bug in C2/H2 implementation?

This Forum is about the Opentherm gateway (OTGW) from Schelte

Moderator: hvxl

Post Reply
rpav
Starting Member
Starting Member
Posts: 31
Joined: Sun Nov 15, 2015 8:55 pm

bug in C2/H2 implementation?

Post by rpav »

Hi,
GW firmware 5.4 @P16F88
OTmonitor 6.1 @Linux-armhf

I would like to switch off both circuit of central heating. So I do the following command:
CS=19
CH=0
C2=19
H2=0

but the result is, that CS is reset (set back to 0)

Here is the log file:

Code: Select all

07:39:50.193941  T80001300  Read-Data   Status: 00010011 00000000
07:39:50.462432  BC000132A  Read-Ack    Status: 00010011 00101010
07:39:51.233557  T900121BC  Write-Data  Control setpoint: 33.73
07:39:51.586052  B500121BC  Write-Ack   Control setpoint: 33.73
07:39:52.205850  T90081AD4  Write-Data  Control setpoint 2: 26.83
07:39:52.574420  B50081AD4  Write-Ack   Control setpoint 2: 26.83
07:39:53.195697  T90383200  Write-Data  DHW setpoint: 50.00
07:39:53.564173  B50383200  Write-Ack   DHW setpoint: 50.00
07:39:54.184092  T80200000  Read-Data   DHW2 temperature: 0.00
07:39:54.218921  Command (via websocket from 192.168.111.203:53656): CS=19
07:39:54.237437  CS: 19.00
07:39:54.553422  BE0200000  Data-Inv    DHW2 temperature: 0.00
07:39:55.174687  T801A0000  Read-Data   DHW temperature: 0.00
07:39:55.543546  BC01A380C  Read-Ack    DHW temperature: 56.05
07:39:56.213417  T80001300  Read-Data   Status: 00010011 00000000
07:39:56.224431  R00001200  Read-Data   Status: 00010010 00000000
07:39:56.531882  B4000122A  Read-Ack    Status: 00010010 00101010
07:39:56.544146  AC000132A  Read-Ack    Status: 00010011 00101010
07:39:57.202692  T001B0000  Read-Data   Outside temperature: 0.00
07:39:57.521309  B401B0B88  Read-Ack    Outside temperature: 11.53
07:39:58.192433  T80190000  Read-Data   Boiler water temperature: 0.00
07:39:58.511171  BC019244C  Read-Ack    Boiler water temperature: 36.30
07:39:59.181059  T801C0000  Read-Data   Return water temperature: 0.00
07:39:59.499535  B401C1CD0  Read-Ack    Return water temperature: 28.81
07:40:00.170551  T801F0000  Read-Data   Flow temperature CH2: 0.00
07:40:00.489061  BC01F18C4  Read-Ack    Flow temperature CH2: 24.77
07:40:01.160231  T00110000  Read-Data   Relative modulation level: 0.00
07:40:01.478713  BC0110000  Read-Ack    Relative modulation level: 0.00
07:40:02.150038  T80001300  Read-Data   Status: 00010011 00000000
07:40:02.160900  R00001200  Read-Data   Status: 00010010 00000000
07:40:02.468240  B40001220  Read-Ack    Status: 00010010 00100000
07:40:02.479355  AC0001320  Read-Ack    Status: 00010011 00100000
07:40:03.189220  T80130000  Read-Data   DHW flow rate: 0.00
07:40:03.458173  B70130000  Unk-DataId  DHW flow rate: 0.00
07:40:04.178937  T001D0000  Read-Data   Solar storage temperature: 0.00
07:40:04.446312  BF01D0000  Unk-DataId  Solar storage temperature: 0.00
07:40:05.168812  T001E0000  Read-Data   Solar collector temperature: 0.00
07:40:05.436289  B601E0000  Data-Inv    Solar collector temperature: 0.00
07:40:06.155953  T00210000  Read-Data   Exhaust temperature: 0
07:40:06.425281  B40210020  Read-Ack    Exhaust temperature: 32
07:40:07.146322  T9081020E  Write-Data  Message ID 129: 526
07:40:07.414542  B5081020E  Write-Ack   Message ID 129: 526
07:40:08.135877  T80001300  Read-Data   Status: 00010011 00000000
07:40:10.724194  R00001200  Read-Data   Status: 00010010 00000000
07:40:10.806855  B40001220  Read-Ack    Status: 00010010 00100000
07:40:10.810090  AC0001320  Read-Ack    Status: 00010011 00100000
07:40:10.813083  T10101580  Write-Data  Room setpoint: 21.50
