Page 1 of 1
time changing on chronotherm 4
Posted: Sun Mar 01, 2015 12:48 pm
by arnoldg
Hello,
I have a chronotherm 4 connected to my openthermgateway and know the time on the chronotherm is changing several times a day.
Why is this and what can i do to prevent it.
Re: time changing on chronotherm 4
Posted: Sun Mar 01, 2015 2:52 pm
by hvxl
Is someone or something sending bad SC commands to the gateway?
Can you provide a otmonitor log for a period covering such an event?
Re: time changing on chronotherm 4
Posted: Sun Mar 01, 2015 8:53 pm
by arnoldg
Well at this time there is nothing connected to the otg so there aren't send any signals from the otg to the thermostate or boiler.
I will hook up a computer to log the data packets.
Re: time changing on chronotherm 4
Posted: Tue Jun 09, 2015 3:42 pm
by adegoeij
I am experiencing the same issue.
By chronotherm 4 (CMT8851M100) time is going back to 00:00 regularly.
My setup is this:
Boiler: AWB 3HR23T
Thermostat: Honeywell Chronotherm IV (CMT8851M100)
Opentherm-GW USB interface connected to Raspberry Pi with rasbian and otmonitor(ARM)
otmonitor is setup in relay mode and Domiticz setup at another Pi reads the status via the relay.
I have the logfile enable and sofar i did not see any SC command to set the time (logging enable since a few hours)
But i will continue monitoring/logging and get back
Re: time changing on chronotherm 4
Posted: Sun Jun 14, 2015 5:59 pm
by hvxl
Same question goes for you then: Can you provide a otmonitor log for a period covering such an event?
Re: time changing on chronotherm 4
Posted: Thu Apr 01, 2021 4:11 pm
by Tomas
I have a very similar issue with same model Chronotherm 4 (T8851M1000), the clock does not work well when connected to the Opentherm Gateway. In my case it does not reset fully back to 00:00 but it runs far slower than it should be. After some research I think this log describes the issue:
Code: Select all
09:24:50.089909 T10142918 Write-Data Day of week and time of day: Mon 09:24
09:24:50.148684 BF0140000 Unk-DataId Day of week and time of day: Unk 00:00
09:24:50.195107 AD0142918 Write-Ack Day of week and time of day: Mon 09:24
09:25:31.057034 T10142918 Write-Data Day of week and time of day: Mon 09:24
09:25:31.150066 BF0140000 Unk-DataId Day of week and time of day: Unk 00:00
09:25:31.154009 AD0142918 Write-Ack Day of week and time of day: Mon 09:24
09:26:31.093830 T90142919 Write-Data Day of week and time of day: Mon 09:25
09:26:31.144204 BF0140000 Unk-DataId Day of week and time of day: Unk 00:00
09:26:31.211638 A50142919 Write-Ack Day of week and time of day: Mon 09:25
09:27:52.075767 T9014291A Write-Data Day of week and time of day: Mon 09:26
09:27:52.167749 BF0140000 Unk-DataId Day of week and time of day: Unk 00:00
09:27:52.168644 A5014291A Write-Ack Day of week and time of day: Mon 09:26
09:28:53.059286 T1014291B Write-Data Day of week and time of day: Mon 09:27
09:28:53.150881 BF0140000 Unk-DataId Day of week and time of day: Unk 00:00
09:28:53.151476 AD014291B Write-Ack Day of week and time of day: Mon 09:27
09:29:43.078857 T1014291B Write-Data Day of week and time of day: Mon 09:27
09:29:43.171775 BF0140000 Unk-DataId Day of week and time of day: Unk 00:00
09:29:43.172409 AD014291B Write-Ack Day of week and time of day: Mon 09:27
Looking at the display, the thermostat resets the time to the value received in the Write-Ack message, which is a time with hours/minutes only. So when the clock of the thermostat is at 09:24:50 when sending the message, it receives an ACK with "09:24" in it and will reset the clock to "09:24:00". Then some time later it will send another message, if that other message is less than 1 minute after the previous (as is the case in the log at 09:25:31) then the internal clock will now be 09:24:31 and it will receive another ACK with "09:24" again resetting the thermostat clock to "09:24:00". Which causes the clock in the thermostat to quickly fall behind the correct time.
To confirm this theory I check with the gateway in monitoring mode. In that case the boiler responds with "Unk-DataId" only, and then the thermostat clock keeps counting time correctly.
I think the solution is to adjust the gateway firmware to only send a Write-Ack with time value in case an "SC" command has been received in the last 61 seconds.
Re: time changing on chronotherm 4
Posted: Sat Apr 10, 2021 10:06 pm
by hvxl
I never experienced this behavior when I was using the Chronotherm Modulation (I assume that's what you are referring to, because the Chronotherm 4 is an on/off thermostat). But I mostly used to send the current time to the OTGW. With that method, the clock of the thermostat was accurate to the second after a while.
Looking back at my old logs, I see that my Chronotherm Modulation would send MsgID 20 at intervals of 1 minute, or just slightly longer. I guess that would prevent the issue from ever happening. But as I mentioned, the clock used to be accurate to the second when I sent the time. If the seconds would be reset to 0 upon receiving the response, I would expect that it would have been up to one minute behind.
So, I'm wondering why your Chronotherm Modulation is requesting MsgID 20 at more irregular intervals than mine did. Does something happen that causes it to start its message sequence over? Understandably you filtered the log you provided, but I would really like to take a look at a full log covering this slowing of the clock.
