Hello,
I've recently received my OTGW from Nodo-Shop (firmware 6.0, PIC16F1847) and I've attempted to set it up between my Nefit ProLine NxT (boiler) and Nefit ModuLine 1010 (thermostat). Per compatibility matrix, only the boiler was supported, but I thought I would be lucky.
Unfortunately the thermostat does not seem to be compatible, even though allegedly it should be per manufacturer documentation. Let me separate some tests that I did:
Boiler + OTGW: works, I see the periodical messages of the standalone mode and can use it to read data from the boiler and actually control the control setpoint.
Thermostat + OTGW: I don't know what happens here. After I plug the thermostat the gateway reports Low power and stops the periodic Read-Data messages. About 1 minute afterwards the thermostat reports error code A61 1008. Per manual, this should mean that OpenTherm communication failed, so I deduce that the thermostat should be OpenTherm enabled (allegedly).
Thermostat + OTGW + Boiler: Output from the gateway seems to be the same as if only the thermostat was connected, with the added change that the boiler flame turns on and off periodically.
I'm not entirely sure how to debug it from here. I wish I could provide some logs that show messages flowing through, but I couldn't get the thermostat to actually communicate with the boiler while the gateway was connected, even with monitor mode enabled. I've tried to work through different reference voltage levels without much success.
Edit: Ok this is very weird. I've flashed the diagnostic firmware and test 2 had actual messages being read, which left me wondering what was happening before the flash. I've then flashed the normal 6.0 firmware and now I see the messages flowing through. I now wonder if the original firmware was an old revision (even though it did say 6.0).
Nefit ProLine NxT + Nefit ModuLine 1010
Moderator: hvxl
-
- Starting Member
- Posts: 2
- Joined: Sun Apr 24, 2022 1:09 pm
Re: Nefit ProLine NxT + Nefit ModuLine 1010
Just to be clear: If a boiler or thermostat is not listed in the equipment matrix, it doesn't necessarily mean that it is not compatible/supported. It only means that nobody has uploaded a log from that device yet.
A famous adage says that "a picture is worth a thousand words". But if it's just a picture of text, then providing the actual text would be more useful. Anyway, the picture shows that the thermostat sent a few Opentherm messages. But because no boiler was connected, it didn't get any response. The thermostat seems to be capable of using a few different protocols. When it didn't get a response, it may just have given up on Opentherm communication at that point. When you later connected the boiler, it may simply not have tried again to initiate Opentherm communications (I'm just guessing here).
Trying the diagnostic firmware is exactly something I would have suggested. So you did know how to debug it! I'm glad that you got things working that way.
The OTGW with PIC16F1847 is a fairly new development. Version 6.0 is the first and only firmware released for that PIC. Development versions would have identified as 6.0a1, 6.0a2, etc. So, if it said 6.0, you had the correct firmware.
I noticed an interesting remark in the thermostat manual: "De bedieningsunit is niet geschikt voor het regelen van warmtebronnen met BUS-systeem OpenTherm van andere fabrikanten" (The control unit is not suitable for controlling heat sources with BUS system OpenTherm from other manufacturers). I wonder why that is. It might be interesting to see a log.
A famous adage says that "a picture is worth a thousand words". But if it's just a picture of text, then providing the actual text would be more useful. Anyway, the picture shows that the thermostat sent a few Opentherm messages. But because no boiler was connected, it didn't get any response. The thermostat seems to be capable of using a few different protocols. When it didn't get a response, it may just have given up on Opentherm communication at that point. When you later connected the boiler, it may simply not have tried again to initiate Opentherm communications (I'm just guessing here).
Trying the diagnostic firmware is exactly something I would have suggested. So you did know how to debug it! I'm glad that you got things working that way.
The OTGW with PIC16F1847 is a fairly new development. Version 6.0 is the first and only firmware released for that PIC. Development versions would have identified as 6.0a1, 6.0a2, etc. So, if it said 6.0, you had the correct firmware.
I noticed an interesting remark in the thermostat manual: "De bedieningsunit is niet geschikt voor het regelen van warmtebronnen met BUS-systeem OpenTherm van andere fabrikanten" (The control unit is not suitable for controlling heat sources with BUS system OpenTherm from other manufacturers). I wonder why that is. It might be interesting to see a log.
Schelte
-
- Starting Member
- Posts: 2
- Joined: Sun Apr 24, 2022 1:09 pm
Re: Nefit ProLine NxT + Nefit ModuLine 1010
So...the plot thickens. I've been iterating with reboots and plugging cables in and out in order to see what happens here. I actually found a way to consistently connect the thermostat:
1. Start the gateway with only the boiler connected. It will default to gateway mode and start doing the standalone-mode command sequence.
2. Move the gateway to monitor mode.
3. Plug the cables for the thermostat. At this point I see in the logs:
At this point the thermostat did what I call the 'connect dance' and actually works - if I edit the setpoint on the physical thermostat I see the control setpoint being edited and hear the flame turning on. With that being said:
4. If I move now to gateway mode, the gateway itself does not recognize the thermostat, and it starts doing the standalone-mode command sequence.
5. Instead, if I press the reset button on the gateway, on the next boot the gateway correctly detects the thermostat and everything works even in gateway mode. I can reset as many times as I want from this point forward, but if I unplug the USB cord, I need to start from 1 again.
I start to think that this thermostat is 'dual-mode' between OpenTherm and EMS 2.0. Maybe what happens is that it first tries to connect using EMS 2.0 ?
That would explain my 'race condition' experience - if this initial dance between the thermostat and the boiler occurs while the gateway is booting up (i.e. while it is in de facto monitoring mode), then I don't need to do anything, because the weird EMS 2.0 related things occur while the gateway doesn't have to process them. But if the gateway boots faster than this hand shake, I need to do the whole monitor-unplug-reset process.
Any thoughts on this ?
1. Start the gateway with only the boiler connected. It will default to gateway mode and start doing the standalone-mode command sequence.
2. Move the gateway to monitor mode.
3. Plug the cables for the thermostat. At this point I see in the logs:
Code: Select all
10:07:02.465088 Medium power
10:07:30.882678 Low power
10:07:30.991605 Error 03 (between 0 and 2 times)
4. If I move now to gateway mode, the gateway itself does not recognize the thermostat, and it starts doing the standalone-mode command sequence.
5. Instead, if I press the reset button on the gateway, on the next boot the gateway correctly detects the thermostat and everything works even in gateway mode. I can reset as many times as I want from this point forward, but if I unplug the USB cord, I need to start from 1 again.
I start to think that this thermostat is 'dual-mode' between OpenTherm and EMS 2.0. Maybe what happens is that it first tries to connect using EMS 2.0 ?
