B= AWB Thermomaster VR24T
T= Isense version 23
The smartpower function is working perfect for me.I have removed the battery's from the Isense.
After 2 weeks testing I have some strange behaviors:
I had no error1, error3 and error4 failures in version 3,4.
In version 4.0a6 I have many.
Once in a while (after a few days) I see a F203 error on the Isense. (Comunication failure)
The boiler is constanty burning.

When I give the gateway a reset (GW=R) it start funcion normal and the F203 error is gone.
I already have replaced the thermostat cable to be sure thaht one is ok.
When this F203 is presence and i reset the gateway it always start on the same point:
It always has to do with the Year.
Code: Select all
07:05:05.276618 Command: GW=R
07:05:06.442747 OpenTherm Gateway 4.0a6
07:05:06.614330 T901607DD Write-Data Year: 2013
07:05:06.717998 B70160000 Unk-DataId Year: 0
07:05:07.623001 T90150916 Write-Data Date: 9 22
07:05:07.726428 B70150000 Unk-DataId Date: 0 0
07:05:08.638446 T1002010B Write-Data Master configuration: 00000001 11
07:05:08.728238 B70020000 Unk-DataId Master configuration: 00000000 0
07:05:08.739822 AD0020000 Write-Ack Master configuration: 00000000 0
07:05:09.663009 T80000200 Read-Data Status: 00000010 00000000
07:05:09.745325 Error 03
07:05:10.790066 T80000200 Read-Data Status: 00000010 00000000
07:05:10.790563 B40000200 Read-Ack Status: 00000010 00000000
07:05:11.651051 T00030000 Read-Data Slave configuration: 00000000 0
07:05:11.814074 B40030118 Read-Ack Slave configuration: 00000001 24
07:05:12.659823 T807F0000 Read-Data Slave product version: 0 0
07:05:12.836075 Error 03
07:05:13.756531 T807F0000 Read-Data Slave product version: 0 0
07:05:13.776847 Error 03
07:05:14.675630 T807F0000 Read-Data Slave product version: 0 0
07:05:14.775063 BC07F0190 Read-Ack Slave product version: 1 144
07:05:15.683281 T00050000 Read-Data Application-specific flags: 00000000 0
07:05:16.691655 T00050000 Read-Data Application-specific flags: 00000000 0
07:05:16.794913 B40058000 Read-Ack Application-specific flags: 10000000 0
07:05:17.699669 T00060000 Read-Data Remote parameter flags: 00000000 00000000
07:05:18.706681 T00060000 Read-Data Remote parameter flags: 00000000 00000000
07:05:19.720603 T00060000 Read-Data Remote parameter flags: 00000000 00000000
07:05:19.813582 B40060301 Read-Ack Remote parameter flags: 00000011 00000001
07:05:20.723855 T80640000 Read-Data Remote override function: 00000000
07:05:20.835849 Error 03
07:05:21.731954 T80640000 Read-Data Remote override function: 00000000
07:05:21.831168 B70640000 Unk-DataId Remote override function: 00000000
07:05:21.853876 A40640000 Read-Ack Remote override function: 00000000
07:05:22.739702 T001D0000 Read-Data Solar storage temperature: 0.00
07:05:22.838860 BF01D0000 Unk-DataId Solar storage temperature: 0.00
07:05:23.756797 T00300000 Read-Data DHW setpoint boundaries: 0 0
07:05:23.849326 B40304126 Read-Ack DHW setpoint boundaries: 65 38
07:05:24.772697 T80310000 Read-Data Max CH setpoint boundaries: 0 0
07:05:24.855139 B70310000 Unk-DataId Max CH setpoint boundaries: 0 0
Maybe if you want something to know, I can help.
Regards,