- I have never had complaints from other Vision owners about it.
- My older Honeywell thermostat will even accept a setpoint of 19.37 degrees. I can't believe Honeywell would put much crappier firmware in a newer thermostat.
Opentherm Gateway
Moderator: hvxl
Re: Opentherm Gateway
If the Vision thermostat sets the room setpoint to 19.0 when requesting 19.5, it would mean that overriding the setpoint would frequently not work with this thermostat. That would surprise me for two reasons:
Schelte
Re: Opentherm Gateway
Looking at the log you sent me I see a number of strange things:
In one of the other logs I also saw that the Honeywell vision seems reluctant to accept an override setpoint. The gateway needs to send the setpoint several times before it is finally accepted.
My investigation clearly shows that the opentherm routines in the Honeywell Vision firmware differ greatly from those of the Honeywell Chronotherm. It's then also very well possible that, contrary to the Chronotherm, the Vision doesn't want to accept just any setpoint. Maybe some other Honeywell Vision owner can confirm this. And if that is the case you will just have to be careful to only specify setpoints of full degrees via the gateway. When you manually change the setpoint on the thermostat, can you only set it to full degrees too?
- All other thermostats I've seen send out opentherm messages at a steady rate of about one every second. Yours averages to almost double that, but it does so very erratically. Sometimes it sends several messages in one second and then nothing for a few seconds. However, the gap sometimes happens before a thermostat message and other times before a boiler message. That is suspicious.
- When first sending the changed setpoint to the thermostat it almost immediately repeats the request a few more times. That's OK. My thermostat does that too. But then the next time it reports the room setpoint, it's still at its old value. And one minute later that's still the case. Only after 2 minutes it finally changes the room setpoint. My Honeywell thermostat does that immediately.
- Then of course there's the point you mentioned: When instructed to go to 21.5 degrees, it only goes to 21 degrees. The gateway only allows for a 0.125 degree deviation, so 0.5 degrees is too much. In the end the gateway gives up and stops sending the remote override setpoint, resulting in the thermostat falling back to its scheduled program.
In one of the other logs I also saw that the Honeywell vision seems reluctant to accept an override setpoint. The gateway needs to send the setpoint several times before it is finally accepted.
My investigation clearly shows that the opentherm routines in the Honeywell Vision firmware differ greatly from those of the Honeywell Chronotherm. It's then also very well possible that, contrary to the Chronotherm, the Vision doesn't want to accept just any setpoint. Maybe some other Honeywell Vision owner can confirm this. And if that is the case you will just have to be careful to only specify setpoints of full degrees via the gateway. When you manually change the setpoint on the thermostat, can you only set it to full degrees too?
Schelte
Re: Opentherm Gateway
Honeywell Vision Modulation Touch
Using the thermostat you can set to .5 degree resolution. Setting Override setpoint throught he gateway will be truncated to the nearest whole degree (16.5 -> 16).
EDIT: The Vision will display an undocumented symbol.. looks like an H with a roof over it..
Using the thermostat you can set to .5 degree resolution. Setting Override setpoint throught he gateway will be truncated to the nearest whole degree (16.5 -> 16).
EDIT: The Vision will display an undocumented symbol.. looks like an H with a roof over it..
Code: Select all
15:43:51.576153 A40000B00 Read-Ack Status: 00001011 00000000
15:43:51.776761 TT: 16.50
15:43:52.008209 T80000B00 Read-Data Status: 00001011 00000000
15:43:52.011969 R00000900 Read-Data Status: 00001001 00000000
15:43:52.126414 BC0000900 Read-Ack Status: 00001001 00000000
15:43:52.130494 A40000B00 Read-Ack Status: 00001011 00000000
15:43:52.571622 T80000B00 Read-Data Status: 00001011 00000000
15:43:52.575728 R00000900 Read-Data Status: 00001001 00000000
15:43:52.681531 BC0000900 Read-Ack Status: 00001001 00000000
15:43:52.685534 A40000B00 Read-Ack Status: 00001011 00000000
15:43:53.126229 T90011900 Write-Data Control setpoint: 25.00
15:43:53.248024 B50011900 Write-Ack Control setpoint: 25.00
15:43:53.674342 T80000B00 Read-Data Status: 00001011 00000000
15:43:53.678475 R00000900 Read-Data Status: 00001001 00000000
15:43:53.795523 BC0000900 Read-Ack Status: 00001001 00000000
15:43:53.799253 A40000B00 Read-Ack Status: 00001011 00000000
15:43:54.237587 T80190000 Read-Data Boiler water temperature: 0.00
15:43:54.354781 B40191B00 Read-Ack Boiler water temperature: 27.00
15:43:54.792955 T80000B00 Read-Data Status: 00001011 00000000
15:43:54.808536 R00000900 Read-Data Status: 00001001 00000000
15:43:54.914771 BC0000900 Read-Ack Status: 00001001 00000000
15:43:54.918430 A40000B00 Read-Ack Status: 00001011 00000000
15:43:55.349562 T80000B00 Read-Data Status: 00001011 00000000
15:43:55.353286 R00000900 Read-Data Status: 00001001 00000000
15:43:55.467729 BC0000900 Read-Ack Status: 00001001 00000000
15:43:55.471716 A40000B00 Read-Ack Status: 00001011 00000000
15:43:55.901687 T80000B00 Read-Data Status: 00001011 00000000
15:43:55.905647 R00000900 Read-Data Status: 00001001 00000000
15:43:56.025894 BC0000900 Read-Ack Status: 00001001 00000000
15:43:56.030201 A40000B00 Read-Ack Status: 00001011 00000000
15:43:56.462928 T80000B00 Read-Data Status: 00001011 00000000
15:43:56.466890 R00000900 Read-Data Status: 00001001 00000000
15:43:56.580797 BC0000900 Read-Ack Status: 00001001 00000000
15:43:56.584649 A40000B00 Read-Ack Status: 00001011 00000000
15:43:57.022079 T80000B00 Read-Data Status: 00001011 00000000
15:43:57.025905 R00000900 Read-Data Status: 00001001 00000000
15:43:57.140482 BC0000900 Read-Ack Status: 00001001 00000000
15:43:57.146024 A40000B00 Read-Ack Status: 00001011 00000000
15:43:57.577246 T80000B00 Read-Data Status: 00001011 00000000
15:43:57.581539 R00000900 Read-Data Status: 00001001 00000000
15:43:57.692279 BC0000900 Read-Ack Status: 00001001 00000000
15:43:57.699822 A40000B00 Read-Ack Status: 00001011 00000000
15:43:58.130357 T90011900 Write-Data Control setpoint: 25.00
15:43:58.258364 B50011900 Write-Ack Control setpoint: 25.00
15:43:58.697031 T80000B00 Read-Data Status: 00001011 00000000
15:43:58.702230 R00000900 Read-Data Status: 00001001 00000000
15:43:58.811085 BC0000900 Read-Ack Status: 00001001 00000000
15:43:58.815378 A40000B00 Read-Ack Status: 00001011 00000000
15:43:59.287413 T80190000 Read-Data Boiler water temperature: 0.00
15:43:59.389197 B40191B00 Read-Ack Boiler water temperature: 27.00
15:43:59.834187 T80000B00 Read-Data Status: 00001011 00000000
15:43:59.838348 R00000900 Read-Data Status: 00001001 00000000
15:43:59.953195 BC0000900 Read-Ack Status: 00001001 00000000
15:43:59.957342 A40000B00 Read-Ack Status: 00001011 00000000
15:44:00.389552 T80000B00 Read-Data Status: 00001011 00000000
15:44:00.393521 R00000900 Read-Data Status: 00001001 00000000
15:44:00.511433 BC0000900 Read-Ack Status: 00001001 00000000
15:44:00.515134 A40000B00 Read-Ack Status: 00001011 00000000
15:44:00.952501 T80000B00 Read-Data Status: 00001011 00000000
15:44:00.956123 R00000900 Read-Data Status: 00001001 00000000
15:44:01.067377 BC0000900 Read-Ack Status: 00001001 00000000
15:44:01.071152 A40000B00 Read-Ack Status: 00001011 00000000
15:44:01.504543 T80000B00 Read-Data Status: 00001011 00000000
15:44:01.508438 R00000900 Read-Data Status: 00001001 00000000
15:44:01.625715 BC0000900 Read-Ack Status: 00001001 00000000
15:44:01.629497 A40000B00 Read-Ack Status: 00001011 00000000
15:44:02.065438 T80000B00 Read-Data Status: 00001011 00000000
15:44:02.069392 R00000900 Read-Data Status: 00001001 00000000
15:44:02.224783 BC0000900 Read-Ack Status: 00001001 00000000
15:44:02.230257 A40000B00 Read-Ack Status: 00001011 00000000
15:44:02.642999 T80000B00 Read-Data Status: 00001011 00000000
15:44:02.647583 R00000900 Read-Data Status: 00001001 00000000
15:44:02.759467 BC0000900 Read-Ack Status: 00001001 00000000
15:44:02.765536 A40000B00 Read-Ack Status: 00001011 00000000
15:44:03.201783 T90011900 Write-Data Control setpoint: 25.00
15:44:03.314500 B50011900 Write-Ack Control setpoint: 25.00
15:44:03.797506 T80190000 Read-Data Boiler water temperature: 0.00
15:44:03.902204 B40191B00 Read-Ack Boiler water temperature: 27.00
15:44:04.337858 T801C0000 Read-Data Return water temperature: 0.00
15:44:04.453236 B401C1A80 Read-Ack Return water temperature: 26.50
15:44:04.894917 T80000B00 Read-Data Status: 00001011 00000000
15:44:04.898823 R00000900 Read-Data Status: 00001001 00000000
15:44:05.018754 BC0000900 Read-Ack Status: 00001001 00000000
15:44:05.023737 A40000B00 Read-Ack Status: 00001011 00000000
15:44:05.453708 T80000B00 Read-Data Status: 00001011 00000000
15:44:05.457591 R00000900 Read-Data Status: 00001001 00000000
15:44:05.578204 BC0000900 Read-Ack Status: 00001001 00000000