07:40:10.815314  BD0101580  Write-Ack   Room setpoint: 21.50
07:40:10.817567  T90171580  Write-Data  Room Setpoint CH2: 21.50
07:40:10.820377  B50171580  Write-Ack   Room Setpoint CH2: 21.50
07:40:11.167140  T10181590  Write-Data  Room temperature: 21.56
07:40:11.435656  BD0181590  Write-Ack   Room temperature: 21.56
07:40:12.156658  T80800000  Read-Data   Message ID 128: 0
07:40:12.425259  BE0800000  Data-Inv    Message ID 128: 0
07:40:13.146390  T10825453  Write-Data  Message ID 130: 21587
07:40:13.415009  BD0825453  Write-Ack   Message ID 130: 21587
07:40:14.134806  T80001300  Read-Data   Status: 00010011 00000000
07:40:14.147106  R00001200  Read-Data   Status: 00010010 00000000
07:40:14.404752  B40001220  Read-Ack    Status: 00010010 00100000
07:40:14.415761  AC0001320  Read-Ack    Status: 00010011 00100000
07:40:14.464518  Command (via websocket from 192.168.111.203:53656): CH=0
07:40:14.477648  CH: 0
07:40:15.124885  T900121BC  Write-Data  Control setpoint: 33.73
07:40:15.137234  R90011300  Write-Data  Control setpoint: 19.00
07:40:15.393255  B50011300  Write-Ack   Control setpoint: 19.00
07:40:15.404236  A500121BC  Write-Ack   Control setpoint: 33.73
07:40:16.114016  T90081AD4  Write-Data  Control setpoint 2: 26.83
07:40:16.382685  B50081AD4  Write-Ack   Control setpoint 2: 26.83
07:40:17.102687  T90383200  Write-Data  DHW setpoint: 50.00
07:40:17.372494  B50383200  Write-Ack   DHW setpoint: 50.00
07:40:18.142385  T80200000  Read-Data   DHW2 temperature: 0.00
07:40:18.494706  BE0200000  Data-Inv    DHW2 temperature: 0.00
07:40:19.115672  T801A0000  Read-Data   DHW temperature: 0.00
07:40:19.484370  BC01A380C  Read-Ack    DHW temperature: 56.05
07:40:20.104126  T80001300  Read-Data   Status: 00010011 00000000
07:40:20.115103  R00001200  Read-Data   Status: 00010010 00000000
07:40:20.473782  B40001220  Read-Ack    Status: 00010010 00100000
07:40:20.484760  AC0001320  Read-Ack    Status: 00010011 00100000
07:40:21.093320  T001B0000  Read-Data   Outside temperature: 0.00
07:40:21.462022  BC01B0B70  Read-Ack    Outside temperature: 11.44
07:40:22.083244  T80190000  Read-Data   Boiler water temperature: 0.00
07:40:22.451876  B401923F4  Read-Ack    Boiler water temperature: 35.95
07:40:23.121880  T801C0000  Read-Data   Return water temperature: 0.00
07:40:23.441876  BC01C1988  Read-Ack    Return water temperature: 25.53
07:40:24.111642  T801F0000  Read-Data   Flow temperature CH2: 0.00
07:40:24.430252  B401F1AF8  Read-Ack    Flow temperature CH2: 26.97
07:40:25.100307  T00110000  Read-Data   Relative modulation level: 0.00
07:40:25.420062  BC0110000  Read-Ack    Relative modulation level: 0.00
07:40:26.091241  T80001300  Read-Data   Status: 00010011 00000000
07:40:26.102246  R00001200  Read-Data   Status: 00010010 00000000
07:40:26.409674  B40001220  Read-Ack    Status: 00010010 00100000
07:40:26.420638  AC0001320  Read-Ack    Status: 00010011 00100000
07:40:27.080640  T80130000  Read-Data   DHW flow rate: 0.00
07:40:27.397948  B70130000  Unk-DataId  DHW flow rate: 0.00
07:40:28.070487  T001D0000  Read-Data   Solar storage temperature: 0.00
07:40:28.387775  BF01D0000  Unk-DataId  Solar storage temperature: 0.00
07:40:29.058769  T001E0000  Read-Data   Solar collector temperature: 0.00
07:40:29.377354  B601E0000  Data-Inv    Solar collector temperature: 0.00
07:40:30.098591  T00210000  Read-Data   Exhaust temperature: 0
07:40:30.365847  B40210020  Read-Ack    Exhaust temperature: 32
07:40:31.087093  T9081020E  Write-Data  Message ID 129: 526
07:40:31.355611  B5081020E  Write-Ack   Message ID 129: 526
