New setup - no statistics showing
andyroo
Post by andyroo »
I'm hoping someone can help or point me to where I'm going wrong or need to look?
I've just installed an OTGW between my Drayton Wiser Thermostat and a Baxi Platinum 40 boiler, the goal was to set a maximum flow temperature which I couldn't when connected directly.
The OTGW is passing OT commands to the boiler as before so everything is working as normal, but I see no statistic data in Opentherm Monitor or the web interface and my log just looks like this over and over again:
\f0\fs24 \cf0 11:55:20.583443  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
                               - Fault indication: no fault (0)\
                               - CH mode: not active (0)\
                               - DHW mode: not active (0)\
                               - Flame status: flame off (0)\
                               - Cooling status: not active (0)\
                               - CH2 mode: not active (0)\
                               - Diagnostic indication: no diagnostics (0)\
                               - Electricity production: not active (0)\
11:55:20.718721  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
                               - CH enable: disabled (0)\
                               - DHW enable: enabled (1)\
                               - Cooling enable: disabled (0)\
                               - OTC active: not active (0)\
                               - CH2 enable: disabled (0)\
                               - Summer/winter mode: winter (0)\
                               - DHW blocking: unblocked (0)\
11:55:21.212509  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:21.756459  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:22.164367  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:22.283157  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:22.765229  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:23.330613  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:23.756636  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:23.852319  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:24.156390  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:24.337617  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:24.748482  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:24.882564  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:25.363023  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:25.911124  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:26.336727  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:26.472103  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:26.735880  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:26.936350  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:27.811638  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:27.844113  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:27.959214  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:28.502650  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:29.012817  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:29.056362  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:29.524655  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:30.072170  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:30.535219  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:30.616699  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:30.910178  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:31.102483  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:31.502981  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:31.641543  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:32.122393  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:32.677118  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:33.093858  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:33.209250  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:33.490575  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:33.716614  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:34.091817  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:34.232919  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:34.694230  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:34.777843  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:35.264938  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:35.688893  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:35.815460  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:36.347743  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:36.830335  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:37.270415  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:37.375690  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:37.674266  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:37.851514  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:38.260848  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:38.396524  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:39.022858  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:39.424205  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:39.858900  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:39.968375  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:40.259515  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:40.457075  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:40.861017  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:41.042675  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:41.448380  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:41.584166  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:42.068512  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:42.616979  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:43.032462  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:43.154895  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:43.650231  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:44.253844  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:44.802561  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:44.844235  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:45.022152  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:45.208268  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:45.620926  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:45.769684  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:46.234387  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:46.777228  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:47.217231  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:47.345830  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:47.915893  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:47.946361  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:48.489143  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:48.522822  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:48.983240  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:49.370531  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:49.791039  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:49.918616  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:50.404466  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:50.943282  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:51.385997  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:51.491148  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:51.780184  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:51.969467  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
11:55:52.377959  B40000200  Read-Ack    Status (MsgID=0): 00000010 00000000\
11:55:53.837568  T80000200  Read-Data   Status (MsgID=0): 00000010 00000000\
I do see a correct 'flame' status when the boiler is fired up but that's it.
Update: The data does populate and is picked up when in 'Monitor' mode. But not in Gateway mode.
I have seen a previous post where someone had this problem and was resolved by an older experimental firmware, however as I'm on v6.5 I assumed I'm on the most recent update so didn't think it was trying that?
Any ideas where I'm going wrong? I'm sure it'll be me :-)
Huge thanks in advance,
Andrew
Re: New setup - no statistics showing
A thermostat repeating the same request over and over is usually a sign that it didn't receive a response, or didn't understand the response it received.
The timings in your log show that the thermostat is quite impatient. On average it only waits around half a second for an answer. Sometimes it already repeats its request after as little as 115ms. According to the specs, up to 800ms is acceptable for a response to be returned to the master device.
My first thought was that the thermostat interface might not produce correct signal levels for the thermostat. But if it works in monitor mode, that cannot be the reason. A difference between monitor mode and gateway mode is that in gateway mode a bit of delay is introduced; 32ms in each direction. So from the point of view of the thermostat, that adds up to 64ms. With such an impatient thermostat, that may be too much.