15:44:05.582241 A40000B00 Read-Ack Status: 00001011 00000000
15:44:06.007103 T80000B00 Read-Data Status: 00001011 00000000
15:44:06.011676 R00000900 Read-Data Status: 00001001 00000000
15:44:06.122979 BC0000900 Read-Ack Status: 00001001 00000000
15:44:06.127175 A40000B00 Read-Ack Status: 00001011 00000000
15:44:06.564081 T80000B00 Read-Data Status: 00001011 00000000
15:44:06.568211 R00000900 Read-Data Status: 00001001 00000000
15:44:06.683253 BC0000900 Read-Ack Status: 00001001 00000000
15:44:06.687169 A40000B00 Read-Ack Status: 00001011 00000000
15:44:07.122138 T80000B00 Read-Data Status: 00001011 00000000
15:44:07.126043 R00000900 Read-Data Status: 00001001 00000000
15:44:07.241199 BC0000900 Read-Ack Status: 00001001 00000000
15:44:07.245371 A40000B00 Read-Ack Status: 00001011 00000000
15:44:07.678343 T80000B00 Read-Data Status: 00001011 00000000
15:44:07.682179 R00000900 Read-Data Status: 00001001 00000000
15:44:07.797532 BC0000900 Read-Ack Status: 00001001 00000000
15:44:07.801757 A40000B00 Read-Ack Status: 00001011 00000000
15:44:08.236573 T90011900 Write-Data Control setpoint: 25.00
15:44:08.355664 B50011900 Write-Ack Control setpoint: 25.00
15:44:08.795459 T80190000 Read-Data Boiler water temperature: 0.00
15:44:08.917423 B40191B00 Read-Ack Boiler water temperature: 27.00
15:44:09.341315 T001B0000 Read-Data Outside temperature: 0.00
15:44:09.349031 R00030000 Read-Data Slave configuration: 00000000 0
15:44:09.466546 BC0030918 Read-Ack Slave configuration: 00001001 24
15:44:09.472048 A401B0B50 Read-Ack Outside temperature: 11.31
15:44:09.906531 T80000B00 Read-Data Status: 00001011 00000000
15:44:09.910744 R00000900 Read-Data Status: 00001001 00000000
15:44:10.026007 BC0000900 Read-Ack Status: 00001001 00000000
15:44:10.030388 A40000B00 Read-Ack Status: 00001011 00000000
15:44:10.468559 T80000B00 Read-Data Status: 00001011 00000000
15:44:10.472739 R00000900 Read-Data Status: 00001001 00000000
15:44:10.582636 BC0000900 Read-Ack Status: 00001001 00000000
15:44:10.586641 A40000B00 Read-Ack Status: 00001011 00000000
15:44:11.028686 T80000B00 Read-Data Status: 00001011 00000000
15:44:11.032755 R00000900 Read-Data Status: 00001001 00000000
15:44:11.131628 BC0000900 Read-Ack Status: 00001001 00000000
15:44:11.135665 A40000B00 Read-Ack Status: 00001011 00000000
15:44:11.576728 T80000B00 Read-Data Status: 00001011 00000000
15:44:11.580616 R00000900 Read-Data Status: 00001001 00000000
15:44:11.696765 BC0000900 Read-Ack Status: 00001001 00000000
15:44:11.700701 A40000B00 Read-Ack Status: 00001011 00000000
15:44:12.133756 T80000B00 Read-Data Status: 00001011 00000000
15:44:12.137808 R00000900 Read-Data Status: 00001001 00000000
15:44:12.255946 BC0000900 Read-Ack Status: 00001001 00000000
15:44:12.259849 A40000B00 Read-Ack Status: 00001011 00000000
15:44:12.697838 T80000B00 Read-Data Status: 00001011 00000000
15:44:12.702259 R00000900 Read-Data Status: 00001001 00000000
15:44:12.818541 BC0000900 Read-Ack Status: 00001001 00000000
15:44:12.822738 A40000B00 Read-Ack Status: 00001011 00000000
15:44:13.284572 T10011800 Write-Data Control setpoint: 24.00
15:44:13.401143 BD0011800 Write-Ack Control setpoint: 24.00
15:44:13.836103 T80190000 Read-Data Boiler water temperature: 0.00
15:44:13.951289 B40191B00 Read-Ack Boiler water temperature: 27.00
15:44:14.399057 T801A0000 Read-Data DHW temperature: 0.00
15:44:14.516116 BC01A1880 Read-Ack DHW temperature: 24.50
15:44:14.958410 T80000B00 Read-Data Status: 00001011 00000000
15:44:14.962447 R00000900 Read-Data Status: 00001001 00000000
15:44:15.070401 BC0000900 Read-Ack Status: 00001001 00000000
15:44:15.074791 A40000B00 Read-Ack Status: 00001011 00000000
15:44:15.506296 T80000B00 Read-Data Status: 00001011 00000000
15:44:15.510457 R00000900 Read-Data Status: 00001001 00000000
15:44:15.626630 BC0000900 Read-Ack Status: 00001001 00000000
15:44:15.631154 A40000B00 Read-Ack Status: 00001011 00000000
15:44:16.060063 T80000B00 Read-Data Status: 00001011 00000000
15:44:16.064167 R00000900 Read-Data Status: 00001001 00000000
15:44:16.184689 BC0000900 Read-Ack Status: 00001001 00000000
15:44:16.188775 A40000B00 Read-Ack Status: 00001011 00000000
15:44:16.624899 T80000B00 Read-Data Status: 00001011 00000000
15:44:16.629391 R00000900 Read-Data Status: 00001001 00000000
15:44:16.733508 BC0000900 Read-Ack Status: 00001001 00000000
15:44:16.737445 A40000B00 Read-Ack Status: 00001011 00000000
15:44:17.180251 T80000B00 Read-Data Status: 00001011 00000000
15:44:17.184253 R00000900 Read-Data Status: 00001001 00000000
15:44:17.301091 BC0000900 Read-Ack Status: 00001001 00000000
15:44:17.305751 A40000B00 Read-Ack Status: 00001011 00000000
15:44:17.782614 T10011800 Write-Data Control setpoint: 24.00
15:44:17.906695 BD0011800 Write-Ack Control setpoint: 24.00
15:44:18.329704 T00090000 Read-Data Remote override room setpoint: 0.00
15:44:18.334822 R00050000 Read-Data Application-specific flags: 00000000 0
15:44:18.458831 BC00500FF Read-Ack Application-specific flags: 00000000 255
15:44:18.462940 AC0091080 Read-Ack Remote override room setpoint: 16.50
15:44:18.892736 T80190000 Read-Data Boiler water temperature: 0.00
15:44:19.014051 B40191B00 Read-Ack Boiler water temperature: 27.00
15:44:19.458808 T00090000 Read-Data Remote override room setpoint: 0.00
15:44:19.463021 R00060000 Read-Data Remote parameter flags: 00000000 00000000
15:44:19.571386 BC0060101 Read-Ack Remote parameter flags: 00000001 00000001
15:44:19.575251 AC0091080 Read-Ack Remote override room setpoint: 16.50
15:44:20.003213 T00090000 Read-Data Remote override room setpoint: 0.00
15:44:20.007319 R80190000 Read-Data Boiler water temperature: 0.00
15:44:20.127775 B40191B00 Read-Ack Boiler water temperature: 27.00
15:44:20.131657 AC0091080 Read-Ack Remote override room setpoint: 16.50
15:44:20.568360 T00090000 Read-Data Remote override room setpoint: 0.00
15:44:20.572393 R801A0000 Read-Data DHW temperature: 0.00
15:44:20.684198 BC01A1880 Read-Ack DHW temperature: 24.50
15:44:20.688539 AC0091080 Read-Ack Remote override room setpoint: 16.50
15:44:21.122055 T80000B00 Read-Data Status: 00001011 00000000
15:44:21.125946 R00000900 Read-Data Status: 00001001 00000000
15:44:21.242903 BC0000900 Read-Ack Status: 00001001 00000000
15:44:21.247171 A40000B00 Read-Ack Status: 00001011 00000000
15:44:21.670169 T80640000 Read-Data Remote override function: 00000000
15:44:21.674227 R007D0000 Read-Data OpenTherm version Slave: 0.00
15:44:21.798660 B407D0203 Read-Ack OpenTherm version Slave: 2.01
15:44:21.803044 A40640003 Read-Ack Remote override function: 00000011
15:44:22.231226 T80000B00 Read-Data Status: 00001011 00000000
15:44:22.235763 R00000900 Read-Data Status: 00001001 00000000
15:44:22.353160 BC0000900 Read-Ack Status: 00001001 00000000
15:44:22.357218 A40000B00 Read-Ack Status: 00001011 00000000
15:44:22.797804 T10011800 Write-Data Control setpoint: 24.00
15:44:22.909631 BD0011800 Write-Ack Control setpoint: 24.00
15:44:23.354567 T10101200 Write-Data Room setpoint: 18.00
15:44:23.358929 R00030000 Read-Data Slave configuration: 00000000 0
15:44:23.472294 BC0030918 Read-Ack Slave configuration: 00001001 24
15:44:23.476222 AD0101200 Write-Ack Room setpoint: 18.00
15:44:23.910313 T80190000 Read-Data Boiler water temperature: 0.00
15:44:24.019441 B40191B00 Read-Ack Boiler water temperature: 27.00
15:44:24.463631 T80000B00 Read-Data Status: 00001011 00000000
15:44:24.467680 R00000900 Read-Data Status: 00001001 00000000
15:44:24.583355 BC0000900 Read-Ack Status: 00001001 00000000
15:44:24.587220 A40000B00 Read-Ack Status: 00001011 00000000
15:44:25.027881 T80000B00 Read-Data Status: 00001011 00000000
15:44:25.045194 R00000900 Read-Data Status: 00001001 00000000
15:44:25.143057 BC0000900 Read-Ack Status: 00001001 00000000
15:44:25.147023 A40000B00 Read-Ack Status: 00001011 00000000
15:44:25.572005 T80000B00 Read-Data Status: 00001011 00000000
15:44:25.575887 R00000900 Read-Data Status: 00001001 00000000
15:44:25.692533 BC0000900 Read-Ack Status: 00001001 00000000
15:44:25.698508 A40000B00 Read-Ack Status: 00001011 00000000
15:44:26.136630 T80000B00 Read-Data Status: 00001011 00000000
15:44:26.140684 R00000900 Read-Data Status: 00001001 00000000
15:44:26.257307 BC0000900 Read-Ack Status: 00001001 00000000
15:44:26.261464 A40000B00 Read-Ack Status: 00001011 00000000
15:44:26.693587 T80000B00 Read-Data Status: 00001011 00000000
15:44:26.697701 R00000900 Read-Data Status: 00001001 00000000
15:44:26.812534 BC0000900 Read-Ack Status: 00001001 00000000
15:44:26.816866 A40000B00 Read-Ack Status: 00001011 00000000
15:44:27.281877 T80000B00 Read-Data Status: 00001011 00000000
15:44:27.286173 R00000900 Read-Data Status: 00001001 00000000
15:44:27.403657 BC0000900 Read-Ack Status: 00001001 00000000
15:44:27.408010 A40000B00 Read-Ack Status: 00001011 00000000
15:44:27.830781 T10011800 Write-Data Control setpoint: 24.00
15:44:27.957640 BD0011800 Write-Ack Control setpoint: 24.00
15:44:28.392835 T1018129E Write-Data Room temperature: 18.62
15:44:28.397271 R00050000 Read-Data Application-specific flags: 00000000 0
15:44:28.518795 BC00500FF Read-Ack Application-specific flags: 00000000 255
15:44:28.522675 A7018129E Unk-DataId Room temperature: 18.62