07:40:32.076856  T80001300  Read-Data   Status: 00010011 00000000
07:40:32.087830  R00001200  Read-Data   Status: 00010010 00000000
07:40:32.345564  B40001220  Read-Ack    Status: 00010010 00100000
07:40:32.356450  AC0001320  Read-Ack    Status: 00010011 00100000
07:40:33.066342  T10101580  Write-Data  Room setpoint: 21.50
07:40:33.334981  BD0101580  Write-Ack   Room setpoint: 21.50
07:40:34.054866  T90171580  Write-Data  Room Setpoint CH2: 21.50
07:40:34.323457  B50171580  Write-Ack   Room Setpoint CH2: 21.50
07:40:35.044617  T10181590  Write-Data  Room temperature: 21.56
07:40:35.313344  BD0181590  Write-Ack   Room temperature: 21.56
07:40:36.083223  T80800000  Read-Data   Message ID 128: 0
07:40:36.366764  BE0800000  Data-Inv    Message ID 128: 0
07:40:37.037853  T10825453  Write-Data  Message ID 130: 21587
07:40:37.355094  BD0825453  Write-Ack   Message ID 130: 21587
07:40:38.076211  T90020004  Write-Data  Master configuration: 00000000 4
07:40:38.344972  B50020004  Write-Ack   Master configuration: 00000000 4
07:40:39.066086  T80001300  Read-Data   Status: 00010011 00000000
07:40:39.077314  R00001200  Read-Data   Status: 00010010 00000000
07:40:39.334740  B40001220  Read-Ack    Status: 00010010 00100000
07:40:39.345709  AC0001320  Read-Ack    Status: 00010011 00100000
07:40:40.055590  T900121C8  Write-Data  Control setpoint: 33.78
07:40:40.066570  R90011300  Write-Data  Control setpoint: 19.00
07:40:40.323947  B50011300  Write-Ack   Control setpoint: 19.00
07:40:40.334923  A500121C8  Write-Ack   Control setpoint: 33.78
07:40:41.044815  T90081AD8  Write-Data  Control setpoint 2: 26.84
07:40:41.313591  B50081AD8  Write-Ack   Control setpoint 2: 26.84
07:40:42.033460  T90383200  Write-Data  DHW setpoint: 50.00
07:40:42.302077  B50383200  Write-Ack   DHW setpoint: 50.00
07:40:43.023310  T80200000  Read-Data   DHW2 temperature: 0.00
07:40:43.291807  BE0200000  Data-Inv    DHW2 temperature: 0.00
07:40:44.013045  T801A0000  Read-Data   DHW temperature: 0.00
07:40:44.280423  BC01A380C  Read-Ack    DHW temperature: 56.05
07:40:45.051559  T80001300  Read-Data   Status: 00010011 00000000
07:40:45.063897  R00001200  Read-Data   Status: 00010010 00000000
07:40:45.403673  B40001220  Read-Ack    Status: 00010010 00100000
07:40:45.414691  AC0001320  Read-Ack    Status: 00010011 00100000
07:40:46.024408  T001B0000  Read-Data   Outside temperature: 0.00
07:40:46.393048  B401B0BA0  Read-Ack    Outside temperature: 11.62
07:40:47.012839  T80190000  Read-Data   Boiler water temperature: 0.00
07:40:47.382843  B40191FC8  Read-Ack    Boiler water temperature: 31.78
07:40:48.002903  T801C0000  Read-Data   Return water temperature: 0.00
07:40:48.371433  B401C1940  Read-Ack    Return water temperature: 25.25
07:40:48.991195  T801F0000  Read-Data   Flow temperature CH2: 0.00
07:40:49.361056  BC01F1A3C  Read-Ack    Flow temperature CH2: 26.23
07:40:50.032166  T00110000  Read-Data   Relative modulation level: 0.00
07:40:50.350853  BC0110000  Read-Ack    Relative modulation level: 0.00
07:40:51.020554  T80001300  Read-Data   Status: 00010011 00000000
07:40:51.031741  R00001200  Read-Data   Status: 00010010 00000000
07:40:51.339045  B40001220  Read-Ack    Status: 00010010 00100000
07:40:51.351440  AC0001320  Read-Ack    Status: 00010011 00100000
07:40:52.010041  T80130000  Read-Data   DHW flow rate: 0.00
07:40:52.328419  B70130000  Unk-DataId  DHW flow rate: 0.00
07:40:53.000812  T001D0000  Read-Data   Solar storage temperature: 0.00
07:40:53.318162  BF01D0000  Unk-DataId  Solar storage temperature: 0.00
