Just a sketch, so I have a Remeha Quinta 30C.
It is connected as follows:

Now I have this box connected between the boiler and the thermostat.
The thermostat can I read but the boiler does not.
I get the following data from the boiler:
This log is created with the diagnosis firmware Opentherm Gateway
The "Round Clock Deluxe" indicates the diagnostic firmware the following:

It shows that it actually has a communication with the Open Therm Gateway.
What I have tried is:
- In place of the modulating clamps are used on the boiler, tried the on / off clamps.
This had the effect that I would be successful boiler connect to the Open Therm Gateway and remove immediately went down the boiler. - Tried other thermostat, same result (Honeywell Modulation (1997-2003))
- Boiler reset with the reset button on the boiler
- Removes resistance between terminal 3 and 11, no effect
- Removes yellow wire, no effect
- Opentherm Gateway taken off several times from the current
- The latest firmware inside shot, gateway 4.0b1 unfortunately does not help that
- The latest monitor tool used Monitor 4.0b3
- Diagnosis (version 1.1) firmware tried above what the outcome
- Tried with the stable version of the firmware (version 3.4)
- Also tried the stable version (3.3) of the monitor
http://otgw.tclcode.com/matrix.cgi
But my idea is Opentherm simply Opentherm and it should just work.
Topic in dutch: http://gathering.tweakers.net/forum/lis ... es/1577141
I'm from the dutch and that is my native language