15:44:28.951166 T80190000 Read-Data Boiler water temperature: 0.00
15:44:29.074091 B40191B00 Read-Ack Boiler water temperature: 27.00
15:44:29.509345 T80000B00 Read-Data Status: 00001011 00000000
15:44:29.513506 R00000900 Read-Data Status: 00001001 00000000
15:44:29.628799 BC0000900 Read-Ack Status: 00001001 00000000
15:44:29.632937 A40000B00 Read-Ack Status: 00001011 00000000
15:44:30.066865 T80000B00 Read-Data Status: 00001011 00000000
15:44:30.071207 R00000900 Read-Data Status: 00001001 00000000
15:44:30.184082 BC0000900 Read-Ack Status: 00001001 00000000
15:44:30.187915 A40000B00 Read-Ack Status: 00001011 00000000
15:44:30.621341 T80000B00 Read-Data Status: 00001011 00000000
15:44:30.625109 R00000900 Read-Data Status: 00001001 00000000
15:44:30.745347 BC0000900 Read-Ack Status: 00001001 00000000
15:44:30.749981 A40000B00 Read-Ack Status: 00001011 00000000
15:44:31.179246 T80000B00 Read-Data Status: 00001011 00000000
15:44:31.183195 R00000900 Read-Data Status: 00001001 00000000
15:44:31.303263 BC0000900 Read-Ack Status: 00001001 00000000
15:44:31.307140 A40000B00 Read-Ack Status: 00001011 00000000
15:44:31.736987 T80000B00 Read-Data Status: 00001011 00000000
15:44:31.741558 R00000900 Read-Data Status: 00001001 00000000
15:44:31.856228 BC0000900 Read-Ack Status: 00001001 00000000
15:44:31.860480 A40000B00 Read-Ack Status: 00001011 00000000
15:44:32.326433 T80000B00 Read-Data Status: 00001011 00000000
15:44:32.330864 R00000900 Read-Data Status: 00001001 00000000
15:44:32.429814 BC0000900 Read-Ack Status: 00001001 00000000
15:44:32.433761 A40000B00 Read-Ack Status: 00001011 00000000
15:44:32.885559 T10011800 Write-Data Control setpoint: 24.00
15:44:33.005319 BD0011800 Write-Ack Control setpoint: 24.00
15:44:33.444848 T900E6400 Write-Data Maximum relative modulation level: 100.00
15:44:33.567323 B500E6400 Write-Ack Maximum relative modulation level: 100.00
15:44:33.989495 T80190000 Read-Data Boiler water temperature: 0.00
15:44:34.115204 B40191B00 Read-Ack Boiler water temperature: 27.00
15:44:34.552652 T80000B00 Read-Data Status: 00001011 00000000
15:44:34.558030 R00000900 Read-Data Status: 00001001 00000000
15:44:34.673876 BC0000900 Read-Ack Status: 00001001 00000000
15:44:34.678066 A40000B00 Read-Ack Status: 00001011 00000000
15:44:35.116416 T80000B00 Read-Data Status: 00001011 00000000
15:44:35.120571 R00000900 Read-Data Status: 00001001 00000000
15:44:35.236936 BC0000900 Read-Ack Status: 00001001 00000000
15:44:35.241101 A40000B00 Read-Ack Status: 00001011 00000000
15:44:35.675699 T80000B00 Read-Data Status: 00001011 00000000
15:44:35.680103 R00000900 Read-Data Status: 00001001 00000000
15:44:35.785772 BC0000900 Read-Ack Status: 00001001 00000000
15:44:35.790354 A40000B00 Read-Ack Status: 00001011 00000000
15:44:36.223096 T80000B00 Read-Data Status: 00001011 00000000
15:44:36.227954 R00000900 Read-Data Status: 00001001 00000000
15:44:36.347157 BC0000900 Read-Ack Status: 00001001 00000000
15:44:36.351202 A40000B00 Read-Ack Status: 00001011 00000000
15:44:36.785310 T80000B00 Read-Data Status: 00001011 00000000
15:44:36.789400 R00000900 Read-Data Status: 00001001 00000000
15:44:36.903918 BC0000900 Read-Ack Status: 00001001 00000000
15:44:36.922752 A40000B00 Read-Ack Status: 00001011 00000000
15:44:37.346197 T80000B00 Read-Data Status: 00001011 00000000
15:44:37.350663 R00000900 Read-Data Status: 00001001 00000000
15:44:37.460025 BC0000900 Read-Ack Status: 00001001 00000000
15:44:37.463828 A40000B00 Read-Ack Status: 00001011 00000000
15:44:37.891858 T00050000 Read-Data Application-specific flags: 00000000 0
15:44:38.016387 BC00500FF Read-Ack Application-specific flags: 00000000 255
15:44:38.455074 T10011800 Write-Data Control setpoint: 24.00
15:44:38.577652 BD0011800 Write-Ack Control setpoint: 24.00
15:44:39.002576 T80190000 Read-Data Boiler water temperature: 0.00
15:44:39.119217 B40191B00 Read-Ack Boiler water temperature: 27.00
15:44:39.569573 T80000B00 Read-Data Status: 00001011 00000000
15:44:39.573684 R00000900 Read-Data Status: 00001001 00000000
15:44:39.685843 BC0000900 Read-Ack Status: 00001001 00000000
15:44:39.690731 A40000B00 Read-Ack Status: 00001011 00000000
15:44:40.126897 T80000B00 Read-Data Status: 00001011 00000000
15:44:40.131144 R00000900 Read-Data Status: 00001001 00000000
15:44:40.243188 BC0000900 Read-Ack Status: 00001001 00000000
15:44:40.247358 A40000B00 Read-Ack Status: 00001011 00000000
15:44:40.684669 T80000B00 Read-Data Status: 00001011 00000000
15:44:40.688467 R00000900 Read-Data Status: 00001001 00000000
15:44:40.799511 BC0000900 Read-Ack Status: 00001001 00000000
15:44:40.803684 A40000B00 Read-Ack Status: 00001011 00000000
15:44:41.233797 T80000B00 Read-Data Status: 00001011 00000000
15:44:41.237900 R00000900 Read-Data Status: 00001001 00000000
15:44:41.358880 BC0000900 Read-Ack Status: 00001001 00000000
15:44:41.363265 A40000B00 Read-Ack Status: 00001011 00000000
15:44:41.792295 T00382300 Read-Data DHW setpoint: 35.00
15:44:41.911505 BC0383C1A Read-Ack DHW setpoint: 60.10
15:44:42.353863 T00394B00 Read-Data Max CH water setpoint: 75.00
15:44:42.358466 R00060000 Read-Data Remote parameter flags: 00000000 00000000
15:44:42.476053 BC0060101 Read-Ack Remote parameter flags: 00000001 00000001
15:44:42.479788 AC0395A00 Read-Ack Max CH water setpoint: 90.00
15:44:42.906822 T10011800 Write-Data Control setpoint: 24.00
15:44:43.025937 BD0011800 Write-Ack Control setpoint: 24.00
15:44:43.464034 T80000B00 Read-Data Status: 00001011 00000000
15:44:43.468369 R00000900 Read-Data Status: 00001001 00000000
15:44:43.586935 BC0000900 Read-Ack Status: 00001001 00000000
15:44:43.591015 A40000B00 Read-Ack Status: 00001011 00000000
15:44:44.021093 T80190000 Read-Data Boiler water temperature: 0.00
15:44:44.142926 B40191B00 Read-Ack Boiler water temperature: 27.00
15:44:44.579682 T80000B00 Read-Data Status: 00001011 00000000
15:44:44.583594 R00000900 Read-Data Status: 00001001 00000000
15:44:44.703162 BC0000900 Read-Ack Status: 00001001 00000000
15:44:44.707340 A40000B00 Read-Ack Status: 00001011 00000000
15:44:45.136218 T80000B00 Read-Data Status: 00001011 00000000
15:44:45.140450 R00000900 Read-Data Status: 00001001 00000000
15:44:45.254032 BC0000900 Read-Ack Status: 00001001 00000000
15:44:45.258132 A40000B00 Read-Ack Status: 00001011 00000000
15:44:45.692961 T80000B00 Read-Data Status: 00001011 00000000
15:44:45.710767 R00000900 Read-Data Status: 00001001 00000000
15:44:45.824001 BC0000900 Read-Ack Status: 00001001 00000000
15:44:45.828697 A40000B00 Read-Ack Status: 00001011 00000000
15:44:46.282333 T00110000 Read-Data Relative modulation level: 0.00
15:44:46.399168 BC0110000 Read-Ack Relative modulation level: 0.00
15:44:46.832313 T80000B00 Read-Data Status: 00001011 00000000
15:44:46.837031 R00000900 Read-Data Status: 00001001 00000000
15:44:46.955350 BC0000900 Read-Ack Status: 00001001 00000000
15:44:46.960003 A40000B00 Read-Ack Status: 00001011 00000000
15:44:47.412513 T80000B00 Read-Data Status: 00001011 00000000
15:44:47.417999 R00000900 Read-Data Status: 00001001 00000000
15:44:47.533465 BC0000900 Read-Ack Status: 00001001 00000000
15:44:47.538087 A40000B00 Read-Ack Status: 00001011 00000000
15:44:47.971416 T90011900 Write-Data Control setpoint: 25.00
15:44:48.092659 B50011900 Write-Ack Control setpoint: 25.00
15:44:48.528680 T80000B00 Read-Data Status: 00001011 00000000
15:44:48.532931 R00000900 Read-Data Status: 00001001 00000000
15:44:48.648487 BC0000900 Read-Ack Status: 00001001 00000000
15:44:48.652693 A40000B00 Read-Ack Status: 00001011 00000000
15:44:49.088578 T80190000 Read-Data Boiler water temperature: 0.00
15:44:49.209575 B40191B00 Read-Ack Boiler water temperature: 27.00
15:44:49.643732 T80000B00 Read-Data Status: 00001011 00000000
15:44:49.647756 R00000900 Read-Data Status: 00001001 00000000
15:44:49.760756 BC0000900 Read-Ack Status: 00001001 00000000
15:44:49.764741 A40000B00 Read-Ack Status: 00001011 00000000
15:44:50.211502 T00120000 Read-Data CH water pressure: 0.00
15:44:50.328515 B40120266 Read-Ack CH water pressure: 2.40
15:44:50.790797 T80000B00 Read-Data Status: 00001011 00000000
15:44:50.795222 R00000900 Read-Data Status: 00001001 00000000
15:44:50.902775 BC0000900 Read-Ack Status: 00001001 00000000
15:44:50.906746 A40000B00 Read-Ack Status: 00001011 00000000
15:44:51.343867 T80000B00 Read-Data Status: 00001011 00000000
15:44:51.348360 R00000900 Read-Data Status: 00001001 00000000
15:44:51.456649 BC0000900 Read-Ack Status: 00001001 00000000
15:44:51.461023 A40000B00 Read-Ack Status: 00001011 00000000
15:44:51.896982 T80000B00 Read-Data Status: 00001011 00000000
15:44:51.902936 R00000900 Read-Data Status: 00001001 00000000
15:44:52.011424 BC0000900 Read-Ack Status: 00001001 00000000
15:44:52.017662 A40000B00 Read-Ack Status: 00001011 00000000
15:44:52.454324 T80000B00 Read-Data Status: 00001011 00000000
15:44:52.458342 R00000900 Read-Data Status: 00001001 00000000
15:44:52.575457 BC0000900 Read-Ack Status: 00001001 00000000
15:44:52.579955 A40000B00 Read-Ack Status: 00001011 00000000
15:44:53.014192 T90011900 Write-Data Control setpoint: 25.00
15:44:53.131719 B50011900 Write-Ack Control setpoint: 25.00