Another possibility could be that the thermostat looks for additional signals, not just Opentherm. In monitor mode, such signals are passed on. In gateway mode they are filtered out. Finally, the thermostat may not like the bit timings of the OTGW, although they are actually very accurate. You can test these last two hypotheses using the diagnostic firmware. Test #3 will report the signals the boiler sends.
I couldn't find much information on the Wiser thermostat, but I get the impression that it is a wireless thermostat that connects to a powered hub. Some thermostats will find out on startup which communication method they can use. The hub may have seen some other protocol from the boiler. And if you didn't power down the hub when you inserted the OTGW in the communication path, it may still be looking for those signals. You can try to power down the hub for a while, and make sure the OTGW is in gateway mode when you power up the hub again.
andyroo
Post by andyroo »
Really interesting, and you're right about the Wiser thermostat. It's wireless with smart TRVs around the house, it just fails to allow me to set an upper temp limit for CH so I'm getting 80degrees on a 40kW boiler which is no good for anyone's gas bill.
I'm hoping the following bits of info help work out what could be going on. I've switched back to Monitor mode to gather some logging and it is as follows when in Monitor mode.
09:05:30.012329  B401A2580  Read-Ack    DHW temperature: 37.50
09:05:30.238237  T80200000  Read-Data   DHW2 temperature: 0.00
09:05:30.605709  B70200000  Unk-DataId  DHW2 temperature: 0.00
09:05:30.756569  T801C0000  Read-Data   Return water temperature: 0.00
09:05:31.009450  B701C0000  Unk-DataId  Return water temperature: 0.00
09:05:31.239011  T80380000  Read-Data   DHW setpoint: 0.00
09:05:31.601173  B40380000  Read-Ack    DHW setpoint: 0.00
09:05:31.744556  T80130000  Read-Data   DHW flow rate: 0.00
09:05:32.000641  B70130000  Unk-DataId  DHW flow rate: 0.00
09:05:32.226511  T00110000  Read-Data   Relative modulation level: 0.00
09:05:32.600429  BC0110000  Read-Ack    Relative modulation level: 0.00
09:05:32.739383  T00210000  Read-Data   Exhaust temperature: 0
09:05:32.998425  B40210015  Read-Ack    Exhaust temperature: 21
09:05:33.220498  T00220000  Read-Data   Boiler heat exchanger temperature: 0.00
09:05:33.595483  BF0220000  Unk-DataId  Boiler heat exchanger temperature: 0.00
09:05:33.736694  T10181000  Write-Data  Room temperature: 16.00
09:05:33.988282  BF0180000  Unk-DataId  Room temperature: 0.00
09:05:34.216128  T90100F80  Write-Data  Room setpoint: 15.50
09:05:34.583822  B70100000  Unk-DataId  Room setpoint: 0.00
09:05:34.732409  T00390000  Read-Data   Max CH water setpoint: 0.00
09:05:34.980210  BC0395000  Read-Ack    Max CH water setpoint: 80.00
09:05:35.215110  T80000200  Read-Data   Status: 00000010 00000000
09:05:35.459871  PR: I=11
09:05:35.580147  B40000200  Read-Ack    Status: 00000010 00000000
09:05:35.724726  T90012300  Write-Data  Control setpoint: 35.00
09:05:35.977018  B50012300  Write-Ack   Control setpoint: 35.00
09:05:36.203292  T80190000  Read-Data   Boiler water temperature: 0.00
09:05:36.569333  BC0193080  Read-Ack    Boiler water temperature: 48.50
09:05:36.716867  T801F0000  Read-Data   Flow temperature CH2: 0.00
09:05:36.974242  B701F0000  Unk-DataId  Flow temperature CH2: 0.00
09:05:37.198449  T00120000  Read-Data   CH water pressure: 0.00
09:05:37.569549  BF0120000  Unk-DataId  CH water pressure: 0.00
09:05:37.707530  T801A0000  Read-Data   DHW temperature: 0.00