Re: time changing on chronotherm 4
Posted: Thu Apr 15, 2021 10:45 am
by Tomas
I've created a longer log of about 10 minutes, the time was correct within ~5 seconds at 10:30 when I switched from monitor to gateway mode and it ended up behind by 4 minutes at 10:40. The log below is shortened to stay within the maximum post size of the forum, but here is the full log:
https://pastebin.com/GBFBLbMe
Code: Select all
10:30:23.507578 GW: 1
10:30:23.883507 T80190000 Read-Data Boiler water temperature: 0.00
10:30:24.864470 T80190000 Read-Data Boiler water temperature: 0.00
10:30:25.893651 T80190000 Read-Data Boiler water temperature: 0.00
10:30:26.018420 BC0194000 Read-Ack Boiler water temperature: 64.00
10:30:26.875499 T10010A00 Write-Data Control setpoint: 10.00
10:30:26.983976 BD0010A00 Write-Ack Control setpoint: 10.00
10:30:27.859351 T80640000 Read-Data Remote override function: 00000000
10:30:27.978621 Error 03
10:30:28.896307 T80000200 Read-Data Status: 00000010 00000000
10:30:28.954382 B40000200 Read-Ack Status: 00000010 00000000
10:30:29.875249 T80190000 Read-Data Boiler water temperature: 0.00
10:30:29.973310 BC0194000 Read-Ack Boiler water temperature: 64.00
10:30:30.871976 T10010A00 Write-Data Control setpoint: 10.00
10:30:30.967557 BD0010A00 Write-Ack Control setpoint: 10.00
10:30:31.897783 T80640000 Read-Data Remote override function: 00000000
10:30:32.877200 T80640000 Read-Data Remote override function: 00000000
10:30:32.964229 B70640000 Unk-DataId Remote override function: 00000000
10:30:32.973635 A40640000 Read-Ack Remote override function: 00000000
10:30:33.897693 T80190000 Read-Data Boiler water temperature: 0.00
10:30:34.003355 BC0194000 Read-Ack Boiler water temperature: 64.00
10:30:34.896713 T10010A00 Write-Data Control setpoint: 10.00
10:30:34.964646 BD0010A00 Write-Ack Control setpoint: 10.00
10:30:35.882747 T00110000 Read-Data Relative modulation level: 0.00
10:30:35.941192 BC0110000 Read-Ack Relative modulation level: 0.00
10:30:36.911160 T10181505 Write-Data Room temperature: 21.02
10:30:36.968612 BF0180000 Unk-DataId Room temperature: 0.00
10:30:37.888071 T90101480 Write-Data Room setpoint: 20.50
10:30:37.980996 B70100000 Unk-DataId Room setpoint: 0.00
10:30:37.983469 AD0100000 Write-Ack Room setpoint: 0.00
10:30:38.888976 T80000200 Read-Data Status: 00000010 00000000
10:30:38.938892 B40000200 Read-Ack Status: 00000010 00000000
10:30:39.903424 T80190000 Read-Data Boiler water temperature: 0.00
10:30:39.963714 BC0194000 Read-Ack Boiler water temperature: 64.00
10:30:40.887305 T10010A00 Write-Data Control setpoint: 10.00
10:30:41.006459 BD0010A00 Write-Ack Control setpoint: 10.00
10:30:41.869738 T00110000 Read-Data Relative modulation level: 0.00
10:30:41.977721 Error 03
10:30:42.899705 T00110000 Read-Data Relative modulation level: 0.00
10:30:43.009126 BC0110000 Read-Ack Relative modulation level: 0.00
10:30:43.889550 T80190000 Read-Data Boiler water temperature: 0.00
10:30:43.978917 BC0194000 Read-Ack Boiler water temperature: 64.00
10:30:44.868735 T10010A00 Write-Data Control setpoint: 10.00
10:30:44.929621 BD0010A00 Write-Ack Control setpoint: 10.00
10:30:45.895141 T10148A1E Write-Data Day of week and time of day: Thu 10:30
10:30:46.870696 T10148A1E Write-Data Day of week and time of day: Thu 10:30
10:30:46.979632 BF0140000 Unk-DataId Day of week and time of day: Unk 00:00
10:30:46.983052 AD0148A1E Write-Ack Day of week and time of day: Thu 10:30
10:30:47.869865 T801C0000 Read-Data Return water temperature: 0.00
10:30:47.980102 BC01C2F00 Read-Ack Return water temperature: 47.00
10:30:48.864268 T80000200 Read-Data Status: 00000010 00000000
10:30:48.933062 B40000200 Read-Ack Status: 00000010 00000000
10:30:49.896162 T80190000 Read-Data Boiler water temperature: 0.00
10:30:49.991107 BC0194000 Read-Ack Boiler water temperature: 64.00
10:30:50.881102 T10010A00 Write-Data Control setpoint: 10.00
10:30:50.987635 BD0010A00 Write-Ack Control setpoint: 10.00
10:30:51.908465 T00110000 Read-Data Relative modulation level: 0.00
10:30:51.955623 BC0110000 Read-Ack Relative modulation level: 0.00
10:30:52.910007 T801A0000 Read-Data DHW temperature: 0.00
10:30:53.889774 T80190000 Read-Data Boiler water temperature: 0.00
10:30:53.962333 BC0194000 Read-Ack Boiler water temperature: 64.00
10:30:54.909810 T10010A00 Write-Data Control setpoint: 10.00
10:30:54.966858 BD0010A00 Write-Ack Control setpoint: 10.00
10:30:55.937625 T801A0000 Read-Data DHW temperature: 0.00
10:30:55.996715 Error 04
10:30:56.005324 EC05A3200
10:30:56.871760 T801A0000 Read-Data DHW temperature: 0.00
10:30:57.925948 T801A0000 Read-Data DHW temperature: 0.00
10:30:57.978487 BC01A3200 Read-Ack DHW temperature: 50.00
10:30:58.881585 T80000200 Read-Data Status: 00000010 00000000
10:30:58.990066 B40000200 Read-Ack Status: 00000010 00000000
10:30:59.896550 T80000200 Read-Data Status: 00000010 00000000
10:30:59.976806 B40000200 Read-Ack Status: 00000010 00000000
10:31:00.905900 T80190000 Read-Data Boiler water temperature: 0.00
10:31:01.012748 BC0194000 Read-Ack Boiler water temperature: 64.00
10:31:01.882778 T10010A00 Write-Data Control setpoint: 10.00
10:31:01.979769 BD0010A00 Write-Ack Control setpoint: 10.00
10:31:02.864291 T10383FFF Write-Data DHW setpoint: 64.00
10:31:02.976360 BD0383FFF Write-Ack DHW setpoint: 64.00
10:31:03.895600 T90395AFC Write-Data Max CH water setpoint: 90.98
10:31:04.004883 B50395AFC Write-Ack Max CH water setpoint: 90.98
10:31:04.891468 T80190000 Read-Data Boiler water temperature: 0.00
10:31:04.948865 BC0194000 Read-Ack Boiler water temperature: 64.00
10:31:05.870759 T10010A00 Write-Data Control setpoint: 10.00
10:31:05.931938 BD0010A00 Write-Ack Control setpoint: 10.00
10:31:06.899258 T00090000 Read-Data Remote override room setpoint: 0.00
10:31:06.958452 BF0090000 Unk-DataId Remote override room setpoint: 0.00
10:31:07.012224 AC0090000 Read-Ack Remote override room setpoint: 0.00
10:31:07.887204 T00090000 Read-Data Remote override room setpoint: 0.00
10:31:07.986143 BF0090000 Unk-DataId Remote override room setpoint: 0.00
10:31:07.989056 AC0090000 Read-Ack Remote override room setpoint: 0.00
10:31:08.862484 T00090000 Read-Data Remote override room setpoint: 0.00
10:31:08.971951 BF0090000 Unk-DataId Remote override room setpoint: 0.00