15:44:53.559194 T80000B00 Read-Data Status: 00001011 00000000
15:44:53.562911 R00000900 Read-Data Status: 00001001 00000000
15:44:53.684413 BC0000900 Read-Ack Status: 00001001 00000000
15:44:53.688515 A40000B00 Read-Ack Status: 00001011 00000000
15:44:54.124111 T80190000 Read-Data Boiler water temperature: 0.00
15:44:54.246463 B40191B00 Read-Ack Boiler water temperature: 27.00
15:44:54.684348 T80000B00 Read-Data Status: 00001011 00000000
15:44:54.688566 R00000900 Read-Data Status: 00001001 00000000
15:44:54.803476 BC0000900 Read-Ack Status: 00001001 00000000
15:44:54.807414 A40000B00 Read-Ack Status: 00001011 00000000
15:44:55.236460 T80000B00 Read-Data Status: 00001011 00000000
15:44:55.240430 R00000900 Read-Data Status: 00001001 00000000
15:44:55.356287 BC0000900 Read-Ack Status: 00001001 00000000
15:44:55.360517 A40000B00 Read-Ack Status: 00001011 00000000
15:44:55.800907 T80000B00 Read-Data Status: 00001011 00000000
15:44:55.805555 R00000900 Read-Data Status: 00001001 00000000
15:44:55.914619 BC0000900 Read-Ack Status: 00001001 00000000
15:44:55.918905 A40000B00 Read-Ack Status: 00001011 00000000
15:44:56.358603 T80000B00 Read-Data Status: 00001011 00000000
15:44:56.362659 R00000900 Read-Data Status: 00001001 00000000
15:44:56.475539 BC0000900 Read-Ack Status: 00001001 00000000
15:44:56.479424 A40000B00 Read-Ack Status: 00001011 00000000
15:44:56.907512 T80000B00 Read-Data Status: 00001011 00000000
15:44:56.911464 R00000900 Read-Data Status: 00001001 00000000
15:44:57.022514 BC0000900 Read-Ack Status: 00001001 00000000
15:44:57.026412 A40000B00 Read-Ack Status: 00001011 00000000
15:44:57.460732 T80000B00 Read-Data Status: 00001011 00000000
15:44:57.465169 R00000900 Read-Data Status: 00001001 00000000
15:44:57.584782 BC0000900 Read-Ack Status: 00001001 00000000
15:44:57.589054 A40000B00 Read-Ack Status: 00001011 00000000
15:44:58.023759 T90011900 Write-Data Control setpoint: 25.00
15:44:58.148898 B50011900 Write-Ack Control setpoint: 25.00
15:44:58.578747 T80000B00 Read-Data Status: 00001011 00000000
15:44:58.582837 R00000900 Read-Data Status: 00001001 00000000
15:44:58.698621 BC0000900 Read-Ack Status: 00001001 00000000
15:44:58.703006 A40000B00 Read-Ack Status: 00001011 00000000
15:44:59.133807 T80190000 Read-Data Boiler water temperature: 0.00
15:44:59.261356 B40191B00 Read-Ack Boiler water temperature: 27.00
15:44:59.691976 T80000B00 Read-Data Status: 00001011 00000000
15:44:59.695719 R00000900 Read-Data Status: 00001001 00000000
15:44:59.862934 BC0000900 Read-Ack Status: 00001001 00000000
15:44:59.866866 A40000B00 Read-Ack Status: 00001011 00000000
15:45:00.285826 T80000B00 Read-Data Status: 00001011 00000000
15:45:00.290046 R00000900 Read-Data Status: 00001001 00000000
15:45:00.403170 BC0000900 Read-Ack Status: 00001001 00000000
15:45:00.407320 A40000B00 Read-Ack Status: 00001011 00000000
15:45:00.845614 T80000B00 Read-Data Status: 00001011 00000000
15:45:00.850149 R00000900 Read-Data Status: 00001001 00000000
15:45:00.957895 BC0000900 Read-Ack Status: 00001001 00000000
15:45:00.962314 A40000B00 Read-Ack Status: 00001011 00000000
15:45:01.398645 T80000B00 Read-Data Status: 00001011 00000000
15:45:01.403288 R00000900 Read-Data Status: 00001001 00000000
15:45:01.512129 BC0000900 Read-Ack Status: 00001001 00000000
15:45:01.516210 A40000B00 Read-Ack Status: 00001011 00000000
15:45:01.951408 T80000B00 Read-Data Status: 00001011 00000000
15:45:01.955292 R00000900 Read-Data Status: 00001001 00000000
15:45:02.074335 BC0000900 Read-Ack Status: 00001001 00000000
15:45:02.082779 A40000B00 Read-Ack Status: 00001011 00000000
15:45:02.531195 T80000B00 Read-Data Status: 00001011 00000000
15:45:02.535612 R00000900 Read-Data Status: 00001001 00000000
15:45:02.659200 BC0000900 Read-Ack Status: 00001001 00000000
15:45:02.662946 A40000B00 Read-Ack Status: 00001011 00000000
15:45:03.087215 T10011800 Write-Data Control setpoint: 24.00
15:45:03.286406 BD0011800 Write-Ack Control setpoint: 24.00
15:45:03.645811 T801C0000 Read-Data Return water temperature: 0.00
15:45:03.762439 B401C1A80 Read-Ack Return water temperature: 26.50
15:45:04.203422 T80190000 Read-Data Boiler water temperature: 0.00
15:45:04.318510 B40191B00 Read-Ack Boiler water temperature: 27.00
15:45:04.781505 T00000A00 Read-Data Status: 00001010 00000000
15:45:04.786026 R80000800 Read-Data Status: 00001000 00000000
15:45:04.904318 B40000800 Read-Ack Status: 00001000 00000000
15:45:04.908986 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:05.341043 T00000A00 Read-Data Status: 00001010 00000000
15:45:05.345244 R80000800 Read-Data Status: 00001000 00000000
15:45:05.459816 B40000800 Read-Ack Status: 00001000 00000000
15:45:05.463842 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:05.891809 T00000A00 Read-Data Status: 00001010 00000000
15:45:05.896036 R80000800 Read-Data Status: 00001000 00000000
15:45:06.017925 B40000800 Read-Ack Status: 00001000 00000000
15:45:06.022028 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:06.456842 T00000A00 Read-Data Status: 00001010 00000000
15:45:06.461202 R80000800 Read-Data Status: 00001000 00000000
15:45:06.578632 B40000800 Read-Ack Status: 00001000 00000000
15:45:06.582614 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:07.010817 T00000A00 Read-Data Status: 00001010 00000000
15:45:07.014741 R80000800 Read-Data Status: 00001000 00000000
15:45:07.129897 B40000800 Read-Ack Status: 00001000 00000000
15:45:07.134044 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:07.571536 T00000A00 Read-Data Status: 00001010 00000000
15:45:07.575366 R80000800 Read-Data Status: 00001000 00000000
15:45:07.687245 B40000800 Read-Ack Status: 00001000 00000000
15:45:07.691972 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:08.119847 T10010A00 Write-Data Control setpoint: 10.00
15:45:08.239914 BD0010A00 Write-Ack Control setpoint: 10.00
15:45:08.681209 T001B0000 Read-Data Outside temperature: 0.00
15:45:08.686507 R80190000 Read-Data Boiler water temperature: 0.00
15:45:08.803127 B40191B00 Read-Ack Boiler water temperature: 27.00
15:45:08.807337 A401B0B60 Read-Ack Outside temperature: 11.38
15:45:09.238142 T80190000 Read-Data Boiler water temperature: 0.00
15:45:09.357118 B40191B00 Read-Ack Boiler water temperature: 27.00
15:45:09.799200 T00000A00 Read-Data Status: 00001010 00000000
15:45:09.803378 R80000800 Read-Data Status: 00001000 00000000
15:45:09.910031 B40000800 Read-Ack Status: 00001000 00000000
15:45:09.914382 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:10.350218 T00000A00 Read-Data Status: 00001010 00000000
15:45:10.354409 R80000800 Read-Data Status: 00001000 00000000
15:45:10.475059 B40000800 Read-Ack Status: 00001000 00000000
15:45:10.479263 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:10.900106 T00000A00 Read-Data Status: 00001010 00000000
15:45:10.907195 R80000800 Read-Data Status: 00001000 00000000
15:45:11.019529 B40000800 Read-Ack Status: 00001000 00000000
15:45:11.024378 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:11.465399 T00000A00 Read-Data Status: 00001010 00000000
15:45:11.469663 R80000800 Read-Data Status: 00001000 00000000
15:45:11.581274 B40000800 Read-Ack Status: 00001000 00000000
15:45:11.585682 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:12.037502 T00000A00 Read-Data Status: 00001010 00000000
15:45:12.041705 R80000800 Read-Data Status: 00001000 00000000
15:45:12.149531 B40000800 Read-Ack Status: 00001000 00000000
15:45:12.153906 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:12.588601 T00000A00 Read-Data Status: 00001010 00000000
15:45:12.593375 R80000800 Read-Data Status: 00001000 00000000
15:45:12.700394 B40000800 Read-Ack Status: 00001000 00000000
15:45:12.704410 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:13.137403 T10010A00 Write-Data Control setpoint: 10.00
15:45:13.254521 BD0010A00 Write-Ack Control setpoint: 10.00
15:45:13.698748 T801A0000 Read-Data DHW temperature: 0.00
15:45:13.813644 BC01A1880 Read-Ack DHW temperature: 24.50
15:45:14.282646 T80190000 Read-Data Boiler water temperature: 0.00
15:45:14.407805 B40191B00 Read-Ack Boiler water temperature: 27.00
15:45:14.837906 T00000A00 Read-Data Status: 00001010 00000000
15:45:14.842005 R80000800 Read-Data Status: 00001000 00000000
15:45:14.956652 B40000800 Read-Ack Status: 00001000 00000000
15:45:14.961430 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:15.392012 T00000A00 Read-Data Status: 00001010 00000000
15:45:15.396401 R80000800 Read-Data Status: 00001000 00000000
15:45:15.515889 B40000800 Read-Ack Status: 00001000 00000000
15:45:15.519985 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:15.951981 T00000A00 Read-Data Status: 00001010 00000000
15:45:15.956772 R80000800 Read-Data Status: 00001000 00000000
15:45:16.070486 B40000800 Read-Ack Status: 00001000 00000000
15:45:16.074467 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:16.501930 T00000A00 Read-Data Status: 00001010 00000000
15:45:16.506207 R80000800 Read-Data Status: 00001000 00000000
15:45:16.621831 B40000800 Read-Ack Status: 00001000 00000000
15:45:16.625845 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:17.082623 T00000A00 Read-Data Status: 00001010 00000000
