Oentherm problem?
Posted: Wed Jan 01, 2014 8:40 pm
Greeting to whoever reads this.
I've come across a possible opentherm conflict bewteen my boiler and honeywell programmer and would like a bit of advice from people in the know.
Programmer in question is a Honeywell sundial rf pack 5 honeywelluk.com/products/Systems/Sundia ... F2-Pack-5/ and boiler is a Ferroli Modena He 32.
Problem that I'm having is that if I set the Dhw temperature to 55deg on the boiler, the setting gets altered to 40 deg by the programmer and I have no way of adjusting it on the programmer. It states in the installation manual that setting the Dhw on this model is not supported, but it's still sending a write command of 0 deg to the boiler. Should it still be sending dhw write commands to the boiler?
I've contacted honeywell and the opentherm association but guess I won't get a reply from them until early next week.
Logs captured with opentherm gateway 3.4
Opentherm gateway in monitor mode:
Opentherm gateway in monitor mode:
19:18:41.867986 T00000300 Read-Data Status: 00000011 00000000
19:18:42.755169 T10380000 Write-Data DHW setpoint: 0.00 ** programmer should not be sending this??
19:18:42.886398 BD0380000 Write-Ack DHW setpoint: 0.00
19:18:43.739455 T10393700 Write-Data Max CH water setpoint: 55.00
19:18:44.626434 T10393700 Write-Data Max CH water setpoint: 55.00
19:18:44.707285 BD0393700 Write-Ack Max CH water setpoint: 55.00
19:18:45.610052 T00000300 Read-Data Status: 00000011 00000000
19:18:45.713524 BC000030A Read-Ack Status: 00000011 00001010
19:18:46.592192 T90013700 Write-Data Control setpoint: 55.00
19:18:47.477801 Error 03
19:18:48.354632 T90013700 Write-Data Control setpoint: 55.00
19:18:48.443264 B50013700 Write-Ack Control setpoint: 55.00
Opentherm gateway in gateway mode:
00:08:41.135354 T80190000 Read-Data Boiler water temperature: 0.00
00:08:41.246895 B40193600 Read-Ack Boiler water temperature: 54.00
00:08:42.026317 T80000200 Read-Data Status: 00000010 00000000
00:08:42.167761 B40000200 Read-Ack Status: 00000010 00000000
00:08:43.000475 T10380000 Write-Data DHW setpoint: 0.00 ** programmer should not be sending this??
00:08:43.013491 R90383700 Write-Data DHW setpoint: 55.00 ( gateway sent this command, not programmer)
00:08:43.149035 B50383700 Write-Ack DHW setpoint: 55.00
00:08:43.987445 T10393700 Write-Data Max CH water setpoint: 55.00
00:08:44.132857 BD0393700 Write-Ack Max CH water setpoint: 55.00
00:08:44.958187 T10010A00 Write-Data Control setpoint: 10.00
00:08:45.465261 BD0010A00 Write-Ack Control setpoint: 10.00
00:08:45.938171 T80190000 Read-Data Boiler water temperature: 0.00
00:08:46.030222 B40193600 Read-Ack Boiler water temperature: 54.00
Am I correct in thinking that the programmer might be faulty?
Kind regards
I've come across a possible opentherm conflict bewteen my boiler and honeywell programmer and would like a bit of advice from people in the know.
Programmer in question is a Honeywell sundial rf pack 5 honeywelluk.com/products/Systems/Sundia ... F2-Pack-5/ and boiler is a Ferroli Modena He 32.
Problem that I'm having is that if I set the Dhw temperature to 55deg on the boiler, the setting gets altered to 40 deg by the programmer and I have no way of adjusting it on the programmer. It states in the installation manual that setting the Dhw on this model is not supported, but it's still sending a write command of 0 deg to the boiler. Should it still be sending dhw write commands to the boiler?
I've contacted honeywell and the opentherm association but guess I won't get a reply from them until early next week.
Logs captured with opentherm gateway 3.4
Opentherm gateway in monitor mode:
Opentherm gateway in monitor mode:
19:18:41.867986 T00000300 Read-Data Status: 00000011 00000000
19:18:42.755169 T10380000 Write-Data DHW setpoint: 0.00 ** programmer should not be sending this??
19:18:42.886398 BD0380000 Write-Ack DHW setpoint: 0.00
19:18:43.739455 T10393700 Write-Data Max CH water setpoint: 55.00
19:18:44.626434 T10393700 Write-Data Max CH water setpoint: 55.00
19:18:44.707285 BD0393700 Write-Ack Max CH water setpoint: 55.00
19:18:45.610052 T00000300 Read-Data Status: 00000011 00000000
19:18:45.713524 BC000030A Read-Ack Status: 00000011 00001010
19:18:46.592192 T90013700 Write-Data Control setpoint: 55.00
19:18:47.477801 Error 03
19:18:48.354632 T90013700 Write-Data Control setpoint: 55.00
19:18:48.443264 B50013700 Write-Ack Control setpoint: 55.00
Opentherm gateway in gateway mode:
00:08:41.135354 T80190000 Read-Data Boiler water temperature: 0.00
00:08:41.246895 B40193600 Read-Ack Boiler water temperature: 54.00
00:08:42.026317 T80000200 Read-Data Status: 00000010 00000000
00:08:42.167761 B40000200 Read-Ack Status: 00000010 00000000
00:08:43.000475 T10380000 Write-Data DHW setpoint: 0.00 ** programmer should not be sending this??
00:08:43.013491 R90383700 Write-Data DHW setpoint: 55.00 ( gateway sent this command, not programmer)
00:08:43.149035 B50383700 Write-Ack DHW setpoint: 55.00
00:08:43.987445 T10393700 Write-Data Max CH water setpoint: 55.00
00:08:44.132857 BD0393700 Write-Ack Max CH water setpoint: 55.00
00:08:44.958187 T10010A00 Write-Data Control setpoint: 10.00
00:08:45.465261 BD0010A00 Write-Ack Control setpoint: 10.00
00:08:45.938171 T80190000 Read-Data Boiler water temperature: 0.00
00:08:46.030222 B40193600 Read-Ack Boiler water temperature: 54.00
Am I correct in thinking that the programmer might be faulty?
Kind regards