09:05:37.969444  B401A2580  Read-Ack    DHW temperature: 37.50
09:05:38.188044  T80200000  Read-Data   DHW2 temperature: 0.00
09:05:38.563195  B70200000  Unk-DataId  DHW2 temperature: 0.00
09:05:38.711800  T801C0000  Read-Data   Return water temperature: 0.00
09:05:38.960754  B701C0000  Unk-DataId  Return water temperature: 0.00
09:05:39.185035  T80380000  Read-Data   DHW setpoint: 0.00
09:05:39.559890  B40380000  Read-Ack    DHW setpoint: 0.00
09:05:39.698003  T80130000  Read-Data   DHW flow rate: 0.00
09:05:39.955526  B70130000  Unk-DataId  DHW flow rate: 0.00
09:05:40.178223  T00110000  Read-Data   Relative modulation level: 0.00
09:05:40.548060  BC0110000  Read-Ack    Relative modulation level: 0.00
09:05:40.693379  T00210000  Read-Data   Exhaust temperature: 0
09:05:40.947547  B40210015  Read-Ack    Exhaust temperature: 21
09:05:41.169990  T00220000  Read-Data   Boiler heat exchanger temperature: 0.00
09:05:41.545063  BF0220000  Unk-DataId  Boiler heat exchanger temperature: 0.00
09:05:41.691253  T10181000  Write-Data  Room temperature: 16.00
09:05:41.952327  BF0180000  Unk-DataId  Room temperature: 0.00
09:05:42.163905  T90100F80  Write-Data  Room setpoint: 15.50
09:05:42.541560  B70100000  Unk-DataId  Room setpoint: 0.00
09:05:42.682152  T00390000  Read-Data   Max CH water setpoint: 0.00
09:05:42.932641  BC0395000  Read-Ack    Max CH water setpoint: 80.00
09:05:43.159630  T80000200  Read-Data   Status: 00000010 00000000
When then running diagnostics in Monitor mode I get the following:
Opentherm gateway diagnostics - Version 2.1
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 2
485,513,487,1014,487,513,487,513,487,513,487,513,487,514,488,511,488,513,487,513,987,1013,487,513,487,513,487,513,487,513,487,513,487,513,486,514,487,512,487,513,487,513,487,513,487,513,487,513,487,513,487,514,486,513,487,513,487,513,487,513,487,513,987.
484,513,487,1013,486,513,487,513,487,512,487,513,487,513,487,513,487,512,488,512,487,513,986,513,487,513,487,1012,487,513,487,513,486,514,487,512,487,513,487,512,487,513,487,513,486,513,487,513,487,513,486,513,487,514,486,513,487,513,487,512,487,513,987.
485,513,486,1013,487,514,486,513,486,513,487,513,487,512,487,513,487,513,487,513,987,513,486,513,488,1012,487,512,487,513,487,513,487,512,487,513,487,513,487,513,486,514,486,514,487,513,486,513,487,513,487,512,487,514,487,512,487,513,487,513,487,513,987.
484,513,487,1013,486,513,487,514,487,512,487,512,487,513,487,513,487,513,486,513,487,513,987,1013,486,514,987,512,487,1013,487,512,487,513,487,513,487,513,487,513,487,513,487,513,487,512,487,513,487,513,487,513,486,514,486,513,487,513,487,513,987.
485,1013,486,513,487,513,487,513,487,513,486,513,487,513,487,513,487,514,486,513,487,512,987,1013,487,513,487,513,987,1012,487,513,487,513,488,511,487,513,487,513,487,512,487,513,487,513,487,512,487,513,487,513,487,513,487,512,487,513,487,513,987.
486,1012,487,513,487,513,487,512,488,513,488,511,487,513,487,513,486,513,487,513,987,1012,487,513,487,513,487,513,986,1013,487,513,486,513,487,513,487,512,487,513,487,513,486,513,487,513,487,513,487,512,487,513,487,513,486,513,487,513,487,513,987.
485,1013,487,512,487,513,487,513,487,513,488,512,486,513,487,513,487,513,487,513,987,1013,487,512,487,513,988,1012,487,513,487,513,487,513,487,513,487,513,486,513,487,513,487,513,487,513,488,512,487,513,486,513,487,513,487,513,487,513,487,513,987.
485,1013,487,513,487,512,987,1013,487,514,486,513,487,512,487,513,487,513,487,513,987,513,486,1013,487,513,487,514,486,512,488,512,487,513,987,1013,487,512,487,513,487,513,487,513,487,513,987,513,487,1012,487,513,986,513,487,513,487.