15:45:17.086653 R80000800 Read-Data Status: 00001000 00000000
15:45:17.180925 B40000800 Read-Ack Status: 00001000 00000000
15:45:17.185047 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:17.646499 T00000A00 Read-Data Status: 00001010 00000000
15:45:17.650372 R80000800 Read-Data Status: 00001000 00000000
15:45:17.762094 B40000800 Read-Ack Status: 00001000 00000000
15:45:17.766267 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:18.200160 T10010A00 Write-Data Control setpoint: 10.00
15:45:18.322483 BD0010A00 Write-Ack Control setpoint: 10.00
15:45:18.787194 T80190000 Read-Data Boiler water temperature: 0.00
15:45:18.904303 B40191B00 Read-Ack Boiler water temperature: 27.00
15:45:19.338801 T00090000 Read-Data Remote override room setpoint: 0.00
15:45:19.343240 R801A0000 Read-Data DHW temperature: 0.00
15:45:19.463539 BC01A1880 Read-Ack DHW temperature: 24.50
15:45:19.467612 AC0091080 Read-Ack Remote override room setpoint: 16.50
15:45:19.895748 T80640000 Read-Data Remote override function: 00000000
15:45:19.899857 R007D0000 Read-Data OpenTherm version Slave: 0.00
15:45:20.012485 B407D0203 Read-Ack OpenTherm version Slave: 2.01
15:45:20.016309 A40640003 Read-Ack Remote override function: 00000011
15:45:20.454512 T00000A00 Read-Data Status: 00001010 00000000
15:45:20.458639 R80000800 Read-Data Status: 00001000 00000000
15:45:20.576680 B40000800 Read-Ack Status: 00001000 00000000
15:45:20.580990 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:21.019683 T00000A00 Read-Data Status: 00001010 00000000
15:45:21.024110 R80000800 Read-Data Status: 00001000 00000000
15:45:21.136837 B40000800 Read-Ack Status: 00001000 00000000
15:45:21.140921 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:21.567791 T00000A00 Read-Data Status: 00001010 00000000
15:45:21.571974 R80000800 Read-Data Status: 00001000 00000000
15:45:21.686961 B40000800 Read-Ack Status: 00001000 00000000
15:45:21.691092 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:22.122813 T00000A00 Read-Data Status: 00001010 00000000
15:45:22.127614 R80000800 Read-Data Status: 00001000 00000000
15:45:22.243734 B40000800 Read-Ack Status: 00001000 00000000
15:45:22.247734 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:22.680797 T00000A00 Read-Data Status: 00001010 00000000
15:45:22.685316 R80000800 Read-Data Status: 00001000 00000000
15:45:22.804860 B40000800 Read-Ack Status: 00001000 00000000
15:45:22.809037 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:23.239137 T10010A00 Write-Data Control setpoint: 10.00
15:45:23.363822 BD0010A00 Write-Ack Control setpoint: 10.00
15:45:23.794934 T80190000 Read-Data Boiler water temperature: 0.00
15:45:23.912876 B40191B00 Read-Ack Boiler water temperature: 27.00
15:45:24.350067 T90101000 Write-Data Room setpoint: 16.00
15:45:24.354173 R00030000 Read-Data Slave configuration: 00000000 0
15:45:24.471639 BC0030918 Read-Ack Slave configuration: 00001001 24
15:45:24.475354 A50101000 Write-Ack Room setpoint: 16.00
15:45:24.899401 T00000A00 Read-Data Status: 00001010 00000000
15:45:24.903806 R80000800 Read-Data Status: 00001000 00000000
15:45:25.028157 B40000800 Read-Ack Status: 00001000 00000000
15:45:25.032342 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:25.466127 T00000A00 Read-Data Status: 00001010 00000000
15:45:25.470748 R80000800 Read-Data Status: 00001000 00000000
15:45:25.582780 B40000800 Read-Ack Status: 00001000 00000000
15:45:25.586975 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:26.023390 T00000A00 Read-Data Status: 00001010 00000000
15:45:26.027514 R80000800 Read-Data Status: 00001000 00000000
15:45:26.141650 B40000800 Read-Ack Status: 00001000 00000000
15:45:26.145675 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:26.586393 T00000A00 Read-Data Status: 00001010 00000000
15:45:26.590457 R80000800 Read-Data Status: 00001000 00000000
15:45:26.689158 B40000800 Read-Ack Status: 00001000 00000000
15:45:26.695054 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:27.129781 T00000A00 Read-Data Status: 00001010 00000000
15:45:27.133755 R80000800 Read-Data Status: 00001000 00000000
15:45:27.255496 B40000800 Read-Ack Status: 00001000 00000000
15:45:27.260055 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:27.696522 T00000A00 Read-Data Status: 00001010 00000000
15:45:27.700846 R80000800 Read-Data Status: 00001000 00000000
15:45:27.818271 B40000800 Read-Ack Status: 00001000 00000000
15:45:27.822235 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:28.287536 T10010A00 Write-Data Control setpoint: 10.00
15:45:28.403462 BD0010A00 Write-Ack Control setpoint: 10.00
15:45:28.830574 T80190000 Read-Data Boiler water temperature: 0.00
15:45:28.956736 B40191B00 Read-Ack Boiler water temperature: 27.00
15:45:29.398642 T1018129E Write-Data Room temperature: 18.62
15:45:29.403170 R00050000 Read-Data Application-specific flags: 00000000 0
15:45:29.510609 BC00500FF Read-Ack Application-specific flags: 00000000 255
15:45:29.514871 A7018129E Unk-DataId Room temperature: 18.62
15:45:29.951744 T00000A00 Read-Data Status: 00001010 00000000
15:45:29.955814 R80000800 Read-Data Status: 00001000 00000000
15:45:30.074547 B40000800 Read-Ack Status: 00001000 00000000
15:45:30.079464 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:30.509876 T00000A00 Read-Data Status: 00001010 00000000
15:45:30.514156 R80000800 Read-Data Status: 00001000 00000000
15:45:30.632716 B40000800 Read-Ack Status: 00001000 00000000
15:45:30.636613 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:31.061960 T00000A00 Read-Data Status: 00001010 00000000
15:45:31.066090 R80000800 Read-Data Status: 00001000 00000000
15:45:31.184724 B40000800 Read-Ack Status: 00001000 00000000
15:45:31.188701 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:31.622763 T00000A00 Read-Data Status: 00001010 00000000
15:45:31.627170 R80000800 Read-Data Status: 00001000 00000000
15:45:31.745067 B40000800 Read-Ack Status: 00001000 00000000
15:45:31.749144 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:32.187985 T00000A00 Read-Data Status: 00001010 00000000
15:45:32.192362 R80000800 Read-Data Status: 00001000 00000000
15:45:32.307899 B40000800 Read-Ack Status: 00001000 00000000
15:45:32.312232 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:32.784296 T10010A00 Write-Data Control setpoint: 10.00
15:45:32.907505 BD0010A00 Write-Ack Control setpoint: 10.00
15:45:33.338278 T900E6400 Write-Data Maximum relative modulation level: 100.00
15:45:33.451611 B500E6400 Write-Ack Maximum relative modulation level: 100.00
15:45:33.898325 T80190000 Read-Data Boiler water temperature: 0.00
15:45:34.015164 B40191B00 Read-Ack Boiler water temperature: 27.00
15:45:34.450260 T00000A00 Read-Data Status: 00001010 00000000
15:45:34.454904 R80000800 Read-Data Status: 00001000 00000000
15:45:34.571878 B40000800 Read-Ack Status: 00001000 00000000
15:45:34.575745 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:35.007551 T00000A00 Read-Data Status: 00001010 00000000
15:45:35.011528 R80000800 Read-Data Status: 00001000 00000000
15:45:35.128477 B40000800 Read-Ack Status: 00001000 00000000
15:45:35.132252 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:35.565369 T00000A00 Read-Data Status: 00001010 00000000
15:45:35.569454 R80000800 Read-Data Status: 00001000 00000000
15:45:35.688406 B40000800 Read-Ack Status: 00001000 00000000
15:45:35.692552 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:36.123495 T00000A00 Read-Data Status: 00001010 00000000
15:45:36.127735 R80000800 Read-Data Status: 00001000 00000000
15:45:36.246870 B40000800 Read-Ack Status: 00001000 00000000
15:45:36.251193 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:36.679590 T00000A00 Read-Data Status: 00001010 00000000
15:45:36.683960 R80000800 Read-Data Status: 00001000 00000000
15:45:36.797608 B40000800 Read-Ack Status: 00001000 00000000
15:45:36.801649 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:37.237634 T00000A00 Read-Data Status: 00001010 00000000
15:45:37.241931 R80000800 Read-Data Status: 00001000 00000000
15:45:37.358616 B40000800 Read-Ack Status: 00001000 00000000
15:45:37.362667 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:37.794826 T00050000 Read-Data Application-specific flags: 00000000 0
15:45:37.913810 BC00500FF Read-Ack Application-specific flags: 00000000 255
15:45:38.349944 T10010A00 Write-Data Control setpoint: 10.00
15:45:38.468915 BD0010A00 Write-Ack Control setpoint: 10.00
15:45:38.906903 T80190000 Read-Data Boiler water temperature: 0.00
15:45:39.033098 B40191B00 Read-Ack Boiler water temperature: 27.00
15:45:39.459945 T00000A00 Read-Data Status: 00001010 00000000
15:45:39.464139 R80000800 Read-Data Status: 00001000 00000000
15:45:39.581181 B40000800 Read-Ack Status: 00001000 00000000
15:45:39.585190 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:40.026033 T00000A00 Read-Data Status: 00001010 00000000
15:45:40.030160 R80000800 Read-Data Status: 00001000 00000000
15:45:40.139260 B40000800 Read-Ack Status: 00001000 00000000
15:45:40.143181 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:40.575672 T00000A00 Read-Data Status: 00001010 00000000
15:45:40.579586 R80000800 Read-Data Status: 00001000 00000000
