000 00000000
22:19:06.614515 T001B0000 Read-Data Outside temperature: 0.00
22:19:06.932501 B601B0000 Data-Inv Outside temperature: 0.00
22:19:07.603615 T80190000 Read-Data Boiler water temperature: 0.00
22:19:07.921599 B4019137C Read-Ack Boiler water temperature: 19.48
22:19:08.593627 T801C0000 Read-Data Return water temperature: 0.00
22:19:08.910583 B401C12D8 Read-Ack Return water temperature: 18.84
22:19:09.582621 T801F0000 Read-Data Flow temperature CH2: 0.00
22:19:09.899618 BE01F0000 Data-Inv Flow temperature CH2: 0.00
22:19:10.571557 T00110000 Read-Data Relative modulation level: 0.00
22:19:10.889542 BC0110000 Read-Ack Relative modulation level: 0.00
22:19:11.611452 T00000000 Read-Data Status: 00000000 00000000
22:19:11.878390 BC0000000 Read-Ack Status: 00000000 00000000
22:19:12.599380 T80130000 Read-Data DHW flow rate: 0.00
22:19:12.867373 B70130000 Unk-DataId DHW flow rate: 0.00
22:19:13.589566 T001D0000 Read-Data Solar storage temperature: 0.00
22:19:13.856521 BF01D0000 Unk-DataId Solar storage temperature: 0.00
22:19:14.578495 T001E0000 Read-Data Solar collector temperature: 0.00
22:19:14.845476 B601E0000 Data-Inv Solar collector temperature: 0.00
22:19:15.567455 T00210000 Read-Data Exhaust temperature: 0
22:19:15.834467 B40210016 Read-Ack Exhaust temperature: 22
22:19:16.556483 T90810500 Write-Data Message ID 129: 1280
22:19:16.823430 B50810500 Write-Ack Message ID 129: 1280
22:19:17.595448 T00000000 Read-Data Status: 00000000 00000000
22:19:17.877413 BC0000000 Read-Ack Status: 00000000 00000000
22:19:18.549405 T90100E00 Write-Data Room setpoint: 14.00
22:19:18.866407 B50100E00 Write-Ack Room setpoint: 14.00
22:19:19.588433 T90170000 Write-Data Room Setpoint CH2: 0.00
22:19:19.855451 B50170000 Write-Ack Room Setpoint CH2: 0.00
22:19:20.577417 T10180FC8 Write-Data Room temperature: 15.78
22:19:20.844450 BD0180FC8 Write-Ack Room temperature: 15.78
22:19:21.566378 T80800000 Read-Data Message ID 128: 0
22:19:21.834393 BE0800000 Data-Inv Message ID 128: 0
22:19:22.555342 T10823D50 Write-Data Message ID 130: 15696
22:19:22.822366 BD0823D50 Write-Ack Message ID 130: 15696
22:19:23.544384 T807F0000 Read-Data Slave product version: 0 0
22:19:23.812375 B407F6401 Read-Ack Slave product version: 100 1
22:19:24.534305 T00000000 Read-Data Status: 00000000 00000000
22:19:24.801387 BC0000000 Read-Ack Status: 00000000 00000000
22:19:25.573257 T90010E00 Write-Data Control setpoint: 14.00
22:19:25.923149 B50010E00 Write-Ack Control setpoint: 14.00
22:19:26.544089 T20080000 Inv-Data Control setpoint 2: 0.00
22:19:26.913237 BE0080000 Data-Inv Control setpoint 2: 0.00
22:19:27.534216 T10380500 Write-Data DHW setpoint: 5.00
22:19:27.902223 BD0380500 Write-Ack DHW setpoint: 5.00
22:19:28.523194 T80200000 Read-Data DHW2 temperature: 0.00
22:19:28.891182 BE0200000 Data-Inv DHW2 temperature: 0.00
22:19:29.563165 T801A0000 Read-Data DHW temperature: 0.00
22:19:29.880237 B401A3E70 Read-Ack DHW temperature: 62.44
22:19:30.551295 T00000000 Read-Data Status: 00000000 00000000
22:19:30.869256 BC0000000 Read-Ack Status: 00000000 00000000
22:19:31.541182 T001B0000 Read-Data Outside temperature: 0.00
22:19:31.859142 B601B0000 Data-Inv Outside temperature: 0.00
22:19:32.530120 T80190000 Read-Data Boiler water temperature: 0.00
22:19:32.847192 B4019137C Read-Ack Boiler water temperature: 19.48
22:19:33.519136 T801C0000 Read-Data Return water temperature: 0.00
22:19:33.837137 B401C12D8 Read-Ack Return water temperature: 18.84
22:19:34.508279 T801F0000 Read-Data Flow temperature CH2: 0.00
22:19:34.826095 BE01F0000 Data-Inv Flow temperature CH2: 0.00
22:19:35.548077 T00110000 Read-Data Relative modulation level: 0.00
22:19:35.815113 BC0110000 Read-Ack Relative modulation level: 0.00
22:19:36.537074 T00000000 Read-Data Status: 00000000 00000000
22:19:36.804064 BC0000000 Read-Ack Status: 00000000 00000000
22:19:37.526054 T80130000 Read-Data DHW flow rate: 0.00
22:19:37.793050 B70130000 Unk-DataId DHW flow rate: 0.00
22:19:38.515040 T001D0000 Read-Data Solar storage temperature: 0.00
22:19:38.782006 BF01D0000 Unk-DataId Solar storage temperature: 0.00
22:19:39.504026 T001E0000 Read-Data Solar collector temperature: 0.00
22:19:39.771997 B601E0000 Data-Inv Solar collector temperature: 0.00
22:19:40.492993 T00210000 Read-Data Exhaust temperature: 0
22:19:40.760016 B40210016 Read-Ack Exhaust temperature: 22
22:19:41.532958 T90810500 Write-Data Message ID 129: 1280
22:19:41.813981 B50810500 Write-Ack Message ID 129: 1280
22:19:42.485929 T00000000 Read-Data Status: 00000000 00000000
22:19:42.802932 BC0000000 Read-Ack Status: 00000000 00000000
22:19:43.524933 T90100E00 Write-Data Room setpoint: 14.00
22:19:43.791919 B50100E00 Write-Ack Room setpoint: 14.00
22:19:44.513904 T90170000 Write-Data Room Setpoint CH2: 0.00
22:19:44.781895 B50170000 Write-Ack Room Setpoint CH2: 0.00
22:19:45.503882 T10180FC8 Write-Data Room temperature: 15.78
22:19:45.772089 BD0180FC8 Write-Ack Room temperature: 15.78
22:19:46.492959 T80800000 Read-Data Message ID 128: 0
22:19:46.759911 BE0800000 Data-Inv Message ID 128: 0
22:19:47.481900 T10823D50 Write-Data Message ID 130: 15696
22:19:47.749104 BD0823D50 Write-Ack Message ID 130: 15696
22:19:48.471105 T00000000 Read-Data Status: 00000000 00000000
22:19:48.737893 BC0000000 Read-Ack Status: 00000000 00000000
22:19:49.509915 T90010E00 Write-Data Control setpoint: 14.00
22:19:49.860883 B50010E00 Write-Ack Control setpoint: 14.00
22:19:50.481858 T20080000 Inv-Data Control setpoint 2: 0.00
22:19:50.849927 BE0080000 Data-Inv Control setpoint 2: 0.00
22:19:51.471831 T10380500 Write-Data DHW setpoint: 5.00
22:19:51.838867 BD0380500 Write-Ack DHW setpoint: 5.00
22:19:52.459878 T80200000 Read-Data DHW2 temperature: 0.00
22:19:52.827791 BE0200000 Data-Inv DHW2 temperature: 0.00
22:19:53.499768 T801A0000 Read-Data DHW temperature: 0.00
22:19:53.816764 B401A3E70 Read-Ack DHW temperature: 62.44
22:19:54.488739 T00000000 Read-Data Status: 00000000 00000000
22:19:54.806721 BC0000000 Read-Ack Status: 00000000 00000000
22:19:55.477736 T001B0000 Read-Data Outside temperature: 0.00
22:19:55.795812 B601B0000 Data-Inv Outside temperature: 0.00
22:19:56.466736 T80190000 Read-Data Boiler water temperature: 0.00
22:19:56.784751 B4019137C Read-Ack Boiler water temperature: 19.48
22:19:57.456719 T801C0000 Read-Data Return water temperature: 0.00
22:19:57.773697 B401C12D8 Read-Ack Return water temperature: 18.84
22:19:58.444718 T801F0000 Read-Data Flow temperature CH2: 0.00
22:19:58.762672 BE01F0000 Data-Inv Flow temperature CH2: 0.00
22:19:59.484730 T00110000 Read-Data Relative modulation level: 0.00
22:19:59.751658 BC0110000 Read-Ack Relative modulation level: 0.00
22:20:00.000872 Command: SC=22:20/7
22:20:00.028682 SC: 22:20/7
22:20:00.475818 T00000000 Read-Data Status: 00000000 00000000
22:20:00.741750 BC0000000 Read-Ack Status: 00000000 00000000
22:20:01.474780 T80130000 Read-Data DHW flow rate: 0.00
22:20:01.476839 R00060000 Read-Data Remote parameter flags: 00000000 00000000
22:20:01.741691 BC0060707 Read-Ack Remote parameter flags: 00000111 00000111
22:20:01.743453 A70130000 Unk-DataId DHW flow rate: 0.00
22:20:02.464704 T001D0000 Read-Data Solar storage temperature: 0.00
22:20:02.466548 R00300000 Read-Data DHW setpoint boundaries: 0 0
22:20:02.730655 BC030410A Read-Ack DHW setpoint boundaries: 65 10
22:20:02.732236 AF01D0000 Unk-DataId Solar storage temperature: 0.00
22:20:03.441606 T001E0000 Read-Data Solar collector temperature: 0.00
22:20:03.708568 B601E0000 Data-Inv Solar collector temperature: 0.00
22:20:04.430633 T00210000 Read-Data Exhaust temperature: 0
22:20:04.697556 B40210016 Read-Ack Exhaust temperature: 22
22:20:05.469584 T90810500 Write-Data Message ID 129: 1280
22:20:05.751549 B50810500 Write-Ack Message ID 129: 1280
22:20:06.422528 T00000000 Read-Data Status: 00000000 00000000
22:20:06.740543 BC0000000 Read-Ack Status: 00000000 00000000
22:20:07.461522 T90100E00 Write-Data Room setpoint: 14.00
22:20:07.729501 B50100E00 Write-Ack Room setpoint: 14.00
22:20:08.451486 T90170000 Write-Data Room Setpoint CH2: 0.00
22:20:08.718470 B50170000 Write-Ack Room Setpoint CH2: 0.00
22:20:09.440464 T10180FC4 Write-Data Room temperature: 15.77
22:20:09.707500 BD0180FC4 Write-Ack Room temperature: 15.77
22:20:10.429513 T80800000 Read-Data Message ID 128: 0
22:20:10.696469 BE0800000 Data-Inv Message ID 128: 0
22:20:11.418442 T10823D50 Write-Data Message ID 130: 15696
22:20:11.685407 BD0823D50 Write-Ack Message ID 130: 15696
22:20:12.407500 T90020004 Write-Data Master configuration: 00000000 4
22:20:12.675464 B50020004 Write-Ack Master configuration: 00000000 4
22:20:13.446431 T00000000 Read-Data Status: 00000000 00000000
22:20:13.797420 BC0000000 Read-Ack Status: 00000000 00000000
22:20:14.419401 T90010E00 Write-Data Control setpoint: 14.00
22:20:14.786383 B50010E00 Write-Ack Control setpoint: 14.00
22:20:15.408448 T20080000 Inv-Data Control setpoint 2: 0.00
22:20:15.776402 BE0080000 Data-Inv Control setpoint 2: 0.00
22:20:16.397371 T10380500 Write-Data DHW setpoint: 5.00
22:20:16.764443 BD0380500 Write-Ack DHW setpoint: 5.00
22:20:17.436369 T80200000 Read-Data DHW2 temperature: 0.00
22:20:17.754325 BE0200000 Data-Inv DHW2 temperature: 0.00
22:20:18.426335 T801A0000 Read-Data DHW temperature: 0.00
22:20:18.743310 B401A3E54 Read-Ack DHW temperature: 62.33
22:20:19.414339 T00000000 Read-Data Status: 00000000 00000000
22:20:19.732345 BC0000000 Read-Ack Status: 00000000 00000000
22:20:20.404249 T001B0000 Read-Data Outside temperature: 0.00
22:20:20.721157 B601B0000 Data-Inv Outside temperature: 0.00
22:20:21.393109 T80190000 Read-Data Boiler water temperature: 0.00
22:20:21.710110 B4019137C Read-Ack Boiler water temperature: 19.48
22:20:50.514588 OpenTherm Gateway 4.2.8
22:20:50.515897 Command: SC=22:20/7
22:20:50.543773 SC: 22:20/7
22:21:00.001303 Command: SC=22:21/7
22:21:00.029511 SC: 22:21/7
22:22:00.001690 Command: SC=22:22/7
22:22:00.029610 SC: 22:22/7
Thnak you.
