I received a brand new board from NodoShop and struggled a lot before succeeding to control my Central Heating.
I believe this is a bug. I want to share it in the hope it will be fixed.
I also found a way to get around it, it could be useful for other users!
Steps to reproduce
- Be in standalone mode (remove Thermostat from header)
- Have an empty list of Alternative Data IDs
- Try to make the boiler heat your house by using CS/CH serial commands
(Note that CS command is honored only for 1min before going back to CS=0. This is written in the doc but it took me time to understand this. So, you need to regularly send CS=x messages and send one CH=1 message.)
Expected behavior
The boiler should heat the house
Actual behavior
Boiler is never heating.
Analysis
The gateway is sending contradictory Status (ID 0) messages (master status). Sometimes it says it enables the CH bit, sometimes it says it disables the CH bit.
The boiler never even activates Central Heating because before it can do that, the gateway has already sent again a CH=0 to the boiler.
09:01:56.666493 R80000100 Read-Data Status (MsgID=0): 00000001 00000000
09:01:56.861462 B40000100 Read-Ack Status (MsgID=0): 00000001 00000000
09:01:57.660599 R80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:01:57.761334 B401932E6 Read-Ack Boiler water temperature (MsgID=25): 50.90
09:01:58.656872 R10015000 Write-Data Control setpoint (MsgID=1): 80.00
09:01:58.764957 BD0015000 Write-Ack Control setpoint (MsgID=1): 80.00
09:01:59.652308 R00000000 Read-Data Status (MsgID=0): 00000000 00000000
09:01:59.772792 BC0000000 Read-Ack Status (MsgID=0): 00000000 00000000
09:02:00.649589 R00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:02:00.774836 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
09:02:01.645980 R001B0000 Read-Data Outside temperature (MsgID=27): 0.00
09:02:01.779431 B601B0000 Data-Inv Outside temperature (MsgID=27): 0.00
09:02:02.644223 R801C0000 Read-Data Return water temperature (MsgID=28): 0.00
09:02:02.785102 B701C0000 Unk-DataId Return water temperature (MsgID=28): 0.00
09:02:03.812008 R900E6400 Write-Data Maximum relative modulation level (MsgID=14): 100.00
09:02:03.817862 B500E6400 Write-Ack Maximum relative modulation level (MsgID=14): 100.00
09:02:04.640376 R00000000 Read-Data Status (MsgID=0): 00000000 00000000
09:02:04.798870 BC0000000 Read-Ack Status (MsgID=0): 00000000 00000000
09:02:05.638310 R80000100 Read-Data Status (MsgID=0): 00000001 00000000
09:02:05.803047 B40000100 Read-Ack Status (MsgID=0): 00000001 00000000
09:02:06.636330 R80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:02:06.809914 B401932CD Read-Ack Boiler water temperature (MsgID=25): 50.80
09:02:07.635943 R10015000 Write-Data Control setpoint (MsgID=1): 80.00
09:02:07.818106 BD0015000 Write-Ack Control setpoint (MsgID=1): 80.00
09:02:08.634461 R80380000 Read-Data DHW setpoint (MsgID=56): 0.00
09:02:08.823002 BC0383200 Read-Ack DHW setpoint (MsgID=56): 50.00
09:02:09.634351 R00390000 Read-Data Max CH water setpoint (MsgID=57): 0.00
09:02:09.733010 BC0395000 Read-Ack Max CH water setpoint (MsgID=57): 80.00
09:02:10.633089 R00000000 Read-Data Status (MsgID=0): 00000000 00000000
09:02:10.738061 BC0000000 Read-Ack Status (MsgID=0): 00000000 00000000
09:02:11.785176 R00120000 Read-Data CH water pressure (MsgID=18): 0.00
09:02:11.874188 B40120166 Read-Ack CH water pressure (MsgID=18): 1.40
It took time for me to understand what to do to make it work.