07:40:53.989289  T001E0000  Read-Data   Solar collector temperature: 0.00
07:40:54.308037  B601E0000  Data-Inv    Solar collector temperature: 0.00
07:40:54.977917  T00210000  Read-Data   Exhaust temperature: 0
07:40:55.296408  B40210020  Read-Ack    Exhaust temperature: 32
07:40:55.967542  T9081020E  Write-Data  Message ID 129: 526
07:40:56.286146  B5081020E  Write-Ack   Message ID 129: 526
07:40:57.006072  T80001300  Read-Data   Status: 00010011 00000000
07:40:57.280306  BC0001320  Read-Ack    Status: 00010011 00100000
07:40:57.995825  T10101580  Write-Data  Room setpoint: 21.50
07:40:58.264580  BD0101580  Write-Ack   Room setpoint: 21.50
07:40:58.985816  T90171580  Write-Data  Room Setpoint CH2: 21.50
07:40:59.254416  B50171580  Write-Ack   Room Setpoint CH2: 21.50
07:40:59.974312  T10181590  Write-Data  Room temperature: 21.56
07:41:00.242941  BD0181590  Write-Ack   Room temperature: 21.56
07:41:00.964069  T80800000  Read-Data   Message ID 128: 0
07:41:01.232578  BE0800000  Data-Inv    Message ID 128: 0
07:41:01.953939  T10825453  Write-Data  Message ID 130: 21587
07:41:02.221177  BD0825453  Write-Ack   Message ID 130: 21587
07:41:02.992205  T00030000  Read-Data   Slave configuration: 00000000 0
07:41:03.275934  BC0032904  Read-Ack    Slave configuration: 00101001 4
07:41:03.945811  T80001300  Read-Data   Status: 00010011 00000000
07:41:04.264294  B40001322  Read-Ack    Status: 00010011 00100010
07:41:04.985423  T900121B0  Write-Data  Control setpoint: 33.69
07:41:05.253912  B500121B0  Write-Ack   Control setpoint: 33.69
07:41:05.975049  T90081ACC  Write-Data  Control setpoint 2: 26.80
07:41:06.243789  B50081ACC  Write-Ack   Control setpoint 2: 26.80
07:41:06.963711  T90383200  Write-Data  DHW setpoint: 50.00
07:41:07.232164  B50383200  Write-Ack   DHW setpoint: 50.00
07:41:07.953174  T80200000  Read-Data   DHW2 temperature: 0.00
07:41:08.221804  BE0200000  Data-Inv    DHW2 temperature: 0.00
07:41:08.624933  Command (via websocket from 192.168.111.203:53660): C2=19
07:41:08.644177  C2: 19.00
07:41:08.942711  T801A0000  Read-Data   DHW temperature: 0.00
07:41:09.211162  BC01A380C  Read-Ack    DHW temperature: 56.05
07:41:09.932282  T80001300  Read-Data   Status: 00010011 00000000
07:41:09.943254  R00000300  Read-Data   Status: 00000011 00000000
07:41:10.200584  BC0000322  Read-Ack    Status: 00000011 00100010
07:41:10.211551  A40001322  Read-Ack    Status: 00010011 00100010
07:41:10.921309  T001B0000  Read-Data   Outside temperature: 0.00
07:41:11.189903  B401B0B88  Read-Ack    Outside temperature: 11.53
07:41:11.961166  T80190000  Read-Data   Boiler water temperature: 0.00
07:41:12.312159  B40191D14  Read-Ack    Boiler water temperature: 29.08
07:41:12.933285  T801C0000  Read-Data   Return water temperature: 0.00
07:41:13.301792  B401C1C8C  Read-Ack    Return water temperature: 28.55
07:41:13.921689  T801F0000  Read-Data   Flow temperature CH2: 0.00
07:41:14.291579  B401F18E8  Read-Ack    Flow temperature CH2: 24.91
07:41:14.911292  T00110000  Read-Data   Relative modulation level: 0.00
07:41:15.281156  BC0110000  Read-Ack    Relative modulation level: 0.00
07:41:15.901031  T80001300  Read-Data   Status: 00010011 00000000
07:41:15.912011  R00000300  Read-Data   Status: 00000011 00000000
07:41:16.270705  B40000302  Read-Ack    Status: 00000011 00000010
07:41:16.281880  AC0001302  Read-Ack    Status: 00010011 00000010
07:41:16.940573  T80130000  Read-Data   DHW flow rate: 0.00
07:41:17.259145  B70130000  Unk-DataId  DHW flow rate: 0.00
07:41:17.930290  T001D0000  Read-Data   Solar storage temperature: 0.00