Re: OpenTherm Gateway 4.2.8
Hi, Schelte, Bororo,
I had exactly the same issue. I upgraded from 4.2.5 to 4.2.8 and the gateway only reported it's version and replied to commands. There was no communication between the boiler and the thermostat. After downgrading to 4.2.7 all worked fine again. After downgrading to 4.2.7, I upgrade to 4.2.8 once more, but again the same behaviour.
If it helps, I have a Remeha Avanta boiler and a Remeha iSense thermostat.
If I can help with creating diagnostics, please let me know.
Thank you.
I had exactly the same issue. I upgraded from 4.2.5 to 4.2.8 and the gateway only reported it's version and replied to commands. There was no communication between the boiler and the thermostat. After downgrading to 4.2.7 all worked fine again. After downgrading to 4.2.7, I upgrade to 4.2.8 once more, but again the same behaviour.
If it helps, I have a Remeha Avanta boiler and a Remeha iSense thermostat.
If I can help with creating diagnostics, please let me know.
Thank you.
Re: OpenTherm Gateway 4.2.8
I removed the firmware from the site for now. I will investigate which of the changes could possibly cause the reported behavior.
Adventurous souls can still download firmware 4.2.8 using this link.
Adventurous souls can still download firmware 4.2.8 using this link.
Schelte
Re: OpenTherm Gateway 4.2.8
I believe I found the cause of the problems you reported. I have published firmware version 4.2.8.1 that should work much better.
In your log I noticed that you enabled the option to "Automatically update the gateway clock". So I tried that too to see if that had anything to do with problem. It didn't, but I found that it can really mess up the firmware upgrade. So I also published a version 4.4.1 of OTmonitor that fixes that. I suggest to pick one of these options when you try to update again:
In your log I noticed that you enabled the option to "Automatically update the gateway clock". So I tried that too to see if that had anything to do with problem. It didn't, but I found that it can really mess up the firmware upgrade. So I also published a version 4.4.1 of OTmonitor that fixes that. I suggest to pick one of these options when you try to update again:
- Upgrade OTmonitor to 4.4.1 first.
- Temporarily disable the "Automatically update the gateway clock" option.
- Start the upgrade in the first half of the minute, so it completes before OTmonitor send an SC command.
Schelte
Re: OpenTherm Gateway 4.2.8
Thank you Schelte, it's fixed now.
I've built otmonitor 4.4.1 and then successfully upgraded OTGW to 4.2.8.1
Kind regards,
Bororo
I've built otmonitor 4.4.1 and then successfully upgraded OTGW to 4.2.8.1
Kind regards,
Bororo
Code: Select all
19:21:26.085778 PR: A=OpenTherm Gateway 4.2.7
19:21:26.089796 Command: SC=19:21/1
19:21:26.117856 SC: 19:21/1
19:21:26.642669 T907E0101 Write-Data Master product version: 1 1
19:21:27.168651 Error 03
19:21:27.646199 T10011774 Write-Data Control setpoint: 23.45
19:21:27.994874 Error 03
19:21:28.620557 T20080000 Inv-Data Control setpoint 2: 0.00
19:21:28.972564 BE0080000 Data-Inv Control setpoint 2: 0.00
19:21:29.660603 T10380500 Write-Data DHW setpoint: 5.00
19:21:29.961597 BD0380500 Write-Ack DHW setpoint: 5.00
19:21:30.648556 T80200000 Read-Data DHW2 temperature: 0.00
19:21:30.950531 BE0200000 Data-Inv DHW2 temperature: 0.00
19:21:31.638541 T801A0000 Read-Data DHW temperature: 0.00
19:21:31.939561 B401A30E8 Read-Ack DHW temperature: 48.91
19:21:56.166481 T80000100 Read-Data Status: 00000001 00000000
19:21:56.467453 B4000010A Read-Ack Status: 00000001 00001010
19:21:57.155417 T001B0000 Read-Data Outside temperature: 0.00
19:21:57.457339 B601B0000 Data-Inv Outside temperature: 0.00
19:21:58.144233 T80190000 Read-Data Boiler water temperature: 0.00
19:21:58.446320 B40191D9C Read-Ack Boiler water temperature: 29.61
19:21:59.184251 T801C0000 Read-Data Return water temperature: 0.00
19:21:59.435273 BC01C1600 Read-Ack Return water temperature: 22.00
19:22:00.001457 Command: SC=19:22/1
19:22:00.063576 SC: 19:22/1
19:22:00.173201 T801F0000 Read-Data Flow temperature CH2: 0.00
19:22:00.488003 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:22:01.162416 T00110000 Read-Data Relative modulation level: 0.00
19:22:01.413039 B40110100 Read-Ack Relative modulation level: 1.00
19:22:02.151409 T80000100 Read-Data Status: 00000001 00000000
19:22:02.403152 B4000010A Read-Ack Status: 00000001 00001010
19:22:03.140038 T80130000 Read-Data DHW flow rate: 0.00
19:22:03.391988 B70130000 Unk-DataId DHW flow rate: 0.00
19:22:04.130032 T001D0000 Read-Data Solar storage temperature: 0.00
19:22:04.380986 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:22:05.169060 T001E0000 Read-Data Solar collector temperature: 0.00
19:22:05.434988 B601E0000 Data-Inv Solar collector temperature: 0.00
19:22:06.122033 T00210000 Read-Data Exhaust temperature: 0
19:22:06.359096 BC0210017 Read-Ack Exhaust temperature: 23
19:22:07.147031 T10810200 Write-Data Message ID 129: 512
19:22:07.412894 BD0810200 Write-Ack Message ID 129: 512
19:22:08.149900 T80000100 Read-Data Status: 00000001 00000000
19:22:08.401873 B4000010A Read-Ack Status: 00000001 00001010
19:22:09.139983 T90101000 Write-Data Room setpoint: 16.00
19:22:09.390979 B50101000 Write-Ack Room setpoint: 16.00
19:22:10.128869 T90170000 Write-Data Room Setpoint CH2: 0.00
19:22:10.379840 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:22:11.117863 T10181000 Write-Data Room temperature: 16.00
19:22:11.368858 BD0181000 Write-Ack Room temperature: 16.00
19:22:12.106914 T80800000 Read-Data Message ID 128: 0
19:22:12.358811 BE0800000 Data-Inv Message ID 128: 0
19:22:13.146813 T90820053 Write-Data Message ID 130: 83
19:22:13.480771 B50820053 Write-Ack Message ID 130: 83
19:22:14.117782 T807F0000 Read-Data Slave product version: 0 0
19:22:14.469754 B407F6401 Read-Ack Slave product version: 100 1
19:22:15.107761 T80000100 Read-Data Status: 00000001 00000000
19:22:15.459728 B4000010A Read-Ack Status: 00000001 00001010
19:22:16.096738 T10011774 Write-Data Control setpoint: 23.45
19:22:16.448861 BD0011774 Write-Ack Control setpoint: 23.45
19:22:17.135977 T20080000 Inv-Data Control setpoint 2: 0.00
19:22:17.437736 BE0080000 Data-Inv Control setpoint 2: 0.00
19:22:18.125851 T10380500 Write-Data DHW setpoint: 5.00
19:22:18.426740 BD0380500 Write-Ack DHW setpoint: 5.00
19:22:19.113683 T80200000 Read-Data DHW2 temperature: 0.00
19:22:19.415642 BE0200000 Data-Inv DHW2 temperature: 0.00
19:22:20.103680 T801A0000 Read-Data DHW temperature: 0.00
19:22:20.404614 BC01A3100 Read-Ack DHW temperature: 49.00
19:22:21.092643 T80000100 Read-Data Status: 00000001 00000000
19:22:21.394652 B4000010A Read-Ack Status: 00000001 00001010
19:22:22.081853 T001B0000 Read-Data Outside temperature: 0.00
19:22:22.383641 B601B0000 Data-Inv Outside temperature: 0.00
19:22:23.120623 T80190000 Read-Data Boiler water temperature: 0.00
19:22:23.372576 B40191D9C Read-Ack Boiler water temperature: 29.61
19:22:24.110580 T801C0000 Read-Data Return water temperature: 0.00
19:22:24.361581 BC01C1600 Read-Ack Return water temperature: 22.00
19:22:25.098599 T801F0000 Read-Data Flow temperature CH2: 0.00
19:22:25.350581 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:22:26.088555 T00110000 Read-Data Relative modulation level: 0.00
19:22:26.339529 B40110100 Read-Ack Relative modulation level: 1.00
19:22:27.077540 T80000100 Read-Data Status: 00000001 00000000
19:22:27.328498 B4000010A Read-Ack Status: 00000001 00001010
19:22:28.066535 T80130000 Read-Data DHW flow rate: 0.00
19:22:28.317484 B70130000 Unk-DataId DHW flow rate: 0.00
19:22:29.106483 T001D0000 Read-Data Solar storage temperature: 0.00
19:22:29.371468 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:22:30.059469 T001E0000 Read-Data Solar collector temperature: 0.00
19:22:30.514016 B601E0000 Data-Inv Solar collector temperature: 0.00
19:22:31.084571 T00210000 Read-Data Exhaust temperature: 0
19:22:31.350448 BC0210017 Read-Ack Exhaust temperature: 23
19:22:32.087453 T10810200 Write-Data Message ID 129: 512
19:22:32.339401 BD0810200 Write-Ack Message ID 129: 512
19:22:33.076424 T80000100 Read-Data Status: 00000001 00000000
19:22:33.328390 B4000010A Read-Ack Status: 00000001 00001010
19:22:34.066384 T90101000 Write-Data Room setpoint: 16.00
19:22:34.317371 B50101000 Write-Ack Room setpoint: 16.00
19:22:35.054481 T90170000 Write-Data Room Setpoint CH2: 0.00
19:22:35.306373 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:22:36.044343 T10181000 Write-Data Room temperature: 16.00
19:22:36.295330 BD0181000 Write-Ack Room temperature: 16.00
19:22:37.083345 T80800000 Read-Data Message ID 128: 0
19:22:37.418333 BE0800000 Data-Inv Message ID 128: 0
19:22:38.055323 T90820053 Write-Data Message ID 130: 83
19:22:38.407280 B50820053 Write-Ack Message ID 130: 83
19:22:39.044273 T80000100 Read-Data Status: 00000001 00000000
19:22:39.396259 B4000010A Read-Ack Status: 00000001 00001010
19:22:40.034310 T10011774 Write-Data Control setpoint: 23.45
19:22:40.385260 BD0011774 Write-Ack Control setpoint: 23.45
19:22:41.073254 T20080000 Inv-Data Control setpoint 2: 0.00
