Hi All,
I'm using latest OpenTherm Gateway (4.2.8.2) + OpenTherm Monitor 4.5 with Geminox THRi 2-17 M75V (Siemens LMU64) and QAA73.100 controller. As my boiler does not support Remote override room setpoint functionality, I'm using OTMonitor as MQTT client which sending data to Home Assistant.
Some time ago I was trying to find out where Max CH value is set in my boiler (value 89,0 C) as I was not able to use OTmonitor functionality for changing this value. I've made pictures of all my QAA73 setting including those accessible via OEM menu. Today I realized, that one of the QAA setting on line 506 named TvSmin is set to 404.0 C. According to LMU64 documentation this setting is Minimum flow setpoint temperature and it's range is 20-90 C. I'm sure (and also have picture) that some days ago there was standard value (20.0 C) so I was suspicious that this is caused by OTGW and disconnected it from the boiler. Unfortunatelly TvSmin returned back to value of 20.0 C. Just for su I also dowgraded to 4.2.5 and OTMonitor from previous year but no change.
Is it possible, that OTGW is interferencing with QAA73.110 and LMU64?
Is there any Geminox user with OTGW and correct value on line 506?
or am I doing something wrong? should all parts start in different sequence? (1. boiler 2. otgw)
I'm using latest OpenTherm Gateway (4.2.8.2) + OpenTherm Monitor 4.5 with Geminox THRi 2-17 M75V (Siemens LMU64) and QAA73.100 controller. As my boiler does not support Remote override room setpoint functionality, I'm using OTMonitor as MQTT client which sending data to Home Assistant.
Some time ago I was trying to find out where Max CH value is set in my boiler (value 89,0 C) as I was not able to use OTmonitor functionality for changing this value. I've made pictures of all my QAA73 setting including those accessible via OEM menu. Today I realized, that one of the QAA setting on line 506 named TvSmin is set to 404.0 C. According to LMU64 documentation this setting is Minimum flow setpoint temperature and it's range is 20-90 C. I'm sure (and also have picture) that some days ago there was standard value (20.0 C) so I was suspicious that this is caused by OTGW and disconnected it from the boiler. Unfortunatelly TvSmin returned back to value of 20.0 C. Just for su I also dowgraded to 4.2.5 and OTMonitor from previous year but no change.
Is it possible, that OTGW is interferencing with QAA73.110 and LMU64?
Is there any Geminox user with OTGW and correct value on line 506?
or am I doing something wrong? should all parts start in different sequence? (1. boiler 2. otgw)
Re: QAA73.110 showing incorrect values when otgw connected
A remote override room setpoint is something that is contrived ("bekokstoofd") between the OTGW and the thermostat. The boiler does not need to support anything special.
TvSmin and TvSmax sound like the values a boiler may report in MsgID 49. According to the equipment matrix, that is not something the QAA773 normally requests. Maybe it only does when it starts and that has just not been captured in any of the uploaded logs. Even then, the min and max values are each transferred in a byte. So the reported value can never be 404.
To investigate, check the OTGW log for MsgID 49. Maybe restart the QAA73 to force it to ask for things it only requests once. If MsgID 49 doesn't occur, you can use the PM=49 command to make the OTGW request it once from the boiler. Of course, that information will not go to the thermostat in that case.
The order of powering up things should not matter. I'm sure I must have used every combination over the years.
TvSmin and TvSmax sound like the values a boiler may report in MsgID 49. According to the equipment matrix, that is not something the QAA773 normally requests. Maybe it only does when it starts and that has just not been captured in any of the uploaded logs. Even then, the min and max values are each transferred in a byte. So the reported value can never be 404.
To investigate, check the OTGW log for MsgID 49. Maybe restart the QAA73 to force it to ask for things it only requests once. If MsgID 49 doesn't occur, you can use the PM=49 command to make the OTGW request it once from the boiler. Of course, that information will not go to the thermostat in that case.
The order of powering up things should not matter. I'm sure I must have used every combination over the years.
Schelte
Re: QAA73.110 showing incorrect values when otgw connected
Hi Schelte,
I've found only logs from 2 days ago and if I understand correctly that Message ID = Max CH setpoint boundaries I see this:
If Max CH setpoint boundaries MsgID 49 is related to LMU64 values 505 and 506 then something is wrong with my boiler as I can see values 80 20, but in the otmonitor log there is value 89 20.
Maybe I'm looking into wrong values as in the LMU64 documentation there is another line (504 TkSmax Maximum boiler setpoint temperature) which is not visible through QAA73.
I will try to connect otgw between QAA73 and LMU64 and will have a look to line 506 if value 404.0 C is still there and then compare it with MsgID 49 values in the log.
P.S: Would it be possible to add MsgID info into the log in future relases of otmonitor? The same way as seen on your website e.g. Max CH setpoint boundaries (MsgID=49)
I've found only logs from 2 days ago and if I understand correctly that Message ID = Max CH setpoint boundaries I see this:
Code: Select all
----------------------------------------------------------------------------------------------------------------
00:30:54.087234 R80310000 Read-Data Max CH setpoint boundaries: 0 0
00:30:54.448878 B40315914 Read-Ack Max CH setpoint boundaries: 89 20
----------------------------------------------------------------------------------------------------------------
00:31:05.317664 BC0060707 Read-Ack Remote parameter flags: 00000111 00000111
- DHW setpoint transfer: enabled (1)
- max CH setpoint transfer: enabled (1)
- DHW setpoint: read/write (1)
- max CH setpoint: read/write (1)
----------------------------------------------------------------------------------------------------------------
Maybe I'm looking into wrong values as in the LMU64 documentation there is another line (504 TkSmax Maximum boiler setpoint temperature) which is not visible through QAA73.
I will try to connect otgw between QAA73 and LMU64 and will have a look to line 506 if value 404.0 C is still there and then compare it with MsgID 49 values in the log.
P.S: Would it be possible to add MsgID info into the log in future relases of otmonitor? The same way as seen on your website e.g. Max CH setpoint boundaries (MsgID=49)
- Attachments
-
- LMU64 parameters
- LMU64.PNG (164.22 KiB) Viewed 6431 times
-
- 506_TvSmin.PNG (233.31 KiB) Viewed 6431 times
-
- 505_TkSnorm.PNG (245.69 KiB) Viewed 6431 times
Re: QAA73.110 showing incorrect values when otgw connected
Just a quick update on this strange behavior - it looks to me that it's caused by OTGW setting GW=1 (gateway mode).
I've made several tests with 2 different OTGW devices and found line 506 TvSmin with incorrect value 404 C only when OTGW in gateway mode.
Switching back to GW=0 solved this issue.