I noticed the messages sent in standalone mode are documented here:
https://otgw.tclcode.com/standalone.html#intro
They always occur in this order:
MsgID 0: Master and Slave Status flags
MsgID 25: Boiler flow water temperature
MsgID 1: Control Setpoint
UserDefined
MsgID 17: Relative Modulation Level
MsgID 27: Outside temperature
MsgID 28: Return water temperature
MsgID 14: Maximum relative modulation level setting
UserDefined
MsgID 56: DHW Setpoint
MsgID 57: Max CH water Setpoint
UserDefined
MsgID 18: Water pressure in CH circuit
When comparing my messages log with this list, we quickly see that correct Status messages (CH=1) are the Status messages in the list, and wrong ones with the bug (CH=0) are those replacing the UserDefined slots.
UserDefined slots are filled by the alternative ID list. But if the list is empty, it send a Status (ID0) message.
The bug is: when filling up a UserDefined slot, if the alternative ID list is empty, the Status sent is an all-zero status, not reflecting the real status the gateway wants to send.
Work Around
The way to get around that is to add a minimum of 1 alternative ID, to make sure that UserDefined slots will never attempt to send the buggy Status message.
[Bug] Flapping CH enable bit in standalone mode
Re: [Bug] Flapping CH enable bit in standalone mode
Thank you for your very detailed analysis. I will work on fixing this bug.
One small remark: Only one alternative ID should be needed. The OTGW goes through the list whenever it is scheduled to send a user defined message, and starts again from the top when the list is exhausted. It doesn't map each alternative ID to a specific slot in the sequence.
Thanks for your answer!
Yes, actually I had noticed the behavior like you say: only 1 alternative ID is enough. With 1 alternative ID, all UserDefined slots are filled with that.
I edited my post accordingly.
Adding an alternative ID solved to "Flapping CH enable bit" problem; the "Central heating mode" stays enabled. However, the flame starts for a random short amount of time and then stops while the CH bit is still enabled and the water temperature is not yet at the desired setpoint. I'm sending the CS=xx command every 4 seconds. Is this also part of the bug or am i doing something wrong?
Logging:
Note: the toggling between CS 65 and CS 66 is me trying to find a workaround for the problem
10:07:07.350526 GW: 1
10:07:07.357965
10:07:07.410501 MM: 70
10:07:07.423700
10:07:07.432640 CS: 66.00
10:07:07.441762
10:07:07.450374 CH: 1
10:07:07.457419
10:07:08.016940 R00780000 Read-Data Burner operation hours: 0
10:07:08.021182
10:07:08.126151 B40780288 Read-Ack Burner operation hours: 648
10:07:08.137545
10:07:09.091022 R00110000 Read-Data Relative modulation level: 0.00
10:07:09.099271
10:07:09.192846 BC0110000 Read-Ack Relative modulation level: 0.00
10:07:09.200512
10:07:10.115927 R80310000 Read-Data Max CH setpoint boundaries: 0 0
10:07:10.131882
10:07:10.239153 B40315500 Read-Ack Max CH setpoint boundaries: 85 0