19:22:41.375221 BE0080000 Data-Inv Control setpoint 2: 0.00
19:22:42.062212 T10380500 Write-Data DHW setpoint: 5.00
19:22:42.364203 BD0380500 Write-Ack DHW setpoint: 5.00
19:22:43.051193 T80200000 Read-Data DHW2 temperature: 0.00
19:22:43.353173 BE0200000 Data-Inv DHW2 temperature: 0.00
19:22:44.040188 T801A0000 Read-Data DHW temperature: 0.00
19:22:44.342157 BC01A3100 Read-Ack DHW temperature: 49.00
19:22:45.029145 T80000100 Read-Data Status: 00000001 00000000
19:22:45.331094 B4000010A Read-Ack Status: 00000001 00001010
19:22:46.019062 T001B0000 Read-Data Outside temperature: 0.00
19:22:46.320052 B601B0000 Data-Inv Outside temperature: 0.00
19:22:47.058380 T80190000 Read-Data Boiler water temperature: 0.00
19:22:47.309275 B40191D9C Read-Ack Boiler water temperature: 29.61
19:22:48.047273 T801C0000 Read-Data Return water temperature: 0.00
19:22:48.299177 BC01C1600 Read-Ack Return water temperature: 22.00
19:22:49.036173 T801F0000 Read-Data Flow temperature CH2: 0.00
19:22:49.288314 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:22:50.025326 T00110000 Read-Data Relative modulation level: 0.00
19:22:50.277146 B40110100 Read-Ack Relative modulation level: 1.00
19:22:51.015113 T80000100 Read-Data Status: 00000001 00000000
19:22:51.266077 B4000010A Read-Ack Status: 00000001 00001010
19:22:52.004073 T80130000 Read-Data DHW flow rate: 0.00
19:22:52.255092 B70130000 Unk-DataId DHW flow rate: 0.00
19:22:53.044165 T001D0000 Read-Data Solar storage temperature: 0.00
19:22:53.309079 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:22:53.996058 T001E0000 Read-Data Solar collector temperature: 0.00
19:22:54.234051 B601E0000 Data-Inv Solar collector temperature: 0.00
19:22:55.022024 T00210000 Read-Data Exhaust temperature: 0
19:22:55.287044 BC0210017 Read-Ack Exhaust temperature: 23
19:22:56.025017 T10810200 Write-Data Message ID 129: 512
19:22:56.276996 BD0810200 Write-Ack Message ID 129: 512
19:22:57.014045 T80000100 Read-Data Status: 00000001 00000000
19:22:57.265997 B4000010A Read-Ack Status: 00000001 00001010
19:22:58.003198 T90101000 Write-Data Room setpoint: 16.00
19:22:58.255037 B50101000 Write-Ack Room setpoint: 16.00
19:22:58.992982 T90170000 Write-Data Room Setpoint CH2: 0.00
19:22:59.243950 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:22:59.980925 T10181000 Write-Data Room temperature: 16.00
19:23:00.001648 Command: SC=19:23/1
19:23:00.029918 SC: 19:23/1
19:23:00.464666 BD0181000 Write-Ack Room temperature: 16.00
19:23:01.021001 T80800000 Read-Data Message ID 128: 0
19:23:01.356002 BE0800000 Data-Inv Message ID 128: 0
19:23:01.993139 T90820053 Write-Data Message ID 130: 83
19:23:02.344953 B50820053 Write-Ack Message ID 130: 83
19:23:02.982018 T90020004 Write-Data Master configuration: 00000000 4
19:23:03.333974 B50020004 Write-Ack Master configuration: 00000000 4
19:23:03.970921 T80000100 Read-Data Status: 00000001 00000000
19:23:04.322697 B4000010A Read-Ack Status: 00000001 00001010
19:23:05.010679 T10011774 Write-Data Control setpoint: 23.45
19:23:05.311694 BD0011774 Write-Ack Control setpoint: 23.45
19:23:05.998805 T20080000 Inv-Data Control setpoint 2: 0.00
19:23:06.301827 BE0080000 Data-Inv Control setpoint 2: 0.00
19:23:06.988808 T10380500 Write-Data DHW setpoint: 5.00
19:23:07.290755 BD0380500 Write-Ack DHW setpoint: 5.00
19:23:07.977744 T80200000 Read-Data DHW2 temperature: 0.00
19:23:08.279750 BE0200000 Data-Inv DHW2 temperature: 0.00
19:23:08.967729 T801A0000 Read-Data DHW temperature: 0.00
19:23:09.268731 BC01A3100 Read-Ack DHW temperature: 49.00
19:23:09.955681 T80000100 Read-Data Status: 00000001 00000000
19:23:10.257666 B4000010A Read-Ack Status: 00000001 00001010
19:23:10.995752 T001B0000 Read-Data Outside temperature: 0.00
19:23:11.246720 B601B0000 Data-Inv Outside temperature: 0.00
19:23:11.984613 T80190000 Read-Data Boiler water temperature: 0.00
19:23:12.235522 BC0191DBC Read-Ack Boiler water temperature: 29.73
19:23:12.973525 T801C0000 Read-Data Return water temperature: 0.00
19:23:13.225486 BC01C1600 Read-Ack Return water temperature: 22.00
19:23:13.962654 T801F0000 Read-Data Flow temperature CH2: 0.00
19:23:14.214613 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:23:14.952584 T00110000 Read-Data Relative modulation level: 0.00
19:23:15.203560 B40110100 Read-Ack Relative modulation level: 1.00
19:23:15.941538 T80000100 Read-Data Status: 00000001 00000000
19:23:16.192523 B4000010A Read-Ack Status: 00000001 00001010
19:23:16.980520 T80130000 Read-Data DHW flow rate: 0.00
19:23:17.246544 B70130000 Unk-DataId DHW flow rate: 0.00
19:23:17.933507 T001D0000 Read-Data Solar storage temperature: 0.00
19:23:18.171488 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:23:18.958478 T001E0000 Read-Data Solar collector temperature: 0.00
19:23:19.224462 B601E0000 Data-Inv Solar collector temperature: 0.00
19:23:19.962458 T00210000 Read-Data Exhaust temperature: 0
19:23:20.213448 BC0210017 Read-Ack Exhaust temperature: 23
19:23:20.951415 T10810200 Write-Data Message ID 129: 512
19:23:21.202415 BD0810200 Write-Ack Message ID 129: 512
19:23:21.940345 T80000100 Read-Data Status: 00000001 00000000
19:23:22.191252 B4000010A Read-Ack Status: 00000001 00001010
19:23:22.929219 T90101000 Write-Data Room setpoint: 16.00
19:23:23.181229 B50101000 Write-Ack Room setpoint: 16.00
19:23:23.918381 T90170000 Write-Data Room Setpoint CH2: 0.00
19:23:24.170348 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:23:24.958346 T10181000 Write-Data Room temperature: 16.00
19:23:25.293335 BD0181000 Write-Ack Room temperature: 16.00
19:23:25.930322 T80800000 Read-Data Message ID 128: 0
19:23:26.282303 BE0800000 Data-Inv Message ID 128: 0
19:23:26.919302 T90820053 Write-Data Message ID 130: 83
19:23:27.271279 B50820053 Write-Ack Message ID 130: 83
19:23:27.958287 T00030000 Read-Data Slave configuration: 00000000 0
19:23:28.260269 B40030904 Read-Ack Slave configuration: 00001001 4
19:23:28.947254 T80000100 Read-Data Status: 00000001 00000000
19:23:29.249255 B4000010A Read-Ack Status: 00000001 00001010
19:23:29.937224 T10011774 Write-Data Control setpoint: 23.45
19:23:30.488422 BD0011774 Write-Ack Control setpoint: 23.45
19:23:30.926277 T20080000 Inv-Data Control setpoint 2: 0.00
19:23:31.228228 BE0080000 Data-Inv Control setpoint 2: 0.00
19:23:31.915235 T10380500 Write-Data DHW setpoint: 5.00
19:23:32.217369 BD0380500 Write-Ack DHW setpoint: 5.00
19:23:32.904553 T80200000 Read-Data DHW2 temperature: 0.00
19:23:33.206324 BE0200000 Data-Inv DHW2 temperature: 0.00
19:23:33.894197 T801A0000 Read-Data DHW temperature: 0.00
19:23:34.195214 B401A30E8 Read-Ack DHW temperature: 48.91
19:23:34.932150 T80000100 Read-Data Status: 00000001 00000000
19:23:35.201464 B4000010A Read-Ack Status: 00000001 00001010
19:23:35.922005 T001B0000 Read-Data Outside temperature: 0.00
19:23:36.172963 B601B0000 Data-Inv Outside temperature: 0.00
19:23:36.910972 T80190000 Read-Data Boiler water temperature: 0.00
19:23:37.161946 BC0191DDC Read-Ack Boiler water temperature: 29.86
19:23:37.900179 T801C0000 Read-Data Return water temperature: 0.00
19:23:38.151122 B401C162C Read-Ack Return water temperature: 22.17
19:23:38.889191 T801F0000 Read-Data Flow temperature CH2: 0.00
19:23:39.141090 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:23:39.879082 T00110000 Read-Data Relative modulation level: 0.00
19:23:40.130035 B40110100 Read-Ack Relative modulation level: 1.00
19:23:40.918006 T80000100 Read-Data Status: 00000001 00000000
19:23:41.184027 B4000010A Read-Ack Status: 00000001 00001010
19:23:41.921007 T80130000 Read-Data DHW flow rate: 0.00
19:23:42.173003 B70130000 Unk-DataId DHW flow rate: 0.00
19:23:42.911027 T001D0000 Read-Data Solar storage temperature: 0.00
19:23:43.161973 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:23:43.899963 T001E0000 Read-Data Solar collector temperature: 0.00
19:23:44.150999 B601E0000 Data-Inv Solar collector temperature: 0.00
19:23:44.888954 T00210000 Read-Data Exhaust temperature: 0
19:23:45.139946 BC0210017 Read-Ack Exhaust temperature: 23
19:23:45.877928 T10810200 Write-Data Message ID 129: 512
19:23:46.128950 BD0810200 Write-Ack Message ID 129: 512
19:23:46.866946 T80000100 Read-Data Status: 00000001 00000000
19:23:47.117884 B4000010A Read-Ack Status: 00000001 00001010
19:23:47.905887 T90101000 Write-Data Room setpoint: 16.00
19:23:48.240881 B50101000 Write-Ack Room setpoint: 16.00
19:23:48.877856 T90170000 Write-Data Room Setpoint CH2: 0.00
19:23:49.229873 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:23:49.866901 T10181000 Write-Data Room temperature: 16.00
19:23:50.219855 BD0181000 Write-Ack Room temperature: 16.00
19:23:50.856844 T80800000 Read-Data Message ID 128: 0
19:23:51.208825 BE0800000 Data-Inv Message ID 128: 0
19:23:51.895821 T90820053 Write-Data Message ID 130: 83
19:23:52.197799 B50820053 Write-Ack Message ID 130: 83
19:23:52.884798 T00060000 Read-Data Remote parameter flags: 00000000 00000000
19:23:53.186805 BC0060707 Read-Ack Remote parameter flags: 00000111 00000111
19:23:53.873825 T80000100 Read-Data Status: 00000001 00000000
19:23:54.175756 B4000010A Read-Ack Status: 00000001 00001010
