Page 1 of 2
Problem starting after power outage
Posted: Mon Dec 30, 2013 3:46 pm
by nlrb
I'm running the OTG with firmware 4.0b1. It is a version without a MAX232 and with a USR-TCP232-T to convert the TTL signals to Ethernet. The USR-TCP232-T is powered by a separate 5V power supply.
Problem I have is the following. When restoring power after a complete power out (i.e. both OTG and USR-TCP232-T are without power) the OTG won't start up. It will blink LEDs A-C once every second. To start up the OTG I have to take the power off (and keep it on the USR-TCP232-T) and put the power back on. Then the LEDs will flash once before the OTG starts.
Don't recall this happing with FW3.4, but this was a long time back so I don't know if it is related.
Any suggestion how to cure this?
Re: Problem starting after power outage
Posted: Mon Dec 30, 2013 6:59 pm
by hvxl
nlrb wrote:Problem I have is the following. When restoring power after a complete power out (i.e. both OTG and USR-TCP232-T are without power) the OTG won't start up. It will blink LEDs A-C once every second.
LEDs A-C? On a reset all 4 LEDs (A-D) blink very briefly. During normal operation LED B should flash twice per second. You are saying that you see the brief reset blink once every second? The only reason I can imagine for that is that the TTL to ethernet device is sending break conditions on the serial line (pulling it low). I have no idea why it would do that. I don't have such a device myself, so I can't verify or debug the behavior you report.
Re: Problem starting after power outage
Posted: Tue Dec 31, 2013 3:22 pm
by nlrb
hvxl wrote:LEDs A-C? On a reset all 4 LEDs (A-D) blink very briefly.
It seems that one LED doesn't work at all anymore. I'll need to look into that.
hvxl wrote:The only reason I can imagine for that is that the TTL to ethernet device is sending break conditions on the serial line (pulling it low). I have no idea why it would do that.
I can connect to the USR-TCP232-T at that point, but nothing is visible in otmonitor. When I only pull the power on the USR-TCP232-T, the LEDs on the OTG will flash very quickly.
Re: Problem starting after power outage
Posted: Thu Jan 02, 2014 6:56 pm
by hvxl
nlrb wrote:When I only pull the power on the USR-TCP232-T, the LEDs on the OTG will flash very quickly.
I can imagine that the USR-TCP232-T device will pull the serial line low when it is powered down. However, in theory, that should not cause the LEDs to flash. The gateway is supposed to wait for the line to go high before resetting. I may have to do some experiments to determine if that works as intended.
I didn't consider this scenario when I wrote the firmware. I now realize it would be better to not let such a situation prevent all opentherm communications.
Re: Problem starting after power outage
Posted: Sun Feb 02, 2014 2:14 pm
by nlrb
I've installed the latest FW (4.0b2), which I believe should fix this ('A continuous BREAK condition on the serial interface should not stop the gateway from handling opentherm messages.'). However, after a complete power failure the LEDs still keep flashing once a second. How long should they do this max.?
Re: Problem starting after power outage
Posted: Sun Feb 02, 2014 3:10 pm
by hvxl
It should not be doing that at all. The LEDs are supposed to flash only once. Unfortunately I don't have a USR-TCP232-T to test with, so my attempt at a fix was purely theoretical. But apparently the device is doing something other than simply pulling the line low.
Re: Problem starting after power outage
Posted: Tue Feb 04, 2014 6:16 pm
by trie
nlrb wrote:I've installed the latest FW (4.0b2), which I believe should fix this ('A continuous BREAK condition on the serial interface should not stop the gateway from handling opentherm messages.'). However, after a complete power failure the LEDs still keep flashing once a second. How long should they do this max.?
I have exact the same problem. The gateway has to be powered off and on again before stuff works again. Leds keep flashing indeed, as if it's constantly rebooting. When disconnecting the USB even more christmassy-light-spectacles appear
I'm using a PL2303 TTL to USB converter to connect to a RPi.
Re: Problem starting after power outage
Posted: Mon Feb 17, 2014 8:34 pm
by nlrb
The situation can be reproduced by an OTG setup without MAX232. If you leave the TTL signals unconnected, then you get this behavior. I can reproduce it without the USR-TCP232-T.
Re: Problem starting after power outage
Posted: Mon Feb 17, 2014 9:23 pm
by hvxl
That's how I tested the firmware. Works for me.