10:31:08.974510 AC0090000 Read-Ack Remote override room setpoint: 0.00
10:31:09.908109 T80000200 Read-Data Status: 00000010 00000000
10:31:10.025755 Error 03
10:31:10.892604 T80000200 Read-Data Status: 00000010 00000000
10:31:11.872370 T80000200 Read-Data Status: 00000010 00000000
10:31:11.930659 B40000200 Read-Ack Status: 00000010 00000000
10:31:12.897388 T80190000 Read-Data Boiler water temperature: 0.00
10:31:12.988876 BC0194000 Read-Ack Boiler water temperature: 64.00
10:31:13.883681 T10010A00 Write-Data Control setpoint: 10.00
10:31:13.943161 BD0010A00 Write-Ack Control setpoint: 10.00
10:31:14.862528 T80190000 Read-Data Boiler water temperature: 0.00
10:31:14.975913 BC0194000 Read-Ack Boiler water temperature: 64.00
10:31:15.898568 T10010A00 Write-Data Control setpoint: 10.00
10:31:16.002650 BD0010A00 Write-Ack Control setpoint: 10.00
10:31:16.876858 T80640000 Read-Data Remote override function: 00000000
10:31:16.987732 B70640000 Unk-DataId Remote override function: 00000000
10:31:16.997877 A40640000 Read-Ack Remote override function: 00000000
10:31:17.877084 T00110000 Read-Data Relative modulation level: 0.00
10:31:18.894683 T00110000 Read-Data Relative modulation level: 0.00
10:31:18.952338 BC0110000 Read-Ack Relative modulation level: 0.00
10:31:19.884062 T80000200 Read-Data Status: 00000010 00000000
10:31:19.976747 B40000200 Read-Ack Status: 00000010 00000000
10:31:20.896180 T80190000 Read-Data Boiler water temperature: 0.00
10:31:20.944470 Error 03
10:31:21.889399 T80190000 Read-Data Boiler water temperature: 0.00
10:31:21.949273 BC0194000 Read-Ack Boiler water temperature: 64.00
10:31:22.882085 T10010A00 Write-Data Control setpoint: 10.00
10:31:22.975108 BD0010A00 Write-Ack Control setpoint: 10.00
10:31:23.899897 T00110000 Read-Data Relative modulation level: 0.00
10:31:24.024504 Error 03
10:31:24.881547 T80190000 Read-Data Boiler water temperature: 0.00
10:31:25.867157 T80190000 Read-Data Boiler water temperature: 0.00
10:31:25.961069 BC0194000 Read-Ack Boiler water temperature: 64.00
10:31:26.905400 T10010A00 Write-Data Control setpoint: 10.00
10:31:26.967068 BD0010A00 Write-Ack Control setpoint: 10.00
10:31:27.887627 T00110000 Read-Data Relative modulation level: 0.00
10:31:28.002277 Error 03
10:31:28.913954 T00110000 Read-Data Relative modulation level: 0.00
10:31:29.007904 BC0110000 Read-Ack Relative modulation level: 0.00
10:31:29.897051 T80000200 Read-Data Status: 00000010 00000000
10:31:29.991666 B40000200 Read-Ack Status: 00000010 00000000
10:31:30.893664 T80190000 Read-Data Boiler water temperature: 0.00
10:31:30.988012 BC0194000 Read-Ack Boiler water temperature: 64.00
10:31:31.883531 T10010A00 Write-Data Control setpoint: 10.00
10:31:31.937755 BD0010A00 Write-Ack Control setpoint: 10.00
10:31:32.909918 T00110000 Read-Data Relative modulation level: 0.00
10:31:33.000787 BC0110000 Read-Ack Relative modulation level: 0.00
10:31:33.892026 T90181508 Write-Data Room temperature: 21.03
10:31:33.950586 BF0180000 Unk-DataId Room temperature: 0.00
10:31:34.871888 T80190000 Read-Data Boiler water temperature: 0.00
10:31:34.981264 Error 03
10:31:35.905446 T80190000 Read-Data Boiler water temperature: 0.00
10:31:35.996713 BC0194000 Read-Ack Boiler water temperature: 64.00
10:31:36.893507 T10010A00 Write-Data Control setpoint: 10.00
10:31:36.951315 BD0010A00 Write-Ack Control setpoint: 10.00
10:31:37.869489 T90101480 Write-Data Room setpoint: 20.50
10:31:37.965708 B70100000 Unk-DataId Room setpoint: 0.00
10:31:37.971380 AD0100000 Write-Ack Room setpoint: 0.00
10:31:38.899090 T10148A1E Write-Data Day of week and time of day: Thu 10:30
10:31:39.884030 T80000200 Read-Data Status: 00000010 00000000
10:31:39.940391 B40000200 Read-Ack Status: 00000010 00000000
10:31:40.859667 T80190000 Read-Data Boiler water temperature: 0.00
10:31:40.966899 BC0194000 Read-Ack Boiler water temperature: 64.00
10:31:41.907617 T10010A00 Write-Data Control setpoint: 10.00
10:31:41.968092 Error 03
10:31:42.886403 T10010A00 Write-Data Control setpoint: 10.00
10:31:43.903954 T10010A00 Write-Data Control setpoint: 10.00
10:31:43.965435 BD0010A00 Write-Ack Control setpoint: 10.00
10:31:44.911273 T80190000 Read-Data Boiler water temperature: 0.00
10:31:44.968280 BC0194000 Read-Ack Boiler water temperature: 64.00
10:31:45.872602 T10010A00 Write-Data Control setpoint: 10.00
10:31:45.980509 BD0010A00 Write-Ack Control setpoint: 10.00
10:31:46.905008 T00110000 Read-Data Relative modulation level: 0.00
10:31:47.000020 BC0110000 Read-Ack Relative modulation level: 0.00
10:31:47.898731 T90148A1F Write-Data Day of week and time of day: Thu 10:31
10:31:47.955151 BF0140000 Unk-DataId Day of week and time of day: Unk 00:00
10:31:48.001172 A50148A1F Write-Ack Day of week and time of day: Thu 10:31
10:31:48.878243 T801C0000 Read-Data Return water temperature: 0.00
10:31:48.989524 B401C2E00 Read-Ack Return water temperature: 46.00
10:31:49.866320 T80000200 Read-Data Status: 00000010 00000000
10:31:50.892573 T80000200 Read-Data Status: 00000010 00000000
10:31:51.002014 B40000200 Read-Ack Status: 00000010 00000000
10:31:51.880367 T80190000 Read-Data Boiler water temperature: 0.00
10:31:51.994877 BC0194000 Read-Ack Boiler water temperature: 64.00
10:31:52.871041 T10010A00 Write-Data Control setpoint: 10.00
10:31:52.967544 BD0010A00 Write-Ack Control setpoint: 10.00
10:31:53.909463 T00110000 Read-Data Relative modulation level: 0.00
10:31:53.967510 BC0110000 Read-Ack Relative modulation level: 0.00
10:31:54.884450 T80190000 Read-Data Boiler water temperature: 0.00
10:31:54.993855 BC0194000 Read-Ack Boiler water temperature: 64.00
10:31:55.885503 T10010A00 Write-Data Control setpoint: 10.00
10:31:55.937484 BD0010A00 Write-Ack Control setpoint: 10.00
10:31:56.910458 T801A0000 Read-Data DHW temperature: 0.00
10:31:57.020629 BC01A3200 Read-Ack DHW temperature: 50.00
10:31:57.890494 T001B0000 Read-Data Outside temperature: 0.00
10:31:57.998523 B401BE0FF Read-Ack Outside temperature: -31.00
10:31:58.874131 T00120000 Read-Data CH water pressure: 0.00
10:31:58.945192 B40120166 Read-Ack CH water pressure: 1.40
10:31:59.869997 T80000200 Read-Data Status: 00000010 00000000
10:31:59.981773 Error 03
10:32:00.903036 T80000200 Read-Data Status: 00000010 00000000
