There is currently no way to dump some of these settings. The problem is that the output might not fit in the available transmit buffer. So such a report would have to be done in increments, which requires a lot of code. Because of the limited resources available in the PIC, I didn't think it was worth it.
But perhaps I can make an enhancement to otmonitor to copy the EEPROM settings from the old firmware to the new one. I'll look into that.
But perhaps I can make an enhancement to otmonitor to copy the EEPROM settings from the old firmware to the new one. I'll look into that.
Schelte
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
Thanks for the quick reply, sounds like a good idea.hvxl wrote:There is currently no way to dump some of these settings. The problem is that the output might not fit in the available transmit buffer. So such a report would have to be done in increments, which requires a lot of code. Because of the limited resources available in the PIC, I didn't think it was worth it.
But perhaps I can make an enhancement to otmonitor to copy the EEPROM settings from the old firmware to the new one. I'll look into that.
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
You do specify a baudrate of 9600 with remserial, right?RedNax wrote:I've found that running and stopping otmonitor-ahf on the PI before starting remserial solves it. Does otmonitor set some special serial parameters?
Schelte
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
A new version of the firmware is available at http://otgw.tclcode.com/development.html. Since I have pretty much exhausted the list of new features I wanted to implement, I changed the version numbering scheme from alpha to beta. There may be a few more beta versions to fix any bugs before the final 4.0 version is going to be released. So please test this firmware and report any issues you find.
This firmware contains:
This firmware contains:
- Option to put the remote override flags in the high byte of MsgID 100.
- Several fixes for the Celcia 20 thermostat.
- A couple of stability improvements.
Schelte
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
casio wrote:Furthermore, I've had two times that the thermostat reported "Fout 203" code.
Both of these bugs should be fixed in firmware 4.0b0. Thanks for reporting.blb wrote:I'm running firmware version 4.0a11 in combination with a Celcia20 Thermostat and I'm having problems returning back from temporary setpoint override.
Schelte
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
Schelte,
With the new firmware 4.0b0 It's working as before thanks!
With the new firmware 4.0b0 It's working as before thanks!
Bernard
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
Hi Schelte,
Thanks for the new FW and thanks for turning OH on by default
.
Unfortunately I have a problem with the SR command in the new FW. When I set a response for message 70 (SR=70:0,0) it only works briefly. After some time the OTG does not respond to message 70 anymore. Something happens and the OTG resets itself? (@13:44:56 - output: "óOpenTherm Gateway 4.0b0"). See log below. Looks related to the auto-reset functionality you built in. In this case it should not reset itself (it is 'normal' for my thermostat to keep requesting Max CH water setpoint as the boiler keeps responding with different values).
Thanks for the new FW and thanks for turning OH on by default

Unfortunately I have a problem with the SR command in the new FW. When I set a response for message 70 (SR=70:0,0) it only works briefly. After some time the OTG does not respond to message 70 anymore. Something happens and the OTG resets itself? (@13:44:56 - output: "óOpenTherm Gateway 4.0b0"). See log below. Looks related to the auto-reset functionality you built in. In this case it should not reset itself (it is 'normal' for my thermostat to keep requesting Max CH water setpoint as the boiler keeps responding with different values).
Code: Select all
13:43:33.234965 PR: A=OpenTherm Gateway 4.0b0
13:43:33.258000 PR: M=G
13:43:33.285046 PR: L=RXOEPC
13:43:33.308069 PR: T=01
13:43:33.329870 PR: V=3
13:43:33.352091 PR: W=A
13:43:33.375089 PR: G=00
13:43:33.416317 PR: P=Low power
13:43:33.419523 T00000300 Read-Data Status: 00000011 00000000
13:43:33.446723 SR: 70:0/0
13:43:33.562425 BC000030A Read-Ack Status: 00000011 00001010
13:43:33.945805 T00000300 Read-Data Status: 00000011 00000000
13:43:34.094775 BC000030A Read-Ack Status: 00000011 00001010
13:43:34.479625 T00050000 Read-Data Application-specific flags: 00000000 0
13:43:34.634644 BC0050000 Read-Ack Application-specific flags: 00000000 0
13:43:35.013688 T10013000 Write-Data Control setpoint: 48.00
13:43:35.160514 BD0013000 Write-Ack Control setpoint: 48.00
13:43:35.544923 T80190000 Read-Data Boiler water temperature: 0.00
13:43:35.694307 B40193480 Read-Ack Boiler water temperature: 52.50
13:43:36.078463 T00000300 Read-Data Status: 00000011 00000000
13:43:36.224426 BC000030A Read-Ack Status: 00000011 00001010
13:43:36.609385 T00000300 Read-Data Status: 00000011 00000000
13:43:36.753300 BC000030A Read-Ack Status: 00000011 00001010