I believe it's only cosmetic issue and undiscoverable in most cases as most users are not going to check regularly LMU values (which are accessible to OEM/serviceman) using QAA73...
And also value 404 C is out of allowed range for this variable.
I've made several tests with 2 different OTGW devices and found line 506 TvSmin with incorrect value 404 C only when OTGW in gateway mode.
Switching back to GW=0 solved this issue.
I believe it's only cosmetic issue and undiscoverable in most cases as most users are not going to check regularly LMU values (which are accessible to OEM/serviceman) using QAA73...
And also value 404 C is out of allowed range for this variable.
Re: QAA73.110 showing incorrect values when otgw connected
In monitor mode (GW=0), the OTGW can't modify any of the Opentherm messages, while in gateway mode (GW=1) it can. However, it should normally produce mostly the same responses to the thermostat that the boiler would. But apparently there is some difference in the messages the thermostat receives between both modes. Logs of both cases would be interesting.
Schelte
Re: QAA73.110 showing incorrect values when otgw connected
Hi,
I've OTGW (4.2.8.2) + OTM (4.4.1) + Geminox THRi 2-17 M 75 H DC "ZP" (Siemens LMU64) + QAA73.110
What value do you want to find out?
I've OTGW (4.2.8.2) + OTM (4.4.1) + Geminox THRi 2-17 M 75 H DC "ZP" (Siemens LMU64) + QAA73.110
What value do you want to find out?
Re: QAA73.110 showing incorrect values when otgw connected
GW=0 --> value 506 (TvSmin) is set to 20.0 C
GW=1 --> value 506 (TvSmin) is set to 404.0 C
GW=1 --> value 506 (TvSmin) is set to 404.0 C
Re: QAA73.110 showing incorrect values when otgw connected
Thank you for confirming this. I believe it's caused by setting QAA73 to "programming" mode and OTGW somehow interfering communication between QAA and LMU. It's only cosmetic defect found and does not affect boiler performance.fojtp wrote:GW=0 --> value 506 (TvSmin) is set to 20.0 C
GW=1 --> value 506 (TvSmin) is set to 404.0 C
Re: QAA73.110 showing incorrect values when otgw connected
hvxl wrote:Logs of both cases would be interesting.
Schelte
Re: QAA73.110 showing incorrect values when otgw connected
I will post logs for both cases during a weekend as it's not possible to physically get there now (covid rules).
Re: QAA73.110 showing incorrect values when otgw connected
Hi Schelte,
I've managed to test QAA73.110 and OTGW today.
As you can see from the log below my OTGW was set to Gateway mode at 10:14:01, then I entered OEM's mode on QAA73 (in this mode I can change some LMU64 (boiler) values) at 10:14:45 and since that time I see only some strange values in the log (10:14:45 till 10:15:59). All this garbage is captured when QAA73 is in "programming" mode and when I exited this mode, everything was back in normal as it's shown in the log at 10:16:00. I've repeated this exercise with OTGW in Monitor mode (10:16:44 - 10:18:06). I did not check all thermostat/boiler parameters accessible via QAA73, but as for line 506 TvSmin it's correct only when OTGW in Monitor mode (20 C) otherwise it's showing 404 C.
I think this behaviour is based on Geminox/Siemens implementation and has nothing to do with OTGW and I can only suggest to other user to disconnect OTGW when programming/changing parameters normally accessible only by installer/producer.
All the best.
Ivan
I've managed to test QAA73.110 and OTGW today.
As you can see from the log below my OTGW was set to Gateway mode at 10:14:01, then I entered OEM's mode on QAA73 (in this mode I can change some LMU64 (boiler) values) at 10:14:45 and since that time I see only some strange values in the log (10:14:45 till 10:15:59). All this garbage is captured when QAA73 is in "programming" mode and when I exited this mode, everything was back in normal as it's shown in the log at 10:16:00. I've repeated this exercise with OTGW in Monitor mode (10:16:44 - 10:18:06). I did not check all thermostat/boiler parameters accessible via QAA73, but as for line 506 TvSmin it's correct only when OTGW in Monitor mode (20 C) otherwise it's showing 404 C.
I think this behaviour is based on Geminox/Siemens implementation and has nothing to do with OTGW and I can only suggest to other user to disconnect OTGW when programming/changing parameters normally accessible only by installer/producer.
All the best.
Ivan
Code: Select all
10:14:00.894483 T001E0000 Read-Data Solar collector temperature (MsgID=30): 0.00
10:14:01.293386 B601E0000 Data-Inv Solar collector temperature (MsgID=30): 0.00
10:14:01.363715 Command: PR=M
10:14:01.381362 PR: M=G
10:14:01.864259 T00210000 Read-Data Exhaust temperature (MsgID=33): 0
10:14:02.148247 BC0210017 Read-Ack Exhaust temperature (MsgID=33): 23
10:14:02.871254 T10810200 Write-Data Message ID 129 (MsgID=129): 512
10:14:03.138230 BD0810200 Write-Ack Message ID 129 (MsgID=129): 512
10:14:03.860412 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:14:04.127363 BC0000102 Read-Ack Status (MsgID=0): 00000001 00000010
10:14:04.849360 T90101000 Write-Data Room setpoint (MsgID=16): 16.00
10:14:05.116360 B50101000 Write-Ack Room setpoint (MsgID=16): 16.00
10:14:05.888349 T90170000 Write-Data Room Setpoint CH2 (MsgID=23): 0.00
10:14:06.239323 B50170000 Write-Ack Room Setpoint CH2 (MsgID=23): 0.00
10:14:06.860334 T10180FDC Write-Data Room temperature (MsgID=24): 15.86
10:14:07.228303 BD0180FDC Write-Ack Room temperature (MsgID=24): 15.86
10:14:07.849337 T80800000 Read-Data Message ID 128 (MsgID=128): 0
10:14:08.216333 BE0800000 Data-Inv Message ID 128 (MsgID=128): 0
10:14:08.838293 T10823753 Write-Data Message ID 130 (MsgID=130): 14163
10:14:09.206293 BD0823753 Write-Ack Message ID 130 (MsgID=130): 14163
10:14:09.877283 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:14:10.195267 BC0000102 Read-Ack Status (MsgID=0): 00000001 00000010
10:14:10.867253 T10011B00 Write-Data Control setpoint (MsgID=1): 27.00
10:14:11.184249 BD0011B00 Write-Ack Control setpoint (MsgID=1): 27.00
10:14:11.856269 T20080000 Inv-Data Control setpoint 2 (MsgID=8): 0.00
10:14:12.173236 BE0080000 Data-Inv Control setpoint 2 (MsgID=8): 0.00
10:14:12.845236 T10380500 Write-Data DHW setpoint (MsgID=56): 5.00
10:14:13.162204 BD0380500 Write-Ack DHW setpoint (MsgID=56): 5.00
10:14:13.834241 T80200000 Read-Data DHW2 temperature (MsgID=32): 0.00
10:14:14.152211 BE0200000 Data-Inv DHW2 temperature (MsgID=32): 0.00
10:14:14.823200 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
10:14:15.140173 BC01A1154 Read-Ack DHW temperature (MsgID=26): 17.33
10:14:15.862181 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:14:16.130153 BC0000102 Read-Ack Status (MsgID=0): 00000001 00000010
10:14:16.852157 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
10:14:17.119145 BC01B01C4 Read-Ack Outside temperature (MsgID=27): 1.77
10:14:17.841123 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
10:14:18.108200 BC0191988 Read-Ack Boiler water temperature (MsgID=25): 25.53
10:14:18.830131 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
10:14:19.097143 B401C1888 Read-Ack Return water temperature (MsgID=28): 24.53
10:14:19.819072 T801F0000 Read-Data Flow temperature CH2 (MsgID=31): 0.00
10:14:20.086079 BE01F0000 Data-Inv Flow temperature CH2 (MsgID=31): 0.00
10:14:20.808119 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
10:14:21.075037 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
10:14:21.847017 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:14:22.128993 BC0000102 Read-Ack Status (MsgID=0): 00000001 00000010
10:14:22.800096 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:14:23.118022 B70130000 Unk-DataId DHW flow rate (MsgID=19): 0.00
10:14:23.841016 T001D0000 Read-Data Solar storage temperature (MsgID=29): 0.00
10:14:24.240990 BF01D0000 Unk-DataId Solar storage temperature (MsgID=29): 0.00
10:14:24.812061 T001E0000 Read-Data Solar collector temperature (MsgID=30): 0.00
10:14:25.096019 B601E0000 Data-Inv Solar collector temperature (MsgID=30): 0.00
10:14:25.817972 T00210000 Read-Data Exhaust temperature (MsgID=33): 0
10:14:26.084963 BC0210017 Read-Ack Exhaust temperature (MsgID=33): 23
10:14:26.806945 T10810200 Write-Data Message ID 129 (MsgID=129): 512