Re: Problem starting after power outage
Posted: Mon Feb 17, 2014 9:56 pm
by nlrb
Really strange. Any idea what can cause the difference in behavior?
Re: Problem starting after power outage
Posted: Mon Feb 17, 2014 11:21 pm
by hvxl
After studying the PIC16F88 data sheet again, I actually do have an idea.
Background: The gateway interprets a BREAK condition on the serial line ("space" (i.e. low) level for more than a full character) as a request to go to self-programming mode. This condition is detected via a framing error on the serial interface. The code then waits for the RB2 input port (which is the same pin as the serial RX port) to go high before jumping to the self-programming code. To really enter self-programming mode, a special character must be received within 1 second. If that doesn't happen, the gateway resets, flashes the LEDs and (re)starts normal operation.
Unfortunately the RB2 input port and the serial RX port have different ideas about what's low and high. The RB2 port uses a TTL input buffer, where anything below 0.8V is low and anything above 2V is high. The area between 0.8V and 2V is undefined and can turn out as either level. The serial RX port however uses a Schmitt trigger buffer. Once the input has been below 1V, the level remains low until the voltage goes above 4V. It then remains high until the voltage drops below 1V again.
The effect you see where the LEDs are flashing once per second means that the serial interface detects a framing error, then RB2 is found to be high, the self-programming code waits 1 second, the gateway resets and the whole thing starts over again.
This is possible due to the different interpretations of the logical levels: When the gateway is powered up, the port starts out at 0V and both RX and RB2 consider the logical level low. However, if the port is floating (or apparently when it is connected to an unpowered USB interface) the voltage may rise high enough for RB2 to consider it high, but not high enough to cross the upper threshold of the RX Schmitt trigger. In other words, probably somewhere between 2 and 4 Volts.
I could modify the firmware to briefly make RB2 an output and pull it high. That should flip the RX pin to high, and as long as it doesn't go below 1V again it will not cause a framing error and the gateway would possibly continue to run. I don't really like doing that though, because RB2 is normally connected to the output of another device. Connecting two outputs together may damage either of the two, although the risk of that is probably quite low if RB2 is only configured as an output for a few microseconds.
A better solution in my opinion is to do it in hardware. If you add a resistor between the RX pin and Vcc (or GND, but Vcc is preferred if that works), that should hopefully give a consistent idea of the logical level to both RX and RB2. Experiment with the value you need. I would start at around 10K. I could also try doing this in firmware using the internal pull-up resistors, but those are called "weak pull-ups" for a reason. They will probably not be strong enough to pull a powered down USB device output above 4V. But if you find that you only need a 33K resistor to Vcc to make the problem go away, that is something we could try.
Re: Problem starting after power outage
Posted: Tue Feb 18, 2014 10:51 pm
by hvxl
nlrb wrote:Hi Schelte,
Thanks very much for looking into this. I've been experimenting with 10k & 33k resistors connected to Vcc or GND. Can't say that I notice any difference.
- No external power supply connected: LEDs flashing frantically (almost continuous).
- Connected to external power supply (but powered off): LEDs flashing once a second. This can start off with 1 flash, then 3 seconds nothing and then all LEDs flashing once a second.
However, I then found that the gateway is acting strange even if it starts up correctly. With no thermostat or boiler connected is keeps issuing status reads about once every seconds (but it sometimes also stops for some seconds). This occurs even in monitor mode
(Original posting lost due to database crash)
When I suggested to start with 10k, I didn't mean to also stop there again. If 10k doesn't work, try lower values.
What does "flashing frantically" look like? Can you make a short video of that?
The gateway is not "acting strange" when it sends messages in case no thermostat is disconnected. It is supposed to do that. And without the boiler connected it doesn't get a response, so it keeps repeating the same message. When (it thinks) the thermostat is connected again, the gateway stops generating messages. If the detection mechanism sometimes concludes that the thermostat is connected when it's not, your 24V may be a bit low or the value of R5/R6 may be off.
Re: Problem starting after power outage
Posted: Wed Feb 19, 2014 1:07 pm
by nlrb
Post of 18-2-2014; re-posting due to database crash.
Hi Schelte,
Thanks very much for looking into this. I've been experimenting with 10k & 33k resistors connected to Vcc or GND. Can't say that I notice any difference.
