OTGW not working: where to start debugging
Posted: Tue Oct 04, 2022 8:49 pm
A while ago I installed an OTGW in a holiday home, but unfortunately I haven't got it working yet. I'm not sure where to look for the problem/solution: the OTGW itself, the settings, or the thermostat? It concerns a Nefit Proline C110 boiler and a Nefit Moduline 2000 thermostat. These will continue to work with each other if the gateway is in between. A piece of log file is attached. In it a number of times 'Error03' (in recent months this has increased to thousands of errors). The temperature readings that come through don't seem realistic either. Where do I start looking?
Code: Select all
20:11:46.259373 T80000200 Read-Data Status: 00000010 00000000
20:11:47.259427 T80000200 Read-Data Status: 00000010 00000000
20:11:49.259960 T80000200 Read-Data Status: 00000010 00000000
20:11:50.258656 T80000200 Read-Data Status: 00000010 00000000
20:11:50.348842 B40000200 Read-Ack Status: 00000010 00000000
20:11:51.261662 T80000200 Read-Data Status: 00000010 00000000
20:11:54.212056 T801A0000 Read-Data DHW temperature: 0.00
20:11:56.254138 T80000200 Read-Data Status: 00000010 00000000
20:11:56.319667 B40000200 Read-Ack Status: 00000010 00000000
20:11:57.254644 T80000200 Read-Data Status: 00000010 00000000
20:11:57.376548 B40000200 Read-Ack Status: 00000010 00000000
20:11:58.257592 T80000200 Read-Data Status: 00000010 00000000
20:11:58.363258 B40000200 Read-Ack Status: 00000010 00000000
20:11:59.400351 T80000200 Read-Data Status: 00000010 00000000
20:11:59.403760 B40000200 Read-Ack Status: 00000010 00000000
20:12:00.254387 T80000200 Read-Data Status: 00000010 00000000
20:12:00.329266 B40000200 Read-Ack Status: 00000010 00000000
20:12:01.253751 T80000200 Read-Data Status: 00000010 00000000
20:12:01.316753 B40000200 Read-Ack Status: 00000010 00000000
20:12:05.292592 T80000200 Read-Data Status: 00000010 00000000
20:12:05.326331 B40000200 Read-Ack Status: 00000010 00000000
20:12:06.249106 T80000200 Read-Data Status: 00000010 00000000
20:12:06.386466 Error 03
20:12:07.249712 T80000200 Read-Data Status: 00000010 00000000
20:12:13.254742 T80000200 Read-Data Status: 00000010 00000000
20:12:15.246923 T80000200 Read-Data Status: 00000010 00000000
20:12:15.306980 B40000200 Read-Ack Status: 00000010 00000000
20:12:16.248511 T80000200 Read-Data Status: 00000010 00000000
20:12:16.360424 B40000200 Read-Ack Status: 00000010 00000000
20:12:17.247118 T80000200 Read-Data Status: 00000010 00000000
20:12:23.246436 T80000200 Read-Data Status: 00000010 00000000
20:12:23.321304 B40000200 Read-Ack Status: 00000010 00000000
20:12:27.240112 T80000200 Read-Data Status: 00000010 00000000
20:12:27.329362 B40000200 Read-Ack Status: 00000010 00000000
20:12:30.240635 T80000200 Read-Data Status: 00000010 00000000
20:12:31.241041 T80000200 Read-Data Status: 00000010 00000000
20:12:31.340760 B40000200 Read-Ack Status: 00000010 00000000
20:12:32.238414 T80000200 Read-Data Status: 00000010 00000000
20:12:32.321213 B40000200 Read-Ack Status: 00000010 00000000
20:12:33.238778 T80000200 Read-Data Status: 00000010 00000000
20:12:34.237920 T80000200 Read-Data Status: 00000010 00000000
20:12:34.359961 B40000200 Read-Ack Status: 00000010 00000000
20:12:35.237482 TBFFC0200 Reserved Message ID 252: 512
20:12:36.239322 T80000200 Read-Data Status: 00000010 00000000
20:12:38.236971 T803C0200 Read-Data Remote parameter 5: 2.00
20:12:41.234531 T80000200 Read-Data Status: 00000010 00000000
20:12:41.326005 B40000200 Read-Ack Status: 00000010 00000000
20:12:43.235539 T80000200 Read-Data Status: 00000010 00000000
20:12:44.238747 T80000200 Read-Data Status: 00000010 00000000
20:12:44.346589 B40000200 Read-Ack Status: 00000010 00000000
20:12:45.237443 T80F00200 Read-Data Message ID 240: 512
20:12:45.326423 B40000200 Read-Ack Status: 00000010 00000000
20:12:49.231335 T80000200 Read-Data Status: 00000010 00000000
20:12:50.233438 T800FC200 Read-Data Boiler capacity and modulation limits: 194 0
20:12:52.231782 T80000200 Read-Data Status: 00000010 00000000
20:12:52.291945 B40000200 Read-Ack Status: 00000010 00000000
20:12:52.435408 T10010000 Write-Data Control setpoint: 0.00
20:12:52.549425 BD0010000 Write-Ack Control setpoint: 0.00
20:12:53.414822 T801A0000 Read-Data DHW temperature: 0.00
20:12:53.484777 B401A0000 Read-Ack DHW temperature: 0.00
20:12:54.774799 T80000200 Read-Data Status: 00000010 00000000
20:12:54.893841 B40000200 Read-Ack Status: 00000010 00000000
20:12:55.228901 T80000200 Read-Data Status: 00000010 00000000
20:12:55.313578 B40000200 Read-Ack Status: 00000010 00000000
20:12:58.230842 T80000200 Read-Data Status: 00000010 00000000
20:12:58.336779 B40000200 Read-Ack Status: 00000010 00000000
20:12:59.228418 T80000200 Read-Data Status: 00000010 00000000
20:12:59.320729 B40000200 Read-Ack Status: 00000010 00000000
20:13:01.226231 T80000200 Read-Data Status: 00000010 00000000
20:13:01.292520 B40000200 Read-Ack Status: 00000010 00000000
20:13:02.226796 T80000200 Read-Data Status: 00000010 00000000
20:13:02.347818 B40000200 Read-Ack Status: 00000010 00000000
20:13:05.517315 T80000200 Read-Data Status: 00000010 00000000
20:13:06.229133 T80000200 Read-Data Status: 00000010 00000000
20:13:06.282910 B40000200 Read-Ack Status: 00000010 00000000
20:13:07.222371 T80000200 Read-Data Status: 00000010 00000000
20:13:07.349192 B40000200 Read-Ack Status: 00000010 00000000
20:13:08.223017 T80000200 Read-Data Status: 00000010 00000000
20:13:08.321046 B40000200 Read-Ack Status: 00000010 00000000
20:13:09.226782 T80000200 Read-Data Status: 00000010 00000000
20:13:09.305133 B40000200 Read-Ack Status: 00000010 00000000
20:13:10.221796 T80000200 Read-Data Status: 00000010 00000000
20:13:10.291482 B40000200 Read-Ack Status: 00000010 00000000
20:13:11.227316 T9FF80200 Write-Data Message ID 248: 512
20:13:12.222090 T80000200 Read-Data Status: 00000010 00000000
20:13:12.323394 B40000200 Read-Ack Status: 00000010 00000000
20:13:14.224249 T80000200 Read-Data Status: 00000010 00000000
20:13:15.220797 T80000200 Read-Data Status: 00000010 00000000
20:13:17.220110 T80000200 Read-Data Status: 00000010 00000000
20:13:20.216895 T80000200 Read-Data Status: 00000010 00000000
20:13:27.215095 T80000200 Read-Data Status: 00000010 00000000
20:13:27.307164 B40000200 Read-Ack Status: 00000010 00000000
20:13:28.215464 T80000200 Read-Data Status: 00000010 00000000
20:13:29.215138 T80000200 Read-Data Status: 00000010 00000000
20:13:29.273100 B40000200 Read-Ack Status: 00000010 00000000