10:14:27.073944 BD0810200 Write-Ack Message ID 129 (MsgID=129): 512
10:14:27.795973 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:14:28.063949 BC0000102 Read-Ack Status (MsgID=0): 00000001 00000010
10:14:28.785900 T90101000 Write-Data Room setpoint (MsgID=16): 16.00
10:14:29.051934 B50101000 Write-Ack Room setpoint (MsgID=16): 16.00
10:14:29.824887 T90170000 Write-Data Room Setpoint CH2 (MsgID=23): 0.00
10:14:30.174984 B50170000 Write-Ack Room Setpoint CH2 (MsgID=23): 0.00
10:14:30.795969 T10180FDC Write-Data Room temperature (MsgID=24): 15.86
10:14:31.163958 BD0180FDC Write-Ack Room temperature (MsgID=24): 15.86
10:14:31.785862 T80800000 Read-Data Message ID 128 (MsgID=128): 0
10:14:32.152879 BE0800000 Data-Inv Message ID 128 (MsgID=128): 0
10:14:32.774844 T10823753 Write-Data Message ID 130 (MsgID=130): 14163
10:14:33.141859 BD0823753 Write-Ack Message ID 130 (MsgID=130): 14163
10:14:33.813828 T90020004 Write-Data Master configuration (MsgID=2): 00000000 4
10:14:34.131850 B50020004 Write-Ack Master configuration (MsgID=2): 00000000 4
10:14:34.802797 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:14:35.120850 BC0000102 Read-Ack Status (MsgID=0): 00000001 00000010
10:14:35.791831 T90011AF0 Write-Data Control setpoint (MsgID=1): 26.94
10:14:36.109788 B50011AF0 Write-Ack Control setpoint (MsgID=1): 26.94
10:14:36.780772 T20080000 Inv-Data Control setpoint 2 (MsgID=8): 0.00
10:14:37.098752 BE0080000 Data-Inv Control setpoint 2 (MsgID=8): 0.00
10:14:37.770756 T10380500 Write-Data DHW setpoint (MsgID=56): 5.00
10:14:38.087735 BD0380500 Write-Ack DHW setpoint (MsgID=56): 5.00
10:14:38.759724 T80200000 Read-Data DHW2 temperature (MsgID=32): 0.00
10:14:39.076719 BE0200000 Data-Inv DHW2 temperature (MsgID=32): 0.00
10:14:39.798706 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
10:14:40.065734 BC01A1154 Read-Ack DHW temperature (MsgID=26): 17.33
10:14:40.787719 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:14:41.055689 B4000010A Read-Ack Status (MsgID=0): 00000001 00001010
10:14:41.776679 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
10:14:42.044670 BC01B01C4 Read-Ack Outside temperature (MsgID=27): 1.77
10:14:42.765660 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
10:14:43.032679 B401919D0 Read-Ack Boiler water temperature (MsgID=25): 25.81
10:14:43.754647 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
10:14:44.022681 B401C1860 Read-Ack Return water temperature (MsgID=28): 24.38
10:14:44.236636 T01000100 Read-Data Status (MsgID=0): 00000001 00000000
10:14:44.615610 BC110D21B Read-Ack Room setpoint (MsgID=16): -45.89
10:14:44.784630 T01000100 Read-Data Status (MsgID=0): 00000001 00000000
10:14:45.075606 BC110D21B Read-Ack Room setpoint (MsgID=16): -45.89
10:14:45.313616 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:14:45.604608 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:14:45.777603 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:14:46.064649 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:14:46.281633 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:14:46.593607 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:14:46.811607 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:14:47.187576 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:14:47.387579 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:14:47.780577 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:14:48.056574 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:14:48.374561 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:14:48.642563 T811001FF Read-Data Room setpoint (MsgID=16): 2.00
10:14:48.967546 BC1E30404 Read-Ack Message ID 227 (MsgID=227): 1028
10:14:49.145533 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:49.427532 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:49.637520 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:49.957526 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:50.145519 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:50.416517 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:50.675514 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:50.945551 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:51.122507 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:51.406512 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:51.632509 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:51.935653 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:52.150498 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:52.528492 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:52.744494 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:53.122479 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:53.350468 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:53.715463 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:53.942453 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:54.309438 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:54.596439 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:54.902421 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:55.117431 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:55.495448 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:55.682434 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:55.956445 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:56.315428 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:56.683406 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:57.068557 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:57.340456 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:57.634707 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:57.934438 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:58.102402 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:58.463372 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:58.682378 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:59.056383 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:59.305355 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:14:59.650357 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:14:59.878362 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:15:00.001523 Command: SC=10:15/3
10:15:00.029389 SC: 10:15/3
10:15:00.243414 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:15:00.536529 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:15:00.837387 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:15:01.118379 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:15:01.430345 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:15:01.651332 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:15:02.023925 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:15:02.252381 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:15:02.617364 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:15:02.802321 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:15:03.077311 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:15:03.285302 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:15:03.606282 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:15:03.811285 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:15:04.200287 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:15:04.368278 T01000200 Read-Data Status (MsgID=0): 00000010 00000000
10:15:04.659262 B4105D20A Read-Ack Application-specific flags (MsgID=5): 11010010 10
10:15:04.828278 T01000200 Read-Data Status (MsgID=0): 00000010 00000000
10:15:05.188266 B4105D20A Read-Ack Application-specific flags (MsgID=5): 11010010 10
10:15:05.400272 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:15:05.782251 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:15:06.027252 T03050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:15:06.375229 BC305B428 Read-Ack Application-specific flags (MsgID=5): 10110100 40
10:15:06.619218 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:15:06.969225 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:15:07.188229 T03050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:15:07.562208 BC305B428 Read-Ack Application-specific flags (MsgID=5): 10110100 40