That would explain my 'race condition' experience - if this initial dance between the thermostat and the boiler occurs while the gateway is booting up (i.e. while it is in de facto monitoring mode), then I don't need to do anything, because the weird EMS 2.0 related things occur while the gateway doesn't have to process them. But if the gateway boots faster than this hand shake, I need to do the whole monitor-unplug-reset process.
Any thoughts on this ?
- Attachments
-
- night-logs.zip
- (259.89 KiB) Downloaded 171 times
-
- connect-dance-2.zip
- (2.2 KiB) Downloaded 157 times
-
- connect-dance-1.zip
- (1.25 KiB) Downloaded 162 times
Last edited by adriansmares on Tue Apr 26, 2022 10:45 am, edited 3 times in total.
Re: Nefit ProLine NxT + Nefit ModuLine 1010
I guess this is what they meant when they indicated that the thermostat is not suitable for OpenTherm equipment from other manufacturers.
The logs show something quite unusual: Boiler responses without requests. Probably the requests are somehow invisible to the OTGW. It doesn't report any message, but it also doesn't report any error. So it seems like the thermostat sends requests using one protocol and the boiler responds using another protocol (or multiple protocols?).
You may be able to get more details about the communication by first starting test 2 of the diagnostic firmware and then connecting the thermostat. Then repeat the same procedure with test 3. But even with that information it is probably going to be difficult to figure out how to convince the thermostat to talk Opentherm after powering on the OTGW.
The logs show something quite unusual: Boiler responses without requests. Probably the requests are somehow invisible to the OTGW. It doesn't report any message, but it also doesn't report any error. So it seems like the thermostat sends requests using one protocol and the boiler responds using another protocol (or multiple protocols?).
You may be able to get more details about the communication by first starting test 2 of the diagnostic firmware and then connecting the thermostat. Then repeat the same procedure with test 3. But even with that information it is probably going to be difficult to figure out how to convince the thermostat to talk Opentherm after powering on the OTGW.
Schelte
-
- Starting Member
- Posts: 2
- Joined: Sun Apr 24, 2022 1:09 pm
Re: Nefit ProLine NxT + Nefit ModuLine 1010
The responses (Read-Ack without Read-Data) seem to be a side effect of the thermostat connection before the PIC is reset. Take a look at this minified log:
I did the diagnostics - the results are not really what I expected:
Test 2 - no weird readings here - the values seem fine (no red in the window either):
Test 3 - this seems to indicate something is very weird:
Test 5 and 6:
I thought that the thermostat will be the one with non standard behavior, but during diagnostics it seems that the boiler has some weird voltages/timings.
Code: Select all
// The gateway is in gateway+standalone mode here, as the thermostat is not connected.
22:19:32.367340 BC0192A00 Read-Ack Boiler water temperature: 42.00
22:19:33.197520 R10010000 Write-Data Control setpoint: 0.00
22:19:33.338880 BD0010000 Write-Ack Control setpoint: 0.00
22:19:34.196638 R00060000 Read-Data Remote parameter flags: 00000000 00000000
22:19:34.323517 B40060301 Read-Ack Remote parameter flags: 00000011 00000001
22:19:35.207589 R00110000 Read-Data Relative modulation level: 0.00
22:19:35.267614 BC0110000 Read-Ack Relative modulation level: 0.00
22:19:36.215702 R001B0000 Read-Data Outside temperature: 0.00
22:19:36.357046 BF01B0000 Unk-DataId Outside temperature: 0.00
22:19:37.203868 R801C0000 Read-Data Return water temperature: 0.00
22:19:37.341092 BC01C2900 Read-Ack Return water temperature: 41.00
22:19:38.218982 R900E6400 Write-Data Maximum relative modulation level: 100.00
22:19:38.367947 B500E6400 Write-Ack Maximum relative modulation level: 100.00
22:19:39.210063 R00300000 Read-Data DHW setpoint boundaries: 0 0
22:19:39.260926 BC0303C1E Read-Ack DHW setpoint boundaries: 60 30
22:19:39.473365 Command: PR=V
22:19:39.482908 Command: PR=T
22:19:39.501095 Command: PR=S
22:19:39.523064 PR: V=5
22:19:39.583212 PR: T=11
22:19:39.592454 PR: S=16.00
22:19:40.207087 R00000000 Read-Data Status: 00000000 00000000
22:19:40.385625 BC0000000 Read-Ack Status: 00000000 00000000
22:19:41.207860 R80190000 Read-Data Boiler water temperature: 0.00
22:19:41.345182 BC0192900 Read-Ack Boiler water temperature: 41.00
22:19:41.365025 Command: PR=M
22:19:41.440839 PR: M=G
22:19:42.231716 R10010000 Write-Data Control setpoint: 0.00
22:19:42.287112 BD0010000 Write-Ack Control setpoint: 0.00
// The mode is changed to monitor.
22:19:42.415647 Command: GW=0
22:19:42.593520 GW: 0
22:19:42.601930 Medium power
// The thermostat is connected now, and after the 'Low Power' message, you can see the initial set of commands.
22:20:07.422958 Low power
22:20:07.696891 B40000200 Read-Ack Status: 00000010 00000000
22:20:07.851785 B50020100 Write-Ack Master configuration: 00000001 0
22:20:08.083584 B400F1819 Read-Ack Boiler capacity and modulation limits: 24 25
22:20:08.549612 B40000200 Read-Ack Status: 00000010 00000000
22:20:08.785762 BD0010000 Write-Ack Control setpoint: 0.00
22:20:08.970666 BD00E0000 Write-Ack Maximum relative modulation level: 0.00
22:20:09.188197 BC0394B00 Read-Ack Max CH water setpoint: 75.00
// The gateway is now in monitor mode, but does not see the requests for some reason.
22:20:09.557914 B40000200 Read-Ack Status: 00000010 00000000
22:20:10.527240 B40000200 Read-Ack Status: 00000010 00000000
22:20:11.503082 B40000200 Read-Ack Status: 00000010 00000000
22:20:12.599479 B40000200 Read-Ack Status: 00000010 00000000
22:20:13.559797 B40000200 Read-Ack Status: 00000010 00000000
22:20:14.529590 B40000200 Read-Ack Status: 00000010 00000000
22:20:15.514217 B40000200 Read-Ack Status: 00000010 00000000
22:20:17.104654 40000200
// I reset the gateway without unplugging anything. The gateway is now in gateway mode.