19:23:54.863754 T10011774 Write-Data Control setpoint: 23.45
19:23:55.164741 BD0011774 Write-Ack Control setpoint: 23.45
19:23:55.851741 T20080000 Inv-Data Control setpoint 2: 0.00
19:23:56.154719 BE0080000 Data-Inv Control setpoint 2: 0.00
19:23:56.841749 T10380500 Write-Data DHW setpoint: 5.00
19:23:57.142739 BD0380500 Write-Ack DHW setpoint: 5.00
19:23:57.880704 T80200000 Read-Data DHW2 temperature: 0.00
19:23:58.132695 BE0200000 Data-Inv DHW2 temperature: 0.00
19:23:58.870681 T801A0000 Read-Data DHW temperature: 0.00
19:23:59.121698 BC01A3100 Read-Ack DHW temperature: 49.00
19:23:59.858690 T80000100 Read-Data Status: 00000001 00000000
19:24:00.000915 Command: SC=19:24/1
19:24:00.028661 SC: 19:24/1
19:24:00.110808 B4000010A Read-Ack Status: 00000001 00001010
19:24:00.848756 T001B0000 Read-Data Outside temperature: 0.00
19:24:01.099678 B601B0000 Data-Inv Outside temperature: 0.00
19:24:01.837670 T80190000 Read-Data Boiler water temperature: 0.00
19:24:02.088637 B40191E00 Read-Ack Boiler water temperature: 30.00
19:24:02.826655 T801C0000 Read-Data Return water temperature: 0.00
19:24:03.077616 B401C162C Read-Ack Return water temperature: 22.17
19:24:03.865688 T801F0000 Read-Data Flow temperature CH2: 0.00
19:24:04.131617 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:24:04.819582 T00110000 Read-Data Relative modulation level: 0.00
19:24:05.056625 B40110100 Read-Ack Relative modulation level: 1.00
19:24:05.844597 T80000100 Read-Data Status: 00000001 00000000
19:24:06.110614 B4000010A Read-Ack Status: 00000001 00001010
19:24:06.847636 T80130000 Read-Data DHW flow rate: 0.00
19:24:07.098551 B70130000 Unk-DataId DHW flow rate: 0.00
19:24:07.837534 T001D0000 Read-Data Solar storage temperature: 0.00
19:24:08.088508 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:24:08.826510 T001E0000 Read-Data Solar collector temperature: 0.00
19:24:09.077478 B601E0000 Data-Inv Solar collector temperature: 0.00
19:24:09.815494 T00210000 Read-Data Exhaust temperature: 0
19:24:10.066470 BC0210017 Read-Ack Exhaust temperature: 23
19:24:10.804461 T10810200 Write-Data Message ID 129: 512
19:24:11.055441 BD0810200 Write-Ack Message ID 129: 512
19:24:11.843432 T80000100 Read-Data Status: 00000001 00000000
19:24:12.178394 B4000010A Read-Ack Status: 00000001 00001010
19:24:12.815381 T90101000 Write-Data Room setpoint: 16.00
19:24:13.167406 B50101000 Write-Ack Room setpoint: 16.00
19:24:13.804391 T90170000 Write-Data Room Setpoint CH2: 0.00
19:24:14.156369 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:24:14.793381 T10181000 Write-Data Room temperature: 16.00
19:24:15.145349 BD0181000 Write-Ack Room temperature: 16.00
19:24:15.833342 T80800000 Read-Data Message ID 128: 0
19:24:16.135336 BE0800000 Data-Inv Message ID 128: 0
19:24:16.822336 T90820053 Write-Data Message ID 130: 83
19:24:17.123345 B50820053 Write-Ack Message ID 130: 83
19:24:17.811326 T900E6400 Write-Data Maximum relative modulation level: 100.00
19:24:18.113335 B500E6400 Write-Ack Maximum relative modulation level: 100.00
19:24:18.800299 T80000100 Read-Data Status: 00000001 00000000
19:24:19.102289 BC0000102 Read-Ack Status: 00000001 00000010
19:24:19.789295 T10011774 Write-Data Control setpoint: 23.45
19:24:20.091264 BD0011774 Write-Ack Control setpoint: 23.45
19:24:20.778280 T20080000 Inv-Data Control setpoint 2: 0.00
19:24:21.080258 BE0080000 Data-Inv Control setpoint 2: 0.00
19:24:21.818243 T10380500 Write-Data DHW setpoint: 5.00
19:24:22.069222 BD0380500 Write-Ack DHW setpoint: 5.00
19:24:22.807220 T80200000 Read-Data DHW2 temperature: 0.00
19:24:23.059217 BE0200000 Data-Inv DHW2 temperature: 0.00
19:24:23.797199 T801A0000 Read-Data DHW temperature: 0.00
19:24:24.048178 B401A30E8 Read-Ack DHW temperature: 48.91
19:24:24.785200 T80000100 Read-Data Status: 00000001 00000000
19:24:25.037155 BC0000102 Read-Ack Status: 00000001 00000010
19:24:25.775396 T001B0000 Read-Data Outside temperature: 0.00
19:24:26.026384 B601B0000 Data-Inv Outside temperature: 0.00
19:24:26.764211 T80190000 Read-Data Boiler water temperature: 0.00
19:24:27.015159 BC0191D58 Read-Ack Boiler water temperature: 29.34
19:24:27.803217 T801C0000 Read-Data Return water temperature: 0.00
19:24:28.069132 BC01C1650 Read-Ack Return water temperature: 22.31
19:24:28.756142 T801F0000 Read-Data Flow temperature CH2: 0.00
19:24:28.994107 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:24:29.782119 T00110000 Read-Data Relative modulation level: 0.00
19:24:30.082759 BC0110000 Read-Ack Relative modulation level: 0.00
19:24:30.785157 T80000100 Read-Data Status: 00000001 00000000
19:24:31.037092 BC0000102 Read-Ack Status: 00000001 00000010
19:24:31.774067 T80130000 Read-Data DHW flow rate: 0.00
19:24:32.025062 B70130000 Unk-DataId DHW flow rate: 0.00
19:24:32.763089 T001D0000 Read-Data Solar storage temperature: 0.00
19:24:33.015065 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:24:33.752030 T001E0000 Read-Data Solar collector temperature: 0.00
19:24:34.004020 B601E0000 Data-Inv Solar collector temperature: 0.00
19:24:34.741997 T00210000 Read-Data Exhaust temperature: 0
19:24:34.992978 BC0210017 Read-Ack Exhaust temperature: 23
19:24:35.780979 T10810200 Write-Data Message ID 129: 512
19:24:36.115970 BD0810200 Write-Ack Message ID 129: 512
19:24:36.752968 T80000100 Read-Data Status: 00000001 00000000
19:24:37.104960 BC0000102 Read-Ack Status: 00000001 00000010
19:24:37.741957 T90101000 Write-Data Room setpoint: 16.00
19:24:38.093933 B50101000 Write-Ack Room setpoint: 16.00
19:24:38.731078 T90170000 Write-Data Room Setpoint CH2: 0.00
19:24:39.082974 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:24:39.769919 T10181000 Write-Data Room temperature: 16.00
19:24:40.071899 BD0181000 Write-Ack Room temperature: 16.00
19:24:40.759890 T80800000 Read-Data Message ID 128: 0
19:24:41.061889 BE0800000 Data-Inv Message ID 128: 0
19:24:41.748883 T90820053 Write-Data Message ID 130: 83
19:24:42.049895 B50820053 Write-Ack Message ID 130: 83
19:24:42.737858 T00120000 Read-Data CH water pressure: 0.00
19:24:43.039844 BC0120185 Read-Ack CH water pressure: 1.52
19:24:43.726897 T80000100 Read-Data Status: 00000001 00000000
19:24:44.028829 BC0000102 Read-Ack Status: 00000001 00000010
19:24:44.715805 T90011770 Write-Data Control setpoint: 23.44
19:24:45.017830 B50011770 Write-Ack Control setpoint: 23.44
19:24:45.755823 T20080000 Inv-Data Control setpoint 2: 0.00
19:24:46.006787 BE0080000 Data-Inv Control setpoint 2: 0.00
19:24:46.744797 T10380500 Write-Data DHW setpoint: 5.00
19:24:46.995757 BD0380500 Write-Ack DHW setpoint: 5.00
19:24:47.733751 T80200000 Read-Data DHW2 temperature: 0.00
19:24:47.985747 BE0200000 Data-Inv DHW2 temperature: 0.00
19:24:48.723743 T801A0000 Read-Data DHW temperature: 0.00
19:24:48.974722 BC01A3100 Read-Ack DHW temperature: 49.00
19:24:49.712759 T80000100 Read-Data Status: 00000001 00000000
19:24:49.963705 BC0000102 Read-Ack Status: 00000001 00000010
19:24:50.700697 T001B0000 Read-Data Outside temperature: 0.00
19:24:50.952705 B601B0000 Data-Inv Outside temperature: 0.00
19:24:51.740681 T80190000 Read-Data Boiler water temperature: 0.00
19:24:52.005669 B40191AA4 Read-Ack Boiler water temperature: 26.64
19:24:52.693680 T801C0000 Read-Data Return water temperature: 0.00
19:24:52.930657 BC01C1650 Read-Ack Return water temperature: 22.31
19:24:53.718684 T801F0000 Read-Data Flow temperature CH2: 0.00
19:24:53.984654 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:24:54.722623 T00110000 Read-Data Relative modulation level: 0.00
19:24:54.973619 BC0110000 Read-Ack Relative modulation level: 0.00
19:24:55.711600 T80000100 Read-Data Status: 00000001 00000000
19:24:55.962589 BC0000102 Read-Ack Status: 00000001 00000010
19:24:56.700592 T80130000 Read-Data DHW flow rate: 0.00
19:24:56.951596 B70130000 Unk-DataId DHW flow rate: 0.00
19:24:57.689597 T001D0000 Read-Data Solar storage temperature: 0.00
19:24:57.941566 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:24:58.678545 T001E0000 Read-Data Solar collector temperature: 0.00
19:24:58.930533 B601E0000 Data-Inv Solar collector temperature: 0.00
19:24:59.718537 T00210000 Read-Data Exhaust temperature: 0
19:25:00.001274 Command: SC=19:25/1
19:25:00.029536 SC: 19:25/1
19:25:00.205834 BC0210017 Read-Ack Exhaust temperature: 23
19:25:01.069330 T10810200 Write-Data Message ID 129: 512
19:25:01.072453 BD0810200 Write-Ack Message ID 129: 512
19:25:01.678564 T80000100 Read-Data Status: 00000001 00000000
19:25:02.031706 BC0000102 Read-Ack Status: 00000001 00000010
19:25:02.668535 T90101000 Write-Data Room setpoint: 16.00
19:25:03.020514 B50101000 Write-Ack Room setpoint: 16.00
19:25:03.707474 T90170000 Write-Data Room Setpoint CH2: 0.00
19:25:04.009443 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:25:04.696431 T10181000 Write-Data Room temperature: 16.00
19:25:04.998421 BD0181000 Write-Ack Room temperature: 16.00
19:25:05.686487 T80800000 Read-Data Message ID 128: 0
19:25:05.987445 BE0800000 Data-Inv Message ID 128: 0
19:25:06.675430 T90820053 Write-Data Message ID 130: 83
19:25:06.976396 B50820053 Write-Ack Message ID 130: 83
