MPC is not an error code. The letters represent the settings for LEDs D,E, and F. You get this output because the result of the subroutine to parse a floating point number is incorrectly interpreted as a pointer to an error code in EEPROM. Because you used
9.999, you get the data at offset 9. If you try 4.999, you get all LEDs: "L=FXOMPC". And 15.999 returns "A=OpenTherm Gateway 5.0". Needless to say, this is another bug.
I've created a test for both of your findings in the test suite. So they will be verified before I release a new firmware version in the future. I've also added a test for OT=-0.004, which should round up to 0.00. At least that one already works correctly.
It looks like you are stress-testing the firmware. Do let me know if you find more bugs.