13:43:37.144681 T00000300 Read-Data Status: 00000011 00000000
13:43:37.293337 BC000030A Read-Ack Status: 00000011 00001010
13:43:37.677935 T00000300 Read-Data Status: 00000011 00000000
13:43:37.823587 BC000030A Read-Ack Status: 00000011 00001010
13:43:38.080278 SR: 78:40/0
13:43:38.214729 T80381400 Read-Data DHW setpoint: 20.00
13:43:38.358815 BC038001A Read-Ack DHW setpoint: 0.10
13:43:38.749693 T00395000 Read-Data Max CH water setpoint: 80.00
13:43:38.892521 B40395010 Read-Ack Max CH water setpoint: 80.06
13:43:39.282985 T10013000 Write-Data Control setpoint: 48.00
13:43:39.422831 BD0013000 Write-Ack Control setpoint: 48.00
13:43:39.837971 T00000300 Read-Data Status: 00000011 00000000
13:43:39.991454 BC000030A Read-Ack Status: 00000011 00001010
13:43:40.370956 T80190000 Read-Data Boiler water temperature: 0.00
13:43:40.517773 B40193480 Read-Ack Boiler water temperature: 52.50
13:43:40.902836 T00000300 Read-Data Status: 00000011 00000000
13:43:41.051543 BC000030A Read-Ack Status: 00000011 00001010
13:43:41.435974 T00000300 Read-Data Status: 00000011 00000000
13:43:41.591013 BC000030A Read-Ack Status: 00000011 00001010
13:43:41.968590 T00000300 Read-Data Status: 00000011 00000000
13:43:42.110475 BC000030A Read-Ack Status: 00000011 00001010
13:43:42.501590 T00000300 Read-Data Status: 00000011 00000000
13:43:42.650514 BC000030A Read-Ack Status: 00000011 00001010
13:43:43.034844 T00110000 Read-Data Relative modulation level: 0.00
13:43:43.189999 BC0113500 Read-Ack Relative modulation level: 53.00
13:43:43.568110 T00000300 Read-Data Status: 00000011 00000000
13:43:43.715940 BC000030A Read-Ack Status: 00000011 00001010
13:43:44.101591 T00000300 Read-Data Status: 00000011 00000000
13:43:44.249575 BC000030A Read-Ack Status: 00000011 00001010
13:43:44.634206 T10012E00 Write-Data Control setpoint: 46.00
13:43:44.789299 BD0012E00 Write-Ack Control setpoint: 46.00
13:43:45.167606 T00000300 Read-Data Status: 00000011 00000000
13:43:45.315030 BC000030A Read-Ack Status: 00000011 00001010
13:43:45.704165 T80190000 Read-Data Boiler water temperature: 0.00
13:43:45.848955 B40193480 Read-Ack Boiler water temperature: 52.50
13:43:46.239742 T00120000 Read-Data CH water pressure: 0.00
13:43:46.388490 BF0120000 Unk-DataId CH water pressure: 0.00
13:43:46.773167 T00000300 Read-Data Status: 00000011 00000000
13:43:46.918916 BC000030A Read-Ack Status: 00000011 00001010
13:43:47.309889 T00000300 Read-Data Status: 00000011 00000000
13:43:47.453706 BC000030A Read-Ack Status: 00000011 00001010
13:43:47.843671 T00000300 Read-Data Status: 00000011 00000000
13:43:47.987674 BC000030A Read-Ack Status: 00000011 00001010
13:43:48.378734 T00000300 Read-Data Status: 00000011 00000000
13:43:48.527397 BC000030A Read-Ack Status: 00000011 00001010
13:43:48.911711 T00000300 Read-Data Status: 00000011 00000000
13:43:49.067364 BC000030A Read-Ack Status: 00000011 00001010
13:43:49.444641 T10012E00 Write-Data Control setpoint: 46.00
13:43:49.587021 BD0012E00 Write-Ack Control setpoint: 46.00
13:43:49.978224 T00000300 Read-Data Status: 00000011 00000000
13:43:50.126862 BC000030A Read-Ack Status: 00000011 00001010
13:43:50.514141 T80190000 Read-Data Boiler water temperature: 0.00
13:43:50.666550 B40193480 Read-Ack Boiler water temperature: 52.50
13:43:51.044573 T00000300 Read-Data Status: 00000011 00000000
13:43:51.192079 BC000030A Read-Ack Status: 00000011 00001010
13:43:51.578059 T00000300 Read-Data Status: 00000011 00000000
13:43:51.724838 BC000030A Read-Ack Status: 00000011 00001010
13:43:52.110822 T00000300 Read-Data Status: 00000011 00000000
13:43:52.265730 BC000030A Read-Ack Status: 00000011 00001010
13:43:52.644177 T00000300 Read-Data Status: 00000011 00000000
13:43:52.791655 BC000030A Read-Ack Status: 00000011 00001010
13:43:53.177160 T00000300 Read-Data Status: 00000011 00000000
13:43:53.316559 BC000030A Read-Ack Status: 00000011 00001010
13:43:53.712432 T00000300 Read-Data Status: 00000011 00000000
13:43:53.864881 BC000030A Read-Ack Status: 00000011 00001010
13:43:54.243171 T10012E00 Write-Data Control setpoint: 46.00
13:43:54.390925 BD0012E00 Write-Ack Control setpoint: 46.00
13:43:54.789927 T00460100 Read-Data Status V/H: 00000001 00000000
13:43:54.956173 BF0460100 Unk-DataId Status V/H: 00000001 00000000
13:43:54.959756 AC0460100 Read-Ack Status V/H: 00000001 00000000
13:43:55.323836 T80190000 Read-Data Boiler water temperature: 0.00
13:43:55.470435 B40193480 Read-Ack Boiler water temperature: 52.50
13:43:55.854981 T00000300 Read-Data Status: 00000011 00000000
13:43:55.995220 BC000030A Read-Ack Status: 00000011 00001010
13:43:56.386056 T00000300 Read-Data Status: 00000011 00000000
13:43:56.530113 BC000030A Read-Ack Status: 00000011 00001010
13:43:56.921307 T00000300 Read-Data Status: 00000011 00000000
13:43:57.064321 BC000030A Read-Ack Status: 00000011 00001010
13:43:57.454007 T00000300 Read-Data Status: 00000011 00000000
13:43:57.603928 BC000030A Read-Ack Status: 00000011 00001010
13:43:57.989581 T00000300 Read-Data Status: 00000011 00000000
13:43:58.143040 BC000030A Read-Ack Status: 00000011 00001010