22:20:17.197794 OpenTherm Gateway 6.0
22:20:17.435621 T80000200 Read-Data Status: 00000010 00000000
22:20:17.558301 B40000200 Read-Ack Status: 00000010 00000000
22:20:18.431239 T80000200 Read-Data Status: 00000010 00000000
22:20:18.543216 B40000200 Read-Ack Status: 00000010 00000000
22:20:19.427424 T80000200 Read-Data Status: 00000010 00000000
22:20:19.472332 B40000200 Read-Ack Status: 00000010 00000000
22:20:20.432130 T80000200 Read-Data Status: 00000010 00000000
22:20:21.985612 B40000200 Read-Ack Status: 00000010 00000000
22:20:21.994788 T80000200 Read-Data Status: 00000010 00000000
22:20:22.009628 B40000200 Read-Ack Status: 00000010 00000000
22:20:22.533386 T80000200 Read-Data Status: 00000010 00000000
22:20:23.916128 B40000200 Read-Ack Status: 00000010 00000000
22:20:23.963954 T80000200 Read-Data Status: 00000010 00000000
22:20:23.972526 B40000200 Read-Ack Status: 00000010 00000000
22:20:24.413105 T80000200 Read-Data Status: 00000010 00000000
22:20:24.522689 B40000200 Read-Ack Status: 00000010 00000000
...
22:20:37.409488 T80000200 Read-Data Status: 00000010 00000000
22:20:37.523134 B40000200 Read-Ack Status: 00000010 00000000
22:20:38.396522 T80000200 Read-Data Status: 00000010 00000000
22:20:38.460891 B40000200 Read-Ack Status: 00000010 00000000
22:20:39.393837 T80000200 Read-Data Status: 00000010 00000000
22:20:39.452630 B40000200 Read-Ack Status: 00000010 00000000
22:20:40.391296 T80000200 Read-Data Status: 00000010 00000000
// I swap the gateway to monitor mode.
22:20:41.116581 Command: GW=0
22:20:41.868339 B40000200 Read-Ack Status: 00000010 00000000
22:20:42.012932 GW: 0
// The Read-Data is continued - so the gateway does see the request now.
22:20:42.023528 T80000200 Read-Data Status: 00000010 00000000
22:20:42.042558 B40000200 Read-Ack Status: 00000010 00000000
22:20:42.635857 T80000200 Read-Data Status: 00000010 00000000
22:20:42.696011 B40000200 Read-Ack Status: 00000010 00000000
22:20:43.384942 T80000200 Read-Data Status: 00000010 00000000
22:20:43.495173 B40000200 Read-Ack Status: 00000010 00000000
22:20:44.384006 T80000200 Read-Data Status: 00000010 00000000
22:20:44.446649 B40000200 Read-Ack Status: 00000010 00000000
22:20:45.385287 T80000200 Read-Data Status: 00000010 00000000
22:20:45.433884 B40000200 Read-Ack Status: 00000010 00000000
22:20:46.386145 T80000200 Read-Data Status: 00000010 00000000
22:20:46.442784 B40000200 Read-Ack Status: 00000010 00000000
22:20:47.385353 T80000200 Read-Data Status: 00000010 00000000
22:20:47.514487 B40000200 Read-Ack Status: 00000010 00000000
22:20:48.387058 T80000200 Read-Data Status: 00000010 00000000
22:20:48.443636 B40000200 Read-Ack Status: 00000010 00000000
22:20:49.537747 T80000200 Read-Data Status: 00000010 00000000
22:20:49.547257 B40000200 Read-Ack Status: 00000010 00000000
22:20:49.734553 T10014B00 Write-Data Control setpoint: 75.00
22:20:49.799176 BD0014B00 Write-Ack Control setpoint: 75.00
22:20:49.975556 T900E1A00 Write-Data Maximum relative modulation level: 26.00
22:20:50.025405 B500E1A00 Write-Ack Maximum relative modulation level: 26.00
Test 2 - no weird readings here - the values seem fine (no red in the window either):
Code: Select all
Opentherm gateway diagnostics - Version 2.0
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 2
.
2613.
.
480,542,479,1046,489,533,488,534,487,536,486,535,486,534,487,535,487,533,489,534,487,535,486,535,486,550,471,537,485,534,487,533,488,534,494,527,488,538,483,532,491,534,486,533,1004,1041,486,536,486,534,487,535,486,536,486,550,470,532,490,535,487,553,984.
80000200 Read-Data Status: 00000010 00000000
487,539,483,1050,485,536,1001,1038,489,532,490,533,488,536,486,535,486,536,486,533,488,533,489,535,486,536,1002,1039,489,535,498,523,501,517,490,532,489,537,485,536,486,532,1005,1038,489,532,490,532,489,534,488,531,491,536,485,537,484,537,1000.
90020100 Write-Data Master configuration: 00000001 0
480,1059,476,535,486,584,436,536,487,535,486,535,486,537,484,533,489,529,492,531,490,536,486,534,1003,530,483,537,484,538,484,1046,490,532,488,533,488,533,489,521,500,533,488,533,488,534,487,533,488,534,487,535,500,516,491,533,489,531,489,534,488,533,1004.
000F0000 Read-Data Boiler capacity and modulation limits: 0 0
468,538,484,1046,489,532,489,535,500,517,491,533,488,537,485,532,489,532,489,531,491,533,488,535,486,533,491,528,491,533,489,534,487,532,489,552,469,533,489,534,487,531,491,532,1005,1034,493,529,492,533,489,544,477,535,487,536,485,539,482,533,488,535,1002.
80000200 Read-Data Status: 00000010 00000000
479,1049,486,532,489,533,1004,1038,488,535,487,533,488,535,486,533,489,532,489,534,487,535,486,532,489,527,494,542,995,1086,440,538,485,536,485,535,486,536,486,534,487,531,490,532,489,532,490,532,489,532,489,535,486,536,486,534,487,532,493,529,1005.
10010000 Write-Data Control setpoint: 0.00
480,1048,488,533,510,510,1005,1036,492,534,486,532,489,534,488,535,488,530,491,530,502,521,1006,526,486,538,483,1050,486,530,490,534,488,530,491,534,487,531,490,551,470,534,488,532,489,536,485,535,487,533,488,535,486,551,470,531,491,536,486,528,1009.
100E0000 Write-Data Maximum relative modulation level: 0.00
487,1039,495,529,492,544,478,533,489,535,486,533,488,536,485,535,487,532,489,534,1003,530,484,537,491,1037,491,532,1004,1040,488,531,490,533,488,532,489,533,490,528,493,533,488,532,489,534,487,534,487,535,487,532,489,533,489,532,489,533,488,536,1001.
00390000 Read-Data Max CH water setpoint: 0.00
481,532,489,1044,491,530,490,535,486,534,488,534,487,533,527,490,492,536,486,534,487,534,488,532,489,533,488,538,484,534,487,531,490,531,490,531,490,537,484,538,484,528,493,537,1000,1038,488,534,488,536,485,560,461,534,488,534,487,530,491,532,490,535,1002.