20:13:30.218653 T80000200 Read-Data Status: 00000010 00000000
20:13:30.330432 B40000200 Read-Ack Status: 00000010 00000000
20:13:31.214289 T80000200 Read-Data Status: 00000010 00000000
20:13:31.312316 B40000200 Read-Ack Status: 00000010 00000000
20:13:32.212379 T80000200 Read-Data Status: 00000010 00000000
20:13:32.300740 B40000200 Read-Ack Status: 00000010 00000000
20:13:33.213312 T80000200 Read-Data Status: 00000010 00000000
20:13:33.282046 B40000200 Read-Ack Status: 00000010 00000000
20:13:35.224942 T80000200 Read-Data Status: 00000010 00000000
20:13:35.318997 B40000200 Read-Ack Status: 00000010 00000000
20:13:37.212644 T80000200 Read-Data Status: 00000010 00000000
20:13:37.288541 B40000200 Read-Ack Status: 00000010 00000000
20:13:38.211626 T80000200 Read-Data Status: 00000010 00000000
20:13:38.273003 B40000200 Read-Ack Status: 00000010 00000000
20:13:46.209600 T80000200 Read-Data Status: 00000010 00000000
20:13:48.206246 T80000200 Read-Data Status: 00000010 00000000
20:13:48.330091 B40000200 Read-Ack Status: 00000010 00000000
20:13:50.485852 T80000200 Read-Data Status: 00000010 00000000
20:13:50.489696 B40000200 Read-Ack Status: 00000010 00000000
20:13:52.779329 T10010000 Write-Data Control setpoint: 0.00
20:13:52.899305 BD0010000 Write-Ack Control setpoint: 0.00
20:13:53.822377 T801A0000 Read-Data DHW temperature: 0.00
20:13:53.883113 B401A0000 Read-Ack DHW temperature: 0.00
20:13:54.594132 T80000200 Read-Data Status: 00000010 00000000
20:13:55.205490 T80000200 Read-Data Status: 00000010 00000000
20:13:55.298912 Error 03
20:13:56.202734 T80000200 Read-Data Status: 00000010 00000000
20:13:57.202778 T80000200 Read-Data Status: 00000010 00000000
20:13:57.332165 B40000200 Read-Ack Status: 00000010 00000000
20:13:58.202573 T80000200 Read-Data Status: 00000010 00000000
20:13:58.312022 B40000200 Read-Ack Status: 00000010 00000000
20:14:04.200724 T80000200 Read-Data Status: 00000010 00000000
20:14:04.288627 B40000200 Read-Ack Status: 00000010 00000000
20:14:05.197368 T80000200 Read-Data Status: 00000010 00000000
20:14:05.273791 B40000200 Read-Ack Status: 00000010 00000000
20:14:07.198503 TBFFF7A00 Reserved Message ID 255: 31232
20:14:10.197645 T80000200 Read-Data Status: 00000010 00000000
20:14:10.266777 B40000200 Read-Ack Status: 00000010 00000000
20:14:12.198337 T80000200 Read-Data Status: 00000010 00000000
20:14:12.306355 B40000200 Read-Ack Status: 00000010 00000000
20:14:13.196848 T80000200 Read-Data Status: 00000010 00000000
20:14:14.193997 T80000200 Read-Data Status: 00000010 00000000
20:14:14.446863 B40000200 Read-Ack Status: 00000010 00000000
20:14:15.196302 T80000200 Read-Data Status: 00000010 00000000
20:14:16.198203 T80000200 Read-Data Status: 00000010 00000000
20:14:16.308119 B40000200 Read-Ack Status: 00000010 00000000
20:14:18.195818 T80000200 Read-Data Status: 00000010 00000000
20:14:18.281730 B40000200 Read-Ack Status: 00000010 00000000
20:14:19.194191 T80000200 Read-Data Status: 00000010 00000000
20:14:19.269040 B40000200 Read-Ack Status: 00000010 00000000
20:14:20.196273 T80000200 Read-Data Status: 00000010 00000000
20:14:20.251009 B40000200 Read-Ack Status: 00000010 00000000
20:14:21.193359 T80000200 Read-Data Status: 00000010 00000000
20:14:21.301096 B40000200 Read-Ack Status: 00000010 00000000
20:14:22.192237 T80000200 Read-Data Status: 00000010 00000000
20:14:22.290017 B40000200 Read-Ack Status: 00000010 00000000
20:14:26.189461 T80000200 Read-Data Status: 00000010 00000000
20:14:28.188788 T80000200 Read-Data Status: 00000010 00000000
20:14:28.266522 B40000200 Read-Ack Status: 00000010 00000000
20:14:29.187194 T80000200 Read-Data Status: 00000010 00000000
20:14:29.250236 B40000200 Read-Ack Status: 00000010 00000000
20:14:30.187876 T80000200 Read-Data Status: 00000010 00000000
20:14:30.313944 Error 03
20:14:31.185562 T80000200 Read-Data Status: 00000010 00000000
20:14:31.290520 B40000200 Read-Ack Status: 00000010 00000000
20:14:32.186121 T80000200 Read-Data Status: 00000010 00000000
20:14:32.389004 B40000200 Read-Ack Status: 00000010 00000000
20:14:34.185978 T80000200 Read-Data Status: 00000010 00000000
20:14:34.312967 B40000200 Read-Ack Status: 00000010 00000000
20:14:35.185740 T80000200 Read-Data Status: 00000010 00000000
20:14:35.297171 B40000200 Read-Ack Status: 00000010 00000000
20:14:37.188896 T87FE0200 Read-Data Message ID 254: 512
20:14:39.185745 T80000200 Read-Data Status: 00000010 00000000
20:14:40.184785 T80000200 Read-Data Status: 00000010 00000000
20:14:40.288255 B40000200 Read-Ack Status: 00000010 00000000
20:14:41.182126 T80000200 Read-Data Status: 00000010 00000000
20:14:41.272935 B40000200 Read-Ack Status: 00000010 00000000
20:14:42.183256 T80000200 Read-Data Status: 00000010 00000000
20:14:42.257927 B40000200 Read-Ack Status: 00000010 00000000
20:14:48.180568 T80000200 Read-Data Status: 00000010 00000000
20:14:48.309310 Error 03
20:14:49.180505 T80000200 Read-Data Status: 00000010 00000000
20:14:49.288145 B40000200 Read-Ack Status: 00000010 00000000
20:14:52.179015 T80000200 Read-Data Status: 00000010 00000000
20:14:53.902963 T80190000 Read-Data Boiler water temperature: 0.00
20:14:53.999599 B40193000 Read-Ack Boiler water temperature: 48.00
20:15:00.179020 T80000200 Read-Data Status: 00000010 00000000
20:15:00.258644 B40000200 Read-Ack Status: 00000010 00000000
20:15:04.232774 T80000200 Read-Data Status: 00000010 00000000
20:15:06.170770 T80000200 Read-Data Status: 00000010 00000000
20:15:06.234780 B40000200 Read-Ack Status: 00000010 00000000
20:15:07.174220 T80000200 Read-Data Status: 00000010 00000000
20:15:07.291646 B40000200 Read-Ack Status: 00000010 00000000
20:15:08.177358 T80000200 Read-Data Status: 00000010 00000000
20:15:09.171469 T80003200 Read-Data Status: 00110010 00000000
20:15:11.170296 T80000200 Read-Data Status: 00000010 00000000
20:15:11.293934 B40000200 Read-Ack Status: 00000010 00000000
20:15:13.169998 T80000200 Read-Data Status: 00000010 00000000
20:15:13.266166 B40000200 Read-Ack Status: 00000010 00000000
20:15:16.167980 T80000200 Read-Data Status: 00000010 00000000
20:15:16.287179 B40000200 Read-Ack Status: 00000010 00000000
20:15:17.167676 T80000200 Read-Data Status: 00000010 00000000
20:15:17.280175 B40000200 Read-Ack Status: 00000010 00000000
20:15:18.171370 T80000200 Read-Data Status: 00000010 00000000
20:15:18.255815 B40000200 Read-Ack Status: 00000010 00000000
20:15:20.165196 T80000200 Read-Data Status: 00000010 00000000
20:15:22.165157 T80000200 Read-Data Status: 00000010 00000000
20:15:22.264626 B40000200 Read-Ack Status: 00000010 00000000