15:45:40.707291 B40000800 Read-Ack Status: 00001000 00000000
15:45:40.711335 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:41.134231 T00000A00 Read-Data Status: 00001010 00000000
15:45:41.138355 R80000800 Read-Data Status: 00001000 00000000
15:45:41.256892 B40000800 Read-Ack Status: 00001000 00000000
15:45:41.261331 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:41.689344 T00000A00 Read-Data Status: 00001010 00000000
15:45:41.693250 R80000800 Read-Data Status: 00001000 00000000
15:45:41.822146 B40000800 Read-Ack Status: 00001000 00000000
15:45:41.826356 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:42.279426 T00382300 Read-Data DHW setpoint: 35.00
15:45:42.405537 BC0383C1A Read-Ack DHW setpoint: 60.10
15:45:42.836237 T00394B00 Read-Data Max CH water setpoint: 75.00
15:45:42.840749 R00060000 Read-Data Remote parameter flags: 00000000 00000000
15:45:42.954251 BC0060101 Read-Ack Remote parameter flags: 00000001 00000001
15:45:42.958298 AC0395A00 Read-Ack Max CH water setpoint: 90.00
15:45:43.392796 T10010A00 Write-Data Control setpoint: 10.00
15:45:43.518459 BD0010A00 Write-Ack Control setpoint: 10.00
15:45:43.949276 T80190000 Read-Data Boiler water temperature: 0.00
15:45:44.076784 B40191B00 Read-Ack Boiler water temperature: 27.00
15:45:44.507852 T00000A00 Read-Data Status: 00001010 00000000
15:45:44.511896 R80000800 Read-Data Status: 00001000 00000000
15:45:44.626721 B40000800 Read-Ack Status: 00001000 00000000
15:45:44.630978 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:45.061761 T00000A00 Read-Data Status: 00001010 00000000
15:45:45.066447 R80000800 Read-Data Status: 00001000 00000000
15:45:45.182992 B40000800 Read-Ack Status: 00001000 00000000
15:45:45.187535 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:45.626189 T00000A00 Read-Data Status: 00001010 00000000
15:45:45.630521 R80000800 Read-Data Status: 00001000 00000000
15:45:45.740731 B40000800 Read-Ack Status: 00001000 00000000
15:45:45.744799 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:46.180477 T00110000 Read-Data Relative modulation level: 0.00
15:45:46.295796 BC0110000 Read-Ack Relative modulation level: 0.00
15:45:46.738083 T00000A00 Read-Data Status: 00001010 00000000
15:45:46.742629 R80000800 Read-Data Status: 00001000 00000000
15:45:46.855111 B40000800 Read-Ack Status: 00001000 00000000
15:45:46.859265 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:47.321083 T00000A00 Read-Data Status: 00001010 00000000
15:45:47.325409 R80000800 Read-Data Status: 00001000 00000000
15:45:47.430759 B40000800 Read-Ack Status: 00001000 00000000
15:45:47.434719 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:47.887009 T10010A00 Write-Data Control setpoint: 10.00
15:45:48.007986 BD0010A00 Write-Ack Control setpoint: 10.00
15:45:48.446440 T00000A00 Read-Data Status: 00001010 00000000
15:45:48.450598 R80000800 Read-Data Status: 00001000 00000000
15:45:48.565897 B40000800 Read-Ack Status: 00001000 00000000
15:45:48.570387 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:49.003130 T80190000 Read-Data Boiler water temperature: 0.00
15:45:49.114174 B40191B00 Read-Ack Boiler water temperature: 27.00
15:45:49.557280 T00000A00 Read-Data Status: 00001010 00000000
15:45:49.561462 R80000800 Read-Data Status: 00001000 00000000
15:45:49.674379 B40000800 Read-Ack Status: 00001000 00000000
15:45:49.678244 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:50.113434 T00120000 Read-Data CH water pressure: 0.00
15:45:50.236360 B40120266 Read-Ack CH water pressure: 2.40
15:45:50.678720 T00000A00 Read-Data Status: 00001010 00000000
15:45:50.682904 R80000800 Read-Data Status: 00001000 00000000
15:45:50.798526 B40000800 Read-Ack Status: 00001000 00000000
15:45:50.802906 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:51.227376 T00000A00 Read-Data Status: 00001010 00000000
15:45:51.231381 R80000800 Read-Data Status: 00001000 00000000
15:45:51.341378 B40000800 Read-Ack Status: 00001000 00000000
15:45:51.345719 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:51.786043 T00000A00 Read-Data Status: 00001010 00000000
15:45:51.790135 R80000800 Read-Data Status: 00001000 00000000
15:45:51.900560 B40000800 Read-Ack Status: 00001000 00000000
15:45:51.904750 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:52.345597 T00000A00 Read-Data Status: 00001010 00000000
15:45:52.349788 R80000800 Read-Data Status: 00001000 00000000
15:45:52.460515 B40000800 Read-Ack Status: 00001000 00000000
15:45:52.464821 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:52.902431 T10010A00 Write-Data Control setpoint: 10.00
15:45:53.018192 BD0010A00 Write-Ack Control setpoint: 10.00
15:45:53.452680 T00000A00 Read-Data Status: 00001010 00000000
15:45:53.456740 R80000800 Read-Data Status: 00001000 00000000
15:45:53.573735 B40000800 Read-Ack Status: 00001000 00000000
15:45:53.577946 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:54.009796 T80190000 Read-Data Boiler water temperature: 0.00
15:45:54.139934 B40191B00 Read-Ack Boiler water temperature: 27.00
15:45:54.568738 T00000A00 Read-Data Status: 00001010 00000000
15:45:54.572721 R80000800 Read-Data Status: 00001000 00000000
15:45:54.685046 B40000800 Read-Ack Status: 00001000 00000000
15:45:54.689170 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:55.126021 T00000A00 Read-Data Status: 00001010 00000000
15:45:55.129809 R80000800 Read-Data Status: 00001000 00000000
15:45:55.247635 B40000800 Read-Ack Status: 00001000 00000000
15:45:55.252241 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:55.681086 T00000A00 Read-Data Status: 00001010 00000000
15:45:55.685640 R80000800 Read-Data Status: 00001000 00000000
15:45:55.801839 B40000800 Read-Ack Status: 00001000 00000000
15:45:55.806124 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:56.234111 T00000A00 Read-Data Status: 00001010 00000000
15:45:56.238364 R80000800 Read-Data Status: 00001000 00000000
15:45:56.355896 B40000800 Read-Ack Status: 00001000 00000000
15:45:56.360743 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:56.795514 T00000A00 Read-Data Status: 00001010 00000000
15:45:56.799699 R80000800 Read-Data Status: 00001000 00000000
15:45:56.909831 B40000800 Read-Ack Status: 00001000 00000000
15:45:56.913893 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:57.354274 T00000A00 Read-Data Status: 00001010 00000000
15:45:57.358187 R80000800 Read-Data Status: 00001000 00000000
15:45:57.476829 B40000800 Read-Ack Status: 00001000 00000000
15:45:57.480924 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:57.903379 T10010A00 Write-Data Control setpoint: 10.00
15:45:58.028331 BD0010A00 Write-Ack Control setpoint: 10.00
15:45:58.464520 T00000A00 Read-Data Status: 00001010 00000000
15:45:58.468784 R80000800 Read-Data Status: 00001000 00000000
15:45:58.587505 B40000800 Read-Ack Status: 00001000 00000000
15:45:58.591566 AC0000A00 Read-Ack Status: 00001010 00000000
15:45:59.026748 T80190000 Read-Data Boiler water temperature: 0.00
15:45:59.141414 B40191B00 Read-Ack Boiler water temperature: 27.00
15:45:59.577405 T00000A00 Read-Data Status: 00001010 00000000
15:45:59.581709 R80000800 Read-Data Status: 00001000 00000000
15:45:59.697368 B40000800 Read-Ack Status: 00001000 00000000
15:45:59.701396 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:00.136348 T00000A00 Read-Data Status: 00001010 00000000
15:46:00.140409 R80000800 Read-Data Status: 00001000 00000000
15:46:00.256781 B40000800 Read-Ack Status: 00001000 00000000
15:46:00.260857 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:00.698871 T00000A00 Read-Data Status: 00001010 00000000
15:46:00.703455 R80000800 Read-Data Status: 00001000 00000000
15:46:00.810627 B40000800 Read-Ack Status: 00001000 00000000
15:46:00.815859 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:01.284517 T00000A00 Read-Data Status: 00001010 00000000
15:46:01.289217 R80000800 Read-Data Status: 00001000 00000000
15:46:01.402625 B40000800 Read-Ack Status: 00001000 00000000
15:46:01.407076 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:01.852269 T00000A00 Read-Data Status: 00001010 00000000
15:46:01.856474 R80000800 Read-Data Status: 00001000 00000000
15:46:01.957766 B40000800 Read-Ack Status: 00001000 00000000
15:46:01.962425 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:02.414718 T00000A00 Read-Data Status: 00001010 00000000
15:46:02.419052 R80000800 Read-Data Status: 00001000 00000000
15:46:02.529829 B40000800 Read-Ack Status: 00001000 00000000
15:46:02.534224 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:02.975353 T10010A00 Write-Data Control setpoint: 10.00
15:46:03.092009 BD0010A00 Write-Ack Control setpoint: 10.00
15:46:03.519031 T801C0000 Read-Data Return water temperature: 0.00
15:46:03.648394 B401C1A80 Read-Ack Return water temperature: 26.50
15:46:04.087057 T80190000 Read-Data Boiler water temperature: 0.00
15:46:04.205056 B40191B00 Read-Ack Boiler water temperature: 27.00
15:46:04.647005 T00000A00 Read-Data Status: 00001010 00000000
15:46:04.651471 R80000800 Read-Data Status: 00001000 00000000
15:46:04.766433 B40000800 Read-Ack Status: 00001000 00000000