80000200 Read-Data Status: 00000010 00000000
479,539,482,1045,490,537,484,534,487,534,488,536,485,532,489,537,485,532,489,534,487,536,485,536,515,505,487,532,489,535,486,537,485,536,485,533,488,531,491,533,488,532,489,533,1005,1039,489,532,488,531,490,537,484,534,512,0,31,476,490,527,494,529,492,594,943.
Error 01
480,538,483,1048,487,533,488,532,489,536,485,533,488,535,487,532,489,544,478,532,488,532,489,532,490,533,487,532,489,535,486,538,484,533,495,527,487,535,486,536,485,535,486,534,1003,1039,488,532,489,535,486,531,490,531,490,536,486,536,485,537,484,554,983.
80000200 Read-Data Status: 00000010 00000000
478,536,485,1045,490,535,486,531,490,534,488,533,488,531,490,534,488,530,491,530,491,533,488,533,516,506,487,532,489,535,487,534,487,533,488,534,488,535,486,533,489,535,486,535,1002,1036,491,531,490,533,488,533,488,532,490,532,489,526,495,526,495,597,940.
80000200 Read-Data Status: 00000010 00000000
478,539,483,1049,486,533,488,532,489,534,488,532,489,534,487,534,488,545,477,533,488,532,489,531,490,536,485,530,492,532,489,532,489,534,494,528,487,532,490,532,489,531,490,536,1001,1038,489,546,475,531,491,536,485,531,490,537,485,533,488,535,486,554,983.
80000200 Read-Data Status: 00000010 00000000
481,536,485,1044,490,535,486,533,488,534,487,533,488,533,489,533,488,532,489,533,488,536,485,535,515,503,490,533,488,531,490,533,488,530,491,532,490,534,486,535,487,533,487,534,1003,1039,488,534,487,532,489,532,489,534,487,529,492,524,497,526,495,597,939.
80000200 Read-Data Status: 00000010 00000000
478,540,481,1048,487,530,490,533,490,532,488,535,486,534,487,535,487,528,494,532,489,531,490,536,485,533,489,532,489,536,486,530,490,532,496,530,485,534,488,530,491,531,490,536,1001,1040,487,533,489,533,488,533,488,534,487,531,490,534,488,533,488,552,985.
80000200 Read-Data Status: 00000010 00000000
481,537,484,1046,489,534,487,531,490,535,486,531,491,532,489,532,490,534,487,531,490,530,491,533,518,501,490,533,488,537,485,534,487,533,488,536,486,534,488,531,489,527,495,537,1000,1036,490,532,490,532,489,533,488,535,511,0,31,477,489,523,498,527,494,596,941.
Error 01
478,536,485,1048,487,531,490,534,486,532,489,533,489,531,490,533,488,545,476,529,492,532,489,532,489,532,489,529,492,530,491,534,487,533,494,526,489,533,488,533,488,534,487,533,1004,1038,488,545,476,534,487,534,487,537,486,533,487,535,486,533,488,554,983.
80000200 Read-Data Status: 00000010 00000000
479,539,482,1046,488,534,488,533,488,531,490,532,489,532,489,533,489,527,494,533,487,535,486,534,517,503,488,532,489,535,486,536,486,533,488,535,486,533,488,534,487,534,488,532,1004,1036,490,531,490,534,487,531,490,532,489,531,490,523,498,524,497,593,943.
80000200 Read-Data Status: 00000010 00000000
482,538,483,1047,488,530,491,533,489,531,490,531,490,534,487,535,486,544,478,532,489,532,489,534,488,533,488,534,487,531,490,531,490,532,496,527,487,532,490,531,490,534,487,534,1004,1036,491,544,477,537,485,536,485,533,489,533,488,534,487,536,486,554,983.
80000200 Read-Data Status: 00000010 00000000
479,540,482,1047,488,533,488,533,489,532,489,534,488,533,488,534,489,531,490,534,487,532,490,531,519,504,489,533,488,534,487,532,490,534,487,536,486,535,486,533,489,531,490,532,1005,1040,488,533,488,533,488,533,489,536,485,531,491,526,495,527,495,593,943.
80000200 Read-Data Status: 00000010 00000000
483,536,485,1048,487,532,489,532,489,535,487,534,487,532,489,534,487,530,493,528,492,533,488,535,487,532,488,535,487,534,488,530,490,533,495,526,489,533,488,532,489,534,488,531,1006,1037,489,533,489,532,489,530,491,533,488,530,492,534,487,536,485,555,982.
80000200 Read-Data Status: 00000010 00000000
478,540,482,1046,489,533,488,535,486,533,489,530,491,535,486,534,488,531,490,538,483,533,488,531,519,502,491,532,489,533,488,533,488,534,487,534,487,537,485,534,487,527,494,533,1004,1037,490,534,487,532,490,533,488,537,508,0,31,475,491,525,496,527,494,597,940.
Error 01
484,536,485,1045,490,533,488,534,488,533,488,531,490,531,490,532,490,543,478,532,489,532,489,538,484,529,492,530,491,532,490,533,488,531,497,524,490,534,487,530,492,532,489,534,1003,1039,488,545,476,532,490,531,490,532,489,532,490,533,488,536,486,551,986.
80000200 Read-Data Status: 00000010 00000000
481,537,485,1045,490,533,487,533,488,533,488,537,485,536,485,531,491,532,489,533,488,527,494,534,515,500,493,533,488,534,488,533,489,529,491,534,487,533,488,535,487,531,490,532,1005,1040,487,530,491,535,488,530,490,535,486,529,492,524,498,526,494,597,939.
80000200 Read-Data Status: 00000010 00000000
483,540,482,1043,490,533,489,534,487,534,486,533,489,533,488,532,489,545,477,531,489,532,490,528,493,533,488,534,487,531,489,532,489,536,492,525,489,531,490,532,490,532,488,531,1006,1036,491,543,477,534,488,532,489,532,489,535,487,531,489,535,486,551,986.
80000200 Read-Data Status: 00000010 00000000
481,536,486,1045,489,534,487,529,492,533,488,532,489,533,489,533,488,531,490,534,487,535,486,536,513,502,491,532,489,534,487,530,491,532,490,534,487,532,489,530,491,529,492,533,1004,1039,487,532,489,535,486,535,487,533,488,527,494,525,496,528,493,594,942.
80000200 Read-Data Status: 00000010 00000000
483,540,481,1048,487,531,490,537,484,532,490,533,488,532,489,531,490,533,491,531,489,532,488,533,489,532,489,531,490,534,487,534,487,532,496,527,487,533,489,533,488,532,489,534,1004,1037,488,535,486,531,490,536,485,533,489,530,491,533,488,533,488,553,984.
80000200 Read-Data Status: 00000010 00000000
482,536,485,1046,489,537,484,536,486,532,488,531,490,533,489,532,489,533,488,534,487,531,490,533,516,504,489,534,487,534,487,534,487,533,488,535,486,534,487,534,487,526,496,531,1005,1041,486,533,488,531,490,532,489,531,502,519,491,523,498,527,494,596,940.