20:15:24.166912 T80000200 Read-Data Status: 00000010 00000000
20:15:24.236352 B40000200 Read-Ack Status: 00000010 00000000
20:15:26.164918 T80000200 Read-Data Status: 00000010 00000000
20:15:27.167704 T80000200 Read-Data Status: 00000010 00000000
20:15:30.166215 T80000200 Read-Data Status: 00000010 00000000
20:15:30.279920 B40000200 Read-Ack Status: 00000010 00000000
20:15:32.160412 T80000200 Read-Data Status: 00000010 00000000
20:15:32.249130 B40000200 Read-Ack Status: 00000010 00000000
20:15:33.169018 T80000200 Read-Data Status: 00000010 00000000
20:15:33.234116 B40000200 Read-Ack Status: 00000010 00000000
20:15:34.160918 T80000200 Read-Data Status: 00000010 00000000
20:15:34.221924 B40000200 Read-Ack Status: 00000010 00000000
20:15:35.159996 T80000200 Read-Data Status: 00000010 00000000
20:15:35.272641 B40000200 Read-Ack Status: 00000010 00000000
20:15:38.157307 T80000200 Read-Data Status: 00000010 00000000
20:15:38.224256 B40000200 Read-Ack Status: 00000010 00000000
20:15:39.158748 T80000200 Read-Data Status: 00000010 00000000
20:15:39.280802 B40000200 Read-Ack Status: 00000010 00000000
20:15:40.161574 T80000200 Read-Data Status: 00000010 00000000
20:15:40.268007 B40000200 Read-Ack Status: 00000010 00000000
20:15:41.156374 T80000200 Read-Data Status: 00000010 00000000
20:15:41.246497 B40000200 Read-Ack Status: 00000010 00000000
20:15:42.159194 T80000200 Read-Data Status: 00000010 00000000
20:15:42.233139 B40000200 Read-Ack Status: 00000010 00000000
20:15:43.158445 T80000200 Read-Data Status: 00000010 00000000
20:15:43.217962 B40000200 Read-Ack Status: 00000010 00000000
20:15:44.157335 T80000200 Read-Data Status: 00000010 00000000
20:15:44.271810 B40000200 Read-Ack Status: 00000010 00000000
20:15:45.157667 T80000200 Read-Data Status: 00000010 00000000
20:15:45.256683 B40000200 Read-Ack Status: 00000010 00000000
20:15:52.150611 T80000200 Read-Data Status: 00000010 00000000
20:15:52.727524 T10010000 Write-Data Control setpoint: 0.00
20:15:52.849867 BD0010000 Write-Ack Control setpoint: 0.00
20:15:54.136173 T801A0000 Read-Data DHW temperature: 0.00
20:15:54.256608 B401A0000 Read-Ack DHW temperature: 0.00
20:15:54.400153 T001B6000 Read-Data Outside temperature: 96.00
20:15:56.151450 T80000200 Read-Data Status: 00000010 00000000
20:15:57.149572 T80000200 Read-Data Status: 00000010 00000000
20:15:58.152663 T80000200 Read-Data Status: 00000010 00000000
20:15:58.264650 B40000200 Read-Ack Status: 00000010 00000000
20:16:00.150945 T80000200 Read-Data Status: 00000010 00000000
20:16:00.234908 B40000200 Read-Ack Status: 00000010 00000000
20:16:01.149429 T80000200 Read-Data Status: 00000010 00000000
20:16:01.218719 B40000200 Read-Ack Status: 00000010 00000000
20:16:02.147410 T80000200 Read-Data Status: 00000010 00000000
20:16:02.271936 B40000200 Read-Ack Status: 00000010 00000000
20:16:03.147566 T80000200 Read-Data Status: 00000010 00000000
20:16:07.147144 T80000200 Read-Data Status: 00000010 00000000
20:16:07.263674 B40000200 Read-Ack Status: 00000010 00000000
20:16:09.143263 T80000200 Read-Data Status: 00000010 00000000
20:16:09.233558 B40000200 Read-Ack Status: 00000010 00000000
20:16:10.147512 T80000200 Read-Data Status: 00000010 00000000
20:16:10.219284 B40000200 Read-Ack Status: 00000010 00000000
20:16:12.142769 T80000200 Read-Data Status: 00000010 00000000
20:16:13.143930 T80000200 Read-Data Status: 00000010 00000000
20:16:13.239296 B40000200 Read-Ack Status: 00000010 00000000
20:16:15.140323 T80000200 Read-Data Status: 00000010 00000000
20:16:16.143183 T80000200 Read-Data Status: 00000010 00000000
20:16:16.263317 B40000200 Read-Ack Status: 00000010 00000000
20:16:19.144365 T80000200 Read-Data Status: 00000010 00000000
20:16:19.216803 B40000200 Read-Ack Status: 00000010 00000000
20:16:21.140980 T80000200 Read-Data Status: 00000010 00000000
20:16:21.257850 B40000200 Read-Ack Status: 00000010 00000000
20:16:25.137809 T80000200 Read-Data Status: 00000010 00000000
20:16:25.264118 B40000200 Read-Ack Status: 00000010 00000000
20:16:27.136529 T80000200 Read-Data Status: 00000010 00000000
20:16:27.235357 B40000200 Read-Ack Status: 00000010 00000000
20:16:28.140930 T80000200 Read-Data Status: 00000010 00000000
20:16:28.218846 B40000200 Read-Ack Status: 00000010 00000000
20:16:30.137033 T80000200 Read-Data Status: 00000010 00000000
20:16:30.256409 B40000200 Read-Ack Status: 00000010 00000000
20:16:31.135969 T80000200 Read-Data Status: 00000010 00000000
20:16:31.239809 B40000200 Read-Ack Status: 00000010 00000000
20:16:35.133455 T80000200 Read-Data Status: 00000010 00000000
20:16:36.133633 T80000200 Read-Data Status: 00000010 00000000
20:16:36.234008 B40000200 Read-Ack Status: 00000010 00000000
20:16:37.134709 T80000200 Read-Data Status: 00000010 00000000
20:16:37.216516 B40000200 Read-Ack Status: 00000010 00000000
20:16:38.134148 T80000200 Read-Data Status: 00000010 00000000
20:16:38.200390 B40000200 Read-Ack Status: 00000010 00000000
20:16:39.131796 T80000200 Read-Data Status: 00000010 00000000
20:16:39.256897 B40000200 Read-Ack Status: 00000010 00000000
20:16:40.132292 T80000200 Read-Data Status: 00000010 00000000
20:16:41.130598 T80000200 Read-Data Status: 00000010 00000000
20:16:43.131199 T80000200 Read-Data Status: 00000010 00000000
20:16:43.192768 B40000200 Read-Ack Status: 00000010 00000000
20:16:44.130373 T80000200 Read-Data Status: 00000010 00000000
20:16:44.247791 B40000200 Read-Ack Status: 00000010 00000000
20:16:45.132240 T80000200 Read-Data Status: 00000010 00000000
20:16:45.233818 B40000200 Read-Ack Status: 00000010 00000000
20:16:46.129212 T80000200 Read-Data Status: 00000010 00000000
20:16:46.216750 B40000200 Read-Ack Status: 00000010 00000000
20:16:47.130663 T80000200 Read-Data Status: 00000010 00000000
20:16:47.200085 B40000200 Read-Ack Status: 00000010 00000000
20:16:52.127544 T80000200 Read-Data Status: 00000010 00000000
20:16:55.000507 T001B0000 Read-Data Outside temperature: 0.00
20:16:59.123755 T80000200 Read-Data Status: 00000010 00000000
20:16:59.223364 B40000200 Read-Ack Status: 00000010 00000000
20:17:03.217978 T80000200 Read-Data Status: 00000010 00000000
20:17:03.233427 B40000200 Read-Ack Status: 00000010 00000000
20:17:04.123650 T80000200 Read-Data Status: 00000010 00000000
20:17:04.216758 B40000200 Read-Ack Status: 00000010 00000000
20:17:05.119404 T80000200 Read-Data Status: 00000010 00000000
20:17:06.120304 T80000200 Read-Data Status: 00000010 00000000
20:17:06.180770 B40000200 Read-Ack Status: 00000010 00000000