10:32:00.960564 B40000260 Read-Ack Status: 00000010 01100000
10:32:01.878633 T80190000 Read-Data Boiler water temperature: 0.00
10:32:01.942143 BC0194000 Read-Ack Boiler water temperature: 64.00
10:32:02.910736 T10010A00 Write-Data Control setpoint: 10.00
10:32:02.970996 BD0010A00 Write-Ack Control setpoint: 10.00
10:32:03.905085 T10383FFF Write-Data DHW setpoint: 64.00
10:32:04.890603 T80190000 Read-Data Boiler water temperature: 0.00
10:32:04.958953 BC0194000 Read-Ack Boiler water temperature: 64.00
10:32:05.912039 T10010A00 Write-Data Control setpoint: 10.00
10:32:06.045003 BD0010A00 Write-Ack Control setpoint: 10.00
10:32:06.950875 T10383FFF Write-Data DHW setpoint: 64.00
10:32:06.952179 BD0383FFF Write-Ack DHW setpoint: 64.00
10:32:07.878940 T90395AFC Write-Data Max CH water setpoint: 90.98
10:32:07.935687 B50395AFC Write-Ack Max CH water setpoint: 90.98
10:32:08.898300 T00090000 Read-Data Remote override room setpoint: 0.00
10:32:08.898615 R00060000 Read-Data Remote parameter flags: 00000000 00000000
10:32:09.012760 B40060301 Read-Ack Remote parameter flags: 00000011 00000001
10:32:09.013468 AC0090000 Read-Ack Remote override room setpoint: 0.00
10:32:09.897922 T80000200 Read-Data Status: 00000010 00000000
10:32:09.998947 Error 03
10:32:10.879683 T80000200 Read-Data Status: 00000010 00000000
10:32:11.903292 T80000200 Read-Data Status: 00000010 00000000
10:32:11.999012 B40000200 Read-Ack Status: 00000010 00000000
10:32:12.886811 T80190000 Read-Data Boiler water temperature: 0.00
10:32:12.988177 BC0194000 Read-Ack Boiler water temperature: 64.00
10:32:13.876171 T10010A00 Write-Data Control setpoint: 10.00
10:32:13.985373 Error 03
10:32:14.908243 T80190000 Read-Data Boiler water temperature: 0.00
10:32:15.003894 BC0194000 Read-Ack Boiler water temperature: 64.00
10:32:15.893486 T10010A00 Write-Data Control setpoint: 10.00
10:32:15.986197 BD0010A00 Write-Ack Control setpoint: 10.00
10:32:16.890003 T80640000 Read-Data Remote override function: 00000000
10:32:16.943124 B70640000 Unk-DataId Remote override function: 00000000
10:32:16.945975 A40640000 Read-Ack Remote override function: 00000000
10:32:17.907110 T00110000 Read-Data Relative modulation level: 0.00
10:32:18.881427 T00110000 Read-Data Relative modulation level: 0.00
10:32:18.977362 BC0110000 Read-Ack Relative modulation level: 0.00
10:32:19.861692 T80000200 Read-Data Status: 00000010 00000000
10:32:19.974678 B40000200 Read-Ack Status: 00000010 00000000
10:32:20.904342 T80190000 Read-Data Boiler water temperature: 0.00
10:32:20.994788 BC0194000 Read-Ack Boiler water temperature: 64.00
10:32:21.878568 T10010A00 Write-Data Control setpoint: 10.00
10:32:21.986509 BD0010A00 Write-Ack Control setpoint: 10.00
10:32:22.874162 T00110000 Read-Data Relative modulation level: 0.00
10:32:22.972775 BC0110000 Read-Ack Relative modulation level: 0.00
10:32:23.898448 T90181508 Write-Data Room temperature: 21.03
10:32:24.022724 Error 04
10:32:24.028326 EF0180002
10:32:24.875717 T80190000 Read-Data Boiler water temperature: 0.00
10:32:25.916990 T80190000 Read-Data Boiler water temperature: 0.00
10:32:25.966370 BC0194000 Read-Ack Boiler water temperature: 64.00
10:32:26.898100 T10010A00 Write-Data Control setpoint: 10.00
10:32:26.952575 BD0010A00 Write-Ack Control setpoint: 10.00
10:32:27.869897 T90181508 Write-Data Room temperature: 21.03
10:32:27.970249 BF01BFFFF Unk-DataId Outside temperature: -0.00
10:32:28.870208 T90181508 Write-Data Room temperature: 21.03
10:32:29.902403 T80000200 Read-Data Status: 00000010 00000000
10:32:29.961277 B40000200 Read-Ack Status: 00000010 00000000
10:32:30.880567 T80190000 Read-Data Boiler water temperature: 0.00
10:32:30.946991 BC0194000 Read-Ack Boiler water temperature: 64.00
10:32:31.866461 T10010A00 Write-Data Control setpoint: 10.00
10:32:31.968460 BD0010A00 Write-Ack Control setpoint: 10.00
10:32:32.907120 T00110000 Read-Data Relative modulation level: 0.00
10:32:32.958934 BC0110000 Read-Ack Relative modulation level: 0.00
10:32:33.888445 T10181512 Write-Data Room temperature: 21.07
10:32:33.943301 BF0180000 Unk-DataId Room temperature: 0.00
10:32:34.879421 T80190000 Read-Data Boiler water temperature: 0.00
10:32:34.989851 Error 03
10:32:35.898572 T80190000 Read-Data Boiler water temperature: 0.00
10:32:35.967036 BC0194000 Read-Ack Boiler water temperature: 64.00
10:32:36.883443 T10010A00 Write-Data Control setpoint: 10.00
10:32:36.941640 BD0010A00 Write-Ack Control setpoint: 10.00
10:32:37.870770 T90101480 Write-Data Room setpoint: 20.50
10:32:37.928290 B70100000 Unk-DataId Room setpoint: 0.00
10:32:37.978949 AD0100000 Write-Ack Room setpoint: 0.00
10:32:38.908160 T90148A1F Write-Data Day of week and time of day: Thu 10:31
10:32:39.880077 T80000200 Read-Data Status: 00000010 00000000
10:32:39.994783 B40000200 Read-Ack Status: 00000010 00000000
10:32:40.872509 T80190000 Read-Data Boiler water temperature: 0.00
10:32:40.933050 BC0194000 Read-Ack Boiler water temperature: 64.00
10:32:41.893422 T10010A00 Write-Data Control setpoint: 10.00
10:32:41.995996 Error 04
10:32:42.000804 ED0810A00
10:32:42.865208 T10010A00 Write-Data Control setpoint: 10.00
10:32:43.901024 T10010A00 Write-Data Control setpoint: 10.00
10:32:44.000573 BD0010A00 Write-Ack Control setpoint: 10.00
10:32:44.892082 T80190000 Read-Data Boiler water temperature: 0.00
10:32:44.992157 BC0194000 Read-Ack Boiler water temperature: 64.00
10:32:45.868689 T10010A00 Write-Data Control setpoint: 10.00
10:32:45.969409 BD0010A00 Write-Ack Control setpoint: 10.00
10:32:46.904679 T00110000 Read-Data Relative modulation level: 0.00
10:32:47.006719 BC0110000 Read-Ack Relative modulation level: 0.00
10:32:47.887081 T90148A20 Write-Data Day of week and time of day: Thu 10:32
10:32:47.988322 BF0140000 Unk-DataId Day of week and time of day: Unk 00:00
10:32:47.999310 A50148A20 Write-Ack Day of week and time of day: Thu 10:32
10:32:48.878890 T801C0000 Read-Data Return water temperature: 0.00
10:32:48.990987 Error 03
10:32:49.907058 T80000200 Read-Data Status: 00000010 00000000
10:32:49.971028 B40000200 Read-Ack Status: 00000010 00000000
10:32:50.888641 T80190000 Read-Data Boiler water temperature: 0.00
10:32:51.007571 BC0194000 Read-Ack Boiler water temperature: 64.00
10:32:51.877824 T10010A00 Write-Data Control setpoint: 10.00