80000200 Read-Data Status: 00000010 00000000
483,538,483,1049,486,533,488,534,487,536,486,532,489,533,488,532,490,546,476,534,486,533,488,533,489,532,489,535,486,535,487,533,487,532,496,527,488,535,487,531,490,533,488,532,1005,1041,486,547,474,533,489,532,489,533,488,534,488,531,490,532,489,550,987.
80000200 Read-Data Status: 00000010 00000000
481,537,484,1046,489,534,488,531,490,536,486,529,492,532,489,534,488,529,491,531,490,529,492,533,517,503,490,533,488,535,486,534,487,532,489,535,487,532,489,531,490,532,490,533,1004,1040,487,532,489,533,488,533,489,533,488,532,490,525,496,527,494,599,938.
80000200 Read-Data Status: 00000010 00000000
481,538,484,1047,487,536,486,534,487,533,488,532,490,532,489,531,490,544,478,535,486,535,486,532,489,532,490,531,490,532,489,532,489,532,496,525,490,534,487,533,489,532,489,534,1003,1039,488,544,477,535,486,533,489,531,490,536,485,531,490,534,488,549,988.
80000200 Read-Data Status: 00000010 00000000
481,537,484,1046,489,535,487,533,488,532,489,533,488,533,489,534,488,531,490,532,489,534,487,534,517,501,491,534,487,531,490,535,487,530,491,534,488,534,487,536,485,529,492,533,1005,1038,489,533,488,532,489,532,489,534,488,530,491,524,497,528,494,593,943.
80000200 Read-Data Status: 00000010 00000000
481,537,484,1049,486,533,488,536,486,529,492,533,488,532,490,532,489,533,491,530,490,533,488,532,489,530,491,531,490,533,488,534,488,531,497,526,488,533,489,534,487,534,488,530,1007,1039,487,531,491,534,487,533,488,532,490,530,491,537,485,536,485,552,985.
80000200 Read-Data Status: 00000010 00000000
481,535,486,1045,490,534,487,531,491,533,488,531,490,534,488,536,486,533,489,530,490,532,490,533,518,502,489,534,488,532,489,532,489,531,491,531,490,533,489,531,490,531,490,535,1003,1040,486,535,486,534,488,534,487,535,511,0,31,475,491,525,496,525,497,594,942.
Error 01
479,539,482,1045,490,536,485,531,492,531,489,532,489,533,489,536,485,543,479,533,488,533,489,531,490,531,490,534,487,530,493,533,487,531,497,528,487,534,487,533,488,534,487,533,1005,1036,490,549,472,532,490,532,489,531,491,533,488,533,489,535,486,552,985.
80000200 Read-Data Status: 00000010 00000000
482,541,480,1046,489,534,488,534,487,533,489,534,488,531,489,535,488,527,494,530,491,532,489,532,519,505,487,531,490,535,486,533,489,533,488,534,488,537,484,532,490,534,488,533,1004,1039,488,530,491,534,488,531,490,533,488,533,489,523,498,526,496,594,942.
80000200 Read-Data Status: 00000010 00000000
480,537,484,1046,489,533,488,534,488,532,490,533,488,532,490,531,490,543,479,532,488,535,487,533,488,530,492,533,488,533,488,535,486,531,497,527,488,533,488,536,486,534,487,534,1003,1041,487,543,478,532,489,532,489,532,490,534,487,533,488,533,489,551,986.
80000200 Read-Data Status: 00000010 00000000
479,539,483,1046,489,536,485,535,487,534,488,531,490,532,490,534,487,529,493,534,487,531,490,535,515,505,488,533,488,534,488,532,489,534,488,535,486,533,489,532,489,531,491,531,1006,1037,490,534,488,537,484,534,488,533,489,528,493,524,497,524,498,592,944.
80000200 Read-Data Status: 00000010 00000000
481,537,484,1048,487,535,486,532,489,531,490,534,488,531,490,533,488,528,496,529,490,531,490,534,487,533,488,532,489,534,488,534,487,532,496,523,491,531,490,533,489,531,490,534,1004,1039,487,531,490,535,487,533,488,530,491,529,493,531,490,535,486,554,983.
80000200 Read-Data Status: 00000010 00000000
481,536,485,1048,488,532,489,531,490,532,489,538,484,531,490,531,491,530,491,532,489,532,489,531,520,499,493,531,490,531,490,534,488,531,490,530,491,531,491,529,492,524,497,533,1005,1036,490,530,491,531,491,534,487,535,511,256,65311,474,492,526,495,526,496,592,944.
Error 01
480,540,481,1045,490,536,486,532,489,530,492,534,487,532,490,533,488,544,478,530,491,535,487,532,489,531,490,534,487,534,488,532,489,536,492,524,491,535,486,534,488,534,487,531,1006,1038,489,545,476,531,491,538,483,532,489,533,488,534,487,533,489,549,988.
80000200 Read-Data Status: 00000010 00000000
480,536,486,1045,490,532,489,531,490,531,491,529,491,530,492,533,489,530,491,534,487,531,490,533,516,504,489,533,488,531,491,531,490,530,491,533,489,532,489,532,490,535,486,533,1004,1038,489,529,492,534,488,532,489,533,488,530,492,525,496,525,496,596,941.
80000200 Read-Data Status: 00000010 00000000
481,537,485,1044,491,533,488,533,489,533,488,533,489,532,489,532,489,542,481,532,489,532,489,533,488,531,491,532,489,533,488,534,488,535,493,524,491,531,490,535,487,534,487,534,1004,1039,488,550,472,532,490,533,488,532,490,532,489,531,491,534,487,551,987.
80000200 Read-Data Status: 00000010 00000000
482,538,483,1045,490,534,488,533,489,530,491,532,490,532,490,530,492,530,491,532,489,534,488,531,520,503,489,536,485,530,492,529,492,531,490,538,484,533,488,536,486,529,492,535,1003,1037,490,532,490,533,488,533,488,537,485,530,491,525,497,527,494,593,944.
80000200 Read-Data Status: 00000010 00000000
481,538,483,1045,490,534,488,535,486,536,486,533,488,534,487,533,489,531,492,531,489,529,492,536,486,533,488,536,486,537,484,534,488,531,496,526,489,534,488,534,487,534,488,531,1006,1041,486,533,488,534,488,534,487,532,490,531,490,536,486,531,490,550,987.
80000200 Read-Data Status: 00000010 00000000
483,537,486,1045,489,533,488,531,490,534,488,534,487,533,489,534,488,529,492,533,489,533,488,528,521,504,489,533,489,532,489,530,493,534,486,535,487,531,490,534,488,528,493,533,1004,1037,490,532,489,536,486,534,487,533,513,0,31,475,491,525,496,526,495,596,941.
