Error 03 with Tado opentherm stat

This Forum is about the Opentherm gateway (OTGW) from Schelte

Moderator: hvxl

Post Reply
Dickuk
Starting Member
Starting Member
Posts: 15
Joined: Fri Nov 02, 2012 10:31 pm

Error 03 with Tado opentherm stat

Post by Dickuk »

I have finally got around to buying an opentherm thermostat (Tado) which I have connected through the opentherm gateway and initially all was well (I was seeing it sending temperatures and also modulating the boiler too)

But after a short time, I am now seeing a lot of Error 03's.

I tried changing the offset on all settings, but the issue is the same.

I cannot figure out why it was stable initially but then went wrong.

Attached is my log, my boiler is an Atag A325ECX

Any help appreciated

Thanks

Richard
Attachments
otlog-20161202.zip
(44.18 KiB) Downloaded 486 times
hvxl
Senior Member
Senior Member
Posts: 2031
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Error 03 with Tado opentherm stat

Post by hvxl »

At least some of those Error 03 occurrences don't seem to match with when an OT message is expected. Possibly there is some noise on the line between the OTGW and the thermostat. At the time the errors started, did you start using some piece of equipment that is close to the OT wiring, or has its power cord running next to it?

Otherwise, run diagnostics test #2 during a period when you experience a lot of Error 03's.
Schelte