13:43:58.522761 T00000300 Read-Data Status: 00000011 00000000
13:43:58.669088 BC000030A Read-Ack Status: 00000011 00001010
13:43:59.053902 T00000300 Read-Data Status: 00000011 00000000
13:43:59.203914 BC000030A Read-Ack Status: 00000011 00001010
13:43:59.586583 T10012E00 Write-Data Control setpoint: 46.00
13:43:59.742825 BD0012E00 Write-Ack Control setpoint: 46.00
13:44:00.121994 T801C0000 Read-Data Return water temperature: 0.00
13:44:00.269095 BC01C0200 Read-Ack Return water temperature: 2.00
13:44:00.653197 T80190000 Read-Data Boiler water temperature: 0.00
13:44:00.802376 B40193480 Read-Ack Boiler water temperature: 52.50
13:44:01.186934 T00000300 Read-Data Status: 00000011 00000000
13:44:01.342255 BC000030A Read-Ack Status: 00000011 00001010
13:44:01.721667 T00000300 Read-Data Status: 00000011 00000000
13:44:01.868422 BC000030A Read-Ack Status: 00000011 00001010
13:44:02.252491 T00000300 Read-Data Status: 00000011 00000000
13:44:02.402094 BC000030A Read-Ack Status: 00000011 00001010
13:44:02.786199 T00000300 Read-Data Status: 00000011 00000000
13:44:02.941983 BC000030A Read-Ack Status: 00000011 00001010
13:44:03.321243 T00000300 Read-Data Status: 00000011 00000000
13:44:03.468487 BC000030A Read-Ack Status: 00000011 00001010
13:44:03.852554 T00000300 Read-Data Status: 00000011 00000000
13:44:04.001928 BC000030A Read-Ack Status: 00000011 00001010
13:44:04.385337 T10012E00 Write-Data Control setpoint: 46.00
13:44:04.541210 BD0012E00 Write-Ack Control setpoint: 46.00
13:44:04.918587 T001B0000 Read-Data Outside temperature: 0.00
13:44:05.072399 B601B0000 Data-Inv Outside temperature: 0.00
13:44:05.075202 AC01B101A Read-Ack Outside temperature: 16.10
13:44:05.451806 T80190000 Read-Data Boiler water temperature: 0.00
13:44:05.601050 B40193480 Read-Ack Boiler water temperature: 52.50
13:44:05.985532 T00000300 Read-Data Status: 00000011 00000000
13:44:06.140533 BC000030A Read-Ack Status: 00000011 00001010
13:44:06.520387 T00000300 Read-Data Status: 00000011 00000000
13:44:06.666333 BC000030A Read-Ack Status: 00000011 00001010
13:44:07.051859 T00000300 Read-Data Status: 00000011 00000000
13:44:07.190850 BC000030A Read-Ack Status: 00000011 00001010
13:44:07.586708 T00000300 Read-Data Status: 00000011 00000000
13:44:07.740061 BC000030A Read-Ack Status: 00000011 00001010
13:44:08.119839 T00000300 Read-Data Status: 00000011 00000000
13:44:08.265635 BC000030A Read-Ack Status: 00000011 00001010
13:44:08.651353 T00000300 Read-Data Status: 00000011 00000000
13:44:08.790470 BC000030A Read-Ack Status: 00000011 00001010
13:44:09.186223 T00000300 Read-Data Status: 00000011 00000000
13:44:09.338920 BC000030A Read-Ack Status: 00000011 00001010
13:44:09.736783 T10012E00 Write-Data Control setpoint: 46.00
13:44:09.879106 BD0012E00 Write-Ack Control setpoint: 46.00
13:44:10.269980 T80190000 Read-Data Boiler water temperature: 0.00
13:44:10.409675 B40193480 Read-Ack Boiler water temperature: 52.50
13:44:10.804933 T801A0000 Read-Data DHW temperature: 0.00
13:44:10.958808 B701A0000 Unk-DataId DHW temperature: 0.00
13:44:11.338177 T00000300 Read-Data Status: 00000011 00000000
13:44:11.484532 BC000030A Read-Ack Status: 00000011 00001010
13:44:11.869624 T00000300 Read-Data Status: 00000011 00000000
13:44:12.009187 BC000030A Read-Ack Status: 00000011 00001010
13:44:12.404268 T00000300 Read-Data Status: 00000011 00000000
13:44:12.558497 BC000030A Read-Ack Status: 00000011 00001010
13:44:12.937617 T00000300 Read-Data Status: 00000011 00000000
13:44:13.085520 BC000030A Read-Ack Status: 00000011 00001010
13:44:13.469004 T00000300 Read-Data Status: 00000011 00000000
13:44:13.617763 BC000030A Read-Ack Status: 00000011 00001010
13:44:14.002374 T00000300 Read-Data Status: 00000011 00000000
13:44:14.148640 BC000030A Read-Ack Status: 00000011 00001010
13:44:14.533688 T10012E00 Write-Data Control setpoint: 46.00
13:44:14.677666 BD0012E00 Write-Ack Control setpoint: 46.00
13:44:15.271869 T80190000 Read-Data Boiler water temperature: 0.00
13:44:15.418146 B40193480 Read-Ack Boiler water temperature: 52.50
13:44:16.376957 T80190000 Read-Data Boiler water temperature: 0.00
13:44:16.523266 B40193480 Read-Ack Boiler water temperature: 52.50
13:44:16.908629 T00090000 Read-Data Remote override room setpoint: 0.00
13:44:17.068423 BF0090000 Unk-DataId Remote override room setpoint: 0.00
13:44:17.071942 AC0090000 Read-Ack Remote override room setpoint: 0.00
13:44:17.441200 T00000300 Read-Data Status: 00000011 00000000
13:44:17.596945 BC000030A Read-Ack Status: 00000011 00001010
13:44:17.974868 T80640000 Read-Data Remote override function: 00000000
13:44:18.128154 B70640000 Unk-DataId Remote override function: 00000000
13:44:18.130934 A40640000 Read-Ack Remote override function: 00000000
13:44:18.508030 T00000300 Read-Data Status: 00000011 00000000
13:44:18.656746 BC000030A Read-Ack Status: 00000011 00001010
13:44:19.041214 T00000300 Read-Data Status: 00000011 00000000
13:44:19.196777 BC000030A Read-Ack Status: 00000011 00001010
13:44:19.576662 T10012E00 Write-Data Control setpoint: 46.00
13:44:19.722805 BD0012E00 Write-Ack Control setpoint: 46.00