10181033  Write-Data  Room temperature: 16.20
485,513,486,1014,486,513,987,1012,487,513,487,513,487,513,486,513,487,514,487,512,987,1013,487,513,487,512,487,513,487,513,487,513,487,513,487,513,988,512,486,513,487,513,487,513,487,1013,486,514,486,513,487,513,487,513,487,514,486,513,987.
485,1012,487,514,487,512,487,513,487,513,487,513,487,513,487,513,487,513,487,513,987,513,488,512,488,1014,486,512,988,1013,487,513,487,513,487,513,487,513,487,513,487,514,487,512,487,513,487,513,487,513,487,513,487,513,487,513,487,514,486,514,988.
485,513,487,1013,487,512,488,513,486,513,487,513,487,514,486,513,487,513,487,513,487,513,487,513,487,512,487,513,487,513,488,512,487,514,486,513,487,513,486,513,487,513,487,512,987,1013,487,513,486,513,487,514,486,513,488,512,487,513,487,513,487,513,986.
Enter test number: PPS=0
Invalid test
1. LED test
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 3
535,977,1015,499,510,499,510,1003,512,497,512,497,512,498,511,497,511,498,1028,992,511,497,511,499,510,498,512,498,511,498,512,498,511,498,511,498,511,498,511,499,512,497,512,498,511,499,511,497,512,502,507,498,512,498,512,497,512,497,511,504,1011.
502,1004,1015,498,512,497,511,1003,512,498,511,498,512,498,511,498,511,499,511,498,1015,499,511,498,512,1002,511,499,510,499,549,460,511,498,512,497,511,498,512,527,482,498,511,519,490,498,512,498,511,498,511,498,512,498,510,499,511,498,511,499,1015.
512,1000,1015,1003,510,499,510,499,511,497,511,499,511,498,511,498,511,497,1016,499,510,498,511,1004,510,498,511,498,510,499,528,481,510,498,511,499,511,498,510,499,510,498,512,500,508,498,511,499,510,499,510,498,511,498,513,497,510,499,511,498,1015.
503,1002,1016,498,512,497,512,1002,511,498,512,497,512,498,511,498,511,497,512,499,1014,1004,510,498,1016,498,511,1002,549,461,511,498,510,499,510,498,512,517,492,498,511,527,482,499,509,499,511,498,510,499,510,499,510,498,511,499,510,498,1020.
510,498,511,499,511,1002,511,498,511,498,513,497,510,499,511,498,510,499,511,497,512,535,979,1003,511,497,511,499,1015,1003,511,498,511,498,516,493,510,500,510,498,511,499,525,483,511,498,511,498,511,499,510,498,512,497,511,498,511,498,523,486,1015.
510,1002,1015,1002,512,498,511,497,512,497,511,499,511,497,512,497,511,498,1016,1003,509,499,510,498,511,499,1016,1002,561,447,511,498,512,497,510,499,511,500,509,497,511,498,511,499,511,497,511,498,1015,1003,1015,1002,1016,497,530.
518,489,512,498,511,498,510,499,511,1002,511,498,511,499,511,498,510,499,511,497,1027,992,511,498,511,498,1015,1010,505,498,511,498,511,498,510,499,511,498,511,497,512,498,512,497,512,497,512,498,510,502,508,498,510,499,510,498,511,499,511,502,1011.
522,486,512,497,513,497,510,498,512,1002,512,498,512,497,512,496,511,498,511,499,511,498,1015,499,510,1003,511,498,511,499,511,498,522,486,511,498,512,497,511,498,514,497,510,499,510,499,510,499,511,497,512,498,512,497,511,498,511,498,511,498,511,498,1016.
554,958,1016,1002,512,497,511,499,510,499,511,498,511,498,510,499,511,497,512,536,473,499,509,499,511,498,511,498,511,499,511,498,510,499,511,499,510,503,505,500,509,501,1013,1004,510,499,511,497,511,499,511,498,511,499,510,498,511,498,516,494,1015.
519,489,512,503,507,496,512,497,511,1004,511,498,510,498,511,498,511,498,512,498,511,497,1016,497,512,1003,511,497,511,498,512,498,534,475,510,499,510,498,511,499,511,503,506,502,507,521,487,499,511,498,511,498,511,499,510,498,510,499,510,499,511,498,1015.