10:15:07.756238 Thermostat disconnected
10:15:07.793231 Error 03
10:15:07.822250 Thermostat connected
10:15:08.699221 T03050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:15:09.012193 BC305B428 Read-Ack Application-specific flags (MsgID=5): 10110100 40
10:15:09.202190 T03050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:15:09.541181 BC305B428 Read-Ack Application-specific flags (MsgID=5): 10110100 40
10:15:09.710172 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:15:10.002609 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:15:10.208208 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:15:10.530194 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:15:10.727171 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:15:11.124184 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:15:11.333162 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:15:11.717205 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:15:11.901193 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:15:12.177165 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:15:12.509154 T010502FF Read-Data Application-specific flags (MsgID=5): 00000010 255
10:15:12.904149 BC1FF0304 Read-Ack Message ID 255 (MsgID=255): 772
10:15:13.141149 T82FF0000 Read-Data Message ID 255 (MsgID=255): 0
10:15:13.498120 BC2FF0484 Read-Ack Message ID 255 (MsgID=255): 1156
10:15:13.691127 T82FF0000 Read-Data Message ID 255 (MsgID=255): 0
10:15:14.091136 BC2FF046A Read-Ack Message ID 255 (MsgID=255): 1130
10:15:14.267191 T82FF0000 Read-Data Message ID 255 (MsgID=255): 0
10:15:14.551131 BC2FF043C Read-Ack Message ID 255 (MsgID=255): 1084
10:15:14.734116 T82FF0000 Read-Data Message ID 255 (MsgID=255): 0
10:15:15.080123 B42FF044F Read-Ack Message ID 255 (MsgID=255): 1103
10:15:15.375102 T82FF0000 Read-Data Message ID 255 (MsgID=255): 0
10:15:15.673103 B42FF044C Read-Ack Message ID 255 (MsgID=255): 1100
10:15:15.842115 T82FF0000 Read-Data Message ID 255 (MsgID=255): 0
10:15:16.133103 B42FF0445 Read-Ack Message ID 255 (MsgID=255): 1093
10:15:16.430095 T01FF0200 Read-Data Message ID 255 (MsgID=255): 512
10:15:16.727084 B4105D20A Read-Ack Application-specific flags (MsgID=5): 11010010 10
10:15:16.919087 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:15:17.256095 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:15:17.442047 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:15:17.716058 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:15:17.891012 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:15:18.245033 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:15:18.542024 T01050200 Read-Data Application-specific flags (MsgID=5): 00000010 0
10:15:18.850008 B4106D20A Read-Ack Remote parameter flags (MsgID=6): 11010010 00001010
10:15:18.855346 AC106D30A Read-Ack Remote parameter flags (MsgID=6): 11010011 00001010
10:15:19.054021 T84060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:15:19.444046 BE4060000 Data-Inv Remote parameter flags (MsgID=6): 00000000 00000000
10:15:19.449265 A44060300 Read-Ack Remote parameter flags (MsgID=6): 00000011 00000000
10:15:19.668066 T84060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:15:20.037021 BE4060000 Data-Inv Remote parameter flags (MsgID=6): 00000000 00000000
10:15:20.042354 A44060300 Read-Ack Remote parameter flags (MsgID=6): 00000011 00000000
10:15:20.268038 T84060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:15:20.630985 BE4060000 Data-Inv Remote parameter flags (MsgID=6): 00000000 00000000
10:15:20.636166 A44060300 Read-Ack Remote parameter flags (MsgID=6): 00000011 00000000
10:15:20.896010 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:15:21.224011 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:15:21.229243 A42060328 Read-Ack Remote parameter flags (MsgID=6): 00000011 00101000
10:15:21.397974 T05060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:15:21.683995 B65060000 Data-Inv Remote parameter flags (MsgID=6): 00000000 00000000
10:15:21.689126 AC5060300 Read-Ack Remote parameter flags (MsgID=6): 00000011 00000000
10:15:21.841962 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:15:22.212987 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:15:22.218411 A42060328 Read-Ack Remote parameter flags (MsgID=6): 00000011 00101000
10:15:22.402962 T05060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:15:22.806961 B65060000 Data-Inv Remote parameter flags (MsgID=6): 00000000 00000000
10:15:22.812239 AC5060300 Read-Ack Remote parameter flags (MsgID=6): 00000011 00000000
10:15:23.006971 T84060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:15:23.399980 BE4060000 Data-Inv Remote parameter flags (MsgID=6): 00000000 00000000
10:15:23.405376 A44060300 Read-Ack Remote parameter flags (MsgID=6): 00000011 00000000
10:15:23.564946 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:15:23.859981 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:15:23.865215 A42060328 Read-Ack Remote parameter flags (MsgID=6): 00000011 00101000
10:15:24.133937 T01060200 Read-Data Remote parameter flags (MsgID=6): 00000010 00000000
10:15:24.441891 BC107D20A Read-Ack Cooling control signal (MsgID=7): -45.96
10:15:24.685910 T83070000 Read-Data Cooling control signal (MsgID=7): 0.00
10:15:24.970907 B4307B428 Read-Ack Cooling control signal (MsgID=7): -75.84
10:15:25.170900 T83070000 Read-Data Cooling control signal (MsgID=7): 0.00
10:15:25.564900 B4307B428 Read-Ack Cooling control signal (MsgID=7): -75.84
10:15:25.771931 T83070000 Read-Data Cooling control signal (MsgID=7): 0.00
10:15:26.157893 B4307B428 Read-Ack Cooling control signal (MsgID=7): -75.84
10:15:26.422876 T83070000 Read-Data Cooling control signal (MsgID=7): 0.00
10:15:26.750874 B4307B428 Read-Ack Cooling control signal (MsgID=7): -75.84
10:15:27.053882 T02070000 Read-Data Cooling control signal (MsgID=7): 0.00
10:15:27.344860 B4207008C Read-Ack Cooling control signal (MsgID=7): 0.55
10:15:27.531916 T02070000 Read-Data Cooling control signal (MsgID=7): 0.00
10:15:27.804858 B4207008C Read-Ack Cooling control signal (MsgID=7): 0.55
10:15:27.978850 T02070000 Read-Data Cooling control signal (MsgID=7): 0.00
10:15:28.333851 B4207008C Read-Ack Cooling control signal (MsgID=7): 0.55
10:15:28.550835 T02070000 Read-Data Cooling control signal (MsgID=7): 0.00
10:15:28.927891 B4207008C Read-Ack Cooling control signal (MsgID=7): 0.55
10:15:29.143900 T02070000 Read-Data Cooling control signal (MsgID=7): 0.00
10:15:29.520816 B4207008C Read-Ack Cooling control signal (MsgID=7): 0.55
10:15:29.716820 T02070000 Read-Data Cooling control signal (MsgID=7): 0.00
10:15:30.139690 B4207008C Read-Ack Cooling control signal (MsgID=7): 0.55
10:15:30.563295 T02070000 Read-Data Cooling control signal (MsgID=7): 0.00
10:15:30.574840 B4207008C Read-Ack Cooling control signal (MsgID=7): 0.55
10:15:30.803871 T81070200 Read-Data Cooling control signal (MsgID=7): 2.00
10:15:31.102843 B410AD20A Read-Ack Number of TSPs (MsgID=10): 210
10:15:31.344808 T030A0000 Read-Data Number of TSPs (MsgID=10): 0
10:15:31.696790 BC30A3C00 Read-Ack Number of TSPs (MsgID=10): 60
10:15:31.931847 T820A0000 Read-Data Number of TSPs (MsgID=10): 0
10:15:32.290780 B420A0024 Read-Ack Number of TSPs (MsgID=10): 0
10:15:32.496748 T820A0000 Read-Data Number of TSPs (MsgID=10): 0
10:15:32.883924 B420A0024 Read-Ack Number of TSPs (MsgID=10): 0
10:15:33.052790 T030A0000 Read-Data Number of TSPs (MsgID=10): 0
10:15:33.343813 BC30A3C00 Read-Ack Number of TSPs (MsgID=10): 60
10:15:33.553743 T010A0200 Read-Data Number of TSPs (MsgID=10): 2
10:15:33.872736 BC110D21B Read-Ack Room setpoint (MsgID=16): -45.89
10:15:34.055740 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:15:34.332740 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:15:34.607740 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:15:34.926729 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:15:35.107808 T81100200 Read-Data Room setpoint (MsgID=16): 2.00
10:15:35.455739 BC113D11B Read-Ack DHW flow rate (MsgID=19): -46.89