20:17:08.123038 T80000200 Read-Data Status: 00000010 00000000
20:17:08.226845 B40000200 Read-Ack Status: 00000010 00000000
20:17:09.121968 T80000200 Read-Data Status: 00000010 00000000
20:17:10.121558 T80000200 Read-Data Status: 00000010 00000000
20:17:12.121960 T80000200 Read-Data Status: 00000010 00000000
20:17:12.233221 B40000200 Read-Ack Status: 00000010 00000000
20:17:13.117125 T80000200 Read-Data Status: 00000010 00000000
20:17:14.122532 T80000200 Read-Data Status: 00000010 00000000
20:17:14.203284 B40000200 Read-Ack Status: 00000010 00000000
20:17:15.115682 T80000200 Read-Data Status: 00000010 00000000
20:17:15.190468 B40000200 Read-Ack Status: 00000010 00000000
20:17:19.116624 T80000200 Read-Data Status: 00000010 00000000
20:17:19.192088 B40000200 Read-Ack Status: 00000010 00000000
20:17:24.112073 T80000200 Read-Data Status: 00000010 00000000
20:17:25.112364 T80000200 Read-Data Status: 00000010 00000000
20:17:25.169573 B40000200 Read-Ack Status: 00000010 00000000
20:17:27.113227 T80000200 Read-Data Status: 00000010 00000000
20:17:27.209009 B40000200 Read-Ack Status: 00000010 00000000
20:17:28.112760 T80000200 Read-Data Status: 00000010 00000000
20:17:28.195704 B40000200 Read-Ack Status: 00000010 00000000
20:17:29.108607 T80000200 Read-Data Status: 00000010 00000000
20:17:29.175717 B40000200 Read-Ack Status: 00000010 00000000
20:17:30.109932 T80000200 Read-Data Status: 00000010 00000000
20:17:30.233013 B40000200 Read-Ack Status: 00000010 00000000
20:17:33.110389 T80000200 Read-Data Status: 00000010 00000000
20:17:33.178630 B40000200 Read-Ack Status: 00000010 00000000
20:17:36.106140 T80000200 Read-Data Status: 00000010 00000000
20:17:37.107174 T80000200 Read-Data Status: 00000010 00000000
20:17:38.105926 T80000200 Read-Data Status: 00000010 00000000
20:17:39.106346 T80000200 Read-Data Status: 00000010 00000000
20:17:39.231122 B40000200 Read-Ack Status: 00000010 00000000
20:17:41.103914 T80000200 Read-Data Status: 00000010 00000000
20:17:41.201352 B40000200 Read-Ack Status: 00000010 00000000
20:17:42.105379 T80000200 Read-Data Status: 00000010 00000000
20:17:42.185610 B40000200 Read-Ack Status: 00000010 00000000
20:17:45.101297 T80000200 Read-Data Status: 00000010 00000000
20:17:45.207923 B40000200 Read-Ack Status: 00000010 00000000
20:17:48.102861 T80000200 Read-Data Status: 00000010 00000000
20:17:48.163341 B40000200 Read-Ack Status: 00000010 00000000
20:17:50.099759 T80000200 Read-Data Status: 00000010 00000000
20:17:51.100115 T80000200 Read-Data Status: 00000010 00000000
20:17:51.184849 B40000200 Read-Ack Status: 00000010 00000000
20:17:52.675260 T10010000 Write-Data Control setpoint: 0.00
20:17:53.824370 T80190000 Read-Data Boiler water temperature: 0.00
20:17:54.398592 T801A0000 Read-Data DHW temperature: 0.00
20:17:54.975371 T001B0000 Read-Data Outside temperature: 0.00
20:17:55.049350 BF01B0000 Unk-DataId Outside temperature: 0.00
20:17:57.098565 T80000200 Read-Data Status: 00000010 00000000
20:17:57.161214 B40000200 Read-Ack Status: 00000010 00000000
20:17:58.099631 T80000200 Read-Data Status: 00000010 00000000
20:17:58.215812 B40000200 Read-Ack Status: 00000010 00000000
20:18:00.098552 T80000200 Read-Data Status: 00000010 00000000
20:18:01.096797 T80000200 Read-Data Status: 00000010 00000000
20:18:01.170606 B40000200 Read-Ack Status: 00000010 00000000
20:18:03.096762 T80000200 Read-Data Status: 00000010 00000000
20:18:03.208029 B40000200 Read-Ack Status: 00000010 00000000
20:18:04.096586 T80000200 Read-Data Status: 00000010 00000000
20:18:04.191653 B40000200 Read-Ack Status: 00000010 00000000
20:18:05.094076 T80000200 Read-Data Status: 00000010 00000000
20:18:05.174131 B40000200 Read-Ack Status: 00000010 00000000
20:18:06.095834 T80000200 Read-Data Status: 00000010 00000000
20:18:06.160012 B40000200 Read-Ack Status: 00000010 00000000
20:18:07.094225 T80000200 Read-Data Status: 00000010 00000000
20:18:07.218046 B40000200 Read-Ack Status: 00000010 00000000
20:18:08.091368 T80000200 Read-Data Status: 00000010 00000000
20:18:08.200311 B40000200 Read-Ack Status: 00000010 00000000
20:18:09.092897 T80000200 Read-Data Status: 00000010 00000000
20:18:09.184221 B40000200 Read-Ack Status: 00000010 00000000
20:18:12.091105 T80000200 Read-Data Status: 00000010 00000000
20:18:12.208168 B40000200 Read-Ack Status: 00000010 00000000
20:18:14.091062 T80000200 Read-Data Status: 00000010 00000000
20:18:16.091434 T80000200 Read-Data Status: 00000010 00000000
20:18:17.093181 T80000200 Read-Data Status: 00000010 00000000
20:18:17.202025 B40000200 Read-Ack Status: 00000010 00000000
20:18:18.089753 T80000200 Read-Data Status: 00000010 00000000
20:18:18.183227 B40000200 Read-Ack Status: 00000010 00000000
20:18:23.088580 T80000200 Read-Data Status: 00000010 00000000
20:18:25.086798 T80000200 Read-Data Status: 00000010 00000000
20:18:25.146513 B40000200 Read-Ack Status: 00000010 00000000
20:18:26.084917 T80060200 Read-Data Remote parameter flags: 00000010 00000000
20:18:26.200886 B40000200 Read-Ack Status: 00000010 00000000
20:18:27.087617 T80000200 Read-Data Status: 00000010 00000000
20:18:27.184799 B40000200 Read-Ack Status: 00000010 00000000
20:18:36.081986 T80000200 Read-Data Status: 00000010 00000000
20:18:36.182825 B40000200 Read-Ack Status: 00000010 00000000
20:18:39.081303 T80000200 Read-Data Status: 00000010 00000000
20:18:41.080118 T80000200 Read-Data Status: 00000010 00000000
20:18:41.175142 B40000200 Read-Ack Status: 00000010 00000000
20:18:43.080154 T80000200 Read-Data Status: 00000010 00000000
20:18:43.144685 B40000200 Read-Ack Status: 00000010 00000000
20:18:46.076535 T80000200 Read-Data Status: 00000010 00000000
20:18:46.166894 B40000200 Read-Ack Status: 00000010 00000000
20:18:48.076883 T80000200 Read-Data Status: 00000010 00000000
20:18:48.136584 B40000200 Read-Ack Status: 00000010 00000000
20:18:51.075005 T80000200 Read-Data Status: 00000010 00000000
20:18:51.159467 B40000200 Read-Ack Status: 00000010 00000000
20:18:55.158071 T80000200 Read-Data Status: 00000010 00000000
20:18:56.071552 T80000200 Read-Data Status: 00000010 00000000
20:18:58.071424 T80000200 Read-Data Status: 00000010 00000000
20:18:59.070329 T80000200 Read-Data Status: 00000010 00000000
20:19:01.074984 T80000200 Read-Data Status: 00000010 00000000
20:19:01.146512 B40000200 Read-Ack Status: 00000010 00000000
20:19:02.108267 T80000200 Read-Data Status: 00000010 00000000
20:19:02.129150 B40000200 Read-Ack Status: 00000010 00000000
20:19:03.069660 T80000200 Read-Data Status: 00000010 00000000
20:19:03.184571 B40000200 Read-Ack Status: 00000010 00000000
