Hi.
Chromotherm touch modulation thermostat.
Elga heatpump
OTGW gateway
Domoticz homeautomation
This configuration worked fine but since few days it seems thermostat get remote setpoint from domoticz as expected. Sometimes therthermostat display shows the remote-sign. Shortly thereafter thermostat takes over and set thermostat-device in Domoticz back to original thermostat setpoint?
Any suggestion how to fix this?
TIA
Bart
thermostat don't accept setpoint via homeautomation
Moderator: hvxl
Re: thermostat don't accept setpoint via homeautomation
Well, it seems that a I found a way to get rid of the unwanted behaviour by not setting values with decimal. (eg (19.5) but just 19 or 20 instead.
Re: thermostat don't accept setpoint via homeautomation
That limitation of the chromotherm touch modulation was already documented in the thermostat compatibility topic.
Schelte
Re: thermostat don't accept setpoint via homeautomation
Hi Schelte
yes sorry. I swapped iSense with Honeywell Touch Modulation and never realized about shortcomings of the latter regarding remote setpointvoverride.
Bart
yes sorry. I swapped iSense with Honeywell Touch Modulation and never realized about shortcomings of the latter regarding remote setpointvoverride.
Bart