Re: OTGW system error
Posted: Thu Feb 24, 2022 7:13 pm
Firmware version 5.3 is now available on the web site.
Domotica - Home Automation Forum
https://www.domoticaforum.eu/
Yes.hvxl wrote:Are you implying that the fix doesn't work?
Well I suppose to be quite strict, I have no way to know if it is the same internal problem in the code, but I certainly observe exactly the same external symptoms as the OP did..hvxl wrote:Are you sure you are experiencing the same problem?
...and for the avoidance of doubt, I can confirm that in the received PS MsgID=0 messages there was never a message received with bit 0 set; so I think that rules out the boiler maintenance LED being caused by an error in the boiler....the Boiler Maintenance LED turns on
Ok I would be happy to do that. But before I start logging something that might be wrong for you, perhaps you can let me know what exact information you want to see via this specific OpenHAB setup? The OpenHAB binding is connecting as a client to the serial port via the USR-TCP232 server, and running the Java pseudo code below; important is to note that it is operating in PS=0 mode..hvxl wrote:Please provide a log.
Code: Select all
// TCP serial port POLLING thread
socket.write("PR=A\r\n");
socket.write("PS=0\r\n);
while (!interrupted) {
inputString = socket.readln();
doSomethingWith(inputString);
}
Code: Select all
// TCP serial port COMMAND thread
while (!interrupted) {
socket.write("CS=" + setPoint.toString() +"\r\n"); // setpoint values between 50.0 and 65.0 (enabled) resp. 0.0 (disabled)
socket.write("CH=" + (isEnabled ? "1" : "0") + "\r\n");
sleep(30000);
}
Code: Select all
2022-03-09 15:19:10.418 [TRACE] [rnal.OpenThermGatewaySocketConnector] - write: CS=50.0
2022-03-09 15:19:10.429 [TRACE] [rnal.OpenThermGatewaySocketConnector] - write: CH=1
2022-03-09 15:19:10.450 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: CS: 50.00
2022-03-09 15:19:10.476 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: CH: 1
2022-03-09 15:19:11.203 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00780000
2022-03-09 15:19:11.340 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC078160E
2022-03-09 15:19:12.228 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00110000
2022-03-09 15:19:12.439 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0110000
2022-03-09 15:19:13.262 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R001B0000
2022-03-09 15:19:13.452 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B601B0000
2022-03-09 15:19:14.289 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R801A0000
2022-03-09 15:19:14.464 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC01A2E19
2022-03-09 15:19:15.314 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R900E6400
2022-03-09 15:19:15.467 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B500E6400
2022-03-09 15:19:16.341 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00740000
2022-03-09 15:19:16.476 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B40740632
2022-03-09 15:19:17.366 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80000100
2022-03-09 15:19:17.596 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0000102
2022-03-09 15:19:18.401 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80190000
2022-03-09 15:19:18.600 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B40192E33
2022-03-09 15:19:19.427 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R90013200
2022-03-09 15:19:19.610 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B50013200
2022-03-09 15:19:20.448 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80380000
2022-03-09 15:19:20.601 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0383700
2022-03-09 15:19:21.472 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00390000
2022-03-09 15:19:21.608 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0394100
2022-03-09 15:19:22.498 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00780000
2022-03-09 15:19:22.726 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC078160E
2022-03-09 15:19:23.516 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R801A0000
2022-03-09 15:19:23.737 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC01A2E19
2022-03-09 15:19:24.542 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80000100
2022-03-09 15:19:24.744 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0000102
2022-03-09 15:19:25.568 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80190000
2022-03-09 15:19:25.758 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0192DE6
2022-03-09 15:19:26.595 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R90013200
2022-03-09 15:19:26.762 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B50013200
2022-03-09 15:19:27.618 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00740000
2022-03-09 15:19:27.770 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B40740632
2022-03-09 15:19:28.641 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00110000
2022-03-09 15:19:28.875 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0110000
2022-03-09 15:19:29.682 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R001B0000
2022-03-09 15:19:29.877 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B601B0000
2022-03-09 15:19:30.701 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00780000
2022-03-09 15:19:30.891 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC078160E
2022-03-09 15:19:31.725 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R900E6400
2022-03-09 15:19:31.894 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B500E6400
2022-03-09 15:19:32.752 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R801A0000
2022-03-09 15:19:32.903 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC01A2E19
2022-03-09 15:19:33.776 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80000100