10:15:35.635718 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:35.915731 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:36.120694 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:36.444692 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:36.659693 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:37.037688 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:37.230684 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:37.498706 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:37.715687 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:38.026676 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:38.271672 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:38.620661 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:38.815660 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:39.213657 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:39.469647 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:39.807645 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:40.002280 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:40.400633 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:40.599631 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:40.994620 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:41.208626 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:41.587611 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:41.792598 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:42.181654 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:42.412633 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:42.774622 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:42.975602 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:43.368591 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:43.622594 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:43.961617 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:44.181627 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:44.555578 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:44.732566 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:45.014562 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:45.208569 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:45.544552 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:45.758559 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:46.137546 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:46.316550 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:46.597533 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:46.768534 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:47.126534 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:47.361568 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:47.720567 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:47.923550 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:48.313522 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:48.529502 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:48.907510 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:49.113484 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:49.500497 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:49.776475 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:50.094529 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:50.311479 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:50.687470 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:50.977462 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:51.281460 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:51.474447 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:51.741454 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:52.010617 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:52.334491 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:52.540416 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:52.863440 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:53.120420 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:53.457408 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:53.651395 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:53.917421 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:54.090405 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:54.446381 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:54.660382 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:55.039374 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:55.330386 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:55.633372 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:55.869378 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:56.226365 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:56.444415 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:56.820363 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:57.026338 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:57.414340 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:57.587340 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:57.873364 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:58.095339 T83130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:58.402309 BC31314CE Read-Ack DHW flow rate (MsgID=19): 20.80
10:15:58.631319 T02130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:15:58.996321 B421300F1 Read-Ack DHW flow rate (MsgID=19): 0.94
10:15:59.042330 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
10:15:59.981448 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
10:16:00.001054 Command: SC=10:16/3
10:16:00.029340 SC: 10:16/3
10:16:00.544591 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
10:16:00.952347 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:16:01.236313 B4000010A Read-Ack Status (MsgID=0): 00000001 00001010
10:16:01.958346 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:16:02.226304 B70130000 Unk-DataId DHW flow rate (MsgID=19): 0.00
10:16:02.947278 T001D0000 Read-Data Solar storage temperature (MsgID=29): 0.00
10:16:03.215297 BF01D0000 Unk-DataId Solar storage temperature (MsgID=29): 0.00
10:16:03.938269 T001E0000 Read-Data Solar collector temperature (MsgID=30): 0.00
10:16:04.337278 B601E0000 Data-Inv Solar collector temperature (MsgID=30): 0.00
10:16:04.958230 T00210000 Read-Data Exhaust temperature (MsgID=33): 0
10:16:05.326218 BC0210018 Read-Ack Exhaust temperature (MsgID=33): 24
10:16:05.948201 T10810200 Write-Data Message ID 129 (MsgID=129): 512
10:16:06.315197 BD0810200 Write-Ack Message ID 129 (MsgID=129): 512
10:16:06.937191 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:16:07.304160 B4000010A Read-Ack Status (MsgID=0): 00000001 00001010
10:16:07.976341 T90101000 Write-Data Room setpoint (MsgID=16): 16.00
10:16:08.294180 B50101000 Write-Ack Room setpoint (MsgID=16): 16.00
10:16:08.965155 T90170000 Write-Data Room Setpoint CH2 (MsgID=23): 0.00
10:16:09.283118 B50170000 Write-Ack Room Setpoint CH2 (MsgID=23): 0.00
10:16:09.954123 T10181014 Write-Data Room temperature (MsgID=24): 16.08
10:16:10.272142 BD0181014 Write-Ack Room temperature (MsgID=24): 16.08
10:16:10.944213 T80800000 Read-Data Message ID 128 (MsgID=128): 0
10:16:11.261111 BE0800000 Data-Inv Message ID 128 (MsgID=128): 0
10:16:11.933154 T10823753 Write-Data Message ID 130 (MsgID=130): 14163
10:16:12.250096 BD0823753 Write-Ack Message ID 130 (MsgID=130): 14163
10:16:12.921080 T00030000 Read-Data Slave configuration (MsgID=3): 00000000 0
10:16:13.239072 B40030904 Read-Ack Slave configuration (MsgID=3): 00001001 4
10:16:13.961078 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:16:14.228081 B4000010A Read-Ack Status (MsgID=0): 00000001 00001010
10:16:14.950045 T10011A04 Write-Data Control setpoint (MsgID=1): 26.02
10:16:15.217032 BD0011A04 Write-Ack Control setpoint (MsgID=1): 26.02
10:16:15.939045 T20080000 Inv-Data Control setpoint 2 (MsgID=8): 0.00
10:16:16.207020 BE0080000 Data-Inv Control setpoint 2 (MsgID=8): 0.00
10:16:16.929015 T10380500 Write-Data DHW setpoint (MsgID=56): 5.00
10:16:17.196021 BD0380500 Write-Ack DHW setpoint (MsgID=56): 5.00
10:16:17.917002 T80200000 Read-Data DHW2 temperature (MsgID=32): 0.00
10:16:18.184987 BE0200000 Data-Inv DHW2 temperature (MsgID=32): 0.00
10:16:18.907018 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
10:16:19.173973 BC01A1154 Read-Ack DHW temperature (MsgID=26): 17.33
