Very long polling with Plugwise devices
Posted: Sun Dec 16, 2012 1:48 am
Hello,
I use 9 plugwise devices (1 circle + and 8 circles) to check power consumption.
Every 5 minutes, Domotiga check the status of each Plugwise device. In my case, this takes about 35 seconds during which any action is impossible. The application is completely frozen.
Do you see the same things with Domotiga and Plugwise?
Could it come from the firmware?
Below, you can see the logs of a query sequence of my Plugwise devices.
Thank you for your help.
Sol-R.
I use 9 plugwise devices (1 circle + and 8 circles) to check power consumption.
Every 5 minutes, Domotiga check the status of each Plugwise device. In my case, this takes about 35 seconds during which any action is impossible. The application is completely frozen.

Do you see the same things with Domotiga and Plugwise?
Could it come from the firmware?
Below, you can see the logs of a query sequence of my Plugwise devices.
Thank you for your help.
Sol-R.
Code: Select all
2012/12/16 00:13:42 [Plugwise] Checking power usage of device 'Informatique' with address 000D6F0001A44F76
2012/12/16 00:13:42 [Plugwise] Calibration Request
2012/12/16 00:13:42 [Plugwise] MAC: 000D6F0001A44F76
2012/12/16 00:13:42 [Plugwise] String: 0026000D6F0001A44F76 CRC: D867
2012/12/16 00:13:42 [Plugwise] Write: 0026000D6F0001A44F76D867
2012/12/16 00:13:43 [Plugwise] Write: 0026000D6F0001A44F76D867
2012/12/16 00:13:43 [Plugwise] Write: 0026000D6F0001A44F76D867
2012/12/16 00:13:43 [Plugwise] Write: 0026000D6F0001A44F76D867
2012/12/16 00:13:44 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:13:44 [Plugwise] Data wrong: 000022E500C19E33
▒002722E5000D6F0001A44F763F7D6492B4DA75EB3D42E715000000005A8F
000022E600C170E1
▒002722E6000D6F0001A44F763F7D6492B4DA75EB3D42E715000000008D02
000022E700C1DAB0
▒002722E7000D6F0001A44F763F7D6492B4DA75EB3D42E715000000003066
2012/12/16 00:13:44 [Plugwise] Data correct: 000022E500C19E33
▒002722E5000D6F0001A44F763F7D6492B4DA75EB3D42E715000000005A8F
000022E600C170E1
▒002722E6000D6F0001A44F763F7D6492B4DA75EB3D42E715000000008D02
000022E700C1DAB0
▒002722E7000D6F0001A44F763F7D6492B4DA75EB3D42E715000000003066
000022E800C1BF49
▒002722E8000D6F0001A44F763F7D6492B4DA75EB3D42E7150000000089BC
2012/12/16 00:13:44 [Plugwise] GetCalibration Result: 002722E5000D6F0001A44F763F7D6492B4DA75EB3D42E715000000005A8F
000022E600C170E1
▒002722E6000D6F0001A44F763F7D6492B4DA75EB3D42E715000000008D
2012/12/16 00:13:44 [Plugwise] Sequence Number: 22E5
2012/12/16 00:13:44 [Plugwise] GainA: 0.989815831184
2012/12/16 00:13:44 [Plugwise] GainB: -4.069146086749E-7
2012/12/16 00:13:44 [Plugwise] OffTot: 0.047583658248
2012/12/16 00:13:44 [Plugwise] OffNoise: 5.877471754111E-39
2012/12/16 00:13:44 [Plugwise] Write: 0012000D6F0001A44F769B9D
2012/12/16 00:13:44 [Plugwise] Write: 0012000D6F0001A44F769B9D
2012/12/16 00:13:44 [Plugwise] Write: 0012000D6F0001A44F769B9D
2012/12/16 00:13:44 [Plugwise] Write: 0012000D6F0001A44F769B9D
2012/12/16 00:13:45 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:13:45 [Plugwise] Data wrong: 000022E900C11518
▒001322E9000D6F0001A44F7600250124000061610000000000096BBF
000022EA00C10AB3
▒001322EA000D6F0001A44F76002501240000616100000000000960D1
000022EB00C1E461
▒001322EB000D6F0001A44F7600250124000061610000000000090C95
2012/12/16 00:13:45 [Plugwise] Data correct: 000022E900C11518
▒001322E9000D6F0001A44F7600250124000061610000000000096BBF
000022EA00C10AB3
▒001322EA000D6F0001A44F76002501240000616100000000000960D1
000022EB00C1E461
▒001322EB000D6F0001A44F7600250124000061610000000000090C95
000022EC00C14E30
▒001322EC000D6F0001A44F760024012400006185000000000010DABB
2012/12/16 00:13:45 [Plugwise] GetPowerInfo Result: 001322E9000D6F0001A44F7600250124000061610000000000096BBF
2012/12/16 00:13:45 [Plugwise] Sequence Number: 22E9
2012/12/16 00:13:45 [Plugwise] Pulses: 0025 (hex) 37
2012/12/16 00:13:45 [Plugwise] Corrected Pulses: 36.670212345971
2012/12/16 00:13:45 [Plugwise] kWh: 0.07819833696
2012/12/16 00:13:45 [Plugwise] Watt: 78.198336960483
2012/12/16 00:13:45 [Plugwise] Checking relay state of device 'Informatique' with address 000D6F0001A44F76
2012/12/16 00:13:45 [Plugwise] MAC: 000D6F0001A44F76
2012/12/16 00:13:45 [Plugwise] String: 0023000D6F0001A44F76 CRC: 8B0D
2012/12/16 00:13:45 [Plugwise] Write: 0023000D6F0001A44F768B0D
2012/12/16 00:13:45 [Plugwise] Write: 0023000D6F0001A44F768B0D
2012/12/16 00:13:45 [Plugwise] Write: 0023000D6F0001A44F768B0D
2012/12/16 00:13:46 [Plugwise] Write: 0023000D6F0001A44F768B0D
2012/12/16 00:13:46 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:13:46 [Plugwise] Data wrong: 000022ED00C129E4
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0001A44F76
▒002422ED000D6F0001A44F760C0C542F000479E801856539090087044E0843A901203B
000022EE00C183B5
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0001A44F76
▒002422EE000D6F0001A44F760C0C542F000479E801856539090087044E0843A9018565
000022EF00C16D67
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0001A44F76
▒002422EF000D6F0001A44F760C0C542F000479E801856539090087044E0843A9017AA6
2012/12/16 00:13:46 [Plugwise] Data correct: 000022ED00C129E4
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0001A44F76
▒002422ED000D6F0001A44F760C0C542F000479E801856539090087044E0843A901203B
000022EE00C183B5
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0001A44F76
▒002422EE000D6F0001A44F760C0C542F000479E801856539090087044E0843A9018565
000022EF00C16D67
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0001A44F76
▒002422EF000D6F0001A44F760C0C542F000479E801856539090087044E0843A9017AA6
000022F000C17384
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0001A44F76
▒002422F0000D6F0001A44F760C0C542F000479E801856539090087044E0843A901A7E5
2012/12/16 00:13:46 [Plugwise] GetDeviceInfo Result: 22ED000D6F0001A44F760C0C542F000479E801856539090087044E0843A9
2012/12/16 00:13:46 [Plugwise] MAC Address: 000D6F0001A44F76
2012/12/16 00:13:46 [Plugwise] Sequence Number: 22ED
2012/12/16 00:13:46 [Plugwise] Log Address: 463 (000479E8)