517,988,1015,499,510,499,511,1002,511,498,511,499,511,498,511,498,511,498,511,498,1016,1002,512,497,512,499,510,498,512,498,534,474,511,498,511,499,511,503,506,503,506,498,511,513,497,498,511,498,511,499,510,498,512,498,512,497,511,499,510,498,1016.
511,541,482,484,510,1004,510,499,510,499,511,498,511,498,516,493,512,497,511,498,1017,496,512,498,511,1002,512,497,1016,1002,1016,1002,1015,1004,512,504,503,498,512,498,510,498,512,497,511,498,511,499,510,503,506,499,510,499,510,498,1016.
541,973,1015,1003,511,498,511,498,512,497,512,498,511,499,511,497,511,498,511,555,455,497,512,498,511,498,511,497,512,498,511,498,511,498,511,498,511,498,515,494,511,500,1014,1003,511,499,510,499,510,499,511,498,510,498,511,499,511,499,510,498,1016.
524,990,1020,998,1016,1001,512,498,511,498,511,498,511,499,510,498,511,499,510,498,512,498,511,498,512,497,1016,1003,535,475,1014,1003,511,498,512,505,1008,503,523,987,510,500,511,498,510,498,511,498,511,499,510,499,510,498,1017.
532,538,449,498,511,1004,510,499,510,498,511,498,512,498,511,497,512,498,512,497,511,498,1016,499,510,1003,511,498,1015,1003,535,474,1016,1002,1017,504,507,1001,510,509,500,499,511,497,512,498,512,497,511,498,512,498,510,499,510,499,1016.
C0192C00  Read-Ack    Boiler water temperature: 44.00
525,988,1016,497,512,498,511,1002,512,497,511,498,511,499,511,498,510,498,511,499,1015,498,516,493,511,498,511,499,511,1002,535,475,511,497,512,497,512,498,511,510,499,499,511,512,496,498,511,499,511,498,512,497,511,499,510,498,511,498,511,498,1016.
511,498,511,516,493,498,511,498,511,1003,511,498,511,497,512,498,510,498,512,497,512,498,1015,1004,510,498,1015,1008,506,498,511,498,511,499,511,498,510,498,512,498,511,499,513,496,510,498,512,497,512,497,511,498,512,497,512,497,511,499,510,499,1015.
503,1001,1017,1002,511,498,511,498,511,498,511,498,512,497,512,498,511,498,512,497,1016,499,510,1003,1016,1002,511,498,548,461,1016,1003,511,498,511,518,996,1029,484,498,512,498,512,497,511,499,510,498,511,499,510,499,511,498,1015.
401A2200  Read-Ack    DHW temperature: 34.00
510,1009,1018,490,511,498,512,1002,511,498,511,499,561,448,511,498,511,498,1016,1003,511,498,512,497,511,498,512,499,511,497,512,497,511,499,511,498,511,499,511,514,495,498,511,498,526,484,512,497,512,497,512,498,511,498,511,499,535,473,513,497,1016.
517,996,1016,497,512,498,511,1003,511,498,511,498,511,498,511,498,511,499,511,497,1016,498,512,498,511,1003,511,498,512,497,511,498,516,493,512,498,511,498,512,499,510,498,515,495,510,498,511,498,511,498,511,499,511,498,511,498,511,498,511,499,1015.
509,1002,1016,1002,511,497,511,499,511,499,510,498,511,498,511,498,511,498,1015,498,511,499,512,1001,511,498,511,498,511,498,523,487,511,497,512,497,512,499,509,498,511,499,510,498,511,498,511,498,511,498,511,498,511,499,510,498,511,499,510,499,1015.
503,1002,1015,498,511,498,511,1003,513,496,512,498,511,498,511,498,511,499,511,498,1015,1003,511,498,1016,498,512,1002,556,453,512,498,511,498,511,498,512,516,493,498,511,522,487,500,510,499,510,499,511,498,511,498,511,498,511,499,511,498,1016.