Error 01
480,540,481,1048,487,535,487,530,491,533,488,534,488,533,488,537,485,543,479,532,489,534,488,531,490,534,487,535,487,535,486,531,490,535,493,526,489,537,484,532,490,533,488,532,1005,1035,492,547,475,532,490,533,488,530,491,534,487,533,489,534,487,553,984.
80000200 Read-Data Status: 00000010 00000000
482,535,486,1046,489,531,490,532,489,533,489,536,486,533,488,534,488,529,492,532,489,535,487,534,515,502,491,535,487,532,489,532,491,532,488,533,489,530,491,533,489,535,486,535,1003,1039,487,529,493,532,490,533,488,530,491,531,491,525,496,526,496,597,939.
80000200 Read-Data Status: 00000010 00000000
483,534,488,1046,489,532,490,534,487,534,488,532,489,533,489,535,486,546,477,531,490,534,487,532,489,533,489,533,488,534,487,534,488,533,495,525,490,533,488,532,490,534,487,530,1007,1037,490,547,475,532,489,531,491,533,488,536,486,533,488,536,485,552,985.
80000200 Read-Data Status: 00000010 00000000
482,1046,488,532,490,529,1008,1040,487,535,487,533,489,531,490,533,489,534,487,530,491,532,490,530,492,532,489,535,1002,1041,1002,1035,492,533,1004,1039,1004,531,483,1048,488,532,489,532,490,531,490,533,489,532,489,533,489,531,1048,256,65312.
Error 01
481,540,482,1047,489,530,1006,1038,489,533,489,534,487,532,490,531,490,533,489,530,492,531,1006,521,492,538,483,1046,502,518,491,532,490,533,1004,530,484,1050,1000,1040,488,532,489,531,490,534,488,535,486,533,489,535,486,538,484,532,1005.
900E1A00 Write-Data Maximum relative modulation level: 26.00
481,1047,488,533,489,533,489,532,489,532,490,534,488,535,487,532,489,530,492,532,489,531,491,531,519,502,491,533,488,535,487,533,489,532,489,537,485,533,489,534,488,534,487,534,1004,532,481,1047,488,535,487,532,490,534,487,528,494,523,498,526,496,595,942.
00000300 Read-Data Status: 00000011 00000000
480,1047,488,534,488,531,490,533,489,531,491,533,488,534,488,534,487,531,493,531,489,533,489,533,488,533,489,534,488,534,487,535,487,533,495,522,493,532,490,532,490,534,487,534,1004,531,482,1048,488,531,491,532,489,530,492,530,491,534,488,534,488,551,987.
00000300 Read-Data Status: 00000011 00000000
480,1044,502,521,489,533,489,534,488,532,489,532,490,530,492,532,490,530,491,532,489,531,490,533,518,501,491,530,492,529,492,533,489,535,486,536,486,538,483,533,489,529,492,532,1005,527,487,1047,488,535,486,531,491,534,512,0,31,475,491,525,496,531,491,596,941.
Error 01
482,1045,490,532,490,535,486,535,487,529,492,536,486,531,490,532,490,543,479,531,490,536,485,533,488,531,490,532,490,534,487,532,490,532,496,524,491,532,489,532,489,531,490,532,1005,535,479,1062,472,534,488,532,490,533,488,530,492,530,491,533,489,551,986.
00000300 Read-Data Status: 00000011 00000000
484,1047,487,535,487,531,490,529,492,533,488,533,488,535,487,531,491,531,490,532,489,531,490,533,516,503,490,532,490,533,488,533,489,532,488,535,486,531,490,531,491,529,492,531,1005,528,486,1044,490,530,492,531,490,535,486,531,490,525,497,526,494,596,941.
00000300 Read-Data Status: 00000011 00000000
482,1045,490,534,487,534,487,529,493,531,491,532,488,532,490,533,488,544,479,532,489,531,490,533,488,536,486,531,490,534,487,534,487,532,496,529,486,531,491,530,491,534,487,532,1005,531,483,1058,476,536,486,534,487,532,490,531,490,534,488,533,488,550,987.
00000300 Read-Data Status: 00000011 00000000
480,1045,504,519,489,534,487,535,487,532,489,533,488,535,487,532,490,528,494,530,491,533,488,533,517,502,492,534,487,533,490,531,489,531,491,533,489,536,486,533,488,532,490,533,1004,532,482,1047,488,533,489,533,488,537,485,527,494,525,497,524,498,595,941.
00000300 Read-Data Status: 00000011 00000000
479,1047,489,530,491,534,488
Code: Select all
Opentherm gateway diagnostics - Version 2.0
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 3
20,1246,65300,1257,65300,1257,65300,1002,20,1001,20,1002,20,1002,20,1001,20,1001,20,1001,20,1286,65300,973,20,1002,20,1001,20,1002,20,1001,20,1002,20,1001,20,1001,20,1002,20,1517,20,994,20,1515,20,1001,20,1002,20,1013,20,989,20,1002,20,1001,20,1517,20,61030,517,1052,1040,1052,518,528,518,528,518,528,519,528,517,528,518,528,518,528,518,529,518,528,518,529,517,529,517,528,518,529,518,528,518,529,518,528,518,528,519,529,518,528,1042,528,519,1052,517,528,518,529,517,528,518,528,518,529,1042,15908,0.
Error 01
20,1001,20,1001,20,1002,20,1001,20,1001,20,1002,20,1002,20,1002,20,1001,20,1001,20,1001,20,1001,20,1002,20,1001,20,1001,20,1008,20,994,20,1002,20,1001,20,1001,20,1517,20,993,20,1515,20,1002,20,1001,20,1257,65300,1258,65300,1257,65300,1258,65300,1773,65300,47738,517,1052,1042,1051,518,528,518,529,518,528,518,527,518,528,518,528,518,528,517,529,518,528,518,529,518,527,518,528,518,528,518,529,517,529,517,528,518,529,518,528,518,529,1041,528,518,1051,518,529,518,528,518,528,518,529,518,529,1041,14787,0.
Error 01
20,1001,20,1002,20,1001,20,1001,20,1002,20,1002,20,1001,20,1001,20,1002,20,1001,20,1029,20,973,20,1002,20,1001,20,1002,20,1001,20,1002,20,1001,20,1002,20,1002,20,1517,20,993,20,1515,20,1002,20,1001,20,1002,20,1001,20,1002,20,1001,20,1517,20,33772,518,1052,1041,1051,518,528,518,529,518,528,519,529,518,528,518,528,518,529,518,528,518,528,519,528,519,528,518,528,518,528,518,527,518,528,518,529,518,528,518,528,518,528,1042,528,519,1052,519,528,518,528,518,528,519,529,518,529,1042,14289,0.