19:25:07.664386 T00300000 Read-Data DHW setpoint boundaries: 0 0
19:25:07.966381 BC030410A Read-Ack DHW setpoint boundaries: 65 10
19:25:08.653366 T80000100 Read-Data Status: 00000001 00000000
19:25:08.955344 BC0000102 Read-Ack Status: 00000001 00000010
19:25:09.693354 T100117AC Write-Data Control setpoint: 23.67
19:25:09.944350 BD00117AC Write-Ack Control setpoint: 23.67
19:25:10.681372 T20080000 Inv-Data Control setpoint 2: 0.00
19:25:10.933333 BE0080000 Data-Inv Control setpoint 2: 0.00
19:25:11.671452 T10380500 Write-Data DHW setpoint: 5.00
19:25:11.922315 BD0380500 Write-Ack DHW setpoint: 5.00
19:25:12.660327 T80200000 Read-Data DHW2 temperature: 0.00
19:25:12.912299 BE0200000 Data-Inv DHW2 temperature: 0.00
19:25:13.649303 T801A0000 Read-Data DHW temperature: 0.00
19:25:13.900287 B401A30E8 Read-Ack DHW temperature: 48.91
19:25:14.638330 T80000100 Read-Data Status: 00000001 00000000
19:25:14.890252 BC0000102 Read-Ack Status: 00000001 00000010
19:25:15.678256 T001B0000 Read-Data Outside temperature: 0.00
19:25:15.943249 B601B0000 Data-Inv Outside temperature: 0.00
19:25:16.631248 T80190000 Read-Data Boiler water temperature: 0.00
19:25:16.868231 BC0191988 Read-Ack Boiler water temperature: 25.53
19:25:17.656259 T801C0000 Read-Data Return water temperature: 0.00
19:25:17.922228 BC01C1674 Read-Ack Return water temperature: 22.45
19:25:18.659244 T801F0000 Read-Data Flow temperature CH2: 0.00
19:25:18.911205 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:25:19.649189 T00110000 Read-Data Relative modulation level: 0.00
19:25:19.900177 BC0110000 Read-Ack Relative modulation level: 0.00
19:25:20.638152 T80000100 Read-Data Status: 00000001 00000000
19:25:20.889143 BC0000102 Read-Ack Status: 00000001 00000010
19:25:21.627184 T80130000 Read-Data DHW flow rate: 0.00
19:25:21.878159 B70130000 Unk-DataId DHW flow rate: 0.00
19:25:22.616142 T001D0000 Read-Data Solar storage temperature: 0.00
19:25:22.868125 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:25:23.655152 T001E0000 Read-Data Solar collector temperature: 0.00
19:25:23.990110 B601E0000 Data-Inv Solar collector temperature: 0.00
19:25:24.628110 T00210000 Read-Data Exhaust temperature: 0
19:25:24.979131 BC0210017 Read-Ack Exhaust temperature: 23
19:25:25.617123 T10810200 Write-Data Message ID 129: 512
19:25:25.968086 BD0810200 Write-Ack Message ID 129: 512
19:25:26.605092 T80000100 Read-Data Status: 00000001 00000000
19:25:26.958060 BC0000102 Read-Ack Status: 00000001 00000010
19:25:27.645078 T90101000 Write-Data Room setpoint: 16.00
19:25:27.947079 B50101000 Write-Ack Room setpoint: 16.00
19:25:28.634233 T90170000 Write-Data Room Setpoint CH2: 0.00
19:25:28.936390 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:25:29.623146 T10181000 Write-Data Room temperature: 16.00
19:25:29.925039 BD0181000 Write-Ack Room temperature: 16.00
19:25:30.663373 T80800000 Read-Data Message ID 128: 0
19:25:30.914116 BE0800000 Data-Inv Message ID 128: 0
19:25:31.602044 T90820053 Write-Data Message ID 130: 83
19:25:31.903056 B50820053 Write-Ack Message ID 130: 83
19:25:32.589994 T00390000 Read-Data Max CH water setpoint: 0.00
19:25:32.893113 BC0395900 Read-Ack Max CH water setpoint: 89.00
19:25:33.630037 T80000100 Read-Data Status: 00000001 00000000
19:25:33.881990 BC0000102 Read-Ack Status: 00000001 00000010
19:25:34.619005 T90011770 Write-Data Control setpoint: 23.44
19:25:34.871016 B50011770 Write-Ack Control setpoint: 23.44
19:25:35.608956 T20080000 Inv-Data Control setpoint 2: 0.00
19:25:35.859936 BE0080000 Data-Inv Control setpoint 2: 0.00
19:25:36.597965 T10380500 Write-Data DHW setpoint: 5.00
19:25:36.848934 BD0380500 Write-Ack DHW setpoint: 5.00
19:25:37.586828 T80200000 Read-Data DHW2 temperature: 0.00
19:25:37.837763 BE0200000 Data-Inv DHW2 temperature: 0.00
19:25:38.575826 T801A0000 Read-Data DHW temperature: 0.00
19:25:38.826760 B401A30E8 Read-Ack DHW temperature: 48.91
19:25:39.615914 T80000100 Read-Data Status: 00000001 00000000
19:25:39.880870 BC0000102 Read-Ack Status: 00000001 00000010
19:25:40.618905 T001B0000 Read-Data Outside temperature: 0.00
19:25:40.869858 B601B0000 Data-Inv Outside temperature: 0.00
19:25:41.607871 T80190000 Read-Data Boiler water temperature: 0.00
19:25:41.858895 BC01918F4 Read-Ack Boiler water temperature: 24.95
19:25:42.596902 T801C0000 Read-Data Return water temperature: 0.00
19:25:42.848843 BC01C1674 Read-Ack Return water temperature: 22.45
19:25:43.585846 T801F0000 Read-Data Flow temperature CH2: 0.00
19:25:43.837811 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:25:44.575852 T00110000 Read-Data Relative modulation level: 0.00
19:25:44.826816 BC0110000 Read-Ack Relative modulation level: 0.00
19:25:45.564821 T80000100 Read-Data Status: 00000001 00000000
19:25:45.815786 BC0000102 Read-Ack Status: 00000001 00000010
19:25:46.603793 T80130000 Read-Data DHW flow rate: 0.00
19:25:46.938769 B70130000 Unk-DataId DHW flow rate: 0.00
19:25:47.575755 T001D0000 Read-Data Solar storage temperature: 0.00
19:25:47.927743 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:25:48.564746 T001E0000 Read-Data Solar collector temperature: 0.00
19:25:48.916724 B601E0000 Data-Inv Solar collector temperature: 0.00
19:25:49.553748 T00210000 Read-Data Exhaust temperature: 0
19:25:49.905717 BC0210017 Read-Ack Exhaust temperature: 23
19:25:50.592729 T10810200 Write-Data Message ID 129: 512
19:25:50.894701 BD0810200 Write-Ack Message ID 129: 512
19:25:51.582712 T80000100 Read-Data Status: 00000001 00000000
19:25:51.884676 BC0000102 Read-Ack Status: 00000001 00000010
19:25:52.571691 T90101000 Write-Data Room setpoint: 16.00
19:25:52.873668 B50101000 Write-Ack Room setpoint: 16.00
19:25:53.560706 T90170000 Write-Data Room Setpoint CH2: 0.00
19:25:53.862654 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:25:54.549667 T10181000 Write-Data Room temperature: 16.00
19:25:54.851643 BD0181000 Write-Ack Room temperature: 16.00
19:25:55.538638 T80800000 Read-Data Message ID 128: 0
19:25:55.840629 BE0800000 Data-Inv Message ID 128: 0
19:25:56.578614 T90820053 Write-Data Message ID 130: 83
19:25:56.829621 B50820053 Write-Ack Message ID 130: 83
19:25:57.567630 T907E0101 Write-Data Master product version: 1 1
19:25:58.016596 B507E0101 Write-Ack Master product version: 1 1
19:25:58.553575 T80000100 Read-Data Status: 00000001 00000000
19:25:58.808562 BC0000102 Read-Ack Status: 00000001 00000010
19:25:59.545544 T90011770 Write-Data Control setpoint: 23.44
19:25:59.797550 B50011770 Write-Ack Control setpoint: 23.44
19:26:00.001654 Command: SC=19:26/1
19:26:00.029555 SC: 19:26/1
19:26:00.562921 T20080000 Inv-Data Control setpoint 2: 0.00
19:26:00.786631 BE0080000 Data-Inv Control setpoint 2: 0.00
19:26:01.524595 T10380500 Write-Data DHW setpoint: 5.00
19:26:01.775528 BD0380500 Write-Ack DHW setpoint: 5.00
19:26:02.563571 T80200000 Read-Data DHW2 temperature: 0.00
19:26:02.829529 BE0200000 Data-Inv DHW2 temperature: 0.00
19:26:03.516583 T801A0000 Read-Data DHW temperature: 0.00
19:26:03.753522 BC01A3100 Read-Ack DHW temperature: 49.00
19:26:04.542553 T80000100 Read-Data Status: 00000001 00000000
19:26:04.807496 BC0000102 Read-Ack Status: 00000001 00000010
19:26:05.545536 T001B0000 Read-Data Outside temperature: 0.00
19:26:05.796535 B601B0000 Data-Inv Outside temperature: 0.00
19:26:06.534502 T80190000 Read-Data Boiler water temperature: 0.00
19:26:06.785486 B401918AC Read-Ack Boiler water temperature: 24.67
19:26:07.523487 T801C0000 Read-Data Return water temperature: 0.00
19:26:07.775454 BC01C1674 Read-Ack Return water temperature: 22.45
19:26:08.512462 T801F0000 Read-Data Flow temperature CH2: 0.00
19:26:08.764432 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:26:09.501451 T00110000 Read-Data Relative modulation level: 0.00
19:26:09.753427 BC0110000 Read-Ack Relative modulation level: 0.00
19:26:10.541396 T80000100 Read-Data Status: 00000001 00000000
19:26:10.875386 BC0000102 Read-Ack Status: 00000001 00000010
19:26:11.513381 T80130000 Read-Data DHW flow rate: 0.00
19:26:11.865374 B70130000 Unk-DataId DHW flow rate: 0.00
19:26:12.502371 T001D0000 Read-Data Solar storage temperature: 0.00
19:26:12.854349 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:26:13.491360 T001E0000 Read-Data Solar collector temperature: 0.00
19:26:13.843326 B601E0000 Data-Inv Solar collector temperature: 0.00
19:26:14.530316 T00210000 Read-Data Exhaust temperature: 0
19:26:14.832299 BC0210017 Read-Ack Exhaust temperature: 23
19:26:15.520396 T10810200 Write-Data Message ID 129: 512
19:26:15.821363 BD0810200 Write-Ack Message ID 129: 512
19:26:16.509371 T80000100 Read-Data Status: 00000001 00000000
19:26:16.811308 BC0000102 Read-Ack Status: 00000001 00000010
19:26:17.498279 T90101000 Write-Data Room setpoint: 16.00
19:26:17.800259 B50101000 Write-Ack Room setpoint: 16.00
19:26:18.487244 T90170000 Write-Data Room Setpoint CH2: 0.00
19:26:18.789229 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:26:19.476231 T10181000 Write-Data Room temperature: 16.00
19:26:19.778190 BD0181000 Write-Ack Room temperature: 16.00
19:26:20.516200 T80800000 Read-Data Message ID 128: 0
19:26:20.767189 BE0800000 Data-Inv Message ID 128: 0