20:19:07.071993 T80000200 Read-Data Status: 00000010 00000000
20:19:08.065645 T80000200 Read-Data Status: 00000010 00000000
20:19:08.253713 B40000200 Read-Ack Status: 00000010 00000000
20:19:10.072269 T80000200 Read-Data Status: 00000010 00000000
20:19:10.143988 B40000200 Read-Ack Status: 00000010 00000000
20:19:12.067305 T80000200 Read-Data Status: 00000010 00000000
20:19:18.064429 T80000200 Read-Data Status: 00000010 00000000
20:19:18.160449 B40000200 Read-Ack Status: 00000010 00000000
20:19:19.062653 T80000200 Read-Data Status: 00000010 00000000
20:19:19.144333 B40000200 Read-Ack Status: 00000010 00000000
20:19:20.063772 T80000200 Read-Data Status: 00000010 00000000
20:19:20.125799 B40000200 Read-Ack Status: 00000010 00000000
20:19:21.061208 T80000200 Read-Data Status: 00000010 00000000
20:19:21.181766 B40000200 Read-Ack Status: 00000010 00000000
20:19:27.059421 T80000200 Read-Data Status: 00000010 00000000
20:19:27.158385 B40000200 Read-Ack Status: 00000010 00000000
20:19:28.059020 T80000200 Read-Data Status: 00000010 00000000
20:19:28.144367 B40000200 Read-Ack Status: 00000010 00000000
20:19:29.056841 T80000200 Read-Data Status: 00000010 00000000
20:19:29.129039 B40000200 Read-Ack Status: 00000010 00000000
20:19:30.059718 T87FF8200 Read-Data Message ID 255: 33280
20:19:36.169537 T80000200 Read-Data Status: 00000010 00000000
20:19:37.054799 T80000200 Read-Data Status: 00000010 00000000
20:19:37.141379 B40000200 Read-Ack Status: 00000010 00000000
20:19:38.056353 T80000200 Read-Data Status: 00000010 00000000
20:19:38.126990 B40000200 Read-Ack Status: 00000010 00000000
20:19:45.051829 T80000200 Read-Data Status: 00000010 00000000
20:19:46.051016 T80000200 Read-Data Status: 00000010 00000000
20:19:46.140115 B40000200 Read-Ack Status: 00000010 00000000
20:19:47.052481 T80000200 Read-Data Status: 00000010 00000000
20:19:47.125252 B40000200 Read-Ack Status: 00000010 00000000
20:19:49.049966 T80000200 Read-Data Status: 00000010 00000000
20:19:50.048491 T80000200 Read-Data Status: 00000010 00000000
20:19:50.150478 B40000200 Read-Ack Status: 00000010 00000000
20:19:54.593178 T001B0000 Read-Data Outside temperature: 0.00
20:19:54.651779 BF01B0000 Unk-DataId Outside temperature: 0.00
20:19:56.047053 T80000200 Read-Data Status: 00000010 00000000
20:19:57.043791 T80000200 Read-Data Status: 00000010 00000000
20:19:57.116909 B40000200 Read-Ack Status: 00000010 00000000
20:20:01.045266 T80000200 Read-Data Status: 00000010 00000000
20:20:02.043595 T80000200 Read-Data Status: 00000010 00000000
20:20:02.105510 B40000200 Read-Ack Status: 00000010 00000000
20:20:03.043783 T80000200 Read-Data Status: 00000010 00000000
20:20:04.043716 T80000200 Read-Data Status: 00000010 00000000
20:20:04.142976 B40000200 Read-Ack Status: 00000010 00000000
20:20:06.042307 T80000200 Read-Data Status: 00000010 00000000
20:20:07.041227 T80000200 Read-Data Status: 00000010 00000000
20:20:07.165216 B40000200 Read-Ack Status: 00000010 00000000
20:20:08.044394 T80000200 Read-Data Status: 00000010 00000000
20:20:10.039754 T80000200 Read-Data Status: 00000010 00000000
20:20:10.118556 B40000200 Read-Ack Status: 00000010 00000000
20:20:11.039447 T80000200 Read-Data Status: 00000010 00000000
20:20:12.042078 T80000200 Read-Data Status: 00000010 00000000
20:20:12.159350 B40000200 Read-Ack Status: 00000010 00000000
20:20:13.041562 T80000200 Read-Data Status: 00000010 00000000
20:20:13.138131 B40000200 Read-Ack Status: 00000010 00000000
20:20:14.037112 T80000200 Read-Data Status: 00000010 00000000
20:20:15.038261 T80000200 Read-Data Status: 00000010 00000000
20:20:15.112536 B40000200 Read-Ack Status: 00000010 00000000
20:20:18.036608 T80000200 Read-Data Status: 00000010 00000000
20:20:19.038544 T80000200 Read-Data Status: 00000010 00000000
20:20:20.036876 T80000200 Read-Data Status: 00000010 00000000
20:20:21.034920 T80000200 Read-Data Status: 00000010 00000000
20:20:21.158639 B40000200 Read-Ack Status: 00000010 00000000
20:20:23.032692 T80000200 Read-Data Status: 00000010 00000000
20:20:23.126823 B40000200 Read-Ack Status: 00000010 00000000
20:20:24.034231 T80000200 Read-Data Status: 00000010 00000000
20:20:24.111184 B40000200 Read-Ack Status: 00000010 00000000
20:20:26.034112 T80000200 Read-Data Status: 00000010 00000000
20:20:28.034716 T80000200 Read-Data Status: 00000010 00000000
20:20:29.033855 T9FF80200 Write-Data Message ID 248: 512
20:20:29.106863 B40000200 Read-Ack Status: 00000010 00000000
20:20:30.031111 T80000200 Read-Data Status: 00000010 00000000
20:20:30.160498 B40000200 Read-Ack Status: 00000010 00000000
20:20:32.031277 T80000200 Read-Data Status: 00000010 00000000
20:20:32.128199 B40000200 Read-Ack Status: 00000010 00000000
20:20:37.029452 T80000200 Read-Data Status: 00000010 00000000
20:20:37.118695 B40000200 Read-Ack Status: 00000010 00000000
20:20:39.028290 T80000200 Read-Data Status: 00000010 00000000
20:20:39.089225 B40000200 Read-Ack Status: 00000010 00000000
20:20:40.029412 T80000200 Read-Data Status: 00000010 00000000
20:20:40.140493 B40000200 Read-Ack Status: 00000010 00000000
20:20:41.027322 T80000200 Read-Data Status: 00000010 00000000
20:20:41.124557 B40000200 Read-Ack Status: 00000010 00000000
20:20:42.025164 T80000200 Read-Data Status: 00000010 00000000
20:20:46.042194 T80000200 Read-Data Status: 00000010 00000000
20:20:46.120667 B40000200 Read-Ack Status: 00000010 00000000
20:20:47.024417 T80000200 Read-Data Status: 00000010 00000000
20:20:47.100924 B40000200 Read-Ack Status: 00000010 00000000
20:20:48.026965 T80000200 Read-Data Status: 00000010 00000000
20:20:48.090212 B40000200 Read-Ack Status: 00000010 00000000
20:20:49.021077 T80000200 Read-Data Status: 00000010 00000000
20:20:50.025846 T80000200 Read-Data Status: 00000010 00000000
20:20:50.122992 B40000200 Read-Ack Status: 00000010 00000000
20:20:52.595780 T10010000 Write-Data Control setpoint: 0.00
20:20:53.745446 T80190000 Read-Data Boiler water temperature: 0.00
20:20:53.853447 B40192E00 Read-Ack Boiler water temperature: 46.00
20:20:54.775418 T80000200 Read-Data Status: 00000010 00000000
20:20:54.839563 B40000200 Read-Ack Status: 00000010 00000000
20:20:55.021812 T80000200 Read-Data Status: 00000010 00000000
20:20:57.020248 T80000200 Read-Data Status: 00000010 00000000
20:20:57.086247 B40000200 Read-Ack Status: 00000010 00000000
20:20:58.020647 T80000200 Read-Data Status: 00000010 00000000
20:20:58.141572 B40000200 Read-Ack Status: 00000010 00000000
20:20:59.017585 T80000200 Read-Data Status: 00000010 00000000