- No external power supply connected: LEDs flashing frantically (almost continuous).
- Connected to external power supply (but powered off): LEDs flashing once a second. This can start off with 1 flash, then 3 seconds nothing and then all LEDs flashing once a second.
However, I then found that the gateway is acting strange even if it starts up correctly. With no thermostat or boiler connected is keeps issuing status reads about once every seconds (but it sometimes also stops for some seconds). This occurs even in monitor mode See log below (contains some power cycles).
Code: Select all
11:08:51.993373 R00000000 Read-Data Status: 00000000 00000000
11:08:57.966416 R00000000 Read-Data Status: 00000000 00000000
11:09:02.536269 Thermostat connected
11:09:09.657993 ROpenTherm R00000000
11:09:13.689506 b2
11:09:13.755126 Thermostat disconnected
11:09:13.833932 R00000000 Read-Data Status: 00000000 00000000
11:09:13.861510 R00000000 Read-Data Status: 00000000 00000000
11:09:13.886048 R00000000 Read-Data Status: 00000000 00000000
11:09:13.913252 R00000000 Read-Data Status: 00000000 00000000
11:09:15.638011 R00000000 Read-Data Status: 00000000 00000000
11:09:16.626706 R00000000 Read-Data Status: 00000000 00000000
11:09:17.631729 R00000000 Read-Data Status: 00000000 00000000
11:09:18.617726 R00000000 Read-Data Status: 00000000 00000000
11:09:19.613418 R00000000 Read-Data Status: 00000000 00000000
11:09:20.608740 R00000000 Read-Data Status: 00000000 00000000
11:09:21.604373 R00000000 Read-Data Status: 00000000 00000000
11:09:22.600233 R00000000 Read-Data Status: 00000000 00000000
11:09:23.597775 R00000000 Read-Data Status: 00000000 00000000
11:09:24.591085 R00000000 Read-Data Status: 00000000 00000000
11:09:25.586536 R00000000 Read-Data Status: 00000000 00000000
11:09:26.582106 R00000000 Read-Data Status: 00000000 00000000
11:09:27.576502 R00000000 Read-Data Status: 00000000 00000000
11:09:28.572907 R00000000 Read-Data Status: 00000000 00000000
11:09:29.568438 R00000000 Read-Data Status: 00000000 00000000
11:09:30.563892 R00000000 Read-Data Status: 00000000 00000000
11:09:31.558599 R00000000 Read-Data Status: 00000000 00000000
11:09:32.555275 R00000000 Read-Data Status: 00000000 00000000
11:09:33.550771 R00000000 Read-Data Status: 00000000 00000000
11:09:34.547962 R00000000 Read-Data Status: 00000000 00000000
11:09:35.541583 R00000000 Read-Data Status: 00000000 00000000
11:09:36.536788 R00000000 Read-Data Status: 00000000 00000000
11:09:37.532241 R00000000 Read-Data Status: 00000000 00000000
11:09:38.527717 R00000000 Read-Data Status: 00000000 00000000
11:09:39.524297 R00000000 Read-Data Status: 00000000 00000000
11:09:40.519108 R00000000 Read-Data Status: 00000000 00000000
11:09:41.514008 R00000000 Read-Data Status: 00000000 00000000
11:09:42.509601 R00000000 Read-Data Status: 00000000 00000000
11:09:43.506169 R00000000 Read-Data Status: 00000000 00000000
11:09:44.500586 R00000000 Read-Data Status: 00000000 00000000
11:09:45.496040 R00000000 Read-Data Status: 00000000 00000000
11:09:46.491414 R00000000 Read-Data Status: 00000000 00000000
11:09:47.486898 R00000000 Read-Data Status: 00000000 00000000
11:09:48.482401 R00000000 Read-Data Status: 00000000 00000000
11:09:49.317327 Thermostat connected
11:19:40.633703 R00000000 Read-Data Status: 00000000 00000000
11:19:41.629132 R00000000 Read-Data Status: 00000000 00000000
11:19:42.624549 R00000000 Read-Data Status: 00000000 00000000
11:19:43.620064 R00000000 Read-Data Status: 00000000 00000000