10:07:10.247091
10:07:11.139000 R801C0000 Read-Data Return water temperature: 0.00
10:07:11.139836
10:07:11.242272 BC01C1900 Read-Ack Return water temperature: 25.00
10:07:11.244778
10:07:12.166476 R900E4600 Write-Data Maximum relative modulation level: 70.00
10:07:12.167534
10:07:12.274366 B500E4600 Write-Ack Maximum relative modulation level: 70.00
10:07:12.275892
10:07:13.205049 R80310000 Read-Data Max CH setpoint boundaries: 0 0
10:07:13.206022
10:07:13.330267 B40315500 Read-Ack Max CH setpoint boundaries: 85 0
10:07:13.330842
10:07:14.239096 R80000100 Read-Data Status: 00000001 00000000
10:07:14.239805
10:07:14.416515 B40000100 Read-Ack Status: 00000001 00000000
10:07:14.419703
10:07:15.276981 R80190000 Read-Data Boiler water temperature: 0.00
10:07:15.277988
10:07:15.375371 BC0191900 Read-Ack Boiler water temperature: 25.00
10:07:15.376923
10:07:16.311403 R10014200 Write-Data Control setpoint: 66.00
10:07:16.313080
10:07:16.434611 BD0014200 Write-Ack Control setpoint: 66.00
10:07:16.435209
10:07:17.351612 R80380000 Read-Data DHW setpoint: 0.00
10:07:17.352324
10:07:17.487602 B40383C00 Read-Ack DHW setpoint: 60.00
10:07:17.489860
10:07:18.408563 R00390000 Read-Data Max CH water setpoint: 0.00
10:07:18.409273
10:07:18.543462 BC0394B00 Read-Ack Max CH water setpoint: 75.00
10:07:18.545290
10:07:19.433259 R007B0000 Read-Data DHW burner operation hours: 0
10:07:19.434731
10:07:19.535743 BC07B0055 Read-Ack DHW burner operation hours: 85
10:07:19.536670
10:07:20.464239 R00120000 Read-Data CH water pressure: 0.00
10:07:20.464646
10:07:20.574633 B401201CC Read-Ack CH water pressure: 1.80
10:07:20.575204
10:07:21.498258 R80000100 Read-Data Status: 00000001 00000000
10:07:21.500506
10:07:21.632297 BC0000102 Read-Ack Status: 00000001 00000010
10:07:21.634119
10:07:22.537504 R80190000 Read-Data Boiler water temperature: 0.00
10:07:22.538870
10:07:22.709972 BC0191A00 Read-Ack Boiler water temperature: 26.00
10:07:22.710642
10:07:23.573848 R10014200 Write-Data Control setpoint: 66.00
10:07:23.574563
10:07:23.668694 BD0014200 Write-Ack Control setpoint: 66.00
10:07:23.670058
10:07:24.608766 R00740000 Read-Data Burner starts: 0
10:07:24.609423
10:07:24.723891 B407411E5 Read-Ack Burner starts: 4581
10:07:24.725257
10:07:25.371866 CS: 66.00
10:07:25.372670
10:07:25.679690 R00110000 Read-Data Relative modulation level: 0.00
10:07:25.681159
10:07:25.779397 BC0110000 Read-Ack Relative modulation level: 0.00
10:07:25.781010
10:07:26.702502 R007B0000 Read-Data DHW burner operation hours: 0
10:07:26.703122
10:07:26.835258 BC07B0055 Read-Ack DHW burner operation hours: 85
10:07:26.837030
10:07:27.727981 R801C0000 Read-Data Return water temperature: 0.00
10:07:27.730117
10:07:27.888655 BC01C1900 Read-Ack Return water temperature: 25.00
10:07:27.889143
10:07:28.374193 CS: 65.00
10:07:28.375406
10:07:28.761208 R900E4600 Write-Data Maximum relative modulation level: 70.00
10:07:28.763017
10:07:28.887534 B500E4600 Write-Ack Maximum relative modulation level: 70.00
10:07:28.889805