19:26:21.505198 T90820053 Write-Data Message ID 130: 83
19:26:21.756169 B50820053 Write-Ack Message ID 130: 83
19:26:22.494197 T807F0000 Read-Data Slave product version: 0 0
19:26:22.745153 B407F6401 Read-Ack Slave product version: 100 1
19:26:23.483211 T80000100 Read-Data Status: 00000001 00000000
19:26:23.735178 BC0000102 Read-Ack Status: 00000001 00000010
19:26:24.472135 T90011770 Write-Data Control setpoint: 23.44
19:26:24.724124 B50011770 Write-Ack Control setpoint: 23.44
19:26:25.461135 T20080000 Inv-Data Control setpoint 2: 0.00
19:26:25.713115 BE0080000 Data-Inv Control setpoint 2: 0.00
19:26:26.501100 T10380500 Write-Data DHW setpoint: 5.00
19:26:26.767128 BD0380500 Write-Ack DHW setpoint: 5.00
19:26:27.454143 T80200000 Read-Data DHW2 temperature: 0.00
19:26:27.691148 BE0200000 Data-Inv DHW2 temperature: 0.00
19:26:28.479113 T801A0000 Read-Data DHW temperature: 0.00
19:26:28.745062 B401A30E8 Read-Ack DHW temperature: 48.91
19:26:29.482090 T80000100 Read-Data Status: 00000001 00000000
19:26:29.734050 BC0000102 Read-Ack Status: 00000001 00000010
19:26:30.472123 T001B0000 Read-Data Outside temperature: 0.00
19:26:30.723135 B601B0000 Data-Inv Outside temperature: 0.00
19:26:31.461212 T80190000 Read-Data Boiler water temperature: 0.00
19:26:31.712080 B40191888 Read-Ack Boiler water temperature: 24.53
19:26:32.450202 T801C0000 Read-Data Return water temperature: 0.00
19:26:32.701055 BC01C1674 Read-Ack Return water temperature: 22.45
19:26:33.439092 T801F0000 Read-Data Flow temperature CH2: 0.00
19:26:33.691055 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:26:34.479046 T00110000 Read-Data Relative modulation level: 0.00
19:26:34.812960 BC0110000 Read-Ack Relative modulation level: 0.00
19:26:35.449964 T80000100 Read-Data Status: 00000001 00000000
19:26:35.801939 BC0000102 Read-Ack Status: 00000001 00000010
19:26:36.439940 T80130000 Read-Data DHW flow rate: 0.00
19:26:36.791960 B70130000 Unk-DataId DHW flow rate: 0.00
19:26:37.428955 T001D0000 Read-Data Solar storage temperature: 0.00
19:26:37.780915 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:26:38.468025 T1014331A Write-Data Day of week and time of day: Mon 19:26
19:26:38.768939 BD014331A Write-Ack Day of week and time of day: Mon 19:26
19:26:39.456913 T90150C1C Write-Data Date: Dec 28
19:26:39.758967 B50150C1C Write-Ack Date: Dec 28
19:26:40.446936 T901607E4 Write-Data Year: 2020
19:26:40.747876 B501607E4 Write-Ack Year: 2020
19:26:41.434974 T001E0000 Read-Data Solar collector temperature: 0.00
19:26:41.737858 B601E0000 Data-Inv Solar collector temperature: 0.00
19:26:42.424848 T00210000 Read-Data Exhaust temperature: 0
19:26:42.725893 BC0210017 Read-Ack Exhaust temperature: 23
19:26:43.413884 T10810200 Write-Data Message ID 129: 512
19:26:43.715832 BD0810200 Write-Ack Message ID 129: 512
19:26:44.452825 T80000100 Read-Data Status: 00000001 00000000
19:26:44.704794 BC0000102 Read-Ack Status: 00000001 00000010
19:26:45.441827 T90101000 Write-Data Room setpoint: 16.00
19:26:45.693780 B50101000 Write-Ack Room setpoint: 16.00
19:26:46.431794 T90170000 Write-Data Room Setpoint CH2: 0.00
19:26:46.682776 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:26:47.420780 T10181000 Write-Data Room temperature: 16.00
19:26:47.671753 BD0181000 Write-Ack Room temperature: 16.00
19:26:48.409738 T80800000 Read-Data Message ID 128: 0
19:26:48.661726 BE0800000 Data-Inv Message ID 128: 0
19:26:49.398746 T90820053 Write-Data Message ID 130: 83
19:26:49.650716 B50820053 Write-Ack Message ID 130: 83
19:26:50.438795 T80000100 Read-Data Status: 00000001 00000000
19:26:50.703755 BC0000102 Read-Ack Status: 00000001 00000010
19:26:51.391684 T90011770 Write-Data Control setpoint: 23.44
19:26:51.628666 B50011770 Write-Ack Control setpoint: 23.44
19:26:52.416669 T20080000 Inv-Data Control setpoint 2: 0.00
19:26:52.682715 BE0080000 Data-Inv Control setpoint 2: 0.00
19:26:53.420680 T10380500 Write-Data DHW setpoint: 5.00
19:26:53.671650 BD0380500 Write-Ack DHW setpoint: 5.00
19:26:54.408645 T80200000 Read-Data DHW2 temperature: 0.00
19:26:54.660630 BE0200000 Data-Inv DHW2 temperature: 0.00
19:26:55.398619 T801A0000 Read-Data DHW temperature: 0.00
19:26:55.649643 B401A30E8 Read-Ack DHW temperature: 48.91
19:26:56.387616 T80000100 Read-Data Status: 00000001 00000000
19:26:56.638577 BC0000102 Read-Ack Status: 00000001 00000010
19:26:57.376600 T001B0000 Read-Data Outside temperature: 0.00
19:26:57.627569 B601B0000 Data-Inv Outside temperature: 0.00
19:26:58.415579 T80190000 Read-Data Boiler water temperature: 0.00
19:26:58.750560 B40191860 Read-Ack Boiler water temperature: 24.38
19:26:59.387583 T801C0000 Read-Data Return water temperature: 0.00
19:26:59.739555 BC01C169C Read-Ack Return water temperature: 22.61
19:27:00.001026 Command: SC=19:27/1
19:27:00.029548 SC: 19:27/1
19:27:00.473182 T801F0000 Read-Data Flow temperature CH2: 0.00
19:27:00.729608 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:27:01.366573 T00110000 Read-Data Relative modulation level: 0.00
19:27:01.718521 BC0110000 Read-Ack Relative modulation level: 0.00
19:27:02.405522 T80000100 Read-Data Status: 00000001 00000000
19:27:02.707483 BC0000102 Read-Ack Status: 00000001 00000010
19:27:03.394469 T80130000 Read-Data DHW flow rate: 0.00
19:27:03.696466 B70130000 Unk-DataId DHW flow rate: 0.00
19:27:04.383480 T001D0000 Read-Data Solar storage temperature: 0.00
19:27:04.685454 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:27:05.372499 T001E0000 Read-Data Solar collector temperature: 0.00
19:27:05.927505 B601E0000 Data-Inv Solar collector temperature: 0.00
19:27:06.362331 T00210000 Read-Data Exhaust temperature: 0
19:27:06.664278 BC0210017 Read-Ack Exhaust temperature: 23
19:27:07.351284 T10810200 Write-Data Message ID 129: 512
19:27:07.652251 BD0810200 Write-Ack Message ID 129: 512
19:27:08.390403 T80000100 Read-Data Status: 00000001 00000000
19:27:08.642370 BC0000102 Read-Ack Status: 00000001 00000010
19:27:09.379375 T90101000 Write-Data Room setpoint: 16.00
19:27:37.775104 OpenTherm Gateway 4.2.8.1
19:27:37.776521 Command: SC=19:27/1
19:27:37.805012 SC: 19:27/1
19:27:38.312895 T90820053 Write-Data Message ID 130: 83
19:27:38.711981 B50820053 Write-Ack Message ID 130: 83
19:27:39.282956 T00030000 Read-Data Slave configuration: 00000000 0
19:27:39.567864 B40030904 Read-Ack Slave configuration: 00001001 4
19:27:40.289862 T80000100 Read-Data Status: 00000001 00000000
19:27:40.556839 BC0000102 Read-Ack Status: 00000001 00000010
19:27:41.278893 T10011774 Write-Data Control setpoint: 23.45
19:27:41.545847 BD0011774 Write-Ack Control setpoint: 23.45
19:27:42.267820 T20080000 Inv-Data Control setpoint 2: 0.00
19:27:42.535799 BE0080000 Data-Inv Control setpoint 2: 0.00
19:27:43.257847 T10380500 Write-Data DHW setpoint: 5.00
19:27:43.524777 BD0380500 Write-Ack DHW setpoint: 5.00
19:27:44.295780 T80200000 Read-Data DHW2 temperature: 0.00
19:27:44.646764 BE0200000 Data-Inv DHW2 temperature: 0.00
19:27:45.268767 T801A0000 Read-Data DHW temperature: 0.00
19:27:45.635741 B401A30E8 Read-Ack DHW temperature: 48.91
19:27:46.257764 T80000100 Read-Data Status: 00000001 00000000
19:27:46.625723 BC0000102 Read-Ack Status: 00000001 00000010
19:27:47.296792 T001B0000 Read-Data Outside temperature: 0.00
19:27:47.614719 B601B0000 Data-Inv Outside temperature: 0.00
19:27:48.285692 T80190000 Read-Data Boiler water temperature: 0.00
19:27:48.603695 B4019183C Read-Ack Boiler water temperature: 24.23
19:27:49.275739 T801C0000 Read-Data Return water temperature: 0.00
19:27:49.592688 BC01C1674 Read-Ack Return water temperature: 22.45
19:27:50.264679 T801F0000 Read-Data Flow temperature CH2: 0.00
19:27:50.582664 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:27:51.253717 T00110000 Read-Data Relative modulation level: 0.00
19:27:51.570652 BC0110000 Read-Ack Relative modulation level: 0.00
19:27:52.242639 T80000100 Read-Data Status: 00000001 00000000
19:27:52.560639 BC0000102 Read-Ack Status: 00000001 00000010
19:27:53.232625 T80130000 Read-Data DHW flow rate: 0.00
19:27:53.549615 B70130000 Unk-DataId DHW flow rate: 0.00
19:27:54.271602 T001D0000 Read-Data Solar storage temperature: 0.00
19:27:54.538579 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:27:55.260481 T001E0000 Read-Data Solar collector temperature: 0.00
19:27:55.527423 B601E0000 Data-Inv Solar collector temperature: 0.00
19:27:56.249389 T00210000 Read-Data Exhaust temperature: 0
19:27:56.516376 BC0210017 Read-Ack Exhaust temperature: 23
19:27:57.238579 T10810200 Write-Data Message ID 129: 512
19:27:57.505533 BD0810200 Write-Ack Message ID 129: 512
19:27:58.227517 T80000100 Read-Data Status: 00000001 00000000
19:27:58.495520 BC0000102 Read-Ack Status: 00000001 00000010
19:27:59.217491 T90101000 Write-Data Room setpoint: 16.00
19:27:59.484480 B50101000 Write-Ack Room setpoint: 16.00
19:28:00.000942 Command: SC=19:28/1
19:28:00.028475 SC: 19:28/1
19:28:00.499560 T90170000 Write-Data Room Setpoint CH2: 0.00
19:28:00.537540 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:28:01.259369 T10181000 Write-Data Room temperature: 16.00
19:28:01.527321 BD0181000 Write-Ack Room temperature: 16.00
