Hi,
I have a Beretta METEO GREEN AND 30 C.S.I. boiler and a BeSMART thermostat from Riello, I connected an OTGW bought from Nodo between the two and I can read the messages they exchange.
The problem is that I cannot control the thermostat with the otmonitor, if I send a Setpoint command the thermostat does nothing.
Is there anything I can do to find the problem or does it mean that my thermostat does not accept opentherm commands?
thank you.
Thermostat not receiving commands from OTGW
Moderator: hvxl
Re: Thermostat not receiving commands from OTGW
Thermostats don't accept commands. They send commands (requests) and receive responses. If a thermostat never sends a request for a setpoint change (MsgID 9), then the OTGW doesn't get an opportunity to send this information on to the thermostat. So, check the summary tab in otmonitor to see if MsgID 9 is listed. Some thermostats have a menu setting to enable this functionality. If neither of these two is available, then this feature won't work with your thermostat.
Most thermostats that can be controlled via an app, like the BeSMART, will not offer this functionality via the OpenTherm interface. Presumably because you can already do it with the app. Which doesn't mean that all thermostats without an accompanying app support it.
Most thermostats that can be controlled via an app, like the BeSMART, will not offer this functionality via the OpenTherm interface. Presumably because you can already do it with the app. Which doesn't mean that all thermostats without an accompanying app support it.

Schelte
Re: Thermostat not receiving commands from OTGW
Thank you for the reply!
I am slowly learning how opentherm works.
this is what I see in the summary tab, there is no MsgID 9:
the last page of this manual https://www.vokera.co.uk/wp-content/upl ... Manual.pdf lists the settings that I can change, but I don't see this functionality.
at this point I think there is no way to use this thermostat
.
I am slowly learning how opentherm works.
this is what I see in the summary tab, there is no MsgID 9:
Code: Select all
Hex Dec Dir Description Freq Value
00 0 Read Status 1 00000000 00000000
01 1 Write Control setpoint 6 5.00
03 3 Read Slave configuration 38 00010001 31
05 5 Read Application-specific flags 2 00000000 0
0B 11 Read TSP setting 5 241 0
0B 11 Write TSP setting 5 240 20
0E 14 Write Maximum relative modulation level 16 100.00
10 16 Write Room setpoint 38 16.20
11 17 Read Relative modulation level 19 0.00
12 18 Read CH water pressure 16 2.50
18 24 Write Room temperature 38 21.60
19 25 Read Boiler water temperature 6 55.90
1A 26 Read DHW temperature 3 34.40
1C 28 Read Return water temperature 16 38.80
30 48 Read DHW setpoint boundaries 38 60 35
31 49 Read Max CH setpoint boundaries 38 80 40
38 56 Read DHW setpoint 38 46.00
39 57 Read Max CH water setpoint 38 80.00
78 120 Read Burner operation hours 20 800
at this point I think there is no way to use this thermostat