10:07:29.799372 R00770000 Read-Data DHW burner starts: 0
10:07:29.799966
10:07:29.922979 BC0770AB2 Read-Ack DHW burner starts: 2738
10:07:29.924486
10:07:30.831894 R80000100 Read-Data Status: 00000001 00000000
10:07:30.832539
10:07:30.991106 BC0000102 Read-Ack Status: 00000001 00000010
10:07:30.993655
10:07:31.369512 CS: 66.00
10:07:31.370124
10:07:31.925103 R80190000 Read-Data Boiler water temperature: 0.00
10:07:31.925707
10:07:31.972184 BC0191900 Read-Ack Boiler water temperature: 25.00
10:07:31.973009
10:07:32.905766 R10014200 Write-Data Control setpoint: 66.00
10:07:32.908011
10:07:33.051636 BD0014200 Write-Ack Control setpoint: 66.00
10:07:33.052368
10:07:33.973633 R80380000 Read-Data DHW setpoint: 0.00
10:07:33.974095
10:07:34.062903 B40383C00 Read-Ack DHW setpoint: 60.00
10:07:34.064691
10:07:34.384201 CS: 65.00
10:07:34.388117
10:07:34.980835 R00390000 Read-Data Max CH water setpoint: 0.00
10:07:34.981460
10:07:35.100036 BC0394B00 Read-Ack Max CH water setpoint: 75.00
10:07:35.101203
10:07:36.010402 R00780000 Read-Data Burner operation hours: 0
10:07:36.010957
10:07:36.159225 B40780288 Read-Ack Burner operation hours: 648
10:07:36.160803
10:07:37.044773 R00120000 Read-Data CH water pressure: 0.00
10:07:37.045458
10:07:37.147610 B401201CC Read-Ack CH water pressure: 1.80
10:07:37.148722
10:07:37.386065 CS: 66.00
10:07:37.388815
10:07:38.067589 R80000100 Read-Data Status: 00000001 00000000
10:07:38.068134
10:07:38.201813 B4000010A Read-Ack Status: 00000001 00001010
10:07:38.203498
10:07:39.106236 R80190000 Read-Data Boiler water temperature: 0.00
10:07:39.110103
10:07:39.253841 B40191D00 Read-Ack Boiler water temperature: 29.00
10:07:39.255098
10:07:40.143396 R10014200 Write-Data Control setpoint: 66.00
10:07:40.144468
10:07:40.241489 BD0014200 Write-Ack Control setpoint: 66.00
10:07:40.243683
10:07:40.424797 CS: 65.00
10:07:40.425315
10:07:41.179612 R80310000 Read-Data Max CH setpoint boundaries: 0 0
10:07:41.182205
10:07:41.294397 B40315500 Read-Ack Max CH setpoint boundaries: 85 0
10:07:41.294972
10:07:42.221676 R00110000 Read-Data Relative modulation level: 0.00
10:07:42.222163
10:07:42.355656 BC0110000 Read-Ack Relative modulation level: 0.00
10:07:42.356355
10:07:43.265096 R80310000 Read-Data Max CH setpoint boundaries: 0 0
10:07:43.265627
10:07:43.375228 CS: 66.00
10:07:43.376666
10:07:43.421773 B40315500 Read-Ack Max CH setpoint boundaries: 85 0
10:07:43.423004
10:07:44.315551 R801C0000 Read-Data Return water temperature: 0.00
10:07:44.316437
10:07:44.388128 BC01C1900 Read-Ack Return water temperature: 25.00
10:07:44.389102
10:07:45.339307 R900E4600 Write-Data Maximum relative modulation level: 70.00
10:07:45.340731
10:07:45.442579 B500E4600 Write-Ack Maximum relative modulation level: 70.00
10:07:45.444734
10:07:46.371307 R007B0000 Read-Data DHW burner operation hours: 0
10:07:46.372690
10:07:46.413886 CS: 65.00
10:07:46.416187
10:07:46.498358 BC07B0055 Read-Ack DHW burner operation hours: 85
10:07:46.499083
10:07:47.413634 R80000100 Read-Data Status: 00000001 00000000