1. LED test
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 5
Power supply: 3.287
Reference: 1.508
Thermostat: 0.760, 2.118
Boiler: 0.000, 2.593
Reference voltage setting (0..9) [5]:
1. LED test
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 6
T: 111.318
B: 221.393
T: 193.725
B: 338.191
T: 111.381
B: 221.846
T: 193.898
B: 337.922
T: 111.574
B: 221.629
T: 193.918
And then when I put the OTGW back into gateway mode and run the diagnostics again I get the following which is slightly different:
1. LED test
4. Delay symmetry
5. Voltage levels
6. Idle times
484,513,487,1013,488,513,486,513,487,513,487,513,487,513,487,513,487,513,487,513,486,514,486,514,487,513,486,514,486,513,487,513,487,513,487,513,487,513,487,513,487,512,487,514,987,1012,487,513,487,513,487,513,487,513,487,513,487,513,487,513,486,514,987.
484,514,486,1013,487,513,486,513,487,513,487,513,487,513,487,512,488,513,486,513,487,513,487,513,487,512,488,512,487,515,487,512,487,513,487,511,487,515,486,512,486,513,487,513,987,1012,487,512,487,513,487,513,487,514,485,513,487,513,486,513,487,513,987.
484,513,487,1013,487,512,487,513,487,513,487,512,487,514,487,512,487,513,487,512,487,513,487,513,487,512,487,513,487,513,487,513,487,513,487,513,487,512,487,513,487,513,487,513,987,1012,487,513,487,513,487,513,487,512,488,512,487,513,487,513,486,513,987.
485,512,488,1013,486,513,487,513,486,513,487,513,487,513,487,513,487,513,486,513,487,513,487,513,486,513,487,513,487,513,487,513,487,513,487,513,487,513,486,513,487,513,487,513,987,1012,487,513,487,513,487,513,487,513,487,513,486,513,487,513,487,513,987.
485,513,486,1014,487,512,487,513,487,512,489,513,485,513,487,513,486,514,486,513,489,510,488,513,486,512,487,513,487,513,486,513,487,513,487,512,487,514,486,513,486,513,487,513,988,1011,487,512,487,513,488,512,486,513,487,513,487,512,487,513,486,514,987.
485,514,486,1014,487,512,486,513,487,513,487,513,487,513,486,513,487,513,487,513,487,512,487,514,486,513,487,513,486,514,486,513,487,513,487,513,486,513,487,513,487,513,487,513,987,1012,487,513,487,513,487,513,487,512,487,513,487,513,487,513,486,514,986.
484,513,487,1012,488,513,486,513,486,513,487,513,487,513,487,512,487,513,487,513,487,513,486,513,488,513,486,513,487,513,487,513,487,512,489,512,486,513,487,513,486,513,487,513,987,1014,485,513,487,513,487,513,486,513,487,513,487,513,487,513,487,513,987.
485,513,488,1013,487,513,487,513,487,513,487,513,487,513,488,512,487,513,487,513,487,513,487,513,487,513,487,513,487,513,487,513,487,513,487,513,488,512,487,514,486,514,486,514,987,1013,487,513,487,513,487,514,487,512,487,513,487,514,486,513,487,514,987.
486,512,487,1013,487,513,486,513,487,513,487,513,487,512,487,514,487,512,487,513,487,513,486,513,487,513,487,513,487,512,487,513,487,513,486,514,487,512,487,513,486,513,487,513,987,1012,487,513,487,512,487,513,487,514,486,513,486,513,487,513,487,512,987.
484,513,487,1013,487,513,486,513,487,513,487,513,486,513,487,513,487,514,485,514,486,513,487,513,486,513,487,513,487,513,486,513,487,513,486,513,488,513,486,513,486,513,487,513,986,1013,487,513,486,513,487,513,486,513,488,512,487,513,486,513,487,513,986.
485,513,487,1013,487,513,488,512,487,512,487,513,487,513,487,513,487,513,487,513,487,513,487,513,487,514,487,512,487,512,487,513,487,513,487,513,487,513,487,512,487,513,487,513
1. LED test
4. Delay symmetry
5. Voltage levels
6. Idle times
530,983,1017,1002,512,499,510,498,512,497,512,498,513,497,511,499,511,498,511,536,473,499,511,499,511,498,512,497,512,498,511,499,510,504,506,499,511,498,511,498,511,500,1015,1002,511,499,511,498,512,498,511,499,510,499,511,498,511,499,523,487,1016.