2012/12/16 00:13:46 [Plugwise] Time in Circle: 3084 12 21551
2012/12/16 00:13:46 [Plugwise] Frequency: 50Hz
2012/12/16 00:13:46 [Plugwise] Hardware version: 6539-0900-8704
2012/12/16 00:13:46 [Plugwise] Firmware: 2011/06/27 08:47:37
2012/12/16 00:13:46 [Plugwise] RelayState: 01 On
2012/12/16 00:13:46 [Plugwise] Checking power usage of device 'Four Micro-ondes' with address 000D6F0000B83184
2012/12/16 00:13:46 [Plugwise] Calibration Request
2012/12/16 00:13:46 [Plugwise] MAC: 000D6F0000B83184
2012/12/16 00:13:46 [Plugwise] String: 0026000D6F0000B83184 CRC: 1904
2012/12/16 00:13:46 [Plugwise] Write: 0026000D6F0000B831841904
2012/12/16 00:13:46 [Plugwise] Write: 0026000D6F0000B831841904
2012/12/16 00:13:47 [Plugwise] Write: 0026000D6F0000B831841904
2012/12/16 00:13:47 [Plugwise] Write: 0026000D6F0000B831841904
2012/12/16 00:13:47 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:13:47 [Plugwise] Data wrong: 000022F100C1D9D5
▒002722F1000D6F0000B831843F7F2297B6167DBC3D8738130000000035AF
000022F200C13707
▒002722F2000D6F0000B831843F7F2297B6167DBC3D87381300000000E222
000022F300C19D56
▒002722F3000D6F0000B831843F7F2297B6167DBC3D873813000000005F46
2012/12/16 00:13:47 [Plugwise] Data correct: 000022F100C1D9D5
▒002722F1000D6F0000B831843F7F2297B6167DBC3D8738130000000035AF
000022F200C13707
▒002722F2000D6F0000B831843F7F2297B6167DBC3D87381300000000E222
000022F300C19D56
▒002722F3000D6F0000B831843F7F2297B6167DBC3D873813000000005F46
000022F400C1FA82
▒002722F4000D6F0000B831843F7F2297B6167DBC3D873813000000005D19
2012/12/16 00:13:47 [Plugwise] GetCalibration Result: 002722F1000D6F0000B831843F7F2297B6167DBC3D8738130000000035AF
000022F200C13707
▒002722F2000D6F0000B831843F7F2297B6167DBC3D87381300000000E2
2012/12/16 00:13:47 [Plugwise] Sequence Number: 22F1
2012/12/16 00:13:47 [Plugwise] GainA: 0.996621549129
2012/12/16 00:13:47 [Plugwise] GainB: -2.242492882942E-6
2012/12/16 00:13:47 [Plugwise] OffTot: 0.066024921834
2012/12/16 00:13:47 [Plugwise] OffNoise: 5.877471754111E-39
2012/12/16 00:13:47 [Plugwise] Write: 0012000D6F0000B831845AFE
2012/12/16 00:13:48 [Plugwise] Write: 0012000D6F0000B831845AFE
2012/12/16 00:13:48 [Plugwise] Write: 0012000D6F0000B831845AFE
2012/12/16 00:13:48 [Plugwise] Write: 0012000D6F0000B831845AFE
2012/12/16 00:13:49 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:13:49 [Plugwise] Data wrong: 000022F500C150D3
▒001322F5000D6F0000B83184000100070000021300000000001094B3
000022F600C1BE01
▒001322F6000D6F0000B831840001000700000213000000000010F8F7
000022F700C11450
▒001322F7000D6F0000B8318400010007000002130000000000102CD4
2012/12/16 00:13:49 [Plugwise] Data correct: 000022F500C150D3
▒001322F5000D6F0000B83184000100070000021300000000001094B3
000022F600C1BE01
▒001322F6000D6F0000B831840001000700000213000000000010F8F7
000022F700C11450
▒001322F7000D6F0000B8318400010007000002130000000000102CD4
000022F800C171A9
▒001322F8000D6F0000B83184000100070000021400000000000D268B
2012/12/16 00:13:49 [Plugwise] GetPowerInfo Result: 001322F5000D6F0000B83184000100070000021300000000001094B3
2012/12/16 00:13:49 [Plugwise] Sequence Number: 22F5
2012/12/16 00:13:49 [Plugwise] Pulses: 0001 (hex) 1
2012/12/16 00:13:49 [Plugwise] Corrected Pulses: 1.062644228471
2012/12/16 00:13:49 [Plugwise] kWh: 0.002266063001
2012/12/16 00:13:49 [Plugwise] Watt: 2.266063001302
2012/12/16 00:13:49 [Plugwise] Checking relay state of device 'Four Micro-ondes' with address 000D6F0000B83184
2012/12/16 00:13:49 [Plugwise] MAC: 000D6F0000B83184
2012/12/16 00:13:49 [Plugwise] String: 0023000D6F0000B83184 CRC: 4A6E
2012/12/16 00:13:49 [Plugwise] Write: 0023000D6F0000B831844A6E
2012/12/16 00:13:49 [Plugwise] Write: 0023000D6F0000B831844A6E
2012/12/16 00:13:49 [Plugwise] Write: 0023000D6F0000B831844A6E
2012/12/16 00:13:50 [Plugwise] Write: 0023000D6F0000B831844A6E
2012/12/16 00:13:50 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:13:50 [Plugwise] Data wrong: 000022F900C1DBF8
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B83184
▒002422F9000D6F0000B831840C0C542F0004793001856539090088044E0844C202B7AA
000022FA00C1C453
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B83184
▒002422FA000D6F0000B831840C0C542F0004793001856539090088044E0844C20222EB
000022FB00C12A81
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B83184
▒002422FB000D6F0000B831840C0C542F0004793001856539090088044E0844C202DD28
2012/12/16 00:13:50 [Plugwise] Data correct: 000022F900C1DBF8
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B83184
▒002422F9000D6F0000B831840C0C542F0004793001856539090088044E0844C202B7AA
000022FA00C1C453
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B83184
▒002422FA000D6F0000B831840C0C542F0004793001856539090088044E0844C20222EB
000022FB00C12A81
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B83184
▒002422FB000D6F0000B831840C0C542F0004793001856539090088044E0844C202DD28
000022FC00C180D0
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B83184
▒002422FC000D6F0000B831840C0C542F0004793001856539090088044E0844C2027876
2012/12/16 00:13:50 [Plugwise] GetDeviceInfo Result: 22F9000D6F0000B831840C0C542F0004793001856539090088044E0844C2
2012/12/16 00:13:50 [Plugwise] MAC Address: 000D6F0000B83184
2012/12/16 00:13:50 [Plugwise] Sequence Number: 22F9
2012/12/16 00:13:50 [Plugwise] Log Address: 457 (00047930)
2012/12/16 00:13:50 [Plugwise] Time in Circle: 3084 12 21551
2012/12/16 00:13:50 [Plugwise] Frequency: 50Hz
2012/12/16 00:13:50 [Plugwise] Hardware version: 6539-0900-8804
2012/12/16 00:13:50 [Plugwise] Firmware: 2011/06/27 08:52:18
2012/12/16 00:13:50 [Plugwise] RelayState: 01 On
2012/12/16 00:13:50 [Plugwise] Checking power usage of device 'Lampe Salon 1' with address 000D6F0000B7E3EA
2012/12/16 00:13:50 [Plugwise] Calibration Request
2012/12/16 00:13:50 [Plugwise] MAC: 000D6F0000B7E3EA
2012/12/16 00:13:50 [Plugwise] String: 0026000D6F0000B7E3EA CRC: 2746
2012/12/16 00:13:50 [Plugwise] Write: 0026000D6F0000B7E3EA2746
2012/12/16 00:13:50 [Plugwise] Write: 0026000D6F0000B7E3EA2746
2012/12/16 00:13:51 [Plugwise] Write: 0026000D6F0000B7E3EA2746
2012/12/16 00:13:51 [Plugwise] Write: 0026000D6F0000B7E3EA2746