10:07:47.415010
10:07:47.572240 B4000010A Read-Ack Status: 00000001 00001010
10:07:47.574090
10:07:48.444410 R80190000 Read-Data Boiler water temperature: 0.00
10:07:48.444854
10:07:48.617110 B40192200 Read-Ack Boiler water temperature: 34.00
10:07:48.618824
10:07:49.371885 CS: 66.00
10:07:49.373614
10:07:49.481230 R10014200 Write-Data Control setpoint: 66.00
10:07:49.481905
10:07:49.640905 BD0014200 Write-Ack Control setpoint: 66.00
10:07:49.643677
10:07:50.517529 R80380000 Read-Data DHW setpoint: 0.00
10:07:50.518134
10:07:50.664963 B40383C00 Read-Ack DHW setpoint: 60.00
10:07:50.666901
10:07:51.576007 R00390000 Read-Data Max CH water setpoint: 0.00
10:07:51.577226
10:07:51.701965 BC0394B00 Read-Ack Max CH water setpoint: 75.00
10:07:51.702719
10:07:52.406638 CS: 65.00
10:07:52.412291
10:07:52.609655 R00740000 Read-Data Burner starts: 0
10:07:52.610238
10:07:52.753164 B407411E6 Read-Ack Burner starts: 4582
10:07:52.753765
10:07:53.633882 R00120000 Read-Data CH water pressure: 0.00
10:07:53.635850
10:07:53.742289 B401201CC Read-Ack CH water pressure: 1.80
10:07:53.744804
10:07:54.661896 R80000100 Read-Data Status: 00000001 00000000
10:07:54.662417
10:07:54.794061 B4000010A Read-Ack Status: 00000001 00001010
10:07:54.794940
10:07:55.374590 CS: 66.00
10:07:55.375831
10:07:55.704050 R80190000 Read-Data Boiler water temperature: 0.00
10:07:55.704640
10:07:55.850823 B40192100 Read-Ack Boiler water temperature: 33.00
10:07:55.852274
10:07:56.743260 R10014200 Write-Data Control setpoint: 66.00
10:07:56.744726
10:07:56.834884 BD0014200 Write-Ack Control setpoint: 66.00
10:07:56.835618
10:07:57.777717 R007B0000 Read-Data DHW burner operation hours: 0
10:07:57.778547
10:07:57.886913 BC07B0055 Read-Ack DHW burner operation hours: 85
10:07:57.887482
10:07:58.377455 CS: 65.00
10:07:58.378089
10:07:58.813408 R00110000 Read-Data Relative modulation level: 0.00
10:07:58.814236
10:07:58.938341 BC0110000 Read-Ack Relative modulation level: 0.00
10:07:58.939430
10:07:59.853315 R00770000 Read-Data DHW burner starts: 0
10:07:59.855210
10:07:59.994200 BC0770AB2 Read-Ack DHW burner starts: 2738
10:07:59.995507
10:08:00.904102 R801C0000 Read-Data Return water temperature: 0.00
10:08:00.904901
10:08:01.052004 BC01C1900 Read-Ack Return water temperature: 25.00
10:08:01.052885
10:08:01.385624 CS: 66.00
10:08:01.388326
10:08:01.931343 R900E4600 Write-Data Maximum relative modulation level: 70.00
10:08:01.932465
10:08:02.034567 B500E4600 Write-Ack Maximum relative modulation level: 70.00
10:08:02.035409
10:08:02.958403 R00780000 Read-Data Burner operation hours: 0
10:08:02.958993
10:08:03.093151 B40780288 Read-Ack Burner operation hours: 648
10:08:03.093988
10:08:03.998318 R80000100 Read-Data Status: 00000001 00000000
10:08:04.003688
10:08:04.181434 B4000010A Read-Ack Status: 00000001 00001010
10:08:04.182100
10:08:04.386500 CS: 65.00
10:08:04.388230
10:08:05.037694 R80190000 Read-Data Boiler water temperature: 0.00
10:08:05.038110