13:44:20.107443 T90101600 Write-Data Room setpoint: 22.00
13:44:20.268439 BF0101600 Unk-DataId Room setpoint: 22.00
13:44:20.271401 A50101600 Write-Ack Room setpoint: 22.00
13:44:20.646190 T80190000 Read-Data Boiler water temperature: 0.00
13:44:20.796362 B40193480 Read-Ack Boiler water temperature: 52.50
13:44:21.187511 T00000300 Read-Data Status: 00000011 00000000
13:44:21.335840 BC000030A Read-Ack Status: 00000011 00001010
13:44:21.726689 T00000300 Read-Data Status: 00000011 00000000
13:44:21.875945 BC000030A Read-Ack Status: 00000011 00001010
13:44:22.763726 OT: 16.30
13:44:23.049399 T00000300 Read-Data Status: 00000011 00000000
13:44:23.196068 BC000030A Read-Ack Status: 00000011 00001010
13:44:24.135968 T00000300 Read-Data Status: 00000011 00000000
13:44:24.281307 BC000030A Read-Ack Status: 00000011 00001010
13:44:24.666046 T10012E00 Write-Data Control setpoint: 46.00
13:44:24.806093 BD0012E00 Write-Ack Control setpoint: 46.00
13:44:25.802721 T10012E00 Write-Data Control setpoint: 46.00
13:44:25.954941 BD0012E00 Write-Ack Control setpoint: 46.00
13:44:26.566026 T80190000 Read-Data Boiler water temperature: 0.00
13:44:26.715087 B40193480 Read-Ack Boiler water temperature: 52.50
13:44:27.858748 T00000300 Read-Data Status: 00000011 00000000
13:44:28.014811 BC000030A Read-Ack Status: 00000011 00001010
13:44:29.135540 T00000300 Read-Data Status: 00000011 00000000
13:44:29.280234 BC000030A Read-Ack Status: 00000011 00001010
13:44:30.558445 T00000300 Read-Data Status: 00000011 00000000
13:44:30.714005 BC000030A Read-Ack Status: 00000011 00001010
13:44:31.751167 T00000300 Read-Data Status: 00000011 00000000
13:44:31.893536 BC000030A Read-Ack Status: 00000011 00001010
13:44:32.762796 T00000300 Read-Data Status: 00000011 00000000
13:44:32.913342 BC000030A Read-Ack Status: 00000011 00001010
13:44:34.030142 T00000300 Read-Data Status: 00000011 00000000
13:44:34.173145 BC000030A Read-Ack Status: 00000011 00001010
13:44:34.563680 T00050000 Read-Data Application-specific flags: 00000000 0
13:44:34.703774 BC0050000 Read-Ack Application-specific flags: 00000000 0
13:44:35.094842 T10012E00 Write-Data Control setpoint: 46.00
13:44:35.238931 BD0012E00 Write-Ack Control setpoint: 46.00
13:44:35.630080 T10473200 Write-Data Control setpoint V/H: 50
13:44:35.772856 B70473200 Unk-DataId Control setpoint V/H: 50
13:44:36.163192 T80190000 Read-Data Boiler water temperature: 0.00
13:44:36.313116 B401935FF Read-Ack Boiler water temperature: 54.00
13:44:36.702193 T00460100 Read-Data Status V/H: 00000001 00000000
13:44:36.864188 BF0460100 Unk-DataId Status V/H: 00000001 00000000
13:44:36.868350 AC0460100 Read-Ack Status V/H: 00000001 00000000
13:44:37.238310 T00000300 Read-Data Status: 00000011 00000000
13:44:37.378841 BC000030A Read-Ack Status: 00000011 00001010
13:44:37.768627 T900E6400 Write-Data Maximum relative modulation level: 100.00
13:44:37.912914 BF00E6400 Unk-DataId Maximum relative modulation level: 100.00
13:44:38.303271 T80381400 Read-Data DHW setpoint: 20.00
13:44:38.452923 BC038001A Read-Ack DHW setpoint: 0.10
13:44:38.836727 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:38.983282 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:39.368047 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:39.512277 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:44:39.922699 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:40.072388 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:40.455904 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:40.612711 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:40.991305 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:41.138024 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:44:41.522420 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:41.672124 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:42.055952 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:42.211649 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:42.590694 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:42.738317 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:44:43.121783 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:43.271862 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:43.655902 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:43.811907 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:44:44.190143 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:44.337584 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:44:44.721109 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:44.872007 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:45.250588 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:45.397886 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:44:45.781794 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:45.931668 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:46.316949 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:46.471495 BC0395003 Read-Ack Max CH water setpoint: 80.01