11:19:44.615420 R00000000 Read-Data Status: 00000000 00000000
11:19:45.303864 Command: PR=M
11:19:45.594033 PR: M=G
11:19:45.612672 R00000000 Read-Data Status: 00000000 00000000
11:19:46.606233 R00000000 Read-Data Status: 00000000 00000000
11:19:47.601688 R00000000 Read-Data Status: 00000000 00000000
11:19:48.597075 R00000000 Read-Data Status: 00000000 00000000
11:19:48.865800 Command: GW=0
11:19:48.891346 GW: 0
11:19:49.592464 R00000000 Read-Data Status: 00000000 00000000
11:19:50.587921 R00000000 Read-Data Status: 00000000 00000000
11:19:51.583379 R00000000 Read-Data Status: 00000000 00000000
11:19:52.578802 R00000000 Read-Data Status: 00000000 00000000
11:19:53.574254 R00000000 Read-Data Status: 00000000 00000000
11:19:54.569679 R00000000 Read-Data Status: 00000000 00000000
11:19:55.565107 R00000000 Read-Data Status: 00000000 00000000
11:19:56.560372 R00000000 Read-Data Status: 00000000 00000000
11:19:57.555821 R00000000 Read-Data Status: 00000000 00000000
11:19:58.551261 R00000000 Read-Data Status: 00000000 00000000
11:19:59.546564 R00000000 Read-Data Status: 00000000 00000000
11:20:00.541960 R00000000 Read-Data Status: 00000000 00000000
11:20:01.098281 Command: GW=1
11:20:01.123924 GW: 1
11:20:01.537387 R00000000 Read-Data Status: 00000000 00000000
11:20:02.532812 R00000000 Read-Data Status: 00000000 00000000
11:20:03.528272 R00000000 Read-Data Status: 00000000 00000000
11:20:04.523672 R00000000 Read-Data Status: 00000000 00000000
11:20:05.518915 R00000000 Read-Data Status: 00000000 00000000
11:20:06.514358 R00000000 Read-Data Status: 00000000 00000000
11:20:07.509793 R00000000 Read-Data Status: 00000000 00000000
11:20:08.505264 R00000000 Read-Data Status: 00000000 00000000
11:20:09.500685 R00000000 Read-Data Status: 00000000 00000000
11:20:10.495934 R00000000 Read-Data Status: 00000000 00000000
11:20:11.491422 R00000000 Read-Data Status: 00000000 00000000
11:20:12.486791 R00000000 Read-Data Status: 00000000 00000000
11:20:13.482249 R00000000 Read-Data Status: 00000000 00000000
11:20:14.477684 R00000000 Read-Data Status: 00000000 00000000
11:20:15.473081 R00000000 Read-Data Status: 00000000 00000000
11:20:16.468382 R00000000 Read-Data Status: 00000000 00000000
11:20:17.463801 R00000000 Read-Data Status: 00000000 00000000
11:20:18.459205 R00000000 Read-Data Status: 00000000 00000000
11:20:19.454637 R00000000 Read-Data Status: 00000000 00000000
11:20:20.449989 R00000000 Read-Data Status: 00000000 00000000
11:20:21.445339 R00000000 Read-Data Status: 00000000 00000000
11:20:22.440715 R00000000 Read-Data Status: 00000000 00000000
11:20:23.436048 R00000000 Read-Data Status: 00000000 00000000
11:20:24.431398 R00000000 Read-Data Status: 00000000 00000000
11:20:25.426815 R00000000 Read-Data Status: 00000000 00000000
11:20:26.443390 Thermostat connected
11:26:19.615200 pÿOpÿOpÿOpÿOpÿOpÿOpÿOpÿOpÿOpenTherm Gateway 4.0b2
11:26:19.646228 Thermostat disconnected
11:26:23.761287 R00000000 Read-Data Status: 00000000 00000000
11:26:24.757072 R00000000 Read-Data Status: 00000000 00000000
11:26:25.752741 R00000000 Read-Data Status: 00000000 00000000
11:26:26.748436 R00000000 Read-Data Status: 00000000 00000000
11:26:27.744267 R00000000 Read-Data Status: 00000000 00000000
11:26:28.740012 R00000000 Read-Data Status: 00000000 00000000
11:26:29.735696 R00000000 Read-Data Status: 00000000 00000000
11:26:30.732591 R00000000 Read-Data Status: 00000000 00000000
11:26:31.726996 R00000000 Read-Data Status: 00000000 00000000
11:26:32.722688 R00000000 Read-Data Status: 00000000 00000000