19:28:02.248323 T80800000 Read-Data Message ID 128: 0
19:28:02.516286 BE0800000 Data-Inv Message ID 128: 0
19:28:03.237474 T90820053 Write-Data Message ID 130: 83
19:28:03.505443 B50820053 Write-Ack Message ID 130: 83
19:28:04.226420 T00060000 Read-Data Remote parameter flags: 00000000 00000000
19:28:04.494434 BC0060707 Read-Ack Remote parameter flags: 00000111 00000111
19:28:05.216457 T80000100 Read-Data Status: 00000001 00000000
19:28:05.483392 BC0000102 Read-Ack Status: 00000001 00000010
19:28:06.205377 T10011774 Write-Data Control setpoint: 23.45
19:28:06.472370 BD0011774 Write-Ack Control setpoint: 23.45
19:28:07.244378 T20080000 Inv-Data Control setpoint 2: 0.00
19:28:07.595373 BE0080000 Data-Inv Control setpoint 2: 0.00
19:28:08.216348 T10380500 Write-Data DHW setpoint: 5.00
19:28:08.584333 BD0380500 Write-Ack DHW setpoint: 5.00
19:28:09.205334 T80200000 Read-Data DHW2 temperature: 0.00
19:28:09.573350 BE0200000 Data-Inv DHW2 temperature: 0.00
19:28:10.195309 T801A0000 Read-Data DHW temperature: 0.00
19:28:10.562319 B401A30E8 Read-Ack DHW temperature: 48.91
19:28:11.234293 T80000100 Read-Data Status: 00000001 00000000
19:28:11.552272 BC0000102 Read-Ack Status: 00000001 00000010
19:28:12.223265 T001B0000 Read-Data Outside temperature: 0.00
19:28:12.541282 B601B0000 Data-Inv Outside temperature: 0.00
19:28:13.212279 T80190000 Read-Data Boiler water temperature: 0.00
19:28:13.530269 B40191818 Read-Ack Boiler water temperature: 24.09
19:28:14.202258 T801C0000 Read-Data Return water temperature: 0.00
19:28:14.519240 BC01C1674 Read-Ack Return water temperature: 22.45
19:28:15.191234 T801F0000 Read-Data Flow temperature CH2: 0.00
19:28:15.508209 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:28:16.180211 T00110000 Read-Data Relative modulation level: 0.00
19:28:16.497208 BC0110000 Read-Ack Relative modulation level: 0.00
19:28:17.219213 T80000100 Read-Data Status: 00000001 00000000
19:28:17.487200 BC0000102 Read-Ack Status: 00000001 00000010
19:28:18.209172 T80130000 Read-Data DHW flow rate: 0.00
19:28:18.476165 B70130000 Unk-DataId DHW flow rate: 0.00
19:28:19.198159 T001D0000 Read-Data Solar storage temperature: 0.00
19:28:19.465137 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:28:20.187151 T001E0000 Read-Data Solar collector temperature: 0.00
19:28:20.454128 B601E0000 Data-Inv Solar collector temperature: 0.00
19:28:21.176143 T00210000 Read-Data Exhaust temperature: 0
19:28:21.443153 BC0210017 Read-Ack Exhaust temperature: 23
19:28:22.165088 T10810200 Write-Data Message ID 129: 512
19:28:22.432085 BD0810200 Write-Ack Message ID 129: 512
19:28:23.204085 T80000100 Read-Data Status: 00000001 00000000
19:28:23.486052 BC0000102 Read-Ack Status: 00000001 00000010
19:28:24.157134 T90101000 Write-Data Room setpoint: 16.00
19:28:24.475099 B50101000 Write-Ack Room setpoint: 16.00
19:28:25.197133 T90170000 Write-Data Room Setpoint CH2: 0.00
19:28:25.464095 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:28:26.186049 T10181000 Write-Data Room temperature: 16.00
19:28:26.453009 BD0181000 Write-Ack Room temperature: 16.00
19:28:27.175061 T80800000 Read-Data Message ID 128: 0
19:28:27.443037 BE0800000 Data-Inv Message ID 128: 0
19:28:28.163989 T90820053 Write-Data Message ID 130: 83
19:28:28.432066 B50820053 Write-Ack Message ID 130: 83
19:28:29.154025 T900E6400 Write-Data Maximum relative modulation level: 100.00
19:28:29.420973 B500E6400 Write-Ack Maximum relative modulation level: 100.00
19:28:30.143137 T80000100 Read-Data Status: 00000001 00000000
19:28:30.481156 BC0000102 Read-Ack Status: 00000001 00000010
19:28:31.182015 T10011774 Write-Data Control setpoint: 23.45
19:28:31.532949 BD0011774 Write-Ack Control setpoint: 23.45
19:28:32.152927 T20080000 Inv-Data Control setpoint 2: 0.00
19:28:32.521917 BE0080000 Data-Inv Control setpoint 2: 0.00
19:28:33.142965 T10380500 Write-Data DHW setpoint: 5.00
19:28:33.510931 BD0380500 Write-Ack DHW setpoint: 5.00
19:28:34.131894 T80200000 Read-Data DHW2 temperature: 0.00
19:28:34.499896 BE0200000 Data-Inv DHW2 temperature: 0.00
19:28:35.170907 T801A0000 Read-Data DHW temperature: 0.00
19:28:35.488861 B401A30E8 Read-Ack DHW temperature: 48.91
19:28:36.160873 T80000100 Read-Data Status: 00000001 00000000
19:28:36.478831 BC0000102 Read-Ack Status: 00000001 00000010
19:28:37.149954 T001B0000 Read-Data Outside temperature: 0.00
19:28:37.467873 B601B0000 Data-Inv Outside temperature: 0.00
19:28:38.139037 T80190000 Read-Data Boiler water temperature: 0.00
19:28:38.456890 B40191818 Read-Ack Boiler water temperature: 24.09
19:28:39.128782 T801C0000 Read-Data Return water temperature: 0.00
19:28:39.445762 BC01C1674 Read-Ack Return water temperature: 22.45
19:28:40.117788 T801F0000 Read-Data Flow temperature CH2: 0.00
19:28:40.434758 BE01F0000 Data-Inv Flow temperature CH2: 0.00
19:28:41.156767 T00110000 Read-Data Relative modulation level: 0.00
19:28:41.423722 BC0110000 Read-Ack Relative modulation level: 0.00
19:28:42.145684 T80000100 Read-Data Status: 00000001 00000000
19:28:42.413684 BC0000102 Read-Ack Status: 00000001 00000010
19:28:43.134671 T80130000 Read-Data DHW flow rate: 0.00
19:28:43.402678 B70130000 Unk-DataId DHW flow rate: 0.00
19:28:44.124676 T001D0000 Read-Data Solar storage temperature: 0.00
19:28:44.391668 BF01D0000 Unk-DataId Solar storage temperature: 0.00
19:28:45.113677 T001E0000 Read-Data Solar collector temperature: 0.00
19:28:45.380657 B601E0000 Data-Inv Solar collector temperature: 0.00
19:28:46.102656 T00210000 Read-Data Exhaust temperature: 0
19:28:46.369638 BC0210017 Read-Ack Exhaust temperature: 23
19:28:47.141633 T10810200 Write-Data Message ID 129: 512
19:28:47.423621 BD0810200 Write-Ack Message ID 129: 512
19:28:48.094599 T80000100 Read-Data Status: 00000001 00000000
19:28:48.412586 BC0000102 Read-Ack Status: 00000001 00000010
19:28:49.134592 T90101000 Write-Data Room setpoint: 16.00
19:28:49.401567 B50101000 Write-Ack Room setpoint: 16.00
19:28:50.123586 T90170000 Write-Data Room Setpoint CH2: 0.00
19:28:50.390539 B50170000 Write-Ack Room Setpoint CH2: 0.00
19:28:51.112551 T10181000 Write-Data Room temperature: 16.00
19:28:51.379531 BD0181000 Write-Ack Room temperature: 16.00
19:28:52.101537 T80800000 Read-Data Message ID 128: 0
19:28:52.369518 BE0800000 Data-Inv Message ID 128: 0
19:28:53.090506 T90820053 Write-Data Message ID 130: 83
19:28:53.358520 B50820053 Write-Ack Message ID 130: 83
19:28:54.079516 T00120000 Read-Data CH water pressure: 0.00
19:28:54.347476 B40120184 Read-Ack CH water pressure: 1.52
19:28:55.119462 T80000100 Read-Data Status: 00000001 00000000
19:28:55.470456 BC0000102 Read-Ack Status: 00000001 00000010
19:28:56.091453 T10011774 Write-Data Control setpoint: 23.45
19:28:56.458437 BD0011774 Write-Ack Control setpoint: 23.45
19:28:57.080452 T20080000 Inv-Data Control setpoint 2: 0.00
Re: OpenTherm Gateway 4.2.8
And I see you didn't take any chances and did the upgrade in the first half of the minute as well
I'm just wondering, why did you build otmonitor 4.4.1?
I'm just wondering, why did you build otmonitor 4.4.1?
Schelte
Re: OpenTherm Gateway 4.2.8
I'm trying to modify some otmonitor settings (e.g. Graph timeline) so for me it's better to use git pull to obtain latest files from your gitlab and then learn/play with building application.
Re: OpenTherm Gateway 4.2.8
OK. I just wanted to make sure there is nothing fundamentally wrong with the binaries I provided.
Schelte
Re: OpenTherm Gateway 4.2.8
Hi Schelte,
I would like to ask you for further details regarding Max CH setpoint as I am not able to change this value via web Configuration.
Any changes made using slider nor manually entered values remained - it's always 89,00.
I tried to change value to 60,00 manually, then click on Set, close webpage and power-cycle otgw.
Then opened webpage/configuration and saw 70 ?! for a while, but clicking somewhere else in otmonitor and back to Heater tab resulted in 89,00 value.
The same behavior I see with reference voltage even I'm sure it was working in previous version. (tried to set VR=V command showing PR: V=3 only)
Best regards,
Boro
I would like to ask you for further details regarding Max CH setpoint as I am not able to change this value via web Configuration.
Any changes made using slider nor manually entered values remained - it's always 89,00.
I tried to change value to 60,00 manually, then click on Set, close webpage and power-cycle otgw.
Then opened webpage/configuration and saw 70 ?! for a while, but clicking somewhere else in otmonitor and back to Heater tab resulted in 89,00 value.
The same behavior I see with reference voltage even I'm sure it was working in previous version. (tried to set VR=V command showing PR: V=3 only)
Best regards,
Boro
Re: OpenTherm Gateway 4.2.8
First of all: Thanks for testing and reporting the issues.
The slider not working was a bug in OTmonitor. A fix is now available in the github repository.
I broke the voltage reference setting in 4.2.8.1. The requested level was actually set, but the administration was not correctly updated. To fix that, I just released firmware 4.2.8.2.