13:44:46.850135 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:46.997775 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:44:47.381242 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:47.531863 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:47.916710 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:48.071667 BC0395003 Read-Ack Max CH water setpoint: 80.01
13:44:48.449771 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:48.597850 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:44:48.983631 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:49.131706 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:49.515952 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:49.671574 BC0395003 Read-Ack Max CH water setpoint: 80.01
13:44:50.049374 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:50.191370 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:44:50.582509 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:50.731281 BC0395003 Read-Ack Max CH water setpoint: 80.01
13:44:51.115484 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:51.271622 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:51.650718 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:51.797563 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:44:52.181963 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:52.331560 BC0395003 Read-Ack Max CH water setpoint: 80.01
13:44:52.715153 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:52.871380 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:53.250193 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:53.397513 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:44:53.781531 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:53.931423 BC0395078 Read-Ack Max CH water setpoint: 80.47
13:44:54.314514 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:54.462236 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:54.863591 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:55.002383 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:56.536955 óOpenTherm Gateway 4.0b0
13:44:56.837964 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:56.990766 BC0395003 Read-Ack Max CH water setpoint: 80.01
13:44:57.368825 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:57.511214 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:44:57.900430 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:58.051058 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:58.429630 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:58.576948 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:44:58.962305 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:59.110791 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:44:59.494153 T00395000 Read-Data Max CH water setpoint: 80.00
13:44:59.650659 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:45:00.029261 T00395000 Read-Data Max CH water setpoint: 80.00
13:45:00.176796 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:45:00.560423 T00395000 Read-Data Max CH water setpoint: 80.00
13:45:00.710725 BC03950FF Read-Ack Max CH water setpoint: 81.00
13:45:01.095664 T00395000 Read-Data Max CH water setpoint: 80.00
13:45:01.250802 B4039500B Read-Ack Max CH water setpoint: 80.04
13:45:01.628767 T00395000 Read-Data Max CH water setpoint: 80.00
13:45:01.776620 BC0395000 Read-Ack Max CH water setpoint: 80.00
13:45:02.160082 T00395000 Read-Data Max CH water setpoint: 80.00
13:45:02.310659 BC0395003 Read-Ack Max CH water setpoint: 80.01
13:45:02.701962 T00395000 Read-Data Max CH water setpoint: 80.00
13:45:02.850617 BC0395005 Read-Ack Max CH water setpoint: 80.02
13:45:03.234404 T00000300 Read-Data Status: 00000011 00000000
13:45:03.390905 BC000030A Read-Ack Status: 00000011 00001010
13:45:03.769294 T00480000 Read-Data Fault flags/code V/H: 00000000 0
13:45:03.916545 BF0480000 Unk-DataId Fault flags/code V/H: 00000000 0
13:45:04.300674 T10012E00 Write-Data Control setpoint: 46.00
13:45:04.450220 BD0012E00 Write-Ack Control setpoint: 46.00
13:45:04.835201 T10473200 Write-Data Control setpoint V/H: 50
13:45:04.990185 B70473200 Unk-DataId Control setpoint V/H: 50
13:45:05.368696 T80190000 Read-Data Boiler water temperature: 0.00
13:45:05.516260 BC0193580 Read-Ack Boiler water temperature: 53.50
13:45:05.900207 T00460100 Read-Data Status V/H: 00000001 00000000
13:45:06.049908 BF0460100 Unk-DataId Status V/H: 00000001 00000000
13:45:06.435429 T00460100 Read-Data Status V/H: 00000001 00000000
13:45:06.589751 BF0460100 Unk-DataId Status V/H: 00000001 00000000
13:45:06.968464 T00110000 Read-Data Relative modulation level: 0.00
13:45:07.116163 BC0112B00 Read-Ack Relative modulation level: 43.00
13:45:07.499498 T00000300 Read-Data Status: 00000011 00000000
13:45:07.649893 BC000030A Read-Ack Status: 00000011 00001010
13:45:08.034935 T801C0000 Read-Data Return water temperature: 0.00
13:45:08.189808 BC01C0200 Read-Ack Return water temperature: 2.00
13:45:08.568195 T001B0000 Read-Data Outside temperature: 0.00
13:45:08.714826 B601B0000 Data-Inv Outside temperature: 0.00
13:45:09.099305 T00120000 Read-Data CH water pressure: 0.00
13:45:09.249378 BF0120000 Unk-DataId CH water pressure: 0.00