2012/12/16 00:13:51 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:13:51 [Plugwise] Data wrong: 000022FD00C1E704
▒002722FD000D6F0000B7E3EA3F7DAECFB628B0473D78C33E00000000A82C
000022FE00C14D55
▒002722FE000D6F0000B7E3EA3F7DAECFB628B0473D78C33E000000001548
000022FF00C1A387
▒002722FF000D6F0000B7E3EA3F7DAECFB628B0473D78C33E00000000C2C5
2012/12/16 00:13:51 [Plugwise] Data correct: 000022FD00C1E704
▒002722FD000D6F0000B7E3EA3F7DAECFB628B0473D78C33E00000000A82C
000022FE00C14D55
▒002722FE000D6F0000B7E3EA3F7DAECFB628B0473D78C33E000000001548
000022FF00C1A387
▒002722FF000D6F0000B7E3EA3F7DAECFB628B0473D78C33E00000000C2C5
0000230000C10398
▒00272300000D6F0000B7E3EA3F7DAECFB628B0473D78C33E00000000F58E
2012/12/16 00:13:51 [Plugwise] GetCalibration Result: 002722FD000D6F0000B7E3EA3F7DAECFB628B0473D78C33E00000000A82C
000022FE00C14D55
▒002722FE000D6F0000B7E3EA3F7DAECFB628B0473D78C33E0000000015
2012/12/16 00:13:51 [Plugwise] Sequence Number: 22FD
2012/12/16 00:13:51 [Plugwise] GainA: 0.990948617458
2012/12/16 00:13:51 [Plugwise] GainB: -2.513655772418E-6
2012/12/16 00:13:51 [Plugwise] OffTot: 0.06073307246
2012/12/16 00:13:51 [Plugwise] OffNoise: 5.877471754111E-39
2012/12/16 00:13:51 [Plugwise] Write: 0012000D6F0000B7E3EA64BC
2012/12/16 00:13:52 [Plugwise] Write: 0012000D6F0000B7E3EA64BC
2012/12/16 00:13:52 [Plugwise] Write: 0012000D6F0000B7E3EA64BC
2012/12/16 00:13:52 [Plugwise] Write: 0012000D6F0000B7E3EA64BC
2012/12/16 00:13:53 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:13:53 [Plugwise] Data wrong: 0000230100C1A9C9
▒00132301000D6F0000B7E3EAFFFFFFFF00000000FFFFFE4F00081DB2
0000230200C1471B
▒00132302000D6F0000B7E3EAFFFFFFFF00000000FFFFFE4F000871F6
0000230300C1ED4A
▒00132303000D6F0000B7E3EAFFFFFFFF00000000FFFFFE4F0008A5D5
2012/12/16 00:13:53 [Plugwise] Data correct: 0000230100C1A9C9
▒00132301000D6F0000B7E3EAFFFFFFFF00000000FFFFFE4F00081DB2
0000230200C1471B
▒00132302000D6F0000B7E3EAFFFFFFFF00000000FFFFFE4F000871F6
0000230300C1ED4A
▒00132303000D6F0000B7E3EAFFFFFFFF00000000FFFFFE4F0008A5D5
0000230400C18A9E
▒00132304000D6F0000B7E3EA0000FFFF00000000FFFFFE4F000F6D85
2012/12/16 00:13:53 [Plugwise] GetPowerInfo Result: 00132301000D6F0000B7E3EAFFFFFFFF00000000FFFFFE4F00081DB2
2012/12/16 00:13:53 [Plugwise] Sequence Number: 2301
2012/12/16 00:13:53 [Plugwise] Pulses: FFFF (hex) -1
2012/12/16 00:13:53 [Plugwise] Corrected Pulses: -0.930218058654
2012/12/16 00:13:53 [Plugwise] kWh: -0.001983667411
2012/12/16 00:13:53 [Plugwise] Watt: -1.983667411334
2012/12/16 00:13:53 [Plugwise] Checking relay state of device 'Lampe Salon 1' with address 000D6F0000B7E3EA
2012/12/16 00:13:53 [Plugwise] MAC: 000D6F0000B7E3EA
2012/12/16 00:13:53 [Plugwise] String: 0023000D6F0000B7E3EA CRC: 742C
2012/12/16 00:13:53 [Plugwise] Write: 0023000D6F0000B7E3EA742C
2012/12/16 00:13:53 [Plugwise] Write: 0023000D6F0000B7E3EA742C
2012/12/16 00:13:53 [Plugwise] Write: 0023000D6F0000B7E3EA742C
2012/12/16 00:13:54 [Plugwise] Write: 0023000D6F0000B7E3EA742C
2012/12/16 00:13:54 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:13:54 [Plugwise] Data wrong: 0000230500C120CF
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B7E3EA
▒00242305000D6F0000B7E3EA0C0C542F0004758800856539090088044E0844C202B8BE
0000230600C1CE1D
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B7E3EA
▒00242306000D6F0000B7E3EA0C0C542F0004758800856539090088044E0844C202477D
0000230700C1644C
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B7E3EA
▒00242307000D6F0000B7E3EA0C0C542F0004758800856539090088044E0844C202E223
2012/12/16 00:13:54 [Plugwise] Data correct: 0000230500C120CF
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B7E3EA
▒00242305000D6F0000B7E3EA0C0C542F0004758800856539090088044E0844C202B8BE
0000230600C1CE1D
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B7E3EA
▒00242306000D6F0000B7E3EA0C0C542F0004758800856539090088044E0844C202477D
0000230700C1644C
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B7E3EA
▒00242307000D6F0000B7E3EA0C0C542F0004758800856539090088044E0844C202E223
0000230800C101B5
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B7E3EA
▒00242308000D6F0000B7E3EA0C0C542F0004758800856539090088044E0844C202D28F
2012/12/16 00:13:54 [Plugwise] GetDeviceInfo Result: 2305000D6F0000B7E3EA0C0C542F0004758800856539090088044E0844C2
2012/12/16 00:13:54 [Plugwise] MAC Address: 000D6F0000B7E3EA
2012/12/16 00:13:54 [Plugwise] Sequence Number: 2305
2012/12/16 00:13:54 [Plugwise] Log Address: 428 (00047588)
2012/12/16 00:13:54 [Plugwise] Time in Circle: 3084 12 21551
2012/12/16 00:13:54 [Plugwise] Frequency: 50Hz
2012/12/16 00:13:54 [Plugwise] Hardware version: 6539-0900-8804
2012/12/16 00:13:54 [Plugwise] Firmware: 2011/06/27 08:52:18
2012/12/16 00:13:54 [Plugwise] RelayState: 00 Off
2012/12/16 00:13:54 [Plugwise] Checking power usage of device 'Lampe Dressing' with address 000D6F00004BC205
2012/12/16 00:13:54 [Plugwise] Calibration Request
2012/12/16 00:13:54 [Plugwise] MAC: 000D6F00004BC205
2012/12/16 00:13:54 [Plugwise] String: 0026000D6F00004BC205 CRC: 08FC
2012/12/16 00:13:54 [Plugwise] Write: 0026000D6F00004BC20508FC
2012/12/16 00:13:54 [Plugwise] Write: 0026000D6F00004BC20508FC
2012/12/16 00:13:55 [Plugwise] Write: 0026000D6F00004BC20508FC
2012/12/16 00:13:55 [Plugwise] Write: 0026000D6F00004BC20508FC
2012/12/16 00:13:55 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:13:55 [Plugwise] Data wrong: 0000230900C1ABE4
▒00272309000D6F00004BC2053F7ECD4434118FD83C8AB82700000000A309
0000230A00C1B44F
▒0027230A000D6F00004BC2053F7ECD4434118FD83C8AB827000000003D7C
0000230B00C15A9D
▒0027230B000D6F00004BC2053F7ECD4434118FD83C8AB82700000000EAF1
2012/12/16 00:13:55 [Plugwise] Data correct: 0000230900C1ABE4
▒00272309000D6F00004BC2053F7ECD4434118FD83C8AB82700000000A309
0000230A00C1B44F
▒0027230A000D6F00004BC2053F7ECD4434118FD83C8AB827000000003D7C
0000230B00C15A9D
▒0027230B000D6F00004BC2053F7ECD4434118FD83C8AB82700000000EAF1
0000230C00C1F0CC
▒0027230C000D6F00004BC2053F7ECD4434118FD83C8AB827000000005795