10:08:05.128166 BC0192000 Read-Ack Boiler water temperature: 32.00
10:08:05.128753
10:08:06.072902 R10014100 Write-Data Control setpoint: 65.00
10:08:06.073429
10:08:06.184914 BD0014100 Write-Ack Control setpoint: 65.00
10:08:06.185381
10:08:07.109538 R80380000 Read-Data DHW setpoint: 0.00
10:08:07.110009
10:08:07.253453 B40383C00 Read-Ack DHW setpoint: 60.00
10:08:07.254530
10:08:07.388349 CS: 66.00
10:08:07.388820
10:08:08.160294 R00390000 Read-Data Max CH water setpoint: 0.00
10:08:08.161044
10:08:08.291056 BC0394B00 Read-Ack Max CH water setpoint: 75.00
10:08:08.292972
10:08:09.198714 R80310000 Read-Data Max CH setpoint boundaries: 0 0
10:08:09.199335
10:08:09.301668 B40315500 Read-Ack Max CH setpoint boundaries: 85 0
10:08:09.302308
10:08:10.226618 R00120000 Read-Data CH water pressure: 0.00
10:08:10.228827
10:08:10.328953 B401201CC Read-Ack CH water pressure: 1.80
10:08:10.329522
10:08:10.373069 CS: 65.00
10:08:10.373664
10:08:11.255486 R00000000 Read-Data Status: 00000000 00000000
10:08:11.256073
10:08:11.387931 BC000000A Read-Ack Status: 00000000 00001010
10:08:11.390128
10:08:12.291553 R80190000 Read-Data Boiler water temperature: 0.00
10:08:12.292520
10:08:12.475934 BC0192000 Read-Ack Boiler water temperature: 32.00
10:08:12.478051
10:08:13.331018 R10010000 Write-Data Control setpoint: 0.00
10:08:13.332056
10:08:13.400278 GW: 1
10:08:13.401045
10:08:13.451968 MM: 70
10:08:13.452571
10:08:13.465614 CS: 66.00
10:08:13.469320
10:08:13.473153 BD0010000 Write-Ack Control setpoint: 0.00
10:08:13.477477
10:08:13.482028 CH: 1
10:08:13.485801
10:08:14.421020 R80310000 Read-Data Max CH setpoint boundaries: 0 0
10:08:14.422107
10:08:14.483058 B40315500 Read-Ack Max CH setpoint boundaries: 85 0
10:08:14.483691
10:08:15.402285 R00110000 Read-Data Relative modulation level: 0.00
10:08:15.402723
10:08:15.534312 BC0110000 Read-Ack Relative modulation level: 0.00
10:08:15.535146
10:08:16.475589 R007B0000 Read-Data DHW burner operation hours: 0
10:08:16.477745
10:08:16.521791 GW: 1
10:08:16.522631
10:08:16.534338 MM: 70
10:08:16.539468
10:08:16.543894 CS: 66.00
10:08:16.548547
10:08:16.552627 CH: 1
10:08:16.556626
10:08:16.601468 BC07B0055 Read-Ack DHW burner operation hours: 85
10:08:16.603588
10:08:17.493065 R801C0000 Read-Data Return water temperature: 0.00
10:08:17.494841
10:08:17.589530 BC01C1900 Read-Ack Return water temperature: 25.00
10:08:17.593056
10:08:18.518800 R900E4600 Write-Data Maximum relative modulation level: 70.00
10:08:18.531563
10:08:18.631087 B500E4600 Write-Ack Maximum relative modulation level: 70.00
10:08:18.631853
10:08:19.491490 GW: 1
10:08:19.493503
10:08:19.533291 MM: 70
10:08:19.535005
10:08:19.544709 CS: 66.00
10:08:19.548850
10:08:19.552840 CH: 1
10:08:19.556764
10:08:19.581487 R00740000 Read-Data Burner starts: 0
10:08:19.583488
10:08:19.683812 B407411E6 Read-Ack Burner starts: 4582
10:08:19.685703
10:08:20.593048 R80000100 Read-Data Status: 00000001 00000000
10:08:20.593908
10:08:20.747706 B40000100 Read-Ack Status: 00000001 00000000
10:08:20.750958