13:45:09.634247 T10012E00 Write-Data Control setpoint: 46.00
13:45:09.789629 BD0012E00 Write-Ack Control setpoint: 46.00
13:45:10.185475 T801A0000 Read-Data DHW temperature: 0.00
13:45:10.329443 B701A0000 Unk-DataId DHW temperature: 0.00
13:45:10.720164 T80190000 Read-Data Boiler water temperature: 0.00
13:45:10.868861 BC0193580 Read-Ack Boiler water temperature: 53.50
13:45:11.253441 T1018166F Write-Data Room temperature: 22.43
13:45:11.399786 BD018166F Write-Ack Room temperature: 22.43
13:45:11.784821 T004E0000 Read-Data Relative humidity exhaust air: 0 0
13:45:11.928834 BF04E0000 Unk-DataId Relative humidity exhaust air: 0 0
13:45:12.319570 T00000300 Read-Data Status: 00000011 00000000
13:45:12.468770 BC000030A Read-Ack Status: 00000011 00001010
13:45:12.853042 T804F0000 Read-Data CO2 level exhaust air: 0
13:45:13.008448 B704F0000 Unk-DataId CO2 level exhaust air: 0
13:45:13.386138 T10473200 Write-Data Control setpoint V/H: 50
13:45:13.528098 B70473200 Unk-DataId Control setpoint V/H: 50
13:45:13.919420 T00000300 Read-Data Status: 00000011 00000000
13:45:14.068261 BC000030A Read-Ack Status: 00000011 00001010
13:45:14.452190 T10012E00 Write-Data Control setpoint: 46.00
13:45:14.608690 BD0012E00 Write-Ack Control setpoint: 46.00
13:45:14.985786 T00090000 Read-Data Remote override room setpoint: 0.00
13:45:15.139132 BF0090000 Unk-DataId Remote override room setpoint: 0.00
13:45:15.142329 AC0090000 Read-Ack Remote override room setpoint: 0.00
13:45:15.518854 T80190000 Read-Data Boiler water temperature: 0.00
13:45:15.667593 BC0193580 Read-Ack Boiler water temperature: 53.50
13:45:16.052154 T80640000 Read-Data Remote override function: 00000000
13:45:16.218423 B70640000 Unk-DataId Remote override function: 00000000
13:45:16.222011 A40640000 Read-Ack Remote override function: 00000000
13:45:16.587237 T00460100 Read-Data Status V/H: 00000001 00000000
13:45:16.733411 BF0460100 Unk-DataId Status V/H: 00000001 00000000
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
I decided to switch on the OH option by default because the opentherm specification already contradicts itself. In chapter 5.3.8.3 it says that the data format is u8 for the high byte and flag8 for the low byte. The function bits should go in the low byte and the high byte is reserved. But then in the Data-ID overview map (chapter 5.4) it says that the type is flag8/-, i.e. flag8 for the high byte, low byte reserved.
The sequence of events is the other way around: The thermostat keeps requesting the same message, the gateway concludes there is a problem and resets, after that it doesn't return a modified MsgID 70 anymore. That is expected, because that information is cleared by a reset.
It's easy to say that "in this case" the gateway should not reset itself. But how is the gateway supposed to distinguish this case from a real problem? To me it also looks like something is wrong if the thermostat requests the same information over 30 times in a row.
I would say the boiler is broken. The Max CH water setpoint is a limit, usually manually configured on the boiler. That should be a fixed value and definitely shouldn't be fluctuating this fast.
The thermostat uses the Max CH water setpoint value to limit the control setpoint it will send to the boiler. So there really is no good reason for it to get this freaked out about a change in the value. Still, you may be able to calm it down by configuring a Max CH water setpoint via the gateway, using the SH command.
How many times will the thermostat at most repeat the request? Would it help if I doubled the amount of repetitions that trigger a reset? I would hate to have to switch off this security feature because of your weird boiler. Are there any other messages that may be repeated this many times?
The sequence of events is the other way around: The thermostat keeps requesting the same message, the gateway concludes there is a problem and resets, after that it doesn't return a modified MsgID 70 anymore. That is expected, because that information is cleared by a reset.
It's easy to say that "in this case" the gateway should not reset itself. But how is the gateway supposed to distinguish this case from a real problem? To me it also looks like something is wrong if the thermostat requests the same information over 30 times in a row.
I would say the boiler is broken. The Max CH water setpoint is a limit, usually manually configured on the boiler. That should be a fixed value and definitely shouldn't be fluctuating this fast.
The thermostat uses the Max CH water setpoint value to limit the control setpoint it will send to the boiler. So there really is no good reason for it to get this freaked out about a change in the value. Still, you may be able to calm it down by configuring a Max CH water setpoint via the gateway, using the SH command.
How many times will the thermostat at most repeat the request? Would it help if I doubled the amount of repetitions that trigger a reset? I would hate to have to switch off this security feature because of your weird boiler. Are there any other messages that may be repeated this many times?