10:32:51.976509 BD0010A00 Write-Ack Control setpoint: 10.00
10:32:52.858962 T00110000 Read-Data Relative modulation level: 0.00
10:32:52.979390 Error 03
10:32:53.900936 T00110000 Read-Data Relative modulation level: 0.00
10:32:53.949230 BC0110000 Read-Ack Relative modulation level: 0.00
10:32:54.876445 T80190000 Read-Data Boiler water temperature: 0.00
10:32:54.978265 BC0194000 Read-Ack Boiler water temperature: 64.00
10:32:55.912078 T10010A00 Write-Data Control setpoint: 10.00
10:32:56.032423 Error 03
10:32:56.882993 T10010A00 Write-Data Control setpoint: 10.00
10:32:57.871200 T10010A00 Write-Data Control setpoint: 10.00
10:32:57.964508 BD0010A00 Write-Ack Control setpoint: 10.00
10:32:58.910151 T801C0000 Read-Data Return water temperature: 0.00
10:32:58.957102 B401C2E00 Read-Ack Return water temperature: 46.00
10:32:59.905428 T80000200 Read-Data Status: 00000010 00000000
10:32:59.963802 B40000200 Read-Ack Status: 00000010 00000000
10:33:00.865240 T80000200 Read-Data Status: 00000010 00000000
10:33:00.932599 B40000200 Read-Ack Status: 00000010 00000000
10:33:01.903917 T80190000 Read-Data Boiler water temperature: 0.00
10:33:02.016982 Error 03
10:33:02.879932 T80190000 Read-Data Boiler water temperature: 0.00
10:33:02.939243 BC0194000 Read-Ack Boiler water temperature: 64.00
10:33:03.873249 T10010A00 Write-Data Control setpoint: 10.00
10:33:03.941754 BD0010A00 Write-Ack Control setpoint: 10.00
10:33:04.889284 T10383FFF Write-Data DHW setpoint: 64.00
10:33:05.011690 Error 03
10:33:05.862784 T80190000 Read-Data Boiler water temperature: 0.00
10:33:05.965280 BC0194000 Read-Ack Boiler water temperature: 64.00
10:33:06.904033 T10010A00 Write-Data Control setpoint: 10.00
10:33:07.009847 BD0010A00 Write-Ack Control setpoint: 10.00
10:33:07.884509 T10383FFF Write-Data DHW setpoint: 64.00
10:33:07.953829 Error 04
10:33:08.010977 E90383FFF
10:33:08.888514 T10383FFF Write-Data DHW setpoint: 64.00
10:33:08.956986 BD0383FFF Write-Ack DHW setpoint: 64.00
10:33:09.891318 T90395AFC Write-Data Max CH water setpoint: 90.98
10:33:10.007984 Error 03
10:33:10.920516 T80000200 Read-Data Status: 00000010 00000000
10:33:11.932493 T80000200 Read-Data Status: 00000010 00000000
10:33:11.979867 BC00002E0 Read-Ack Status: 00000010 11100000
10:33:12.896398 T80190000 Read-Data Boiler water temperature: 0.00
10:33:12.954105 BC0194000 Read-Ack Boiler water temperature: 64.00
10:33:13.887140 T10010A00 Write-Data Control setpoint: 10.00
10:33:13.970975 BD1FF0A00 Write-Ack Message ID 255: 2560
10:33:14.914906 T10010A00 Write-Data Control setpoint: 10.00
10:33:15.898446 T80190000 Read-Data Boiler water temperature: 0.00
10:33:15.963473 BC0194000 Read-Ack Boiler water temperature: 64.00
10:33:16.920829 T10010A00 Write-Data Control setpoint: 10.00
10:33:17.901948 T10010A00 Write-Data Control setpoint: 10.00
10:33:18.895344 T10010A00 Write-Data Control setpoint: 10.00
10:33:19.899297 T10010A00 Write-Data Control setpoint: 10.00
10:33:19.959569 BD0010A00 Write-Ack Control setpoint: 10.00
10:33:20.880056 T80000200 Read-Data Status: 00000010 00000000
10:33:21.909605 T80000200 Read-Data Status: 00000010 00000000
10:33:22.880265 T80000200 Read-Data Status: 00000010 00000000
10:33:22.985640 B40000200 Read-Ack Status: 00000010 00000000
10:33:23.876635 T80190000 Read-Data Boiler water temperature: 0.00
10:33:24.899770 T80190000 Read-Data Boiler water temperature: 0.00
10:33:25.880300 T80190000 Read-Data Boiler water temperature: 0.00
10:33:26.895247 T80190000 Read-Data Boiler water temperature: 0.00
10:33:26.954736 BC0194000 Read-Ack Boiler water temperature: 64.00
10:33:27.933613 T10010A00 Write-Data Control setpoint: 10.00
10:33:27.995562 BD0010A00 Write-Ack Control setpoint: 10.00
10:33:28.865970 T90395AFC Write-Data Max CH water setpoint: 90.98
10:33:29.897292 T90395AFC Write-Data Max CH water setpoint: 90.98
10:33:29.948038 B50395AFC Write-Ack Max CH water setpoint: 90.98
10:33:30.885149 T80000200 Read-Data Status: 00000010 00000000
10:33:30.946693 BC00002E0 Read-Ack Status: 00000010 11100000
10:33:31.868443 T80190000 Read-Data Boiler water temperature: 0.00
10:33:31.968195 B40193F00 Read-Ack Boiler water temperature: 63.00
10:33:32.897916 T10010A00 Write-Data Control setpoint: 10.00
10:33:32.997931 BD0010A00 Write-Ack Control setpoint: 10.00
10:33:33.889117 T00090000 Read-Data Remote override room setpoint: 0.00
10:33:33.892395 R00300000 Read-Data DHW setpoint boundaries: 0 0
10:33:33.939375 B40303F26 Read-Ack DHW setpoint boundaries: 63 38
10:33:33.994889 AC0090000 Read-Ack Remote override room setpoint: 0.00
10:33:34.872666 T80640000 Read-Data Remote override function: 00000000
10:33:34.875908 R00050000 Read-Data Application-specific flags: 00000000 0
10:33:34.928518 BC0050000 Read-Ack Application-specific flags: 00000000 0
10:33:34.986083 A40640000 Read-Ack Remote override function: 00000000
10:33:35.904541 T80190000 Read-Data Boiler water temperature: 0.00
10:33:35.958358 B40193F00 Read-Ack Boiler water temperature: 63.00
10:33:36.875126 T10010A00 Write-Data Control setpoint: 10.00
10:33:36.987890 BD0010A00 Write-Ack Control setpoint: 10.00
10:33:37.861837 T00110000 Read-Data Relative modulation level: 0.00
10:33:37.963338 BC0110000 Read-Ack Relative modulation level: 0.00
10:33:38.903047 T9018151C Write-Data Room temperature: 21.11
10:33:39.889376 T9018151C Write-Data Room temperature: 21.11
10:33:39.945860 BF0180000 Unk-DataId Room temperature: 0.00
10:33:40.911156 T80000200 Read-Data Status: 00000010 00000000
10:33:40.972200 B40000200 Read-Ack Status: 00000010 00000000
10:33:41.890484 T80190000 Read-Data Boiler water temperature: 0.00
10:33:42.006802 Error 03
10:33:42.872748 T80190000 Read-Data Boiler water temperature: 0.00
10:33:43.899087 T80190000 Read-Data Boiler water temperature: 0.00
10:33:43.952153 B40193F00 Read-Ack Boiler water temperature: 63.00
10:33:44.877688 T10010A00 Write-Data Control setpoint: 10.00
10:33:44.982754 BD0010A00 Write-Ack Control setpoint: 10.00
10:33:45.912124 T80190000 Read-Data Boiler water temperature: 0.00
10:33:46.886990 T80190000 Read-Data Boiler water temperature: 0.00
10:33:46.994076 B40193F00 Read-Ack Boiler water temperature: 63.00
10:33:47.875615 T10010A00 Write-Data Control setpoint: 10.00