2022-03-09 15:19:33.912 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0000102
2022-03-09 15:19:34.806 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80190000
2022-03-09 15:19:35.028 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0192DE6
2022-03-09 15:19:35.835 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R90013200
2022-03-09 15:19:36.037 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B50013200
2022-03-09 15:19:36.866 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80380000
2022-03-09 15:19:37.046 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0383700
2022-03-09 15:19:37.885 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00390000
2022-03-09 15:19:38.060 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0394100
2022-03-09 15:19:38.911 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00740000
2022-03-09 15:19:39.064 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B40740632
2022-03-09 15:19:39.934 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00780000
2022-03-09 15:19:40.166 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC078160E
2022-03-09 15:19:40.971 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80000100
2022-03-09 15:19:41.169 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0000102
2022-03-09 15:19:41.992 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80190000
2022-03-09 15:19:42.181 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0192DE6
2022-03-09 15:19:43.016 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R90013200
2022-03-09 15:19:43.185 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B50013200
2022-03-09 15:19:44.044 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R801A0000
2022-03-09 15:19:44.197 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC01A2E19
2022-03-09 15:19:45.065 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00110000
2022-03-09 15:19:45.202 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0110000
2022-03-09 15:19:46.090 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R001B0000
2022-03-09 15:19:46.318 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B601B0000
2022-03-09 15:19:47.126 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00740000
2022-03-09 15:19:47.326 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B40740632
2022-03-09 15:19:48.149 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R900E6400
2022-03-09 15:19:48.334 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B500E6400
2022-03-09 15:19:49.175 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00780000
2022-03-09 15:19:49.343 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC078160E
2022-03-09 15:19:50.201 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80000100
2022-03-09 15:19:50.333 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0000102
2022-03-09 15:19:50.423 [TRACE] [rnal.OpenThermGatewaySocketConnector] - write: CS=50.0
2022-03-09 15:19:50.431 [TRACE] [rnal.OpenThermGatewaySocketConnector] - write: CH=1
2022-03-09 15:19:50.457 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: CS: 50.00
2022-03-09 15:19:50.458 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: CH: 1
2022-03-09 15:19:51.225 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80190000
2022-03-09 15:19:51.453 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B40192D99
2022-03-09 15:19:52.257 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R90013200
2022-03-09 15:19:52.458 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B50013200
2022-03-09 15:19:53.281 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80380000
2022-03-09 15:19:53.466 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0383700
2022-03-09 15:19:54.311 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00390000
2022-03-09 15:19:54.586 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0394100
2022-03-09 15:19:55.326 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R801A0000
2022-03-09 15:19:55.596 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC01A2E19
2022-03-09 15:19:56.350 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00740000
2022-03-09 15:19:56.583 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B40740632
2022-03-09 15:19:57.375 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80000100
2022-03-09 15:19:57.590 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0000102
2022-03-09 15:19:58.399 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80190000
2022-03-09 15:19:58.711 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0192D80
2022-03-09 15:19:59.434 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R90013200
2022-03-09 15:19:59.714 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B50013200
2022-03-09 15:20:00.457 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00780000
2022-03-09 15:20:00.723 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC078160E
2022-03-09 15:20:01.486 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00110000
2022-03-09 15:20:01.738 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC0110000
2022-03-09 15:20:02.506 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R001B0000
2022-03-09 15:20:02.742 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B601B0000
2022-03-09 15:20:03.532 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R801A0000
2022-03-09 15:20:03.749 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: BC01A2E19
2022-03-09 15:20:04.558 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R900E6400
2022-03-09 15:20:04.757 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B500E6400
2022-03-09 15:20:05.585 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R00740000
2022-03-09 15:20:05.766 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: B40740632
2022-03-09 15:20:06.606 [TRACE] [rnal.OpenThermGatewaySocketConnector] - read: R80000100