11:26:37.701205 R00000000 Read-Data Status: 00000000 00000000
11:26:37.720238 R00000000 Read-Data Status: 00000000 00000000
11:26:38.696840 R00000000 Read-Data Status: 00000000 00000000
11:26:39.692606 R00000000 Read-Data Status: 00000000 00000000
11:26:40.688308 R00000000 Read-Data Status: 00000000 00000000
11:26:41.684044 R00000000 Read-Data Status: 00000000 00000000
11:26:42.679668 R00000000 Read-Data Status: 00000000 00000000
11:26:43.675418 R00000000 Read-Data Status: 00000000 00000000
11:26:44.671154 R00000000 Read-Data Status: 00000000 00000000
11:26:45.666830 R00000000 Read-Data Status: 00000000 00000000
11:26:46.662467 R00000000 Read-Data Status: 00000000 00000000
11:26:47.658162 R00000000 Read-Data Status: 00000000 00000000
11:26:48.653906 R00000000 Read-Data Status: 00000000 00000000
11:26:49.407493 Command: GW=1
11:26:49.426257 GW: 1
11:26:49.649569 R00000000 Read-Data Status: 00000000 00000000
11:26:50.645251 R00000000 Read-Data Status: 00000000 00000000
11:26:51.640948 R00000000 Read-Data Status: 00000000 00000000
11:26:52.636704 R00000000 Read-Data Status: 00000000 00000000
11:26:53.632398 R00000000 Read-Data Status: 00000000 00000000
11:26:54.628150 R00000000 Read-Data Status: 00000000 00000000
11:26:54.663683 Command: PR=A
11:26:54.706923 PR: A=OpenTherm Gateway 4.0b2
11:26:55.623726 R00000000 Read-Data Status: 00000000 00000000
11:26:56.619493 R00000000 Read-Data Status: 00000000 00000000
11:26:57.615148 R00000000 Read-Data Status: 00000000 00000000
11:26:58.610908 R00000000 Read-Data Status: 00000000 00000000
11:26:59.606560 R00000000 Read-Data Status: 00000000 00000000
11:27:00.602257 R00000000 Read-Data Status: 00000000 00000000
11:27:01.597901 R00000000 Read-Data Status: 00000000 00000000
11:27:02.593495 R00000000 Read-Data Status: 00000000 00000000
11:27:03.589135 R00000000 Read-Data Status: 00000000 00000000
11:27:04.584767 R00000000 Read-Data Status: 00000000 00000000
11:27:05.580418 R00000000 Read-Data Status: 00000000 00000000
11:27:06.575973 R00000000 Read-Data Status: 00000000 00000000
11:27:07.571721 R00000000 Read-Data Status: 00000000 00000000
11:27:08.567250 R00000000 Read-Data Status: 00000000 00000000
11:27:09.562848 R00000000 Read-Data Status: 00000000 00000000
11:27:10.558508 R00000000 Read-Data Status: 00000000 00000000
11:27:52.875703 OpenTherm Gateway 4.0b3
11:27:52.906784 Thermostat disconnected
11:27:57.021091 R00000000 Read-Data Status: 00000000 00000000
11:27:58.016648 R00000000 Read-Data Status: 00000000 00000000
11:27:59.012155 R00000000 Read-Data Status: 00000000 00000000
11:28:00.007663 R00000000 Read-Data Status: 00000000 00000000
11:28:01.003167 R00000000 Read-Data Status: 00000000 00000000
11:28:07.971390 R00000000 Read-Data Status: 00000000 00000000
11:28:07.991532 R00000000 Read-Data Status: 00000000 00000000
11:28:08.966873 R00000000 Read-Data Status: 00000000 00000000
11:28:08.985756 R00000000 Read-Data Status: 00000000 00000000
11:28:09.962343 R00000000 Read-Data Status: 00000000 00000000
11:28:10.957806 R00000000 Read-Data Status: 00000000 00000000
11:28:11.953323 R00000000 Read-Data Status: 00000000 00000000
11:28:12.948812 R00000000 Read-Data Status: 00000000 00000000
11:28:13.944327 R00000000 Read-Data Status: 00000000 00000000
11:28:14.939844 R00000000 Read-Data Status: 00000000 00000000
11:28:15.935212 R00000000 Read-Data Status: 00000000 00000000
11:28:16.930700 R00000000 Read-Data Status: 00000000 00000000
11:28:17.926209 R00000000 Read-Data Status: 00000000 00000000