07:41:18.248901  BF01D0000  Unk-DataId  Solar storage temperature: 0.00
07:41:18.920110  T001E0000  Read-Data   Solar collector temperature: 0.00
07:41:19.237378  B601E0000  Data-Inv    Solar collector temperature: 0.00
07:41:19.908389  T00210000  Read-Data   Exhaust temperature: 0
07:41:20.227009  B40210020  Read-Ack    Exhaust temperature: 32
07:41:20.898111  T9081020E  Write-Data  Message ID 129: 526
07:41:21.216890  B5081020E  Write-Ack   Message ID 129: 526
07:41:21.886791  T80001300  Read-Data   Status: 00010011 00000000
07:41:21.897740  R00000300  Read-Data   Status: 00000011 00000000
07:41:22.206384  B40000302  Read-Ack    Status: 00000011 00000010
07:41:22.217360  AC0001302  Read-Ack    Status: 00010011 00000010
07:41:22.877395  T10101580  Write-Data  Room setpoint: 21.50
07:41:23.051605  Command (via websocket from 192.168.111.203:53660): H2=0
07:41:23.065658  H2: 0
07:41:23.195521  BD0101580  Write-Ack   Room setpoint: 21.50
07:41:23.915392  T90171580  Write-Data  Room Setpoint CH2: 21.50
07:41:24.184130  B50171580  Write-Ack   Room Setpoint CH2: 21.50
07:41:24.905270  T10181590  Write-Data  Room temperature: 21.56
07:41:25.173992  BD0181590  Write-Ack   Room temperature: 21.56
07:41:25.895017  T80800000  Read-Data   Message ID 128: 0
07:41:26.163657  BE0800000  Data-Inv    Message ID 128: 0
07:41:26.883386  T10825453  Write-Data  Message ID 130: 21587
07:41:27.151878  BD0825453  Write-Ack   Message ID 130: 21587
07:41:27.872995  T00060000  Read-Data   Remote parameter flags: 00000000 00000000
07:41:28.185562  BC0060707  Read-Ack    Remote parameter flags: 00000111 00000111
07:41:28.862787  T80001300  Read-Data   Status: 00010011 00000000
07:41:28.873753  R00000300  Read-Data   Status: 00000011 00000000
07:41:29.131127  B40000302  Read-Ack    Status: 00000011 00000010
07:41:29.142098  AC0001302  Read-Ack    Status: 00010011 00000010
07:41:29.901875  T900121BC  Write-Data  Control setpoint: 33.73
07:41:30.184374  B500121BC  Write-Ack   Control setpoint: 33.73
07:41:30.855556  T90081AD4  Write-Data  Control setpoint 2: 26.83
07:41:30.866489  R90081300  Write-Data  Control setpoint 2: 19.00
07:41:31.173730  B50081300  Write-Ack   Control setpoint 2: 19.00
07:41:31.184700  A50081AD4  Write-Ack   Control setpoint 2: 26.83
07:41:31.894638  T90383200  Write-Data  DHW setpoint: 50.00
07:41:32.163212  B50383200  Write-Ack   DHW setpoint: 50.00
07:41:32.883219  T80200000  Read-Data   DHW2 temperature: 0.00
07:41:33.153097  BE0200000  Data-Inv    DHW2 temperature: 0.00
07:41:33.872856  T801A0000  Read-Data   DHW temperature: 0.00
07:41:34.141469  BC01A380C  Read-Ack    DHW temperature: 56.05
07:41:34.862469  T80001300  Read-Data   Status: 00010011 00000000
07:41:34.873688  R00000300  Read-Data   Status: 00000011 00000000
07:41:35.130959  B40000302  Read-Ack    Status: 00000011 00000010
07:41:35.141954  AC0001302  Read-Ack    Status: 00010011 00000010
07:41:35.851878  T001B0000  Read-Data   Outside temperature: 0.00
07:41:36.120652  B401B0B88  Read-Ack    Outside temperature: 11.53
07:41:36.840487  T80190000  Read-Data   Boiler water temperature: 0.00
07:41:37.108981  B40191E84  Read-Ack    Boiler water temperature: 30.52
07:41:37.830066  T801C0000  Read-Data   Return water temperature: 0.00
07:41:38.098508  BC01C1D58  Read-Ack    Return water temperature: 29.34
07:41:38.869540  T801F0000  Read-Data   Flow temperature CH2: 0.00
07:41:39.221861  B401F1860  Read-Ack    Flow temperature CH2: 24.38
Last edited by rpav on Sun Sep 25, 2022 10:43 am, edited 1 time in total.
rpav
Starting Member
Starting Member
Posts: 31
Joined: Sun Nov 15, 2015 8:55 pm