Schelte
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
I guess the protocol should define this - otherwise you can't determine a real problem.hvxl wrote:It's easy to say that "in this case" the gateway should not reset itself. But how is the gateway supposed to distinguish this case from a real problem? To me it also looks like something is wrong if the thermostat requests the same information over 30 times in a row.
The boiler isn't broken, but Daalderop has an interesting interpretation of the spec (as do most vendors).hvxl wrote:I would say the boiler is broken. The Max CH water setpoint is a limit, usually manually configured on the boiler. That should be a fixed value and definitely shouldn't be fluctuating this fast.
I don't know, but normally the thermostat will read a value 3-4 times to make sure it is stable and it has read it correctly. I suppose the same happens in this case.hvxl wrote:How many times will the thermostat at most repeat the request? Would it help if I doubled the amount of repetitions that trigger a reset? I would hate to have to switch off this security feature because of your weird boiler. Are there any other messages that may be repeated this many times?
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
Hi Schelte,Dickuk wrote:Thanks for the quick reply, sounds like a good idea.hvxl wrote:There is currently no way to dump some of these settings. The problem is that the output might not fit in the available transmit buffer. So such a report would have to be done in increments, which requires a lot of code. Because of the limited resources available in the PIC, I didn't think it was worth it.
But perhaps I can make an enhancement to otmonitor to copy the EEPROM settings from the old firmware to the new one. I'll look into that.
I noticed that you have put a 4.0b of otmonitor and have downloaded, I see the option is there for moving the EEPROM settings over to the new firmware, I'll give it a try and let you know how I get on.
Thanks
Richard
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
I've seen a sequence of 94 times - don't know if that is the longest though. So doubling it from 30 to 60 would not help. In my case only this message (57) is repeating this often.hvxl wrote:How many times will the thermostat at most repeat the request? Would it help if I doubled the amount of repetitions that trigger a reset? I would hate to have to switch off this security feature because of your weird boiler. Are there any other messages that may be repeated this many times?
BTW: note the typo in otmonitor message 87.
Code: Select all
18:17:10.126862 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:10.280540 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:10.658353 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:10.804659 B4039503E Read-Ack Max CH water setpoint: 80.24
18:17:11.588784 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:11.737417 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:12.123432 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:12.289479 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:13.027701 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:13.174715 BC0395003 Read-Ack Max CH water setpoint: 80.01
18:17:13.559138 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:13.713217 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:14.090566 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:14.230758 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:14.619959 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:14.769138 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:15.165350 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:15.307515 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:15.684524 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:15.825523 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:16.215707 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:16.363447 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:16.747199 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:16.901144 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:17.278617 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:17.419715 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:17.809560 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:17.957742 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:18.341113 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:18.495911 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:18.874240 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:19.020165 BC0395022 Read-Ack Max CH water setpoint: 80.13
18:17:19.403565 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:19.551636 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:19.935217 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:20.090138 B4039500D Read-Ack Max CH water setpoint: 80.05
18:17:20.467969 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:20.614386 B4039501A Read-Ack Max CH water setpoint: 80.10
18:17:20.997416 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:21.146397 BC0395003 Read-Ack Max CH water setpoint: 80.01
18:17:21.530757 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:21.684630 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:22.062003 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:22.202609 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:22.591275 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:22.740553 BC0395003 Read-Ack Max CH water setpoint: 80.01
18:17:23.124628 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:23.279078 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:23.655913 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:23.796988 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:24.186757 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:24.334896 BC0395003 Read-Ack Max CH water setpoint: 80.01
18:17:24.718181 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:24.873087 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:25.251388 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:25.397337 B40395002 Read-Ack Max CH water setpoint: 80.01
18:17:25.800046 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:25.949153 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:26.333412 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:26.487092 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:26.864406 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:27.005159 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:27.393876 T00573200 Read-Data Nominal ventialtion value: 50
18:17:27.543014 BF0573200 Unk-DataId Nominal ventialtion value: 50
18:17:27.927179 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:28.081162 BC0395003 Read-Ack Max CH water setpoint: 80.01
18:17:28.458277 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:28.600639 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:28.991210 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:29.137445 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:29.520616 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:29.675609 BC0395003 Read-Ack Max CH water setpoint: 80.01
18:17:30.054185 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:30.211110 B40395043 Read-Ack Max CH water setpoint: 80.26
18:17:30.584278 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:30.731454 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:31.114951 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:31.269783 BC0395003 Read-Ack Max CH water setpoint: 80.01
18:17:31.648060 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:31.794071 B4039503B Read-Ack Max CH water setpoint: 80.23
18:17:32.177428 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:32.325989 BC0395003 Read-Ack Max CH water setpoint: 80.01
18:17:32.709139 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:32.864293 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:33.248049 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:33.401912 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:33.779426 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:33.919865 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:34.308856 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:34.458061 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:34.841952 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:34.995752 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:35.373341 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:35.514094 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:35.902518 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:36.051804 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:36.430050 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:36.576143 B40395023 Read-Ack Max CH water setpoint: 80.14
