OT errors to switch relay

Posted: Wed Jan 22, 2014 12:58 pm
by HILTON
Hi Im new to this forum so hello to everyone. :D

Im a commercial industrial heating engineer. I have a good knowledge of work with opentherm but nothing regarding it programming.

What i need is when an OT boiler has a fault i need it to simply switcha relay to turn on a light. This in principle is very easy but i have no clue how to do this.
im also suprised no commecrial manufactures have a simple pcb to do the function. Although vaillant produce it but much larger to do diffrent things so i know it can be done.

I would appreciate any help you coud give me.

Kind regards

Hilton

Re: OT errors to switch relay

Posted: Thu Jan 23, 2014 10:59 am
by hvxl
The OT Gateway has configurable outputs, originally intended to drive LEDs. You can configure one (or more) outputs to come on when the boiler reports a problem (e.g. LD=M, which is actually the default). If you connect some simple circuitry to that output to drive a relay, I think you're all set.

Re: OT errors to switch relay

Posted: Fri Jan 24, 2014 11:38 pm
by HILTON
Thank you very much HVXL il look into it