10:33:47.933251 BD0010A00 Write-Ack Control setpoint: 10.00
10:33:48.898074 T00110000 Read-Data Relative modulation level: 0.00
10:33:49.004228 Error 03
10:33:49.880373 T00110000 Read-Data Relative modulation level: 0.00
10:33:50.868799 T80000200 Read-Data Status: 00000010 00000000
10:33:50.968325 B40000200 Read-Ack Status: 00000010 00000000
10:33:51.898707 T80190000 Read-Data Boiler water temperature: 0.00
10:33:51.961873 B40193F00 Read-Ack Boiler water temperature: 63.00
10:33:52.886816 T10010A00 Write-Data Control setpoint: 10.00
10:33:52.956593 BD0010A00 Write-Ack Control setpoint: 10.00
10:33:53.917177 T00110000 Read-Data Relative modulation level: 0.00
10:33:53.982707 BC0110000 Read-Ack Relative modulation level: 0.00
10:33:54.887614 T90101480 Write-Data Room setpoint: 20.50
10:33:54.991421 B70100000 Unk-DataId Room setpoint: 0.00
10:33:55.001688 AD0100000 Write-Ack Room setpoint: 0.00
10:33:55.873682 T80190000 Read-Data Boiler water temperature: 0.00
10:33:55.984610 B40193F00 Read-Ack Boiler water temperature: 63.00
10:33:56.904220 T10010A00 Write-Data Control setpoint: 10.00
10:33:57.007241 BD0010A00 Write-Ack Control setpoint: 10.00
10:33:57.900741 T10148A21 Write-Data Day of week and time of day: Thu 10:33
10:33:57.963057 BF0140000 Unk-DataId Day of week and time of day: Unk 00:00
10:33:57.966681 AD0148A21 Write-Ack Day of week and time of day: Thu 10:33
10:33:58.890198 T801C0000 Read-Data Return water temperature: 0.00
10:33:59.005647 B401C2D00 Read-Ack Return water temperature: 45.00
10:33:59.877868 T801A0000 Read-Data DHW temperature: 0.00
10:33:59.996883 Error 03
10:34:00.908167 T80000200 Read-Data Status: 00000010 00000000
10:34:00.972916 B40000200 Read-Ack Status: 00000010 00000000
10:34:01.891718 T80190000 Read-Data Boiler water temperature: 0.00
10:34:01.953024 B40193F00 Read-Ack Boiler water temperature: 63.00
10:34:02.878079 T10010A00 Write-Data Control setpoint: 10.00
10:34:02.934589 BD0010A00 Write-Ack Control setpoint: 10.00
10:34:03.911220 T10383FFF Write-Data DHW setpoint: 64.00
10:34:03.967324 BD0383FFF Write-Ack DHW setpoint: 64.00
10:34:04.888159 T90395AFC Write-Data Max CH water setpoint: 90.98
10:34:04.996249 B50395AFC Write-Ack Max CH water setpoint: 90.98
10:34:05.888224 T80190000 Read-Data Boiler water temperature: 0.00
10:34:05.938657 B40193F00 Read-Ack Boiler water temperature: 63.00
10:34:06.909683 T10010A00 Write-Data Control setpoint: 10.00
10:34:06.966775 BD0010A00 Write-Ack Control setpoint: 10.00
10:34:07.899801 T00090000 Read-Data Remote override room setpoint: 0.00
10:34:07.956997 BF0090000 Unk-DataId Remote override room setpoint: 0.00
10:34:08.012823 AC0090000 Read-Ack Remote override room setpoint: 0.00
10:34:08.889998 T80640000 Read-Data Remote override function: 00000000
10:34:08.939779 B70640000 Unk-DataId Remote override function: 00000000
10:34:08.984673 A40640000 Read-Ack Remote override function: 00000000
10:34:09.904750 T00110000 Read-Data Relative modulation level: 0.00
10:34:10.057928 Error 04
10:34:10.061193 EC01101FF
10:34:10.889286 T80000200 Read-Data Status: 00000010 00000000
10:34:11.875634 T80000200 Read-Data Status: 00000010 00000000
10:34:11.985714 B40000200 Read-Ack Status: 00000010 00000000
10:34:12.904240 T80190000 Read-Data Boiler water temperature: 0.00
10:34:12.961767 B40193F00 Read-Ack Boiler water temperature: 63.00
10:34:13.897746 T10010A00 Write-Data Control setpoint: 10.00
10:34:14.011108 Error 03
10:34:14.878237 T10010A00 Write-Data Control setpoint: 10.00
10:34:15.897121 T80190000 Read-Data Boiler water temperature: 0.00
10:34:15.950932 B40193F00 Read-Ack Boiler water temperature: 63.00
10:34:16.901786 T10010A00 Write-Data Control setpoint: 10.00
10:34:16.952838 BD0010A00 Write-Ack Control setpoint: 10.00
10:34:17.923797 T00110000 Read-Data Relative modulation level: 0.00
10:34:18.892593 T00110000 Read-Data Relative modulation level: 0.00
10:34:18.945007 BC0110000 Read-Ack Relative modulation level: 0.00
10:34:19.871256 T10181522 Write-Data Room temperature: 21.13
10:34:19.978207 BF0180000 Unk-DataId Room temperature: 0.00
10:34:20.910498 T80000200 Read-Data Status: 00000010 00000000
10:34:21.002686 B40000200 Read-Ack Status: 00000010 00000000
10:34:21.896038 T80190000 Read-Data Boiler water temperature: 0.00
10:34:21.952247 B40193F00 Read-Ack Boiler water temperature: 63.00
10:34:22.872506 T10010A00 Write-Data Control setpoint: 10.00
10:34:22.973220 BD0010A00 Write-Ack Control setpoint: 10.00
10:34:23.927935 T00110000 Read-Data Relative modulation level: 0.00
10:34:23.977807 BC0110000 Read-Ack Relative modulation level: 0.00
10:34:24.892987 T90101480 Write-Data Room setpoint: 20.50
10:34:25.865173 T80190000 Read-Data Boiler water temperature: 0.00
10:34:25.964634 B40193F00 Read-Ack Boiler water temperature: 63.00
10:34:26.902574 T10010A00 Write-Data Control setpoint: 10.00
10:34:26.967681 BD0010A00 Write-Ack Control setpoint: 10.00
10:34:27.898344 T90101480 Write-Data Room setpoint: 20.50
10:34:27.971278 Error 03
10:34:28.907153 T90101480 Write-Data Room setpoint: 20.50
10:34:29.012480 B70100000 Unk-DataId Room setpoint: 0.00
10:34:29.028504 AD0100000 Write-Ack Room setpoint: 0.00
10:34:29.899917 T10148A21 Write-Data Day of week and time of day: Thu 10:33
10:34:29.958834 BF0140000 Unk-DataId Day of week and time of day: Unk 00:00
10:34:30.004745 AD0148A21 Write-Ack Day of week and time of day: Thu 10:33
10:34:30.896111 T80000200 Read-Data Status: 00000010 00000000
10:34:31.012386 B40000200 Read-Ack Status: 00000010 00000000
10:34:31.886210 T80190000 Read-Data Boiler water temperature: 0.00
10:34:31.952810 B40193F00 Read-Ack Boiler water temperature: 63.00
10:34:32.870637 T10010A00 Write-Data Control setpoint: 10.00
10:34:32.932680 BD0010A00 Write-Ack Control setpoint: 10.00
10:34:33.910086 T00110000 Read-Data Relative modulation level: 0.00
10:34:33.967420 BC0110000 Read-Ack Relative modulation level: 0.00
10:34:34.885095 T801C0000 Read-Data Return water temperature: 0.00
10:34:34.995702 Error 03
10:34:35.863840 T80190000 Read-Data Boiler water temperature: 0.00
10:34:36.899051 T80190000 Read-Data Boiler water temperature: 0.00
10:34:36.953394 B40193F00 Read-Ack Boiler water temperature: 63.00
10:34:37.884954 T10010A00 Write-Data Control setpoint: 10.00