15:46:04.770566 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:05.191739 T00000A00 Read-Data Status: 00001010 00000000
15:46:05.195419 R80000800 Read-Data Status: 00001000 00000000
15:46:05.319395 B40000800 Read-Ack Status: 00001000 00000000
15:46:05.323582 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:05.784201 T00000A00 Read-Data Status: 00001010 00000000
15:46:05.788576 R80000800 Read-Data Status: 00001000 00000000
15:46:05.977013 B40000800 Read-Ack Status: 00001000 00000000
15:46:05.981224 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:06.340236 T00000A00 Read-Data Status: 00001010 00000000
15:46:06.344659 R80000800 Read-Data Status: 00001000 00000000
15:46:06.456818 B40000800 Read-Ack Status: 00001000 00000000
15:46:06.461136 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:06.988828 T00000A00 Read-Data Status: 00001010 00000000
15:46:06.992952 R80000800 Read-Data Status: 00001000 00000000
15:46:07.000575 B40000800 Read-Ack Status: 00001000 00000000
15:46:07.007947 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:07.459621 T00000A00 Read-Data Status: 00001010 00000000
15:46:07.463442 R80000800 Read-Data Status: 00001000 00000000
15:46:07.572581 B40000800 Read-Ack Status: 00001000 00000000
15:46:07.577911 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:08.009616 T10010A00 Write-Data Control setpoint: 10.00
15:46:08.126967 BD0010A00 Write-Ack Control setpoint: 10.00
15:46:08.566091 T001B0000 Read-Data Outside temperature: 0.00
15:46:08.570302 R80190000 Read-Data Boiler water temperature: 0.00
15:46:08.687858 B40191B00 Read-Ack Boiler water temperature: 27.00
15:46:08.692243 AC01B0B80 Read-Ack Outside temperature: 11.50
15:46:09.125489 T80190000 Read-Data Boiler water temperature: 0.00
15:46:09.242901 B40191B00 Read-Ack Boiler water temperature: 27.00
15:46:09.681864 T00000A00 Read-Data Status: 00001010 00000000
15:46:09.685847 R80000800 Read-Data Status: 00001000 00000000
15:46:09.803779 B40000800 Read-Ack Status: 00001000 00000000
15:46:09.807690 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:10.239708 T00000A00 Read-Data Status: 00001010 00000000
15:46:10.243758 R80000800 Read-Data Status: 00001000 00000000
15:46:10.357910 B40000800 Read-Ack Status: 00001000 00000000
15:46:10.362030 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:10.792804 T00000A00 Read-Data Status: 00001010 00000000
15:46:10.797023 R80000800 Read-Data Status: 00001000 00000000
15:46:10.913995 B40000800 Read-Ack Status: 00001000 00000000
15:46:10.918174 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:11.351993 T00000A00 Read-Data Status: 00001010 00000000
15:46:11.355958 R80000800 Read-Data Status: 00001000 00000000
15:46:11.471851 B40000800 Read-Ack Status: 00001000 00000000
15:46:11.477024 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:11.908083 T00000A00 Read-Data Status: 00001010 00000000
15:46:11.912478 R80000800 Read-Data Status: 00001000 00000000
15:46:12.030508 B40000800 Read-Ack Status: 00001000 00000000
15:46:12.034300 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:12.462961 T00000A00 Read-Data Status: 00001010 00000000
15:46:12.467326 R80000800 Read-Data Status: 00001000 00000000
15:46:12.581230 B40000800 Read-Ack Status: 00001000 00000000
15:46:12.585307 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:13.019206 T10010A00 Write-Data Control setpoint: 10.00
15:46:13.145210 BD0010A00 Write-Ack Control setpoint: 10.00
15:46:13.572789 T801A0000 Read-Data DHW temperature: 0.00
15:46:13.698252 BC01A1880 Read-Ack DHW temperature: 24.50
15:46:14.129245 T80190000 Read-Data Boiler water temperature: 0.00
15:46:14.258594 B40191B00 Read-Ack Boiler water temperature: 27.00
15:46:14.699213 T00000A00 Read-Data Status: 00001010 00000000
15:46:14.703792 R80000800 Read-Data Status: 00001000 00000000
15:46:14.809719 B40000800 Read-Ack Status: 00001000 00000000
15:46:14.813709 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:15.285360 T00000A00 Read-Data Status: 00001010 00000000
15:46:15.289625 R80000800 Read-Data Status: 00001000 00000000
15:46:15.402439 B40000800 Read-Ack Status: 00001000 00000000
15:46:15.407156 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:15.840185 T00000A00 Read-Data Status: 00001010 00000000
15:46:15.844754 R80000800 Read-Data Status: 00001000 00000000
15:46:15.958453 B40000800 Read-Ack Status: 00001000 00000000
15:46:15.962392 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:16.396714 T00000A00 Read-Data Status: 00001010 00000000
15:46:16.400618 R80000800 Read-Data Status: 00001000 00000000
15:46:16.514661 B40000800 Read-Ack Status: 00001000 00000000
15:46:16.519152 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:16.953874 T00000A00 Read-Data Status: 00001010 00000000
15:46:16.957651 R80000800 Read-Data Status: 00001000 00000000
15:46:17.070883 B40000800 Read-Ack Status: 00001000 00000000
15:46:17.075069 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:17.526701 T00000A00 Read-Data Status: 00001010 00000000
15:46:17.530820 R80000800 Read-Data Status: 00001000 00000000
15:46:17.645871 B40000800 Read-Ack Status: 00001000 00000000
15:46:17.649984 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:18.084158 T10010A00 Write-Data Control setpoint: 10.00
15:46:18.204205 BD0010A00 Write-Ack Control setpoint: 10.00
15:46:18.638684 T00090000 Read-Data Remote override room setpoint: 0.00
15:46:18.642617 R801A0000 Read-Data DHW temperature: 0.00
15:46:18.750158 BC01A1880 Read-Ack DHW temperature: 24.50
15:46:18.754141 AC0091080 Read-Ack Remote override room setpoint: 16.50
15:46:19.198443 T80190000 Read-Data Boiler water temperature: 0.00
15:46:19.312248 B40191B00 Read-Ack Boiler water temperature: 27.00
15:46:19.783979 T80640000 Read-Data Remote override function: 00000000
15:46:19.788082 R007D0000 Read-Data OpenTherm version Slave: 0.00
15:46:19.907533 B407D0203 Read-Ack OpenTherm version Slave: 2.01
15:46:19.912082 A40640003 Read-Ack Remote override function: 00000011
15:46:20.435607 T00000A00 Read-Data Status: 00001010 00000000
15:46:20.440050 R80000800 Read-Data Status: 00001000 00000000
15:46:20.445671 B40000800 Read-Ack Status: 00001000 00000000
15:46:20.452807 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:20.896028 T00000A00 Read-Data Status: 00001010 00000000
15:46:20.900184 R80000800 Read-Data Status: 00001000 00000000
15:46:21.018185 B40000800 Read-Ack Status: 00001000 00000000
15:46:21.022316 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:21.458115 T00000A00 Read-Data Status: 00001010 00000000
15:46:21.462862 R80000800 Read-Data Status: 00001000 00000000
15:46:21.574191 B40000800 Read-Ack Status: 00001000 00000000
15:46:21.578582 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:22.011464 T00000A00 Read-Data Status: 00001010 00000000
15:46:22.015875 R80000800 Read-Data Status: 00001000 00000000
15:46:22.130324 B40000800 Read-Ack Status: 00001000 00000000
15:46:22.137246 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:22.572253 T00000A00 Read-Data Status: 00001010 00000000
15:46:22.576779 R80000800 Read-Data Status: 00001000 00000000
15:46:22.686620 B40000800 Read-Ack Status: 00001000 00000000
15:46:22.691177 AC0000A00 Read-Ack Status: 00001010 00000000
15:46:23.125808 T10010A00 Write-Data Control setpoint: 10.00
15:46:23.245608 BD0010A00 Write-Ack Control setpoint: 10.00
15:46:23.681323 T90101000 Write-Data Room setpoint: 16.00
Last edited by RedNax on Sun Oct 13, 2013 7:16 am, edited 1 time in total.
-
- Starting Member
- Posts: 22
- Joined: Tue Oct 01, 2013 3:27 pm
Re: Opentherm Gateway
My hardware is indeed slow. It's running on a raspberry pi.
I will connect it to my normal computer and resend you a log, maybe it's of any help for you. But proberly the gaps are explained.
As REDNAX confirmes, manually you can set it at half degrees.
It however accepts 16.5 temperatures, but just rounds it down.
guess it doesn't leaves me anything but changing my script to just send whole degrees to the gateway.
Grrr.. especially bought this thermostat two weeks ago bc. it seemed to supports a lot of functions according to the matrix ;(
Let's hope the project expands, and more people upload their log's so i'll know what thermostat to buy next time
Does anyone have some advice of a good thermostat? bought this one on marktplaats, but i can just sell it and buy another.
I first wanted to buy a isense, but they told me that that one is only working with a remeha cv ketel, not with a atag, even though its using opentherm.
I will connect it to my normal computer and resend you a log, maybe it's of any help for you. But proberly the gaps are explained.
As REDNAX confirmes, manually you can set it at half degrees.
It however accepts 16.5 temperatures, but just rounds it down.
guess it doesn't leaves me anything but changing my script to just send whole degrees to the gateway.
Grrr.. especially bought this thermostat two weeks ago bc. it seemed to supports a lot of functions according to the matrix ;(
Let's hope the project expands, and more people upload their log's so i'll know what thermostat to buy next time

Does anyone have some advice of a good thermostat? bought this one on marktplaats, but i can just sell it and buy another.