11:28:18.921674 R00000000 Read-Data Status: 00000000 00000000
11:28:19.917036 R00000000 Read-Data Status: 00000000 00000000
11:28:20.912502 R00000000 Read-Data Status: 00000000 00000000
11:28:21.907945 R00000000 Read-Data Status: 00000000 00000000
11:28:22.903458 R00000000 Read-Data Status: 00000000 00000000
11:28:23.898994 R00000000 Read-Data Status: 00000000 00000000
11:28:24.894475 R00000000 Read-Data Status: 00000000 00000000
11:28:25.890024 R00000000 Read-Data Status: 00000000 00000000
11:28:26.885425 R00000000 Read-Data Status: 00000000 00000000
11:28:27.880857 R00000000 Read-Data Status: 00000000 00000000
11:28:28.442734 Command: PR=A
11:28:28.485959 PR: A=OpenTherm Gateway 4.0b3
11:28:28.876323 R00000000 Read-Data Status: 00000000 00000000
11:28:29.871829 R00000000 Read-Data Status: 00000000 00000000
11:28:30.586758 Command: GW=1
11:28:30.612875 GW: 1
11:28:30.867295 R00000000 Read-Data Status: 00000000 00000000
11:28:31.862802 R00000000 Read-Data Status: 00000000 00000000
11:28:32.858215 R00000000 Read-Data Status: 00000000 00000000
11:28:33.853714 R00000000 Read-Data Status: 00000000 00000000
11:28:34.849204 R00000000 Read-Data Status: 00000000 00000000
11:28:35.844552 R00000000 Read-Data Status: 00000000 00000000
11:28:36.049713 Thermostat connected
11:29:24.566518 R00000000 Read-Data Status: 00000000 00000000
11:29:25.562052 R00000000 Read-Data Status: 00000000 00000000
11:29:26.557606 R00000000 Read-Data Status: 00000000 00000000
11:29:27.553114 R00000000 Read-Data Status: 00000000 00000000
11:29:28.548675 R00000000 Read-Data Status: 00000000 00000000
11:29:29.544259 R00000000 Read-Data Status: 00000000 00000000
11:29:30.539856 R00000000 Read-Data Status: 00000000 00000000
11:29:31.535523 R00000000 Read-Data Status: 00000000 00000000
11:29:32.530912 R00000000 Read-Data Status: 00000000 00000000
11:29:33.526504 R00000000 Read-Data Status: 00000000 00000000
11:29:34.522153 R00000000 Read-Data Status: 00000000 00000000
11:29:35.517643 R00000000 Read-Data Status: 00000000 00000000
11:29:38.504363 R00000000 Read-Data Status: 00000000 00000000
11:29:38.522918 R00000000 Read-Data Status: 00000000 00000000
11:29:39.499941 R00000000 Read-Data Status: 00000000 00000000
11:29:42.486575 R00000000 Read-Data Status: 00000000 00000000
11:29:42.505431 R00000000 Read-Data Status: 00000000 00000000
11:29:43.482104 R00000000 Read-Data Status: 00000000 00000000
11:29:44.477664 R00000000 Read-Data Status: 00000000 00000000
11:29:45.473187 R00000000 Read-Data Status: 00000000 00000000
11:29:46.468589 R00000000 Read-Data Status: 00000000 00000000
11:29:47.463070 R00000000 Read-Data Status: 00000000 00000000
11:29:48.459671 R00000000 Read-Data Status: 00000000 00000000
11:29:49.455213 R00000000 Read-Data Status: 00000000 00000000
11:29:50.450746 R00000000 Read-Data Status: 00000000 00000000
11:29:51.348670 Thermostat connected
I've flashed new FW without a problem, so the PIC looks to be OK I guess.
Any clue?
Re: Problem starting after power outage
Posted: Wed Feb 19, 2014 1:09 pm
by nlrb
It looks to be a grounding issue. If I just hold my finger to the GND then the OTG will start up. I've made a video of it. Let me see if I can post it later.
Re: Problem starting after power outage
Posted: Wed Feb 19, 2014 3:05 pm
by nlrb
I've uploaded the video
here. In the video it looks like the LEDs are on constantly once the power is switched on. However, the human eye can see that the LEDs go off briefly numerous of times per second.