10:08:21.632107 R80190000 Read-Data Boiler water temperature: 0.00
10:08:21.633302
10:08:21.724846 B40191B00 Read-Ack Boiler water temperature: 27.00
10:08:21.726258
10:08:22.513626 CS: 66.00
10:08:22.514690
10:08:22.661863 R10014200 Write-Data Control setpoint: 66.00
10:08:22.665887
10:08:22.778097 BD0014200 Write-Ack Control setpoint: 66.00
10:08:22.780076
10:08:23.698097 R80380000 Read-Data DHW setpoint: 0.00
10:08:23.700997
10:08:23.832146 B40383C00 Read-Ack DHW setpoint: 60.00
10:08:23.834955
10:08:24.761515 R00390000 Read-Data Max CH water setpoint: 0.00
10:08:24.768219
10:08:24.885611 BC0394B00 Read-Ack Max CH water setpoint: 75.00
10:08:24.889880
10:08:25.508933 CS: 65.00
10:08:25.514280
10:08:25.780541 R007B0000 Read-Data DHW burner operation hours: 0
10:08:25.782916
10:08:25.936663 BC07B0055 Read-Ack DHW burner operation hours: 85
10:08:25.939299
10:08:26.814288 R00120000 Read-Data CH water pressure: 0.00
10:08:26.815122
10:08:26.926075 B401201CC Read-Ack CH water pressure: 1.80
10:08:26.927011
10:08:27.846937 R80000100 Read-Data Status: 00000001 00000000
10:08:27.848303
10:08:27.976298 BC0000102 Read-Ack Status: 00000001 00000010
10:08:27.980017
10:08:28.509221 CS: 66.00
10:08:28.510403
10:08:28.893772 R80190000 Read-Data Boiler water temperature: 0.00
10:08:28.900294
10:08:29.040388 BC0191900 Read-Ack Boiler water temperature: 25.00
10:08:29.044037
10:08:29.923835 R10014200 Write-Data Control setpoint: 66.00
10:08:29.925879
10:08:30.020122 BD0014200 Write-Ack Control setpoint: 66.00
10:08:30.021701
10:08:30.957679 R00770000 Read-Data DHW burner starts: 0
10:08:30.959670
10:08:31.074606 BC0770AB2 Read-Ack DHW burner starts: 2738
10:08:31.076335
10:08:31.510820 CS: 65.00
10:08:31.513151
10:08:31.995546 R00110000 Read-Data Relative modulation level: 0.00
10:08:31.997724
10:08:32.124309 BC0110000 Read-Ack Relative modulation level: 0.00
10:08:32.126792
10:08:33.049321 R00780000 Read-Data Burner operation hours: 0
10:08:33.050044
10:08:33.179902 B40780288 Read-Ack Burner operation hours: 648
10:08:33.181815
10:08:34.082039 R801C0000 Read-Data Return water temperature: 0.00
10:08:34.082873
10:08:34.184000 BC01C1900 Read-Ack Return water temperature: 25.00
10:08:34.185721
10:08:34.517926 CS: 66.00
10:08:34.519586
10:08:35.108957 R900E4600 Write-Data Maximum relative modulation level: 70.00
10:08:35.109384
10:08:35.220008 B500E4600 Write-Ack Maximum relative modulation level: 70.00
10:08:35.220506
10:08:36.147276 R80310000 Read-Data Max CH setpoint boundaries: 0 0
10:08:36.148000
10:08:36.274382 B40315500 Read-Ack Max CH setpoint boundaries: 85 0
10:08:36.275217
10:08:37.186675 R80000100 Read-Data Status: 00000001 00000000
10:08:37.187229
10:08:37.348020 BC0000102 Read-Ack Status: 00000001 00000010
10:08:37.349950
10:08:37.508627 CS: 65.00
10:08:37.510457
10:08:38.220203 R80190000 Read-Data Boiler water temperature: 0.00
10:08:38.220971
10:08:38.319566 BC0191900 Read-Ack Boiler water temperature: 25.00
10:08:38.322217
10:08:39.254955 R10014100 Write-Data Control setpoint: 65.00