But at least the Max CH setpoint is working correctly when I test it. Your test procedure is a bit strange, though. Why do you power-cycle the gateway? That may be the reason it doesn't work for you.
The Max CH setpoint is a parameter in the boiler. The OTGW first needs to check the level of support the boiler provides for this parameter. It does that by requesting MsgID 6. If the boiler supports changing the parameter (ID6:LB1), the OTGW will request the bounds via MsgID 49. Until the OTGW obtains the necessary information from the boiler, it will ignore any SH command.
After a reset, the OTGW doesn't have any slots where it can insert its own messages (unless you have configured them with the UI command). It will collect slots by looking for Unknown-DataID responses from the boiler. Once a specific ID has produced an Unknown-DataID response three times in a row, the OTGW will start replacing requests for that DataID with its own messages. As you may understand, it can take a while before the OTGW can find slots for sending MsgID 6 and 49.
Once the OTGW knows that the boiler supports changing the Max CH setpoint, then following an SH command, the OTGW has to wait for a slot it can use to send a Write-Data request for MsgID 57. If you power-cycle the OTGW before that time, then the parameter will not have been changed.
Have a look at the log. It's fun to see all of this happening:
To summarize: There are 3 possible reasons why your SH command had no effect:
I hope this clears things up a bit.
The slider not working was a bug in OTmonitor. A fix is now available in the github repository.
I broke the voltage reference setting in 4.2.8.1. The requested level was actually set, but the administration was not correctly updated. To fix that, I just released firmware 4.2.8.2.
But at least the Max CH setpoint is working correctly when I test it. Your test procedure is a bit strange, though. Why do you power-cycle the gateway? That may be the reason it doesn't work for you.
The Max CH setpoint is a parameter in the boiler. The OTGW first needs to check the level of support the boiler provides for this parameter. It does that by requesting MsgID 6. If the boiler supports changing the parameter (ID6:LB1), the OTGW will request the bounds via MsgID 49. Until the OTGW obtains the necessary information from the boiler, it will ignore any SH command.
After a reset, the OTGW doesn't have any slots where it can insert its own messages (unless you have configured them with the UI command). It will collect slots by looking for Unknown-DataID responses from the boiler. Once a specific ID has produced an Unknown-DataID response three times in a row, the OTGW will start replacing requests for that DataID with its own messages. As you may understand, it can take a while before the OTGW can find slots for sending MsgID 6 and 49.
Once the OTGW knows that the boiler supports changing the Max CH setpoint, then following an SH command, the OTGW has to wait for a slot it can use to send a Write-Data request for MsgID 57. If you power-cycle the OTGW before that time, then the parameter will not have been changed.
Have a look at the log. It's fun to see all of this happening:
Code: Select all
### Reset
15:23:44.620834 OpenTherm Gateway 4.2.8.2
### Unknown ID 26 (#1)
15:23:45.829597 T801A0000 Read-Data DHW temperature: 0.00
15:23:45.958338 B701A0000 Unk-DataId DHW temperature: 0.00
### Unknown ID 26 (#2)
15:23:53.907897 T801A0000 Read-Data DHW temperature: 0.00
15:23:54.036595 B701A0000 Unk-DataId DHW temperature: 0.00
### Unknown ID 26 (#3)
15:24:01.905484 T801A0000 Read-Data DHW temperature: 0.00
15:24:02.034615 B701A0000 Unk-DataId DHW temperature: 0.00
### Unknown ID 26 (#4, the slot can now be used by OTGW)
15:24:11.106794 T801A0000 Read-Data DHW temperature: 0.00
15:24:11.113393 R00060000 Read-Data Remote parameter flags: 00000000 00000000
15:24:11.233793 BC0060303 Read-Ack Remote parameter flags: 00000011 00000011
- DHW setpoint transfer: enabled (1)
- max CH setpoint transfer: enabled (1)
- DHW setpoint: read/write (1)
- max CH setpoint: read/write (1)
15:24:11.279122 A701A0000 Unk-DataId DHW temperature: 0.00
### Unknown ID 26
15:24:17.583227 T801A0000 Read-Data DHW temperature: 0.00
15:24:17.592659 R80310000 Read-Data Max CH setpoint boundaries: 0 0
15:24:17.714003 B40314B14 Read-Ack Max CH setpoint boundaries: 75 20
15:24:17.720783 A701A0000 Unk-DataId DHW temperature: 0.00
### SH command
15:24:24.682787 Command: SH=72.7
15:24:24.707936 SH: 72.70
### Unknown ID 26
15:24:25.682752 T801A0000 Read-Data DHW temperature: 0.00
15:24:25.688613 R903948B4 Write-Data Max CH water setpoint: 72.70
15:24:25.811664 B503948B4 Write-Ack Max CH water setpoint: 72.70
15:24:25.820007 A701A0000 Unk-DataId DHW temperature: 0.00
- Your boiler does not support writing this parameter, i.e. MsgID 6 received an Unknown-DataID response or the response has ID6:LB1 = 0.
- You performed the SH command before the OTGW had a chance to request MsgID 6.
- You reset the OTGW before it had a chance to send MsgID 57.
I hope this clears things up a bit.
Schelte
Re: OpenTherm Gateway 4.2.8
Hi Schelte,
thank you for updated version of otmonitor.
I made some quick tests and found only 1 issue - after changing reference voltage using slider and clicking on Set, slider is moved back to "default" 1.250 value.
The log showing attempts for VR change but it's not changed:
I tried to record my screen if it helps:
https://youtu.be/JF41sn1FVeI
As for Max CH setpoint I will investigate more in documentation. I was not able to find any settings with value 89,00...
The power-cycle exercise was based on my (wrong) understanding that some values are stored in eprom and power-cycle is needed for storing/applying such values.
thank you for updated version of otmonitor.
I made some quick tests and found only 1 issue - after changing reference voltage using slider and clicking on Set, slider is moved back to "default" 1.250 value.
The log showing attempts for VR change but it's not changed:
Code: Select all
21:41:32.056453 Command (via websocket): SH=60
21:41:32.076920 SH: 60.00
21:41:32.167870 BD0180FA8 Write-Ack Room temperature: 15.66
21:41:32.839896 T80800000 Read-Data Message ID 128: 0
21:41:33.157883 BE0800000 Data-Inv Message ID 128: 0
21:41:33.829869 T10824050 Write-Data Message ID 130: 16464
21:41:34.147047 BD0824050 Write-Ack Message ID 130: 16464
21:41:34.869047 T10149529 Write-Data Day of week and time of day: Thu 21:41
21:41:35.134941 BD0149529 Write-Ack Day of week and time of day: Thu 21:41
21:41:35.856857 T10150107 Write-Data Date: Jan 7
21:41:36.124880 BD0150107 Write-Ack Date: Jan 7
21:41:36.846821 T101607E5 Write-Data Year: 2021
21:41:37.113812 BD01607E5 Write-Ack Year: 2021
21:41:37.835810 T807F0000 Read-Data Slave product version: 0 0
21:41:38.102789 B407F6401 Read-Ack Slave product version: 100 1
21:41:38.824668 T00000000 Read-Data Status: 00000000 00000000
21:41:39.092636 BC0000000 Read-Ack Status: 00000000 00000000
21:41:39.814603 T90010E00 Write-Data Control setpoint: 14.00
21:41:40.080595 B50010E00 Write-Ack Control setpoint: 14.00
21:41:40.852782 T20080000 Inv-Data Control setpoint 2: 0.00
21:41:41.134756 BE0080000 Data-Inv Control setpoint 2: 0.00
21:41:41.806757 T10380500 Write-Data DHW setpoint: 5.00
21:41:42.123730 BD0380500 Write-Ack DHW setpoint: 5.00
21:41:42.845723 T80200000 Read-Data DHW2 temperature: 0.00
21:41:43.112728 BE0200000 Data-Inv DHW2 temperature: 0.00
21:41:43.834722 T801A0000 Read-Data DHW temperature: 0.00
21:41:44.101695 B401A1354 Read-Ack DHW temperature: 19.33
21:41:44.823678 T00000000 Read-Data Status: 00000000 00000000
21:41:45.090664 BC0000000 Read-Ack Status: 00000000 00000000
21:41:45.813652 T001B0000 Read-Data Outside temperature: 0.00
21:41:46.079659 B601B0000 Data-Inv Outside temperature: 0.00
21:41:46.801699 T80190000 Read-Data Boiler water temperature: 0.00
21:41:47.068650 B40191354 Read-Ack Boiler water temperature: 19.33
21:41:47.790610 T801C0000 Read-Data Return water temperature: 0.00
21:41:48.058622 B401C137C Read-Ack Return water temperature: 19.48
21:41:48.830637 T801F0000 Read-Data Flow temperature CH2: 0.00
21:41:49.181675 BE01F0000 Data-Inv Flow temperature CH2: 0.00
21:41:49.802593 T00110000 Read-Data Relative modulation level: 0.00
21:41:50.169635 BC0110000 Read-Ack Relative modulation level: 0.00
21:41:50.791470 T00000000 Read-Data Status: 00000000 00000000
21:41:51.159408 BC0000000 Read-Ack Status: 00000000 00000000
21:41:51.842377 T80130000 Read-Data DHW flow rate: 0.00
21:41:51.844846 R90393C00 Write-Data Max CH water setpoint: 60.00
21:41:52.159392 BF0390000 Unk-DataId Max CH water setpoint: 0.00
21:41:52.161931 A70130000 Unk-DataId DHW flow rate: 0.00
21:41:52.820564 T001D0000 Read-Data Solar storage temperature: 0.00
21:41:53.137556 BF01D0000 Unk-DataId Solar storage temperature: 0.00
21:41:53.809557 T001E0000 Read-Data Solar collector temperature: 0.00
21:41:53.815266 Command (via websocket): VR=4
21:41:53.830510 VR: 3
21:41:54.126516 B601E0000 Data-Inv Solar collector temperature: 0.00
21:41:54.798505 T00210000 Read-Data Exhaust temperature: 0
21:41:55.115512 BC0210014 Read-Ack Exhaust temperature: 20
21:41:55.787593 T90810500 Write-Data Message ID 129: 1280
21:41:56.104492 B50810500 Write-Ack Message ID 129: 1280
21:41:56.726836 Command (via websocket): VR=5
21:41:56.742472 VR: 3
21:41:56.775446 T00000000 Read-Data Status: 00000000 00000000
21:41:57.765483 T00000000 Read-Data Status: 00000000 00000000
21:41:58.771430 T90170000 Write-Data Room Setpoint CH2: 0.00
21:41:59.761478 T90170000 Write-Data Room Setpoint CH2: 0.00
21:42:00.001626 Command: SC=21:42/4
21:42:00.029457 SC: 21:42/4
21:42:00.583848 Command (via websocket): VR=4
21:42:00.599414 VR: 3
https://youtu.be/JF41sn1FVeI
As for Max CH setpoint I will investigate more in documentation. I was not able to find any settings with value 89,00...
The power-cycle exercise was based on my (wrong) understanding that some values are stored in eprom and power-cycle is needed for storing/applying such values.
Re: OpenTherm Gateway 4.2.8
This looks suspiciously like what would happen with firmware 4.2.8.1. Are you sure you have loaded 4.2.8.2? Check with PR=A. If so, please also check PR=B. It should report PR: B=12:51 07-01-2021
Schelte
Re: OpenTherm Gateway 4.2.8
aaarrrgh... my fault, i should stop experimenting with git pull and customisation ans simply download your version from website. i'm sorry.