I first wanted to buy a isense, but they told me that that one is only working with a remeha cv ketel, not with a atag, even though its using opentherm.
Re: Opentherm Gateway
How quaint that the Honeywell Vision and Touch won't accept half degrees over the opentherm interface. I guess they thought it would be easier to just deal with the byte containing the units. In hindsight I have been really lucky with my choice of thermostat. The installer was initially going to use a Vision for me too, but I insisted on getting the Chronotherm.
I think it's nonsense that the Remeha iSense won't work with an ATAG heater. But it does have even more issues with its opentherm implementation than the Honeywell Vision. So it was good advice for the wrong reasons.
Is it really a big deal that the thermostat only accepts full degrees? I find that in normal use I hardly ever need to send half degree values through the opentherm interface.
You don't have go through a lot of trouble to create a log with a different computer. The confirmation that otmonitor was running on a Raspberry Pi is good enough for me.
I think it's nonsense that the Remeha iSense won't work with an ATAG heater. But it does have even more issues with its opentherm implementation than the Honeywell Vision. So it was good advice for the wrong reasons.
Is it really a big deal that the thermostat only accepts full degrees? I find that in normal use I hardly ever need to send half degree values through the opentherm interface.
You don't have go through a lot of trouble to create a log with a different computer. The confirmation that otmonitor was running on a Raspberry Pi is good enough for me.
Schelte
Re: Opentherm Gateway
I'm also experimenting with the Honeywell Vision Modulation Touch. When I do a temperature setpoint override via the gateway at my thermostat a "H with a roof over it" symbol also appears.RedNax wrote:Honeywell Vision Modulation Touch
Using the thermostat you can set to .5 degree resolution. Setting Override setpoint throught he gateway will be truncated to the nearest whole degree (16.5 -> 16).
EDIT: The Vision will display an undocumented symbol.. looks like an H with a roof over it..
1000 00000000
I couldn't override the setpoint yesterday. Once it accepted it, but most of the time not. I tested with 0.5 increments. After I read about the full degree increments I reconnected everything today and I got strange frequency errors on my boiler (AGPO Ferolli MegaDens 5) and it went flipping with connection and the error (F35). So I disconnected everything, because I don't want to fry the electric board of the boiler.

The gateway I used is borrowed to test before I buy one, but I have one concern that I can damage my boiler or thermostat with it by hardware or sending signals which are not recognized/implemented on the equipment.
Re: Opentherm Gateway
That is a Honeywell "Hometronic" symbol, I also noticed it after sending setpoint overrides.RedNax wrote:Honeywell Vision Modulation Touch
EDIT: The Vision will display an undocumented symbol.. looks like an H with a roof over it..
Some info:
historical-products.ecc.emea.honeywell. ... _le01.html
http://www.zaatsidee.nl/pdf/Hometronictech.pdf
Re: Opentherm Gateway
If you take a look at the gateway schematic, you'll see that there are only a few components connected to the boiler, opto-isolated from the rest of the circuitry. The power for that part of the device actually comes from the boiler, so there's really not much chance for the gateway to fry the electric board of the boiler. The worst it could possibly do is short-circuit the two wires from the boiler. An opentherm interface should be able to cope with that.Joep wrote:So I disconnected everything, because I don't want to fry the electric board of the boiler.
If you are seriously considering using the gateway I'll be happy to work with you to figure out the issues. But then I will need a clearer description, because I have no idea what "strange frequency errors" and "flipping with connection and the error" means. Please also collect logs covering the problem scenario(s).
Schelte
Re: Opentherm Gateway
Thank you for your comment. I really want to incorporate the gateway in my home automation
The boiler reported: Main frequency error. The print may have been defective. Replace it. When I connected the cables directly to my Honeywell thermostat everything started working again. Maybe it was a bad wiring problem, because last Sunday everything worked for 2 hours testing.
I'm going to buy new wires and test again. I'll report my findings here with logging if it goes wrong again.

The boiler reported: Main frequency error. The print may have been defective. Replace it. When I connected the cables directly to my Honeywell thermostat everything started working again. Maybe it was a bad wiring problem, because last Sunday everything worked for 2 hours testing.
I'm going to buy new wires and test again. I'll report my findings here with logging if it goes wrong again.

Re: Opentherm Gateway
That does sound scary. I can understand your trepidation.Joep wrote:The boiler reported: Main frequency error. The print may have been defective. Replace it.
You may send the logs directly to me. I will let you know my email address via PM.
Schelte
Re: Opentherm Gateway
I tri to run the script for the first time.
Interface is 192.168.178.55 poort 1001 (works with ot monitor)
What must be in the script?
LOG
communication: Object reference not set to an instance of an object.
17-10-2013 20:33:20 Warning Attempt to send to COM port 8, port is not open
17-10-2013 20:33:20 debugOTGW3 SendMessageSerial;Message: = SerialPort: 8
17-10-2013 20:33:20 debugOTGW2 SendMessage;Message: =
17-10-2013 20:33:20 debugOTGW2 Send Openthermcommand: =
17-10-2013 20:33:20 debugOTGW2 OTCommand: OTValue:
17-10-2013 20:33:20 debugOTGW SendMessage;Error opening COM8 ,error: Error: Unable to obtain a handle to the COM port
17-10-2013 20:33:20 Error In OpenComPort, error opening port: Unable to obtain a handle to the COM port
17-10-2013 20:33:20 debugOTGW1 Parameters used:
17-10-2013 20:33:20 debugOTGW Debug Level: 3
17-10-2013 20:33:20 Event Running script in background: BLB_OT_monitor_02.vb
script
[Startup]
Version=0.2
Telnet=False
SerialControlInScript=False
SerialPort=8
SerialPortConfig=9600,N,8,1
TCPAddress=192.168.178.55
TCPPort=1001
HouseCode=W
DevLocation=CV
DevLocationswitched=False
Debug=3
[Gateway]
FirstDC=1
Celcia20=False
LEDS=RHOM
ReferenceVoltage=1.25
DevLocation2=Zolder
[Devices]
TemporaryTemperature=W7
OutsideTemperature=?22
[OTPSCodes]
FirstDC=10
dev_type_string=Remeha Calenta
DevLocation2=Huis
[OTDatabase]
Path=C:\Program Files\HomeSeer HSPRO\data\OT\OT.mdb
Whats wrong?
Interface is 192.168.178.55 poort 1001 (works with ot monitor)
What must be in the script?
LOG
communication: Object reference not set to an instance of an object.
17-10-2013 20:33:20 Warning Attempt to send to COM port 8, port is not open
17-10-2013 20:33:20 debugOTGW3 SendMessageSerial;Message: = SerialPort: 8
17-10-2013 20:33:20 debugOTGW2 SendMessage;Message: =
17-10-2013 20:33:20 debugOTGW2 Send Openthermcommand: =
17-10-2013 20:33:20 debugOTGW2 OTCommand: OTValue:
17-10-2013 20:33:20 debugOTGW SendMessage;Error opening COM8 ,error: Error: Unable to obtain a handle to the COM port
17-10-2013 20:33:20 Error In OpenComPort, error opening port: Unable to obtain a handle to the COM port
17-10-2013 20:33:20 debugOTGW1 Parameters used:
17-10-2013 20:33:20 debugOTGW Debug Level: 3
17-10-2013 20:33:20 Event Running script in background: BLB_OT_monitor_02.vb
script
[Startup]
Version=0.2
Telnet=False
SerialControlInScript=False
SerialPort=8
SerialPortConfig=9600,N,8,1
TCPAddress=192.168.178.55
TCPPort=1001
HouseCode=W
DevLocation=CV
DevLocationswitched=False
Debug=3
[Gateway]
FirstDC=1
Celcia20=False
LEDS=RHOM
ReferenceVoltage=1.25
DevLocation2=Zolder
[Devices]
TemporaryTemperature=W7
OutsideTemperature=?22
[OTPSCodes]
FirstDC=10
dev_type_string=Remeha Calenta
DevLocation2=Huis
[OTDatabase]
Path=C:\Program Files\HomeSeer HSPRO\data\OT\OT.mdb
Whats wrong?
Re: Opentherm Gateway
Thank you very much for the great support. It's better than the support of my boiler vendor, LOLhvxl wrote:That does sound scary. I can understand your trepidation.Joep wrote:The boiler reported: Main frequency error. The print may have been defective. Replace it.
You may send the logs directly to me. I will let you know my email address via PM.

I reconnected the gateway with new cables, and it's running for one hour now. I think my suspicion was correct, bad wiring.
Still one question. When running otmonitor.exe (great tool btw!) is it possible to feed it or start commands (like OT=) via de command line, so I can run otmonitor on my domotica controller and let my scripting feed it the outside temperature from my weatherstation for example?
Re: Opentherm Gateway
You can open a socket to port 7686 and send your commands.Joep wrote:Still one question. When running otmonitor.exe (great tool btw!) is it possible to feed it or start commands (like OT=) via de command line, so I can run otmonitor on my domotica controller and let my scripting feed it the outside temperature from my weatherstation for example?
Schelte
Re: Opentherm Gateway
There's an issue with my setup when using cmd09 (TT=). The override sp won't be reset on the next thermostat program change. Since my boiler doesn't support the command the gateway returns:
07:14:49.607548 B70640000 Unk-DataId Remote override function: 00000000
07:14:26.584485 T80640000 Read-Data Remote override function: 00000000
07:14:26.754702 AC0640001 Read-Ack Remote override function: 00000001
Which translates to:
enable overruling remote setpoint by manual setpoint change
and
disable overruling remote setpoint by program setpoint change << which seems to be the cause of my warm room this morning.
I've looked at the configuration commands on the site, but couldn't find one to change the gateways response for the 0x64 cmd.
EDIT: SR=100:3 should solve this i guess...
Unfortunately, it didn't have the desired effect:
07:41:26.293955 AC0640001 Read-Ack Remote override function: 00000001
07:14:49.607548 B70640000 Unk-DataId Remote override function: 00000000
07:14:26.584485 T80640000 Read-Data Remote override function: 00000000
07:14:26.754702 AC0640001 Read-Ack Remote override function: 00000001
Which translates to:
enable overruling remote setpoint by manual setpoint change
and
disable overruling remote setpoint by program setpoint change << which seems to be the cause of my warm room this morning.
I've looked at the configuration commands on the site, but couldn't find one to change the gateways response for the 0x64 cmd.
EDIT: SR=100:3 should solve this i guess...
Unfortunately, it didn't have the desired effect:
07:41:26.293955 AC0640001 Read-Ack Remote override function: 00000001