10:16:19.945960 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:16:20.226949 B4000010A Read-Ack Status (MsgID=0): 00000001 00001010
10:16:20.898938 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
10:16:21.215970 BC01B01C4 Read-Ack Outside temperature (MsgID=27): 1.77
10:16:21.937893 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
10:16:22.204916 B40191E84 Read-Ack Boiler water temperature (MsgID=25): 30.52
10:16:22.927960 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
10:16:23.194909 B401C183C Read-Ack Return water temperature (MsgID=28): 24.23
10:16:23.916915 T801F0000 Read-Data Flow temperature CH2 (MsgID=31): 0.00
10:16:24.183919 BE01F0000 Data-Inv Flow temperature CH2 (MsgID=31): 0.00
10:16:24.905877 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
10:16:25.172857 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
10:16:25.894836 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:16:26.161814 B4000010A Read-Ack Status (MsgID=0): 00000001 00001010
10:16:26.883906 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:16:27.150839 B70130000 Unk-DataId DHW flow rate (MsgID=19): 0.00
10:16:27.922823 T001D0000 Read-Data Solar storage temperature (MsgID=29): 0.00
10:16:28.273853 BF01D0000 Unk-DataId Solar storage temperature (MsgID=29): 0.00
10:16:28.895866 T001E0000 Read-Data Solar collector temperature (MsgID=30): 0.00
10:16:29.262795 B601E0000 Data-Inv Solar collector temperature (MsgID=30): 0.00
10:16:29.883831 T00210000 Read-Data Exhaust temperature (MsgID=33): 0
10:16:30.251887 BC0210018 Read-Ack Exhaust temperature (MsgID=33): 24
10:16:30.872793 T10810200 Write-Data Message ID 129 (MsgID=129): 512
10:16:31.240799 BD0810200 Write-Ack Message ID 129 (MsgID=129): 512
10:16:31.912779 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:16:32.229716 B4000010A Read-Ack Status (MsgID=0): 00000001 00001010
10:16:32.901729 T90101000 Write-Data Room setpoint (MsgID=16): 16.00
10:16:33.219706 B50101000 Write-Ack Room setpoint (MsgID=16): 16.00
10:16:33.890753 T90170000 Write-Data Room Setpoint CH2 (MsgID=23): 0.00
10:16:34.207694 B50170000 Write-Ack Room Setpoint CH2 (MsgID=23): 0.00
10:16:34.879683 T90181020 Write-Data Room temperature (MsgID=24): 16.12
10:16:35.197738 B50181020 Write-Ack Room temperature (MsgID=24): 16.12
10:16:35.868716 T80800000 Read-Data Message ID 128 (MsgID=128): 0
10:16:36.186671 BE0800000 Data-Inv Message ID 128 (MsgID=128): 0
10:16:36.857655 T10823753 Write-Data Message ID 130 (MsgID=130): 14163
10:16:37.175645 BD0823753 Write-Ack Message ID 130 (MsgID=130): 14163
10:16:38.008849 T00060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:16:38.164496 BC0060707 Read-Ack Remote parameter flags (MsgID=6): 00000111 00000111
10:16:38.886470 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:16:39.153435 B4000010A Read-Ack Status (MsgID=0): 00000001 00001010
10:16:39.875451 T900119E8 Write-Data Control setpoint (MsgID=1): 25.91
10:16:40.142623 B500119E8 Write-Ack Control setpoint (MsgID=1): 25.91
10:16:40.863599 T20080000 Inv-Data Control setpoint 2 (MsgID=8): 0.00
10:16:41.132580 BE0080000 Data-Inv Control setpoint 2 (MsgID=8): 0.00
10:16:41.854437 T10380500 Write-Data DHW setpoint (MsgID=56): 5.00
10:16:42.120386 BD0380500 Write-Ack DHW setpoint (MsgID=56): 5.00
10:16:42.842385 T80200000 Read-Data DHW2 temperature (MsgID=32): 0.00
10:16:43.110381 BE0200000 Data-Inv DHW2 temperature (MsgID=32): 0.00
10:16:43.882572 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
10:16:44.037976 Command (via websocket): GW=0
10:16:44.053524 GW: 0
10:16:44.163521 BC01A1154 Read-Ack DHW temperature (MsgID=26): 17.33
10:16:44.850488 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:16:45.088519 B4000010A Read-Ack Status (MsgID=0): 00000001 00001010
10:16:45.876502 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
10:16:46.141503 BC01B01C4 Read-Ack Outside temperature (MsgID=27): 1.77
10:16:46.829457 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
10:16:47.066485 B40191E84 Read-Ack Boiler water temperature (MsgID=25): 30.52
10:16:47.854486 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
10:16:48.119467 B401C1818 Read-Ack Return water temperature (MsgID=28): 24.09
10:16:48.857463 T801F0000 Read-Data Flow temperature CH2 (MsgID=31): 0.00
10:16:49.109490 BE01F0000 Data-Inv Flow temperature CH2 (MsgID=31): 0.00
10:16:49.846470 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
10:16:50.098414 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
10:16:50.835401 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:16:50.960484 Command (via websocket): GW=R
10:16:52.135567 OpenTherm Gateway 5.0
10:16:52.139137 Command: SC=10:16/3
10:16:52.167387 SC: 10:16/3
10:16:52.814395 T10146A10 Write-Data Day of week and time of day (MsgID=20): Wed 10:16
10:16:53.065381 BD0146A10 Write-Ack Day of week and time of day (MsgID=20): Wed 10:16
10:16:53.853370 T9015011B Write-Data Date (MsgID=21): Jan 27
10:16:54.187394 B5015011B Write-Ack Date (MsgID=21): Jan 27
10:16:54.825350 T101607E5 Write-Data Year (MsgID=22): 2021
10:16:55.177323 BD01607E5 Write-Ack Year (MsgID=22): 2021
10:16:55.814323 T001D0000 Read-Data Solar storage temperature (MsgID=29): 0.00
10:16:56.166331 BF01D0000 Unk-DataId Solar storage temperature (MsgID=29): 0.00
10:16:56.803306 T001E0000 Read-Data Solar collector temperature (MsgID=30): 0.00
10:16:57.155270 B601E0000 Data-Inv Solar collector temperature (MsgID=30): 0.00
10:16:57.843287 T00210000 Read-Data Exhaust temperature (MsgID=33): 0
10:16:58.144277 BC0210018 Read-Ack Exhaust temperature (MsgID=33): 24
10:16:58.832243 T10810200 Write-Data Message ID 129 (MsgID=129): 512
10:16:59.133259 BD0810200 Write-Ack Message ID 129 (MsgID=129): 512
10:16:59.820279 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:17:00.001663 Command: SC=10:17/3
10:17:00.029275 SC: 10:17/3
10:17:00.123425 B4000010A Read-Ack Status (MsgID=0): 00000001 00001010
10:17:00.810276 T90101000 Write-Data Room setpoint (MsgID=16): 16.00
10:17:01.112727 B50101000 Write-Ack Room setpoint (MsgID=16): 16.00
10:17:01.799409 T90170000 Write-Data Room Setpoint CH2 (MsgID=23): 0.00
10:17:02.100256 B50170000 Write-Ack Room Setpoint CH2 (MsgID=23): 0.00
10:17:02.788249 T90181038 Write-Data Room temperature (MsgID=24): 16.22
10:17:03.090323 B50181038 Write-Ack Room temperature (MsgID=24): 16.22
10:17:03.827336 T80800000 Read-Data Message ID 128 (MsgID=128): 0
10:17:04.079189 BE0800000 Data-Inv Message ID 128 (MsgID=128): 0
10:17:04.817167 T10823753 Write-Data Message ID 130 (MsgID=130): 14163
10:17:05.068170 BD0823753 Write-Ack Message ID 130 (MsgID=130): 14163
10:17:05.806173 T900E6400 Write-Data Maximum relative modulation level (MsgID=14): 100.00
10:17:06.057134 B500E6400 Write-Ack Maximum relative modulation level (MsgID=14): 100.00
10:17:06.795129 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:17:07.046095 B4000010A Read-Ack Status (MsgID=0): 00000001 00001010
10:17:07.784139 T100119DC Write-Data Control setpoint (MsgID=1): 25.86
10:17:08.035105 BD00119DC Write-Ack Control setpoint (MsgID=1): 25.86
10:17:08.773083 T20080000 Inv-Data Control setpoint 2 (MsgID=8): 0.00
10:17:09.025062 BE0080000 Data-Inv Control setpoint 2 (MsgID=8): 0.00
10:17:09.813075 T10380500 Write-Data DHW setpoint (MsgID=56): 5.00
10:17:10.078062 BD0380500 Write-Ack DHW setpoint (MsgID=56): 5.00
10:17:10.816116 T80200000 Read-Data DHW2 temperature (MsgID=32): 0.00
10:17:11.067064 BE0200000 Data-Inv DHW2 temperature (MsgID=32): 0.00
10:17:11.805048 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
10:17:12.056100 BC01A1154 Read-Ack DHW temperature (MsgID=26): 17.33
10:17:12.793043 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:17:13.045012 B4000010A Read-Ack Status (MsgID=0): 00000001 00001010
10:17:13.782981 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
10:17:14.034011 BC01B01B0 Read-Ack Outside temperature (MsgID=27): 1.69
10:17:14.772033 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
10:17:15.022978 B40191E84 Read-Ack Boiler water temperature (MsgID=25): 30.52
10:17:15.760943 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
10:17:16.013001 B401C183C Read-Ack Return water temperature (MsgID=28): 24.23