20:20:59.124310 B40000200 Read-Ack Status: 00000010 00000000
20:21:04.014576 T80000200 Read-Data Status: 00000010 00000000
20:21:06.017648 T80000200 Read-Data Status: 00000010 00000000
20:21:06.088034 B40000200 Read-Ack Status: 00000010 00000000
20:21:07.014691 T80000200 Read-Data Status: 00000010 00000000
20:21:07.142665 B40000200 Read-Ack Status: 00000010 00000000
20:21:08.018830 T80000200 Read-Data Status: 00000010 00000000
20:21:08.125182 B40000200 Read-Ack Status: 00000010 00000000
20:21:09.015202 T80000200 Read-Data Status: 00000010 00000000
20:21:09.112332 B40000200 Read-Ack Status: 00000010 00000000
20:21:11.030972 T80000200 Read-Data Status: 00000010 00000000
20:21:12.124518 Error FF
20:21:14.013046 T80000200 Read-Data Status: 00000010 00000000
20:21:14.102803 B40000200 Read-Ack Status: 00000010 00000000
20:21:16.012441 T80000200 Read-Data Status: 00000010 00000000
20:21:16.071200 B40000200 Read-Ack Status: 00000010 00000000
20:21:17.011849 T80000200 Read-Data Status: 00000010 00000000
20:21:17.119186 B40000200 Read-Ack Status: 00000010 00000000
20:21:18.010712 T80000200 Read-Data Status: 00000010 00000000
20:21:21.007488 T80000200 Read-Data Status: 00000010 00000000
20:21:23.008614 T80000200 Read-Data Status: 00000010 00000000
20:21:23.101327 B40000200 Read-Ack Status: 00000010 00000000
20:21:24.010470 T80000200 Read-Data Status: 00000010 00000000
20:21:24.085375 B40000200 Read-Ack Status: 00000010 00000000
20:21:30.006768 T80000200 Read-Data Status: 00000010 00000000
20:21:30.066657 B40000200 Read-Ack Status: 00000010 00000000
20:21:34.005072 T80000200 Read-Data Status: 00000010 00000000
20:21:34.073985 B40000200 Read-Ack Status: 00000010 00000000
20:21:36.004812 T80000200 Read-Data Status: 00000010 00000000
20:21:36.111322 B40000200 Read-Ack Status: 00000010 00000000
20:21:39.001227 T80000200 Read-Data Status: 00000010 00000000
20:21:39.062431 B40000200 Read-Ack Status: 00000010 00000000
20:21:40.003288 T80000200 Read-Data Status: 00000010 00000000
20:21:43.003668 T80000200 Read-Data Status: 00000010 00000000
20:21:43.074395 B40000200 Read-Ack Status: 00000010 00000000
20:21:44.999037 T80000200 Read-Data Status: 00000010 00000000
20:21:45.110653 B40000200 Read-Ack Status: 00000010 00000000
20:21:47.998019 T80000200 Read-Data Status: 00000010 00000000
20:21:48.063599 B40000200 Read-Ack Status: 00000010 00000000
20:21:48.996345 T80000200 Read-Data Status: 00000010 00000000
20:21:50.997481 T80000200 Read-Data Status: 00000010 00000000
20:21:51.086075 B40000200 Read-Ack Status: 00000010 00000000
20:21:51.995334 T80000200 Read-Data Status: 00000010 00000000
20:21:52.073323 B40000200 Read-Ack Status: 00000010 00000000
20:21:55.317401 T80000200 Read-Data Status: 00000010 00000000
20:21:55.994321 T80000200 Read-Data Status: 00000010 00000000
20:21:58.991917 T80000200 Read-Data Status: 00000010 00000000
20:21:59.101114 B40000200 Read-Ack Status: 00000010 00000000
20:22:00.995576 T80000200 Read-Data Status: 00000010 00000000
20:22:01.070530 B40000200 Read-Ack Status: 00000010 00000000
20:22:01.990493 T80000200 Read-Data Status: 00000010 00000000
20:22:02.066426 Error 03
20:22:02.993188 T80000200 Read-Data Status: 00000010 00000000
20:22:03.110449 B40000200 Read-Ack Status: 00000010 00000000
20:22:03.990523 T80000200 Read-Data Status: 00000010 00000000
20:22:04.093579 B40000200 Read-Ack Status: 00000010 00000000
20:22:06.989047 T80000200 Read-Data Status: 00000010 00000000
20:22:07.988711 T80000200 Read-Data Status: 00000010 00000000
20:22:08.104991 B40000200 Read-Ack Status: 00000010 00000000
20:22:08.989916 T80000200 Read-Data Status: 00000010 00000000
20:22:09.988823 T80000200 Read-Data Status: 00000010 00000000
20:22:10.069986 B40000200 Read-Ack Status: 00000010 00000000
20:22:10.986862 T80000200 Read-Data Status: 00000010 00000000
20:22:11.055277 B40000200 Read-Ack Status: 00000010 00000000
20:22:12.986104 T80000200 Read-Data Status: 00000010 00000000
20:22:13.093705 B40000200 Read-Ack Status: 00000010 00000000
20:22:14.984755 T80000200 Read-Data Status: 00000010 00000000
20:22:15.061861 B40000200 Read-Ack Status: 00000010 00000000
20:22:15.985182 T80000200 Read-Data Status: 00000010 00000000
20:22:16.046911 B40000200 Read-Ack Status: 00000010 00000000
20:22:16.983408 T80000200 Read-Data Status: 00000010 00000000
20:22:17.099901 B40000200 Read-Ack Status: 00000010 00000000
20:22:18.984346 T80000200 Read-Data Status: 00000010 00000000
20:22:19.069789 B40000200 Read-Ack Status: 00000010 00000000
20:22:19.982755 T80000200 Read-Data Status: 00000010 00000000
20:22:20.053812 B40000200 Read-Ack Status: 00000010 00000000
20:22:20.983888 T80000200 Read-Data Status: 00000010 00000000
20:22:21.041190 B40000200 Read-Ack Status: 00000010 00000000
20:22:21.989182 T80000200 Read-Data Status: 00000010 00000000
20:22:22.094307 B40000200 Read-Ack Status: 00000010 00000000
20:22:22.983510 T80000200 Read-Data Status: 00000010 00000000
20:22:23.983269 T80000200 Read-Data Status: 00000010 00000000
20:22:26.979910 T83000200 Read-Data Status: 00000010 00000000
20:22:27.981544 T80000200 Read-Data Status: 00000010 00000000
20:22:28.073505 B40000200 Read-Ack Status: 00000010 00000000
20:22:28.979420 T80000200 Read-Data Status: 00000010 00000000
20:22:29.055429 B40000200 Read-Ack Status: 00000010 00000000
20:22:29.977873 T80000200 Read-Data Status: 00000010 00000000
20:22:31.976202 T80000200 Read-Data Status: 00000010 00000000
20:22:32.080287 B40000200 Read-Ack Status: 00000010 00000000
20:22:36.019919 T80000200 Read-Data Status: 00000010 00000000
20:22:36.085264 B40000200 Read-Ack Status: 00000010 00000000
20:22:36.975598 T80000200 Read-Data Status: 00000010 00000000
20:22:37.071600 B40000200 Read-Ack Status: 00000010 00000000
20:22:37.975107 T80000200 Read-Data Status: 00000010 00000000
20:22:38.052411 B40000200 Read-Ack Status: 00000010 00000000
20:22:38.975357 T80000200 Read-Data Status: 00000010 00000000
20:22:39.040827 B40000200 Read-Ack Status: 00000010 00000000
20:22:39.974777 T80000200 Read-Data Status: 00000010 00000000
20:22:40.093579 B40000200 Read-Ack Status: 00000010 00000000
20:22:40.973693 T80000200 Read-Data Status: 00000010 00000000
20:22:44.977099 T80000200 Read-Data Status: 00000010 00000000
20:22:45.089538 B40000200 Read-Ack Status: 00000010 00000000
20:22:46.972335 T80000200 Read-Data Status: 00000010 00000000
20:22:47.054389 B40000200 Read-Ack Status: 00000010 00000000
20:22:47.971451 T80000200 Read-Data Status: 00000010 00000000
20:22:48.038930 B40000200 Read-Ack Status: 00000010 00000000
