Posted: Sun Oct 20, 2013 10:17 am
by Edwin
I want to use the opentherm monitor for the first time
I use usb for testing it and have a celcia 20 connect to it for test,
no boiler yet.
i go to settings and select the celcia 20 and overide the temp. On the thermostat there is a error (fout 203)
I also see nothing happening in the statistics
What is wrong or what do i wrong?
How can i check in this setup that the openthermgateway is working?
when i start opentherm gateway diagnostics i get:error 01 a lot of numbers with the numbers at the end in red 349,652
I bought it already asembled on openthermgateway.com
Thanks
Edwin
Re: Help using openthermonitor
Posted: Sun Oct 20, 2013 1:50 pm
by Digit
How can i check in this setup that the openthermgateway is working?
Adding a boiler to the mix will help I guess, Opentherm is 2-way communication but you left out one side of it.
Re: Help using openthermonitor
Posted: Sun Oct 20, 2013 2:33 pm
by Bwired
Yes, you need both to make it work....
Re: Help using openthermonitor
Posted: Sun Oct 20, 2013 3:05 pm
by Edwin
Bwired wrote:Yes, you need both to make it work....
So... I cant test the gateway without a boiler just to see if the gateway is comunicating?
Re: Help using openthermonitor
Posted: Sun Oct 20, 2013 4:34 pm
by Digit
Well, not the things you are trying to test.
The thermostat is in error mode, it doesn't "see" a boiler - it's missing its counterpart to be able to do it's job.
So testing override is a bit premature.
What did you expect to see in the statistics?
And then ask yourself: what device provides this information?
Just connect the boiler... just do it.

Re: Help using openthermonitor
Posted: Sun Oct 20, 2013 4:59 pm
by hvxl
Believe it or not, that sounds good. The thermostat is sending an opentherm message every second. The diagnostic firmware measures the times and reports them. Only the last two times fall outside the opentherm specifications. That is a known issue with a Celcia. So now you can flash the actual gateway firmware. If you use firmware version 3.4, you will have to issue the command IT=1. After that you should see opentherm messages from the thermostat on the log tab. It's probably going to be the same message over and over because the thermostat never gets a response from the boiler. Then connect the boiler and see everything come to life.
Re: Help using openthermonitor
Posted: Sun Oct 20, 2013 5:10 pm
by Edwin
thank you, thats what i ment
i dont have the opentherm boiler yet ,thats why i wanted to test it so much as possible.
greetings
edwin
Re: Help using openthermonitor
Posted: Sun Oct 20, 2013 5:38 pm
by Edwin
ok the firmware is flashed,and its working
Thanks to you all.
Re: Help using openthermonitor
Posted: Sun Oct 20, 2013 11:49 pm
by Bwired
great