Error 01
20,1001,20,1001,20,1001,20,1002,20,1001,20,1001,20,1001,20,1003,20,1001,20,1001,20,1001,20,1002,20,1001,20,1001,20,1001,20,1009,20,995,20,1001,20,1001,20,1002,20,1517,20,993,20,1515,20,1002,20,1001,20,1002,20,1001,20,1002,20,1001,20,1518,20.
Error 01
518,1052,1041,1052,518,528,518,529,518,529,518,529,518,529,518,529,518,529,518,529,518,528,518,528,518,529,518,528,518,528,518,528,518,529,518,529,518,528,518,529,518,528,1042,528,518,1052,518,528,518,529,519,529,518,529,518,529,1042,1052,1042.
40000302 Read-Ack Status: 00000011 00000010
20,1243,65300,1258,65300,1258,65300,1257,65300,1257,65300,1258,65300,1258,65300,1001,20,1001,20,1002,20,1285,65300,974,20,1001,20,1002,20,1001,20,1002,20,1001,20,1002,20,1001,20,1002,20,1517,20,993,20,1516,20,1001,20,1001,20,1002,20,1001,20,1001,20,1002,20,1516,20.
Error 01
517,1051,1040,1051,518,529,518,528,517,528,518,528,518,528,518,527,518,529,518,528,518,528,518,529,518,529,518,528,518,528,518,529,518,528,518,529,518,528,519,528,518,528,1041,528,517,1052,517,528,518,529,518,529,517,528,519,528,1042,1052,1041,41333,20,1001,20,1518,20,1507,20,1002,20,1001,20,1002,20,1001,20,1002,20,1001,20,1001,20,1002,20,1001,20,1518,20,2023,20,1507,20,1518,20,2023,20,992,20,1515,20,1002,20,1001,20,1002,20,1002,20,1001,20,1001,20,1518,20,37232,517,528,518,529,518,24064,0,0,0,0,0,0,00,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,00,0,0,0,0,0,0,0,0,0,0,0,0.
Error 03
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
Opentherm gateway diagnostics - Version 2.0
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 3
924,8,1013,8,1014,7,1014,8,1014,8,1033,7,6770.
Error 03
5899.
20,1000,20,1002,20,1001,20,1001,20,1002,20,1001,20,1001,20,1002,20,1000,20,1001,20,1030,20,973,20,1002,20,1001,20,1001,20,1001,20,1001,20,1001,20,1002,20,1001,20,1518,20,993,20,1515,20,1001,20,1001,20,1002,20,1001,20,1002,20,1001,20,1517,20.
Error 01
517,529,518,528,519,1051,518,528,518,529,517,529,518,528,518,528,518,528,518,529,518,528,518,529,518,529,518,529,518,529,518,528,518,529,518,528,518,529,518,528,518,529,519,528,1042,528,518,1053,518,528,518,529,518,529,1042,1052,1041,1052,1041.
C000030A Read-Ack Status: 00000011 00001010
20,1002,20,1001,20,1002,20,1001,20,1002,20,1001,20,1002,20,1002,20,1001,20,1001,20,1002,20,1000,20,1002,20,1002,20,1001,20,1008,20,995,20,1001,20,1002,20,1001,20,1518,20,993,20,1515,20,1001,20,1001,20,1001,20,1002,20,1001,20,1002,20,1517,20.
Error 01
517,529,518,529,518,1052,518,528,518,529,518,528,519,529,518,528,518,529,518,529,518,529,518,528,518,528,518,528,518,529,518,528,518,528,517,529,517,529,518,529,518,528,518,529,1041,528,518,1052,518,529,518,528,518,529,1042,1052,1041,1052,1041.
C000030A Read-Ack Status: 00000011 00001010
20,1001,20,1001,20,1001,20,1001,20,1002,20,1001,20,1002,20,1001,20,1001,20,1001,20,1030,20,973,20,1002,20,1001,20,1001,20,1002,20,1001,20,1001,20,1002,20,1001,20,1517,20,993,20,1515,20,1001,20,1001,20,1013,20,989,20,1001,20,1002,20,1517,20,58989,518,529,519,529,519,1052,518,529,519,529,519,529,519,529,519,529,518,529,519,529,519,530,518,529,519,529,519,530,519,529,518,529,519,529,518,529,519,529,518,529,519,529,519,529,1042,529,519,1053,519,529,519,529,518,529,1041,1053,1042,24962,0.
Error 01
20,1001,20,1002,20,1001,20,1002,20,1001,20,1002,20,1001,20,1003,20,1000,20,1001,20,1002,20,1001,20,1001,20,1001,20,1004,20,1006,20,995,20,1001,20,1001,20,1002,20,1517,20,994,20,1514,20,1002,20,1001,20,1001,20,1002,20,1001,20,1003,20,1516,20,44639,518,529,518,528,519,1052,518,530,518,529,519,529,519,529,519,529,518,529,518,529,518,529,518,529,518,529,518,529,518,529,519,529,519,528,519,529,518,529,518,529,519,529,518,529,1042,529,518,1052,519,529,518,529,518,529,1042,1052,1042,24924,0.
Error 01
20,1001,20,1002,20,1001,20,1001,20,1002,20,1002,20,1001,20,1001,20,1001,20,1002,20,1030,20,972,20,1002,20,1001,20,1002,20,1001,20,1002,20,1001,20,1002,20,1001,20,1518,20,993,20,1515,20,1002,20,1001,20,1001,20,1002,20,1001,20,1002,20,1517,20,29183,518,529,519,529,519,1053,519,529,519,529,519,529,518,530,519,529,519,529,519,529,519,529,519,529,518,529,518,529,519,529,518,529,518,529,519,529,518,529,519,529,518,530,518,529,1041,529,519,1052,519,529,519,529,518,529,1043,1054,1042,25856,0.
Error 01
20,1002,20,1001,20,1002,20,1001,20,1002,20,1001,20,1002,20,1002,20,1001,20,1001,20,1002,20,1001,20,1001,20,1001,20,1002,20,1008,20,994,20,1002,20,1001,20,1002,20,1517,20,993,20,1514,20,1002,20,1001,20,1002,20,1001,20,1001,20,1002,20,1518,20.
Error 01
517,529,517,529,518,1052,518,529,518,528,518,529,518,529,518,528,518,529,518,529,518,529,518,528,518,528,519,528,519,528,518,529,518,528,519,528,518,529,518,528,519,528,518,528,1041,528,518,1051,519,528,518,529,518,529,1041,1052,1041,1052,1041.
C000030A Read-Ack Status: 00000011 00001010
20,981,20,1002,20,1001,20,1002,20,1002,20,1002,20,1002,20,1001,20,1258,65300,1257,65300,1030,20,1230,65300,1257,65300,1259,65300,1256,65300,1258,65300,1001,20,1003,20,1001,20,1002,20,1517,20,993,20,1516,20,1001,20,1002,20,1002,20,1001,20,1001,20,1002,20,1517,20.