20:22:53.324034 T80190000 Read-Data Boiler water temperature: 0.00
20:22:53.384806 B40192E00 Read-Ack Boiler water temperature: 46.00
20:22:55.246973 T80000200 Read-Data Status: 00000010 00000000
20:22:55.350886 B40000200 Read-Ack Status: 00000010 00000000
20:22:55.970066 T80000200 Read-Data Status: 00000010 00000000
20:22:56.054604 B40000200 Read-Ack Status: 00000010 00000000
20:22:56.967383 T98000200 Write-Data Status: 00000010 00000000
20:22:59.968763 T80000200 Read-Data Status: 00000010 00000000
20:23:01.966302 T80000200 Read-Data Status: 00000010 00000000
20:23:02.029917 B40000200 Read-Ack Status: 00000010 00000000
20:23:03.966941 T80000200 Read-Data Status: 00000010 00000000
20:23:04.073024 B40000200 Read-Ack Status: 00000010 00000000
20:23:04.963304 T80000200 Read-Data Status: 00000010 00000000
20:23:05.057078 B40000200 Read-Ack Status: 00000010 00000000
20:23:05.961568 T80000200 Read-Data Status: 00000010 00000000
20:23:06.048259 Error 03
20:23:06.962407 T80000200 Read-Data Status: 00000010 00000000
20:23:07.023221 B40000200 Read-Ack Status: 00000010 00000000
20:23:08.962998 T80000200 Read-Data Status: 00000010 00000000
20:23:10.961745 T80000200 Read-Data Status: 00000010 00000000
20:23:11.028721 B40000200 Read-Ack Status: 00000010 00000000
20:23:11.961451 T80000200 Read-Data Status: 00000010 00000000
20:23:12.084947 B40000200 Read-Ack Status: 00000010 00000000
20:23:13.960904 T80000200 Read-Data Status: 00000010 00000000
20:23:14.056937 B40000200 Read-Ack Status: 00000010 00000000
20:23:14.958950 T80000200 Read-Data Status: 00000010 00000000
20:23:15.037794 B40000200 Read-Ack Status: 00000010 00000000
20:23:19.956846 T80000200 Read-Data Status: 00000010 00000000
20:23:20.030136 B40000200 Read-Ack Status: 00000010 00000000
20:23:21.959514 T80000200 Read-Data Status: 00000010 00000000
20:23:22.068406 B40000200 Read-Ack Status: 00000010 00000000
20:23:22.955456 T80000200 Read-Data Status: 00000010 00000000
20:23:23.053199 B40000200 Read-Ack Status: 00000010 00000000
20:23:28.957620 T80000200 Read-Data Status: 00000010 00000000
20:23:29.028367 B40000200 Read-Ack Status: 00000010 00000000
20:23:32.035520 T80000200 Read-Data Status: 00000010 00000000
20:23:32.053828 B40000200 Read-Ack Status: 00000010 00000000
20:23:32.949726 T80000200 Read-Data Status: 00000010 00000000
20:23:33.039166 B40000200 Read-Ack Status: 00000010 00000000
20:23:33.952595 T80000200 Read-Data Status: 00000010 00000000
20:23:34.022200 B40000200 Read-Ack Status: 00000010 00000000
20:23:35.951187 T80000200 Read-Data Status: 00000010 00000000
20:23:36.061531 B40000200 Read-Ack Status: 00000010 00000000
20:23:37.948596 T80000200 Read-Data Status: 00000010 00000000
20:23:38.949971 T80000200 Read-Data Status: 00000010 00000000
20:23:39.015259 B40000200 Read-Ack Status: 00000010 00000000
20:23:39.950029 T80000200 Read-Data Status: 00000010 00000000
20:23:40.069412 B40000200 Read-Ack Status: 00000010 00000000
20:23:40.947744 T80000200 Read-Data Status: 00000010 00000000
20:23:41.054179 B40000200 Read-Ack Status: 00000010 00000000
20:23:44.948111 T80000200 Read-Data Status: 00000010 00000000
20:23:45.060747 B40000200 Read-Ack Status: 00000010 00000000
20:23:47.949007 T80000200 Read-Data Status: 00000010 00000000
20:23:48.946238 T80000200 Read-Data Status: 00000010 00000000
20:23:49.066424 B40000200 Read-Ack Status: 00000010 00000000
20:23:49.944935 T80000200 Read-Data Status: 00000010 00000000
20:23:50.056539 B40000200 Read-Ack Status: 00000010 00000000
20:23:50.944032 T80000200 Read-Data Status: 00000010 00000000
20:23:52.516373 T10010000 Write-Data Control setpoint: 0.00
20:23:53.093332 T100E0000 Write-Data Maximum relative modulation level: 0.00
20:23:53.216820 BD00E0000 Write-Ack Maximum relative modulation level: 0.00
20:23:53.356865 T80190000 Read-Data Boiler water temperature: 0.00
20:23:53.430436 B40192E00 Read-Ack Boiler water temperature: 46.00
20:23:54.941690 T80000200 Read-Data Status: 00000010 00000000
20:23:56.942582 T80000200 Read-Data Status: 00000010 00000000
20:23:57.940212 T80000200 Read-Data Status: 00000010 00000000
20:23:57.998843 B40000200 Read-Ack Status: 00000010 00000000
20:23:58.941270 T80000200 Read-Data Status: 00000010 00000000
20:23:59.053038 B40000200 Read-Ack Status: 00000010 00000000
20:24:00.937163 T80000200 Read-Data Status: 00000010 00000000
20:24:01.021521 B40000200 Read-Ack Status: 00000010 00000000
20:24:07.934485 T80000200 Read-Data Status: 00000010 00000000
20:24:08.935715 T80000200 Read-Data Status: 00000010 00000000
20:24:09.037494 B40000200 Read-Ack Status: 00000010 00000000
20:24:16.991616 T80000200 Read-Data Status: 00000010 00000000
20:24:17.051429 B40000200 Read-Ack Status: 00000010 00000000
20:24:24.929276 T80000200 Read-Data Status: 00000010 00000000
20:24:24.998383 B40000200 Read-Ack Status: 00000010 00000000
20:24:25.926527 T80000200 Read-Data Status: 00000010 00000000
20:24:26.930266 T80000800 Read-Data Status: 00001000 00000000
20:24:31.925104 T8000C200 Read-Data Status: 11000010 00000000
20:24:34.923855 T80000200 Read-Data Status: 00000010 00000000
20:24:34.982841 B40000200 Read-Ack Status: 00000010 00000000
20:24:38.925605 T80000200 Read-Data Status: 00000010 00000000
20:24:38.987294 B40000200 Read-Ack Status: 00000010 00000000
20:24:41.923609 T80000200 Read-Data Status: 00000010 00000000
20:24:42.018651 B40000200 Read-Ack Status: 00000010 00000000
20:24:42.920868 T80000200 Read-Data Status: 00000010 00000000
20:24:43.918192 T80000200 Read-Data Status: 00000010 00000000
20:24:43.981895 B40000200 Read-Ack Status: 00000010 00000000
20:24:44.920789 T80000200 Read-Data Status: 00000010 00000000
20:24:45.922329 T83FFC200 Read-Data Message ID 255: 49664
20:24:48.918344 T80000200 Read-Data Status: 00000010 00000000
20:24:49.046247 B40000200 Read-Ack Status: 00000010 00000000
20:24:49.918190 T80000200 Read-Data Status: 00000010 00000000
20:24:53.644841 T80190000 Read-Data Boiler water temperature: 0.00
20:24:53.750992 B40192D00 Read-Ack Boiler water temperature: 45.00
20:24:53.891314 T801A0000 Read-Data DHW temperature: 0.00
20:24:53.965654 B401A0000 Read-Ack DHW temperature: 0.00
20:24:54.682399 T80000200 Read-Data Status: 00000010 00000000
20:24:55.255367 T80000200 Read-Data Status: 00000010 00000000
20:24:55.373602 B40000200 Read-Ack Status: 00000010 00000000
20:24:56.918375 T80000200 Read-Data Status: 00000010 00000000
20:24:57.917388 T80000200 Read-Data Status: 00000010 00000000
20:24:57.975176 B40000200 Read-Ack Status: 00000010 00000000