10:08:39.256205
10:08:39.408036 BD0014100 Write-Ack Control setpoint: 65.00
10:08:39.409383
10:08:40.330903 R80380000 Read-Data DHW setpoint: 0.00
10:08:40.334491
10:08:40.430764 B40383C00 Read-Ack DHW setpoint: 60.00
10:08:40.431988
10:08:40.533527 CS: 66.00
10:08:40.534074
10:08:41.331741 R00390000 Read-Data Max CH water setpoint: 0.00
10:08:41.332747
10:08:41.479465 BC0394B00 Read-Ack Max CH water setpoint: 75.00
10:08:41.480168
10:08:42.378254 R80310000 Read-Data Max CH setpoint boundaries: 0 0
10:08:42.379039
10:08:42.534435 B40315500 Read-Ack Max CH setpoint boundaries: 85 0
10:08:42.535412
10:08:43.412203 R00120000 Read-Data CH water pressure: 0.00
10:08:43.414482
10:08:43.517062 CS: 65.00
10:08:43.517467
10:08:43.558839 B401201CC Read-Ack CH water pressure: 1.80
10:08:43.559733
10:08:44.446504 R80000100 Read-Data Status: 00000001 00000000
10:08:44.450970
10:08:44.630279 BC0000102 Read-Ack Status: 00000001 00000010
10:08:44.631787
10:08:45.480307 R80190000 Read-Data Boiler water temperature: 0.00
10:08:45.481065
10:08:45.631123 BC0191900 Read-Ack Boiler water temperature: 25.00
10:08:45.631759
10:08:46.513149 CS: 66.00
10:08:46.513574
10:08:46.564140 R10014200 Write-Data Control setpoint: 66.00
10:08:46.565076
10:08:46.611987 BD0014200 Write-Ack Control setpoint: 66.00
10:08:46.612777
10:08:47.555868 R007B0000 Read-Data DHW burner operation hours: 0
10:08:47.556385
10:08:47.700967 BC07B0055 Read-Ack DHW burner operation hours: 85
10:08:47.701567
10:08:48.592623 R00110000 Read-Data Relative modulation level: 0.00
10:08:48.593187
10:08:48.725725 BC0110000 Read-Ack Relative modulation level: 0.00
10:08:48.726512
10:08:49.543781 CS: 65.00
10:08:49.544509
10:08:49.635748 R00740000 Read-Data Burner starts: 0
10:08:49.637287
10:08:49.776035 B407411E6 Read-Ack Burner starts: 4582
10:08:49.778202
10:08:50.665473 R801C0000 Read-Data Return water temperature: 0.00
10:08:50.666131
10:08:50.774486 BC01C1900 Read-Ack Return water temperature: 25.00
10:08:50.777455
10:08:51.700788 R900E4600 Write-Data Maximum relative modulation level: 70.00
10:08:51.707610
10:08:51.815008 B500E4600 Write-Ack Maximum relative modulation level: 70.00
10:08:51.824034
10:08:52.513215 CS: 66.00
10:08:52.518455
10:08:52.758750 R007B0000 Read-Data DHW burner operation hours: 0
10:08:52.762617
10:08:52.884010 BC07B0055 Read-Ack DHW burner operation hours: 85
10:08:52.888740
10:08:53.788833 R80000100 Read-Data Status: 00000001 00000000
10:08:53.793684
10:08:53.934623 BC0000102 Read-Ack Status: 00000001 00000010
10:08:53.941885
Something is not working as intended. At 10:08:11.255486, the OTGW seems to have cleared the control setpoint.
Which firmware are you using? Then I can try to reproduce the situation.
Thank you for the reply. I'm on firmware 5.5.
I can reproduce the issue with firmware 5.5. A fix I already made for firmware 5.6 (to be released soon) also resolves this problem.
Thank you for the effort!
Can confirm that the issue is fixed in version 5.6!