Error 01
517,528,518,528,518,1051,518,528,518,529,518,529,518,528,518,528,518,528,518,528,518,529,518,528,519,528,518,528,519,528,518,528,519,529,518,528,518,529,518,529,518,529,518,528,1041,529,518,1052,518,529,518,528,518,529,1042,1051,1041,1052,1041.
C000030A Read-Ack Status: 00000011 00001010
20,1002,20,1002,20,1001,20,1002,20,1001,20,1001,20,1002,20,1003,20,1001,20,1001,20,1001,20,1002,20,1002,20,1001,20,1002,20,1008,20,995,20,1002,20,1001,20,1002,20,1518,20,993,20,1515,20,1002,20,1001,20,1002,20,1001,20,1001,20,1002,20,1518,20,59691,517,529,518,528,519,1052,518,528,518,529,518,528,518,529,518,528,518,528,518,529,518,529,518,528,518,529,518,528,519,528,518,528,519,528,518,529,518,528,518,529,518,529,518,528,1041,529,518,1052,518,528,518,528,518,529,1041,1052,1042,17322,0.
Error 01
65300,984,20,1002,20,1001,20,1001,20,1002,20,1002,20,1002,20,1001,20,1002,20,1001,20,1029,20,973,20,1002,20,1001,20,1004,20,1000,20,1001,20,1002,20,1002,20,1001,20,1518,20,993,20,1515,20,1002,20,1002,20,1013,20,990,20,1001,20,1002,20,1518,20,45957,518,529,518,528,518,1052,518,529,518,528,518,529,518,528,518,529,519,528,518,529,518,529,518,528,518,528,519,528,518,529,519,528,519,528,518,527,518,529,518,528,518,529,518,529,1041,529,518,1052,518,528,518,529,518,529,1042,1053,1041,16396,0.
Error 03
20,1000,20,1002,20,1001,20,1002,20,1257,65300,1258,65300,1257,65300,1258,65300,1257,65300,1257,65300,1257,65300,1001,20,1002,20,1001,20,1002,20,1008,20,994,20,1002,20,1001,20,1001,20,1518,20,993,20,1515,20,1001,20,1001,20,1002,20,1001,20,1001,20,1002,20,1518,20,31787,517,528,518,528,518,1052,518,528,519,528,518,528,518,528,518,528,518,528,518,528,518,529,518,529,518,528,519,528,518,528,519,528,519,528,518,529,518,528,517,529,518,528,518,528,1042,528,518,1053,517,529,518,529,519,528,1041,1052,1041,16199,0.
Error 01
20,1001,20,1002,20,1001,20,1001,20,1002,20,1001,20,1002,20,1001,20,1001,20,1001,20,1030,20,973,20,1001,20,1001,20,1003,20,1000,20,1001,20,1002,20,1001,20,1002,20,1517,20,993,20,1516,20,1002,20,1000,20,1001,20,1002,20,1002,20,1001,20,1517,20.
Error 01
517,528,518,528,517,1051,518,529,517,529,517,529,518,528,518,528,518,528,518,528,518,529,518,528,518,529,518,529,518,528,518,529,518,529,518,528,519,528,518,528,518,529,518,528,1042,529,518,1051,518,528,518,529,518,528,1042,1052,1041,1051,1042.
C000030A Read-Ack Status: 00000011 00001010
20,1001,20,1002,20,1001,20,1002,20,1001,20,1002,20,1002,20,1002,20,1001,20,1002,20,1001,20,1001,20,1002,20,1002,20,1001,20,1008,20,995,20,1002,20,1001,20,1001,20,1518,20,993,20,1516,20,1001,20,1002,20,1001,20,1003,20,1000,20,1002,20,1518,20.
Error 01
518,528,518,529,518,1051,518,528,518,529,518,528,518,528,518,529,517,529,518,528,518,529,518,528,518,529,518,528,518,529,518,529,518,529,518,528,518,529,518,529,518,529,518,528,1042,528,518,1053,517,529,518,528,518,529,1040,1052,1041,1052,1041.
C000030A Read-Ack Status: 00000011 00001010
20,988,20,1001,20,1003,20,1001,20,1002,20,1001,20,1002,20,1002,20,1001,20,1001,20,1030,20,974,20,1001,20,1003,20,1000,20,1002,20,1001,20,1002,20,1002,20,1001,20,1518,20,994,20,1515,20,1002,20,1001,20,1002,20,1002,20,1001,20,1002,20,1517,20,60108,517,529,518,528,519,1052,519,528,519,528,519,528,519,528,519,529,518,528,517,529,518,529,518,528,519,528,518,529,518,529,518,528,519,528,518,529,518,528,518,529,518,529,518,528,1042,528,518,1052,518,529,518,528,519,529,1041,1052,1041,9742,0,0,0,0,0,0,00,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,00,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,00,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0,0.
Error 01
Code: Select all
pentherm gateway diagnostics - Version 2.0
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number:
5
Power supply: 4.993
Reference: 1.482
Thermostat: 0.906, 1.038, 2.213
Boiler: 0.000, 2.803, 2.808
Opentherm gateway diagnostics - Version 2.0
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 6
T: 902.104
B: 82.558
T: 847.695
B: 69.249
T: 860.990
B: 53.195
T: 877.195
B: 41.203
T: 889.041
B: 28.078
T: 902.216
B: 83.944
T: 846.262
B: 70.157
T: 860.225
B: 55.754
T: 874.495
B: 41.980
T: 888.506
B: 28.681
T: 901.790
B: 84.826
- Attachments
-
- logs.zip
- (14.67 KiB) Downloaded 185 times
Last edited by adriansmares on Tue Apr 26, 2022 11:55 pm, edited 1 time in total.
Re: Nefit ProLine NxT + Nefit ModuLine 1010
I also expected something very different from test 2. Somehow the thermostat detects a difference between the diagnostic firmware and the gateway firmware in monitor mode. I don't have a clue how that is possible. In both cases the comparators are configured to pass through the signal unmodified. I have no ideas how to continue from here without specialist equipment.
Schelte
-
- Starting Member
- Posts: 2
- Joined: Sun Apr 24, 2022 1:09 pm
Re: Nefit ProLine NxT + Nefit ModuLine 1010
That's fine, thanks a lot. I don't have any ideas left for now either and also this thermostat is very basic, I cannot even override the temperature remotely as it does not implement the temperature override reading. Since the standalone mode seems to work fine with the boiler itself, I'll probably toy with that in the meantime.
Last edited by adriansmares on Wed Apr 27, 2022 4:55 pm, edited 1 time in total.