2012/12/16 00:13:55 [Plugwise] GetCalibration Result: 00272309000D6F00004BC2053F7ECD4434118FD83C8AB82700000000A309
0000230A00C1B44F
▒0027230A000D6F00004BC2053F7ECD4434118FD83C8AB827000000003D
2012/12/16 00:13:55 [Plugwise] Sequence Number: 2309
2012/12/16 00:13:55 [Plugwise] GainA: 0.995319604874
2012/12/16 00:13:55 [Plugwise] GainB: 1.355650738333E-7
2012/12/16 00:13:55 [Plugwise] OffTot: 0.016933513805
2012/12/16 00:13:55 [Plugwise] OffNoise: 5.877471754111E-39
2012/12/16 00:13:55 [Plugwise] Write: 0012000D6F00004BC2054B06
2012/12/16 00:13:56 [Plugwise] Write: 0012000D6F00004BC2054B06
2012/12/16 00:13:56 [Plugwise] Write: 0012000D6F00004BC2054B06
2012/12/16 00:13:56 [Plugwise] Write: 0012000D6F00004BC2054B06
2012/12/16 00:13:57 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:13:57 [Plugwise] Data wrong: 0000230D00C19718
▒0013230D000D6F00004BC2050000000000000000FFFFFDD4000AB5CB
0000230E00C13D49
▒0013230E000D6F00004BC2050000000000000000FFFFFDD4000A61E8
0000230F00C1D39B
▒0013230F000D6F00004BC2050000000000000000FFFFFDD4000A0DAC
2012/12/16 00:13:57 [Plugwise] Data correct: 0000230D00C19718
▒0013230D000D6F00004BC2050000000000000000FFFFFDD4000AB5CB
0000230E00C13D49
▒0013230E000D6F00004BC2050000000000000000FFFFFDD4000A61E8
0000230F00C1D39B
▒0013230F000D6F00004BC2050000000000000000FFFFFDD4000A0DAC
0000231000C14638
▒00132310000D6F00004BC2050000000000000000FFFFFDD40002F999
2012/12/16 00:13:57 [Plugwise] GetPowerInfo Result: 0013230D000D6F00004BC2050000000000000000FFFFFDD4000AB5CB
2012/12/16 00:13:57 [Plugwise] Sequence Number: 230D
2012/12/16 00:13:57 [Plugwise] Pulses: 0000 (hex) 0
2012/12/16 00:13:57 [Plugwise] Corrected Pulses: 0
2012/12/16 00:13:57 [Plugwise] kWh: 0
2012/12/16 00:13:57 [Plugwise] Watt: 0
2012/12/16 00:13:57 [Plugwise] Checking relay state of device 'Lampe Dressing' with address 000D6F00004BC205
2012/12/16 00:13:57 [Plugwise] MAC: 000D6F00004BC205
2012/12/16 00:13:57 [Plugwise] String: 0023000D6F00004BC205 CRC: 5B96
2012/12/16 00:13:57 [Plugwise] Write: 0023000D6F00004BC2055B96
2012/12/16 00:13:57 [Plugwise] Write: 0023000D6F00004BC2055B96
2012/12/16 00:13:57 [Plugwise] Write: 0023000D6F00004BC2055B96
2012/12/16 00:13:58 [Plugwise] Write: 0023000D6F00004BC2055B96
2012/12/16 00:13:58 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:13:58 [Plugwise] Data wrong: 0000231100C1EC69
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BC205
▒00242311000D6F00004BC2050C0C542F0004790000856539090088044E0844C2021EAA
0000231200C102BB
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BC205
▒00242312000D6F00004BC2050C0C542F0004790000856539090088044E0844C202E169
0000231300C1A8EA
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BC205
▒00242313000D6F00004BC2050C0C542F0004790000856539090088044E0844C2024437
2012/12/16 00:13:58 [Plugwise] Data correct: 0000231100C1EC69
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BC205
▒00242311000D6F00004BC2050C0C542F0004790000856539090088044E0844C2021EAA
0000231200C102BB
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BC205
▒00242312000D6F00004BC2050C0C542F0004790000856539090088044E0844C202E169
0000231300C1A8EA
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BC205
▒00242313000D6F00004BC2050C0C542F0004790000856539090088044E0844C2024437
0000231400C1CF3E
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BC205
▒00242314000D6F00004BC2050C0C542F0004790000856539090088044E0844C2020ECE
2012/12/16 00:13:58 [Plugwise] GetDeviceInfo Result: 2311000D6F00004BC2050C0C542F0004790000856539090088044E0844C2
2012/12/16 00:13:58 [Plugwise] MAC Address: 000D6F00004BC205
2012/12/16 00:13:58 [Plugwise] Sequence Number: 2311
2012/12/16 00:13:58 [Plugwise] Log Address: 456 (00047900)
2012/12/16 00:13:58 [Plugwise] Time in Circle: 3084 12 21551
2012/12/16 00:13:58 [Plugwise] Frequency: 50Hz
2012/12/16 00:13:58 [Plugwise] Hardware version: 6539-0900-8804
2012/12/16 00:13:58 [Plugwise] Firmware: 2011/06/27 08:52:18
2012/12/16 00:13:58 [Plugwise] RelayState: 00 Off
2012/12/16 00:13:58 [Plugwise] Checking power usage of device 'Frigo' with address 000D6F0000B7E3F1
2012/12/16 00:13:58 [Plugwise] Calibration Request
2012/12/16 00:13:58 [Plugwise] MAC: 000D6F0000B7E3F1
2012/12/16 00:13:58 [Plugwise] String: 0026000D6F0000B7E3F1 CRC: 0C82
2012/12/16 00:13:58 [Plugwise] Write: 0026000D6F0000B7E3F10C82
2012/12/16 00:13:58 [Plugwise] Write: 0026000D6F0000B7E3F10C82
2012/12/16 00:13:59 [Plugwise] Write: 0026000D6F0000B7E3F10C82
2012/12/16 00:13:59 [Plugwise] Write: 0026000D6F0000B7E3F10C82
2012/12/16 00:13:59 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:13:59 [Plugwise] Data wrong: 0000231500C1656F
▒00272315000D6F0000B7E3F13F802BBFB617C53F3CBFD83B000000002248
0000231600C18BBD
▒00272316000D6F0000B7E3F13F802BBFB617C53F3CBFD83B00000000F5C5
0000231700C121EC
▒00272317000D6F0000B7E3F13F802BBFB617C53F3CBFD83B0000000048A1
2012/12/16 00:13:59 [Plugwise] Data correct: 0000231500C1656F
▒00272315000D6F0000B7E3F13F802BBFB617C53F3CBFD83B000000002248
0000231600C18BBD
▒00272316000D6F0000B7E3F13F802BBFB617C53F3CBFD83B00000000F5C5
0000231700C121EC
▒00272317000D6F0000B7E3F13F802BBFB617C53F3CBFD83B0000000048A1
0000231800C14415
▒00272318000D6F0000B7E3F13F802BBFB617C53F3CBFD83B00000000F17B
2012/12/16 00:13:59 [Plugwise] GetCalibration Result: 00272315000D6F0000B7E3F13F802BBFB617C53F3CBFD83B000000002248
0000231600C18BBD
▒00272316000D6F0000B7E3F13F802BBFB617C53F3CBFD83B00000000F5
2012/12/16 00:13:59 [Plugwise] Sequence Number: 2315
2012/12/16 00:13:59 [Plugwise] GainA: 1.001335024834
2012/12/16 00:13:59 [Plugwise] GainB: -2.261556574013E-6
2012/12/16 00:13:59 [Plugwise] OffTot: 0.02341853641
2012/12/16 00:13:59 [Plugwise] OffNoise: 5.877471754111E-39
2012/12/16 00:13:59 [Plugwise] Write: 0012000D6F0000B7E3F14F78
2012/12/16 00:13:59 [Plugwise] Write: 0012000D6F0000B7E3F14F78
2012/12/16 00:14:00 [Plugwise] Write: 0012000D6F0000B7E3F14F78
2012/12/16 00:14:00 [Plugwise] Write: 0012000D6F0000B7E3F14F78
2012/12/16 00:14:00 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:14:00 [Plugwise] Data wrong: 0000231900C1EE44
▒00132319000D6F0000B7E3F10000000000000000FFFFFDAA00056481