511,1003,1015,1002,512,497,512,498,512,498,511,499,516,492,512,499,509,499,511,536,473,499,511,498,511,499,510,499,511,498,511,499,510,499,511,498,511,499,511,498,511,498,1016,1003,511,498,511,498,511,499,510,499,511,503,506,498,511,498,519,491,1016.
558,955,1016,1003,511,499,510,498,517,492,512,498,512,498,511,498,512,497,511,535,474,498,512,498,511,498,512,498,511,498,511,498,512,497,512,498,511,498,511,498,511,499,1015,1004,510,498,511,499,510,504,506,498,511,499,510,499,510,498,516,494,1015.
536,976,1016,1002,512,498,511,498,511,498,512,497,513,497,510,499,512,497,511,548,462,497,511,499,511,497,513,497,511,498,512,497,511,499,511,498,511,499,515,493,512,499,1015,1004,510,499,510,499,511,498,511,498,511,498,511,498,511,507,503,498,1016.
511,1003,1016,1003,511,498,512,498,511,499,510,498,512,498,511,499,511,499,510,536,474,498,510,499,512,497,516,494,511,498,511,499,511,498,512,498,512,497,511,498,511,499,1016,1003,511,499,511,498,511,498,511,499,511,498,511,498,512,499,518,490,1017.
546,968,1015,1003,512,502,507,498,511,497,512,498,511,499,510,499,512,497,512,541,468,498,511,498,512,497,512,498,511,498,511,499,511,499,510,499,511,498,511,498,511,499,1016,1002,511,499,516,493,511,498,511,499,511,499,510,499,511,499,518,491,1016.
535,979,1016,1002,511,498,513,497,512,497,512,498,511,498,512,498,511,498,511,498,512,497,512,498,512,498,512,497,511,499,512,497,512,498,511,498,511,498,529,481,511,498,1016,1003,511,498,512,498,511,498,510,499,511,499,511,498,511,512,498,498,1016.
546,968,1016,1003,510,499,511,498,511,498,511,499,511,498,511,498,511,498,512,535,475,497,511,503,506,499,510,499,511,498,511,498,512,498,511,499,510,498,511,499,511,499,1015,1004,510,498,511,499,510,500,511,497,512,498,511,498,511,498,516,494,1016.
550,963,1017,1002,511,498,511,498,512,498,511,498,512,498,511,498,511,499,511,556,453,498,512,498,511,499,512,497,512,497,512,498,511,498,511,499,511,498,515,494,511,499,1015,1005,510,498,512,497,511,499,511,499,511,498,511,498,511,501,510,498,1015.
523,991,1016,1003,511,499,510,498,512,497,512,498,512,497,512,498,512,497,511,535,474,498,512,497,512,498,512,497,512,497,512,498,511,498,512,499,510,499,511,498,510,508,1007,1002,512,497,512,498,511,498,511,498,512,498,511,498,511,498,516,493,1016.
1. LED test
4. Delay symmetry
5. Voltage levels
6. Idle times
Power supply: 3.287
Reference: 1.505
Thermostat: 0.760, 2.121
1. LED test
4. Delay symmetry
5. Voltage levels
6. Idle times
B: 373.169
T: 127.586
B: 404.483
T: 75.772
T: 448.462
B: 373.383
T: 127.314
B: 404.631
T: 75.478
T: 448.485
I'm hoping that all means more to you than me. It definitely seems like in Gateway mode there's that ping pong of empty status updates flying back and forth and that then goes away in Monitor mode. How to resolve it though is beyond me, but I'm more than happy to try any tests you can think of.
Really appreciate your time and help on this.
Switching between gateway- and monitor mode is a feature only the gateway firmware provides. The diagnostic firmware always just passes on messages between the thermostat and boiler (like monitor mode), when a thermostat is connected. Unless we have a different idea about switching the OTGW into gateway mode, you must have received a "Invalid test" response when you issued the GW=1 command.
So it seems your hub sometimes just ends up in this state where it keeps requesting the status message over and over. It doesn't exclusively happen in gateway mode. Then I would again suggest to power down the hub, wait a while, and power it up again. Try this a couple of times with the OTGW in gateway mode and in monitor mode to see if there is some pattern you can recognize.