OTGW communication to Boiler violates OT Protocol v2.2

This Forum is about the Opentherm gateway (OTG) from Schelte

Moderator: hvxl

OTGW communication to Boiler violates OT Protocol v2.2

Postby marsm2m » Sun Nov 03, 2019 6:45 pm

Hello,

HW from Nodo Shop.
PIC16F88P with FW gateway_v4.2.5.hex
OTGW in Gateway mode
Boiler: TERMET WINDSOR 25
Thermostat: Honeywell CT11011

Issue:
As presented on the attached waveform (OTGW425_to_Boiler_Tx_feedback.png), pulses are not as specified in the "Opentherm Protocol v2.2", chapter "3.4.2 Bit Rate and Timing".
Second waveform (OTGW425_Boiler_Response.png) presents response from Boiler.
Although it works, is it possible to be fixed in the OTGW firmware? Very short pulses produces EMI incompatibilities and shall be avoided.
If nobody tried to fix it then I could try but have only sources for 4.2.4. Where sources for 4.2.5 can be found?

Thank You in advance
Attachments
OTGW425_Boiler_Response.png
OTGW425_Boiler_Response.png (163.24 KiB) Viewed 890 times
OTGW425_to_Boiler_Tx_feedback.png
OTGW425_to_Boiler_Tx_feedback.png (137.45 KiB) Viewed 890 times
marsm2m
Starting Member
Starting Member
 
Posts: 3
Joined: November 2019

Re: OTGW communication to Boiler violates OT Protocol v2.2

Postby hvxl » Sun Nov 03, 2019 10:46 pm

It is unclear to me where you observed those spikes. But if you can improve the OTGW, I'm all for it. The 4.2.5 sources can be found on the OTGW download page.
Schelte
hvxl
Senior Member
Senior Member
 
Posts: 1322
Joined: June 2010