10:34:37.938076 BD0010A00 Write-Ack Control setpoint: 10.00
10:34:38.920933 T801C0000 Read-Data Return water temperature: 0.00
10:34:39.885132 T801C0000 Read-Data Return water temperature: 0.00
10:34:39.987249 B401C2D00 Read-Ack Return water temperature: 45.00
10:34:40.874715 T80000200 Read-Data Status: 00000010 00000000
10:34:40.968008 B40000200 Read-Ack Status: 00000010 00000000
10:34:41.904175 T80190000 Read-Data Boiler water temperature: 0.00
10:34:42.020482 Error 04
10:34:42.023563 E40393F00
10:34:42.890533 T80190000 Read-Data Boiler water temperature: 0.00
10:34:43.916277 T80190000 Read-Data Boiler water temperature: 0.00
10:34:43.967906 B40193F00 Read-Ack Boiler water temperature: 63.00
10:34:44.890247 T10010A00 Write-Data Control setpoint: 10.00
10:34:44.990312 BD0010A00 Write-Ack Control setpoint: 10.00
10:34:45.877293 T80190000 Read-Data Boiler water temperature: 0.00
10:34:45.979960 B40193F00 Read-Ack Boiler water temperature: 63.00
10:34:46.901680 T10010A00 Write-Data Control setpoint: 10.00
10:34:46.995827 BD0010A00 Write-Ack Control setpoint: 10.00
10:34:47.889217 T00110000 Read-Data Relative modulation level: 0.00
10:34:47.950238 BC0110000 Read-Ack Relative modulation level: 0.00
10:34:48.866644 T801A0000 Read-Data DHW temperature: 0.00
10:34:48.977096 BC01A3200 Read-Ack DHW temperature: 50.00
10:34:49.917123 T001B0000 Read-Data Outside temperature: 0.00
10:34:49.983308 B401BE0FF Read-Ack Outside temperature: -31.00
10:34:50.899202 T80000200 Read-Data Status: 00000010 00000000
10:34:50.997140 BC00002E0 Read-Ack Status: 00000010 11100000
10:34:51.894811 T80190000 Read-Data Boiler water temperature: 0.00
10:34:51.991090 B40193F00 Read-Ack Boiler water temperature: 63.00
10:34:52.870991 T10010A00 Write-Data Control setpoint: 10.00
10:34:52.993293 Error 03
10:34:53.900917 T10010A00 Write-Data Control setpoint: 10.00
10:34:53.991862 BD0010A00 Write-Ack Control setpoint: 10.00
10:34:54.876771 T00110000 Read-Data Relative modulation level: 0.00
10:34:54.943752 BC0110000 Read-Ack Relative modulation level: 0.00
10:34:55.863059 T80190000 Read-Data Boiler water temperature: 0.00
10:34:55.964293 B40193F00 Read-Ack Boiler water temperature: 63.00
10:34:56.905691 T10010A00 Write-Data Control setpoint: 10.00
10:34:57.870430 T10010A00 Write-Data Control setpoint: 10.00
10:34:57.985133 BD0010A00 Write-Ack Control setpoint: 10.00
10:34:58.906184 T00120000 Read-Data CH water pressure: 0.00
10:34:58.969180 B40120166 Read-Ack CH water pressure: 1.40
10:34:59.904540 T80000200 Read-Data Status: 00000010 00000000
10:35:00.016674 B40000260 Read-Ack Status: 00000010 01100000
10:35:00.877689 T80000200 Read-Data Status: 00000010 00000000
10:35:00.947438 B40000260 Read-Ack Status: 00000010 01100000
10:35:01.897013 T80000200 Read-Data Status: 00000010 00000000
10:35:01.983338 B40000260 Read-Ack Status: 00000010 01100000
10:35:02.935712 T80190000 Read-Data Boiler water temperature: 0.00
10:35:02.995932 Error 03
10:35:03.885278 T80190000 Read-Data Boiler water temperature: 0.00
10:35:04.921032 T80190000 Read-Data Boiler water temperature: 0.00
10:35:04.981577 B40193F00 Read-Ack Boiler water temperature: 63.00
10:35:05.913179 T10010A00 Write-Data Control setpoint: 10.00
10:35:06.015808 BD0010A00 Write-Ack Control setpoint: 10.00
10:35:06.896618 T80190000 Read-Data Boiler water temperature: 0.00
10:35:06.949509 Error 03
10:35:07.894462 T80190000 Read-Data Boiler water temperature: 0.00
10:35:07.994715 B40193F00 Read-Ack Boiler water temperature: 63.00
10:35:08.874550 T10010A00 Write-Data Control setpoint: 10.00
10:35:08.983295 BD0010A00 Write-Ack Control setpoint: 10.00
10:35:09.920889 T10383FFF Write-Data DHW setpoint: 64.00
10:35:10.040334 Error 04
10:35:10.048315 ED0383FBF
10:35:10.893748 T10383FFF Write-Data DHW setpoint: 64.00
10:35:11.883588 T80000200 Read-Data Status: 00000010 00000000
10:35:11.937927 BC00002E0 Read-Ack Status: 00000010 11100000
10:35:12.920058 T80190000 Read-Data Boiler water temperature: 0.00
10:35:12.969914 B40193F00 Read-Ack Boiler water temperature: 63.00
10:35:13.886401 T10010A00 Write-Data Control setpoint: 10.00
10:35:14.002187 Error 04
10:35:14.008711 E90010A00
10:35:14.874257 T10010A00 Write-Data Control setpoint: 10.00
10:35:15.958673 T10010A00 Write-Data Control setpoint: 10.00
10:35:15.969606 BD0010A00 Write-Ack Control setpoint: 10.00
10:35:16.879476 T80190000 Read-Data Boiler water temperature: 0.00
10:35:16.992183 B40193F00 Read-Ack Boiler water temperature: 63.00
10:35:17.855905 T10010A00 Write-Data Control setpoint: 10.00
10:35:17.958496 BD0010A00 Write-Ack Control setpoint: 10.00
10:35:18.905609 T10383FFF Write-Data DHW setpoint: 64.00
10:35:18.967502 BD0383FFF Write-Ack DHW setpoint: 64.00
10:35:19.889189 T90395AFC Write-Data Max CH water setpoint: 90.98
10:35:19.948031 B50395AFC Write-Ack Max CH water setpoint: 90.98
10:35:20.872478 T00090000 Read-Data Remote override room setpoint: 0.00
10:35:20.875546 R00050000 Read-Data Application-specific flags: 00000000 0
10:35:20.980867 Error 03
10:35:21.887583 T80000200 Read-Data Status: 00000010 00000000
10:35:22.000475 B40000200 Read-Ack Status: 00000010 00000000
10:35:22.876156 T80190000 Read-Data Boiler water temperature: 0.00
10:35:22.942330 B40193F00 Read-Ack Boiler water temperature: 63.00
10:35:23.898815 T10010A00 Write-Data Control setpoint: 10.00
10:35:24.004915 BD0010A00 Write-Ack Control setpoint: 10.00
10:35:24.894964 T00090000 Read-Data Remote override room setpoint: 0.00
10:35:24.901603 R00050000 Read-Data Application-specific flags: 00000000 0
10:35:25.873873 T00090000 Read-Data Remote override room setpoint: 0.00
10:35:25.878466 R00050000 Read-Data Application-specific flags: 00000000 0
10:35:25.973864 BC0050000 Read-Ack Application-specific flags: 00000000 0
10:35:25.977825 AC0090000 Read-Ack Remote override room setpoint: 0.00
10:35:26.916969 T80190000 Read-Data Boiler water temperature: 0.00
10:35:26.964619 B40193F00 Read-Ack Boiler water temperature: 63.00
10:35:27.883691 T10010A00 Write-Data Control setpoint: 10.00
10:35:27.993814 Error 03
10:35:28.867390 T10010A00 Write-Data Control setpoint: 10.00
10:35:29.882936 T10010A00 Write-Data Control setpoint: 10.00
10:35:29.986177 BD0010A00 Write-Ack Control setpoint: 10.00