10:17:16.800946 T801F0000 Read-Data Flow temperature CH2 (MsgID=31): 0.00
10:17:17.134944 BE01F0000 Data-Inv Flow temperature CH2 (MsgID=31): 0.00
10:17:17.771968 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
10:17:18.123970 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
10:17:18.760879 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:17:19.113954 B4000010A Read-Ack Status (MsgID=0): 00000001 00001010
10:17:19.750905 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
10:17:20.102890 B70130000 Unk-DataId DHW flow rate (MsgID=19): 0.00
10:17:20.638882 T001D0000 Read-Data Solar storage temperature (MsgID=29): 0.00
10:17:20.893887 BF01D0000 Unk-DataId Solar storage temperature (MsgID=29): 0.00
10:17:21.047932 T01000100 Read-Data Status (MsgID=0): 00000001 00000000
10:17:21.288885 BC110D21B Read-Ack Room setpoint (MsgID=16): -45.89
10:17:21.406869 Error 03
10:17:21.479927 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:21.749852 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:17:21.952867 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:22.278852 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:22.497844 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:22.738844 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:17:22.936856 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:23.267887 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:23.446838 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:23.726822 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:23.892833 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:24.256832 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:24.443862 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:24.716789 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:17:24.863847 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:25.112813 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:17:25.261787 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:25.507837 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:17:25.641774 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:25.903834 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:26.077779 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:26.432825 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:26.693784 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:27.025767 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:27.192765 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:27.485769 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:27.725753 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:28.015914 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:28.170733 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:28.410741 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:28.549732 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:28.806723 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:28.951792 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:29.201738 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:29.400707 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:29.662712 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:17:29.847708 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:30.191847 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:30.528666 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:30.784732 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:17:30.958736 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:31.244705 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:31.440803 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:31.773808 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:17:31.927698 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:32.169669 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:32.364673 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:32.629656 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:17:32.780670 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:33.025649 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:17:33.219650 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:33.553636 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:33.701633 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:33.949626 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:34.121618 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:34.409649 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:34.615599 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:34.938623 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:17:35.090672 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:35.334631 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:17:35.510615 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:35.794599 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:17:35.960625 T02100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:36.323607 BC210001E Read-Ack Room setpoint (MsgID=16): 0.12
10:17:36.533592 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:36.783573 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:36.932584 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:37.179558 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:37.350566 T83100000 Read-Data Room setpoint (MsgID=16): 0.00
10:17:37.708583 BC3101E08 Read-Ack Room setpoint (MsgID=16): 30.03
10:17:37.899562 T811001FF Read-Data Room setpoint (MsgID=16): 2.00
10:17:38.168558 BC1E30404 Read-Ack Message ID 227 (MsgID=227): 1028
10:17:38.340556 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:17:38.697557 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:17:38.852531 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:17:39.093539 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:17:39.322548 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:17:39.686532 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:17:39.885552 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:17:40.146511 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:17:40.299519 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:17:40.542520 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:17:40.777500 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:17:41.071498 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:17:41.214491 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:17:41.466499 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:17:41.602484 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:17:41.862506 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:17:41.996486 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:17:42.258473 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:17:42.408478 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:17:42.653473 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:17:42.807478 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:17:43.049464 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:17:43.189467 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:17:43.444483 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:17:43.610466 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:17:43.905498 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:17:44.107452 T02E30000 Read-Data Message ID 227 (MsgID=227): 0
10:17:44.434447 BC2E30000 Read-Ack Message ID 227 (MsgID=227): 0
10:17:44.608425 T01000200 Read-Data Status (MsgID=0): 00000010 00000000
10:17:44.894445 B4105D20A Read-Ack Application-specific flags (MsgID=5): 11010010 10
10:17:45.066455 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:17:45.423434 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:17:45.603438 T03050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:17:45.883469 BC305B428 Read-Ack Application-specific flags (MsgID=5): 10110100 40
10:17:46.054424 T03050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:17:46.412410 BC305B428 Read-Ack Application-specific flags (MsgID=5): 10110100 40