18:17:36.959291 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:37.107710 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:37.490330 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:37.646041 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:38.023681 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:38.169980 BC039501B Read-Ack Max CH water setpoint: 80.11
18:17:38.552926 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:38.702396 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:39.084418 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:39.239621 BC0395003 Read-Ack Max CH water setpoint: 80.01
18:17:39.617799 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:39.764062 B40395013 Read-Ack Max CH water setpoint: 80.07
18:17:40.147325 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:40.308948 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:40.680567 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:40.833933 BC0395003 Read-Ack Max CH water setpoint: 80.01
18:17:41.229506 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:41.372074 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:41.760649 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:41.909598 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:42.294088 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:42.448009 B4039508C Read-Ack Max CH water setpoint: 80.55
18:17:42.825108 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:42.965779 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:43.354546 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:43.503555 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:43.887537 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:44.040540 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:44.418854 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:44.559231 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:44.947911 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:45.097121 BC0395003 Read-Ack Max CH water setpoint: 80.01
18:17:45.481294 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:45.635541 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:46.012523 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:46.153532 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:46.542432 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:46.692784 BC0395003 Read-Ack Max CH water setpoint: 80.01
18:17:47.075018 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:47.229518 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:47.606251 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:47.747189 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:48.135737 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:48.285492 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:48.668747 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:48.823115 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:49.200047 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:49.341172 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:49.731427 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:49.879293 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:50.262675 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:50.417228 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:50.795779 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:50.941607 B40395034 Read-Ack Max CH water setpoint: 80.20
18:17:51.325101 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:51.473124 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:51.855045 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:52.010870 BC0395003 Read-Ack Max CH water setpoint: 80.01
18:17:52.389588 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:52.535277 B4039502C Read-Ack Max CH water setpoint: 80.17
18:17:52.918774 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:53.066753 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:53.449845 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:53.604808 B4039508C Read-Ack Max CH water setpoint: 80.55
18:17:53.983290 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:54.129068 BC0395024 Read-Ack Max CH water setpoint: 80.14
18:17:54.512268 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:54.660674 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:55.043586 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:55.198704 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:55.576807 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:55.723272 B4039501C Read-Ack Max CH water setpoint: 80.11
18:17:56.123947 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:56.274951 B4039508C Read-Ack Max CH water setpoint: 80.55
18:17:56.661118 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:56.813115 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:57.190344 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:57.330916 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:57.719567 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:57.869004 B40395001 Read-Ack Max CH water setpoint: 80.00
18:17:58.252616 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:58.407012 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:17:58.784240 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:58.923600 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:17:59.313620 T00395000 Read-Data Max CH water setpoint: 80.00
18:17:59.463927 BC0395003 Read-Ack Max CH water setpoint: 80.01
18:17:59.846766 T00395000 Read-Data Max CH water setpoint: 80.00
18:18:00.011358 BC03950FF Read-Ack Max CH water setpoint: 81.00
18:18:00.377866 T00395000 Read-Data Max CH water setpoint: 80.00
18:18:00.518854 BC0395000 Read-Ack Max CH water setpoint: 80.00
18:18:00.909196 T00395000 Read-Data Max CH water setpoint: 80.00
18:18:01.056889 BC03950FF Read-Ack Max CH water setpoint: 81.00
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
The specs say no valid response for 1 min. should be considered a communications fault. So I'm planning to go with that. Due to the higher message rate used by the Honeywell Vision thermostat, that corresponds with about 110 repetitions before the gateway would reset.nlrb wrote:I've seen a sequence of 94 times - don't know if that is the longest though. So doubling it from 30 to 60 would not help. In my case only this message (57) is repeating this often.
I don't know if you intended your log to be an example of a sequence of 94 repeated messages, but there's one other message in between, which would restart the counter.
Fixed, to be included in the next otmonitor version.nlrb wrote:BTW: note the typo in otmonitor message 87.
Schelte
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
Hi SchelteDickuk wrote:Hi Schelte,Dickuk wrote:Thanks for the quick reply, sounds like a good idea.hvxl wrote:There is currently no way to dump some of these settings. The problem is that the output might not fit in the available transmit buffer. So such a report would have to be done in increments, which requires a lot of code. Because of the limited resources available in the PIC, I didn't think it was worth it.
But perhaps I can make an enhancement to otmonitor to copy the EEPROM settings from the old firmware to the new one. I'll look into that.
I noticed that you have put a 4.0b of otmonitor and have downloaded, I see the option is there for moving the EEPROM settings over to the new firmware, I'll give it a try and let you know how I get on.
Thanks
Richard
I have loaded the new otmonitor but when I select my new firmware file the 'Program' button is greyed out.
I'm using a TCP connection through an RS232/IP box which is next to the boiler and this always worked with otmonitor before.
I'm running otmonitor as admin too.
Any ideas?
Thanks
Richard

Re: Opentherm Gateway 4.0 alpha/beta testers wanted
That was a bug. Try otmonitor 4.0b1.Dickuk wrote:I have loaded the new otmonitor but when I select my new firmware file the 'Program' button is greyed out.
Schelte
Re: Opentherm Gateway 4.0 alpha/beta testers wanted
Would you make some sort of command line otmonitor? Maybe ncurses..?hvxl wrote:That was a bug. Try otmonitor 4.0b1.
Even just the ability to flash firmware without GUI will be perfect!
ps: sorry if "wanted/to-do's" should be placed somewhere out of this thread.
It's nice to be important, but it's more important to be nice...