20:24:58.915321 T80000200 Read-Data Status: 00000010 00000000
20:24:59.027376 B40000200 Read-Ack Status: 00000010 00000000
20:25:00.911861 T80000200 Read-Data Status: 00000010 00000000
20:25:00.996648 B40000200 Read-Ack Status: 00000010 00000000
20:25:01.912588 T80000200 Read-Data Status: 00000010 00000000
20:25:01.988671 B40000200 Read-Ack Status: 00000010 00000000
20:25:03.912513 T80006200 Read-Data Status: 01100010 00000000
20:25:07.910265 T80000200 Read-Data Status: 00000010 00000000
20:25:09.910588 T80000200 Read-Data Status: 00000010 00000000
20:25:10.000217 B40000200 Read-Ack Status: 00000010 00000000
20:25:10.907861 T80000200 Read-Data Status: 00000010 00000000
20:25:10.978809 B40000200 Read-Ack Status: 00000010 00000000
20:25:16.905532 T81FF6000 Read-Data Message ID 255: 24576
20:25:17.100905 B40000200 Read-Ack Status: 00000010 00000000
20:25:18.905048 T80000200 Read-Data Status: 00000010 00000000
20:25:18.997077 B40000200 Read-Ack Status: 00000010 00000000
20:25:19.907340 T80000200 Read-Data Status: 00000010 00000000
20:25:19.981311 B40000200 Read-Ack Status: 00000010 00000000
20:25:21.906993 T80000200 Read-Data Status: 00000010 00000000
20:25:22.020306 B40000200 Read-Ack Status: 00000010 00000000
20:25:23.905311 T80000200 Read-Data Status: 00000010 00000000
20:25:26.905110 T80000200 Read-Data Status: 00000010 00000000
20:25:27.012158 B40000200 Read-Ack Status: 00000010 00000000
20:25:28.899743 T80000200 Read-Data Status: 00000010 00000000
20:25:28.980172 B40000200 Read-Ack Status: 00000010 00000000
20:25:30.901137 T81FFE200 Read-Data Message ID 255: 57856
20:25:31.936707 T80000200 Read-Data Status: 00000010 00000000
20:25:32.004554 B40000200 Read-Ack Status: 00000010 00000000
20:25:32.898014 T8FC00200 Read-Data Message ID 192: 512
20:25:36.897555 T80000200 Read-Data Status: 00000010 00000000
20:25:36.996329 B40000200 Read-Ack Status: 00000010 00000000
20:25:37.895942 T80000200 Read-Data Status: 00000010 00000000
20:25:37.973608 B40000200 Read-Ack Status: 00000010 00000000
20:25:38.901971 T80000200 Read-Data Status: 00000010 00000000
20:25:39.899663 T80000200 Read-Data Status: 00000010 00000000
20:25:40.019733 B40000200 Read-Ack Status: 00000010 00000000
20:25:41.894419 T80000200 Read-Data Status: 00000010 00000000
20:25:43.894262 T80000200 Read-Data Status: 00000010 00000000
20:25:45.895469 T80000200 Read-Data Status: 00000010 00000000
20:25:45.997502 B40000200 Read-Ack Status: 00000010 00000000
20:25:47.892037 T80000200 Read-Data Status: 00000010 00000000
20:25:48.892903 T80000200 Read-Data Status: 00000010 00000000
20:25:50.893396 T80000200 Read-Data Status: 00000010 00000000
20:25:53.614804 T80190000 Read-Data Boiler water temperature: 0.00
20:25:54.189880 T801A0000 Read-Data DHW temperature: 0.00
20:25:54.293673 B401A0000 Read-Ack DHW temperature: 0.00
20:25:55.004530 T80000200 Read-Data Status: 00000010 00000000
20:25:55.066385 B40000200 Read-Ack Status: 00000010 00000000
20:25:56.888389 T80000200 Read-Data Status: 00000010 00000000
20:25:56.964239 B40000200 Read-Ack Status: 00000010 00000000
20:26:03.888349 T80000200 Read-Data Status: 00000010 00000000
20:26:03.995455 B40000200 Read-Ack Status: 00000010 00000000
20:26:04.882979 T80180200 Read-Data Room temperature: 2.00
20:26:05.887942 T80000200 Read-Data Status: 00000010 00000000
20:26:05.965414 B40000200 Read-Ack Status: 00000010 00000000
20:26:06.883120 TBFFD8200 Reserved Message ID 253: 33280
20:26:08.882364 T80000200 Read-Data Status: 00000010 00000000
20:26:08.987863 B40000200 Read-Ack Status: 00000010 00000000
20:26:10.880520 T80000200 Read-Data Status: 00000010 00000000
20:26:10.957120 B40000200 Read-Ack Status: 00000010 00000000
20:26:11.880742 T80000200 Read-Data Status: 00000010 00000000
20:26:11.940622 B40000200 Read-Ack Status: 00000010 00000000
20:26:13.881971 T80000200 Read-Data Status: 00000010 00000000
20:26:13.978754 B40000200 Read-Ack Status: 00000010 00000000
20:26:18.880501 T80000200 Read-Data Status: 00000010 00000000
20:26:18.973190 B40000200 Read-Ack Status: 00000010 00000000
20:26:21.876816 T80000200 Read-Data Status: 00000010 00000000
20:26:21.995260 B40000200 Read-Ack Status: 00000010 00000000
20:26:22.876016 T80000200 Read-Data Status: 00000010 00000000
20:26:23.877533 T80000200 Read-Data Status: 00000010 00000000
20:26:23.965577 B40000200 Read-Ack Status: 00000010 00000000
20:26:24.877363 T80000200 Read-Data Status: 00000010 00000000
20:26:24.948218 B40000200 Read-Ack Status: 00000010 00000000
20:26:26.874915 T80000200 Read-Data Status: 00000010 00000000
20:26:26.988274 B40000200 Read-Ack Status: 00000010 00000000
20:26:27.876475 T80000200 Read-Data Status: 00000010 00000000
20:26:27.971354 B40000200 Read-Ack Status: 00000010 00000000
20:26:28.875915 T80000200 Read-Data Status: 00000010 00000000
20:26:30.873724 T80000200 Read-Data Status: 00000010 00000000
20:26:32.875223 T80000200 Read-Data Status: 00000010 00000000
20:26:32.962608 B40000200 Read-Ack Status: 00000010 00000000
20:26:34.870820 T80000200 Read-Data Status: 00000010 00000000
20:26:34.931392 B40000200 Read-Ack Status: 00000010 00000000
20:26:37.868812 T80000200 Read-Data Status: 00000010 00000000
20:26:37.957582 B40000200 Read-Ack Status: 00000010 00000000
20:26:39.868920 T80000200 Read-Data Status: 00000010 00000000
20:26:39.994497 B40000200 Read-Ack Status: 00000010 00000000
20:26:40.868627 T83000200 Read-Data Status: 00000010 00000000
20:26:41.868241 T80000200 Read-Data Status: 00000010 00000000
20:26:41.957854 B40000200 Read-Ack Status: 00000010 00000000
20:26:42.868501 T80000200 Read-Data Status: 00000010 00000000
20:26:42.947981 B40000200 Read-Ack Status: 00000010 00000000
20:26:46.865285 T80001A00 Read-Data Status: 00011010 00000000
20:26:47.866363 T80000200 Read-Data Status: 00000010 00000000
20:26:47.939010 B40000200 Read-Ack Status: 00000010 00000000
20:26:48.865938 T80000200 Read-Data Status: 00000010 00000000
20:26:48.923878 B40000200 Read-Ack Status: 00000010 00000000
20:26:49.862451 T80000200 Read-Data Status: 00000010 00000000
20:26:50.863332 T80000200 Read-Data Status: 00000010 00000000
20:26:50.963571 B40000200 Read-Ack Status: 00000010 00000000
20:26:52.441113 T10010000 Write-Data Control setpoint: 0.00
20:26:52.537672 BD0010000 Write-Ack Control setpoint: 0.00
20:26:52.648848 T100E0000 Write-Data Maximum relative modulation level: 0.00
20:26:54.948624 T80000200 Read-Data Status: 00000010 00000000
20:26:56.861143 T80060200 Read-Data Remote parameter flags: 00000010 00000000
Error 03: 22684