0000231A00C1F1EF
▒0013231A000D6F0000B7E3F10000000000000000FFFFFDAA00056FEF
0000231B00C11F3D
▒0013231B000D6F0000B7E3F10000000000000000FFFFFDAA000503AB
2012/12/16 00:14:00 [Plugwise] Data correct: 0000231900C1EE44
▒00132319000D6F0000B7E3F10000000000000000FFFFFDAA00056481
0000231A00C1F1EF
▒0013231A000D6F0000B7E3F10000000000000000FFFFFDAA00056FEF
0000231B00C11F3D
▒0013231B000D6F0000B7E3F10000000000000000FFFFFDAA000503AB
0000231C00C1B56C
▒0013231C000D6F0000B7E3F10000000000000000FFFFFDAA0005D788
2012/12/16 00:14:00 [Plugwise] GetPowerInfo Result: 00132319000D6F0000B7E3F10000000000000000FFFFFDAA00056481
2012/12/16 00:14:00 [Plugwise] Sequence Number: 2319
2012/12/16 00:14:00 [Plugwise] Pulses: 0000 (hex) 0
2012/12/16 00:14:00 [Plugwise] Corrected Pulses: 0
2012/12/16 00:14:00 [Plugwise] kWh: 0
2012/12/16 00:14:00 [Plugwise] Watt: 0
2012/12/16 00:14:00 [Plugwise] Checking relay state of device 'Frigo' with address 000D6F0000B7E3F1
2012/12/16 00:14:00 [Plugwise] MAC: 000D6F0000B7E3F1
2012/12/16 00:14:00 [Plugwise] String: 0023000D6F0000B7E3F1 CRC: 5FE8
2012/12/16 00:14:00 [Plugwise] Write: 0023000D6F0000B7E3F15FE8
2012/12/16 00:14:01 [Plugwise] Write: 0023000D6F0000B7E3F15FE8
2012/12/16 00:14:01 [Plugwise] Write: 0023000D6F0000B7E3F15FE8
2012/12/16 00:14:01 [Plugwise] Write: 0023000D6F0000B7E3F15FE8
2012/12/16 00:14:02 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:14:02 [Plugwise] Data wrong: 0000231D00C1D2B8
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B7E3F1
▒0024231D000D6F0000B7E3F10C0C542F0004792801856539090088044E0844C202E4CE
0000231E00C178E9
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B7E3F1
▒0024231E000D6F0000B7E3F10C0C542F0004792801856539090088044E0844C2024190
0000231F00C1963B
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B7E3F1
▒0024231F000D6F0000B7E3F10C0C542F0004792801856539090088044E0844C202BE53
2012/12/16 00:14:02 [Plugwise] Data correct: 0000231D00C1D2B8
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B7E3F1
▒0024231D000D6F0000B7E3F10C0C542F0004792801856539090088044E0844C202E4CE
0000231E00C178E9
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B7E3F1
▒0024231E000D6F0000B7E3F10C0C542F0004792801856539090088044E0844C2024190
0000231F00C1963B
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B7E3F1
▒0024231F000D6F0000B7E3F10C0C542F0004792801856539090088044E0844C202BE53
0000232000C188D8
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000B7E3F1
▒00242320000D6F0000B7E3F10C0C542F0004792801856539090088044E0844C2026310
2012/12/16 00:14:02 [Plugwise] GetDeviceInfo Result: 231D000D6F0000B7E3F10C0C542F0004792801856539090088044E0844C2
2012/12/16 00:14:02 [Plugwise] MAC Address: 000D6F0000B7E3F1
2012/12/16 00:14:02 [Plugwise] Sequence Number: 231D
2012/12/16 00:14:02 [Plugwise] Log Address: 457 (00047928)
2012/12/16 00:14:02 [Plugwise] Time in Circle: 3084 12 21551
2012/12/16 00:14:02 [Plugwise] Frequency: 50Hz
2012/12/16 00:14:02 [Plugwise] Hardware version: 6539-0900-8804
2012/12/16 00:14:02 [Plugwise] Firmware: 2011/06/27 08:52:18
2012/12/16 00:14:02 [Plugwise] RelayState: 01 On
2012/12/16 00:14:02 [Plugwise] Checking power usage of device 'Accessoires Cuisine' with address 000D6F00004BA11D
PuTT2012/12/16 00:14:02 [Plugwise] Calibration Request
Y2012/12/16 00:14:02 [Plugwise] MAC: 000D6F00004BA11D
2012/12/16 00:14:02 [Plugwise] String: 0026000D6F00004BA11D CRC: E143
2012/12/16 00:14:02 [Plugwise] Write: 0026000D6F00004BA11DE143
2012/12/16 00:14:02 [Plugwise] Write: 0026000D6F00004BA11DE143
2012/12/16 00:14:02 [Plugwise] Write: 0026000D6F00004BA11DE143
2012/12/16 00:14:03 [Plugwise] Write: 0026000D6F00004BA11DE143
2012/12/16 00:14:03 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:14:03 [Plugwise] Data wrong: 0000232100C12289
▒00272321000D6F00004BA11D3F7C3270338A5AEA3D4FA458000000000C3A
0000232200C1CC5B
▒00272322000D6F00004BA11D3F7C3270338A5AEA3D4FA45800000000DBB7
0000232300C1660A
▒00272323000D6F00004BA11D3F7C3270338A5AEA3D4FA4580000000066D3
2012/12/16 00:14:03 [Plugwise] Data correct: 0000232100C12289
▒00272321000D6F00004BA11D3F7C3270338A5AEA3D4FA458000000000C3A
0000232200C1CC5B
▒00272322000D6F00004BA11D3F7C3270338A5AEA3D4FA45800000000DBB7
0000232300C1660A
▒00272323000D6F00004BA11D3F7C3270338A5AEA3D4FA4580000000066D3
0000232400C101DE
▒00272324000D6F00004BA11D3F7C3270338A5AEA3D4FA45800000000648C
2012/12/16 00:14:03 [Plugwise] GetCalibration Result: 00272321000D6F00004BA11D3F7C3270338A5AEA3D4FA458000000000C3A
0000232200C1CC5B
▒00272322000D6F00004BA11D3F7C3270338A5AEA3D4FA45800000000DB
2012/12/16 00:14:03 [Plugwise] Sequence Number: 2321
2012/12/16 00:14:03 [Plugwise] GainA: 0.985144615173
2012/12/16 00:14:03 [Plugwise] GainB: 6.442662936479E-8
2012/12/16 00:14:03 [Plugwise] OffTot: 0.050693839788
2012/12/16 00:14:03 [Plugwise] OffNoise: 5.877471754111E-39
2012/12/16 00:14:03 [Plugwise] Write: 0012000D6F00004BA11DA2B9
2012/12/16 00:14:03 [Plugwise] Write: 0012000D6F00004BA11DA2B9
2012/12/16 00:14:04 [Plugwise] Write: 0012000D6F00004BA11DA2B9
2012/12/16 00:14:04 [Plugwise] Write: 0012000D6F00004BA11DA2B9
2012/12/16 00:14:04 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:14:04 [Plugwise] Data wrong: 0000232500C1AB8F
▒00132325000D6F00004BA11D00000002000000B900000000000DF981
0000232600C1455D
▒00132326000D6F00004BA11D00000002000000B900000000000D95C5
0000232700C1EF0C
▒00132327000D6F00004BA11D00000002000000B900000000000D41E6
2012/12/16 00:14:04 [Plugwise] Data correct: 0000232500C1AB8F
▒00132325000D6F00004BA11D00000002000000B900000000000DF981
0000232600C1455D
▒00132326000D6F00004BA11D00000002000000B900000000000D95C5
0000232700C1EF0C
▒00132327000D6F00004BA11D00000002000000B900000000000D41E6
0000232800C18AF5
▒00132328000D6F00004BA11D00010002000000BA000000000007ED85
2012/12/16 00:14:04 [Plugwise] GetPowerInfo Result: 00132325000D6F00004BA11D00000002000000B900000000000DF981
2012/12/16 00:14:04 [Plugwise] Sequence Number: 2325
2012/12/16 00:14:04 [Plugwise] Pulses: 0000 (hex) 0
2012/12/16 00:14:04 [Plugwise] Corrected Pulses: 0
2012/12/16 00:14:04 [Plugwise] kWh: 0