10:35:30.886194 T80640000 Read-Data Remote override function: 00000000
10:35:30.983896 B70640000 Unk-DataId Remote override function: 00000000
10:35:30.988616 A40640000 Read-Ack Remote override function: 00000000
10:35:31.872817 T80000200 Read-Data Status: 00000010 00000000
10:35:31.972884 B40000200 Read-Ack Status: 00000010 00000000
10:35:32.889560 T80190000 Read-Data Boiler water temperature: 0.00
10:35:33.004006 B40193F00 Read-Ack Boiler water temperature: 63.00
10:35:33.877609 T10010A00 Write-Data Control setpoint: 10.00
10:35:33.978485 BD0010A00 Write-Ack Control setpoint: 10.00
10:35:34.878517 T00110000 Read-Data Relative modulation level: 0.00
10:35:34.928182 BC0110000 Read-Ack Relative modulation level: 0.00
10:35:35.910395 T90181520 Write-Data Room temperature: 21.13
10:35:35.970888 BF0180000 Unk-DataId Room temperature: 0.00
10:35:36.888765 T80190000 Read-Data Boiler water temperature: 0.00
10:35:36.996747 B40193F00 Read-Ack Boiler water temperature: 63.00
10:35:37.876103 T10010A00 Write-Data Control setpoint: 10.00
10:35:37.973208 BD0010A00 Write-Ack Control setpoint: 10.00
10:35:38.893496 T90101480 Write-Data Room setpoint: 20.50
10:35:39.024901 B70100000 Unk-DataId Room setpoint: 0.00
10:35:39.028868 AD0100000 Write-Ack Room setpoint: 0.00
10:35:39.883114 T10148A22 Write-Data Day of week and time of day: Thu 10:34
10:35:39.948057 BF0140000 Unk-DataId Day of week and time of day: Unk 00:00
10:35:39.996452 AD0148A22 Write-Ack Day of week and time of day: Thu 10:34
10:35:40.883364 T801C0000 Read-Data Return water temperature: 0.00
10:35:40.978346 B401C2D00 Read-Ack Return water temperature: 45.00
10:35:41.862340 T80000200 Read-Data Status: 00000010 00000000
10:35:41.967285 B40000200 Read-Ack Status: 00000010 00000000
10:35:42.902631 T80190000 Read-Data Boiler water temperature: 0.00
10:35:43.001246 B40193F00 Read-Ack Boiler water temperature: 63.00
10:35:43.886875 T10010A00 Write-Data Control setpoint: 10.00
10:35:43.989521 BD0010A00 Write-Ack Control setpoint: 10.00
10:35:44.874748 T00110000 Read-Data Relative modulation level: 0.00
10:35:44.978114 BC0110000 Read-Ack Relative modulation level: 0.00
10:35:45.900035 T801A0000 Read-Data DHW temperature: 0.00
10:35:45.984101 BC01A3200 Read-Ack DHW temperature: 50.00
10:35:46.887213 T80190000 Read-Data Boiler water temperature: 0.00
10:35:46.997235 B40193F00 Read-Ack Boiler water temperature: 63.00
10:35:47.869324 T10010A00 Write-Data Control setpoint: 10.00
10:35:47.970165 BD0010A00 Write-Ack Control setpoint: 10.00
10:35:48.903547 T001B0000 Read-Data Outside temperature: 0.00
10:35:49.006522 Error 04
10:35:49.009773 E401BE8FF
10:35:49.891591 T001B0000 Read-Data Outside temperature: 0.00
10:35:50.875880 T001B0000 Read-Data Outside temperature: 0.00
10:35:50.968446 B401BE0FF Read-Ack Outside temperature: -31.00
10:35:51.904397 T80000200 Read-Data Status: 00000010 00000000
10:35:51.962458 BC00002E0 Read-Ack Status: 00000010 11100000
10:35:52.890704 T80190000 Read-Data Boiler water temperature: 0.00
10:35:52.946116 B40193F00 Read-Ack Boiler water temperature: 63.00
10:35:53.876693 T10010A00 Write-Data Control setpoint: 10.00
10:35:53.931160 BD0010A00 Write-Ack Control setpoint: 10.00
10:35:54.894377 T00110000 Read-Data Relative modulation level: 0.00
10:35:54.996688 BC0110000 Read-Ack Relative modulation level: 0.00
10:35:55.913123 T00120000 Read-Data CH water pressure: 0.00
10:35:55.963674 B40120166 Read-Ack CH water pressure: 1.40
10:35:56.876566 T80190000 Read-Data Boiler water temperature: 0.00
10:35:57.899510 T80190000 Read-Data Boiler water temperature: 0.00
10:35:57.996070 B40193F00 Read-Ack Boiler water temperature: 63.00
10:35:58.881405 T10010A00 Write-Data Control setpoint: 10.00
10:35:58.980256 BD0010A00 Write-Ack Control setpoint: 10.00
10:35:59.860825 T80000200 Read-Data Status: 00000010 00000000
10:35:59.981504 Error 03
One hypothesis would be that it changes the message sequence in response to failed messages, because I also have this:
https://www.domoticaforum.eu/viewtopic. ... 804#p97804
Re: time changing on chronotherm 4
Posted: Fri Apr 16, 2021 12:07 am
by hvxl
I attempted to simulate your situation using the interface firmware. I made a script that generates appropriate response, but skips a couple every now and then, which is what it would also look like to your thermostat. (When the OTGW detects an error in gateway mode, it doesn't send anything to the thermostat.) But after running like that for 3 hours, the clock is still correct. So, either I'm not reproducing the situation accurately enough, or your Chronotherm Modulation behaves different than mine. Maybe it has different firmware. On startup, mine says:
- T107E0100 Write-Data Master product version: 1 0
Of course there is no guarantee that information is actually updated with new firmware.
Re: time changing on chronotherm 4
Posted: Fri Apr 16, 2021 9:51 am
by Tomas
What is the best way to get that attribute? Pull the plug from the thermostat to the gateway, reconnect it while OpenTherm Monitor is logging, or is there some smarter way to make it send the software version?
It also seems there are different Chronotherm Modulation versions, mine has a sticker on the back with "T8851M1000" maybe yours is a slightly different or updated model?
Re: time changing on chronotherm 4
Posted: Fri Apr 16, 2021 10:50 pm
by hvxl
The sticker on my Chronotherm Modulation says: T8851M1000 4T40 AD5C 0837 5.
Pulling the thermostat plug from the gateway for a few seconds would work for getting the thermostat to report its software version again. You can also pull the thermostat off the wall and put it back. I don't know any smarter way to do it.
Re: time changing on chronotherm 4
Posted: Wed Dec 22, 2021 6:18 pm
by Tomas
Update on this: I haven't managed to make the thermostat report a software version. But I did manage to find another Chronotherm with the same model (T8851M1000), now connected to the same boiler and gateway. This one does not have the same behavior. When it receives a time input from the gateway it only changes the minutes and just keeps counting the seconds as it was. So it doesn't drift.
So it's very likely that there was either a problem with the thermostat or a bug in the firmware version that was fixed in the one I have now.