10:17:46.611398 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:17:46.872421 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:17:47.049413 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:17:47.401405 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:17:47.571389 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:17:47.861416 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:17:48.042382 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:17:48.390384 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:17:48.524369 T03050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:17:48.786364 BC305B428 Read-Ack Application-specific flags (MsgID=5): 10110100 40
10:17:48.956361 T03050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:17:49.246362 BC305B428 Read-Ack Application-specific flags (MsgID=5): 10110100 40
10:17:49.401358 T03050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:17:49.641356 BC305B428 Read-Ack Application-specific flags (MsgID=5): 10110100 40
10:17:49.788334 T03050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:17:50.037344 BC305B428 Read-Ack Application-specific flags (MsgID=5): 10110100 40
10:17:50.219363 T03050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:17:50.566325 BC305B428 Read-Ack Application-specific flags (MsgID=5): 10110100 40
10:17:50.772337 T82050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
10:17:51.026323 B420500A0 Read-Ack Application-specific flags (MsgID=5): 00000000 160
10:17:51.201317 T01050200 Read-Data Application-specific flags (MsgID=5): 00000010 0
10:17:51.555320 B4106D20A Read-Ack Remote parameter flags (MsgID=6): 11010010 00001010
10:17:51.721309 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:52.015391 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:17:52.280318 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:52.545305 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:17:52.659281 Error 03
10:17:52.743327 Error 03
10:17:53.167305 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:53.400292 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:17:53.577276 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:53.929300 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:17:54.113275 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:54.389281 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:17:54.561255 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:54.918278 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:17:55.053255 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:55.314245 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:17:55.448248 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:55.710238 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:17:55.844253 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:56.105230 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:17:56.251276 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:56.501252 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:17:56.697231 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:56.961226 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:17:57.171218 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:57.490219 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:17:57.637199 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:57.886203 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:17:58.067194 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:58.346181 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:17:58.512192 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:58.875193 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:17:59.034164 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:59.270195 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:17:59.444188 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:17:59.730176 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:17:59.894179 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:00.001281 Command: SC=10:18/3
10:18:00.029187 SC: 10:18/3
10:18:00.540774 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:18:00.546546 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:00.719189 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:18:00.884155 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:01.248207 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:18:01.406158 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:01.644159 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:18:01.824184 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:02.105137 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:18:02.295176 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:02.633139 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:18:02.798130 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:03.029128 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:18:03.182107 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:03.425131 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:18:03.581096 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:03.820137 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:18:03.955104 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:04.216139 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:18:04.350089 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:04.612126 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:18:04.775078 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:05.007066 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:18:05.164113 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:05.403073 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:18:05.566064 T03060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:05.799062 B43068C28 Read-Ack Remote parameter flags (MsgID=6): 10001100 00101000
10:18:05.933228 T82060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
10:18:06.194104 B42060028 Read-Ack Remote parameter flags (MsgID=6): 00000000 00101000
10:18:06.932256 T00210000 Read-Data Exhaust temperature (MsgID=33): 0
10:18:07.184125 BC0210018 Read-Ack Exhaust temperature (MsgID=33): 24
10:18:07.921089 T10810200 Write-Data Message ID 129 (MsgID=129): 512
10:18:08.173064 BD0810200 Write-Ack Message ID 129 (MsgID=129): 512
10:18:08.960074 T80000100 Read-Data Status (MsgID=0): 00000001 00000000
10:18:09.226024 B4000010A Read-Ack Status (MsgID=0): 00000001 00001010
10:18:09.913001 T90101000 Write-Data Room setpoint (MsgID=16): 16.00
10:18:10.151004 B50101000 Write-Ack Room setpoint (MsgID=16): 16.00
Re: QAA73.110 showing incorrect values when otgw connected
Whoa. That disregards the Opentherm spec in multiple ways:
I notice some Error 03 reports while the QAA73 is in programming mode. Maybe there is some additional communication outside of the OT messages going on. It may also just be that the devices are tripped up by the delay introduced by the OTGW in gateway mode. During QAA73 programming mode the message frequency increases dramatically. So maybe the thermostat feels it doesn't get the responses in time.
Very strange. But interesting to see how manufacturers manage to abuse a standard protocol, while there are 128 messages available they could have used without violating the specs. Thanks for sharing.
- The thermostat starts sending message where the spare bits are not all set to 0, as they should be.
- The boiler responds with a different MessageID than requested. This is not explicitly forbidden by the spec, but it is implied that the MessageIDs should be the same.
- The thermostat sends Read-Data requests for MsgIDs 7 and 16, which are defined as Write-Data only messages.
I notice some Error 03 reports while the QAA73 is in programming mode. Maybe there is some additional communication outside of the OT messages going on. It may also just be that the devices are tripped up by the delay introduced by the OTGW in gateway mode. During QAA73 programming mode the message frequency increases dramatically. So maybe the thermostat feels it doesn't get the responses in time.
Very strange. But interesting to see how manufacturers manage to abuse a standard protocol, while there are 128 messages available they could have used without violating the specs. Thanks for sharing.
Schelte