2012/12/16 00:14:04 [Plugwise] Watt: 0
2012/12/16 00:14:04 [Plugwise] Checking relay state of device 'Accessoires Cuisine' with address 000D6F00004BA11D
2012/12/16 00:14:04 [Plugwise] MAC: 000D6F00004BA11D
2012/12/16 00:14:04 [Plugwise] String: 0023000D6F00004BA11D CRC: B229
2012/12/16 00:14:04 [Plugwise] Write: 0023000D6F00004BA11DB229
2012/12/16 00:14:05 [Plugwise] Write: 0023000D6F00004BA11DB229
2012/12/16 00:14:05 [Plugwise] Write: 0023000D6F00004BA11DB229
2012/12/16 00:14:05 [Plugwise] Write: 0023000D6F00004BA11DB229
2012/12/16 00:14:06 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:14:06 [Plugwise] Data wrong: 0000232900C120A4
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BA11D
▒00242329000D6F00004BA11D0C0C542F0004793001856539090088044E0844C202C886
0000232A00C13F0F
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BA11D
▒0024232A000D6F00004BA11D0C0C542F0004793001856539090088044E0844C2025DC7
0000232B00C1D1DD
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BA11D
▒0024232B000D6F00004BA11D0C0C542F0004793001856539090088044E0844C202A204
2012/12/16 00:14:06 [Plugwise] Data correct: 0000232900C120A4
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BA11D
▒00242329000D6F00004BA11D0C0C542F0004793001856539090088044E0844C202C886
0000232A00C13F0F
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BA11D
▒0024232A000D6F00004BA11D0C0C542F0004793001856539090088044E0844C2025DC7
0000232B00C1D1DD
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BA11D
▒0024232B000D6F00004BA11D0C0C542F0004793001856539090088044E0844C202A204
0000232C00C17B8C
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BA11D
▒0024232C000D6F00004BA11D0C0C542F0004793001856539090088044E0844C202075A
2012/12/16 00:14:06 [Plugwise] GetDeviceInfo Result: 2329000D6F00004BA11D0C0C542F0004793001856539090088044E0844C2
2012/12/16 00:14:06 [Plugwise] MAC Address: 000D6F00004BA11D
2012/12/16 00:14:06 [Plugwise] Sequence Number: 2329
2012/12/16 00:14:06 [Plugwise] Log Address: 457 (00047930)
2012/12/16 00:14:06 [Plugwise] Time in Circle: 3084 12 21551
2012/12/16 00:14:06 [Plugwise] Frequency: 50Hz
2012/12/16 00:14:06 [Plugwise] Hardware version: 6539-0900-8804
2012/12/16 00:14:06 [Plugwise] Firmware: 2011/06/27 08:52:18
2012/12/16 00:14:06 [Plugwise] RelayState: 01 On
2012/12/16 00:14:06 [Plugwise] Checking power usage of device 'Lampe Salon 2' with address 000D6F0000D31ABC
2012/12/16 00:14:06 [Plugwise] Calibration Request
2012/12/16 00:14:06 [Plugwise] MAC: 000D6F0000D31ABC
2012/12/16 00:14:06 [Plugwise] String: 0026000D6F0000D31ABC CRC: A498
2012/12/16 00:14:06 [Plugwise] Write: 0026000D6F0000D31ABCA498
2012/12/16 00:14:06 [Plugwise] Write: 0026000D6F0000D31ABCA498
2012/12/16 00:14:06 [Plugwise] Write: 0026000D6F0000D31ABCA498
2012/12/16 00:14:07 [Plugwise] Write: 0026000D6F0000D31ABCA498
2012/12/16 00:14:07 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:14:07 [Plugwise] Data wrong: 0000232D00C11C58
▒0027232D000D6F0000D31ABC3F7EB857B6229CCF3D5F88A500000000FDD0
0000232E00C1B609
▒0027232E000D6F0000D31ABC3F7EB857B6229CCF3D5F88A50000000040B4
0000232F00C158DB
▒0027232F000D6F0000D31ABC3F7EB857B6229CCF3D5F88A5000000009739
2012/12/16 00:14:07 [Plugwise] Data correct: 0000232D00C11C58
▒0027232D000D6F0000D31ABC3F7EB857B6229CCF3D5F88A500000000FDD0
0000232E00C1B609
▒0027232E000D6F0000D31ABC3F7EB857B6229CCF3D5F88A50000000040B4
0000232F00C158DB
▒0027232F000D6F0000D31ABC3F7EB857B6229CCF3D5F88A5000000009739
0000233000C1CD78
▒00272330000D6F0000D31ABC3F7EB857B6229CCF3D5F88A5000000001F84
2012/12/16 00:14:07 [Plugwise] GetCalibration Result: 0027232D000D6F0000D31ABC3F7EB857B6229CCF3D5F88A500000000FDD0
0000232E00C1B609
▒0027232E000D6F0000D31ABC3F7EB857B6229CCF3D5F88A50000000040
2012/12/16 00:14:07 [Plugwise] Sequence Number: 232D
2012/12/16 00:14:07 [Plugwise] GainA: 0.995000302792
2012/12/16 00:14:07 [Plugwise] GainB: -2.423115574857E-6
2012/12/16 00:14:07 [Plugwise] OffTot: 0.054573673755
2012/12/16 00:14:07 [Plugwise] OffNoise: 5.877471754111E-39
2012/12/16 00:14:07 [Plugwise] Write: 0012000D6F0000D31ABCE762
2012/12/16 00:14:07 [Plugwise] Write: 0012000D6F0000D31ABCE762
2012/12/16 00:14:08 [Plugwise] Write: 0012000D6F0000D31ABCE762
2012/12/16 00:14:08 [Plugwise] Write: 0012000D6F0000D31ABCE762
2012/12/16 00:14:08 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:14:08 [Plugwise] Data wrong: 0000233100C16729
▒00132331000D6F0000D31ABC0000000000000000FFFFFF06000DC9FC
0000233200C189FB
▒00132332000D6F0000D31ABC0000000000000000FFFFFF060006FB6D
0000233300C123AA
▒00132333000D6F0000D31ABC0000000000000000FFFFFF0600062F4E
2012/12/16 00:14:08 [Plugwise] Data correct: 0000233100C16729
▒00132331000D6F0000D31ABC0000000000000000FFFFFF06000DC9FC
0000233200C189FB
▒00132332000D6F0000D31ABC0000000000000000FFFFFF060006FB6D
0000233300C123AA
▒00132333000D6F0000D31ABC0000000000000000FFFFFF0600062F4E
0000233400C1447E
▒00132334000D6F0000D31ABC0000000000000000FFFFFF06000623E5
2012/12/16 00:14:08 [Plugwise] GetPowerInfo Result: 00132331000D6F0000D31ABC0000000000000000FFFFFF06000DC9FC
2012/12/16 00:14:08 [Plugwise] Sequence Number: 2331
2012/12/16 00:14:08 [Plugwise] Pulses: 0000 (hex) 0
2012/12/16 00:14:08 [Plugwise] Corrected Pulses: 0
2012/12/16 00:14:08 [Plugwise] kWh: 0
2012/12/16 00:14:08 [Plugwise] Watt: 0
2012/12/16 00:14:08 [Plugwise] Checking relay state of device 'Lampe Salon 2' with address 000D6F0000D31ABC
2012/12/16 00:14:08 [Plugwise] MAC: 000D6F0000D31ABC
2012/12/16 00:14:08 [Plugwise] String: 0023000D6F0000D31ABC CRC: F7F2
2012/12/16 00:14:08 [Plugwise] Write: 0023000D6F0000D31ABCF7F2
2012/12/16 00:14:09 [Plugwise] Write: 0023000D6F0000D31ABCF7F2
2012/12/16 00:14:09 [Plugwise] Write: 0023000D6F0000D31ABCF7F2
2012/12/16 00:14:09 [Plugwise] Write: 0023000D6F0000D31ABCF7F2
2012/12/16 00:14:10 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:14:10 [Plugwise] Data wrong: 0000233500C1EE2F
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000D31ABC
▒00242335000D6F0000D31ABC0C0C542F0004725800856539090088044E0844C20267D2
0000233600C100FD
