OTGW stops when burner starts
Re: OTGW stops when burner starts
Fortunately that matches with what I see in the simulator when I simulate a rogue signal from the boiler. So my fix stands a chance of actually addressing your problem.
thunderbird
Post by thunderbird »
Good News! The fix helps (as you expected). I see the Error 03 and after that some R messages only. During the first few seconds the message interval is not regular.
Overall it seems to be fixed! Many, many, many thanks! Are you going to 'officially' release this version?
R10010A00
BD0010A00
Error 03
R00000000
R00000000
R00000000
BC0000000
R00110000
BC0110000
R001B0000
B601B0000
R801C0000
BC01C2F00
R00000000
BC0000000
R80190000
B40194100
R10010A00
BD0010A00
R80380000
Error 03
R80380000
R80380000
R80380000
B40383C00
R00390000
B40393200
R00000000
BC0000000
R00000000
That's the original reason I made otmonitor. It reports timestamps for each message, so you can see if the message interval is not regular and which side is causing that. With your logs there's no way to tell.
It looks like your boiler goes off its rocker for a short while at the end of its ventilation cycle.
Now I have your confirmation that it works, I will officially release this firmware.
Astroturf
Post by Astroturf »
Hello Schelte,
Would it be possible to release the source for 4.2.6?
I'm using a patched 4.2.5 (patch to use the DS18B20 sensor for RWT).
Thank you.
Unless you have the same problem as thunderbird, you can just keep on using 4.2.5. I expect there is a version 4.3 to come. I will post the sources again with that release.
thunderbird
Hi, I just installed 5.1 and it seems that this problem (crashing OTGW when burner starts) is back in town. I did not go deep to check if the problem is exactly the same, but it seems so.
Do you know if the patch of 4.2.6 is also in 5.1 (or not)?
Of course I didn't take the fix out again. That would be silly.
Reproducing the problematic signal from the boiler in the simulator with firmware 5.1 also gives the expected result: Just an "Error 03" report and the OTGW keeps on running fine.