Re: bug in C2/H2 implementation?

Post by rpav »

Hmm, it can be somewhere else.
Command (via websocket from 192.168.111.203:53656): CS=19 always ends with "timeout", but is executed. It is also very strange.
I guess that OTGW stops sending CS value do boiler. See log @07:39:51.233557
Last edited by rpav on Sun Sep 25, 2022 10:44 am, edited 1 time in total.
hvxl
Senior Member
Senior Member
Posts: 2029
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: bug in C2/H2 implamantation?

Post by hvxl »

See the changelog for version 5.2, which states: "Limit the validity of a CS command. A remotely set control setpoint expires after just over a minute. This is a safety feature to prevent runaway heating when the controlling program loses its connection, or crashes."

This deserves to be mentioned in the description of the CS command too. I will update that.

But the subject of your post refers to C2. Is your complaint that the C2 command doesn't have the same timeout? I may look into adding that.
Schelte
rpav
Starting Member
Starting Member
Posts: 31
Joined: Sun Nov 15, 2015 8:55 pm

Re: bug in C2/H2 implementation?

Post by rpav »

hvxl wrote: Sun Sep 25, 2022 9:48 am "Limit the validity of a CS command. A remotely set control setpoint expires after just over a minute. This is a safety feature to prevent runaway heating when the controlling program loses its connection, or crashes."
I see! Thank you, it is clear now.
I think that CS and C2 should behave in the same way, so yes, the same timeout should be apply for C2 as well. And customization of the timeout should be nice too. I guess that one minute timeout is too short (I would like to use cron to run the script that will do the decision about setpoint setting).

Why CS command executed via web (http://192.168.111.44:8080/command?CS=19) return "timeout" instead of CS=19?

Thank you,
Roman
hvxl
Senior Member
Senior Member
Posts: 2029
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: bug in C2/H2 implementation?

Post by hvxl »

Due to the limited resources available in the PIC, the CS command shares its timeout timer with the SC (set clock) command. Either of these commands will reset the timer. For the SC command, only a timeout of 1 minute makes sense. That's why the CS command also ended up with a timeout of 1 minute.

The timeout is actually 62.9 seconds (due to available pre- and postscaler options). So running your script via cron every minute should be fine.

I have committed a fix for the CS response from the web API in git. Thanks for reporting the issue.
Schelte
rpav
Starting Member
Starting Member
Posts: 31
Joined: Sun Nov 15, 2015 8:55 pm

Re: bug in C2/H2 implementation?

Post by rpav »

OK, all is clear now.
Thank you,
R.