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000D31ABC
▒00242336000D6F0000D31ABC0C0C542F0004725800856539090088044E0844C2029811
0000233700C1AAAC
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000D31ABC
▒00242337000D6F0000D31ABC0C0C542F0004725800856539090088044E0844C2023D4F
2012/12/16 00:14:10 [Plugwise] Data correct: 0000233500C1EE2F
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000D31ABC
▒00242335000D6F0000D31ABC0C0C542F0004725800856539090088044E0844C20267D2
0000233600C100FD
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000D31ABC
▒00242336000D6F0000D31ABC0C0C542F0004725800856539090088044E0844C2029811
0000233700C1AAAC
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000D31ABC
▒00242337000D6F0000D31ABC0C0C542F0004725800856539090088044E0844C2023D4F
0000233800C1CF55
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F0000D31ABC
▒00242338000D6F0000D31ABC0C0C542F0004725800856539090088044E0844C2020DE3
2012/12/16 00:14:10 [Plugwise] GetDeviceInfo Result: 2335000D6F0000D31ABC0C0C542F0004725800856539090088044E0844C2
2012/12/16 00:14:10 [Plugwise] MAC Address: 000D6F0000D31ABC
2012/12/16 00:14:10 [Plugwise] Sequence Number: 2335
2012/12/16 00:14:10 [Plugwise] Log Address: 402 (00047258)
2012/12/16 00:14:10 [Plugwise] Time in Circle: 3084 12 21551
2012/12/16 00:14:10 [Plugwise] Frequency: 50Hz
2012/12/16 00:14:10 [Plugwise] Hardware version: 6539-0900-8804
2012/12/16 00:14:10 [Plugwise] Firmware: 2011/06/27 08:52:18
2012/12/16 00:14:10 [Plugwise] RelayState: 00 Off
2012/12/16 00:14:10 [Plugwise] Checking power usage of device 'Congélateur' with address 000D6F00004BA090
2012/12/16 00:14:10 [Plugwise] Calibration Request
2012/12/16 00:14:10 [Plugwise] MAC: 000D6F00004BA090
2012/12/16 00:14:10 [Plugwise] String: 0026000D6F00004BA090 CRC: 61C9
2012/12/16 00:14:10 [Plugwise] Write: 0026000D6F00004BA09061C9
2012/12/16 00:14:10 [Plugwise] Write: 0026000D6F00004BA09061C9
2012/12/16 00:14:10 [Plugwise] Write: 0026000D6F00004BA09061C9
2012/12/16 00:14:11 [Plugwise] Write: 0026000D6F00004BA09061C9
2012/12/16 00:14:11 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:14:11 [Plugwise] Data wrong: 0000233900C16504
▒00272339000D6F00004BA0903F7D49F8B62E100B3C072CE0000000001BC0
0000233A00C17AAF
▒0027233A000D6F00004BA0903F7D49F8B62E100B3C072CE00000000085B5
0000233B00C1947D
▒0027233B000D6F00004BA0903F7D49F8B62E100B3C072CE0000000005238
2012/12/16 00:14:11 [Plugwise] Data correct: 0000233900C16504
▒00272339000D6F00004BA0903F7D49F8B62E100B3C072CE0000000001BC0
0000233A00C17AAF
▒0027233A000D6F00004BA0903F7D49F8B62E100B3C072CE00000000085B5
0000233B00C1947D
▒0027233B000D6F00004BA0903F7D49F8B62E100B3C072CE0000000005238
0000233C00C13E2C
▒0027233C000D6F00004BA0903F7D49F8B62E100B3C072CE000000000EF5C
2012/12/16 00:14:11 [Plugwise] GetCalibration Result: 00272339000D6F00004BA0903F7D49F8B62E100B3C072CE0000000001BC0
0000233A00C17AAF
▒0027233A000D6F00004BA0903F7D49F8B62E100B3C072CE00000000085
2012/12/16 00:14:11 [Plugwise] Sequence Number: 2339
2012/12/16 00:14:11 [Plugwise] GainA: 0.989409923553
2012/12/16 00:14:11 [Plugwise] GainB: -2.593735871415E-6
2012/12/16 00:14:11 [Plugwise] OffTot: 0.008250445127
2012/12/16 00:14:11 [Plugwise] OffNoise: 5.877471754111E-39
2012/12/16 00:14:11 [Plugwise] Write: 0012000D6F00004BA0902233
2012/12/16 00:14:11 [Plugwise] Write: 0012000D6F00004BA0902233
2012/12/16 00:14:11 [Plugwise] Write: 0012000D6F00004BA0902233
2012/12/16 00:14:12 [Plugwise] Write: 0012000D6F00004BA0902233
2012/12/16 00:14:12 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:14:12 [Plugwise] Data wrong: 0000233D00C159F8
▒0013233D000D6F00004BA09000200106000025AD00000000000C4C86
0000233E00C1F3A9
▒0013233E000D6F00004BA09000200106000025AD00000000000C98A5
0000233F00C11D7B
▒0013233F000D6F00004BA09000200106000025AD00000000000CF4E1
2012/12/16 00:14:12 [Plugwise] Data correct: 0000233D00C159F8
▒0013233D000D6F00004BA09000200106000025AD00000000000C4C86
0000233E00C1F3A9
▒0013233E000D6F00004BA09000200106000025AD00000000000C98A5
0000233F00C11D7B
▒0013233F000D6F00004BA09000200106000025AD00000000000CF4E1
0000234000C10539
▒00132340000D6F00004BA09000210106000025CE0000000000047430
2012/12/16 00:14:12 [Plugwise] GetPowerInfo Result: 0013233D000D6F00004BA09000200106000025AD00000000000C4C86
2012/12/16 00:14:12 [Plugwise] Sequence Number: 233D
2012/12/16 00:14:12 [Plugwise] Pulses: 0020 (hex) 32
2012/12/16 00:14:12 [Plugwise] Corrected Pulses: 31.666712013306
2012/12/16 00:14:12 [Plugwise] kWh: 0.067528494056
2012/12/16 00:14:12 [Plugwise] Watt: 67.52849405627
2012/12/16 00:14:12 [Plugwise] Checking relay state of device 'Congélateur' with address 000D6F00004BA090
2012/12/16 00:14:12 [Plugwise] MAC: 000D6F00004BA090
2012/12/16 00:14:12 [Plugwise] String: 0023000D6F00004BA090 CRC: 32A3
2012/12/16 00:14:12 [Plugwise] Write: 0023000D6F00004BA09032A3
2012/12/16 00:14:12 [Plugwise] Write: 0023000D6F00004BA09032A3
2012/12/16 00:14:13 [Plugwise] Write: 0023000D6F00004BA09032A3
2012/12/16 00:14:13 [Plugwise] Write: 0023000D6F00004BA09032A3
2012/12/16 00:14:13 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:14:13 [Plugwise] Data wrong: 0000234100C1AF68
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BA090
▒00242341000D6F00004BA0900C0C542F00046FA001856539090088044E0844C202A5BA
0000234200C141BA
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BA090
▒00242342000D6F00004BA0900C0C542F00046FA001856539090088044E0844C2025A79
0000234300C1EBEB
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BA090
▒00242343000D6F00004BA0900C0C542F00046FA001856539090088044E0844C202FF27
2012/12/16 00:14:13 [Plugwise] Data correct: 0000234100C1AF68
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BA090
▒00242341000D6F00004BA0900C0C542F00046FA001856539090088044E0844C202A5BA
0000234200C141BA
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BA090
▒00242342000D6F00004BA0900C0C542F00046FA001856539090088044E0844C2025A79
0000234300C1EBEB
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BA090
▒00242343000D6F00004BA0900C0C542F00046FA001856539090088044E0844C202FF27
0000234400C18C3F
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004BA090
▒00242344000D6F00004BA0900C0C542F00046FA001856539090088044E0844C202B5DE
2012/12/16 00:14:13 [Plugwise] GetDeviceInfo Result: 2341000D6F00004BA0900C0C542F00046FA001856539090088044E0844C2
2012/12/16 00:14:13 [Plugwise] MAC Address: 000D6F00004BA090
2012/12/16 00:14:13 [Plugwise] Sequence Number: 2341
2012/12/16 00:14:13 [Plugwise] Log Address: 381 (00046FA0)
2012/12/16 00:14:13 [Plugwise] Time in Circle: 3084 12 21551
2012/12/16 00:14:13 [Plugwise] Frequency: 50Hz
2012/12/16 00:14:13 [Plugwise] Hardware version: 6539-0900-8804
2012/12/16 00:14:13 [Plugwise] Firmware: 2011/06/27 08:52:18
2012/12/16 00:14:13 [Plugwise] RelayState: 01 On
2012/12/16 00:14:13 [Plugwise] Checking power usage of device 'Four' with address 000D6F00004B9B70
2012/12/16 00:14:13 [Plugwise] Calibration Request
2012/12/16 00:14:13 [Plugwise] MAC: 000D6F00004B9B70
2012/12/16 00:14:13 [Plugwise] String: 0026000D6F00004B9B70 CRC: 3318
2012/12/16 00:14:13 [Plugwise] Write: 0026000D6F00004B9B703318
2012/12/16 00:14:14 [Plugwise] Write: 0026000D6F00004B9B703318
2012/12/16 00:14:14 [Plugwise] Write: 0026000D6F00004B9B703318
2012/12/16 00:14:14 [Plugwise] Write: 0026000D6F00004B9B703318
2012/12/16 00:14:15 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:14:15 [Plugwise] Data wrong: 0000234500C1266E
▒00272345000D6F00004B9B703F81200FB6338CA03D503A9B0000000006C0
0000234600C1C8BC
▒00272346000D6F00004B9B703F81200FB6338CA03D503A9B00000000D14D
0000234700C162ED
▒00272347000D6F00004B9B703F81200FB6338CA03D503A9B000000006C29
2012/12/16 00:14:15 [Plugwise] Data correct: 0000234500C1266E
▒00272345000D6F00004B9B703F81200FB6338CA03D503A9B0000000006C0
0000234600C1C8BC
▒00272346000D6F00004B9B703F81200FB6338CA03D503A9B00000000D14D
0000234700C162ED
▒00272347000D6F00004B9B703F81200FB6338CA03D503A9B000000006C29
0000234800C10714
▒00272348000D6F00004B9B703F81200FB6338CA03D503A9B00000000D5F3
2012/12/16 00:14:15 [Plugwise] GetCalibration Result: 00272345000D6F00004B9B703F81200FB6338CA03D503A9B0000000006C0
0000234600C1C8BC
▒00272346000D6F00004B9B703F81200FB6338CA03D503A9B00000000D1
2012/12/16 00:14:15 [Plugwise] Sequence Number: 2345
2012/12/16 00:14:15 [Plugwise] GainA: 1.008790850639
2012/12/16 00:14:15 [Plugwise] GainB: -2.675493306015E-6
2012/12/16 00:14:15 [Plugwise] OffTot: 0.05083714053
2012/12/16 00:14:15 [Plugwise] OffNoise: 5.877471754111E-39
2012/12/16 00:14:15 [Plugwise] Write: 0012000D6F00004B9B7070E2
2012/12/16 00:14:15 [Plugwise] Write: 0012000D6F00004B9B7070E2
2012/12/16 00:14:15 [Plugwise] Write: 0012000D6F00004B9B7070E2
2012/12/16 00:14:16 [Plugwise] Write: 0012000D6F00004B9B7070E2
2012/12/16 00:14:16 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:14:16 [Plugwise] Data wrong: 0000234900C1AD45
▒00132349000D6F00004B9B700001000400000139000000000006CF46
0000234A00C1B2EE
▒0013234A000D6F00004B9B70000000030000013900000000000A866C
0000234B00C15C3C
▒0013234B000D6F00004B9B70000000030000013900000000000AEA28
2012/12/16 00:14:16 [Plugwise] Data correct: 0000234900C1AD45
▒00132349000D6F00004B9B700001000400000139000000000006CF46
0000234A00C1B2EE
▒0013234A000D6F00004B9B70000000030000013900000000000A866C
0000234B00C15C3C
▒0013234B000D6F00004B9B70000000030000013900000000000AEA28
0000234C00C1F66D
▒0013234C000D6F00004B9B70000000030000013900000000000A3E0B
2012/12/16 00:14:16 [Plugwise] GetPowerInfo Result: 00132349000D6F00004B9B700001000400000139000000000006CF46
2012/12/16 00:14:16 [Plugwise] Sequence Number: 2349
2012/12/16 00:14:16 [Plugwise] Pulses: 0001 (hex) 1
2012/12/16 00:14:16 [Plugwise] Corrected Pulses: 1.059625315676
2012/12/16 00:14:16 [Plugwise] kWh: 0.002259625243
2012/12/16 00:14:16 [Plugwise] Watt: 2.259625243109
2012/12/16 00:14:16 [Plugwise] Checking relay state of device 'Four' with address 000D6F00004B9B70
2012/12/16 00:14:16 [Plugwise] MAC: 000D6F00004B9B70
2012/12/16 00:14:16 [Plugwise] String: 0023000D6F00004B9B70 CRC: 6072
2012/12/16 00:14:16 [Plugwise] Write: 0023000D6F00004B9B706072
2012/12/16 00:14:16 [Plugwise] Write: 0023000D6F00004B9B706072
2012/12/16 00:14:17 [Plugwise] Write: 0023000D6F00004B9B706072
2012/12/16 00:14:17 [Plugwise] Write: 0023000D6F00004B9B706072
2012/12/16 00:14:17 [Plugwise] Needed to interrogate the stick more then once!
2012/12/16 00:14:17 [Plugwise] Data wrong: 0000234D00C191B9
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004B9B70
▒0024234D000D6F00004B9B700C0C542F000478A001856539090088044E0844C2024A2C
0000234E00C13BE8
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004B9B70
▒0024234E000D6F00004B9B700C0C542F000478A001856539090088044E0844C202EF72
0000234F00C1D53A
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004B9B70
▒0024234F000D6F00004B9B700C0C542F000478A001856539090088044E0844C20210B1
2012/12/16 00:14:17 [Plugwise] Data correct: 0000234D00C191B9
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004B9B70
▒0024234D000D6F00004B9B700C0C542F000478A001856539090088044E0844C2024A2C
0000234E00C13BE8
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004B9B70
▒0024234E000D6F00004B9B700C0C542F000478A001856539090088044E0844C202EF72
0000234F00C1D53A
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004B9B70
▒0024234F000D6F00004B9B700C0C542F000478A001856539090088044E0844C20210B1
0000235000C14099
# APSRequestNodeInfo: Source MAC: 000D6F0001A5A045# APSRequestNodeInfo: Destination MAC:
000D6F00004B9B70
▒00242350000D6F00004B9B700C0C542F000478A001856539090088044E0844C202AB4D
2012/12/16 00:14:17 [Plugwise] GetDeviceInfo Result: 234D000D6F00004B9B700C0C542F000478A001856539090088044E0844C2
2012/12/16 00:14:17 [Plugwise] MAC Address: 000D6F00004B9B70
2012/12/16 00:14:17 [Plugwise] Sequence Number: 234D
2012/12/16 00:14:17 [Plugwise] Log Address: 453 (000478A0)
2012/12/16 00:14:17 [Plugwise] Time in Circle: 3084 12 21551
2012/12/16 00:14:17 [Plugwise] Frequency: 50Hz
2012/12/16 00:14:17 [Plugwise] Hardware version: 6539-0900-8804
2012/12/16 00:14:17 [Plugwise] Firmware: 2011/06/27 08:52:18
2012/12/16 00:14:17 [Plugwise] RelayState: 01 On